(gelöst)(Frage) ModubusTCP Adapter ?
-
@wendy2702 super Danke!!!
es läuft was, aber nicht wiklich korrektk.
modbus.1 2021-02-13 11:07:43.784 debug (11206) Closing client on purpose. modbus.1 2021-02-13 11:07:42.783 debug (11206) Cleaning up request fifo. modbus.1 2021-02-13 11:07:42.782 debug (11206) Socket closed with error modbus.1 2021-02-13 11:07:42.671 info (11206) Disconnected from slave 192.168.0.98 modbus.1 2021-02-13 11:07:42.670 debug (11206) Closing client on purpose. modbus.1 2021-02-13 11:07:42.618 warn (11206) Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"} modbus.1 2021-02-13 11:07:42.617 debug (11206) Received pdu describes an error. modbus.1 2021-02-13 11:07:42.572 debug (11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes modbus.1 2021-02-13 11:07:42.494 debug (11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes modbus.1 2021-02-13 11:07:42.493 debug (11206) Poll device 1 modbus.1 2021-02-13 11:07:41.440 warn (11206) Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"} modbus.1 2021-02-13 11:07:41.439 debug (11206) Received pdu describes an error. modbus.1 2021-02-13 11:07:41.353 debug (11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes modbus.1 2021-02-13 11:07:41.281 debug (11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes modbus.1 2021-02-13 11:07:41.280 debug (11206) Poll device 1 modbus.1 2021-02-13 11:07:40.228 warn (11206) Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"} modbus.1 2021-02-13 11:07:40.227 debug (11206) Received pdu describes an error. modbus.1 2021-02-13 11:07:40.139 debug (11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes modbus.1 2021-02-13 11:07:40.048 debug (11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes modbus.1 2021-02-13 11:07:40.047 debug (11206) Poll device 1 modbus.1 2021-02-13 11:07:38.995 warn (11206) Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"} modbus.1 2021-02-13 11:07:38.994 debug (11206) Received pdu describes an error. modbus.1 2021-02-13 11:07:38.904 debug (11206) Poll holdingRegs DevID(1) address 40100 - 71 bytes modbus.1 2021-02-13 11:07:38.857 debug (11206) Poll holdingRegs DevID(1) address 40000 - 100 bytes modbus.1 2021-02-13 11:07:38.856 debug (11206) Poll device 1 modbus.1 2021-02-13 11:07:37.804 warn (11206) Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
die Objekte (Holding Register) aus dem "Spoiler" werden angelegt, die Werte stimmen aber gar nicht. der nächste Beitrag im Beitrag, sagt, dass die "Kommastelle" noch per JS-Script umgemodelt werden muss. OK, aber die Werte machen dann auch keinen Sinn, irgendwas passt da nicht.
Der Adapter bleibt auf Gelg, die Werte werden auch nicht upgedatet.modbus.1 2021-02-13 11:29:27.514 info (12625) Disconnected from slave 192.168.0.98 modbus.1 2021-02-13 11:29:27.513 debug (12625) Closing client on purpose. modbus.1 2021-02-13 11:29:26.511 debug (12625) Cleaning up request fifo. modbus.1 2021-02-13 11:29:26.511 debug (12625) Clearing timeout of the current request. modbus.1 2021-02-13 11:29:26.509 debug (12625) Socket closed with error modbus.1 2021-02-13 11:29:26.505 debug (12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes modbus.1 2021-02-13 11:29:26.504 debug (12625) Poll device 1 modbus.1 2021-02-13 11:29:25.413 debug (12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes modbus.1 2021-02-13 11:29:25.412 debug (12625) Poll device 1 modbus.1 2021-02-13 11:29:24.316 debug (12625) Poll holdingRegs DevID(1) address 40083 - 1 bytes modbus.1 2021-02-13 11:29:24.314 debug (12625) Poll device 1 modbus.1 2021-02-13 11:29:24.311 info (12625) Connected to slave 192.168.0.98
-
@humidor Das könnte an unterschiedlichen Firmware Versionen liegen oder eventuell an unterschiedlichen WR Typen.
Soweit ich mich erinnere ist das anpassen per Javascript notwendig da Solaredge mit Faktoren für Register arbeitet.
Frage doch mal in dem Verlinkten Thread.
Zum Testen kannst du mal die beiden Register 40100 und 40000 entfernen.
Welchen WR genau hast du denn?
Hast du denn auch die Adapter Einstellungen aus dem anderen Thread übernommen?
-
@wendy2702 SE17k mit akt. FW meines Wissen, hatten gerade ein Update weil mehr Optimizer montiert wurden
-
@humidor Schau mal hier.
Wurde auch mit Modbus realisiert.
https://forum.iobroker.net/topic/23020/solaredge-mit-zigbee-einbinden
-
@wendy2702 inzwischen ist es mir etwas klarer
die Instanz geht nur auf Grün, wenn eine Abfrage läuft, sonst Gelb.
ich sehe allerdings Fehler :modbus.1 2021-02-13 12:55:10.673 debug (17194) Closing client on purpose. modbus.1 2021-02-13 12:55:09.671 debug (17194) Cleaning up request fifo. modbus.1 2021-02-13 12:55:09.671 debug (17194) Socket closed with error modbus.1 2021-02-13 12:55:09.601 info (17194) Disconnected from slave 192.168.0.98 modbus.1 2021-02-13 12:55:09.600 debug (17194) Closing client on purpose. modbus.1 2021-02-13 12:55:09.550 warn (17194) Poll error count: 12 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"} modbus.1 2021-02-13 12:55:09.549 debug (17194) Received pdu describes an error. modbus.1 2021-02-13 12:55:09.463 debug (17194) Poll holdingRegs DevID(1) address 40100 - 71 bytes modbus.1 2021-02-13 12:55:09.327 debug (17194) Poll holdingRegs DevID(1) address 40000 - 100 bytes modbus.1 2021-02-13 12:55:09.327 debug (17194) Poll device 1 modbus.1 2021-02-13 12:55:09.326 info (17194) Connected to slave 192.168.0.98 modbus.1 2021-02-13 12:55:05.735 debug (17194) sendTo "listUart" to system.adapter.admin.0 from system.adapter.modbus.1 modbus.1 2021-02-13 12:55:05.735 info (17194) List of port: [{"path":"/dev/ttyAMA0"}] modbus.1 2021-02-13 12:55:04.492 debug (17194) system.adapter.admin.0: logging true modbus.1 2021-02-13 12:54:40.388 debug (17194) Closing client on purpose. modbus.1 2021-02-13 12:54:39.386 debug (17194) Cleaning up request fifo. modbus.1 2021-02-13 12:54:39.386 debug (17194) Socket closed with error modbus.1 2021-02-13 12:54:39.323 info (17194) Disconnected from slave 192.168.0.98 modbus.1 2021-02-13 12:54:39.322 debug (17194) Closing client on purpose. modbus.1 2021-02-13 12:54:39.271 warn (17194) Poll error count: 11 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"} modbus.1 2021-02-13 12:54:39.269 debug (17194) Received pdu describes an error. modbus.1 2021-02-13 12:54:39.174 debug (17194) Poll holdingRegs DevID(1) address 40100 - 71 bytes modbus.1 2021-02-13 12:54:36.496 debug (17194) Poll holdingRegs DevID(1) address 40000 - 100 bytes modbus.1 2021-02-13 12:54:36.496 debug (17194) Poll device 1
auch ist die Instanz vom SMA dauerhaft Grün und die Polltime etwa 800ms.
die Instanz vom SE pollt nicht, öffnet u schließt den Socket ständig
ab 40100 bleiben die Objekte leer, obwohl im Log als gepollt drin
wenn ich das Log richtig interpretiere, dann stimmt da ein Wert oder Adresse nicht?
Tja, was heißt das: Received pdu describes an error. -
wurde im anderen Thread Link Text fertig gestellt!
DANKE!!!! erledigt. ev. Fragen kommen noch.
-
@humidor sagte in (gelöst)(Frage) ModubusTCP Adapter ?:
wurde im anderen Thread fertig gestellt!
DANKE!!!! erledigt. ev. Fragen kommen noch.
Bitte verlinken und dann auf [gelöst] setzen
-
@humidor sagte in (gelöst)(Frage) ModubusTCP Adapter ?:
Update habe ich bisher keines gemacht (never change a running system)
Die Einstellung sollte überdacht werden. Die Updates werden ja nicht wegen einer höheren Versionsnummer vergeben sondern weil Fehler beseitigt worden sind.
-
@thomas-braun Bei SMA wurde vor einigen Jahren damit sogar erst Modbus implementiert.
-
@wendy2702 Ich habe über Sunny Explorer Modbus via TCP aktiviert und im Sunny Portal zeigt er diese Änderung auch erfolgreich an.
Aber der Modbus Adapter bleibt gelb.
Webconnect habe ich auch aktiviert. Brauch es noch etwas?
-
@maxpd Hast du Register eingetragen im Adapter?
-
@wendy2702 Ich entschuldige mich für die Störung ^^
-
-
@wendy2702 Ja genau. Er ist auf grün gewechselt. Außer ich geb ein Register an mit dem er nicht klar kommt, dann gehts direkt wieder auf Gelb.
Bei Eigenverbrauch gibt er momentan nur Quatsch aus und bei Einspeisung hat er ein Problem mit der Datenadresse.
Da muss ich noch experimentieren.
-
@maxpd Eigenverbrauch/Einspeisung geht nur wenn du den Sunny Homemager 2 hast soweit mir bekannt ist.
Hast du den?
Hier ist ne fertige CSV zum importieren mit den "wichtigsten" Registern wenn man, wie ich keinen Homemanager 2 hat.
https://forum.iobroker.net/topic/42173/gelöst-frage-modubustcp-adapter/10?page=1
Die kannst du ja noch manuel hinzufügen.
-
@wendy2702 JA, habe den Homemanager 2. Da das in diesem Topic angehängte Dokument von 2014 ist ist die Frage ob es für den HM2 noch gültig ist?
-
@maxpd Kommt eher auf die Kombination Typ WR / SW / Homemanager 2 und dessen SW an.
Du musst dir bei SMA passend zu deinem WR und dessen SW Stand die passenden Register raussuchen.
Mit dem HM2 habe ich mich persönlich bisher nur am rand beschäftigt da ich das Teil nicht habe.
-
@wendy2702 ok, versuche mich schlau zu machen. einen filter werden sie diesbezüglich wohl nicht haben.
-
@maxpd sagte in (gelöst)(Frage) ModubusTCP Adapter ?:
einen filter werden sie diesbezüglich wohl nicht haben
Was meinst du mit Filter?
-
@wendy2702 Ein Filter um die passende kombination für sich auf deren Website zu finden.
Ich habe aber nun über Google eine Excel gefunden in der mein WR drin ist mit der passenden SW. Allerdings ist da keine Spur von Werten, die einen Verbrauch oder Überschuss anzeigen.