  1. ioBroker Community Home
  2. Deutsch
  3. Tester
  4. Test Adapter Zendure Solarflow

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.6k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.1k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    2.8k

Test Adapter Zendure Solarflow

Geplant Angeheftet Gesperrt Verschoben Tester
2.0k Beiträge 99 Kommentatoren 892.4k Aufrufe 94 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • R Online
    R Online
    romestylez
    schrieb am zuletzt editiert von
    #1906

    Ich sehe immer wieder folgendes

    	[checkStatesJob] Last update for deviceKey XXXXXXX was at Sat Oct 04 2025 20:55:00 GMT+0200 (Mitteleuropäische Sommerzeit), device seems to be online - so maybe connection is broken - restart adapter in 20 seconds!
    

    Der Adapter wird dann halt 20 Sekunden später neugestartet. Das ist irgendwie etwas nervig und lässt sich leider nicht deaktivieren. Das Gerät ist "offline" weil es an der minimalen Ladegrenze ist und damit gibts halt kein "Last update" mehr.

    Könnte man bitte eine Option schaffen dieses Verhalten zu deaktivieren ?

    nograxN 1 Antwort Letzte Antwort
    0
    • T The_Stig

      @nograx, bin auf Version 2.0.4., rein lokal. Aktuell ist es bei mir so, dass der DischargeLimit immer zur vollen Stunden kurz auf 20% gesetzt wird und nach ein paar Sekunden dann wieder auf den eigentlichen im Control-Ordner gesetzten Wert wieder zurückgesetzt wird. In den Daten sieht das dann so aus:
      805c738d-fbc6-4e6a-ac26-ef0d7965c4ea-image.png
      Ich dachte erst, ich hätte irgendein altes Skript laufen, habe aber mal deaktiviert und habe das Problem trotzdem. Setzt du da in deinem Adapter da irgendwelche Werte regelmäßig automatisiert aus irgendeinem GRund? Sonst bin ich ideenlos, warum das so passiert.

      T Offline
      T Offline
      The_Stig
      schrieb am zuletzt editiert von
      #1907

      @nograx: Ergänzung: Sieht so aus, als ob mein stündlicher MQTT-Restart das auslöst oder eben ein Restart deines Adapters. Ist ja kurios, dass das dann einmal auf 20% zurückgesetzt und dann wieder direkt auf den eigentlich eingestellten Wert gesetzt wird.

      1 Antwort Letzte Antwort
      0
      • M Online
        M Online
        Murphy 0
        schrieb am zuletzt editiert von
        #1908

        Mit Adapter 2.04 rein offline habe ich seit Wochen keinen einzigen Mqtt Abbruch mehr gehabt. Mache keinen Reset des Mqtt Servers mehr.
        Leider kann ich nicht sagen ob die 2.04 das Problem gelöst hat oder mein Skript mit reduzierten Schreibvorgängen da ich das zeitgleich gemacht hatte.

        1 Antwort Letzte Antwort
        0
        • R romestylez

          Ich sehe immer wieder folgendes

          	[checkStatesJob] Last update for deviceKey XXXXXXX was at Sat Oct 04 2025 20:55:00 GMT+0200 (Mitteleuropäische Sommerzeit), device seems to be online - so maybe connection is broken - restart adapter in 20 seconds!
          

          Der Adapter wird dann halt 20 Sekunden später neugestartet. Das ist irgendwie etwas nervig und lässt sich leider nicht deaktivieren. Das Gerät ist "offline" weil es an der minimalen Ladegrenze ist und damit gibts halt kein "Last update" mehr.

          Könnte man bitte eine Option schaffen dieses Verhalten zu deaktivieren ?

          nograxN Offline
          nograxN Offline
          nograx
          Developer
          schrieb am zuletzt editiert von nograx
          #1909

          @romestylez sagte in Test Adapter Zendure Solarflow:

          Ich sehe immer wieder folgendes

          	[checkStatesJob] Last update for deviceKey XXXXXXX was at Sat Oct 04 2025 20:55:00 GMT+0200 (Mitteleuropäische Sommerzeit), device seems to be online - so maybe connection is broken - restart adapter in 20 seconds!
          

          Der Adapter wird dann halt 20 Sekunden später neugestartet. Das ist irgendwie etwas nervig und lässt sich leider nicht deaktivieren. Das Gerät ist "offline" weil es an der minimalen Ladegrenze ist und damit gibts halt kein "Last update" mehr.

          Könnte man bitte eine Option schaffen dieses Verhalten zu deaktivieren ?

          Kannst du das mal mit der neusten 3.0.2 testen? Vorher werden Updates für die Akkupacks nicht berücksichtigt um das lastUpdate zu setzen. So sorgen die Updates von der Temperatur oder Spannung nun endlich für einen frischen Timestamp...

          R 2 Antworten Letzte Antwort
          0
          • nograxN nograx

            @romestylez sagte in Test Adapter Zendure Solarflow:

            Ich sehe immer wieder folgendes

            	[checkStatesJob] Last update for deviceKey XXXXXXX was at Sat Oct 04 2025 20:55:00 GMT+0200 (Mitteleuropäische Sommerzeit), device seems to be online - so maybe connection is broken - restart adapter in 20 seconds!
            

            Der Adapter wird dann halt 20 Sekunden später neugestartet. Das ist irgendwie etwas nervig und lässt sich leider nicht deaktivieren. Das Gerät ist "offline" weil es an der minimalen Ladegrenze ist und damit gibts halt kein "Last update" mehr.

            Könnte man bitte eine Option schaffen dieses Verhalten zu deaktivieren ?

            Kannst du das mal mit der neusten 3.0.2 testen? Vorher werden Updates für die Akkupacks nicht berücksichtigt um das lastUpdate zu setzen. So sorgen die Updates von der Temperatur oder Spannung nun endlich für einen frischen Timestamp...

            R Online
            R Online
            romestylez
            schrieb am zuletzt editiert von
            #1910

            @nograx said in Test Adapter Zendure Solarflow:

            @romestylez sagte in Test Adapter Zendure Solarflow:

            Ich sehe immer wieder folgendes

            	[checkStatesJob] Last update for deviceKey XXXXXXX was at Sat Oct 04 2025 20:55:00 GMT+0200 (Mitteleuropäische Sommerzeit), device seems to be online - so maybe connection is broken - restart adapter in 20 seconds!
            

            Der Adapter wird dann halt 20 Sekunden später neugestartet. Das ist irgendwie etwas nervig und lässt sich leider nicht deaktivieren. Das Gerät ist "offline" weil es an der minimalen Ladegrenze ist und damit gibts halt kein "Last update" mehr.

            Könnte man bitte eine Option schaffen dieses Verhalten zu deaktivieren ?

            Kannst du das mal mit der neusten 3.0.2 testen? Vorher werden Updates für die Akkupacks nicht berücksichtigt um das lastUpdate zu setzen. So sorgen die Updates von der Temperatur oder Spannung nun endlich für einen frischen Timestamp...

            Ist installiert ich beobachte es mal :) Danke für die super Arbeit !

            1 Antwort Letzte Antwort
            0
            • K Offline
              K Offline
              Kiter1988
              schrieb am zuletzt editiert von
              #1911

              Version 3.0.2
              Hub2000
              Ace1500

              Folgendes musste seit ein paar Tagen feststellen.
              Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
              Vorher stand dort immer 900

              Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
              Eine Ladung kommt nicht mehr zustande.

              Woran kann das liegen ?
              Betroffene Scripte habe ich ausgeschaltet.
              Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

              nograxN 1 Antwort Letzte Antwort
              0
              • K Kiter1988

                Version 3.0.2
                Hub2000
                Ace1500

                Folgendes musste seit ein paar Tagen feststellen.
                Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                Vorher stand dort immer 900

                Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                Eine Ladung kommt nicht mehr zustande.

                Woran kann das liegen ?
                Betroffene Scripte habe ich ausgeschaltet.
                Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                nograxN Offline
                nograxN Offline
                nograx
                Developer
                schrieb am zuletzt editiert von
                #1912

                @kiter1988 sagte in Test Adapter Zendure Solarflow:

                Version 3.0.2
                Hub2000
                Ace1500

                Folgendes musste seit ein paar Tagen feststellen.
                Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                Vorher stand dort immer 900

                Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                Eine Ladung kommt nicht mehr zustande.

                Woran kann das liegen ?
                Betroffene Scripte habe ich ausgeschaltet.
                Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                Setzt du das beim Hub oder beim Ace? Seit der Adapter Version 3.0 wird ja der Cloud Key genutzt, da bin ich mir nicht sicher was für Nebeneffekte in so einem Beispiel auftreten... im Zweifel bitte mal ein wenig rumprobieren...

                K 1 Antwort Letzte Antwort
                0
                • nograxN nograx

                  @kiter1988 sagte in Test Adapter Zendure Solarflow:

                  Version 3.0.2
                  Hub2000
                  Ace1500

                  Folgendes musste seit ein paar Tagen feststellen.
                  Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                  Vorher stand dort immer 900

                  Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                  Eine Ladung kommt nicht mehr zustande.

                  Woran kann das liegen ?
                  Betroffene Scripte habe ich ausgeschaltet.
                  Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                  Setzt du das beim Hub oder beim Ace? Seit der Adapter Version 3.0 wird ja der Cloud Key genutzt, da bin ich mir nicht sicher was für Nebeneffekte in so einem Beispiel auftreten... im Zweifel bitte mal ein wenig rumprobieren...

                  K Offline
                  K Offline
                  Kiter1988
                  schrieb am zuletzt editiert von
                  #1913

                  @nograx said in Test Adapter Zendure Solarflow:

                  @kiter1988 sagte in Test Adapter Zendure Solarflow:

                  Version 3.0.2
                  Hub2000
                  Ace1500

                  Folgendes musste seit ein paar Tagen feststellen.
                  Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                  Vorher stand dort immer 900

                  Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                  Eine Ladung kommt nicht mehr zustande.

                  Woran kann das liegen ?
                  Betroffene Scripte habe ich ausgeschaltet.
                  Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                  Setzt du das beim Hub oder beim Ace? Seit der Adapter Version 3.0 wird ja der Cloud Key genutzt, da bin ich mir nicht sicher was für Nebeneffekte in so einem Beispiel auftreten... im Zweifel bitte mal ein wenig rumprobieren...

                  Ich steuere alles über den Hub, ich habe nun fast alle kombinationen aus probiert.
                  Bleibt mir wohl nur ein Downgrade des Adapters, auf 2.0 oder so.

                  Arne DieckmannA 1 Antwort Letzte Antwort
                  0
                  • K Kiter1988

                    @nograx said in Test Adapter Zendure Solarflow:

                    @kiter1988 sagte in Test Adapter Zendure Solarflow:

                    Version 3.0.2
                    Hub2000
                    Ace1500

                    Folgendes musste seit ein paar Tagen feststellen.
                    Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                    Vorher stand dort immer 900

                    Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                    Eine Ladung kommt nicht mehr zustande.

                    Woran kann das liegen ?
                    Betroffene Scripte habe ich ausgeschaltet.
                    Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                    Setzt du das beim Hub oder beim Ace? Seit der Adapter Version 3.0 wird ja der Cloud Key genutzt, da bin ich mir nicht sicher was für Nebeneffekte in so einem Beispiel auftreten... im Zweifel bitte mal ein wenig rumprobieren...

                    Ich steuere alles über den Hub, ich habe nun fast alle kombinationen aus probiert.
                    Bleibt mir wohl nur ein Downgrade des Adapters, auf 2.0 oder so.

                    Arne DieckmannA Offline
                    Arne DieckmannA Offline
                    Arne Dieckmann
                    schrieb am zuletzt editiert von
                    #1914

                    @kiter1988 said in Test Adapter Zendure Solarflow:

                    @nograx said in Test Adapter Zendure Solarflow:

                    @kiter1988 sagte in Test Adapter Zendure Solarflow:

                    Version 3.0.2
                    Hub2000
                    Ace1500

                    Folgendes musste seit ein paar Tagen feststellen.
                    Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                    Vorher stand dort immer 900

                    Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                    Eine Ladung kommt nicht mehr zustande.

                    Woran kann das liegen ?
                    Betroffene Scripte habe ich ausgeschaltet.
                    Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                    Setzt du das beim Hub oder beim Ace? Seit der Adapter Version 3.0 wird ja der Cloud Key genutzt, da bin ich mir nicht sicher was für Nebeneffekte in so einem Beispiel auftreten... im Zweifel bitte mal ein wenig rumprobieren...

                    Ich steuere alles über den Hub, ich habe nun fast alle kombinationen aus probiert.
                    Bleibt mir wohl nur ein Downgrade des Adapters, auf 2.0 oder so.

                    Bei mir genau das gleiche Phänomen. Hub2000, Ace1500, lokaler MQTT Server.

                    Der Ace wird nur für die "Zwangsladung bei zu lange nicht 100% SOC" verwendet, gesteuert über die Hub Config Datenpunkte. Sobald der acMode auf 1, autoModel auf 0 und setInputLimit auf 900 gesetzt sind, ändert sich der setInputLimit von 0 auf 900 auf -900 auf 0 und wieder von vorne.

                    Bin zurück auf 2.0.4.

                    nograxN 1 Antwort Letzte Antwort
                    1
                    • Arne DieckmannA Arne Dieckmann

                      @kiter1988 said in Test Adapter Zendure Solarflow:

                      @nograx said in Test Adapter Zendure Solarflow:

                      @kiter1988 sagte in Test Adapter Zendure Solarflow:

                      Version 3.0.2
                      Hub2000
                      Ace1500

                      Folgendes musste seit ein paar Tagen feststellen.
                      Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                      Vorher stand dort immer 900

                      Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                      Eine Ladung kommt nicht mehr zustande.

                      Woran kann das liegen ?
                      Betroffene Scripte habe ich ausgeschaltet.
                      Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                      Setzt du das beim Hub oder beim Ace? Seit der Adapter Version 3.0 wird ja der Cloud Key genutzt, da bin ich mir nicht sicher was für Nebeneffekte in so einem Beispiel auftreten... im Zweifel bitte mal ein wenig rumprobieren...

                      Ich steuere alles über den Hub, ich habe nun fast alle kombinationen aus probiert.
                      Bleibt mir wohl nur ein Downgrade des Adapters, auf 2.0 oder so.

                      Bei mir genau das gleiche Phänomen. Hub2000, Ace1500, lokaler MQTT Server.

                      Der Ace wird nur für die "Zwangsladung bei zu lange nicht 100% SOC" verwendet, gesteuert über die Hub Config Datenpunkte. Sobald der acMode auf 1, autoModel auf 0 und setInputLimit auf 900 gesetzt sind, ändert sich der setInputLimit von 0 auf 900 auf -900 auf 0 und wieder von vorne.

                      Bin zurück auf 2.0.4.

                      nograxN Offline
                      nograxN Offline
                      nograx
                      Developer
                      schrieb am zuletzt editiert von
                      #1915

                      @arne-dieckmann sagte in Test Adapter Zendure Solarflow:

                      @kiter1988 said in Test Adapter Zendure Solarflow:

                      @nograx said in Test Adapter Zendure Solarflow:

                      @kiter1988 sagte in Test Adapter Zendure Solarflow:

                      Version 3.0.2
                      Hub2000
                      Ace1500

                      Folgendes musste seit ein paar Tagen feststellen.
                      Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                      Vorher stand dort immer 900

                      Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                      Eine Ladung kommt nicht mehr zustande.

                      Woran kann das liegen ?
                      Betroffene Scripte habe ich ausgeschaltet.
                      Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                      Setzt du das beim Hub oder beim Ace? Seit der Adapter Version 3.0 wird ja der Cloud Key genutzt, da bin ich mir nicht sicher was für Nebeneffekte in so einem Beispiel auftreten... im Zweifel bitte mal ein wenig rumprobieren...

                      Ich steuere alles über den Hub, ich habe nun fast alle kombinationen aus probiert.
                      Bleibt mir wohl nur ein Downgrade des Adapters, auf 2.0 oder so.

                      Bei mir genau das gleiche Phänomen. Hub2000, Ace1500, lokaler MQTT Server.

                      Der Ace wird nur für die "Zwangsladung bei zu lange nicht 100% SOC" verwendet, gesteuert über die Hub Config Datenpunkte. Sobald der acMode auf 1, autoModel auf 0 und setInputLimit auf 900 gesetzt sind, ändert sich der setInputLimit von 0 auf 900 auf -900 auf 0 und wieder von vorne.

                      Bin zurück auf 2.0.4.

                      Hm, ok das ist ein Ansatz, vll passt meine Logik da nicht. Schaue ich mir an (kann es selber leider nicht testen).

                      Arne DieckmannA 1 Antwort Letzte Antwort
                      0
                      • nograxN nograx

                        @romestylez sagte in Test Adapter Zendure Solarflow:

                        Ich sehe immer wieder folgendes

                        	[checkStatesJob] Last update for deviceKey XXXXXXX was at Sat Oct 04 2025 20:55:00 GMT+0200 (Mitteleuropäische Sommerzeit), device seems to be online - so maybe connection is broken - restart adapter in 20 seconds!
                        

                        Der Adapter wird dann halt 20 Sekunden später neugestartet. Das ist irgendwie etwas nervig und lässt sich leider nicht deaktivieren. Das Gerät ist "offline" weil es an der minimalen Ladegrenze ist und damit gibts halt kein "Last update" mehr.

                        Könnte man bitte eine Option schaffen dieses Verhalten zu deaktivieren ?

                        Kannst du das mal mit der neusten 3.0.2 testen? Vorher werden Updates für die Akkupacks nicht berücksichtigt um das lastUpdate zu setzen. So sorgen die Updates von der Temperatur oder Spannung nun endlich für einen frischen Timestamp...

                        R Online
                        R Online
                        romestylez
                        schrieb am zuletzt editiert von romestylez
                        #1916

                        @nograx Problem besteht immer noch leider.

                        Last Update: Thu Oct 09 2025 07:17:29 GMT+0200 (Mitteleuropäische Sommerzeit)

                        Aber z.B. wifiState ist von 07:46:09 also relativ aktuell (eventuell nach dem automatischen Neustart). Es wäre schön wenn dieser automatische Neustart aufhört denn das Gerät ist definitiv erreichbar z.B. per ping stellt sich die Frage wieso "lastUpdate" nicht aktualisiert wird.

                        Was ich auch sehr oft sehe schon seit langer Zeit. Das ist auch richtig denn ich verwende ausschließlich den CT-Mode also Mode 9.

                        zendure-solarflow.0
                        2025-10-09 07:46:06.737 warn Operation mode (autoModel) is not set to '0', we can't set the output limit!

                        zendure-solarflow.0
                        2025-10-09 07:46:05.811 warn Operation mode (autoModel) is not set to '0', we can't set the output limit!

                        zendure-solarflow.0
                        2025-10-09 07:46:05.035 warn Operation mode (autoModel) is not set to '0', we can't set the output limit!

                        zendure-solarflow.0
                        2025-10-09 07:46:04.724 warn Operation mode (autoModel) is not set to '0', we can't set the output limit!

                        zendure-solarflow.0
                        2025-10-09 07:46:03.913 warn Operation mode (autoModel) is not set to '0', we can't set the output limit!

                        zendure-solarflow.0
                        2025-10-09 07:46:00.344 warn Operation mode (autoModel) is not set to '0', we can't set the output limit!

                        1 Antwort Letzte Antwort
                        0
                        • nograxN nograx

                          @arne-dieckmann sagte in Test Adapter Zendure Solarflow:

                          @kiter1988 said in Test Adapter Zendure Solarflow:

                          @nograx said in Test Adapter Zendure Solarflow:

                          @kiter1988 sagte in Test Adapter Zendure Solarflow:

                          Version 3.0.2
                          Hub2000
                          Ace1500

                          Folgendes musste seit ein paar Tagen feststellen.
                          Bei meinen Versuchen den Akku mit Netzstrom zu laden ist mir aufgefallen, dass der Datenpunkt "setInputLimit" den Wert 0 hat.
                          Vorher stand dort immer 900

                          Wenn ich den Ladevorgang starte, wechselt der Wert von 0W auf -900W und zurück auf 0W immer und immer wieder.
                          Eine Ladung kommt nicht mehr zustande.

                          Woran kann das liegen ?
                          Betroffene Scripte habe ich ausgeschaltet.
                          Hatte auch alles schon neugestartet, Hub, Ace, MQTT Broker und den Adapter.

                          Setzt du das beim Hub oder beim Ace? Seit der Adapter Version 3.0 wird ja der Cloud Key genutzt, da bin ich mir nicht sicher was für Nebeneffekte in so einem Beispiel auftreten... im Zweifel bitte mal ein wenig rumprobieren...

                          Ich steuere alles über den Hub, ich habe nun fast alle kombinationen aus probiert.
                          Bleibt mir wohl nur ein Downgrade des Adapters, auf 2.0 oder so.

                          Bei mir genau das gleiche Phänomen. Hub2000, Ace1500, lokaler MQTT Server.

                          Der Ace wird nur für die "Zwangsladung bei zu lange nicht 100% SOC" verwendet, gesteuert über die Hub Config Datenpunkte. Sobald der acMode auf 1, autoModel auf 0 und setInputLimit auf 900 gesetzt sind, ändert sich der setInputLimit von 0 auf 900 auf -900 auf 0 und wieder von vorne.

                          Bin zurück auf 2.0.4.

                          Hm, ok das ist ein Ansatz, vll passt meine Logik da nicht. Schaue ich mir an (kann es selber leider nicht testen).

                          Arne DieckmannA Offline
                          Arne DieckmannA Offline
                          Arne Dieckmann
                          schrieb am zuletzt editiert von
                          #1917

                          @nograx said in Test Adapter Zendure Solarflow:

                          @arne-dieckmann sagte in Test Adapter Zendure Solarflow:

                          Bei mir genau das gleiche Phänomen. Hub2000, Ace1500, lokaler MQTT Server.

                          Der Ace wird nur für die "Zwangsladung bei zu lange nicht 100% SOC" verwendet, gesteuert über die Hub Config Datenpunkte. Sobald der acMode auf 1, autoModel auf 0 und setInputLimit auf 900 gesetzt sind, ändert sich der setInputLimit von 0 auf 900 auf -900 auf 0 und wieder von vorne.

                          Bin zurück auf 2.0.4.

                          Hm, ok das ist ein Ansatz, vll passt meine Logik da nicht. Schaue ich mir an (kann es selber leider nicht testen).

                          Habe heute die 3.0.4 installiert, damit funktioniert die Logik wieder mit acMode 1, autoModel 0 und setInputLimit 900.

                          Perfekt! Danke!

                          WildshunterW 1 Antwort Letzte Antwort
                          1
                          • Arne DieckmannA Arne Dieckmann

                            @nograx said in Test Adapter Zendure Solarflow:

                            @arne-dieckmann sagte in Test Adapter Zendure Solarflow:

                            Bei mir genau das gleiche Phänomen. Hub2000, Ace1500, lokaler MQTT Server.

                            Der Ace wird nur für die "Zwangsladung bei zu lange nicht 100% SOC" verwendet, gesteuert über die Hub Config Datenpunkte. Sobald der acMode auf 1, autoModel auf 0 und setInputLimit auf 900 gesetzt sind, ändert sich der setInputLimit von 0 auf 900 auf -900 auf 0 und wieder von vorne.

                            Bin zurück auf 2.0.4.

                            Hm, ok das ist ein Ansatz, vll passt meine Logik da nicht. Schaue ich mir an (kann es selber leider nicht testen).

                            Habe heute die 3.0.4 installiert, damit funktioniert die Logik wieder mit acMode 1, autoModel 0 und setInputLimit 900.

                            Perfekt! Danke!

                            WildshunterW Offline
                            WildshunterW Offline
                            Wildshunter
                            schrieb am zuletzt editiert von
                            #1918

                            @arne-dieckmann
                            wer setzt bitte einen Hyper 2000 ein und kann bitte die in der letzten Version passenden/aktuell funktionsfähigen Objekte beschreiben oder wo kann ich das gesammelt nachlesen? Durch die Ansammlungen von Objekten die auch anscheinend für andere Zendure Modelle sind, komme ich da nicht mehr durch....
                            Danke!!!!!!

                            M 1 Antwort Letzte Antwort
                            0
                            • WildshunterW Wildshunter

                              @arne-dieckmann
                              wer setzt bitte einen Hyper 2000 ein und kann bitte die in der letzten Version passenden/aktuell funktionsfähigen Objekte beschreiben oder wo kann ich das gesammelt nachlesen? Durch die Ansammlungen von Objekten die auch anscheinend für andere Zendure Modelle sind, komme ich da nicht mehr durch....
                              Danke!!!!!!

                              M Online
                              M Online
                              Murphy 0
                              schrieb am zuletzt editiert von
                              #1919

                              @wildshunter
                              ich setze am Hyper die Version 2.04 ein.
                              Der Hyper lädt nur AC seitig. Mqtt über lokalen Mosquitto.

                              IMG_3673.jpeg

                              So sieht bei mir der Controlbereich aus.
                              Steuerung über Blockly benutze ich nur setDeviceAutomationInOutLimit.
                              Läuft seit Monaten ohne Problem.
                              Mqtt Probleme auch keine mehr.

                              J 1 Antwort Letzte Antwort
                              0
                              • tobetobeT tobetobe

                                @nograx
                                Hallo,
                                Vielen Dank für deine wertvolle Arbeit. Ich bin mit meinem SF 800 pro mit den bisherigen 2.x Adaptern sehr gut gefahren. Vor einigen Tagen bin ich dann auf 3.0 umgestiegen. Die ioBroker States wurden dann allerdings nicht mehr aktualisiert. Auch wird der Datenbaum nur unvollständig angelegt. Der OrdnerR3…. fehlt komplett. Update auf 3.0.1 brachte keine Verbesserung.

                                Noch ein Bug oder mache ich ggf etwas falsch? Keine Eile - ich kann auf die letzte 2-er Version zurückgreifen

                                Grüße Thomas

                                tobetobeT Offline
                                tobetobeT Offline
                                tobetobe
                                schrieb am zuletzt editiert von
                                #1920

                                @nograx

                                Vielen Dank für die 3.0.7/3.0.8 die das Problem mit den Daten vom SF 800 pro behoben haben. Das Warten hat sich gelohnt…

                                @tobetobe sagte in Test Adapter Zendure Solarflow:

                                @nograx
                                Hallo,
                                Vielen Dank für deine wertvolle Arbeit. Ich bin mit meinem SF 800 pro mit den bisherigen 2.x Adaptern sehr gut gefahren. Vor einigen Tagen bin ich dann auf 3.0 umgestiegen. Die ioBroker States wurden dann allerdings nicht mehr aktualisiert. Auch wird der Datenbaum nur unvollständig angelegt. Der OrdnerR3…. fehlt komplett. Update auf 3.0.1 brachte keine Verbesserung.

                                Noch ein Bug oder mache ich ggf etwas falsch? Keine Eile - ich kann auf die letzte 2-er Version zurückgreifen

                                Grüße Thomas

                                Beste Grüße
                                tobetobe

                                nograxN 1 Antwort Letzte Antwort
                                0
                                • tobetobeT tobetobe

                                  @nograx

                                  Vielen Dank für die 3.0.7/3.0.8 die das Problem mit den Daten vom SF 800 pro behoben haben. Das Warten hat sich gelohnt…

                                  @tobetobe sagte in Test Adapter Zendure Solarflow:

                                  @nograx
                                  Hallo,
                                  Vielen Dank für deine wertvolle Arbeit. Ich bin mit meinem SF 800 pro mit den bisherigen 2.x Adaptern sehr gut gefahren. Vor einigen Tagen bin ich dann auf 3.0 umgestiegen. Die ioBroker States wurden dann allerdings nicht mehr aktualisiert. Auch wird der Datenbaum nur unvollständig angelegt. Der OrdnerR3…. fehlt komplett. Update auf 3.0.1 brachte keine Verbesserung.

                                  Noch ein Bug oder mache ich ggf etwas falsch? Keine Eile - ich kann auf die letzte 2-er Version zurückgreifen

                                  Grüße Thomas

                                  nograxN Offline
                                  nograxN Offline
                                  nograx
                                  Developer
                                  schrieb am zuletzt editiert von
                                  #1921

                                  @tobetobe sagte in Test Adapter Zendure Solarflow:

                                  @nograx

                                  Vielen Dank für die 3.0.7/3.0.8 die das Problem mit den Daten vom SF 800 pro behoben haben. Das Warten hat sich gelohnt…

                                  @tobetobe sagte in Test Adapter Zendure Solarflow:

                                  @nograx
                                  Hallo,
                                  Vielen Dank für deine wertvolle Arbeit. Ich bin mit meinem SF 800 pro mit den bisherigen 2.x Adaptern sehr gut gefahren. Vor einigen Tagen bin ich dann auf 3.0 umgestiegen. Die ioBroker States wurden dann allerdings nicht mehr aktualisiert. Auch wird der Datenbaum nur unvollständig angelegt. Der OrdnerR3…. fehlt komplett. Update auf 3.0.1 brachte keine Verbesserung.

                                  Noch ein Bug oder mache ich ggf etwas falsch? Keine Eile - ich kann auf die letzte 2-er Version zurückgreifen

                                  Grüße Thomas

                                  Sorry, ganz vergessen dir hier Bescheid zu geben...

                                  S tobetobeT 2 Antworten Letzte Antwort
                                  0
                                  • nograxN nograx

                                    @tobetobe sagte in Test Adapter Zendure Solarflow:

                                    @nograx

                                    Vielen Dank für die 3.0.7/3.0.8 die das Problem mit den Daten vom SF 800 pro behoben haben. Das Warten hat sich gelohnt…

                                    @tobetobe sagte in Test Adapter Zendure Solarflow:

                                    @nograx
                                    Hallo,
                                    Vielen Dank für deine wertvolle Arbeit. Ich bin mit meinem SF 800 pro mit den bisherigen 2.x Adaptern sehr gut gefahren. Vor einigen Tagen bin ich dann auf 3.0 umgestiegen. Die ioBroker States wurden dann allerdings nicht mehr aktualisiert. Auch wird der Datenbaum nur unvollständig angelegt. Der OrdnerR3…. fehlt komplett. Update auf 3.0.1 brachte keine Verbesserung.

                                    Noch ein Bug oder mache ich ggf etwas falsch? Keine Eile - ich kann auf die letzte 2-er Version zurückgreifen

                                    Grüße Thomas

                                    Sorry, ganz vergessen dir hier Bescheid zu geben...

                                    S Online
                                    S Online
                                    Schimi
                                    schrieb am zuletzt editiert von
                                    #1922

                                    @nograx

                                    Hey, habe gerade bei meinem 2400AC etwas mit dem MQTT Modus gespielt...

                                    wenn ich "setDeviceAutomationInOutLimit" auf z.B. 400 setze... speist er wie erwartet 400Watt ins netz ein....

                                    Wenn ich auf z.B. -400 setze, speist er 2400Watt ins Netz ein.... Der negative wert wird nicht richtig übernommen...

                                    Wenn ich "acMode" auf "AC input mode (1)" stelle und bei "setInputLimit" 250 eintrage, dann lädt er wie erwartert den akku mit 250Watt.

                                    Sobald ich nun wieder bei "setDeviceAutomationInOutLimit" was eintrage, wechselt er in "AC output mode (2)" und spest entsprechend ins Netz...

                                    bediene ich das falsch oder ist da der Wurm drin?

                                    auch ein "smartMode" finde ich nirgends...

                                    M 1 Antwort Letzte Antwort
                                    0
                                    • S Schimi

                                      @nograx

                                      Hey, habe gerade bei meinem 2400AC etwas mit dem MQTT Modus gespielt...

                                      wenn ich "setDeviceAutomationInOutLimit" auf z.B. 400 setze... speist er wie erwartet 400Watt ins netz ein....

                                      Wenn ich auf z.B. -400 setze, speist er 2400Watt ins Netz ein.... Der negative wert wird nicht richtig übernommen...

                                      Wenn ich "acMode" auf "AC input mode (1)" stelle und bei "setInputLimit" 250 eintrage, dann lädt er wie erwartert den akku mit 250Watt.

                                      Sobald ich nun wieder bei "setDeviceAutomationInOutLimit" was eintrage, wechselt er in "AC output mode (2)" und spest entsprechend ins Netz...

                                      bediene ich das falsch oder ist da der Wurm drin?

                                      auch ein "smartMode" finde ich nirgends...

                                      M Offline
                                      M Offline
                                      Mabbi
                                      schrieb am zuletzt editiert von Mabbi
                                      #1923

                                      @schimi
                                      Wenn du mit mqtt testest, dann schau dir mal das java-script von @maxclaudi an, das beantwortet auch deine Frage zum Smartmode = 1, was sinnvoll für die Lebensdauer Deines internen flash Speichers im AC2400 sein sollte.

                                      P.S.: Zendure hat mich heute morgen freigeschaltet....freu, meine :pray: wurden erhört.

                                      ee799a48-2bf6-4a46-970e-c360c0a9fbdd-grafik.png
                                      :+1:

                                      War anfangs enttäuscht als ich den 2. AC2400 angeklemmt habe und sich das 'Energiesystem' in der App nicht höher als 2400 W In & Out einstellen lies, ergo teilten sich die beiden AC 2400 das 2400 W Limit zu je 1200 W auf, da hätte ich ja auch die zus. Akkupacks unter den 1. AC 2400 stapeln können.

                                      Aber nach einem Nachweis über meine Verkabelung/Schaltschrank hat Zendure mich heute morgen freigeschaltet...

                                      5e440519-d624-4ee2-80d4-c78abb7368c0-grafik.png

                                      Falls Ihr mehr als einen AC 2400 plant, lasst das von einem Elektriker bauen.
                                      Zendure forderte von mir (kein Scherz) eine gestempelte Rechnung des Elektrofachbetriebes, der die Installation gemacht hat. Nach der Vorlage dieser hat die Freischaltung ca. 12 Stunden gedauert.

                                      SMA Wechselrichter Probleme seit letztem Update

                                      S 1 Antwort Letzte Antwort
                                      1
                                      • M Offline
                                        M Offline
                                        Mabbi
                                        schrieb am zuletzt editiert von Mabbi
                                        #1924

                                        Nachtrag:

                                        ...und was beweisen uns unsere Frauen dann ohne mit der Wimper zu zucken ...egal was wir bauen, es reicht nicht.

                                        653b476b-5137-4a47-81dd-3c5df78cf68a-grafik.png

                                        45 Minuten Herd + 1 Waschmaschine plus unseren guten alten Ablufttrockner alles nach Sonnenuntergang.
                                        Beide Akkus haben bei 15% abgeschaltet. Fairerweise waren die Packs auch nur zu ca. 62% voll geworden heute.

                                        Aber immerhin haben Sie brav knappe 4500W kombiniert ausgespuckt als es abgefordert wurde :)

                                        SMA Wechselrichter Probleme seit letztem Update

                                        1 Antwort Letzte Antwort
                                        0
                                        • M Mabbi

                                          @schimi
                                          Wenn du mit mqtt testest, dann schau dir mal das java-script von @maxclaudi an, das beantwortet auch deine Frage zum Smartmode = 1, was sinnvoll für die Lebensdauer Deines internen flash Speichers im AC2400 sein sollte.

                                          P.S.: Zendure hat mich heute morgen freigeschaltet....freu, meine :pray: wurden erhört.

                                          ee799a48-2bf6-4a46-970e-c360c0a9fbdd-grafik.png
                                          :+1:

                                          War anfangs enttäuscht als ich den 2. AC2400 angeklemmt habe und sich das 'Energiesystem' in der App nicht höher als 2400 W In & Out einstellen lies, ergo teilten sich die beiden AC 2400 das 2400 W Limit zu je 1200 W auf, da hätte ich ja auch die zus. Akkupacks unter den 1. AC 2400 stapeln können.

                                          Aber nach einem Nachweis über meine Verkabelung/Schaltschrank hat Zendure mich heute morgen freigeschaltet...

                                          5e440519-d624-4ee2-80d4-c78abb7368c0-grafik.png

                                          Falls Ihr mehr als einen AC 2400 plant, lasst das von einem Elektriker bauen.
                                          Zendure forderte von mir (kein Scherz) eine gestempelte Rechnung des Elektrofachbetriebes, der die Installation gemacht hat. Nach der Vorlage dieser hat die Freischaltung ca. 12 Stunden gedauert.

                                          S Online
                                          S Online
                                          Schimi
                                          schrieb am zuletzt editiert von
                                          #1925

                                          @mabbi

                                          nicht zur Nachahmung... die wollen einfach irgendwas haben... ne Rechnung mit chatGPt erstellt hat vor "Monaten" auch zur Freischaltung verholfen 😉

                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          573

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe