  4. Sensostar Modbus auslesen

NEWS

  • Wartung am 15.11. – Forum ab 22:00 Uhr nicht erreichbar
    BluefoxB
    Bluefox
    11
    2
    203

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    7.9k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.7k

Sensostar Modbus auslesen

Sensostar Modbus auslesen

Scheduled Pinned Locked Moved Hardware
79 Posts 6 Posters 4.6k Views 5 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • HomoranH Homoran

    @stephan-a Lass dir doch nicht alles aus der Nase ziehen!
    Gib doch mal zusammenhängend alle notwendigen Informationen:

    Du hast also ein Gerät (Wärmezähler??) das über Modbus auslesbar sein soll??
    Daran hängt ein Adapter??
    Daran hängt ein Waveshare RTU2ETH??
    daran hängt dein ioBroker Server??

    Oder andersrum
    Dein iobroker Server baut die Verbindung zum Waveshare auf.

    und dann???
    steht die weitere Kommunikation?

    ist in dem Waveshare die serielle Seite aktiv??
    korrekt konfiguriert???

    S Offline
    S Offline
    Stephan a
    wrote on last edited by
    #24

    @homoran - gut, ich mache keine neuen Thread auf und bleibe hier.

    HIer die Ausgangslage:

    @homoran sagte in Sensostar Modbus auslesen:

    Du hast also ein Gerät (Wärmezähler??) das über Modbus auslesbar sein soll??

    Ja, ich habe 2 Sensostar U und 2 modbus Adapter.

    @homoran sagte in Sensostar Modbus auslesen:

    Daran hängt ein Adapter??
    Daran hängt ein Waveshare ETH2RS485??
    daran hängt dein ioBroker Server??

    Ich habe einen 2 Kanal Waveshare to ETH Adapter.
    4 laufende modbus Instanzen sind auf dem 1 Kanal. Die laufen ohne Probleme.
    Am 2. Kanal Waveshare ist ein Engelmann modbus Adapter angeschlossen. Der zweite Zähler ist noch ohne Adapter.
    Über modbus Instanzen kommen die Werte vom Waveschare in den iobocker.

    @homoran sagte in Sensostar Modbus auslesen:

    und dann???
    steht die weitere Kommunikation?
    ist in dem Waveshare die serielle Seite aktiv??
    korrekt konfiguriert???

    Die Instanzen im iobroker laufen und sind alle grün.
    HIer die Einstellungen im Waveshare:
    052728cb-c2af-4726-979e-452cda4f58fe-grafik.png

    Der Engelmannmodbus hat:
    Kommunikationsparameter 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit)

    Bei vir-com sind Daten:
    54ecfeb1-dfec-41b5-9b36-2b076d0ae978-grafik.png

    Der 2. Kanal die RXD steht auf "1". Also werden keine Daten empfangen.

    Der Adapter ist in den Grundeinstellunen, nur die Anzahl der abzurufenden Register sind auf 1 gesetzt:
    1c13484a-3da5-4fe0-a64d-f2035282d61c-grafik.png
    c1e44349-edf3-4d5d-8b68-caf2d82d7111-grafik.png

    Eine Änderung der Verbindungsparameter von TCP auf TCP OVER RTU hat keine Veränderung gebracht.
    Der Registerwert im iobrocker ist "null", er ist kurz grün und geht dann auf rot.

    HIer noch die vir-com Einstellungen:
    d6885b41-a0a0-4381-9d7b-9eaa8a242b77-grafik.png
    cfbed71c-331d-4999-a493-0d6da8e24e43-grafik.png

    Das Problem sind die Werte vom Engelmannzähler Modbusmodul, dass scheinbar keine Daten liefert.
    Was ich nicht abfragen kann, ist die Modbusadresse vom Modul. Hier habe ich die ID 1 eingetragen und auch 2 versucht, ohne Äderung der angezeigten Werte.

    So das ist der aktuelle Stand.

    Viele Grüße
    Stephan

    HomoranH 1 Reply Last reply
    0
    • S Stephan a

      @homoran - gut, ich mache keine neuen Thread auf und bleibe hier.

      HIer die Ausgangslage:

      @homoran sagte in Sensostar Modbus auslesen:

      Du hast also ein Gerät (Wärmezähler??) das über Modbus auslesbar sein soll??

      Ja, ich habe 2 Sensostar U und 2 modbus Adapter.

      @homoran sagte in Sensostar Modbus auslesen:

      Daran hängt ein Adapter??
      Daran hängt ein Waveshare ETH2RS485??
      daran hängt dein ioBroker Server??

      Ich habe einen 2 Kanal Waveshare to ETH Adapter.
      4 laufende modbus Instanzen sind auf dem 1 Kanal. Die laufen ohne Probleme.
      Am 2. Kanal Waveshare ist ein Engelmann modbus Adapter angeschlossen. Der zweite Zähler ist noch ohne Adapter.
      Über modbus Instanzen kommen die Werte vom Waveschare in den iobocker.

      @homoran sagte in Sensostar Modbus auslesen:

      und dann???
      steht die weitere Kommunikation?
      ist in dem Waveshare die serielle Seite aktiv??
      korrekt konfiguriert???

      Die Instanzen im iobroker laufen und sind alle grün.
      HIer die Einstellungen im Waveshare:
      052728cb-c2af-4726-979e-452cda4f58fe-grafik.png

      Der Engelmannmodbus hat:
      Kommunikationsparameter 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit)

      Bei vir-com sind Daten:
      54ecfeb1-dfec-41b5-9b36-2b076d0ae978-grafik.png

      Der 2. Kanal die RXD steht auf "1". Also werden keine Daten empfangen.

      Der Adapter ist in den Grundeinstellunen, nur die Anzahl der abzurufenden Register sind auf 1 gesetzt:
      1c13484a-3da5-4fe0-a64d-f2035282d61c-grafik.png
      c1e44349-edf3-4d5d-8b68-caf2d82d7111-grafik.png

      Eine Änderung der Verbindungsparameter von TCP auf TCP OVER RTU hat keine Veränderung gebracht.
      Der Registerwert im iobrocker ist "null", er ist kurz grün und geht dann auf rot.

      HIer noch die vir-com Einstellungen:
      d6885b41-a0a0-4381-9d7b-9eaa8a242b77-grafik.png
      cfbed71c-331d-4999-a493-0d6da8e24e43-grafik.png

      Das Problem sind die Werte vom Engelmannzähler Modbusmodul, dass scheinbar keine Daten liefert.
      Was ich nicht abfragen kann, ist die Modbusadresse vom Modul. Hier habe ich die ID 1 eingetragen und auch 2 versucht, ohne Äderung der angezeigten Werte.

      So das ist der aktuelle Stand.

      HomoranH Do not disturb
      HomoranH Do not disturb
      Homoran
      Global Moderator Administrators
      wrote on last edited by
      #25

      @stephan-a sagte in Sensostar Modbus auslesen:

      Daran hängt ein Adapter??

      die Frage

      @homoran sagte in Sensostar Modbus auslesen:

      @stephan-a sagte in Sensostar Modbus auslesen:

      der Engelmann modbus Adapter.

      was ist das genau?
      Welche Konfiguration erwartet der?

      wurde imner noch nicht beantwortet.

      Was ist das und welche Funktion an welcher Stelle der gesamten Kette sitzt der?

      kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

      der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

      S 1 Reply Last reply
      0
      • HomoranH Homoran

        @stephan-a sagte in Sensostar Modbus auslesen:

        Daran hängt ein Adapter??

        die Frage

        @homoran sagte in Sensostar Modbus auslesen:

        @stephan-a sagte in Sensostar Modbus auslesen:

        der Engelmann modbus Adapter.

        was ist das genau?
        Welche Konfiguration erwartet der?

        wurde imner noch nicht beantwortet.

        Was ist das und welche Funktion an welcher Stelle der gesamten Kette sitzt der?

        S Offline
        S Offline
        Stephan a
        wrote on last edited by
        #26

        @homoran sagte in Sensostar Modbus auslesen:

        @homoran sagte in Sensostar Modbus auslesen:

        der Engelmann modbus Adapter.

        was ist das genau?
        Welche Konfiguration erwartet der?

        wurde imner noch nicht beantwortet.
        Was ist das und welche Funktion an welcher Stelle der gesamten Kette sitzt der?

        Das ist das Engelmannmodbusadaptermodul "Modbus-Modul RTU":
        https://www.zaehlershop.com/epages/61607473.sf/de_DE/?ObjectID=362300935

        Hier nochmal die Kofiguration vom Engelmannmodbusadaptermodul:
        Kommunikationsparameter: 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit)

        So ist die Kette aufgebaut:
        Engelmannzähler Sensostar mit eingebautem Modbusadaptermodul - Datenkabel A/B zum Waveshare to ETH Adapter - per LAN-Kabel zum pi mit laufendem iobrocker mit den Instanzen.

        Viele Grüße
        Stephan

        HomoranH P 2 Replies Last reply
        0
        • S Stephan a

          @homoran sagte in Sensostar Modbus auslesen:

          @homoran sagte in Sensostar Modbus auslesen:

          der Engelmann modbus Adapter.

          was ist das genau?
          Welche Konfiguration erwartet der?

          wurde imner noch nicht beantwortet.
          Was ist das und welche Funktion an welcher Stelle der gesamten Kette sitzt der?

          Das ist das Engelmannmodbusadaptermodul "Modbus-Modul RTU":
          https://www.zaehlershop.com/epages/61607473.sf/de_DE/?ObjectID=362300935

          Hier nochmal die Kofiguration vom Engelmannmodbusadaptermodul:
          Kommunikationsparameter: 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit)

          So ist die Kette aufgebaut:
          Engelmannzähler Sensostar mit eingebautem Modbusadaptermodul - Datenkabel A/B zum Waveshare to ETH Adapter - per LAN-Kabel zum pi mit laufendem iobrocker mit den Instanzen.

          HomoranH Do not disturb
          HomoranH Do not disturb
          Homoran
          Global Moderator Administrators
          wrote on last edited by
          #27

          @stephan-a sagte in Sensostar Modbus auslesen:

          Engelmannzähler Sensostar mit eingebautem Modbusadaptermodul - Datenkabel A/B zum Waveshare to ETH Adapter

          @homoran sagte in Sensostar Modbus auslesen:

          steht die weitere Kommunikation?

          ich sehe keine Informationen!

          wie gesagt nutze ich keine usätzlichen Komplikationen wie den RTU2ETH, aber in vergleichbaren Fällen gab es Informationen zu der Kommunikation auf der seriellen Seite.
          in etwa: gesendete und emfangene Pakete

          Wie du schreibst ist die Modbus-instanz auf grün.
          Also müsste das Problem auf der seriellen Seite liegen.

          Arum kommen dazu trotz mehrfacher Nachfrage keine Informationen?

          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

          1 Reply Last reply
          0
          • S Stephan a

            @homoran sagte in Sensostar Modbus auslesen:

            @homoran sagte in Sensostar Modbus auslesen:

            der Engelmann modbus Adapter.

            was ist das genau?
            Welche Konfiguration erwartet der?

            wurde imner noch nicht beantwortet.
            Was ist das und welche Funktion an welcher Stelle der gesamten Kette sitzt der?

            Das ist das Engelmannmodbusadaptermodul "Modbus-Modul RTU":
            https://www.zaehlershop.com/epages/61607473.sf/de_DE/?ObjectID=362300935

            Hier nochmal die Kofiguration vom Engelmannmodbusadaptermodul:
            Kommunikationsparameter: 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit)

            So ist die Kette aufgebaut:
            Engelmannzähler Sensostar mit eingebautem Modbusadaptermodul - Datenkabel A/B zum Waveshare to ETH Adapter - per LAN-Kabel zum pi mit laufendem iobrocker mit den Instanzen.

            P Offline
            P Offline
            peterfido
            wrote on last edited by peterfido
            #28

            @stephan-a Die Modbus RTU Verbindungen, die ich so nutze, haben als Parität EVEN.
            Screenshot_20250815_161408_Chrome.jpg

            Gruß

            Peterfido


            Proxmox auf Intel NUC12WSHi5
            ioBroker: Debian (VM)
            CCU: Debmatic (VM)
            Influx: Debian (VM)
            Grafana: Debian (VM)
            eBus: Debian (VM)
            Zigbee: Debian (VM) mit zigbee2mqtt

            S 1 Reply Last reply
            1
            • HomoranH Homoran

              @stephan-a was sagt das debug-log beim Starten der Instanz?

              HomoranH Do not disturb
              HomoranH Do not disturb
              Homoran
              Global Moderator Administrators
              wrote on last edited by
              #29

              @homoran sagte in Sensostar Modbus auslesen:

              @stephan-a was sagt das debug-log beim Starten der Instanz?

              hab ich bisher nicht gesehen!

              @stephan-a sagte in Sensostar Modbus auslesen:

              Der Registerwert im iobrocker ist "null"

              du hast ja auch kein Polling aktiviert!

              fang doch erstmal mit einem

              @konni sagte in Sensostar Modbus auslesen:

              Grundsätzlich kann ich mit dem Modbuscanner 35 Register auf einmal auslesen, aber nur von 30001 bis 30031

              an.
              Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

              kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

              der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

              S 1 Reply Last reply
              0
              • P peterfido

                @stephan-a Die Modbus RTU Verbindungen, die ich so nutze, haben als Parität EVEN.
                Screenshot_20250815_161408_Chrome.jpg

                S Offline
                S Offline
                Stephan a
                wrote on last edited by
                #30

                @peterfido sagte in Sensostar Modbus auslesen:

                @stephan-a Die Modbux RTU Verbindungen, die ich so nutze, haben als Parität EVEN.

                Mit EVEN bricht die TCP Verbindung ab. Habe es wieder zurück gestellt. Danke

                d7233f20-118f-4bde-97d6-798711bc228c-grafik.png

                Viele Grüße
                Stephan

                HomoranH 1 Reply Last reply
                0
                • HomoranH Homoran

                  @homoran sagte in Sensostar Modbus auslesen:

                  @stephan-a was sagt das debug-log beim Starten der Instanz?

                  hab ich bisher nicht gesehen!

                  @stephan-a sagte in Sensostar Modbus auslesen:

                  Der Registerwert im iobrocker ist "null"

                  du hast ja auch kein Polling aktiviert!

                  fang doch erstmal mit einem

                  @konni sagte in Sensostar Modbus auslesen:

                  Grundsätzlich kann ich mit dem Modbuscanner 35 Register auf einmal auslesen, aber nur von 30001 bis 30031

                  an.
                  Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                  S Offline
                  S Offline
                  Stephan a
                  wrote on last edited by Homoran
                  #31

                  @homoran sagte in Sensostar Modbus auslesen:

                  @homoran sagte in Sensostar Modbus auslesen:

                  @stephan-a was sagt das debug-log beim Starten der Instanz?

                  hab ich bisher nicht gesehen!

                  modbus.5
                  	2025-08-15 16:28:16.271	info	Connected to slave 192.168.10.172
                  modbus.5
                  	2025-08-15 16:28:15.753	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.4, js-controller: 7.0.6
                  modbus.5
                  	2025-08-15 16:28:08.792	info	terminating
                  modbus.5
                  	2025-08-15 16:28:08.515	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                  modbus.5
                  	2025-08-15 16:28:08.511	info	terminating
                  modbus.5
                  	2025-08-15 16:28:08.286	info	Got terminate signal TERMINATE_YOURSELF
                  

                  MOD-EDIT: Code in code-tags gesetzt!

                  @homoran sagte in Sensostar Modbus auslesen:

                  du hast ja auch kein Polling aktiviert!

                  Ok. Was und Wo?

                  Viele Grüße
                  Stephan

                  HomoranH 1 Reply Last reply
                  0
                  • S Stephan a

                    @homoran sagte in Sensostar Modbus auslesen:

                    @homoran sagte in Sensostar Modbus auslesen:

                    @stephan-a was sagt das debug-log beim Starten der Instanz?

                    hab ich bisher nicht gesehen!

                    modbus.5
                    	2025-08-15 16:28:16.271	info	Connected to slave 192.168.10.172
                    modbus.5
                    	2025-08-15 16:28:15.753	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.4, js-controller: 7.0.6
                    modbus.5
                    	2025-08-15 16:28:08.792	info	terminating
                    modbus.5
                    	2025-08-15 16:28:08.515	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                    modbus.5
                    	2025-08-15 16:28:08.511	info	terminating
                    modbus.5
                    	2025-08-15 16:28:08.286	info	Got terminate signal TERMINATE_YOURSELF
                    

                    MOD-EDIT: Code in code-tags gesetzt!

                    @homoran sagte in Sensostar Modbus auslesen:

                    du hast ja auch kein Polling aktiviert!

                    Ok. Was und Wo?

                    HomoranH Do not disturb
                    HomoranH Do not disturb
                    Homoran
                    Global Moderator Administrators
                    wrote on last edited by Homoran
                    #32

                    @stephan-a
                    Das ist kein debug-log!

                    siehe https://forum.iobroker.net/topic/51555/hinweise-für-gute-forenbeiträge/1

                    @stephan-a sagte in Sensostar Modbus auslesen:

                    Was und Wo?

                    erübrigt sich wahrscheinlich, wenn

                    @homoran sagte in Sensostar Modbus auslesen:

                    fang doch erstmal mit einem
                    @konni sagte in Sensostar Modbus auslesen:

                    Grundsätzlich kann ich mit dem Modbuscanner 35 Register auf einmal auslesen, aber nur von 30001 bis 30031

                    an.
                    Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                    1 Reply Last reply
                    0
                    • S Stephan a

                      @peterfido sagte in Sensostar Modbus auslesen:

                      @stephan-a Die Modbux RTU Verbindungen, die ich so nutze, haben als Parität EVEN.

                      Mit EVEN bricht die TCP Verbindung ab. Habe es wieder zurück gestellt. Danke

                      d7233f20-118f-4bde-97d6-798711bc228c-grafik.png

                      HomoranH Do not disturb
                      HomoranH Do not disturb
                      Homoran
                      Global Moderator Administrators
                      wrote on last edited by
                      #33

                      @stephan-a sagte in Sensostar Modbus auslesen:

                      Mit EVEN bricht die TCP Verbindung ab

                      ääähh???

                      wo hast du das verändert?
                      even gehört zu den seriellen Parametern.
                      Das hat nichts mit TCP zu tun!

                      Was stand denn in diesem Fall im debug-log?
                      das könnte uns möglicherweise weiterhelfen

                      kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                      der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                      S 1 Reply Last reply
                      0
                      • HomoranH Homoran

                        @stephan-a sagte in Sensostar Modbus auslesen:

                        Mit EVEN bricht die TCP Verbindung ab

                        ääähh???

                        wo hast du das verändert?
                        even gehört zu den seriellen Parametern.
                        Das hat nichts mit TCP zu tun!

                        Was stand denn in diesem Fall im debug-log?
                        das könnte uns möglicherweise weiterhelfen

                        S Offline
                        S Offline
                        Stephan a
                        wrote on last edited by
                        #34

                        @homoran
                        Mit even hat die Instanz beim ersten Start ca. 4 mal so lange benötigt um auf grün zu gehen.

                        Ich habe die ursprünglichen 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit wieder eingestellt.
                        Polling ist jetzt aktiviert.

                        Hier der Log vom Neustart der Instanz - erst auf grün dann auf:
                        1576267d-6076-43b5-82d7-1642b3731814-grafik.png

                        modbus.5
                        	2025-08-15 21:50:28.045	info	Disconnected from slave 192.168.10.172
                        modbus.5
                        	2025-08-15 21:50:28.044	debug	Closing client on purpose.
                        modbus.5
                        	2025-08-15 21:50:27.050	debug	Cleaning up request fifo.
                        modbus.5
                        	2025-08-15 21:50:27.049	debug	Clearing timeout of the current request.
                        modbus.5
                        	2025-08-15 21:50:27.048	debug	Socket closed with error
                        modbus.5
                        	2025-08-15 21:50:27.046	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":5000}
                        modbus.5
                        	2025-08-15 21:50:27.044	error	Client in error state.
                        modbus.5
                        	2025-08-15 21:50:27.043	error	Request timed out.
                        modbus.5
                        	2025-08-15 21:50:27.043	warn	Error: undefined
                        modbus.5
                        	2025-08-15 21:50:22.035	debug	[DevID_1/holdingRegs] Poll address 40001 - 2 registers
                        modbus.5
                        	2025-08-15 21:50:22.034	debug	Initialization of scale factors done!
                        modbus.5
                        	2025-08-15 21:50:22.031	debug	[DevID_1] Poll start ---------------------
                        modbus.5
                        	2025-08-15 21:50:22.029	info	Connected to slave 192.168.10.172
                        modbus.5
                        	2025-08-15 21:50:21.745	debug	Add holdingRegisters.40001_Energie: {"_id":"holdingRegisters.40001_Energie","type":"state","common":{"name":"","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40001,"deviceId":1,"type":"int32be","len":2,"offset":0,"factor":1,"poll":true}}
                        modbus.5
                        	2025-08-15 21:50:21.744	debug	Initialize Objects for holdingRegs: [{"_address":"40001","name":"Energie","description":"","unit":"","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":"","cw":"","isScale":"","address":40001,"deviceId":1,"id":"holdingRegisters.40001_Energie"}]
                        modbus.5
                        	2025-08-15 21:50:21.743	debug	Initialize Objects for inputRegs: []
                        modbus.5
                        	2025-08-15 21:50:21.741	debug	Initialize Objects for coils: []
                        modbus.5
                        	2025-08-15 21:50:21.740	debug	Initialize Objects for disInputs: []
                        modbus.5
                        	2025-08-15 21:50:21.504	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.4, js-controller: 7.0.6
                        modbus.5
                        	2025-08-15 21:50:21.118	debug	Plugin sentry Initialize Plugin (enabled=true)
                        modbus.5
                        	2025-08-15 21:50:14.761	info	terminating
                        modbus.5
                        	2025-08-15 21:50:14.386	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                        modbus.5
                        	2025-08-15 21:50:14.385	debug	Plugin sentry destroyed
                        modbus.5
                        	2025-08-15 21:50:14.383	info	terminating
                        modbus.5
                        	2025-08-15 21:50:14.255	debug	Closing client on purpose.
                        modbus.5
                        	2025-08-15 21:50:14.247	info	Got terminate signal TERMINATE_YOURSELF
                        

                        Hier noch das Register laut Engelmann:
                        7b1f5c4d-efe3-4b31-a126-a467a4018582-grafik.png

                        Die Anzahl der abzufragenden Register ist:
                        6087ee06-3beb-433e-8b9c-444526a16a69-grafik.png

                        09b9338f-e0a3-49a8-9a28-cfbaf0d5d38e-grafik.png

                        Viele Grüße
                        Stephan

                        HomoranH 1 Reply Last reply
                        0
                        • S Stephan a

                          @homoran
                          Mit even hat die Instanz beim ersten Start ca. 4 mal so lange benötigt um auf grün zu gehen.

                          Ich habe die ursprünglichen 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit wieder eingestellt.
                          Polling ist jetzt aktiviert.

                          Hier der Log vom Neustart der Instanz - erst auf grün dann auf:
                          1576267d-6076-43b5-82d7-1642b3731814-grafik.png

                          modbus.5
                          	2025-08-15 21:50:28.045	info	Disconnected from slave 192.168.10.172
                          modbus.5
                          	2025-08-15 21:50:28.044	debug	Closing client on purpose.
                          modbus.5
                          	2025-08-15 21:50:27.050	debug	Cleaning up request fifo.
                          modbus.5
                          	2025-08-15 21:50:27.049	debug	Clearing timeout of the current request.
                          modbus.5
                          	2025-08-15 21:50:27.048	debug	Socket closed with error
                          modbus.5
                          	2025-08-15 21:50:27.046	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":5000}
                          modbus.5
                          	2025-08-15 21:50:27.044	error	Client in error state.
                          modbus.5
                          	2025-08-15 21:50:27.043	error	Request timed out.
                          modbus.5
                          	2025-08-15 21:50:27.043	warn	Error: undefined
                          modbus.5
                          	2025-08-15 21:50:22.035	debug	[DevID_1/holdingRegs] Poll address 40001 - 2 registers
                          modbus.5
                          	2025-08-15 21:50:22.034	debug	Initialization of scale factors done!
                          modbus.5
                          	2025-08-15 21:50:22.031	debug	[DevID_1] Poll start ---------------------
                          modbus.5
                          	2025-08-15 21:50:22.029	info	Connected to slave 192.168.10.172
                          modbus.5
                          	2025-08-15 21:50:21.745	debug	Add holdingRegisters.40001_Energie: {"_id":"holdingRegisters.40001_Energie","type":"state","common":{"name":"","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40001,"deviceId":1,"type":"int32be","len":2,"offset":0,"factor":1,"poll":true}}
                          modbus.5
                          	2025-08-15 21:50:21.744	debug	Initialize Objects for holdingRegs: [{"_address":"40001","name":"Energie","description":"","unit":"","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":"","cw":"","isScale":"","address":40001,"deviceId":1,"id":"holdingRegisters.40001_Energie"}]
                          modbus.5
                          	2025-08-15 21:50:21.743	debug	Initialize Objects for inputRegs: []
                          modbus.5
                          	2025-08-15 21:50:21.741	debug	Initialize Objects for coils: []
                          modbus.5
                          	2025-08-15 21:50:21.740	debug	Initialize Objects for disInputs: []
                          modbus.5
                          	2025-08-15 21:50:21.504	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.4, js-controller: 7.0.6
                          modbus.5
                          	2025-08-15 21:50:21.118	debug	Plugin sentry Initialize Plugin (enabled=true)
                          modbus.5
                          	2025-08-15 21:50:14.761	info	terminating
                          modbus.5
                          	2025-08-15 21:50:14.386	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                          modbus.5
                          	2025-08-15 21:50:14.385	debug	Plugin sentry destroyed
                          modbus.5
                          	2025-08-15 21:50:14.383	info	terminating
                          modbus.5
                          	2025-08-15 21:50:14.255	debug	Closing client on purpose.
                          modbus.5
                          	2025-08-15 21:50:14.247	info	Got terminate signal TERMINATE_YOURSELF
                          

                          Hier noch das Register laut Engelmann:
                          7b1f5c4d-efe3-4b31-a126-a467a4018582-grafik.png

                          Die Anzahl der abzufragenden Register ist:
                          6087ee06-3beb-433e-8b9c-444526a16a69-grafik.png

                          09b9338f-e0a3-49a8-9a28-cfbaf0d5d38e-grafik.png

                          HomoranH Do not disturb
                          HomoranH Do not disturb
                          Homoran
                          Global Moderator Administrators
                          wrote on last edited by
                          #35

                          @stephan-a sagte in Sensostar Modbus auslesen:

                          warn Error: undefined

                          irgendwo klemmt es mit der Kommunikation des Endgeräts
                          an das Register kommt der ioBroker nicht ran

                          @stephan-a sagte in Sensostar Modbus auslesen:

                          Hier noch das Register laut Engelmann:

                          und warum machst du nicht was ich schreibe??

                          zum dritten Mal:

                          @homoran sagte in Sensostar Modbus auslesen:

                          fang doch erstmal mit einem
                          @konni sagte in Sensostar Modbus auslesen:

                          Grundsätzlich kann ich mit dem Modbuscanner 35 Register auf einmal auslesen, aber nur von 30001 bis 30031

                          an.
                          Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                          S 1 Reply Last reply
                          0
                          • HomoranH Homoran

                            @stephan-a sagte in Sensostar Modbus auslesen:

                            warn Error: undefined

                            irgendwo klemmt es mit der Kommunikation des Endgeräts
                            an das Register kommt der ioBroker nicht ran

                            @stephan-a sagte in Sensostar Modbus auslesen:

                            Hier noch das Register laut Engelmann:

                            und warum machst du nicht was ich schreibe??

                            zum dritten Mal:

                            @homoran sagte in Sensostar Modbus auslesen:

                            fang doch erstmal mit einem
                            @konni sagte in Sensostar Modbus auslesen:

                            Grundsätzlich kann ich mit dem Modbuscanner 35 Register auf einmal auslesen, aber nur von 30001 bis 30031

                            an.
                            Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                            S Offline
                            S Offline
                            Stephan a
                            wrote on last edited by
                            #36

                            @homoran

                            Ich habe das Holding Register 40001 gelöscht und das Input Register 30001 eingetragen.
                            Hier der Log mit Register 30001.

                            modbus.5
                            	2025-08-16 06:39:30.072	info	Disconnected from slave 192.168.10.172
                            modbus.5
                            	2025-08-16 06:39:30.071	debug	Closing client on purpose.
                            modbus.5
                            	2025-08-16 06:39:29.076	debug	Cleaning up request fifo.
                            modbus.5
                            	2025-08-16 06:39:29.075	debug	Clearing timeout of the current request.
                            modbus.5
                            	2025-08-16 06:39:29.074	debug	Socket closed with error
                            modbus.5
                            	2025-08-16 06:39:29.073	warn	[DevID_1] Poll error count: 2 code: {"err":"timeout","timeout":5000}
                            modbus.5
                            	2025-08-16 06:39:29.072	error	Client in error state.
                            modbus.5
                            	2025-08-16 06:39:29.071	error	Request timed out.
                            modbus.5
                            	2025-08-16 06:39:29.071	warn	Error: undefined
                            modbus.5
                            	2025-08-16 06:39:24.069	debug	[DevID_1/inputRegs] Poll address 30001 - 2 registers
                            modbus.5
                            	2025-08-16 06:39:24.068	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            	2025-08-16 06:39:24.067	info	Connected to slave 192.168.10.172
                            modbus.5
                            	2025-08-16 06:38:24.061	info	Disconnected from slave 192.168.10.172
                            modbus.5
                            	2025-08-16 06:38:24.060	debug	Closing client on purpose.
                            modbus.5
                            	2025-08-16 06:38:23.068	debug	Cleaning up request fifo.
                            modbus.5
                            	2025-08-16 06:38:23.067	debug	Clearing timeout of the current request.
                            modbus.5
                            	2025-08-16 06:38:23.066	debug	Socket closed with error
                            modbus.5
                            	2025-08-16 06:38:23.061	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":5000}
                            modbus.5
                            	2025-08-16 06:38:23.059	error	Client in error state.
                            modbus.5
                            	2025-08-16 06:38:23.059	error	Request timed out.
                            modbus.5
                            	2025-08-16 06:38:23.058	warn	Error: undefined
                            modbus.5
                            	2025-08-16 06:38:18.052	debug	[DevID_1/inputRegs] Poll address 30001 - 2 registers
                            modbus.5
                            	2025-08-16 06:38:18.051	debug	Initialization of scale factors done!
                            modbus.5
                            	2025-08-16 06:38:18.047	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            	2025-08-16 06:38:18.045	info	Connected to slave 192.168.10.172
                            modbus.5
                            	2025-08-16 06:38:16.111	debug	Remove old object modbus.5.holdingRegisters.40001_Energie
                            modbus.5
                            	2025-08-16 06:38:16.055	debug	Initialize Objects for holdingRegs: []
                            modbus.5
                            	2025-08-16 06:38:16.054	debug	Add inputRegisters.30001_Energie: {"_id":"inputRegisters.30001_Energie","type":"state","common":{"name":"","role":"level","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":30001,"deviceId":1,"type":"int32be","len":2,"offset":0,"factor":1}}
                            modbus.5
                            	2025-08-16 06:38:16.052	debug	Initialize Objects for inputRegs: [{"_address":"30001","name":"Energie","description":"","unit":"","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":30001,"deviceId":1,"id":"inputRegisters.30001_Energie"}]
                            modbus.5
                            	2025-08-16 06:38:16.050	debug	Initialize Objects for coils: []
                            modbus.5
                            	2025-08-16 06:38:16.049	debug	Initialize Objects for disInputs: []
                            modbus.5
                            	2025-08-16 06:38:14.892	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.4, js-controller: 7.0.6
                            modbus.5
                            	2025-08-16 06:38:11.713	debug	Plugin sentry Initialize Plugin (enabled=true)
                            modbus.5
                            	2025-08-16 06:37:54.455	info	terminating
                            modbus.5
                            	2025-08-16 06:37:54.234	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                            modbus.5
                            	2025-08-16 06:37:54.233	debug	Plugin sentry destroyed
                            modbus.5
                            	2025-08-16 06:37:54.232	info	terminating
                            modbus.5
                            	2025-08-16 06:37:53.947	debug	Closing client on purpose.
                            modbus.5
                            	2025-08-16 06:37:53.942	info	Got terminate signal TERMINATE_YOURSELF
                            

                            0c3c8275-d16f-4a78-a671-28831911e53e-grafik.png

                            @homoran sagte in Sensostar Modbus auslesen:

                            @homoran sagte in Sensostar Modbus auslesen:

                            Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                            Steuern will ich den Zähler auch nicht, sondern nur auslesen.

                            Viele Grüße
                            Stephan

                            1 Reply Last reply
                            0
                            • P Offline
                              P Offline
                              peterfido
                              wrote on last edited by
                              #37

                              @stephan-a sagte in Sensostar Modbus auslesen:

                              @peterfido sagte in Sensostar Modbus auslesen:

                              @stephan-a Die Modbux RTU Verbindungen, die ich so nutze, haben als Parität EVEN.
                              

                              Mit EVEN bricht die TCP Verbindung ab. Habe es wieder zurück gestellt. Danke

                              d7233f20-118f-4bde-97d6-798711bc228c-grafik.png

                              Was ist denn das für eine Destination IP?

                              Gruß

                              Peterfido


                              Proxmox auf Intel NUC12WSHi5
                              ioBroker: Debian (VM)
                              CCU: Debmatic (VM)
                              Influx: Debian (VM)
                              Grafana: Debian (VM)
                              eBus: Debian (VM)
                              Zigbee: Debian (VM) mit zigbee2mqtt

                              S HomoranH 3 Replies Last reply
                              0
                              • P peterfido

                                @stephan-a sagte in Sensostar Modbus auslesen:

                                @peterfido sagte in Sensostar Modbus auslesen:

                                @stephan-a Die Modbux RTU Verbindungen, die ich so nutze, haben als Parität EVEN.
                                

                                Mit EVEN bricht die TCP Verbindung ab. Habe es wieder zurück gestellt. Danke

                                d7233f20-118f-4bde-97d6-798711bc228c-grafik.png

                                Was ist denn das für eine Destination IP?

                                S Offline
                                S Offline
                                Stephan a
                                wrote on last edited by
                                #38

                                @peterfido

                                Beide IP's kamen automatisch. Hier habe ich nichts selbst eingetragen.

                                Viele Grüße
                                Stephan

                                1 Reply Last reply
                                0
                                • P peterfido

                                  @stephan-a sagte in Sensostar Modbus auslesen:

                                  @peterfido sagte in Sensostar Modbus auslesen:

                                  @stephan-a Die Modbux RTU Verbindungen, die ich so nutze, haben als Parität EVEN.
                                  

                                  Mit EVEN bricht die TCP Verbindung ab. Habe es wieder zurück gestellt. Danke

                                  d7233f20-118f-4bde-97d6-798711bc228c-grafik.png

                                  Was ist denn das für eine Destination IP?

                                  HomoranH Do not disturb
                                  HomoranH Do not disturb
                                  Homoran
                                  Global Moderator Administrators
                                  wrote on last edited by Homoran
                                  #39

                                  @peterfido sagte in Sensostar Modbus auslesen:

                                  Was ist denn das für eine Destination IP?

                                  das könnte die IP sein unter der der Waveshare erreichbar ist.

                                  EDIT: blödsinn, das ist dev ID

                                  @Stephan-a
                                  Dein Problem liegt sehr wahrscheinlich in der seriellen Strecke!
                                  nicht im ioBroker <->Waveshare per Ethernet

                                  Was ist da nicht established?
                                  und vorauf beziehen sich die RX und TX mit 0
                                  da klemmt die Kommunikation

                                  welche IPs kamen automatisch??
                                  und wer ist ...1.3?

                                  die 180.154.125.252 gehört zu china telecom

                                  kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                  der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                  1 Reply Last reply
                                  0
                                  • P peterfido

                                    @stephan-a sagte in Sensostar Modbus auslesen:

                                    @peterfido sagte in Sensostar Modbus auslesen:

                                    @stephan-a Die Modbux RTU Verbindungen, die ich so nutze, haben als Parität EVEN.
                                    

                                    Mit EVEN bricht die TCP Verbindung ab. Habe es wieder zurück gestellt. Danke

                                    d7233f20-118f-4bde-97d6-798711bc228c-grafik.png

                                    Was ist denn das für eine Destination IP?

                                    HomoranH Do not disturb
                                    HomoranH Do not disturb
                                    Homoran
                                    Global Moderator Administrators
                                    wrote on last edited by
                                    #40

                                    @peterfido wenn ich das hier

                                    https://www.waveshare.com/wiki/RS485_TO_ETH_(B)

                                    richtig interpretiere werden dest id und dest port nur benötigt, wenn der RTU2ETH der Master und ioBroker der Slave wäre

                                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                    P 1 Reply Last reply
                                    0
                                    • HomoranH Homoran

                                      @peterfido wenn ich das hier

                                      https://www.waveshare.com/wiki/RS485_TO_ETH_(B)

                                      richtig interpretiere werden dest id und dest port nur benötigt, wenn der RTU2ETH der Master und ioBroker der Slave wäre

                                      P Offline
                                      P Offline
                                      peterfido
                                      wrote on last edited by
                                      #41

                                      @homoran

                                      In der Anleitung steht unter Anderm:

                                      • externes Netzteil zwischen 12-24V muss immer anschlossen sein
                                        (Achtung, die Änderung der Auslesezeit von 600 Sekunden auf 120 Sekunden muss trotzdem per Befehl an das Gerät gemeldet werden)
                                      

                                      Was wird da von zehn auf zwei Minuten parametriert? Wie oft das Modbus die Daten vom Zähler holt / aktualisiert?

                                      Die Standard-Slave ID ist laut Anleitung 1. Welche ID hat der Modbus Adapter?

                                      Gruß

                                      Peterfido


                                      Proxmox auf Intel NUC12WSHi5
                                      ioBroker: Debian (VM)
                                      CCU: Debmatic (VM)
                                      Influx: Debian (VM)
                                      Grafana: Debian (VM)
                                      eBus: Debian (VM)
                                      Zigbee: Debian (VM) mit zigbee2mqtt

                                      S 1 Reply Last reply
                                      0
                                      • P peterfido

                                        @homoran

                                        In der Anleitung steht unter Anderm:

                                        • externes Netzteil zwischen 12-24V muss immer anschlossen sein
                                          (Achtung, die Änderung der Auslesezeit von 600 Sekunden auf 120 Sekunden muss trotzdem per Befehl an das Gerät gemeldet werden)
                                        

                                        Was wird da von zehn auf zwei Minuten parametriert? Wie oft das Modbus die Daten vom Zähler holt / aktualisiert?

                                        Die Standard-Slave ID ist laut Anleitung 1. Welche ID hat der Modbus Adapter?

                                        S Offline
                                        S Offline
                                        Stephan a
                                        wrote on last edited by Stephan a
                                        #42

                                        @peterfido

                                        Der Engelmann Zähler läuft im Auslieferzustand mit Batterie. Die Auslesezeit vom Zähler ist 600 Sekunden.
                                        Es kann alternativ ein externens Netzgerät angeschlossen werden. Dann kann die Auslesezeit auf 120 Sekunden geändert werden.

                                        Die Save ID ist 1:
                                        d901b3f6-7621-446f-b5ec-316e81331eeb-grafik.png

                                        Viele Grüße
                                        Stephan

                                        P 1 Reply Last reply
                                        0
                                        • S Stephan a

                                          @peterfido

                                          Der Engelmann Zähler läuft im Auslieferzustand mit Batterie. Die Auslesezeit vom Zähler ist 600 Sekunden.
                                          Es kann alternativ ein externens Netzgerät angeschlossen werden. Dann kann die Auslesezeit auf 120 Sekunden geändert werden.

                                          Die Save ID ist 1:
                                          d901b3f6-7621-446f-b5ec-316e81331eeb-grafik.png

                                          P Offline
                                          P Offline
                                          peterfido
                                          wrote on last edited by
                                          #43

                                          @stephan-a

                                          Somit bringen kürzere Intervalle als 120 Sekunden keinen Vorteil. Das muss aber erstmal von 600 Sekunden umparametriert werden. Wenn die Kommunikation hakt, wird der noch auf 10 Minuten stehen.

                                          Master und Slave dürfen nicht die selbe ID haben.

                                          Gruß

                                          Peterfido


                                          Proxmox auf Intel NUC12WSHi5
                                          ioBroker: Debian (VM)
                                          CCU: Debmatic (VM)
                                          Influx: Debian (VM)
                                          Grafana: Debian (VM)
                                          eBus: Debian (VM)
                                          Zigbee: Debian (VM) mit zigbee2mqtt

                                          S 1 Reply Last reply
                                          0
                                          Reply
                                          • Reply as topic
                                          Log in to reply
                                          • Oldest to Newest
                                          • Newest to Oldest
                                          • Most Votes


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          132

                                          Online

                                          32.4k

                                          Users

                                          81.3k

                                          Topics

                                          1.3m

                                          Posts
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Login

                                          • Don't have an account? Register

                                          • Login or register to search.
                                          • First post
                                            Last post
                                          0
                                          • Recent
                                          • Tags
                                          • Unread 0
                                          • Categories
                                          • Unreplied
                                          • Popular
                                          • GitHub
                                          • Docu
                                          • Hilfe