  4. (gelöst)(Frage) ModubusTCP Adapter ?

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.8k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.4k

(gelöst)(Frage) ModubusTCP Adapter ?

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
57 Beiträge 5 Kommentatoren 7.0k Aufrufe 4 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • HumidorH Humidor

    @wendy2702 super Danke!!
    denke es hat funktioniert!
    Bildschirmfoto 2021-02-13 um 10.08.29.png

    bin gespannt!

    YESSSS!!!
    Bildschirmfoto 2021-02-13 um 10.10.02.png :+1: :grin: :hugging_face: :left-facing_fist:

    wendy2702W Offline
    wendy2702W Offline
    wendy2702
    schrieb am zuletzt editiert von wendy2702
    #15

    @humidor sagte in (Frage) ModubusTCP Adapter ?:

    @wendy2702 super Danke!!
    denke es hat funktioniert!

    Dann setze bitte vor dem Titel im ersten Beitrag ein [Gelöst]

    SOrry, hatte den SolarEdge vergessen.

    Bitte keine Fragen per PN, die gehören ins Forum!

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    1 Antwort Letzte Antwort
    0
    • HumidorH Humidor

      für den Solar Edge gibt es keinen Adapter, oder?
      dh damit ich diesen auch abfragen kann, muss ich den Modbus Adapter ein 2. mal installieren?

      wendy2702W Offline
      wendy2702W Offline
      wendy2702
      schrieb am zuletzt editiert von
      #16

      @humidor sagte in (Frage) ModubusTCP Adapter ?:

      für den Solar Edge gibt es keinen Adapter, oder?
      dh damit ich diesen auch abfragen kann, muss ich den Modbus Adapter ein 2. mal installieren?

      Ja.

      Ich habe 4x Modbus laufen :-)

      Bitte keine Fragen per PN, die gehören ins Forum!

      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

      HumidorH 1 Antwort Letzte Antwort
      0
      • wendy2702W wendy2702

        @humidor sagte in (Frage) ModubusTCP Adapter ?:

        @wendy2702 Hi,
        ja diese Beschreibung kenne ich, lese daraus aber nur die Definition der Schnittstelle.
        Mir fehlen die Codestellen usw. wie im Adapter dann diese einzutragen sind.

        Mal in das Excel im ZIP geschaut?

        HumidorH Offline
        HumidorH Offline
        Humidor
        schrieb am zuletzt editiert von
        #17

        @wendy2702 sagte in (Frage) ModubusTCP Adapter ?:

        @humidor sagte in (Frage) ModubusTCP Adapter ?:

        @wendy2702 Hi,
        

        ja diese Beschreibung kenne ich, lese daraus aber nur die Definition der Schnittstelle.
        Mir fehlen die Codestellen usw. wie im Adapter dann diese einzutragen sind.

        Mal in das Excel im ZIP geschaut?

        ach ich Depp, hab die Karteireiter komplett übersehen, darin ist ja eine Flut an Infos !!! super!! dh ich kann mir auch die Grid-Voltage holen und sehen wenn mein Netz ein Problem hat ;)

        BG

        1 Antwort Letzte Antwort
        0
        • wendy2702W wendy2702

          @humidor sagte in (Frage) ModubusTCP Adapter ?:

          für den Solar Edge gibt es keinen Adapter, oder?
          dh damit ich diesen auch abfragen kann, muss ich den Modbus Adapter ein 2. mal installieren?

          Ja.

          Ich habe 4x Modbus laufen :-)

          HumidorH Offline
          HumidorH Offline
          Humidor
          schrieb am zuletzt editiert von Humidor
          #18

          @wendy2702 perfekt!

          zufällig jemand auch die Settings für den SE ?
          denke das sollte es sein Link Text

          es scheint der Adapter hat noch keine Kommunikation mit dem SE?
          der Adapter bleibt Gelb, Wert aus einem Register = 0
          Bildschirmfoto 2021-02-13 um 10.36.56.png

          ist dort die ID anders?

          SolarEdge Wechselrichter unterstützen Register Mapping für die Geräte-IDs (DID) 101, 102 und 103
          

          BG

          wendy2702W 2 Antworten Letzte Antwort
          0
          • HumidorH Humidor

            @wendy2702 perfekt!

            zufällig jemand auch die Settings für den SE ?
            denke das sollte es sein Link Text

            es scheint der Adapter hat noch keine Kommunikation mit dem SE?
            der Adapter bleibt Gelb, Wert aus einem Register = 0
            Bildschirmfoto 2021-02-13 um 10.36.56.png

            ist dort die ID anders?

            SolarEdge Wechselrichter unterstützen Register Mapping für die Geräte-IDs (DID) 101, 102 und 103
            
            wendy2702W Offline
            wendy2702W Offline
            wendy2702
            schrieb am zuletzt editiert von
            #19

            @humidor Habe keinen Solaredge aber Geräte ID 1 ist richtig ?

            Stell doch mal das loggen für die Instanz auf "Debug"

            Bitte keine Fragen per PN, die gehören ins Forum!

            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

            1 Antwort Letzte Antwort
            0
            • HumidorH Humidor

              @wendy2702 perfekt!

              zufällig jemand auch die Settings für den SE ?
              denke das sollte es sein Link Text

              es scheint der Adapter hat noch keine Kommunikation mit dem SE?
              der Adapter bleibt Gelb, Wert aus einem Register = 0
              Bildschirmfoto 2021-02-13 um 10.36.56.png

              ist dort die ID anders?

              SolarEdge Wechselrichter unterstützen Register Mapping für die Geräte-IDs (DID) 101, 102 und 103
              
              wendy2702W Offline
              wendy2702W Offline
              wendy2702
              schrieb am zuletzt editiert von
              #20

              @humidor https://forum.iobroker.net/topic/38322/tutorial-solaredge-modbus-iobroker-grafana?_=1613209416803

              Bitte keine Fragen per PN, die gehören ins Forum!

              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

              HumidorH 1 Antwort Letzte Antwort
              0
              • wendy2702W wendy2702

                @humidor https://forum.iobroker.net/topic/38322/tutorial-solaredge-modbus-iobroker-grafana?_=1613209416803

                HumidorH Offline
                HumidorH Offline
                Humidor
                schrieb am zuletzt editiert von Humidor
                #21

                @wendy2702 1502 geht der Adapter auf Rot

                modbus.1	2021-02-13 10:46:17.023	debug	(9646) Closing client on purpose.
                modbus.1	2021-02-13 10:46:16.022	debug	(9646) Cleaning up request fifo.
                modbus.1	2021-02-13 10:46:16.021	debug	(9646) Socket closed with error
                modbus.1	2021-02-13 10:46:16.019	warn	(9646) On error: {"errno":"ECONNREFUSED","code":"ECONNREFUSED","syscall":"connect","address":"192.168.0.98","port":1502}
                modbus.1	2021-02-13 10:46:16.019	error	(9646) Client in error state.
                modbus.1	2021-02-13 10:46:16.018	error	(9646) Socket Error
                modbus.1	2021-02-13 10:46:15.381	info	(9646) starting. Version 3.1.10 in /opt/iobroker/node_modules/iobroker.modbus, node: v10.23.2, js-controller: 3.1.6
                

                kann mich noch erinner, dass der SE Support 502 freigeschaltet hat. ID 1 wird zBpsp im evcc verwendet

                denke mein Wert ist falsch:

                modbus.1	2021-02-13 10:49:23.055	debug	(9898) Closing client on purpose.
                modbus.1	2021-02-13 10:49:22.053	debug	(9898) Cleaning up request fifo.
                modbus.1	2021-02-13 10:49:22.052	debug	(9898) Socket closed with error
                modbus.1	2021-02-13 10:49:22.008	info	(9898) Disconnected from slave 192.168.0.98
                modbus.1	2021-02-13 10:49:22.006	debug	(9898) Closing client on purpose.
                modbus.1	2021-02-13 10:49:21.954	warn	(9898) Poll error count: 6 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                modbus.1	2021-02-13 10:49:21.953	debug	(9898) Received pdu describes an error.
                modbus.1	2021-02-13 10:49:21.936	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                modbus.1	2021-02-13 10:49:21.935	debug	(9898) Poll device 1
                modbus.1	2021-02-13 10:49:20.883	warn	(9898) Poll error count: 5 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                modbus.1	2021-02-13 10:49:20.882	debug	(9898) Received pdu describes an error.
                modbus.1	2021-02-13 10:49:20.827	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                modbus.1	2021-02-13 10:49:20.826	debug	(9898) Poll device 1
                modbus.1	2021-02-13 10:49:19.774	warn	(9898) Poll error count: 4 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                modbus.1	2021-02-13 10:49:19.773	debug	(9898) Received pdu describes an error.
                modbus.1	2021-02-13 10:49:19.711	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                modbus.1	2021-02-13 10:49:19.711	debug	(9898) Poll device 1
                modbus.1	2021-02-13 10:49:18.659	warn	(9898) Poll error count: 3 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                modbus.1	2021-02-13 10:49:18.658	debug	(9898) Received pdu describes an error.
                modbus.1	2021-02-13 10:49:18.618	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                modbus.1	2021-02-13 10:49:18.617	debug	(9898) Poll device 1
                modbus.1	2021-02-13 10:49:17.564	warn	(9898) Poll error count: 2 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                modbus.1	2021-02-13 10:49:17.562	debug	(9898) Received pdu describes an error.
                modbus.1	2021-02-13 10:49:17.532	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                modbus.1	2021-02-13 10:49:17.530	debug	(9898) Poll device 1
                modbus.1	2021-02-13 10:49:16.478	warn	(9898) Poll error count: 1 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                modbus.1	2021-02-13 10:49:16.476	debug	(9898) Received pdu describes an error.
                modbus.1	2021-02-13 10:49:16.398	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                modbus.1	2021-02-13 10:49:16.396	debug	(9898) Poll device 1
                modbus.1	2021-02-13 10:49:16.394	info	(9898) Connected to slave 192.168.0.98
                modbus.1	2021-02-13 10:49:16.036	info	(9898) starting. Version 3.1.10 in /opt/iobroker/node_modules/iobroker.modbus, node: v10.23.2, js-controller: 3.1.6
                

                Bildschirmfoto 2021-02-13 um 10.51.40.png

                BG

                wendy2702W 1 Antwort Letzte Antwort
                0
                • HumidorH Humidor

                  @wendy2702 1502 geht der Adapter auf Rot

                  modbus.1	2021-02-13 10:46:17.023	debug	(9646) Closing client on purpose.
                  modbus.1	2021-02-13 10:46:16.022	debug	(9646) Cleaning up request fifo.
                  modbus.1	2021-02-13 10:46:16.021	debug	(9646) Socket closed with error
                  modbus.1	2021-02-13 10:46:16.019	warn	(9646) On error: {"errno":"ECONNREFUSED","code":"ECONNREFUSED","syscall":"connect","address":"192.168.0.98","port":1502}
                  modbus.1	2021-02-13 10:46:16.019	error	(9646) Client in error state.
                  modbus.1	2021-02-13 10:46:16.018	error	(9646) Socket Error
                  modbus.1	2021-02-13 10:46:15.381	info	(9646) starting. Version 3.1.10 in /opt/iobroker/node_modules/iobroker.modbus, node: v10.23.2, js-controller: 3.1.6
                  

                  kann mich noch erinner, dass der SE Support 502 freigeschaltet hat. ID 1 wird zBpsp im evcc verwendet

                  denke mein Wert ist falsch:

                  modbus.1	2021-02-13 10:49:23.055	debug	(9898) Closing client on purpose.
                  modbus.1	2021-02-13 10:49:22.053	debug	(9898) Cleaning up request fifo.
                  modbus.1	2021-02-13 10:49:22.052	debug	(9898) Socket closed with error
                  modbus.1	2021-02-13 10:49:22.008	info	(9898) Disconnected from slave 192.168.0.98
                  modbus.1	2021-02-13 10:49:22.006	debug	(9898) Closing client on purpose.
                  modbus.1	2021-02-13 10:49:21.954	warn	(9898) Poll error count: 6 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                  modbus.1	2021-02-13 10:49:21.953	debug	(9898) Received pdu describes an error.
                  modbus.1	2021-02-13 10:49:21.936	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                  modbus.1	2021-02-13 10:49:21.935	debug	(9898) Poll device 1
                  modbus.1	2021-02-13 10:49:20.883	warn	(9898) Poll error count: 5 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                  modbus.1	2021-02-13 10:49:20.882	debug	(9898) Received pdu describes an error.
                  modbus.1	2021-02-13 10:49:20.827	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                  modbus.1	2021-02-13 10:49:20.826	debug	(9898) Poll device 1
                  modbus.1	2021-02-13 10:49:19.774	warn	(9898) Poll error count: 4 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                  modbus.1	2021-02-13 10:49:19.773	debug	(9898) Received pdu describes an error.
                  modbus.1	2021-02-13 10:49:19.711	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                  modbus.1	2021-02-13 10:49:19.711	debug	(9898) Poll device 1
                  modbus.1	2021-02-13 10:49:18.659	warn	(9898) Poll error count: 3 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                  modbus.1	2021-02-13 10:49:18.658	debug	(9898) Received pdu describes an error.
                  modbus.1	2021-02-13 10:49:18.618	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                  modbus.1	2021-02-13 10:49:18.617	debug	(9898) Poll device 1
                  modbus.1	2021-02-13 10:49:17.564	warn	(9898) Poll error count: 2 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                  modbus.1	2021-02-13 10:49:17.562	debug	(9898) Received pdu describes an error.
                  modbus.1	2021-02-13 10:49:17.532	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                  modbus.1	2021-02-13 10:49:17.530	debug	(9898) Poll device 1
                  modbus.1	2021-02-13 10:49:16.478	warn	(9898) Poll error count: 1 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                  modbus.1	2021-02-13 10:49:16.476	debug	(9898) Received pdu describes an error.
                  modbus.1	2021-02-13 10:49:16.398	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                  modbus.1	2021-02-13 10:49:16.396	debug	(9898) Poll device 1
                  modbus.1	2021-02-13 10:49:16.394	info	(9898) Connected to slave 192.168.0.98
                  modbus.1	2021-02-13 10:49:16.036	info	(9898) starting. Version 3.1.10 in /opt/iobroker/node_modules/iobroker.modbus, node: v10.23.2, js-controller: 3.1.6
                  

                  Bildschirmfoto 2021-02-13 um 10.51.40.png

                  wendy2702W Offline
                  wendy2702W Offline
                  wendy2702
                  schrieb am zuletzt editiert von
                  #22

                  @humidor sagte in (Frage) ModubusTCP Adapter ?:

                  kann mich noch erinner, dass der SE Support 502 freigeschaltet hat. ID 1 wird zBpsp im evcc verwendet

                  Hast du keine Möglichkeit das selber am WR zu Prüfen?

                  Würde auch direkt am WR Prüfen ob MOdbus wirklich aktiviert ist.

                  Bitte keine Fragen per PN, die gehören ins Forum!

                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                  HumidorH 1 Antwort Letzte Antwort
                  0
                  • wendy2702W wendy2702

                    @humidor sagte in (Frage) ModubusTCP Adapter ?:

                    kann mich noch erinner, dass der SE Support 502 freigeschaltet hat. ID 1 wird zBpsp im evcc verwendet

                    Hast du keine Möglichkeit das selber am WR zu Prüfen?

                    Würde auch direkt am WR Prüfen ob MOdbus wirklich aktiviert ist.

                    HumidorH Offline
                    HumidorH Offline
                    Humidor
                    schrieb am zuletzt editiert von Humidor
                    #23

                    @wendy2702 ja ist es, hab den SE schon in openWB, evcc abgefragt mit besagten Einstellungen
                    IMG_20210213_105619.JPG

                    BG

                    wendy2702W 1 Antwort Letzte Antwort
                    0
                    • HumidorH Humidor

                      @wendy2702 ja ist es, hab den SE schon in openWB, evcc abgefragt mit besagten Einstellungen
                      IMG_20210213_105619.JPG

                      wendy2702W Offline
                      wendy2702W Offline
                      wendy2702
                      schrieb am zuletzt editiert von wendy2702
                      #24

                      @humidor Wenn ich das Tutorial anschaue werden füR Solaredge Holdingsregister verwendet.

                      Hier gibt es auch ein CSV zum Import:

                      https://forum.iobroker.net/topic/38322/tutorial-solaredge-modbus-iobroker-grafana?_=1613209416803

                      Ist im Spoiler

                      Bitte keine Fragen per PN, die gehören ins Forum!

                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                      HumidorH 1 Antwort Letzte Antwort
                      1
                      • wendy2702W wendy2702

                        @humidor Wenn ich das Tutorial anschaue werden füR Solaredge Holdingsregister verwendet.

                        Hier gibt es auch ein CSV zum Import:

                        https://forum.iobroker.net/topic/38322/tutorial-solaredge-modbus-iobroker-grafana?_=1613209416803

                        Ist im Spoiler

                        HumidorH Offline
                        HumidorH Offline
                        Humidor
                        schrieb am zuletzt editiert von Humidor
                        #25

                        @wendy2702 super Danke!!!

                        es läuft was, aber nicht wiklich korrektk.

                        modbus.1	2021-02-13 11:07:43.784	debug	(11206) Closing client on purpose.
                        modbus.1	2021-02-13 11:07:42.783	debug	(11206) Cleaning up request fifo.
                        modbus.1	2021-02-13 11:07:42.782	debug	(11206) Socket closed with error
                        modbus.1	2021-02-13 11:07:42.671	info	(11206) Disconnected from slave 192.168.0.98
                        modbus.1	2021-02-13 11:07:42.670	debug	(11206) Closing client on purpose.
                        modbus.1	2021-02-13 11:07:42.618	warn	(11206) Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                        modbus.1	2021-02-13 11:07:42.617	debug	(11206) Received pdu describes an error.
                        modbus.1	2021-02-13 11:07:42.572	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                        modbus.1	2021-02-13 11:07:42.494	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                        modbus.1	2021-02-13 11:07:42.493	debug	(11206) Poll device 1
                        modbus.1	2021-02-13 11:07:41.440	warn	(11206) Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                        modbus.1	2021-02-13 11:07:41.439	debug	(11206) Received pdu describes an error.
                        modbus.1	2021-02-13 11:07:41.353	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                        modbus.1	2021-02-13 11:07:41.281	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                        modbus.1	2021-02-13 11:07:41.280	debug	(11206) Poll device 1
                        modbus.1	2021-02-13 11:07:40.228	warn	(11206) Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                        modbus.1	2021-02-13 11:07:40.227	debug	(11206) Received pdu describes an error.
                        modbus.1	2021-02-13 11:07:40.139	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                        modbus.1	2021-02-13 11:07:40.048	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                        modbus.1	2021-02-13 11:07:40.047	debug	(11206) Poll device 1
                        modbus.1	2021-02-13 11:07:38.995	warn	(11206) Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                        modbus.1	2021-02-13 11:07:38.994	debug	(11206) Received pdu describes an error.
                        modbus.1	2021-02-13 11:07:38.904	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                        modbus.1	2021-02-13 11:07:38.857	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                        modbus.1	2021-02-13 11:07:38.856	debug	(11206) Poll device 1
                        modbus.1	2021-02-13 11:07:37.804	warn	(11206) Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                        

                        die Objekte (Holding Register) aus dem "Spoiler" werden angelegt, die Werte stimmen aber gar nicht. der nächste Beitrag im Beitrag, sagt, dass die "Kommastelle" noch per JS-Script umgemodelt werden muss. OK, aber die Werte machen dann auch keinen Sinn, irgendwas passt da nicht.
                        Der Adapter bleibt auf Gelg, die Werte werden auch nicht upgedatet.

                        modbus.1	2021-02-13 11:29:27.514	info	(12625) Disconnected from slave 192.168.0.98
                        modbus.1	2021-02-13 11:29:27.513	debug	(12625) Closing client on purpose.
                        modbus.1	2021-02-13 11:29:26.511	debug	(12625) Cleaning up request fifo.
                        modbus.1	2021-02-13 11:29:26.511	debug	(12625) Clearing timeout of the current request.
                        modbus.1	2021-02-13 11:29:26.509	debug	(12625) Socket closed with error
                        modbus.1	2021-02-13 11:29:26.505	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                        modbus.1	2021-02-13 11:29:26.504	debug	(12625) Poll device 1
                        modbus.1	2021-02-13 11:29:25.413	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                        modbus.1	2021-02-13 11:29:25.412	debug	(12625) Poll device 1
                        modbus.1	2021-02-13 11:29:24.316	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                        modbus.1	2021-02-13 11:29:24.314	debug	(12625) Poll device 1
                        modbus.1	2021-02-13 11:29:24.311	info	(12625) Connected to slave 192.168.0.98
                        

                        BG

                        wendy2702W 1 Antwort Letzte Antwort
                        0
                        • HumidorH Humidor

                          @wendy2702 super Danke!!!

                          es läuft was, aber nicht wiklich korrektk.

                          modbus.1	2021-02-13 11:07:43.784	debug	(11206) Closing client on purpose.
                          modbus.1	2021-02-13 11:07:42.783	debug	(11206) Cleaning up request fifo.
                          modbus.1	2021-02-13 11:07:42.782	debug	(11206) Socket closed with error
                          modbus.1	2021-02-13 11:07:42.671	info	(11206) Disconnected from slave 192.168.0.98
                          modbus.1	2021-02-13 11:07:42.670	debug	(11206) Closing client on purpose.
                          modbus.1	2021-02-13 11:07:42.618	warn	(11206) Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          modbus.1	2021-02-13 11:07:42.617	debug	(11206) Received pdu describes an error.
                          modbus.1	2021-02-13 11:07:42.572	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                          modbus.1	2021-02-13 11:07:42.494	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                          modbus.1	2021-02-13 11:07:42.493	debug	(11206) Poll device 1
                          modbus.1	2021-02-13 11:07:41.440	warn	(11206) Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          modbus.1	2021-02-13 11:07:41.439	debug	(11206) Received pdu describes an error.
                          modbus.1	2021-02-13 11:07:41.353	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                          modbus.1	2021-02-13 11:07:41.281	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                          modbus.1	2021-02-13 11:07:41.280	debug	(11206) Poll device 1
                          modbus.1	2021-02-13 11:07:40.228	warn	(11206) Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          modbus.1	2021-02-13 11:07:40.227	debug	(11206) Received pdu describes an error.
                          modbus.1	2021-02-13 11:07:40.139	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                          modbus.1	2021-02-13 11:07:40.048	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                          modbus.1	2021-02-13 11:07:40.047	debug	(11206) Poll device 1
                          modbus.1	2021-02-13 11:07:38.995	warn	(11206) Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          modbus.1	2021-02-13 11:07:38.994	debug	(11206) Received pdu describes an error.
                          modbus.1	2021-02-13 11:07:38.904	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                          modbus.1	2021-02-13 11:07:38.857	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                          modbus.1	2021-02-13 11:07:38.856	debug	(11206) Poll device 1
                          modbus.1	2021-02-13 11:07:37.804	warn	(11206) Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          

                          die Objekte (Holding Register) aus dem "Spoiler" werden angelegt, die Werte stimmen aber gar nicht. der nächste Beitrag im Beitrag, sagt, dass die "Kommastelle" noch per JS-Script umgemodelt werden muss. OK, aber die Werte machen dann auch keinen Sinn, irgendwas passt da nicht.
                          Der Adapter bleibt auf Gelg, die Werte werden auch nicht upgedatet.

                          modbus.1	2021-02-13 11:29:27.514	info	(12625) Disconnected from slave 192.168.0.98
                          modbus.1	2021-02-13 11:29:27.513	debug	(12625) Closing client on purpose.
                          modbus.1	2021-02-13 11:29:26.511	debug	(12625) Cleaning up request fifo.
                          modbus.1	2021-02-13 11:29:26.511	debug	(12625) Clearing timeout of the current request.
                          modbus.1	2021-02-13 11:29:26.509	debug	(12625) Socket closed with error
                          modbus.1	2021-02-13 11:29:26.505	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                          modbus.1	2021-02-13 11:29:26.504	debug	(12625) Poll device 1
                          modbus.1	2021-02-13 11:29:25.413	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                          modbus.1	2021-02-13 11:29:25.412	debug	(12625) Poll device 1
                          modbus.1	2021-02-13 11:29:24.316	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                          modbus.1	2021-02-13 11:29:24.314	debug	(12625) Poll device 1
                          modbus.1	2021-02-13 11:29:24.311	info	(12625) Connected to slave 192.168.0.98
                          
                          wendy2702W Offline
                          wendy2702W Offline
                          wendy2702
                          schrieb am zuletzt editiert von wendy2702
                          #26

                          @humidor Das könnte an unterschiedlichen Firmware Versionen liegen oder eventuell an unterschiedlichen WR Typen.

                          Soweit ich mich erinnere ist das anpassen per Javascript notwendig da Solaredge mit Faktoren für Register arbeitet.

                          Frage doch mal in dem Verlinkten Thread.

                          Zum Testen kannst du mal die beiden Register 40100 und 40000 entfernen.

                          Welchen WR genau hast du denn?

                          Hast du denn auch die Adapter Einstellungen aus dem anderen Thread übernommen?

                          Bitte keine Fragen per PN, die gehören ins Forum!

                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                          HumidorH 1 Antwort Letzte Antwort
                          0
                          • wendy2702W wendy2702

                            @humidor Das könnte an unterschiedlichen Firmware Versionen liegen oder eventuell an unterschiedlichen WR Typen.

                            Soweit ich mich erinnere ist das anpassen per Javascript notwendig da Solaredge mit Faktoren für Register arbeitet.

                            Frage doch mal in dem Verlinkten Thread.

                            Zum Testen kannst du mal die beiden Register 40100 und 40000 entfernen.

                            Welchen WR genau hast du denn?

                            Hast du denn auch die Adapter Einstellungen aus dem anderen Thread übernommen?

                            HumidorH Offline
                            HumidorH Offline
                            Humidor
                            schrieb am zuletzt editiert von Humidor
                            #27

                            @wendy2702 SE17k mit akt. FW meines Wissen, hatten gerade ein Update weil mehr Optimizer montiert wurden

                            Bildschirmfoto 2021-02-13 um 11.33.08.png

                            BG

                            wendy2702W 1 Antwort Letzte Antwort
                            0
                            • HumidorH Humidor

                              @wendy2702 SE17k mit akt. FW meines Wissen, hatten gerade ein Update weil mehr Optimizer montiert wurden

                              Bildschirmfoto 2021-02-13 um 11.33.08.png

                              wendy2702W Offline
                              wendy2702W Offline
                              wendy2702
                              schrieb am zuletzt editiert von
                              #28

                              @humidor Schau mal hier.

                              Wurde auch mit Modbus realisiert.

                              https://forum.iobroker.net/topic/23020/solaredge-mit-zigbee-einbinden

                              Bitte keine Fragen per PN, die gehören ins Forum!

                              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                              HumidorH 1 Antwort Letzte Antwort
                              0
                              • wendy2702W wendy2702

                                @humidor Schau mal hier.

                                Wurde auch mit Modbus realisiert.

                                https://forum.iobroker.net/topic/23020/solaredge-mit-zigbee-einbinden

                                HumidorH Offline
                                HumidorH Offline
                                Humidor
                                schrieb am zuletzt editiert von Humidor
                                #29

                                @wendy2702 inzwischen ist es mir etwas klarer
                                die Instanz geht nur auf Grün, wenn eine Abfrage läuft, sonst Gelb.
                                ich sehe allerdings Fehler :

                                modbus.1	2021-02-13 12:55:10.673	debug	(17194) Closing client on purpose.
                                modbus.1	2021-02-13 12:55:09.671	debug	(17194) Cleaning up request fifo.
                                modbus.1	2021-02-13 12:55:09.671	debug	(17194) Socket closed with error
                                modbus.1	2021-02-13 12:55:09.601	info	(17194) Disconnected from slave 192.168.0.98
                                modbus.1	2021-02-13 12:55:09.600	debug	(17194) Closing client on purpose.
                                modbus.1	2021-02-13 12:55:09.550	warn	(17194) Poll error count: 12 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                modbus.1	2021-02-13 12:55:09.549	debug	(17194) Received pdu describes an error.
                                modbus.1	2021-02-13 12:55:09.463	debug	(17194) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                                modbus.1	2021-02-13 12:55:09.327	debug	(17194) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                                modbus.1	2021-02-13 12:55:09.327	debug	(17194) Poll device 1
                                modbus.1	2021-02-13 12:55:09.326	info	(17194) Connected to slave 192.168.0.98
                                modbus.1	2021-02-13 12:55:05.735	debug	(17194) sendTo "listUart" to system.adapter.admin.0 from system.adapter.modbus.1
                                modbus.1	2021-02-13 12:55:05.735	info	(17194) List of port: [{"path":"/dev/ttyAMA0"}]
                                modbus.1	2021-02-13 12:55:04.492	debug	(17194) system.adapter.admin.0: logging true
                                modbus.1	2021-02-13 12:54:40.388	debug	(17194) Closing client on purpose.
                                modbus.1	2021-02-13 12:54:39.386	debug	(17194) Cleaning up request fifo.
                                modbus.1	2021-02-13 12:54:39.386	debug	(17194) Socket closed with error
                                modbus.1	2021-02-13 12:54:39.323	info	(17194) Disconnected from slave 192.168.0.98
                                modbus.1	2021-02-13 12:54:39.322	debug	(17194) Closing client on purpose.
                                modbus.1	2021-02-13 12:54:39.271	warn	(17194) Poll error count: 11 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                modbus.1	2021-02-13 12:54:39.269	debug	(17194) Received pdu describes an error.
                                modbus.1	2021-02-13 12:54:39.174	debug	(17194) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                                modbus.1	2021-02-13 12:54:36.496	debug	(17194) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                                modbus.1	2021-02-13 12:54:36.496	debug	(17194) Poll device 1
                                

                                auch ist die Instanz vom SMA dauerhaft Grün und die Polltime etwa 800ms.
                                die Instanz vom SE pollt nicht, öffnet u schließt den Socket ständig
                                ab 40100 bleiben die Objekte leer, obwohl im Log als gepollt drin
                                wenn ich das Log richtig interpretiere, dann stimmt da ein Wert oder Adresse nicht?
                                Tja, was heißt das: Received pdu describes an error.

                                BG

                                HumidorH 1 Antwort Letzte Antwort
                                0
                                • HumidorH Humidor

                                  @wendy2702 inzwischen ist es mir etwas klarer
                                  die Instanz geht nur auf Grün, wenn eine Abfrage läuft, sonst Gelb.
                                  ich sehe allerdings Fehler :

                                  modbus.1	2021-02-13 12:55:10.673	debug	(17194) Closing client on purpose.
                                  modbus.1	2021-02-13 12:55:09.671	debug	(17194) Cleaning up request fifo.
                                  modbus.1	2021-02-13 12:55:09.671	debug	(17194) Socket closed with error
                                  modbus.1	2021-02-13 12:55:09.601	info	(17194) Disconnected from slave 192.168.0.98
                                  modbus.1	2021-02-13 12:55:09.600	debug	(17194) Closing client on purpose.
                                  modbus.1	2021-02-13 12:55:09.550	warn	(17194) Poll error count: 12 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                  modbus.1	2021-02-13 12:55:09.549	debug	(17194) Received pdu describes an error.
                                  modbus.1	2021-02-13 12:55:09.463	debug	(17194) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                                  modbus.1	2021-02-13 12:55:09.327	debug	(17194) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                                  modbus.1	2021-02-13 12:55:09.327	debug	(17194) Poll device 1
                                  modbus.1	2021-02-13 12:55:09.326	info	(17194) Connected to slave 192.168.0.98
                                  modbus.1	2021-02-13 12:55:05.735	debug	(17194) sendTo "listUart" to system.adapter.admin.0 from system.adapter.modbus.1
                                  modbus.1	2021-02-13 12:55:05.735	info	(17194) List of port: [{"path":"/dev/ttyAMA0"}]
                                  modbus.1	2021-02-13 12:55:04.492	debug	(17194) system.adapter.admin.0: logging true
                                  modbus.1	2021-02-13 12:54:40.388	debug	(17194) Closing client on purpose.
                                  modbus.1	2021-02-13 12:54:39.386	debug	(17194) Cleaning up request fifo.
                                  modbus.1	2021-02-13 12:54:39.386	debug	(17194) Socket closed with error
                                  modbus.1	2021-02-13 12:54:39.323	info	(17194) Disconnected from slave 192.168.0.98
                                  modbus.1	2021-02-13 12:54:39.322	debug	(17194) Closing client on purpose.
                                  modbus.1	2021-02-13 12:54:39.271	warn	(17194) Poll error count: 11 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                  modbus.1	2021-02-13 12:54:39.269	debug	(17194) Received pdu describes an error.
                                  modbus.1	2021-02-13 12:54:39.174	debug	(17194) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                                  modbus.1	2021-02-13 12:54:36.496	debug	(17194) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                                  modbus.1	2021-02-13 12:54:36.496	debug	(17194) Poll device 1
                                  

                                  auch ist die Instanz vom SMA dauerhaft Grün und die Polltime etwa 800ms.
                                  die Instanz vom SE pollt nicht, öffnet u schließt den Socket ständig
                                  ab 40100 bleiben die Objekte leer, obwohl im Log als gepollt drin
                                  wenn ich das Log richtig interpretiere, dann stimmt da ein Wert oder Adresse nicht?
                                  Tja, was heißt das: Received pdu describes an error.

                                  HumidorH Offline
                                  HumidorH Offline
                                  Humidor
                                  schrieb am zuletzt editiert von Humidor
                                  #30

                                  wurde im anderen Thread Link Text fertig gestellt!

                                  DANKE!!!! erledigt. ev. Fragen kommen noch.

                                  BG

                                  HomoranH Thomas BraunT 2 Antworten Letzte Antwort
                                  0
                                  • HumidorH Humidor

                                    wurde im anderen Thread Link Text fertig gestellt!

                                    DANKE!!!! erledigt. ev. Fragen kommen noch.

                                    HomoranH Nicht stören
                                    HomoranH Nicht stören
                                    Homoran
                                    Global Moderator Administrators
                                    schrieb am zuletzt editiert von
                                    #31

                                    @humidor sagte in (gelöst)(Frage) ModubusTCP Adapter ?:

                                    wurde im anderen Thread fertig gestellt!

                                    DANKE!!!! erledigt. ev. Fragen kommen noch.

                                    Bitte verlinken und dann auf [gelöst] setzen

                                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                    1 Antwort Letzte Antwort
                                    0
                                    • HumidorH Humidor

                                      wurde im anderen Thread Link Text fertig gestellt!

                                      DANKE!!!! erledigt. ev. Fragen kommen noch.

                                      Thomas BraunT Online
                                      Thomas BraunT Online
                                      Thomas Braun
                                      Most Active
                                      schrieb am zuletzt editiert von Thomas Braun
                                      #32

                                      @humidor sagte in (gelöst)(Frage) ModubusTCP Adapter ?:

                                      Update habe ich bisher keines gemacht (never change a running system)

                                      Die Einstellung sollte überdacht werden. Die Updates werden ja nicht wegen einer höheren Versionsnummer vergeben sondern weil Fehler beseitigt worden sind.

                                      Linux-Werkzeugkasten:
                                      https://forum.iobroker.net/topic/42952/der-kleine-iobroker-linux-werkzeugkasten
                                      NodeJS Fixer Skript:
                                      https://forum.iobroker.net/topic/68035/iob-node-fix-skript
                                      iob_diag: curl -sLf -o diag.sh https://iobroker.net/diag.sh && bash diag.sh

                                      wendy2702W 1 Antwort Letzte Antwort
                                      0
                                      • Thomas BraunT Thomas Braun

                                        @humidor sagte in (gelöst)(Frage) ModubusTCP Adapter ?:

                                        Update habe ich bisher keines gemacht (never change a running system)

                                        Die Einstellung sollte überdacht werden. Die Updates werden ja nicht wegen einer höheren Versionsnummer vergeben sondern weil Fehler beseitigt worden sind.

                                        wendy2702W Offline
                                        wendy2702W Offline
                                        wendy2702
                                        schrieb am zuletzt editiert von
                                        #33

                                        @thomas-braun Bei SMA wurde vor einigen Jahren damit sogar erst Modbus implementiert.

                                        Bitte keine Fragen per PN, die gehören ins Forum!

                                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                        M 1 Antwort Letzte Antwort
                                        0
                                        • wendy2702W wendy2702

                                          @thomas-braun Bei SMA wurde vor einigen Jahren damit sogar erst Modbus implementiert.

                                          M Offline
                                          M Offline
                                          maxpd
                                          schrieb am zuletzt editiert von
                                          #34

                                          @wendy2702 Ich habe über Sunny Explorer Modbus via TCP aktiviert und im Sunny Portal zeigt er diese Änderung auch erfolgreich an.

                                          Aber der Modbus Adapter bleibt gelb.

                                          Webconnect habe ich auch aktiviert. Brauch es noch etwas?

                                          2dcce6b2-b6ff-4f38-b03d-418a12a146a0-image.png

                                          7f275ba8-91b7-4ab6-a445-c90682910569-image.png

                                          Gruß
                                          maxpd

                                          Raspi 4 8gb | iobroker + pivccu3 | 46 Adapter | 68 Scripte, 120 Devices

                                          wendy2702W 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          414

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe