    Sensostar Modbus auslesen

    This topic has been deleted. Only users with topic management privileges can see it.
    • S
      Stephan a @Homoran last edited by

      Danke an Alle die mich unterstützen.

      Mein Probem ist, dass die im iobrocker angezeiten Werte alle "null" sind:
      66bcb54e-45f2-4b1d-ba31-a49f5dc02e90-grafik.png

      Die Instanz ist aber grün:
      d8189393-12e4-4001-8d9c-3db6c957fb45-grafik.png

      Die Abfrageanzahlg steht auf "1".

      @peterfido
      Die Wartezeiten im Adaper sind:
      d4960dda-e663-405d-9096-dfd35e480263-grafik.png

      Wie sind deine Verzögerungswerte?

      Homoran 2 Replies Last reply Reply Quote 0
      • Homoran
        Homoran Global Moderator Administrators @Stephan a last edited by

        @stephan-a was sagt das debug-log beim Starten der Instanz?

        Homoran 1 Reply Last reply Reply Quote 0
        • Homoran
          Homoran Global Moderator Administrators @Stephan a last edited by

          @stephan-a sagte in Sensostar Modbus auslesen:

          der Engelmann modbus Adapter.

          was ist das genau?
          Welche Konfiguration erwartet der?

          1 Reply Last reply Reply Quote 0
          • Homoran
            Homoran Global Moderator Administrators @Stephan a last edited by Homoran

            @stephan-a Lass dir doch nicht alles aus der Nase ziehen!
            Gib doch mal zusammenhängend alle notwendigen Informationen:

            Du hast also ein Gerät (Wärmezähler??) das über Modbus auslesbar sein soll??
            Daran hängt ein Adapter??
            Daran hängt ein Waveshare RTU2ETH??
            daran hängt dein ioBroker Server??

            Oder andersrum
            Dein iobroker Server baut die Verbindung zum Waveshare auf.

            und dann???
            steht die weitere Kommunikation?

            ist in dem Waveshare die serielle Seite aktiv??
            korrekt konfiguriert???

            S 1 Reply Last reply Reply Quote 0
            • S
              Stephan a @Homoran last edited by

              @homoran - gut, ich mache keine neuen Thread auf und bleibe hier.

              HIer die Ausgangslage:

              @homoran sagte in Sensostar Modbus auslesen:

              Du hast also ein Gerät (Wärmezähler??) das über Modbus auslesbar sein soll??

              Ja, ich habe 2 Sensostar U und 2 modbus Adapter.

              @homoran sagte in Sensostar Modbus auslesen:

              Daran hängt ein Adapter??
              Daran hängt ein Waveshare ETH2RS485??
              daran hängt dein ioBroker Server??

              Ich habe einen 2 Kanal Waveshare to ETH Adapter.
              4 laufende modbus Instanzen sind auf dem 1 Kanal. Die laufen ohne Probleme.
              Am 2. Kanal Waveshare ist ein Engelmann modbus Adapter angeschlossen. Der zweite Zähler ist noch ohne Adapter.
              Über modbus Instanzen kommen die Werte vom Waveschare in den iobocker.

              @homoran sagte in Sensostar Modbus auslesen:

              und dann???
              steht die weitere Kommunikation?
              ist in dem Waveshare die serielle Seite aktiv??
              korrekt konfiguriert???

              Die Instanzen im iobroker laufen und sind alle grün.
              HIer die Einstellungen im Waveshare:
              052728cb-c2af-4726-979e-452cda4f58fe-grafik.png

              Der Engelmannmodbus hat:
              Kommunikationsparameter 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit)

              Bei vir-com sind Daten:
              54ecfeb1-dfec-41b5-9b36-2b076d0ae978-grafik.png

              Der 2. Kanal die RXD steht auf "1". Also werden keine Daten empfangen.

              Der Adapter ist in den Grundeinstellunen, nur die Anzahl der abzurufenden Register sind auf 1 gesetzt:
              1c13484a-3da5-4fe0-a64d-f2035282d61c-grafik.png
              c1e44349-edf3-4d5d-8b68-caf2d82d7111-grafik.png

              Eine Änderung der Verbindungsparameter von TCP auf TCP OVER RTU hat keine Veränderung gebracht.
              Der Registerwert im iobrocker ist "null", er ist kurz grün und geht dann auf rot.

              HIer noch die vir-com Einstellungen:
              d6885b41-a0a0-4381-9d7b-9eaa8a242b77-grafik.png
              cfbed71c-331d-4999-a493-0d6da8e24e43-grafik.png

              Das Problem sind die Werte vom Engelmannzähler Modbusmodul, dass scheinbar keine Daten liefert.
              Was ich nicht abfragen kann, ist die Modbusadresse vom Modul. Hier habe ich die ID 1 eingetragen und auch 2 versucht, ohne Äderung der angezeigten Werte.

              So das ist der aktuelle Stand.

              Homoran 1 Reply Last reply Reply Quote 0
              • Homoran
                Homoran Global Moderator Administrators @Stephan a last edited by

                @stephan-a sagte in Sensostar Modbus auslesen:

                Daran hängt ein Adapter??

                die Frage

                @homoran sagte in Sensostar Modbus auslesen:

                @stephan-a sagte in Sensostar Modbus auslesen:

                der Engelmann modbus Adapter.

                was ist das genau?
                Welche Konfiguration erwartet der?

                wurde imner noch nicht beantwortet.

                Was ist das und welche Funktion an welcher Stelle der gesamten Kette sitzt der?

                S 1 Reply Last reply Reply Quote 0
                • S
                  Stephan a @Homoran last edited by

                  @homoran sagte in Sensostar Modbus auslesen:

                  @homoran sagte in Sensostar Modbus auslesen:

                  der Engelmann modbus Adapter.

                  was ist das genau?
                  Welche Konfiguration erwartet der?

                  wurde imner noch nicht beantwortet.
                  Was ist das und welche Funktion an welcher Stelle der gesamten Kette sitzt der?

                  Das ist das Engelmannmodbusadaptermodul "Modbus-Modul RTU":
                  https://www.zaehlershop.com/epages/61607473.sf/de_DE/?ObjectID=362300935

                  Hier nochmal die Kofiguration vom Engelmannmodbusadaptermodul:
                  Kommunikationsparameter: 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit)

                  So ist die Kette aufgebaut:
                  Engelmannzähler Sensostar mit eingebautem Modbusadaptermodul - Datenkabel A/B zum Waveshare to ETH Adapter - per LAN-Kabel zum pi mit laufendem iobrocker mit den Instanzen.

                  Homoran P 2 Replies Last reply Reply Quote 0
                  • Homoran
                    Homoran Global Moderator Administrators @Stephan a last edited by

                    @stephan-a sagte in Sensostar Modbus auslesen:

                    Engelmannzähler Sensostar mit eingebautem Modbusadaptermodul - Datenkabel A/B zum Waveshare to ETH Adapter

                    @homoran sagte in Sensostar Modbus auslesen:

                    steht die weitere Kommunikation?

                    ich sehe keine Informationen!

                    wie gesagt nutze ich keine usätzlichen Komplikationen wie den RTU2ETH, aber in vergleichbaren Fällen gab es Informationen zu der Kommunikation auf der seriellen Seite.
                    in etwa: gesendete und emfangene Pakete

                    Wie du schreibst ist die Modbus-instanz auf grün.
                    Also müsste das Problem auf der seriellen Seite liegen.

                    Arum kommen dazu trotz mehrfacher Nachfrage keine Informationen?

                    1 Reply Last reply Reply Quote 0
                    • P
                      peterfido @Stephan a last edited by peterfido

                      @stephan-a Die Modbus RTU Verbindungen, die ich so nutze, haben als Parität EVEN.
                      Screenshot_20250815_161408_Chrome.jpg

                      S 1 Reply Last reply Reply Quote 1
                      • Homoran
                        Homoran Global Moderator Administrators @Homoran last edited by

                        @homoran sagte in Sensostar Modbus auslesen:

                        @stephan-a was sagt das debug-log beim Starten der Instanz?

                        hab ich bisher nicht gesehen!

                        @stephan-a sagte in Sensostar Modbus auslesen:

                        Der Registerwert im iobrocker ist "null"

                        du hast ja auch kein Polling aktiviert!

                        fang doch erstmal mit einem

                        @konni sagte in Sensostar Modbus auslesen:

                        Grundsätzlich kann ich mit dem Modbuscanner 35 Register auf einmal auslesen, aber nur von 30001 bis 30031

                        an.
                        Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                        S 1 Reply Last reply Reply Quote 0
                        • S
                          Stephan a @peterfido last edited by

                          @peterfido sagte in Sensostar Modbus auslesen:

                          @stephan-a Die Modbux RTU Verbindungen, die ich so nutze, haben als Parität EVEN.

                          Mit EVEN bricht die TCP Verbindung ab. Habe es wieder zurück gestellt. Danke

                          d7233f20-118f-4bde-97d6-798711bc228c-grafik.png

                          Homoran 1 Reply Last reply Reply Quote 0
                          • S
                            Stephan a @Homoran last edited by Homoran

                            @homoran sagte in Sensostar Modbus auslesen:

                            @homoran sagte in Sensostar Modbus auslesen:

                            @stephan-a was sagt das debug-log beim Starten der Instanz?

                            hab ich bisher nicht gesehen!

                            modbus.5
                            	2025-08-15 16:28:16.271	info	Connected to slave 192.168.10.172
                            modbus.5
                            	2025-08-15 16:28:15.753	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.4, js-controller: 7.0.6
                            modbus.5
                            	2025-08-15 16:28:08.792	info	terminating
                            modbus.5
                            	2025-08-15 16:28:08.515	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                            modbus.5
                            	2025-08-15 16:28:08.511	info	terminating
                            modbus.5
                            	2025-08-15 16:28:08.286	info	Got terminate signal TERMINATE_YOURSELF
                            

                            MOD-EDIT: Code in code-tags gesetzt!

                            @homoran sagte in Sensostar Modbus auslesen:

                            du hast ja auch kein Polling aktiviert!

                            Ok. Was und Wo?

                            Homoran 1 Reply Last reply Reply Quote 0
                            • Homoran
                              Homoran Global Moderator Administrators @Stephan a last edited by Homoran

                              @stephan-a
                              Das ist kein debug-log!

                              siehe https://forum.iobroker.net/topic/51555/hinweise-für-gute-forenbeiträge/1

                              @stephan-a sagte in Sensostar Modbus auslesen:

                              Was und Wo?

                              erübrigt sich wahrscheinlich, wenn

                              @homoran sagte in Sensostar Modbus auslesen:

                              fang doch erstmal mit einem
                              @konni sagte in Sensostar Modbus auslesen:

                              Grundsätzlich kann ich mit dem Modbuscanner 35 Register auf einmal auslesen, aber nur von 30001 bis 30031

                              an.
                              Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                              1 Reply Last reply Reply Quote 0
                              • Homoran
                                Homoran Global Moderator Administrators @Stephan a last edited by

                                @stephan-a sagte in Sensostar Modbus auslesen:

                                Mit EVEN bricht die TCP Verbindung ab

                                ääähh???

                                wo hast du das verändert?
                                even gehört zu den seriellen Parametern.
                                Das hat nichts mit TCP zu tun!

                                Was stand denn in diesem Fall im debug-log?
                                das könnte uns möglicherweise weiterhelfen

                                S 1 Reply Last reply Reply Quote 0
                                • S
                                  Stephan a @Homoran last edited by

                                  @homoran
                                  Mit even hat die Instanz beim ersten Start ca. 4 mal so lange benötigt um auf grün zu gehen.

                                  Ich habe die ursprünglichen 9600 bps, 8N1 Datenformat (8 Datenbits, Non-Parity, 1 Stoppbit wieder eingestellt.
                                  Polling ist jetzt aktiviert.

                                  Hier der Log vom Neustart der Instanz - erst auf grün dann auf:
                                  1576267d-6076-43b5-82d7-1642b3731814-grafik.png

                                  modbus.5
                                  	2025-08-15 21:50:28.045	info	Disconnected from slave 192.168.10.172
                                  modbus.5
                                  	2025-08-15 21:50:28.044	debug	Closing client on purpose.
                                  modbus.5
                                  	2025-08-15 21:50:27.050	debug	Cleaning up request fifo.
                                  modbus.5
                                  	2025-08-15 21:50:27.049	debug	Clearing timeout of the current request.
                                  modbus.5
                                  	2025-08-15 21:50:27.048	debug	Socket closed with error
                                  modbus.5
                                  	2025-08-15 21:50:27.046	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":5000}
                                  modbus.5
                                  	2025-08-15 21:50:27.044	error	Client in error state.
                                  modbus.5
                                  	2025-08-15 21:50:27.043	error	Request timed out.
                                  modbus.5
                                  	2025-08-15 21:50:27.043	warn	Error: undefined
                                  modbus.5
                                  	2025-08-15 21:50:22.035	debug	[DevID_1/holdingRegs] Poll address 40001 - 2 registers
                                  modbus.5
                                  	2025-08-15 21:50:22.034	debug	Initialization of scale factors done!
                                  modbus.5
                                  	2025-08-15 21:50:22.031	debug	[DevID_1] Poll start ---------------------
                                  modbus.5
                                  	2025-08-15 21:50:22.029	info	Connected to slave 192.168.10.172
                                  modbus.5
                                  	2025-08-15 21:50:21.745	debug	Add holdingRegisters.40001_Energie: {"_id":"holdingRegisters.40001_Energie","type":"state","common":{"name":"","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40001,"deviceId":1,"type":"int32be","len":2,"offset":0,"factor":1,"poll":true}}
                                  modbus.5
                                  	2025-08-15 21:50:21.744	debug	Initialize Objects for holdingRegs: [{"_address":"40001","name":"Energie","description":"","unit":"","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":"","cw":"","isScale":"","address":40001,"deviceId":1,"id":"holdingRegisters.40001_Energie"}]
                                  modbus.5
                                  	2025-08-15 21:50:21.743	debug	Initialize Objects for inputRegs: []
                                  modbus.5
                                  	2025-08-15 21:50:21.741	debug	Initialize Objects for coils: []
                                  modbus.5
                                  	2025-08-15 21:50:21.740	debug	Initialize Objects for disInputs: []
                                  modbus.5
                                  	2025-08-15 21:50:21.504	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.4, js-controller: 7.0.6
                                  modbus.5
                                  	2025-08-15 21:50:21.118	debug	Plugin sentry Initialize Plugin (enabled=true)
                                  modbus.5
                                  	2025-08-15 21:50:14.761	info	terminating
                                  modbus.5
                                  	2025-08-15 21:50:14.386	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                  modbus.5
                                  	2025-08-15 21:50:14.385	debug	Plugin sentry destroyed
                                  modbus.5
                                  	2025-08-15 21:50:14.383	info	terminating
                                  modbus.5
                                  	2025-08-15 21:50:14.255	debug	Closing client on purpose.
                                  modbus.5
                                  	2025-08-15 21:50:14.247	info	Got terminate signal TERMINATE_YOURSELF
                                  

                                  Hier noch das Register laut Engelmann:
                                  7b1f5c4d-efe3-4b31-a126-a467a4018582-grafik.png

                                  Die Anzahl der abzufragenden Register ist:
                                  6087ee06-3beb-433e-8b9c-444526a16a69-grafik.png

                                  09b9338f-e0a3-49a8-9a28-cfbaf0d5d38e-grafik.png

                                  Homoran 1 Reply Last reply Reply Quote 0
                                  • Homoran
                                    Homoran Global Moderator Administrators @Stephan a last edited by

                                    @stephan-a sagte in Sensostar Modbus auslesen:

                                    warn Error: undefined

                                    irgendwo klemmt es mit der Kommunikation des Endgeräts
                                    an das Register kommt der ioBroker nicht ran

                                    @stephan-a sagte in Sensostar Modbus auslesen:

                                    Hier noch das Register laut Engelmann:

                                    und warum machst du nicht was ich schreibe??

                                    zum dritten Mal:

                                    @homoran sagte in Sensostar Modbus auslesen:

                                    fang doch erstmal mit einem
                                    @konni sagte in Sensostar Modbus auslesen:

                                    Grundsätzlich kann ich mit dem Modbuscanner 35 Register auf einmal auslesen, aber nur von 30001 bis 30031

                                    an.
                                    Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                                    S 1 Reply Last reply Reply Quote 0
                                    • S
                                      Stephan a @Homoran last edited by

                                      @homoran

                                      Ich habe das Holding Register 40001 gelöscht und das Input Register 30001 eingetragen.
                                      Hier der Log mit Register 30001.

                                      modbus.5
                                      	2025-08-16 06:39:30.072	info	Disconnected from slave 192.168.10.172
                                      modbus.5
                                      	2025-08-16 06:39:30.071	debug	Closing client on purpose.
                                      modbus.5
                                      	2025-08-16 06:39:29.076	debug	Cleaning up request fifo.
                                      modbus.5
                                      	2025-08-16 06:39:29.075	debug	Clearing timeout of the current request.
                                      modbus.5
                                      	2025-08-16 06:39:29.074	debug	Socket closed with error
                                      modbus.5
                                      	2025-08-16 06:39:29.073	warn	[DevID_1] Poll error count: 2 code: {"err":"timeout","timeout":5000}
                                      modbus.5
                                      	2025-08-16 06:39:29.072	error	Client in error state.
                                      modbus.5
                                      	2025-08-16 06:39:29.071	error	Request timed out.
                                      modbus.5
                                      	2025-08-16 06:39:29.071	warn	Error: undefined
                                      modbus.5
                                      	2025-08-16 06:39:24.069	debug	[DevID_1/inputRegs] Poll address 30001 - 2 registers
                                      modbus.5
                                      	2025-08-16 06:39:24.068	debug	[DevID_1] Poll start ---------------------
                                      modbus.5
                                      	2025-08-16 06:39:24.067	info	Connected to slave 192.168.10.172
                                      modbus.5
                                      	2025-08-16 06:38:24.061	info	Disconnected from slave 192.168.10.172
                                      modbus.5
                                      	2025-08-16 06:38:24.060	debug	Closing client on purpose.
                                      modbus.5
                                      	2025-08-16 06:38:23.068	debug	Cleaning up request fifo.
                                      modbus.5
                                      	2025-08-16 06:38:23.067	debug	Clearing timeout of the current request.
                                      modbus.5
                                      	2025-08-16 06:38:23.066	debug	Socket closed with error
                                      modbus.5
                                      	2025-08-16 06:38:23.061	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":5000}
                                      modbus.5
                                      	2025-08-16 06:38:23.059	error	Client in error state.
                                      modbus.5
                                      	2025-08-16 06:38:23.059	error	Request timed out.
                                      modbus.5
                                      	2025-08-16 06:38:23.058	warn	Error: undefined
                                      modbus.5
                                      	2025-08-16 06:38:18.052	debug	[DevID_1/inputRegs] Poll address 30001 - 2 registers
                                      modbus.5
                                      	2025-08-16 06:38:18.051	debug	Initialization of scale factors done!
                                      modbus.5
                                      	2025-08-16 06:38:18.047	debug	[DevID_1] Poll start ---------------------
                                      modbus.5
                                      	2025-08-16 06:38:18.045	info	Connected to slave 192.168.10.172
                                      modbus.5
                                      	2025-08-16 06:38:16.111	debug	Remove old object modbus.5.holdingRegisters.40001_Energie
                                      modbus.5
                                      	2025-08-16 06:38:16.055	debug	Initialize Objects for holdingRegs: []
                                      modbus.5
                                      	2025-08-16 06:38:16.054	debug	Add inputRegisters.30001_Energie: {"_id":"inputRegisters.30001_Energie","type":"state","common":{"name":"","role":"level","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":30001,"deviceId":1,"type":"int32be","len":2,"offset":0,"factor":1}}
                                      modbus.5
                                      	2025-08-16 06:38:16.052	debug	Initialize Objects for inputRegs: [{"_address":"30001","name":"Energie","description":"","unit":"","type":"int32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":30001,"deviceId":1,"id":"inputRegisters.30001_Energie"}]
                                      modbus.5
                                      	2025-08-16 06:38:16.050	debug	Initialize Objects for coils: []
                                      modbus.5
                                      	2025-08-16 06:38:16.049	debug	Initialize Objects for disInputs: []
                                      modbus.5
                                      	2025-08-16 06:38:14.892	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.4, js-controller: 7.0.6
                                      modbus.5
                                      	2025-08-16 06:38:11.713	debug	Plugin sentry Initialize Plugin (enabled=true)
                                      modbus.5
                                      	2025-08-16 06:37:54.455	info	terminating
                                      modbus.5
                                      	2025-08-16 06:37:54.234	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                      modbus.5
                                      	2025-08-16 06:37:54.233	debug	Plugin sentry destroyed
                                      modbus.5
                                      	2025-08-16 06:37:54.232	info	terminating
                                      modbus.5
                                      	2025-08-16 06:37:53.947	debug	Closing client on purpose.
                                      modbus.5
                                      	2025-08-16 06:37:53.942	info	Got terminate signal TERMINATE_YOURSELF
                                      

                                      0c3c8275-d16f-4a78-a671-28831911e53e-grafik.png

                                      @homoran sagte in Sensostar Modbus auslesen:

                                      @homoran sagte in Sensostar Modbus auslesen:

                                      Ich glaube sowieso nicht, dass es bei einem Zähler viel zu steuern gibt.

                                      Steuern will ich den Zähler auch nicht, sondern nur auslesen.

                                      1 Reply Last reply Reply Quote 0
                                      • P
                                        peterfido last edited by

                                        @stephan-a sagte in Sensostar Modbus auslesen:

                                        @peterfido sagte in Sensostar Modbus auslesen:

                                        @stephan-a Die Modbux RTU Verbindungen, die ich so nutze, haben als Parität EVEN.
                                        

                                        Mit EVEN bricht die TCP Verbindung ab. Habe es wieder zurück gestellt. Danke

                                        d7233f20-118f-4bde-97d6-798711bc228c-grafik.png

                                        Was ist denn das für eine Destination IP?

                                        S Homoran 3 Replies Last reply Reply Quote 0
                                        • S
                                          Stephan a @peterfido last edited by

                                          @peterfido

                                          Beide IP's kamen automatisch. Hier habe ich nichts selbst eingetragen.

                                          1 Reply Last reply Reply Quote 0
                                          • Homoran
                                            Homoran Global Moderator Administrators @peterfido last edited by Homoran

                                            @peterfido sagte in Sensostar Modbus auslesen:

                                            Was ist denn das für eine Destination IP?

                                            das könnte die IP sein unter der der Waveshare erreichbar ist.

                                            EDIT: blödsinn, das ist dev ID

                                            @Stephan-a
                                            Dein Problem liegt sehr wahrscheinlich in der seriellen Strecke!
                                            nicht im ioBroker <->Waveshare per Ethernet

                                            Was ist da nicht established?
                                            und vorauf beziehen sich die RX und TX mit 0
                                            da klemmt die Kommunikation

                                            welche IPs kamen automatisch??
                                            und wer ist ...1.3?

                                            die 180.154.125.252 gehört zu china telecom

                                            1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            841
                                            Online

                                            32.0k
                                            Users

                                            80.4k
                                            Topics

                                            1.3m
                                            Posts

                                            6
                                            76
                                            949
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo