  4. [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.2k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.9k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.3k

[Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana

Geplant Angeheftet Gesperrt Verschoben Praktische Anwendungen (Showcase)
solaredgemodbusgrafana
606 Beiträge 91 Kommentatoren 207.6k Aufrufe 99 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • GlasfaserG Glasfaser

    @m1r0o sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

    ich sehe alle Daten, bis auf Ertrag total, Einspeisung total und AC Power total.

    Das Thema ist .. denke ich mal schon geklärt , das es nur über eine feste RS485 Verkabelung vom Smartmeter zum WR vorliegen muß , wenn eine zusätzliche Modbus Abfrage erfolgt ... ( z. B , durch ioBroker , Windows Programm usw. )

    Mhh ... :thinking_face:
    das verstehe ich jetzt nicht , bzw. ist deine Angabe richtig !?

    Ich würde eher sagen , es wird gar nichts vom Smartmeter ausgelesen !?

    Denn der Smartmeter wird ab Register 40123 abgefragt
    und ab da ist alles vorhanden bei dir vorhanden , nur diese 3 Register nicht !?

    Centurytt 0C Offline
    Centurytt 0C Offline
    Centurytt 0
    schrieb am zuletzt editiert von Centurytt 0
    #411

    @glasfaser
    @M1R0O
    Absolut richtig. Steht auch hier beschrieben: https://knowledge-center.solaredge.com/sites/kc/files/sunspec-implementation-technical-note.pdf

    Einige der Adressen hält der WR selbst vor. Aber alles mit Zähler um eben Ertrag Export usw. berechnen zu können brauchts eine verdrahtete Verbindung. Nochmal, ich weiß nicht wer dir den Floh ins Ohr gesetzt hat, dass dieser Typ Zähler eine Wifi Verbindung aufbaut. Das kann das Ding schlichtweg nicht.
    b5014b2a-8b5d-4574-a344-059205d6c44b-image.png

    Deshalb siehst du im Monitoring Portal auch keine Daten zu Ertrag, Verbrauch usw. weil auch Solaredge den Zähler braucht um das zu Berechnen. Oder woher will der WR das alleine wissen wieviel Last auf deinem Netz läuft.

    GlasfaserG M 2 Antworten Letzte Antwort
    0
    • Centurytt 0C Centurytt 0

      @glasfaser
      @M1R0O
      Absolut richtig. Steht auch hier beschrieben: https://knowledge-center.solaredge.com/sites/kc/files/sunspec-implementation-technical-note.pdf

      Einige der Adressen hält der WR selbst vor. Aber alles mit Zähler um eben Ertrag Export usw. berechnen zu können brauchts eine verdrahtete Verbindung. Nochmal, ich weiß nicht wer dir den Floh ins Ohr gesetzt hat, dass dieser Typ Zähler eine Wifi Verbindung aufbaut. Das kann das Ding schlichtweg nicht.
      b5014b2a-8b5d-4574-a344-059205d6c44b-image.png

      Deshalb siehst du im Monitoring Portal auch keine Daten zu Ertrag, Verbrauch usw. weil auch Solaredge den Zähler braucht um das zu Berechnen. Oder woher will der WR das alleine wissen wieviel Last auf deinem Netz läuft.

      GlasfaserG Offline
      GlasfaserG Offline
      Glasfaser
      schrieb am zuletzt editiert von Glasfaser
      #412

      @centurytt-0 sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

      ich weiß nicht wer dir den Floh ins Ohr gesetzt hat, dass dieser Typ Zähler eine Wifi Verbindung aufbaut. Das kann das Ding schlichtweg nicht.

      Alles gut ...
      das war hier nur ein Überbegriff im Thread , dann nennen wir es nich Wlan sondern
      .

      dann so ...Funkfrequenz Kommunikation zwischen Smartmeter und WR :

      c0328198-7edf-4dee-a2b0-b771469f6ab7-grafik.png

      beim SolarEdge Inline Energiezähler MTR-240-3PC1-D-A-MW

      Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

      Centurytt 0C 1 Antwort Letzte Antwort
      0
      • GlasfaserG Glasfaser

        @centurytt-0 sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

        ich weiß nicht wer dir den Floh ins Ohr gesetzt hat, dass dieser Typ Zähler eine Wifi Verbindung aufbaut. Das kann das Ding schlichtweg nicht.

        Alles gut ...
        das war hier nur ein Überbegriff im Thread , dann nennen wir es nich Wlan sondern
        .

        dann so ...Funkfrequenz Kommunikation zwischen Smartmeter und WR :

        c0328198-7edf-4dee-a2b0-b771469f6ab7-grafik.png

        beim SolarEdge Inline Energiezähler MTR-240-3PC1-D-A-MW

        Centurytt 0C Offline
        Centurytt 0C Offline
        Centurytt 0
        schrieb am zuletzt editiert von Centurytt 0
        #413

        @glasfaser

        Ja eh aber er hat den hier: SE-MTR-3Y-400V-A ? der hat keine kabellose Kommunikation ... :-)

        GlasfaserG 1 Antwort Letzte Antwort
        0
        • Centurytt 0C Centurytt 0

          @glasfaser
          @M1R0O
          Absolut richtig. Steht auch hier beschrieben: https://knowledge-center.solaredge.com/sites/kc/files/sunspec-implementation-technical-note.pdf

          Einige der Adressen hält der WR selbst vor. Aber alles mit Zähler um eben Ertrag Export usw. berechnen zu können brauchts eine verdrahtete Verbindung. Nochmal, ich weiß nicht wer dir den Floh ins Ohr gesetzt hat, dass dieser Typ Zähler eine Wifi Verbindung aufbaut. Das kann das Ding schlichtweg nicht.
          b5014b2a-8b5d-4574-a344-059205d6c44b-image.png

          Deshalb siehst du im Monitoring Portal auch keine Daten zu Ertrag, Verbrauch usw. weil auch Solaredge den Zähler braucht um das zu Berechnen. Oder woher will der WR das alleine wissen wieviel Last auf deinem Netz läuft.

          M Offline
          M Offline
          M1R0O
          schrieb am zuletzt editiert von M1R0O
          #414

          @centurytt-0 @Glasfaser
          Ich denke auch dass es geklärt ist.
          Ich weiß nur nicht, ob wir aneinander vorbei reden.
          Auch der MTR-240-3PC1-D-A-MW hat eine drahtlose Kommunikation via Funk.
          Ich sehe über modbus_tcp alle Werte, bis auf die o.g.. Über das Portal von SE oder den direkten WR-Zugang via WLAN erhalte ich alle Werte, auch für Export, Import, etc. Offensichtlich ist hierfür eine RS485 Verbindung nötig.
          Nun ja, ich warte einfach auf die RS485 Verbindung, um auch den Rest via modbus zu erhalten.

          GlasfaserG 1 Antwort Letzte Antwort
          0
          • Centurytt 0C Centurytt 0

            @glasfaser

            Ja eh aber er hat den hier: SE-MTR-3Y-400V-A ? der hat keine kabellose Kommunikation ... :-)

            GlasfaserG Offline
            GlasfaserG Offline
            Glasfaser
            schrieb am zuletzt editiert von Glasfaser
            #415

            @centurytt-0 sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

            Ja eh aber er hat den hier: SE-MTR-3Y-400V-A ?

            Nein , den neuen Inline Energiezähler!!!!

            Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

            Centurytt 0C 1 Antwort Letzte Antwort
            0
            • GlasfaserG Glasfaser

              @centurytt-0 sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

              Ja eh aber er hat den hier: SE-MTR-3Y-400V-A ?

              Nein , den neuen Inline Energiezähler!!!!

              Centurytt 0C Offline
              Centurytt 0C Offline
              Centurytt 0
              schrieb am zuletzt editiert von Centurytt 0
              #416

              @glasfaser

              AAAAsoooo ... ja dann ok alles zurück und sorry für meine Begriffstutzigkeit :-)

              1 Antwort Letzte Antwort
              0
              • M M1R0O

                @centurytt-0 @Glasfaser
                Ich denke auch dass es geklärt ist.
                Ich weiß nur nicht, ob wir aneinander vorbei reden.
                Auch der MTR-240-3PC1-D-A-MW hat eine drahtlose Kommunikation via Funk.
                Ich sehe über modbus_tcp alle Werte, bis auf die o.g.. Über das Portal von SE oder den direkten WR-Zugang via WLAN erhalte ich alle Werte, auch für Export, Import, etc. Offensichtlich ist hierfür eine RS485 Verbindung nötig.
                Nun ja, ich warte einfach auf die RS485 Verbindung, um auch den Rest via modbus zu erhalten.

                GlasfaserG Offline
                GlasfaserG Offline
                Glasfaser
                schrieb am zuletzt editiert von
                #417

                @m1r0o sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                Ich weiß nur nicht, ob wir aneinander vorbei reden.

                ja , denn in den von dir zuvor beigefügten Screenshots sehen ich keine richtigen Werte dazu ,
                auch nicht mal ein aktuell Screenshot wie jetzt aktuell die Datenpunkte dazu gefüllt werden weil du jetzt schreibts ich sehe alles .. außer ...

                Sorry , deshalb ist es hier sehr undeutig und meine Fragen dazu !

                Bitte mal ein aktuelles Screenshot von allen Datenpunkten vom ioBroker !

                Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                M 1 Antwort Letzte Antwort
                0
                • GlasfaserG Glasfaser

                  @m1r0o sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                  Ich weiß nur nicht, ob wir aneinander vorbei reden.

                  ja , denn in den von dir zuvor beigefügten Screenshots sehen ich keine richtigen Werte dazu ,
                  auch nicht mal ein aktuell Screenshot wie jetzt aktuell die Datenpunkte dazu gefüllt werden weil du jetzt schreibts ich sehe alles .. außer ...

                  Sorry , deshalb ist es hier sehr undeutig und meine Fragen dazu !

                  Bitte mal ein aktuelles Screenshot von allen Datenpunkten vom ioBroker !

                  M Offline
                  M Offline
                  M1R0O
                  schrieb am zuletzt editiert von M1R0O
                  #418

                  @glasfaser
                  Hier die Screenshots


                  Bildschirm­foto 2023-08-20 um 14.29.23.png

                  Bildschirm­foto 2023-08-20 um 14.29.35.png

                  Bildschirm­foto 2023-08-20 um 14.29.55.png

                  Wie du siehst, habe ich gerade allerdings ein anderes Problem. Mein WR kann keine Verbindung mehr zum Internet herstellen ("Host wird aufgelöst"). Warum auch immer... ist n anderes Thema

                  GlasfaserG Centurytt 0C 2 Antworten Letzte Antwort
                  0
                  • M M1R0O

                    @glasfaser
                    Hier die Screenshots


                    Bildschirm­foto 2023-08-20 um 14.29.23.png

                    Bildschirm­foto 2023-08-20 um 14.29.35.png

                    Bildschirm­foto 2023-08-20 um 14.29.55.png

                    Wie du siehst, habe ich gerade allerdings ein anderes Problem. Mein WR kann keine Verbindung mehr zum Internet herstellen ("Host wird aufgelöst"). Warum auch immer... ist n anderes Thema

                    GlasfaserG Offline
                    GlasfaserG Offline
                    Glasfaser
                    schrieb am zuletzt editiert von Glasfaser
                    #419

                    @m1r0o

                    Also laut Screenshot schon befüllt ... aber alles Müll / falsche Werte bei den anderen Datenpunkten ab Smartmeter .

                    so sollte es zb. aussehen .

                    ebe82924-6840-4966-8fd5-bbe8fd718338-grafik.png

                    Mhh .

                    hier ist alles 0

                    ist der WR aus !?

                    5ef98b47-b698-4d8d-885b-c35846a60bd6-grafik.png

                    EDIT :

                    Mein WR kann keine Verbindung mehr zum Internet herstellen

                    du fragst doch den WR per interne IP im Modbus ab , da brauchst du doch kein I Net !

                    Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                    M 1 Antwort Letzte Antwort
                    0
                    • GlasfaserG Glasfaser

                      @m1r0o

                      Also laut Screenshot schon befüllt ... aber alles Müll / falsche Werte bei den anderen Datenpunkten ab Smartmeter .

                      so sollte es zb. aussehen .

                      ebe82924-6840-4966-8fd5-bbe8fd718338-grafik.png

                      Mhh .

                      hier ist alles 0

                      ist der WR aus !?

                      5ef98b47-b698-4d8d-885b-c35846a60bd6-grafik.png

                      EDIT :

                      Mein WR kann keine Verbindung mehr zum Internet herstellen

                      du fragst doch den WR per interne IP im Modbus ab , da brauchst du doch kein I Net !

                      M Offline
                      M Offline
                      M1R0O
                      schrieb am zuletzt editiert von
                      #420

                      @glasfaser sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                      @m1r0o

                      Also laut Screenshot schon befüllt ... aber alles Müll / falsche Werte bei den anderen Datenpunkten ab Smartmeter .

                      Ok. Wird dann wohl an der fehlenden Kabelverbindung liegen.

                      @glasfaser sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                      du fragst doch den WR per interne IP im Modbus ab , da brauchst du doch kein I Net !

                      Das stimmt. Ist auch ein anderes Problem.

                      GlasfaserG 1 Antwort Letzte Antwort
                      0
                      • M M1R0O

                        @glasfaser sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                        @m1r0o

                        Also laut Screenshot schon befüllt ... aber alles Müll / falsche Werte bei den anderen Datenpunkten ab Smartmeter .

                        Ok. Wird dann wohl an der fehlenden Kabelverbindung liegen.

                        @glasfaser sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                        du fragst doch den WR per interne IP im Modbus ab , da brauchst du doch kein I Net !

                        Das stimmt. Ist auch ein anderes Problem.

                        GlasfaserG Offline
                        GlasfaserG Offline
                        Glasfaser
                        schrieb am zuletzt editiert von Glasfaser
                        #421

                        @m1r0o

                        Letzter Test ... dieses Interessiert mich noch !
                        ... mit andern Registern

                        Neue Modbus Instanz !!!
                        , dann :

                        _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                        40001	SunSpecID	C_SunSpec_ID		uint32be	2	1	0		state		true	false	false	false
                        40003	SunSpecDID	C_SunSpec_DID		uint16be	1	1	0		state		true	false	false	false
                        40004	SunSpecLength	C_SunSpec_Length		uint16be	1	1	0		state		true	false	false	false
                        40005	Manufacturer	C_Manufacturer		string	16	1	0		state		true	false	false	false
                        40021	Model	C_Model		string	16	1	0		state		true	false	false	false
                        40045	Version	C_Version		string	8	1	0		state		true	false	false	false
                        40053	SerialNumber	C_SerialNumber		string	16	1	0		state		true	false	false	false
                        40069	DeviceAddress	C_DeviceAddress		uint16be	1	1	0		state		true	false	false	false
                        40070	PhaseTypes	C_SunSpec_DID		uint16be	1	1	0		state		true	false	false	false
                        40071	SunSpecLength	C_SunSpec_Length		uint16be	1	1	0		state		true	false	false	false
                        40072	CurrentTotal	I_AC_Current	A	uint16be	1	1	0		value		true	false	false	false
                        40073	CurrentL1	I_AC_CurrentA	A	uint16be	1	1	0		value		true	false	false	false
                        40074	CurrentL2	I_AC_CurrentB	A	uint16be	1	1	0		value		true	false	false	false
                        40075	CurrentL3	I_AC_CurrentC	A	uint16be	1	1	0		value		true	false	false	false
                        40076	CurrentSF	I_AC_Current_SF		int16be	1	1	0		state		true	false	false	false
                        40080	VoltageL1N	I_AC_VoltageAN	V	uint16be	1	1	0		value		true	false	false	false
                        40081	VoltageL2N	I_AC_VoltageBN	V	uint16be	1	1	0		value		true	false	false	false
                        40082	VoltageL3N	I_AC_VoltageCN	V	uint16be	1	1	0		value		true	false	false	false
                        40083	VoltageSF	I_AC_Voltage_SF		int16be	1	1	0		state		true	false	false	false
                        40084	Power	I_AC_Power	W	uint16be	1	1	0		value		true	false	false	false
                        40085	PowerSF	I_AC_Power_SF		int16be	1	1	0		state		true	false	false	false
                        40086	Frequency	I_AC_Frequency	Hz	uint16be	1	1	0		value		true	false	false	false
                        40087	FrequencySF	I_AC_Frequency_SF		int16be	1	1	0		state		true	false	false	false
                        40088	VA	I_AC_VA	VA	int16be	1	1	0		value		true	false	false	false
                        40089	VASF	I_AC_VA_SF		int16be	1	1	0		state		true	false	false	false
                        40090	VAR	I_AC_VAR	VAR	int16be	1	1	0		value		true	false	false	false
                        40091	VARSF	I_AC_VAR_SF		int16be	1	1	0		state		true	false	false	false
                        40092	PF	I_AC_PF	%	int16be	1	1	0		value		true	false	false	false
                        40093	PFSF	I_AC_PF_SF		int16be	1	1	0		state		true	false	false	false
                        40094	TotalEnergy	I_AC_Energy_WH	Wh	uint32be	2	1	0		value		true	false	false	false
                        40096	TotalEnergySF	I_AC_Energy_WH_SF		int16be	1	1	0		state		true	false	false	false
                        40097	DCCurrent	I_DC_Current	A	uint16be	1	1	0		value		true	false	false	false
                        40098	DCCurrentSF	I_DC_Current_SF		int16be	1	1	0		state		true	false	false	false
                        40099	DCVoltage	I_DC_Voltage	V	uint16be	1	1	0		value		true	false	false	false
                        40100	DCVoltageSF	I_DC_Voltage_SF		int16be	1	1	0		state		true	false	false	false
                        40101	DCPower	I_DC_Power	W	int16be	1	1	0		value		true	false	false	false
                        40102	DCPowerSF	I_DC_Power_SF		int16be	1	1	0		state		true	false	false	false
                        40104	Temp	I_Temp_SF		int16be	1	1	0		state		true	false	false	false
                        40107	TempSF	I_Temp_Sink	°C	int16be	1	1	0		value		true	false	false	false
                        40108	Status	I_Status		uint16be	1	1	0		state		true	false	false	false
                        40109	StatusVendor	I_Status_Vendor		uint16be	1	1	0		state		true	false	false	false
                        40140	MeterModel	M_C_Model		string	16	1	0		state		true	false	false	false
                        40164	MeterVersion	M_C_Version		string	8	1	0		state		true	false	false	false
                        40172	MeterSerialNumber	M_C_SerialNumber		string	16	1	0		state		true	false	false	false
                        40191	MeterCurrentTotal	M_AC_Current	A	int16be	1	1	0		value		true	false	false	false
                        40192	MeterCurrentL1	M_AC_Current_A	A	int16be	1	1	0		value		true	false	false	false
                        40193	MeterCurrentL2	M_AC_Current_B	A	int16be	1	1	0		value		true	false	false	false
                        40194	MeterCurrentL3	M_AC_Current_C	A	int16be	1	1	0		value		true	false	false	false
                        40195	MeterCurrentSF	M_AC_Current_SF		int16be	1	1	0		state		true	false	false	false
                        40196	MeterVoltageLN	M_AC_Voltage_L_N	V	int16be	1	1	0		value		true	false	false	false
                        40197	MeterVoltageL1N	M_AC_Voltage_A_N	V	int16be	1	1	0		value		true	false	false	false
                        40198	MeterVoltageL2N	M_AC_Voltage_B_N	V	int16be	1	1	0		value		true	false	false	false
                        40199	MeterVoltageL3N	M_AC_Voltage_C_N	V	int16be	1	1	0		value		true	false	false	false
                        40204	MeterVoltageSF	M_AC_Voltage_SF		int16be	1	1	0		state		true	false	false	false
                        40205	MeterFrequency	M_AC_Freq	Hz	int16be	1	1	0		value		true	false	false	false
                        40206	MeterFrequencySF	M_AC_Freq_SF		int16be	1	1	0		state		true	false	false	false
                        40207	MeterPowerTotal	M_AC_Power	W	int16be	1	1	0		value		true	false	false	false
                        40208	MeterPowerL1	M_AC_Power_A	W	int16be	1	1	0		value		true	false	false	false
                        40209	MeterPowerL2	M_AC_Power_B	W	int16be	1	1	0		value		true	false	false	false
                        40210	MeterPowerL3	M_AC_Power_C	W	int16be	1	1	0		value		true	false	false	false
                        40211	MeterPowerSF	M_AC_Power_SF		int16be	1	1	0		state		true	false	false	false
                        40212	MeterApparentPowerTotal	M_AC_VA	VA	int16be	1	1	0		value		true	false	false	false
                        40213	MeterApparentPowerL1	M_AC_VA_A	VA	int16be	1	1	0		value		true	false	false	false
                        40214	MeterApparentPowerL2	M_AC_VA_B	VA	int16be	1	1	0		value		true	false	false	false
                        40215	MeterApparentPowerL3	M_AC_VA_C	VA	int16be	1	1	0		value		true	false	false	false
                        40216	MeterApparentPowerSF	M_AC_VA_SF		int16be	1	1	0		state		true	false	false	false
                        40217	MeterReactivePowerTotal	M_AC_VAR	VAR	int16be	1	1	0		value		true	false	false	false
                        40218	MeterReactivePowerL1	M_AC_VAR_A	VAR	int16be	1	1	0		value		true	false	false	false
                        40219	MeterReactivePowerL2	M_AC_VAR_B	VAR	int16be	1	1	0		value		true	false	false	false
                        40220	MeterReactivePowerL3	M_AC_VAR_C	VAR	int16be	1	1	0		value		true	false	false	false
                        40221	MeterReactivePowerSF	M_AC_VAR_SF		int16be	1	1	0		state		true	false	false	false
                        40227	MeterEnergyExportedTotal	M_Exported	Wh	uint32be	2	1	0		value		true	false	false	false
                        40229	MeterEnergyExportedL1	M_Exported_A	Wh	uint32be	2	1	0		value		true	false	false	false
                        40231	MeterEnergyExportedL2	M_Exported_B	Wh	uint32be	2	1	0		value		true	false	false	false
                        40233	MeterEnergyExportedL3	M_Exported_C	Wh	uint32be	2	1	0		value		true	false	false	false
                        40235	MeterEnergyImportedTotal	M_Imported	Wh	uint32be	2	1	0		value		true	false	false	false
                        40237	MeterEnergyImportedL1	M_Imported_A	Wh	uint32be	2	1	0		value		true	false	false	false
                        40239	MeterEnergyImportedL2	M_Imported_B	Wh	uint32be	2	1	0		value		true	false	false	false
                        40241	MeterEnergyImportedL3	M_Imported_C	Wh	uint32be	2	1	0		value		true	false	false	false
                        40243	MeterEnergySF	M_Energy_W_SF		int16be	1	1	0		state		true	false	false	false
                        

                        Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                        M 1 Antwort Letzte Antwort
                        0
                        • GlasfaserG Glasfaser

                          @m1r0o

                          Letzter Test ... dieses Interessiert mich noch !
                          ... mit andern Registern

                          Neue Modbus Instanz !!!
                          , dann :

                          _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                          40001	SunSpecID	C_SunSpec_ID		uint32be	2	1	0		state		true	false	false	false
                          40003	SunSpecDID	C_SunSpec_DID		uint16be	1	1	0		state		true	false	false	false
                          40004	SunSpecLength	C_SunSpec_Length		uint16be	1	1	0		state		true	false	false	false
                          40005	Manufacturer	C_Manufacturer		string	16	1	0		state		true	false	false	false
                          40021	Model	C_Model		string	16	1	0		state		true	false	false	false
                          40045	Version	C_Version		string	8	1	0		state		true	false	false	false
                          40053	SerialNumber	C_SerialNumber		string	16	1	0		state		true	false	false	false
                          40069	DeviceAddress	C_DeviceAddress		uint16be	1	1	0		state		true	false	false	false
                          40070	PhaseTypes	C_SunSpec_DID		uint16be	1	1	0		state		true	false	false	false
                          40071	SunSpecLength	C_SunSpec_Length		uint16be	1	1	0		state		true	false	false	false
                          40072	CurrentTotal	I_AC_Current	A	uint16be	1	1	0		value		true	false	false	false
                          40073	CurrentL1	I_AC_CurrentA	A	uint16be	1	1	0		value		true	false	false	false
                          40074	CurrentL2	I_AC_CurrentB	A	uint16be	1	1	0		value		true	false	false	false
                          40075	CurrentL3	I_AC_CurrentC	A	uint16be	1	1	0		value		true	false	false	false
                          40076	CurrentSF	I_AC_Current_SF		int16be	1	1	0		state		true	false	false	false
                          40080	VoltageL1N	I_AC_VoltageAN	V	uint16be	1	1	0		value		true	false	false	false
                          40081	VoltageL2N	I_AC_VoltageBN	V	uint16be	1	1	0		value		true	false	false	false
                          40082	VoltageL3N	I_AC_VoltageCN	V	uint16be	1	1	0		value		true	false	false	false
                          40083	VoltageSF	I_AC_Voltage_SF		int16be	1	1	0		state		true	false	false	false
                          40084	Power	I_AC_Power	W	uint16be	1	1	0		value		true	false	false	false
                          40085	PowerSF	I_AC_Power_SF		int16be	1	1	0		state		true	false	false	false
                          40086	Frequency	I_AC_Frequency	Hz	uint16be	1	1	0		value		true	false	false	false
                          40087	FrequencySF	I_AC_Frequency_SF		int16be	1	1	0		state		true	false	false	false
                          40088	VA	I_AC_VA	VA	int16be	1	1	0		value		true	false	false	false
                          40089	VASF	I_AC_VA_SF		int16be	1	1	0		state		true	false	false	false
                          40090	VAR	I_AC_VAR	VAR	int16be	1	1	0		value		true	false	false	false
                          40091	VARSF	I_AC_VAR_SF		int16be	1	1	0		state		true	false	false	false
                          40092	PF	I_AC_PF	%	int16be	1	1	0		value		true	false	false	false
                          40093	PFSF	I_AC_PF_SF		int16be	1	1	0		state		true	false	false	false
                          40094	TotalEnergy	I_AC_Energy_WH	Wh	uint32be	2	1	0		value		true	false	false	false
                          40096	TotalEnergySF	I_AC_Energy_WH_SF		int16be	1	1	0		state		true	false	false	false
                          40097	DCCurrent	I_DC_Current	A	uint16be	1	1	0		value		true	false	false	false
                          40098	DCCurrentSF	I_DC_Current_SF		int16be	1	1	0		state		true	false	false	false
                          40099	DCVoltage	I_DC_Voltage	V	uint16be	1	1	0		value		true	false	false	false
                          40100	DCVoltageSF	I_DC_Voltage_SF		int16be	1	1	0		state		true	false	false	false
                          40101	DCPower	I_DC_Power	W	int16be	1	1	0		value		true	false	false	false
                          40102	DCPowerSF	I_DC_Power_SF		int16be	1	1	0		state		true	false	false	false
                          40104	Temp	I_Temp_SF		int16be	1	1	0		state		true	false	false	false
                          40107	TempSF	I_Temp_Sink	°C	int16be	1	1	0		value		true	false	false	false
                          40108	Status	I_Status		uint16be	1	1	0		state		true	false	false	false
                          40109	StatusVendor	I_Status_Vendor		uint16be	1	1	0		state		true	false	false	false
                          40140	MeterModel	M_C_Model		string	16	1	0		state		true	false	false	false
                          40164	MeterVersion	M_C_Version		string	8	1	0		state		true	false	false	false
                          40172	MeterSerialNumber	M_C_SerialNumber		string	16	1	0		state		true	false	false	false
                          40191	MeterCurrentTotal	M_AC_Current	A	int16be	1	1	0		value		true	false	false	false
                          40192	MeterCurrentL1	M_AC_Current_A	A	int16be	1	1	0		value		true	false	false	false
                          40193	MeterCurrentL2	M_AC_Current_B	A	int16be	1	1	0		value		true	false	false	false
                          40194	MeterCurrentL3	M_AC_Current_C	A	int16be	1	1	0		value		true	false	false	false
                          40195	MeterCurrentSF	M_AC_Current_SF		int16be	1	1	0		state		true	false	false	false
                          40196	MeterVoltageLN	M_AC_Voltage_L_N	V	int16be	1	1	0		value		true	false	false	false
                          40197	MeterVoltageL1N	M_AC_Voltage_A_N	V	int16be	1	1	0		value		true	false	false	false
                          40198	MeterVoltageL2N	M_AC_Voltage_B_N	V	int16be	1	1	0		value		true	false	false	false
                          40199	MeterVoltageL3N	M_AC_Voltage_C_N	V	int16be	1	1	0		value		true	false	false	false
                          40204	MeterVoltageSF	M_AC_Voltage_SF		int16be	1	1	0		state		true	false	false	false
                          40205	MeterFrequency	M_AC_Freq	Hz	int16be	1	1	0		value		true	false	false	false
                          40206	MeterFrequencySF	M_AC_Freq_SF		int16be	1	1	0		state		true	false	false	false
                          40207	MeterPowerTotal	M_AC_Power	W	int16be	1	1	0		value		true	false	false	false
                          40208	MeterPowerL1	M_AC_Power_A	W	int16be	1	1	0		value		true	false	false	false
                          40209	MeterPowerL2	M_AC_Power_B	W	int16be	1	1	0		value		true	false	false	false
                          40210	MeterPowerL3	M_AC_Power_C	W	int16be	1	1	0		value		true	false	false	false
                          40211	MeterPowerSF	M_AC_Power_SF		int16be	1	1	0		state		true	false	false	false
                          40212	MeterApparentPowerTotal	M_AC_VA	VA	int16be	1	1	0		value		true	false	false	false
                          40213	MeterApparentPowerL1	M_AC_VA_A	VA	int16be	1	1	0		value		true	false	false	false
                          40214	MeterApparentPowerL2	M_AC_VA_B	VA	int16be	1	1	0		value		true	false	false	false
                          40215	MeterApparentPowerL3	M_AC_VA_C	VA	int16be	1	1	0		value		true	false	false	false
                          40216	MeterApparentPowerSF	M_AC_VA_SF		int16be	1	1	0		state		true	false	false	false
                          40217	MeterReactivePowerTotal	M_AC_VAR	VAR	int16be	1	1	0		value		true	false	false	false
                          40218	MeterReactivePowerL1	M_AC_VAR_A	VAR	int16be	1	1	0		value		true	false	false	false
                          40219	MeterReactivePowerL2	M_AC_VAR_B	VAR	int16be	1	1	0		value		true	false	false	false
                          40220	MeterReactivePowerL3	M_AC_VAR_C	VAR	int16be	1	1	0		value		true	false	false	false
                          40221	MeterReactivePowerSF	M_AC_VAR_SF		int16be	1	1	0		state		true	false	false	false
                          40227	MeterEnergyExportedTotal	M_Exported	Wh	uint32be	2	1	0		value		true	false	false	false
                          40229	MeterEnergyExportedL1	M_Exported_A	Wh	uint32be	2	1	0		value		true	false	false	false
                          40231	MeterEnergyExportedL2	M_Exported_B	Wh	uint32be	2	1	0		value		true	false	false	false
                          40233	MeterEnergyExportedL3	M_Exported_C	Wh	uint32be	2	1	0		value		true	false	false	false
                          40235	MeterEnergyImportedTotal	M_Imported	Wh	uint32be	2	1	0		value		true	false	false	false
                          40237	MeterEnergyImportedL1	M_Imported_A	Wh	uint32be	2	1	0		value		true	false	false	false
                          40239	MeterEnergyImportedL2	M_Imported_B	Wh	uint32be	2	1	0		value		true	false	false	false
                          40241	MeterEnergyImportedL3	M_Imported_C	Wh	uint32be	2	1	0		value		true	false	false	false
                          40243	MeterEnergySF	M_Energy_W_SF		int16be	1	1	0		state		true	false	false	false
                          

                          M Offline
                          M Offline
                          M1R0O
                          schrieb am zuletzt editiert von
                          #422

                          @glasfaser
                          Kann ich so nicht importieren:
                          Bildschirm­foto 2023-08-20 um 15.10.11.png

                          GlasfaserG L 2 Antworten Letzte Antwort
                          0
                          • M M1R0O

                            @glasfaser
                            Kann ich so nicht importieren:
                            Bildschirm­foto 2023-08-20 um 15.10.11.png

                            GlasfaserG Offline
                            GlasfaserG Offline
                            Glasfaser
                            schrieb am zuletzt editiert von
                            #423

                            @m1r0o

                            funktioniert ohne Fehlermeldung der Import .

                            159b9739-a477-4300-bc69-9edaeb91b9d3-grafik.png

                            Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                            M 1 Antwort Letzte Antwort
                            0
                            • M M1R0O

                              @glasfaser
                              Kann ich so nicht importieren:
                              Bildschirm­foto 2023-08-20 um 15.10.11.png

                              L Offline
                              L Offline
                              lisalisa
                              schrieb am zuletzt editiert von
                              #424

                              @m1r0o die erste Zeile nicht kopieren, die ist bei dir doppelt
                              _address name description unit type len factor offset formula role room poll wp cw isScale

                              1 Antwort Letzte Antwort
                              0
                              • GlasfaserG Glasfaser

                                @m1r0o

                                funktioniert ohne Fehlermeldung der Import .

                                159b9739-a477-4300-bc69-9edaeb91b9d3-grafik.png

                                M Offline
                                M Offline
                                M1R0O
                                schrieb am zuletzt editiert von M1R0O
                                #425

                                @glasfaser

                                Bei mir nicht, keine Ahnung warum. Immder der gleiche Fehler

                                @lisalisa sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                                @m1r0o die erste Zeile nicht kopieren, die ist bei dir doppelt
                                _address name description unit type len factor offset formula role room poll wp cw isScale

                                ändert nichts

                                L GlasfaserG 2 Antworten Letzte Antwort
                                0
                                • M M1R0O

                                  @glasfaser

                                  Bei mir nicht, keine Ahnung warum. Immder der gleiche Fehler

                                  @lisalisa sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                                  @m1r0o die erste Zeile nicht kopieren, die ist bei dir doppelt
                                  _address name description unit type len factor offset formula role room poll wp cw isScale

                                  ändert nichts

                                  L Offline
                                  L Offline
                                  lisalisa
                                  schrieb am zuletzt editiert von lisalisa
                                  #426

                                  @m1r0o teste mal Import mit oder ohne "Erweiterten Modus", Kopf blau oder schwarz
                                  1e8b287e-8b84-4482-9380-6c5980d833f3-image.png

                                  1 Antwort Letzte Antwort
                                  0
                                  • M M1R0O

                                    @glasfaser

                                    Bei mir nicht, keine Ahnung warum. Immder der gleiche Fehler

                                    @lisalisa sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                                    @m1r0o die erste Zeile nicht kopieren, die ist bei dir doppelt
                                    _address name description unit type len factor offset formula role room poll wp cw isScale

                                    ändert nichts

                                    GlasfaserG Offline
                                    GlasfaserG Offline
                                    Glasfaser
                                    schrieb am zuletzt editiert von
                                    #427

                                    @m1r0o

                                    der Eintrag bei 0 ist doppelt

                                    79881d15-dd57-4e6e-b8e9-45907011e326-grafik.png

                                    Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                                    1 Antwort Letzte Antwort
                                    0
                                    • M Offline
                                      M Offline
                                      M1R0O
                                      schrieb am zuletzt editiert von M1R0O
                                      #428

                                      @lisalisa @Glasfaser
                                      1 von beidem hat funktioniert.

                                      Werte sind aber alle 0
                                      Bildschirm­foto 2023-08-20 um 15.39.06.png

                                      GlasfaserG 1 Antwort Letzte Antwort
                                      0
                                      • M M1R0O

                                        @lisalisa @Glasfaser
                                        1 von beidem hat funktioniert.

                                        Werte sind aber alle 0
                                        Bildschirm­foto 2023-08-20 um 15.39.06.png

                                        GlasfaserG Offline
                                        GlasfaserG Offline
                                        Glasfaser
                                        schrieb am zuletzt editiert von
                                        #429

                                        @m1r0o

                                        ... dann warten wir auf die Festverkabelung RS485 von dir .

                                        ... mehr weiß ich leider auch nicht , war ein Versuch Wert !

                                        Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                                        M 2 Antworten Letzte Antwort
                                        0
                                        • GlasfaserG Glasfaser

                                          @m1r0o

                                          ... dann warten wir auf die Festverkabelung RS485 von dir .

                                          ... mehr weiß ich leider auch nicht , war ein Versuch Wert !

                                          M Offline
                                          M Offline
                                          M1R0O
                                          schrieb am zuletzt editiert von
                                          #430

                                          @glasfaser
                                          Auf jeden Fall. Tausend Dank an dich und alle HelferInnen

                                          1 Antwort Letzte Antwort
                                          2
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          648

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe