  4. Einrichten Modbus Adapter / Solar X3 Gen4

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.6k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.1k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.0k

Einrichten Modbus Adapter / Solar X3 Gen4

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
147 Beiträge 19 Kommentatoren 20.5k Aufrufe 18 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • wendy2702W Online
    wendy2702W Online
    wendy2702
    schrieb am zuletzt editiert von
    #35

    @mcwoolf sagte in Einrichten Modbus Adapter / Solar X3 Gen4:

    PE11

    Das Gerät kenne ich nicht. Aber zweimal Server ist eigentlich falsch.

    Man hat immer einen Server und mindestens einen Client.

    Bitte keine Fragen per PN, die gehören ins Forum!

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    McWoolfM 1 Antwort Letzte Antwort
    0
    • wendy2702W wendy2702

      @mcwoolf sagte in Einrichten Modbus Adapter / Solar X3 Gen4:

      PE11

      Das Gerät kenne ich nicht. Aber zweimal Server ist eigentlich falsch.

      Man hat immer einen Server und mindestens einen Client.

      McWoolfM Offline
      McWoolfM Offline
      McWoolf
      schrieb am zuletzt editiert von
      #36

      @wendy2702
      Ja das denke ich auch, aber anders bekomme ich keine Verbindung.

      Lieben Dank an die Helfer hier.
      GLG Wolfi

      Configuration:
      Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
      RAM: 8 GB

      JS-controler: 5.0.17
      Node.js: 18.19.0
      NPM: 10.2.3

      wendy2702W 1 Antwort Letzte Antwort
      0
      • McWoolfM McWoolf

        @wendy2702
        Ja das denke ich auch, aber anders bekomme ich keine Verbindung.

        wendy2702W Online
        wendy2702W Online
        wendy2702
        schrieb am zuletzt editiert von
        #37

        @mcwoolf Mit dem Device kann ich dir leider nicht helfen.

        Sorry

        Bitte keine Fragen per PN, die gehören ins Forum!

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        McWoolfM 1 Antwort Letzte Antwort
        0
        • wendy2702W wendy2702

          @mcwoolf Mit dem Device kann ich dir leider nicht helfen.

          Sorry

          McWoolfM Offline
          McWoolfM Offline
          McWoolf
          schrieb am zuletzt editiert von McWoolf
          #38

          @wendy2702

          Die Verbindung ist auch nicht wirklich mehr das Problem, nur eben dass ich keine Daten aus dem Solax raus bekommen. Sobald ich ein Eingangsregister in den Modbus-Adapter eintrage, kommen diese Meldungen. s.O.

          2dbe2294-b3ab-4e41-bf86-367fadb61cb8-image.png
          e612c0d0-4349-4e94-a425-c679304088ab-image.png
          4af9b57d-28cf-4e33-88a4-69675180e63d-image.png
          5c2855fb-b313-4f11-a2b5-cebecceeae54-image.png

          Lieben Dank an die Helfer hier.
          GLG Wolfi

          Configuration:
          Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
          RAM: 8 GB

          JS-controler: 5.0.17
          Node.js: 18.19.0
          NPM: 10.2.3

          wendy2702W 1 Antwort Letzte Antwort
          0
          • McWoolfM McWoolf

            @wendy2702

            Die Verbindung ist auch nicht wirklich mehr das Problem, nur eben dass ich keine Daten aus dem Solax raus bekommen. Sobald ich ein Eingangsregister in den Modbus-Adapter eintrage, kommen diese Meldungen. s.O.

            2dbe2294-b3ab-4e41-bf86-367fadb61cb8-image.png
            e612c0d0-4349-4e94-a425-c679304088ab-image.png
            4af9b57d-28cf-4e33-88a4-69675180e63d-image.png
            5c2855fb-b313-4f11-a2b5-cebecceeae54-image.png

            wendy2702W Online
            wendy2702W Online
            wendy2702
            schrieb am zuletzt editiert von
            #39

            @mcwoolf Kannst du mal im Adapter auf TCP stellen. Die Umsetzung RTU --> TCP sollte doch das Gateway schon machen.

            Bitte keine Fragen per PN, die gehören ins Forum!

            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

            McWoolfM 1 Antwort Letzte Antwort
            0
            • wendy2702W wendy2702

              @mcwoolf Kannst du mal im Adapter auf TCP stellen. Die Umsetzung RTU --> TCP sollte doch das Gateway schon machen.

              McWoolfM Offline
              McWoolfM Offline
              McWoolf
              schrieb am zuletzt editiert von
              #40

              @wendy2702
              Verbindung steht --> dennoch keine Daten.

              Kannst du bitte mal meine Einstellungen kontrollieren?

              e37d16e7-9dbc-4a76-9d8b-4daf129d5d0c-image.png

              2415e68c-443a-467a-b855-3c1e8dd2f3a9-image.png

              stimmt das so??

              Lieben Dank an die Helfer hier.
              GLG Wolfi

              Configuration:
              Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
              RAM: 8 GB

              JS-controler: 5.0.17
              Node.js: 18.19.0
              NPM: 10.2.3

              wendy2702W 1 Antwort Letzte Antwort
              0
              • McWoolfM McWoolf

                @wendy2702
                Verbindung steht --> dennoch keine Daten.

                Kannst du bitte mal meine Einstellungen kontrollieren?

                e37d16e7-9dbc-4a76-9d8b-4daf129d5d0c-image.png

                2415e68c-443a-467a-b855-3c1e8dd2f3a9-image.png

                stimmt das so??

                wendy2702W Online
                wendy2702W Online
                wendy2702
                schrieb am zuletzt editiert von
                #41

                @mcwoolf Hast du das bei Holding eingetragen?

                Kannst du mal das komplette Modbus Doc bereitstellen oder nimm mal einen "einfachen" Wert wie Spannung oder Temperature.

                Function Code 03 sind eigentlich Holding Register Wie kommst du an die 40000 ?

                Bitte keine Fragen per PN, die gehören ins Forum!

                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                McWoolfM 1 Antwort Letzte Antwort
                0
                • wendy2702W wendy2702

                  @mcwoolf Hast du das bei Holding eingetragen?

                  Kannst du mal das komplette Modbus Doc bereitstellen oder nimm mal einen "einfachen" Wert wie Spannung oder Temperature.

                  Function Code 03 sind eigentlich Holding Register Wie kommst du an die 40000 ?

                  McWoolfM Offline
                  McWoolfM Offline
                  McWoolf
                  schrieb am zuletzt editiert von McWoolf
                  #42

                  @wendy2702
                  Ja war bei Holding eingetragen, ich bilde mir ein Matthias Kleine hat das gesagt dass Holding 40000 und Eingangsregister 30000 sind. deshalb.

                  Hybrid-X1X3-G4-ModbusTCPRTU-V3.21-English_0622-public-version.pdf

                  Das ist die komplette Doku

                  Lieben Dank an die Helfer hier.
                  GLG Wolfi

                  Configuration:
                  Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
                  RAM: 8 GB

                  JS-controler: 5.0.17
                  Node.js: 18.19.0
                  NPM: 10.2.3

                  McWoolfM 1 Antwort Letzte Antwort
                  0
                  • McWoolfM McWoolf

                    @wendy2702
                    Ja war bei Holding eingetragen, ich bilde mir ein Matthias Kleine hat das gesagt dass Holding 40000 und Eingangsregister 30000 sind. deshalb.

                    Hybrid-X1X3-G4-ModbusTCPRTU-V3.21-English_0622-public-version.pdf

                    Das ist die komplette Doku

                    McWoolfM Offline
                    McWoolfM Offline
                    McWoolf
                    schrieb am zuletzt editiert von
                    #43

                    @mcwoolf sagte in Einrichten Modbus Adapter / Solar X3 Gen4:

                    @wendy2702
                    Ja war bei Holding eingetragen, ich bilde mir ein Matthias Kleine hat das gesagt dass Holding 40000 und Eingangsregister 30000 sind. deshalb.

                    Hybrid-X1X3-G4-ModbusTCPRTU-V3.21-English_0622-public-version.pdf

                    Das ist die komplette Doku

                    2023-01-20 13:06:32.652 - info: modbus.0 (7038) Connected to slave 192.168.1.244
                    2023-01-20 13:06:37.655 - warn: modbus.0 (7038) Error: undefined
                    2023-01-20 13:06:37.655 - error: modbus.0 (7038) Request timed out.
                    2023-01-20 13:06:37.655 - error: modbus.0 (7038) Client in error state.
                    2023-01-20 13:06:37.656 - warn: modbus.0 (7038) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                    2023-01-20 13:06:38.655 - info: modbus.0 (7038) Disconnected from slave 192.168.1.244
                    

                    23ec069e-a118-44f2-8f4a-9f74b2764a21-image.png
                    Das kommt sobald ich ein Eingangsregister anlege.

                    Lieben Dank an die Helfer hier.
                    GLG Wolfi

                    Configuration:
                    Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
                    RAM: 8 GB

                    JS-controler: 5.0.17
                    Node.js: 18.19.0
                    NPM: 10.2.3

                    wendy2702W 1 Antwort Letzte Antwort
                    0
                    • McWoolfM McWoolf

                      @mcwoolf sagte in Einrichten Modbus Adapter / Solar X3 Gen4:

                      @wendy2702
                      Ja war bei Holding eingetragen, ich bilde mir ein Matthias Kleine hat das gesagt dass Holding 40000 und Eingangsregister 30000 sind. deshalb.

                      Hybrid-X1X3-G4-ModbusTCPRTU-V3.21-English_0622-public-version.pdf

                      Das ist die komplette Doku

                      2023-01-20 13:06:32.652 - info: modbus.0 (7038) Connected to slave 192.168.1.244
                      2023-01-20 13:06:37.655 - warn: modbus.0 (7038) Error: undefined
                      2023-01-20 13:06:37.655 - error: modbus.0 (7038) Request timed out.
                      2023-01-20 13:06:37.655 - error: modbus.0 (7038) Client in error state.
                      2023-01-20 13:06:37.656 - warn: modbus.0 (7038) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                      2023-01-20 13:06:38.655 - info: modbus.0 (7038) Disconnected from slave 192.168.1.244
                      

                      23ec069e-a118-44f2-8f4a-9f74b2764a21-image.png
                      Das kommt sobald ich ein Eingangsregister anlege.

                      wendy2702W Online
                      wendy2702W Online
                      wendy2702
                      schrieb am zuletzt editiert von
                      #44

                      @mcwoolf Ich schreibe mal auf was mir so auffällt.

                      DOKU WR ID = 1 ---- Adapter = 2 laut Screenshot
                      Doku Port 502 --- Adapter 26

                      Dann sollte aus meiner Sicht iobroker der Master sein und das Gateway Slave. Master - Master funktioniert aus meiner Sicht und Kenntnisstand nicht, lasse mich aber gerne belehren.

                      Dann im Eingangsregister, und nur dort ein Register "0" eintragen mit Unsigned 16 bit little endian.

                      Was kann man hier für Protocol auswählen:

                      8a60677e-a6ae-4c97-9f17-69150a49409b-grafik.png

                      und hier:

                      e2a89823-cf74-4d74-8576-2a0b80518c9c-grafik.png

                      Bitte keine Fragen per PN, die gehören ins Forum!

                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                      McWoolfM 1 Antwort Letzte Antwort
                      0
                      • wendy2702W wendy2702

                        @mcwoolf Ich schreibe mal auf was mir so auffällt.

                        DOKU WR ID = 1 ---- Adapter = 2 laut Screenshot
                        Doku Port 502 --- Adapter 26

                        Dann sollte aus meiner Sicht iobroker der Master sein und das Gateway Slave. Master - Master funktioniert aus meiner Sicht und Kenntnisstand nicht, lasse mich aber gerne belehren.

                        Dann im Eingangsregister, und nur dort ein Register "0" eintragen mit Unsigned 16 bit little endian.

                        Was kann man hier für Protocol auswählen:

                        8a60677e-a6ae-4c97-9f17-69150a49409b-grafik.png

                        und hier:

                        e2a89823-cf74-4d74-8576-2a0b80518c9c-grafik.png

                        McWoolfM Offline
                        McWoolfM Offline
                        McWoolf
                        schrieb am zuletzt editiert von
                        #45

                        @wendy2702

                        m WR ist auch die ID auf 2 gestellt
                        in der Doku ist auch der Port des WR, ich habe aber einen PE11 dazwischen und bei dem ist Port 26 eingetragen.
                        Oder bin ich da auch auf dem Holzweg??
                        Bei Protokoll habe ich jetzt mal auf "modbus" gestellt :dizzy_face:

                        Lieben Dank an die Helfer hier.
                        GLG Wolfi

                        Configuration:
                        Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
                        RAM: 8 GB

                        JS-controler: 5.0.17
                        Node.js: 18.19.0
                        NPM: 10.2.3

                        McWoolfM 1 Antwort Letzte Antwort
                        0
                        • McWoolfM McWoolf

                          @wendy2702

                          m WR ist auch die ID auf 2 gestellt
                          in der Doku ist auch der Port des WR, ich habe aber einen PE11 dazwischen und bei dem ist Port 26 eingetragen.
                          Oder bin ich da auch auf dem Holzweg??
                          Bei Protokoll habe ich jetzt mal auf "modbus" gestellt :dizzy_face:

                          McWoolfM Offline
                          McWoolfM Offline
                          McWoolf
                          schrieb am zuletzt editiert von
                          #46

                          @mcwoolf sagte in Einrichten Modbus Adapter / Solar X3 Gen4:

                          @wendy2702

                          m WR ist auch die ID auf 2 gestellt
                          in der Doku ist auch der Port des WR, ich habe aber einen PE11 dazwischen und bei dem ist Port 26 eingetragen.
                          Oder bin ich da auch auf dem Holzweg??
                          Bei Protokoll habe ich jetzt mal auf "modbus" gestellt :dizzy_face:

                          Hier die aktuellen Einstellungen des Umsetzers:

                          f4d7edb5-ee7e-4143-aca6-5414b2053b2f-image.png

                          420de46c-7062-4bb8-b087-7641711ff502-image.png

                          und vom modbus-adapter

                          6a3b994d-b582-4ba4-be12-91216e181516-image.png

                          dc9c6028-e72a-4a63-9f65-778fc98c9dfb-image.png

                          und das aktuelle Log:

                          2023-01-20 17:30:55.132 - error: modbus.0 (12400) Socket Error
                          2023-01-20 17:30:55.132 - error: modbus.0 (12400) Client in error state.
                          2023-01-20 17:30:55.132 - warn: modbus.0 (12400) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                          2023-01-20 17:30:55.132 - debug: modbus.0 (12400) Socket closed with error
                          2023-01-20 17:30:55.132 - debug: modbus.0 (12400) Cleaning up request fifo.
                          2023-01-20 17:30:56.133 - debug: modbus.0 (12400) Closing client on purpose.
                          2023-01-20 17:31:27.642 - info: shelly.0 (1420) [MQTT] Client Disconnect: 192.168.30.40 (shellyht / shellyht-024898 / SHHT-1#024898#1)
                          2023-01-20 17:31:56.135 - error: modbus.0 (12400) Socket Error
                          2023-01-20 17:31:56.135 - error: modbus.0 (12400) Client in error state.
                          2023-01-20 17:31:56.135 - warn: modbus.0 (12400) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                          2023-01-20 17:31:56.135 - debug: modbus.0 (12400) Socket closed with error
                          2023-01-20 17:31:56.136 - debug: modbus.0 (12400) Cleaning up request fifo.
                          2023-01-20 17:31:57.136 - debug: modbus.0 (12400) Closing client on purpose.
                          2023-01-20 17:32:57.139 - error: modbus.0 (12400) Socket Error
                          2023-01-20 17:32:57.139 - error: modbus.0 (12400) Client in error state.
                          2023-01-20 17:32:57.139 - warn: modbus.0 (12400) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                          2023-01-20 17:32:57.140 - debug: modbus.0 (12400) Socket closed with error
                          2023-01-20 17:32:57.140 - debug: modbus.0 (12400) Cleaning up request fifo.
                          2023-01-20 17:32:58.140 - debug: modbus.0 (12400) Closing client on purpose.
                          2023-01-20 17:33:07.696 - info: admin.0 (1262) ==> Connected system.user.admin from ::ffff:192.168.1.20
                          2023-01-20 17:33:58.142 - error: modbus.0 (12400) Socket Error
                          2023-01-20 17:33:58.142 - error: modbus.0 (12400) Client in error state.
                          2023-01-20 17:33:58.142 - warn: modbus.0 (12400) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                          2023-01-20 17:33:58.143 - debug: modbus.0 (12400) Socket closed with error
                          2023-01-20 17:33:58.143 - debug: modbus.0 (12400) Cleaning up request fifo.
                          2023-01-20 17:33:59.143 - debug: modbus.0 (12400) Closing client on purpose.
                          2023-01-20 17:34:02.027 - info: admin.0 (1262) <== Disconnect system.user.admin from ::ffff:192.168.1.20 modbus
                          

                          Lieben Dank an die Helfer hier.
                          GLG Wolfi

                          Configuration:
                          Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
                          RAM: 8 GB

                          JS-controler: 5.0.17
                          Node.js: 18.19.0
                          NPM: 10.2.3

                          wendy2702W 1 Antwort Letzte Antwort
                          0
                          • McWoolfM McWoolf

                            @mcwoolf sagte in Einrichten Modbus Adapter / Solar X3 Gen4:

                            @wendy2702

                            m WR ist auch die ID auf 2 gestellt
                            in der Doku ist auch der Port des WR, ich habe aber einen PE11 dazwischen und bei dem ist Port 26 eingetragen.
                            Oder bin ich da auch auf dem Holzweg??
                            Bei Protokoll habe ich jetzt mal auf "modbus" gestellt :dizzy_face:

                            Hier die aktuellen Einstellungen des Umsetzers:

                            f4d7edb5-ee7e-4143-aca6-5414b2053b2f-image.png

                            420de46c-7062-4bb8-b087-7641711ff502-image.png

                            und vom modbus-adapter

                            6a3b994d-b582-4ba4-be12-91216e181516-image.png

                            dc9c6028-e72a-4a63-9f65-778fc98c9dfb-image.png

                            und das aktuelle Log:

                            2023-01-20 17:30:55.132 - error: modbus.0 (12400) Socket Error
                            2023-01-20 17:30:55.132 - error: modbus.0 (12400) Client in error state.
                            2023-01-20 17:30:55.132 - warn: modbus.0 (12400) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                            2023-01-20 17:30:55.132 - debug: modbus.0 (12400) Socket closed with error
                            2023-01-20 17:30:55.132 - debug: modbus.0 (12400) Cleaning up request fifo.
                            2023-01-20 17:30:56.133 - debug: modbus.0 (12400) Closing client on purpose.
                            2023-01-20 17:31:27.642 - info: shelly.0 (1420) [MQTT] Client Disconnect: 192.168.30.40 (shellyht / shellyht-024898 / SHHT-1#024898#1)
                            2023-01-20 17:31:56.135 - error: modbus.0 (12400) Socket Error
                            2023-01-20 17:31:56.135 - error: modbus.0 (12400) Client in error state.
                            2023-01-20 17:31:56.135 - warn: modbus.0 (12400) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                            2023-01-20 17:31:56.135 - debug: modbus.0 (12400) Socket closed with error
                            2023-01-20 17:31:56.136 - debug: modbus.0 (12400) Cleaning up request fifo.
                            2023-01-20 17:31:57.136 - debug: modbus.0 (12400) Closing client on purpose.
                            2023-01-20 17:32:57.139 - error: modbus.0 (12400) Socket Error
                            2023-01-20 17:32:57.139 - error: modbus.0 (12400) Client in error state.
                            2023-01-20 17:32:57.139 - warn: modbus.0 (12400) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                            2023-01-20 17:32:57.140 - debug: modbus.0 (12400) Socket closed with error
                            2023-01-20 17:32:57.140 - debug: modbus.0 (12400) Cleaning up request fifo.
                            2023-01-20 17:32:58.140 - debug: modbus.0 (12400) Closing client on purpose.
                            2023-01-20 17:33:07.696 - info: admin.0 (1262) ==> Connected system.user.admin from ::ffff:192.168.1.20
                            2023-01-20 17:33:58.142 - error: modbus.0 (12400) Socket Error
                            2023-01-20 17:33:58.142 - error: modbus.0 (12400) Client in error state.
                            2023-01-20 17:33:58.142 - warn: modbus.0 (12400) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                            2023-01-20 17:33:58.143 - debug: modbus.0 (12400) Socket closed with error
                            2023-01-20 17:33:58.143 - debug: modbus.0 (12400) Cleaning up request fifo.
                            2023-01-20 17:33:59.143 - debug: modbus.0 (12400) Closing client on purpose.
                            2023-01-20 17:34:02.027 - info: admin.0 (1262) <== Disconnect system.user.admin from ::ffff:192.168.1.20 modbus
                            
                            wendy2702W Online
                            wendy2702W Online
                            wendy2702
                            schrieb am zuletzt editiert von
                            #47

                            @mcwoolf nach meiner Erfahrung muss der Port durchgehend passen und derselbe sein da die Gateways eigentlich nur von TCP nach RTU umsetzen aber keine Werte ändern.

                            Bitte keine Fragen per PN, die gehören ins Forum!

                            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                            McWoolfM 1 Antwort Letzte Antwort
                            0
                            • wendy2702W wendy2702

                              @mcwoolf nach meiner Erfahrung muss der Port durchgehend passen und derselbe sein da die Gateways eigentlich nur von TCP nach RTU umsetzen aber keine Werte ändern.

                              McWoolfM Offline
                              McWoolfM Offline
                              McWoolf
                              schrieb am zuletzt editiert von
                              #48

                              @wendy2702

                              Ich bekomme aber immer einen Socket Fehler

                              Lieben Dank an die Helfer hier.
                              GLG Wolfi

                              Configuration:
                              Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
                              RAM: 8 GB

                              JS-controler: 5.0.17
                              Node.js: 18.19.0
                              NPM: 10.2.3

                              GlasfaserG 1 Antwort Letzte Antwort
                              0
                              • McWoolfM McWoolf

                                @wendy2702

                                Ich bekomme aber immer einen Socket Fehler

                                GlasfaserG Offline
                                GlasfaserG Offline
                                Glasfaser
                                schrieb am zuletzt editiert von
                                #49

                                @mcwoolf

                                Wenn du schon meherer Geräte id´s ankreuzt ,

                                d2ba1280-ebdf-4657-b5b0-0870f6679fe8-grafik.png

                                dann auch die Slave id eintragen !

                                Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                                McWoolfM 1 Antwort Letzte Antwort
                                0
                                • GlasfaserG Glasfaser

                                  @mcwoolf

                                  Wenn du schon meherer Geräte id´s ankreuzt ,

                                  d2ba1280-ebdf-4657-b5b0-0870f6679fe8-grafik.png

                                  dann auch die Slave id eintragen !

                                  McWoolfM Offline
                                  McWoolfM Offline
                                  McWoolf
                                  schrieb am zuletzt editiert von
                                  #50

                                  @glasfaser

                                  Danke für die Info, hatte ich beim screenshot vergessen.
                                  Und war nur zum testen

                                  Lieben Dank an die Helfer hier.
                                  GLG Wolfi

                                  Configuration:
                                  Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
                                  RAM: 8 GB

                                  JS-controler: 5.0.17
                                  Node.js: 18.19.0
                                  NPM: 10.2.3

                                  1 Antwort Letzte Antwort
                                  0
                                  • McWoolfM McWoolf

                                    @mcwoolf Ich muss leider alles revidieren, der USR-TCP232-304 kann kein RTU!!!!

                                    Kein wunder dass ich keine Daten bekomme.

                                    K Offline
                                    K Offline
                                    klassisch
                                    Most Active
                                    schrieb am zuletzt editiert von
                                    #51

                                    @mcwoolf sagte in Einrichten Modbus Adapter / Solar X3 Gen4:

                                    @mcwoolf Ich muss leider alles revidieren, der USR-TCP232-304 kann kein RTU!!!!

                                    Aber der ioBroker Adapter

                                    21b6f644-191d-4a8f-9410-d2322fcde2e8-grafik.png

                                    Die Übersetzung RTU TCP darf nur an einer Stelle erfolgen
                                    Entweder im TCP Server ODER im ioBroker

                                    1 Antwort Letzte Antwort
                                    0
                                    • McWoolfM Offline
                                      McWoolfM Offline
                                      McWoolf
                                      schrieb am zuletzt editiert von
                                      #52

                                      @klassisch

                                      Also jetzt habts mich komplett durcheinander gebracht, was muss ich jetzt wo einstellen??
                                      TCP-Server jetzt doch auf meinen übersetzter?? Dafür nur TCP auf iobroker??

                                      Lieben Dank an die Helfer hier.
                                      GLG Wolfi

                                      Configuration:
                                      Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
                                      RAM: 8 GB

                                      JS-controler: 5.0.17
                                      Node.js: 18.19.0
                                      NPM: 10.2.3

                                      K 1 Antwort Letzte Antwort
                                      0
                                      • McWoolfM McWoolf

                                        @klassisch

                                        Also jetzt habts mich komplett durcheinander gebracht, was muss ich jetzt wo einstellen??
                                        TCP-Server jetzt doch auf meinen übersetzter?? Dafür nur TCP auf iobroker??

                                        K Offline
                                        K Offline
                                        klassisch
                                        Most Active
                                        schrieb am zuletzt editiert von klassisch
                                        #53

                                        @mcwoolf Der USRIOT ist bei mir immer Server weil er austeilt. der ioBroker client, weil er Bröckchen bekommt.
                                        Wenn das entsprechende Konverter Gerät kein Modbus RTU kann (und die kleinen USRIOT können kein RTU und der 410S stottern manchmal dabei), dann stellt man dort einfach TCP ein, also TCP Server.
                                        Die Transformation nach RTU nimmt dann der ioBroker vor, wenn man ihn entsprechend konfiguriert (Dort dann RTU over TCP einstellen, wie oben gezeigt)

                                        McWoolfM 1 Antwort Letzte Antwort
                                        0
                                        • K klassisch

                                          @mcwoolf Der USRIOT ist bei mir immer Server weil er austeilt. der ioBroker client, weil er Bröckchen bekommt.
                                          Wenn das entsprechende Konverter Gerät kein Modbus RTU kann (und die kleinen USRIOT können kein RTU und der 410S stottern manchmal dabei), dann stellt man dort einfach TCP ein, also TCP Server.
                                          Die Transformation nach RTU nimmt dann der ioBroker vor, wenn man ihn entsprechend konfiguriert (Dort dann RTU over TCP einstellen, wie oben gezeigt)

                                          McWoolfM Offline
                                          McWoolfM Offline
                                          McWoolf
                                          schrieb am zuletzt editiert von
                                          #54

                                          @klassisch

                                          Und wenn ich genau das mache, dann bekomme ich wieder einen Socket Fehler.

                                          2023-01-20 19:20:21.425 - error: modbus.0 (14724) Socket Error
                                          2023-01-20 19:20:21.425 - error: modbus.0 (14724) Client in error state.
                                          2023-01-20 19:20:21.425 - warn: modbus.0 (14724) On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.1.244","port":26}
                                          

                                          Lieben Dank an die Helfer hier.
                                          GLG Wolfi

                                          Configuration:
                                          Intel Nuc: 11th Gen Intel(R) Core(TM) i7-1165G7 @ 2.80GHz (1 Socket)
                                          RAM: 8 GB

                                          JS-controler: 5.0.17
                                          Node.js: 18.19.0
                                          NPM: 10.2.3

                                          GlasfaserG 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          743

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe