Navigation

    Logo
    • Register
    • Login
    • Search
    • Recent
    • Tags
    • Unread
    • Categories
    • Unreplied
    • Popular
    • GitHub
    • Docu
    • Hilfe
    1. Home
    2. Deutsch
    3. ioBroker Allgemein
    4. Probleme mit modbus Stromzähler, keine Werte

    NEWS

    • Neues Video "KI im Smart Home" - ioBroker plus n8n

    • Neues Video über Aliase, virtuelle Geräte und Kategorien

    • Wir empfehlen: Node.js 22.x

    Probleme mit modbus Stromzähler, keine Werte

    This topic has been deleted. Only users with topic management privileges can see it.
    • bahnuhr
      bahnuhr Forum Testing Most Active @obstbauer last edited by

      @obstbauer

      Das ist wieder mbus.1

      Ich denke modbus klappt nicht

      O 1 Reply Last reply Reply Quote 0
      • Homoran
        Homoran Global Moderator Administrators @obstbauer last edited by

        @obstbauer Danke!
        aber nur mbus Meldungen

        hast du vielleicht auf mbus gefiltert?

        wurde die modbus Instanz neu gestartet?
        das muss im log zu sehen sein.

        1 Reply Last reply Reply Quote 0
        • O
          obstbauer @bahnuhr last edited by

          @bahnuhr ja sorry ich arbeite daran
          weiß gerade nicht wie ich modbus auf debug schalte, das ist das was mir bei Protokolle angezeigt wird, da taucht nur mbus auf, entschuldigung für die Verwirrung

          Homoran bahnuhr 2 Replies Last reply Reply Quote 0
          • Homoran
            Homoran Global Moderator Administrators @obstbauer last edited by Homoran

            @obstbauer sagte in Probleme mit modbus Stromzähler, keine Werte:

            weiß gerade nicht wie ich modbus auf debug schalte

            hab dir doch was zum lesen verlinkt
            https://forum.iobroker.net/topic/51555/hinweise-für-gute-forenbeiträge/1

            1 Reply Last reply Reply Quote 0
            • bahnuhr
              bahnuhr Forum Testing Most Active @obstbauer last edited by

              @obstbauer
              e2b15c67-f2d7-4aa4-b9ae-106867e6c76f-image.png
              Dort auf debug stellen.

              Und dann instanz neu starten.
              Und dann log hier als code-tag posten.

              1 Reply Last reply Reply Quote 0
              • O
                obstbauer last edited by

                so ich denke jetzt habe ichs, sorry....

                2023-06-30 21:13:47.306 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:47.362 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:47.413 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
                2023-06-30 21:13:47.414 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:47.468 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:48.519 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
                2023-06-30 21:13:48.521 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:48.582 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:48.635 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
                2023-06-30 21:13:48.636 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:48.693 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:49.746 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
                2023-06-30 21:13:49.747 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:49.802 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:49.857 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
                2023-06-30 21:13:49.858 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:49.913 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:50.966 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
                2023-06-30 21:13:50.967 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:51.022 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:51.073 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
                2023-06-30 21:13:51.074 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:51.128 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:52.181 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
                2023-06-30 21:13:52.181 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:52.237 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:52.288 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
                2023-06-30 21:13:52.288 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:52.343 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:53.395 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
                2023-06-30 21:13:53.396 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:53.452 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:53.503 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
                2023-06-30 21:13:53.504 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:53.558 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:54.609 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
                2023-06-30 21:13:54.610 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:54.667 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:54.718 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
                2023-06-30 21:13:54.718 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:54.773 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:55.825 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
                2023-06-30 21:13:55.825 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:55.882 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
                2023-06-30 21:13:55.933 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
                2023-06-30 21:13:55.935 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
                2023-06-30 21:13:55.993 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
                
                bahnuhr Homoran 2 Replies Last reply Reply Quote 0
                • bahnuhr
                  bahnuhr Forum Testing Most Active @obstbauer last edited by

                  @obstbauer
                  So, da steht doch überall done.

                  Also scheint es doch zu klappen.

                  Also nochmal die Frage:
                  Was klappt jetzt nicht bei modbus ?

                  O 1 Reply Last reply Reply Quote 0
                  • O
                    obstbauer last edited by

                    hier noch mit dem Neustart

                    
                    modbus.0
                    2023-06-30 21:17:13.084	debug	[DevID_1/inputRegs] Poll address 30256 DONE
                    
                    modbus.0
                    2023-06-30 21:17:13.026	debug	[DevID_1/inputRegs] Poll address 30256 - 2 registers
                    
                    modbus.0
                    2023-06-30 21:17:13.026	debug	[DevID_1] Poll start ---------------------
                    
                    modbus.0
                    2023-06-30 21:17:11.972	debug	[DevID_2/inputRegs] Poll address 30256 DONE
                    
                    modbus.0
                    2023-06-30 21:17:11.912	debug	[DevID_2/inputRegs] Poll address 30256 - 2 registers
                    
                    modbus.0
                    2023-06-30 21:17:11.912	debug	Initialization of scale factors done!
                    
                    modbus.0
                    2023-06-30 21:17:11.911	debug	[DevID_2] Poll start ---------------------
                    
                    modbus.0
                    2023-06-30 21:17:11.857	debug	[DevID_1/inputRegs] Poll address 30256 DONE
                    
                    modbus.0
                    2023-06-30 21:17:11.786	debug	[DevID_1/inputRegs] Poll address 30256 - 2 registers
                    
                    modbus.0
                    2023-06-30 21:17:11.785	debug	Initialization of scale factors done!
                    
                    modbus.0
                    2023-06-30 21:17:11.783	debug	[DevID_1] Poll start ---------------------
                    
                    modbus.0
                    2023-06-30 21:17:11.782	info	Connected to slave
                    
                    modbus.0
                    2023-06-30 21:17:11.774	debug	connect to serial /dev/ttyACM0 with 9600
                    
                    modbus.0
                    2023-06-30 21:17:11.416	debug	Remove old object modbus.0.inputRegisters.2.30100_Spannung
                    
                    modbus.0
                    2023-06-30 21:17:11.415	debug	Remove old object modbus.0.inputRegisters.1.30100_Spannung
                    
                    modbus.0
                    2023-06-30 21:17:11.314	debug	Initialize Objects for holdingRegs: []
                    
                    modbus.0
                    2023-06-30 21:17:11.312	debug	Add inputRegisters.2.30256_Spannung: {"_id":"inputRegisters.2.30256_Spannung","type":"state","common":{"name":"Spannung","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"V"},"native":{"regType":"inputRegs","address":30256,"deviceId":2,"type":"int32be","len":2,"offset":0,"factor":1}}
                    
                    modbus.0
                    2023-06-30 21:17:11.312	debug	Initialize Objects for inputRegs: [{"_address":30256,"deviceId":1,"name":"Spannung","description":"Spannung","unit":"V","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":30256,"id":"inputRegisters.1.30256_Spannung","fullId":"modbus.0.inputRegisters.1.30256_Spannung"},{"_address":30256,"deviceId":2,"name":"Spannung","description":"Spannung","unit":"V","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":30256,"id":"inputRegisters.2.30256_Spannung"}]
                    
                    modbus.0
                    2023-06-30 21:17:11.311	debug	Initialize Objects for coils: []
                    
                    modbus.0
                    2023-06-30 21:17:11.311	debug	Initialize Objects for disInputs: []
                    
                    modbus.0
                    2023-06-30 21:17:11.310	debug	Initialize Objects for holdingRegs: []
                    
                    modbus.0
                    2023-06-30 21:17:11.310	debug	Add inputRegisters.1.30256_Spannung: {"_id":"inputRegisters.1.30256_Spannung","type":"state","common":{"name":"Spannung","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"V"},"native":{"regType":"inputRegs","address":30256,"deviceId":1,"type":"int32be","len":2,"offset":0,"factor":1}}
                    
                    modbus.0
                    2023-06-30 21:17:11.308	debug	Initialize Objects for inputRegs: [{"_address":30256,"deviceId":1,"name":"Spannung","description":"Spannung","unit":"V","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":30256,"id":"inputRegisters.1.30256_Spannung"},{"_address":30256,"deviceId":2,"name":"Spannung","description":"Spannung","unit":"V","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":"30256"}]
                    
                    modbus.0
                    2023-06-30 21:17:11.307	debug	Initialize Objects for coils: []
                    
                    modbus.0
                    2023-06-30 21:17:11.306	debug	Initialize Objects for disInputs: []
                    
                    modbus.0
                    2023-06-30 21:17:11.092	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
                    
                    modbus.0
                    2023-06-30 21:17:10.689	debug	Plugin sentry Initialize Plugin (enabled=true)
                    
                    modbus.0
                    2023-06-30 21:17:05.988	debug	Cleaning up request fifo.
                    
                    modbus.0
                    2023-06-30 21:17:05.988	debug	Clearing timeout of the current request.
                    
                    modbus.0
                    2023-06-30 21:17:05.984	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                    
                    modbus.0
                    2023-06-30 21:17:05.982	debug	Plugin sentry destroyed
                    
                    modbus.0
                    2023-06-30 21:17:05.979	info	terminating
                    
                    1 Reply Last reply Reply Quote 0
                    • O
                      obstbauer @bahnuhr last edited by

                      @bahnuhr ich bekomme 0 Volt angezeigt bei den Objekten obwohl Spannung anliegt

                      bahnuhr 1 Reply Last reply Reply Quote 0
                      • Homoran
                        Homoran Global Moderator Administrators @obstbauer last edited by Homoran

                        @obstbauer wie @bahnuhr schon schrieb klappt alles
                        (zumindest mit Abfrage und Antwort)

                        was hat dein Zähler als Offset zu seinem hex0100 angegeben?

                        1 Reply Last reply Reply Quote 0
                        • bahnuhr
                          bahnuhr Forum Testing Most Active @obstbauer last edited by

                          @obstbauer
                          Dann kann es doch nur an den Einstellungen in der Instanz liegen.

                          Meine sind so:
                          b86f431e-a68d-43a1-bb48-a51dc429353b-image.png

                          a5a05fd2-b7b5-4c6b-b028-7605f6b2480d-image.png

                          Aber da brauchst du natürlich deine.
                          Aber zum Vergleich kann es ja nicht schaden.

                          Homoran 1 Reply Last reply Reply Quote 0
                          • Homoran
                            Homoran Global Moderator Administrators @bahnuhr last edited by

                            @bahnuhr sagte in Probleme mit modbus Stromzähler, keine Werte:

                            Meine sind so:

                            du hast außerdem Modbus TCP, hier geht's um RTU

                            bahnuhr 1 Reply Last reply Reply Quote 0
                            • bahnuhr
                              bahnuhr Forum Testing Most Active @Homoran last edited by

                              @homoran sagte in Probleme mit modbus Stromzähler, keine Werte:

                              du hast außerdem Modbus TCP, hier geht's um RTU

                              ja, schon klar.
                              Wollte damit ja auch nur kundtun, dass es an seinen Einstellungen liegt.
                              RTU hat bei mir nicht geklappt.

                              1 Reply Last reply Reply Quote 0
                              • O
                                obstbauer last edited by

                                ja ich habe RTU, seriell 2 Adern, und es klappt leider noch nicht 😕
                                immerhin wissen wir jetzt worum es geht und ich habe etwas gelernt

                                1 Reply Last reply Reply Quote 0
                                • Homoran
                                  Homoran Global Moderator Administrators last edited by

                                  @obstbauer stell mal alias aus und nimm die Roh-adressen
                                  außerdem erst mal nur einen Zähler und da nur eine Adresse

                                  O 1 Reply Last reply Reply Quote 0
                                  • O
                                    obstbauer @Homoran last edited by

                                    @homoran das hat leider nicht funktioniert
                                    ich werde mal das Windows Programm nehmen und den usb stick über ein Windows Notebook testen

                                    Homoran 3 Replies Last reply Reply Quote 0
                                    • Homoran
                                      Homoran Global Moderator Administrators @obstbauer last edited by Homoran

                                      @obstbauer sagte in Probleme mit modbus Stromzähler, keine Werte:

                                      das hat leider nicht funktioniert

                                      was?

                                      ich habe mir jetzt exakt das selbe Equipment besorgt und muss dich enttäuschen - es klappt!
                                      Screenshot_20230701-144227_Firefox.jpg
                                      leider hattest du diese Frage nicht beantwortet

                                      @homoran sagte in Probleme mit modbus Stromzähler, keine Werte:

                                      was hat dein Zähler als Offset zu seinem hex0100 angegeben?

                                      wie befürchtet ist das nämlich nicht 30000 sondern 30001!

                                      dann klappt es mit
                                      Screenshot_20230701-144313_Firefox.jpg

                                      1 Reply Last reply Reply Quote 1
                                      • Homoran
                                        Homoran Global Moderator Administrators @obstbauer last edited by Homoran

                                        @obstbauer sagte in Probleme mit modbus Stromzähler, keine Werte:

                                        das hat leider nicht funktioniert

                                        • Alias aus
                                          normale Adressen erscheinen automatisch
                                          Screenshot_20230701-145734_Firefox.jpg

                                        Ergebnisse auch
                                        Screenshot_20230701-145659_Firefox.jpg

                                        und immer mehr
                                        Screenshot_20230701-150154_Firefox.jpg

                                        1 Reply Last reply Reply Quote 0
                                        • Homoran
                                          Homoran Global Moderator Administrators @obstbauer last edited by Homoran

                                          @obstbauer hab noch weiter getestet.
                                          Der Zähler ist im unteren Bereich nicht sehr empindlich. ist er aber auch nicht für spezifiziert.
                                          ein 3W LED Leuchtmittel reichte nicht, ein 5W lockt dem Zähler ab und zu etwas aus der Anzeige. (sowohl lokal am Display als auch über Modbus

                                          Screenshot_20230701-154110_Firefox.jpg

                                          P 1 Reply Last reply Reply Quote 0
                                          • P
                                            peterfido @Homoran last edited by

                                            @obstbauer Die Angabe 0,25A - 5A auf dem Zähler (Fotos aus dem Link im ersten Post) ist der Messbereich, auf den der Zähler geeicht ist. Da drunter und darüber sollte man mit Abweichungen rechnen.

                                            Homoran 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate
                                            FAQ Cloud / IOT
                                            HowTo: Node.js-Update
                                            HowTo: Backup/Restore
                                            Downloads
                                            BLOG

                                            899
                                            Online

                                            32.1k
                                            Users

                                            80.7k
                                            Topics

                                            1.3m
                                            Posts

                                            4
                                            39
                                            2427
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo