  4. Probleme mit modbus Stromzähler, keine Werte
    5.3k
39 Beiträge 4 Kommentatoren 4.2k Aufrufe 3 Beobachtet
  • O obstbauer
    2023-06-30 20:38:35.213  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:38:35.213  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:38:35.215  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:38:38.669  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:38:38.669  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:38:48.749  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:38:48.749  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:38:48.754  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:38:52.205  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:38:52.205  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:02.285  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:39:02.285  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:02.287  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:39:05.741  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:39:05.741  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:15.821  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:39:15.821  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:15.823  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:39:19.277  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:39:19.277  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:29.357  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:39:29.357  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:29.361  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:39:32.813  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:39:32.813  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:42.893  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:39:42.893  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:42.897  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:39:46.349  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:39:46.349  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:56.461  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:39:56.461  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:39:56.465  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:39:59.917  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:39:59.917  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:40:09.997  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:40:09.997  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:40:10.000  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:40:13.453  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:40:13.453  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:40:23.533  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:40:23.533  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:40:23.540  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:40:26.989  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:40:26.989  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:40:37.069  - warn: mbus.1 (2589) M-Bus ID 1 err: Error: Error: Failed to send/receive M-Bus request frame[1].
    2023-06-30 20:40:37.069  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    2023-06-30 20:40:37.076  - info: mbus.1 (2589) State value to set for "mbus.1.BMT-21004.data.lastStatus" has to be type "string" but received type "object"
    2023-06-30 20:40:40.529  - warn: mbus.1 (2589) M-Bus ID 2 err: Error: Error: Failed to send/receive M-Bus request frame[2].
    2023-06-30 20:40:40.529  - warn: mbus.1 (2589) M-Bus Devices with errors: 2 from 4
    bahnuhrB Online
    bahnuhrB Online
    bahnuhr
    @obstbauer
    Das ist wieder mbus.1
    Ich denke modbus klappt nicht
    Danke.
    O 1 Antwort Letzte Antwort
    • O obstbauer
      @obstbauer Danke!
      aber nur mbus Meldungen
      hast du vielleicht auf mbus gefiltert?
      wurde die modbus Instanz neu gestartet?
      das muss im log zu sehen sein.
      • bahnuhrB bahnuhr
        @obstbauer
        O Offline
        O Offline
        obstbauer
        @bahnuhr ja sorry ich arbeite daran
        weiß gerade nicht wie ich modbus auf debug schalte, das ist das was mir bei Protokolle angezeigt wird, da taucht nur mbus auf, entschuldigung für die Verwirrung
        HomoranH bahnuhrB 2 Antworten Letzte Antwort
        • O obstbauer
          @obstbauer sagte in Probleme mit modbus Stromzähler, keine Werte:
          hab dir doch was zum lesen verlinkt
          • O obstbauer
            bahnuhrB Online
            bahnuhrB Online
            bahnuhr
            @obstbauer
            Dort auf debug stellen.
            Und dann instanz neu starten.
            Und dann log hier als code-tag posten.
            Danke.
            • O Offline
              O Offline
              obstbauer
              so ich denke jetzt habe ichs, sorry....
              2023-06-30 21:13:47.306 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:47.362 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:47.413 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
              2023-06-30 21:13:47.414 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:47.468 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:48.519 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
              2023-06-30 21:13:48.521 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:48.582 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:48.635 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
              2023-06-30 21:13:48.636 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:48.693 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:49.746 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
              2023-06-30 21:13:49.747 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:49.802 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:49.857 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
              2023-06-30 21:13:49.858 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:49.913 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:50.966 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
              2023-06-30 21:13:50.967 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:51.022 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:51.073 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
              2023-06-30 21:13:51.074 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:51.128 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:52.181 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
              2023-06-30 21:13:52.181 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:52.237 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:52.288 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
              2023-06-30 21:13:52.288 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:52.343 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:53.395 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
              2023-06-30 21:13:53.396 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:53.452 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:53.503 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
              2023-06-30 21:13:53.504 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:53.558 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:54.609 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
              2023-06-30 21:13:54.610 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:54.667 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:54.718 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
              2023-06-30 21:13:54.718 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:54.773 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:55.825 - debug: modbus.0 (655156) [DevID_1] Poll start ---------------------
              2023-06-30 21:13:55.825 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:55.882 - debug: modbus.0 (655156) [DevID_1/inputRegs] Poll address 30100 DONE
              2023-06-30 21:13:55.933 - debug: modbus.0 (655156) [DevID_2] Poll start ---------------------
              2023-06-30 21:13:55.935 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 - 2 registers
              2023-06-30 21:13:55.993 - debug: modbus.0 (655156) [DevID_2/inputRegs] Poll address 30100 DONE
              bahnuhrB HomoranH 2 Antworten Letzte Antwort
              • O obstbauer
                bahnuhrB Online
                bahnuhrB Online
                bahnuhr
                @obstbauer
                So, da steht doch überall done.
                Also scheint es doch zu klappen.
                Also nochmal die Frage:
                Was klappt jetzt nicht bei modbus ?
                Danke.
                • O Offline
                  O Offline
                  obstbauer
                  hier noch mit dem Neustart
                  modbus.0
                  2023-06-30 21:17:13.084	debug	[DevID_1/inputRegs] Poll address 30256 DONE
                  modbus.0
                  2023-06-30 21:17:13.026	debug	[DevID_1/inputRegs] Poll address 30256 - 2 registers
                  modbus.0
                  2023-06-30 21:17:13.026	debug	[DevID_1] Poll start ---------------------
                  modbus.0
                  2023-06-30 21:17:11.972	debug	[DevID_2/inputRegs] Poll address 30256 DONE
                  modbus.0
                  2023-06-30 21:17:11.912	debug	[DevID_2/inputRegs] Poll address 30256 - 2 registers
                  modbus.0
                  2023-06-30 21:17:11.912	debug	Initialization of scale factors done!
                  modbus.0
                  2023-06-30 21:17:11.911	debug	[DevID_2] Poll start ---------------------
                  modbus.0
                  2023-06-30 21:17:11.857	debug	[DevID_1/inputRegs] Poll address 30256 DONE
                  modbus.0
                  2023-06-30 21:17:11.786	debug	[DevID_1/inputRegs] Poll address 30256 - 2 registers
                  modbus.0
                  2023-06-30 21:17:11.785	debug	Initialization of scale factors done!
                  modbus.0
                  2023-06-30 21:17:11.783	debug	[DevID_1] Poll start ---------------------
                  modbus.0
                  2023-06-30 21:17:11.782	info	Connected to slave
                  modbus.0
                  2023-06-30 21:17:11.774	debug	connect to serial /dev/ttyACM0 with 9600
                  modbus.0
                  2023-06-30 21:17:11.416	debug	Remove old object modbus.0.inputRegisters.2.30100_Spannung
                  modbus.0
                  2023-06-30 21:17:11.415	debug	Remove old object modbus.0.inputRegisters.1.30100_Spannung
                  modbus.0
                  2023-06-30 21:17:11.314	debug	Initialize Objects for holdingRegs: []
                  modbus.0
                  2023-06-30 21:17:11.312	debug	Add inputRegisters.2.30256_Spannung: {"_id":"inputRegisters.2.30256_Spannung","type":"state","common":{"name":"Spannung","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"V"},"native":{"regType":"inputRegs","address":30256,"deviceId":2,"type":"int32be","len":2,"offset":0,"factor":1}}
                  modbus.0
                  2023-06-30 21:17:11.312	debug	Initialize Objects for inputRegs: [{"_address":30256,"deviceId":1,"name":"Spannung","description":"Spannung","unit":"V","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":30256,"id":"inputRegisters.1.30256_Spannung","fullId":"modbus.0.inputRegisters.1.30256_Spannung"},{"_address":30256,"deviceId":2,"name":"Spannung","description":"Spannung","unit":"V","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":30256,"id":"inputRegisters.2.30256_Spannung"}]
                  modbus.0
                  2023-06-30 21:17:11.311	debug	Initialize Objects for coils: []
                  modbus.0
                  2023-06-30 21:17:11.311	debug	Initialize Objects for disInputs: []
                  modbus.0
                  2023-06-30 21:17:11.310	debug	Initialize Objects for holdingRegs: []
                  modbus.0
                  2023-06-30 21:17:11.310	debug	Add inputRegisters.1.30256_Spannung: {"_id":"inputRegisters.1.30256_Spannung","type":"state","common":{"name":"Spannung","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"V"},"native":{"regType":"inputRegs","address":30256,"deviceId":1,"type":"int32be","len":2,"offset":0,"factor":1}}
                  modbus.0
                  2023-06-30 21:17:11.308	debug	Initialize Objects for inputRegs: [{"_address":30256,"deviceId":1,"name":"Spannung","description":"Spannung","unit":"V","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":30256,"id":"inputRegisters.1.30256_Spannung"},{"_address":30256,"deviceId":2,"name":"Spannung","description":"Spannung","unit":"V","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":"30256"}]
                  modbus.0
                  2023-06-30 21:17:11.307	debug	Initialize Objects for coils: []
                  modbus.0
                  2023-06-30 21:17:11.306	debug	Initialize Objects for disInputs: []
                  modbus.0
                  2023-06-30 21:17:11.092	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
                  modbus.0
                  2023-06-30 21:17:10.689	debug	Plugin sentry Initialize Plugin (enabled=true)
                  modbus.0
                  2023-06-30 21:17:05.988	debug	Cleaning up request fifo.
                  modbus.0
                  2023-06-30 21:17:05.988	debug	Clearing timeout of the current request.
                  modbus.0
                  2023-06-30 21:17:05.984	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                  modbus.0
                  2023-06-30 21:17:05.982	debug	Plugin sentry destroyed
                  modbus.0
                  2023-06-30 21:17:05.979	info	terminating
                  • bahnuhrB bahnuhr
                    @obstbauer
                    O Offline
                    O Offline
                    obstbauer
                    @bahnuhr ich bekomme 0 Volt angezeigt bei den Objekten obwohl Spannung anliegt
                    • O obstbauer
                      @obstbauer wie @bahnuhr schon schrieb klappt alles
                      (zumindest mit Abfrage und Antwort)
                      was hat dein Zähler als Offset zu seinem hex0100 angegeben?
                      • O obstbauer
                        bahnuhrB Online
                        bahnuhrB Online
                        bahnuhr
                        @obstbauer
                        Dann kann es doch nur an den Einstellungen in der Instanz liegen.
                        Meine sind so:
                        Aber da brauchst du natürlich deine.
                        Aber zum Vergleich kann es ja nicht schaden.
                        Danke.
                        • bahnuhrB bahnuhr
                          @obstbauer
                          Meine sind so:
                          @bahnuhr sagte in Probleme mit modbus Stromzähler, keine Werte:
                          Meine sind so:
                          du hast außerdem Modbus TCP, hier geht's um RTU
                            Meine sind so:
                            bahnuhrB Online
                            bahnuhrB Online
                            bahnuhr
                            @homoran sagte in Probleme mit modbus Stromzähler, keine Werte:
                            ja, schon klar.
                            Wollte damit ja auch nur kundtun, dass es an seinen Einstellungen liegt.
                            RTU hat bei mir nicht geklappt.
                            Danke.
                            • O Offline
                              O Offline
                              obstbauer
                              ja ich habe RTU, seriell 2 Adern, und es klappt leider noch nicht :/
                              immerhin wissen wir jetzt worum es geht und ich habe etwas gelernt
                                @obstbauer stell mal alias aus und nimm die Roh-adressen
                                außerdem erst mal nur einen Zähler und da nur eine Adresse
                                  O Offline
                                  O Offline
                                  obstbauer
                                  @homoran das hat leider nicht funktioniert
                                  ich werde mal das Windows Programm nehmen und den usb stick über ein Windows Notebook testen
                                  HomoranH 3 Antworten Letzte Antwort
                                  • O obstbauer
                                    was?
                                    ich habe mir jetzt exakt das selbe Equipment besorgt und muss dich enttäuschen - es klappt!
                                    leider hattest du diese Frage nicht beantwortet
                                    wie befürchtet ist das nämlich nicht 30000 sondern 30001!
                                    dann klappt es mit
                                    • O obstbauer
                                      • Alias aus
                                        normale Adressen erscheinen automatisch
                                      Ergebnisse auch
                                      und immer mehr
                                      • O obstbauer
                                        @obstbauer hab noch weiter getestet.
                                        Der Zähler ist im unteren Bereich nicht sehr empindlich. ist er aber auch nicht für spezifiziert.
                                        ein 3W LED Leuchtmittel reichte nicht, ein 5W lockt dem Zähler ab und zu etwas aus der Anzeige. (sowohl lokal am Display als auch über Modbus
                                        P 1 Antwort Letzte Antwort
                                          peterfido
                                          @obstbauer Die Angabe 0,25A - 5A auf dem Zähler (Fotos aus dem Link im ersten Post) ist der Messbereich, auf den der Zähler geeicht ist. Da drunter und darüber sollte man mit Abweichungen rechnen.
                                          Peterfido