    4. (gelöst)(Frage) ModubusTCP Adapter ?

    NEWS

    • Neues Video über Aliase, virtuelle Geräte und Kategorien

    • Wir empfehlen: Node.js 22.x

    • Neuer Blog: Fotos und Eindrücke aus Solingen

    (gelöst)(Frage) ModubusTCP Adapter ?

    This topic has been deleted. Only users with topic management privileges can see it.
    • wendy2702
      wendy2702 @Humidor last edited by

      @humidor Ja.

      Humidor 1 Reply Last reply Reply Quote 0
      • Humidor
        Humidor @wendy2702 last edited by

        @wendy2702 OK, hättest du dazu einen Link einer Beschreibung? in der vom SMA was ich habe, stehen diese nicht drin.

        wendy2702 1 Reply Last reply Reply Quote 0
        • wendy2702
          wendy2702 @Humidor last edited by

          @humidor Das wundert mich ein wenig da mein neuer STP15000 genau die gleichen Register verwendet.

          Anleitung findet man bei SMA unter den Downloads zu dem WR. Hast du einen TL20 oder TL30 ?

          Wichtig ist auch noch die Firmware Version.

          Hier mal ein Beispiel

          SMA_Modbus-de-en_V25.zip

          Humidor 1 Reply Last reply Reply Quote 0
          • wendy2702
            wendy2702 @Humidor last edited by wendy2702

            @humidor Hier mal ein Export. Eigentlich als CSV, kann ich aber aktuell auf dem Smartphone so nicht speichern.

            Das sollte man als CSV importieren können.

            deviceId	address	name	description	unit	type	len	factor	offset	formula	role	room	
            3	30775	PVLeistung		Watt	int32be	2	1	0		value		
            3	30531	Gesamtertrag		kWh	uint32be	2	1	0		value		
            3	30201	Status			uint32be	2	1	0		value		
            3	30537	Tagesertrag_kWh		kWh	uint32be	2	1	0		value		
            3	30535	Tagesertrag_Wh		Wh	uint32be	2	1	0		value		
            3	30057	Seriennummer			uint32be	2	1	0		value		
            3	30953	Temperatur		Grad	int32be	2	0.1	0		value		
            3	30771	DC_Spannung_Eingang_1		V	int32be	2	0.01	0		value		
            3	30773	DC_Leistung_Eingang_1		Watt	int32be	2	1	0		value		
            3	30803	Grid Frequency		Hz	int32be	2	0.01	0		value		
            3	30769	DC_Strom_Eingang_1		A	int32be	2	0.01	0		value		
            3	30957	DC_Strom_Eingang_2		A	int32be	2	0.01	0		value		
            3	30959	DC_Spannung_Eingang_2		V	int32be	2	0.01	0		value		
            3	30961	DC_Leistung_Eingang_2		Watt	int32be	2	1	0		value		
            3	30051	Test			uint32be	2	1	0		value		
            
            

            Hier noch ne CSV Datei:

            STP6000_register.csv

            Humidor 1 Reply Last reply Reply Quote 0
            • Humidor
              Humidor @wendy2702 last edited by

              @wendy2702 Hi,
              ja diese Beschreibung kenne ich, lese daraus aber nur die Definition der Schnittstelle.
              Mir fehlen die Codestellen usw. wie im Adapter dann diese einzutragen sind.
              Link Text
              Ich habe den SMA STP6000-TL20, die FW Version ist nicht aktuell, Update habe ich bisher keines gemacht (never change a running system)

              wendy2702 1 Reply Last reply Reply Quote 0
              • Humidor
                Humidor @wendy2702 last edited by Humidor

                @wendy2702 super Danke!!
                denke es hat funktioniert!
                Bildschirmfoto 2021-02-13 um 10.08.29.png

                bin gespannt!

                YESSSS!!!
                Bildschirmfoto 2021-02-13 um 10.10.02.png 👍 😁 🤗 🤛

                Humidor wendy2702 2 Replies Last reply Reply Quote 0
                • wendy2702
                  wendy2702 @Humidor last edited by

                  @humidor sagte in (Frage) ModubusTCP Adapter ?:

                  @wendy2702 Hi,
                  ja diese Beschreibung kenne ich, lese daraus aber nur die Definition der Schnittstelle.
                  Mir fehlen die Codestellen usw. wie im Adapter dann diese einzutragen sind.

                  Mal in das Excel im ZIP geschaut?

                  Humidor 1 Reply Last reply Reply Quote 0
                  • Humidor
                    Humidor @Humidor last edited by

                    für den Solar Edge gibt es keinen Adapter, oder?
                    dh damit ich diesen auch abfragen kann, muss ich den Modbus Adapter ein 2. mal installieren?

                    wendy2702 1 Reply Last reply Reply Quote 0
                    • wendy2702
                      wendy2702 @Humidor last edited by wendy2702

                      @humidor sagte in (Frage) ModubusTCP Adapter ?:

                      @wendy2702 super Danke!!
                      denke es hat funktioniert!

                      Dann setze bitte vor dem Titel im ersten Beitrag ein [Gelöst]

                      SOrry, hatte den SolarEdge vergessen.

                      1 Reply Last reply Reply Quote 0
                      • wendy2702
                        wendy2702 @Humidor last edited by

                        @humidor sagte in (Frage) ModubusTCP Adapter ?:

                        für den Solar Edge gibt es keinen Adapter, oder?
                        dh damit ich diesen auch abfragen kann, muss ich den Modbus Adapter ein 2. mal installieren?

                        Ja.

                        Ich habe 4x Modbus laufen 🙂

                        Humidor 1 Reply Last reply Reply Quote 0
                        • Humidor
                          Humidor @wendy2702 last edited by

                          @wendy2702 sagte in (Frage) ModubusTCP Adapter ?:

                          @humidor sagte in (Frage) ModubusTCP Adapter ?:

                          @wendy2702 Hi,
                          

                          ja diese Beschreibung kenne ich, lese daraus aber nur die Definition der Schnittstelle.
                          Mir fehlen die Codestellen usw. wie im Adapter dann diese einzutragen sind.

                          Mal in das Excel im ZIP geschaut?

                          ach ich Depp, hab die Karteireiter komplett übersehen, darin ist ja eine Flut an Infos !!! super!! dh ich kann mir auch die Grid-Voltage holen und sehen wenn mein Netz ein Problem hat 😉

                          1 Reply Last reply Reply Quote 0
                          • Humidor
                            Humidor @wendy2702 last edited by Humidor

                            @wendy2702 perfekt!

                            zufällig jemand auch die Settings für den SE ?
                            denke das sollte es sein Link Text

                            es scheint der Adapter hat noch keine Kommunikation mit dem SE?
                            der Adapter bleibt Gelb, Wert aus einem Register = 0
                            Bildschirmfoto 2021-02-13 um 10.36.56.png

                            ist dort die ID anders?

                            SolarEdge Wechselrichter unterstützen Register Mapping für die Geräte-IDs (DID) 101, 102 und 103
                            
                            wendy2702 2 Replies Last reply Reply Quote 0
                            • wendy2702
                              wendy2702 @Humidor last edited by

                              @humidor Habe keinen Solaredge aber Geräte ID 1 ist richtig ?

                              Stell doch mal das loggen für die Instanz auf "Debug"

                              1 Reply Last reply Reply Quote 0
                              • wendy2702
                                wendy2702 @Humidor last edited by

                                @humidor https://forum.iobroker.net/topic/38322/tutorial-solaredge-modbus-iobroker-grafana?_=1613209416803

                                Humidor 1 Reply Last reply Reply Quote 0
                                • Humidor
                                  Humidor @wendy2702 last edited by Humidor

                                  @wendy2702 1502 geht der Adapter auf Rot

                                  modbus.1	2021-02-13 10:46:17.023	debug	(9646) Closing client on purpose.
                                  modbus.1	2021-02-13 10:46:16.022	debug	(9646) Cleaning up request fifo.
                                  modbus.1	2021-02-13 10:46:16.021	debug	(9646) Socket closed with error
                                  modbus.1	2021-02-13 10:46:16.019	warn	(9646) On error: {"errno":"ECONNREFUSED","code":"ECONNREFUSED","syscall":"connect","address":"192.168.0.98","port":1502}
                                  modbus.1	2021-02-13 10:46:16.019	error	(9646) Client in error state.
                                  modbus.1	2021-02-13 10:46:16.018	error	(9646) Socket Error
                                  modbus.1	2021-02-13 10:46:15.381	info	(9646) starting. Version 3.1.10 in /opt/iobroker/node_modules/iobroker.modbus, node: v10.23.2, js-controller: 3.1.6
                                  

                                  kann mich noch erinner, dass der SE Support 502 freigeschaltet hat. ID 1 wird zBpsp im evcc verwendet

                                  denke mein Wert ist falsch:

                                  modbus.1	2021-02-13 10:49:23.055	debug	(9898) Closing client on purpose.
                                  modbus.1	2021-02-13 10:49:22.053	debug	(9898) Cleaning up request fifo.
                                  modbus.1	2021-02-13 10:49:22.052	debug	(9898) Socket closed with error
                                  modbus.1	2021-02-13 10:49:22.008	info	(9898) Disconnected from slave 192.168.0.98
                                  modbus.1	2021-02-13 10:49:22.006	debug	(9898) Closing client on purpose.
                                  modbus.1	2021-02-13 10:49:21.954	warn	(9898) Poll error count: 6 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                                  modbus.1	2021-02-13 10:49:21.953	debug	(9898) Received pdu describes an error.
                                  modbus.1	2021-02-13 10:49:21.936	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                                  modbus.1	2021-02-13 10:49:21.935	debug	(9898) Poll device 1
                                  modbus.1	2021-02-13 10:49:20.883	warn	(9898) Poll error count: 5 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                                  modbus.1	2021-02-13 10:49:20.882	debug	(9898) Received pdu describes an error.
                                  modbus.1	2021-02-13 10:49:20.827	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                                  modbus.1	2021-02-13 10:49:20.826	debug	(9898) Poll device 1
                                  modbus.1	2021-02-13 10:49:19.774	warn	(9898) Poll error count: 4 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                                  modbus.1	2021-02-13 10:49:19.773	debug	(9898) Received pdu describes an error.
                                  modbus.1	2021-02-13 10:49:19.711	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                                  modbus.1	2021-02-13 10:49:19.711	debug	(9898) Poll device 1
                                  modbus.1	2021-02-13 10:49:18.659	warn	(9898) Poll error count: 3 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                                  modbus.1	2021-02-13 10:49:18.658	debug	(9898) Received pdu describes an error.
                                  modbus.1	2021-02-13 10:49:18.618	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                                  modbus.1	2021-02-13 10:49:18.617	debug	(9898) Poll device 1
                                  modbus.1	2021-02-13 10:49:17.564	warn	(9898) Poll error count: 2 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                                  modbus.1	2021-02-13 10:49:17.562	debug	(9898) Received pdu describes an error.
                                  modbus.1	2021-02-13 10:49:17.532	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                                  modbus.1	2021-02-13 10:49:17.530	debug	(9898) Poll device 1
                                  modbus.1	2021-02-13 10:49:16.478	warn	(9898) Poll error count: 1 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                                  modbus.1	2021-02-13 10:49:16.476	debug	(9898) Received pdu describes an error.
                                  modbus.1	2021-02-13 10:49:16.398	debug	(9898) Poll inputRegs DevID(1) address 40084 - 1 bytes
                                  modbus.1	2021-02-13 10:49:16.396	debug	(9898) Poll device 1
                                  modbus.1	2021-02-13 10:49:16.394	info	(9898) Connected to slave 192.168.0.98
                                  modbus.1	2021-02-13 10:49:16.036	info	(9898) starting. Version 3.1.10 in /opt/iobroker/node_modules/iobroker.modbus, node: v10.23.2, js-controller: 3.1.6
                                  

                                  Bildschirmfoto 2021-02-13 um 10.51.40.png

                                  wendy2702 1 Reply Last reply Reply Quote 0
                                  • wendy2702
                                    wendy2702 @Humidor last edited by

                                    @humidor sagte in (Frage) ModubusTCP Adapter ?:

                                    kann mich noch erinner, dass der SE Support 502 freigeschaltet hat. ID 1 wird zBpsp im evcc verwendet

                                    Hast du keine Möglichkeit das selber am WR zu Prüfen?

                                    Würde auch direkt am WR Prüfen ob MOdbus wirklich aktiviert ist.

                                    Humidor 1 Reply Last reply Reply Quote 0
                                    • Humidor
                                      Humidor @wendy2702 last edited by Humidor

                                      @wendy2702 ja ist es, hab den SE schon in openWB, evcc abgefragt mit besagten Einstellungen
                                      IMG_20210213_105619.JPG

                                      wendy2702 1 Reply Last reply Reply Quote 0
                                      • wendy2702
                                        wendy2702 @Humidor last edited by wendy2702

                                        @humidor Wenn ich das Tutorial anschaue werden füR Solaredge Holdingsregister verwendet.

                                        Hier gibt es auch ein CSV zum Import:

                                        https://forum.iobroker.net/topic/38322/tutorial-solaredge-modbus-iobroker-grafana?_=1613209416803

                                        Ist im Spoiler

                                        Humidor 1 Reply Last reply Reply Quote 1
                                        • Humidor
                                          Humidor @wendy2702 last edited by Humidor

                                          @wendy2702 super Danke!!!

                                          es läuft was, aber nicht wiklich korrektk.

                                          modbus.1	2021-02-13 11:07:43.784	debug	(11206) Closing client on purpose.
                                          modbus.1	2021-02-13 11:07:42.783	debug	(11206) Cleaning up request fifo.
                                          modbus.1	2021-02-13 11:07:42.782	debug	(11206) Socket closed with error
                                          modbus.1	2021-02-13 11:07:42.671	info	(11206) Disconnected from slave 192.168.0.98
                                          modbus.1	2021-02-13 11:07:42.670	debug	(11206) Closing client on purpose.
                                          modbus.1	2021-02-13 11:07:42.618	warn	(11206) Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                          modbus.1	2021-02-13 11:07:42.617	debug	(11206) Received pdu describes an error.
                                          modbus.1	2021-02-13 11:07:42.572	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                                          modbus.1	2021-02-13 11:07:42.494	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                                          modbus.1	2021-02-13 11:07:42.493	debug	(11206) Poll device 1
                                          modbus.1	2021-02-13 11:07:41.440	warn	(11206) Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                          modbus.1	2021-02-13 11:07:41.439	debug	(11206) Received pdu describes an error.
                                          modbus.1	2021-02-13 11:07:41.353	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                                          modbus.1	2021-02-13 11:07:41.281	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                                          modbus.1	2021-02-13 11:07:41.280	debug	(11206) Poll device 1
                                          modbus.1	2021-02-13 11:07:40.228	warn	(11206) Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                          modbus.1	2021-02-13 11:07:40.227	debug	(11206) Received pdu describes an error.
                                          modbus.1	2021-02-13 11:07:40.139	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                                          modbus.1	2021-02-13 11:07:40.048	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                                          modbus.1	2021-02-13 11:07:40.047	debug	(11206) Poll device 1
                                          modbus.1	2021-02-13 11:07:38.995	warn	(11206) Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                          modbus.1	2021-02-13 11:07:38.994	debug	(11206) Received pdu describes an error.
                                          modbus.1	2021-02-13 11:07:38.904	debug	(11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes
                                          modbus.1	2021-02-13 11:07:38.857	debug	(11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes
                                          modbus.1	2021-02-13 11:07:38.856	debug	(11206) Poll device 1
                                          modbus.1	2021-02-13 11:07:37.804	warn	(11206) Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                          

                                          die Objekte (Holding Register) aus dem "Spoiler" werden angelegt, die Werte stimmen aber gar nicht. der nächste Beitrag im Beitrag, sagt, dass die "Kommastelle" noch per JS-Script umgemodelt werden muss. OK, aber die Werte machen dann auch keinen Sinn, irgendwas passt da nicht.
                                          Der Adapter bleibt auf Gelg, die Werte werden auch nicht upgedatet.

                                          modbus.1	2021-02-13 11:29:27.514	info	(12625) Disconnected from slave 192.168.0.98
                                          modbus.1	2021-02-13 11:29:27.513	debug	(12625) Closing client on purpose.
                                          modbus.1	2021-02-13 11:29:26.511	debug	(12625) Cleaning up request fifo.
                                          modbus.1	2021-02-13 11:29:26.511	debug	(12625) Clearing timeout of the current request.
                                          modbus.1	2021-02-13 11:29:26.509	debug	(12625) Socket closed with error
                                          modbus.1	2021-02-13 11:29:26.505	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                                          modbus.1	2021-02-13 11:29:26.504	debug	(12625) Poll device 1
                                          modbus.1	2021-02-13 11:29:25.413	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                                          modbus.1	2021-02-13 11:29:25.412	debug	(12625) Poll device 1
                                          modbus.1	2021-02-13 11:29:24.316	debug	(12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes
                                          modbus.1	2021-02-13 11:29:24.314	debug	(12625) Poll device 1
                                          modbus.1	2021-02-13 11:29:24.311	info	(12625) Connected to slave 192.168.0.98
                                          
                                          wendy2702 1 Reply Last reply Reply Quote 0
                                          • wendy2702
                                            wendy2702 @Humidor last edited by wendy2702

                                            @humidor Das könnte an unterschiedlichen Firmware Versionen liegen oder eventuell an unterschiedlichen WR Typen.

                                            Soweit ich mich erinnere ist das anpassen per Javascript notwendig da Solaredge mit Faktoren für Register arbeitet.

                                            Frage doch mal in dem Verlinkten Thread.

                                            Zum Testen kannst du mal die beiden Register 40100 und 40000 entfernen.

                                            Welchen WR genau hast du denn?

                                            Hast du denn auch die Adapter Einstellungen aus dem anderen Thread übernommen?

                                            Humidor 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate
                                            FAQ Cloud / IOT
                                            HowTo: Node.js-Update
                                            HowTo: Backup/Restore
                                            Downloads
                                            BLOG

                                            695
                                            Online

                                            32.1k
                                            Users

                                            80.6k
                                            Topics

                                            1.3m
                                            Posts

                                            5
                                            57
                                            5941
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo