  4. Modbus TCP Problem

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.2k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.9k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.2k

Modbus TCP Problem

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
34 Beiträge 5 Kommentatoren 3.4k Aufrufe 5 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • GlasfaserG Glasfaser

    @wendy2702

    Das Problem ist . man liest den Thread von oben nach unten ...

    @bytec
    Also bitte auch die Veränderung im Beitrag mitteilen . Modbus Instanz usw. !

    Nimm mal die Abfrage 88 raus , was ist dann !?

    B Offline
    B Offline
    bytec
    schrieb am zuletzt editiert von bytec
    #15

    @glasfaser

    Also 88 stimmt.

    Wenn ich jetzt 88 rausnehme geht auch das 77er mache ich das 88er wieder rein geht dieses nicht mehr Wert 0 in gelb
    Versteh das nicht. Wenn ich also ein viertes Register abfragen will geht das letzte nicht.

    Also hat es nichts mit dem 77er speziell zu tun und wie gesagt sie gehen alle richtig in Loxone in einem Modus Client auf dem Rechner und mit dem Kommandozeilen Tool modpull unter linux.

    könnte natürlich jetzt mehrere Instanzen machen aber damit haben wir da Problem ja auch nicht wirklich gelöst.

    GlasfaserG 1 Antwort Letzte Antwort
    0
    • wendy2702W wendy2702

      @bytec Ne, wird nicht gelesen. Habe nicht gesehen in welche Richtung das LOg neuer war.

      Aber ich denke wenn du Register 77 auslesen willst musst du 78 eintragen?

      Zeige doch mal die Modbus Beschreibung des Gerätes.

      GlasfaserG Online
      GlasfaserG Online
      Glasfaser
      schrieb am zuletzt editiert von
      #16

      @bytec

      @wendy2702 sagte in Modbus TCP Problem:
      Zeige doch mal die Modbus Beschreibung des Gerätes.

      Wir sind nur am raten ... gibt doch mal alle Infos dazu !!

      Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

      B 1 Antwort Letzte Antwort
      0
      • GlasfaserG Glasfaser

        @bytec

        @wendy2702 sagte in Modbus TCP Problem:
        Zeige doch mal die Modbus Beschreibung des Gerätes.

        Wir sind nur am raten ... gibt doch mal alle Infos dazu !!

        B Offline
        B Offline
        bytec
        schrieb am zuletzt editiert von
        #17

        @glasfaser

        Bildschirm­foto 2023-01-14 um 18.48.34.png

        1 Antwort Letzte Antwort
        0
        • B bytec

          @glasfaser

          Also 88 stimmt.

          Wenn ich jetzt 88 rausnehme geht auch das 77er mache ich das 88er wieder rein geht dieses nicht mehr Wert 0 in gelb
          Versteh das nicht. Wenn ich also ein viertes Register abfragen will geht das letzte nicht.

          Also hat es nichts mit dem 77er speziell zu tun und wie gesagt sie gehen alle richtig in Loxone in einem Modus Client auf dem Rechner und mit dem Kommandozeilen Tool modpull unter linux.

          könnte natürlich jetzt mehrere Instanzen machen aber damit haben wir da Problem ja auch nicht wirklich gelöst.

          GlasfaserG Online
          GlasfaserG Online
          Glasfaser
          schrieb am zuletzt editiert von
          #18

          @bytec sagte in Modbus TCP Problem:

          und wie gesagt sie gehen alle richtig in Loxone in einem Modus Client auf dem Rechner

          Gegenfrage ... läßt dein Modbus eigentlich 2 Client´s zu, das Register abzufragen !?

          Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

          B 1 Antwort Letzte Antwort
          0
          • GlasfaserG Glasfaser

            @bytec sagte in Modbus TCP Problem:

            und wie gesagt sie gehen alle richtig in Loxone in einem Modus Client auf dem Rechner

            Gegenfrage ... läßt dein Modbus eigentlich 2 Client´s zu, das Register abzufragen !?

            B Offline
            B Offline
            bytec
            schrieb am zuletzt editiert von
            #19

            @glasfaser

            ja sonst würden ja die anderen Clients wie oben geschrieben auch nicht gehen

            Bildschirm­foto 2023-01-14 um 18.50.24.png

            der Client läuft die ganze Zeit nebenbei und pollt die richtigen Werte

            1 Antwort Letzte Antwort
            0
            • B bytec

              @wendy2702

              stimmt könnte man auch ohne Formeln machen aber auch ohne Formel kommt das Register nicht.

              modbus.1
              2023-01-14 18:07:01.363	debug	Closing client on purpose.
              
              modbus.1
              2023-01-14 18:07:00.364	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":false,"ack":true,"ts":1673716020363,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014383}
              
              modbus.1
              2023-01-14 18:07:00.362	debug	Cleaning up request fifo.
              
              modbus.1
              2023-01-14 18:07:00.362	debug	Socket closed with error
              
              modbus.1
              2023-01-14 18:07:00.339	info	Disconnected from slave 192.168.0.56
              
              modbus.1
              2023-01-14 18:07:00.339	debug	Closing client on purpose.
              
              modbus.1
              2023-01-14 18:07:00.336	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":false,"ack":true,"ts":1673716020335,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014383}
              
              modbus.1
              2023-01-14 18:07:00.288	warn	Poll error count: 6 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
              
              modbus.1
              2023-01-14 18:07:00.287	debug	Received pdu describes an error.
              
              modbus.1
              2023-01-14 18:07:00.215	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.39_Vorlauf__oben:{"val":34.8,"ack":true,"ts":1673716020214,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014327}
              
              modbus.1
              2023-01-14 18:07:00.214	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.4_Vorlauf_unten:{"val":29.4,"ack":true,"ts":1673716020213,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673715884570}
              
              modbus.1
              2023-01-14 18:07:00.213	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
              
              modbus.1
              2023-01-14 18:07:00.212	debug	[DevID_1/inputRegs/39] Calculation result = 34.8, type = number
              
              modbus.1
              2023-01-14 18:07:00.212	debug	[DevID_1/inputRegs/39] Formula = x / 10
              
              modbus.1
              2023-01-14 18:07:00.212	debug	[DevID_1/inputRegs/39] Input Value = 348
              
              modbus.1
              2023-01-14 18:07:00.212	debug	[DevID_1/inputRegs] Poll address 39 DONE
              
              modbus.1
              2023-01-14 18:07:00.173	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
              
              modbus.1
              2023-01-14 18:07:00.172	debug	[DevID_1/inputRegs/4] Calculation result = 29.4, type = number
              
              modbus.1
              2023-01-14 18:07:00.172	debug	[DevID_1/inputRegs/4] Formula = x / 10
              
              modbus.1
              2023-01-14 18:07:00.172	debug	[DevID_1/inputRegs/4] Input Value = 294
              
              modbus.1
              2023-01-14 18:07:00.172	debug	[DevID_1/inputRegs] Poll address 4 DONE
              
              modbus.1
              2023-01-14 18:07:00.143	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
              
              modbus.1
              2023-01-14 18:07:00.142	debug	[DevID_1] Poll start ---------------------
              
              modbus.1
              2023-01-14 18:06:59.137	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":false,"ack":true,"ts":1673716019135,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014383}
              
              modbus.1
              2023-01-14 18:06:59.092	warn	Poll error count: 5 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
              
              modbus.1
              2023-01-14 18:06:59.092	debug	Received pdu describes an error.
              
              modbus.1
              2023-01-14 18:06:59.088	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.39_Vorlauf__oben:{"val":34.8,"ack":true,"ts":1673716019087,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014327}
              
              modbus.1
              2023-01-14 18:06:59.044	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.4_Vorlauf_unten:{"val":29.4,"ack":true,"ts":1673716019042,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673715884570}
              
              modbus.1
              2023-01-14 18:06:59.042	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
              
              modbus.1
              2023-01-14 18:06:59.041	debug	[DevID_1/inputRegs/39] Calculation result = 34.8, type = number
              
              modbus.1
              2023-01-14 18:06:59.041	debug	[DevID_1/inputRegs/39] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:59.040	debug	[DevID_1/inputRegs/39] Input Value = 348
              
              modbus.1
              2023-01-14 18:06:59.040	debug	[DevID_1/inputRegs] Poll address 39 DONE
              
              modbus.1
              2023-01-14 18:06:59.003	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
              
              modbus.1
              2023-01-14 18:06:59.002	debug	[DevID_1/inputRegs/4] Calculation result = 29.4, type = number
              
              modbus.1
              2023-01-14 18:06:59.002	debug	[DevID_1/inputRegs/4] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:59.002	debug	[DevID_1/inputRegs/4] Input Value = 294
              
              modbus.1
              2023-01-14 18:06:59.002	debug	[DevID_1/inputRegs] Poll address 4 DONE
              
              modbus.1
              2023-01-14 18:06:58.967	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
              
              modbus.1
              2023-01-14 18:06:58.966	debug	[DevID_1] Poll start ---------------------
              
              modbus.1
              2023-01-14 18:06:57.960	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":false,"ack":true,"ts":1673716017959,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014383}
              
              modbus.1
              2023-01-14 18:06:57.915	warn	Poll error count: 4 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
              
              modbus.1
              2023-01-14 18:06:57.915	debug	Received pdu describes an error.
              
              modbus.1
              2023-01-14 18:06:57.839	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.39_Vorlauf__oben:{"val":34.8,"ack":true,"ts":1673716017837,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014327}
              
              modbus.1
              2023-01-14 18:06:57.837	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.4_Vorlauf_unten:{"val":29.4,"ack":true,"ts":1673716017836,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673715884570}
              
              modbus.1
              2023-01-14 18:06:57.835	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
              
              modbus.1
              2023-01-14 18:06:57.834	debug	[DevID_1/inputRegs/39] Calculation result = 34.8, type = number
              
              modbus.1
              2023-01-14 18:06:57.834	debug	[DevID_1/inputRegs/39] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:57.834	debug	[DevID_1/inputRegs/39] Input Value = 348
              
              modbus.1
              2023-01-14 18:06:57.834	debug	[DevID_1/inputRegs] Poll address 39 DONE
              
              modbus.1
              2023-01-14 18:06:57.802	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
              
              modbus.1
              2023-01-14 18:06:57.801	debug	[DevID_1/inputRegs/4] Calculation result = 29.4, type = number
              
              modbus.1
              2023-01-14 18:06:57.801	debug	[DevID_1/inputRegs/4] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:57.801	debug	[DevID_1/inputRegs/4] Input Value = 294
              
              modbus.1
              2023-01-14 18:06:57.801	debug	[DevID_1/inputRegs] Poll address 4 DONE
              
              modbus.1
              2023-01-14 18:06:57.770	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
              
              modbus.1
              2023-01-14 18:06:57.769	debug	[DevID_1] Poll start ---------------------
              
              modbus.1
              2023-01-14 18:06:56.764	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":false,"ack":true,"ts":1673716016763,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014383}
              
              modbus.1
              2023-01-14 18:06:56.718	warn	Poll error count: 3 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
              
              modbus.1
              2023-01-14 18:06:56.718	debug	Received pdu describes an error.
              
              modbus.1
              2023-01-14 18:06:56.704	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.39_Vorlauf__oben:{"val":34.8,"ack":true,"ts":1673716016703,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014327}
              
              modbus.1
              2023-01-14 18:06:56.660	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
              
              modbus.1
              2023-01-14 18:06:56.659	debug	[DevID_1/inputRegs/39] Calculation result = 34.8, type = number
              
              modbus.1
              2023-01-14 18:06:56.659	debug	[DevID_1/inputRegs/39] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:56.659	debug	[DevID_1/inputRegs/39] Input Value = 348
              
              modbus.1
              2023-01-14 18:06:56.659	debug	[DevID_1/inputRegs] Poll address 39 DONE
              
              modbus.1
              2023-01-14 18:06:56.648	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.4_Vorlauf_unten:{"val":29.4,"ack":true,"ts":1673716016647,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673715884570}
              
              modbus.1
              2023-01-14 18:06:56.605	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
              
              modbus.1
              2023-01-14 18:06:56.604	debug	[DevID_1/inputRegs/4] Calculation result = 29.4, type = number
              
              modbus.1
              2023-01-14 18:06:56.604	debug	[DevID_1/inputRegs/4] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:56.604	debug	[DevID_1/inputRegs/4] Input Value = 294
              
              modbus.1
              2023-01-14 18:06:56.604	debug	[DevID_1/inputRegs] Poll address 4 DONE
              
              modbus.1
              2023-01-14 18:06:56.568	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
              
              modbus.1
              2023-01-14 18:06:56.568	debug	[DevID_1] Poll start ---------------------
              
              modbus.1
              2023-01-14 18:06:55.564	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":false,"ack":true,"ts":1673716015563,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014383}
              
              modbus.1
              2023-01-14 18:06:55.517	warn	Poll error count: 2 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
              
              modbus.1
              2023-01-14 18:06:55.517	debug	Received pdu describes an error.
              
              modbus.1
              2023-01-14 18:06:55.460	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.39_Vorlauf__oben:{"val":34.8,"ack":true,"ts":1673716015460,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014327}
              
              modbus.1
              2023-01-14 18:06:55.459	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.4_Vorlauf_unten:{"val":29.4,"ack":true,"ts":1673716015458,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673715884570}
              
              modbus.1
              2023-01-14 18:06:55.455	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
              
              modbus.1
              2023-01-14 18:06:55.455	debug	[DevID_1/inputRegs/39] Calculation result = 34.8, type = number
              
              modbus.1
              2023-01-14 18:06:55.455	debug	[DevID_1/inputRegs/39] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:55.454	debug	[DevID_1/inputRegs/39] Input Value = 348
              
              modbus.1
              2023-01-14 18:06:55.454	debug	[DevID_1/inputRegs] Poll address 39 DONE
              
              modbus.1
              2023-01-14 18:06:55.422	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
              
              modbus.1
              2023-01-14 18:06:55.421	debug	[DevID_1/inputRegs/4] Calculation result = 29.4, type = number
              
              modbus.1
              2023-01-14 18:06:55.421	debug	[DevID_1/inputRegs/4] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:55.421	debug	[DevID_1/inputRegs/4] Input Value = 294
              
              modbus.1
              2023-01-14 18:06:55.421	debug	[DevID_1/inputRegs] Poll address 4 DONE
              
              modbus.1
              2023-01-14 18:06:55.390	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
              
              modbus.1
              2023-01-14 18:06:55.390	debug	[DevID_1] Poll start ---------------------
              
              modbus.1
              2023-01-14 18:06:54.384	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":false,"ack":true,"ts":1673716014383,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014383}
              
              modbus.1
              2023-01-14 18:06:54.337	warn	Poll error count: 1 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
              
              modbus.1
              2023-01-14 18:06:54.337	debug	Received pdu describes an error.
              
              modbus.1
              2023-01-14 18:06:54.328	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.39_Vorlauf__oben:{"val":34.8,"ack":true,"ts":1673716014327,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014327}
              
              modbus.1
              2023-01-14 18:06:54.282	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
              
              modbus.1
              2023-01-14 18:06:54.281	debug	[DevID_1/inputRegs/39] Calculation result = 34.8, type = number
              
              modbus.1
              2023-01-14 18:06:54.281	debug	[DevID_1/inputRegs/39] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:54.281	debug	[DevID_1/inputRegs/39] Input Value = 348
              
              modbus.1
              2023-01-14 18:06:54.281	debug	[DevID_1/inputRegs] Poll address 39 DONE
              
              modbus.1
              2023-01-14 18:06:54.280	silly	States user redis pmessage modbus.1.*/modbus.1.inputRegisters.4_Vorlauf_unten:{"val":29.4,"ack":true,"ts":1673716014279,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673715884570}
              
              modbus.1
              2023-01-14 18:06:54.231	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
              
              modbus.1
              2023-01-14 18:06:54.230	debug	[DevID_1/inputRegs/4] Calculation result = 29.4, type = number
              
              modbus.1
              2023-01-14 18:06:54.230	debug	[DevID_1/inputRegs/4] Formula = x / 10
              
              modbus.1
              2023-01-14 18:06:54.230	debug	[DevID_1/inputRegs/4] Input Value = 294
              
              modbus.1
              2023-01-14 18:06:54.229	debug	[DevID_1/inputRegs] Poll address 4 DONE
              
              modbus.1
              2023-01-14 18:06:54.228	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":true,"ack":true,"ts":1673716014227,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673716014227}
              
              modbus.1
              2023-01-14 18:06:54.182	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
              
              modbus.1
              2023-01-14 18:06:54.182	debug	Initialization of scale factors done!
              
              modbus.1
              2023-01-14 18:06:54.181	debug	[DevID_1] Poll start ---------------------
              
              modbus.1
              2023-01-14 18:06:54.181	info	Connected to slave 192.168.0.56
              
              modbus.1
              2023-01-14 18:06:54.152	silly	States user redis pmessage modbus.1.*/modbus.1.info.connection:{"val":false,"ack":true,"ts":1673716014151,"q":0,"from":"system.adapter.modbus.1","user":"system.user.admin","lc":1673715944879}
              
              modbus.1
              2023-01-14 18:06:54.043	silly	States system redis pmessage system.adapter.modbus.1.logLevel/system.adapter.modbus.1.logLevel:{"val":"silly","ack":true,"ts":1673716013996,"q":0,"from":"system.adapter.modbus.1","lc":1673713683159}
              
              modbus.1
              2023-01-14 18:06:54.020	debug	Initialize Objects for holdingRegs: []
              
              modbus.1
              2023-01-14 18:06:54.020	debug	Add inputRegisters.88_Rücklauf_oben: {"_id":"inputRegisters.88_Rücklauf_oben","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":88,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
              
              modbus.1
              2023-01-14 18:06:54.020	debug	Add inputRegisters.77_Rücklauf_unten: {"_id":"inputRegisters.77_Rücklauf_unten","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":77,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
              
              modbus.1
              2023-01-14 18:06:54.020	debug	Add inputRegisters.39_Vorlauf__oben: {"_id":"inputRegisters.39_Vorlauf__oben","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":39,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
              
              modbus.1
              2023-01-14 18:06:54.019	debug	Add inputRegisters.4_Vorlauf_unten: {"_id":"inputRegisters.4_Vorlauf_unten","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":4,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
              
              modbus.1
              2023-01-14 18:06:54.019	debug	Initialize Objects for inputRegs: [{"_address":4,"name":"Vorlauf unten","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"x / 10","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":4,"id":"inputRegisters.4_Vorlauf_unten"},{"_address":39,"name":"Vorlauf oben","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"x / 10","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":39,"id":"inputRegisters.39_Vorlauf__oben"},{"_address":77,"name":"Rücklauf unten","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":77,"id":"inputRegisters.77_Rücklauf_unten"},{"_address":88,"name":"Rücklauf oben","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"x / 10","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":88,"id":"inputRegisters.88_Rücklauf_oben"}]
              
              modbus.1
              2023-01-14 18:06:54.019	debug	Initialize Objects for coils: []
              
              modbus.1
              2023-01-14 18:06:54.018	debug	Initialize Objects for disInputs: []
              
              modbus.1
              2023-01-14 18:06:53.959	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v14.17.0, js-controller: 4.0.24
              
              modbus.1
              2023-01-14 18:06:53.857	debug	Plugin sentry Initialize Plugin (enabled=true)
              

              Komischerweise steht bei PollAdress 77 was von 12 register wenn ich es alleine in einer Instanz Polle dann nur 1 Register

              GlasfaserG Online
              GlasfaserG Online
              Glasfaser
              schrieb am zuletzt editiert von Glasfaser
              #20

              @bytec sagte in Modbus TCP Problem:

              2023-01-14 18:07:00.173 debug [DevID_1/inputRegs] Poll address 39 - 1 registers

              2023-01-14 18:07:00.143 debug [DevID_1/inputRegs] Poll address 4 - 1 registers

              das wäre richtig = 1 Register

              ab hier 12

              2023-01-14 18:07:00.213 debug [DevID_1/inputRegs] Poll address 77 - 12 registers

              kannst du bitte ein Debug log zeigen , wo 77 funktioniert !

              EDIT :

              Bzw. 78 ... komme gerade nicht mit ... da :

              @bytec sagte in Modbus TCP Problem:
              dem auszulesenden Register dazuzählen also ich möchte 77 muss dann aber 78 eingeben. Dies funktioniert so bei den anderen Registern.

              Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

              B 1 Antwort Letzte Antwort
              0
              • GlasfaserG Glasfaser

                @bytec sagte in Modbus TCP Problem:

                2023-01-14 18:07:00.173 debug [DevID_1/inputRegs] Poll address 39 - 1 registers

                2023-01-14 18:07:00.143 debug [DevID_1/inputRegs] Poll address 4 - 1 registers

                das wäre richtig = 1 Register

                ab hier 12

                2023-01-14 18:07:00.213 debug [DevID_1/inputRegs] Poll address 77 - 12 registers

                kannst du bitte ein Debug log zeigen , wo 77 funktioniert !

                EDIT :

                Bzw. 78 ... komme gerade nicht mit ... da :

                @bytec sagte in Modbus TCP Problem:
                dem auszulesenden Register dazuzählen also ich möchte 77 muss dann aber 78 eingeben. Dies funktioniert so bei den anderen Registern.

                B Offline
                B Offline
                bytec
                schrieb am zuletzt editiert von
                #21

                @glasfaser

                Also aktuelle Einstellung im Bild werden 4 / 39 / 77 korrekt ausgelesen 88 kommt eine gelbe 0

                Laut dem Log steht bei 77 ja wieder 12 register ...

                Bildschirm­foto 2023-01-14 um 19.03.17.png

                2023-01-14 19:02:04.751	debug	Closing client on purpose.
                
                modbus.1
                2023-01-14 19:02:03.750	debug	Cleaning up request fifo.
                
                modbus.1
                2023-01-14 19:02:03.750	debug	Socket closed with error
                
                modbus.1
                2023-01-14 19:02:03.729	info	Disconnected from slave 192.168.0.56
                
                modbus.1
                2023-01-14 19:02:03.729	debug	Closing client on purpose.
                
                modbus.1
                2023-01-14 19:02:03.678	warn	Poll error count: 6 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                
                modbus.1
                2023-01-14 19:02:03.678	debug	Received pdu describes an error.
                
                modbus.1
                2023-01-14 19:02:03.627	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
                
                modbus.1
                2023-01-14 19:02:03.627	debug	[DevID_1/inputRegs/39] Calculation result = 34.5, type = number
                
                modbus.1
                2023-01-14 19:02:03.627	debug	[DevID_1/inputRegs/39] Formula = x / 10
                
                modbus.1
                2023-01-14 19:02:03.626	debug	[DevID_1/inputRegs/39] Input Value = 345
                
                modbus.1
                2023-01-14 19:02:03.626	debug	[DevID_1/inputRegs] Poll address 39 DONE
                
                modbus.1
                2023-01-14 19:02:03.589	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
                
                modbus.1
                2023-01-14 19:02:03.588	debug	[DevID_1/inputRegs/4] Calculation result = 29.3, type = number
                
                modbus.1
                2023-01-14 19:02:03.588	debug	[DevID_1/inputRegs/4] Formula = x / 10
                
                modbus.1
                2023-01-14 19:02:03.588	debug	[DevID_1/inputRegs/4] Input Value = 293
                
                modbus.1
                2023-01-14 19:02:03.588	debug	[DevID_1/inputRegs] Poll address 4 DONE
                
                modbus.1
                2023-01-14 19:02:03.555	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
                
                modbus.1
                2023-01-14 19:02:03.554	debug	[DevID_1] Poll start ---------------------
                
                modbus.1
                2023-01-14 19:02:02.504	warn	Poll error count: 5 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                
                modbus.1
                2023-01-14 19:02:02.504	debug	Received pdu describes an error.
                
                modbus.1
                2023-01-14 19:02:02.442	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
                
                modbus.1
                2023-01-14 19:02:02.442	debug	[DevID_1/inputRegs/39] Calculation result = 34.5, type = number
                
                modbus.1
                2023-01-14 19:02:02.442	debug	[DevID_1/inputRegs/39] Formula = x / 10
                
                modbus.1
                2023-01-14 19:02:02.442	debug	[DevID_1/inputRegs/39] Input Value = 345
                
                modbus.1
                2023-01-14 19:02:02.442	debug	[DevID_1/inputRegs] Poll address 39 DONE
                
                modbus.1
                2023-01-14 19:02:02.410	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
                
                modbus.1
                2023-01-14 19:02:02.409	debug	[DevID_1/inputRegs/4] Calculation result = 29.3, type = number
                
                modbus.1
                2023-01-14 19:02:02.409	debug	[DevID_1/inputRegs/4] Formula = x / 10
                
                modbus.1
                2023-01-14 19:02:02.409	debug	[DevID_1/inputRegs/4] Input Value = 293
                
                modbus.1
                2023-01-14 19:02:02.409	debug	[DevID_1/inputRegs] Poll address 4 DONE
                
                modbus.1
                2023-01-14 19:02:02.380	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
                
                modbus.1
                2023-01-14 19:02:02.380	debug	[DevID_1] Poll start ---------------------
                
                modbus.1
                2023-01-14 19:02:01.329	warn	Poll error count: 4 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                
                modbus.1
                2023-01-14 19:02:01.329	debug	Received pdu describes an error.
                
                modbus.1
                2023-01-14 19:02:01.273	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
                
                modbus.1
                2023-01-14 19:02:01.272	debug	[DevID_1/inputRegs/39] Calculation result = 34.5, type = number
                
                modbus.1
                2023-01-14 19:02:01.272	debug	[DevID_1/inputRegs/39] Formula = x / 10
                
                modbus.1
                2023-01-14 19:02:01.272	debug	[DevID_1/inputRegs/39] Input Value = 345
                
                modbus.1
                2023-01-14 19:02:01.272	debug	[DevID_1/inputRegs] Poll address 39 DONE
                
                modbus.1
                2023-01-14 19:02:01.240	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
                
                modbus.1
                2023-01-14 19:02:01.240	debug	[DevID_1/inputRegs/4] Calculation result = 29.3, type = number
                
                modbus.1
                2023-01-14 19:02:01.240	debug	[DevID_1/inputRegs/4] Formula = x / 10
                
                modbus.1
                2023-01-14 19:02:01.239	debug	[DevID_1/inputRegs/4] Input Value = 293
                
                modbus.1
                2023-01-14 19:02:01.239	debug	[DevID_1/inputRegs] Poll address 4 DONE
                
                modbus.1
                2023-01-14 19:02:01.206	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
                
                modbus.1
                2023-01-14 19:02:01.205	debug	[DevID_1] Poll start ---------------------
                
                modbus.1
                2023-01-14 19:02:00.154	warn	Poll error count: 3 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                
                modbus.1
                2023-01-14 19:02:00.154	debug	Received pdu describes an error.
                
                modbus.1
                2023-01-14 19:02:00.097	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
                
                modbus.1
                2023-01-14 19:02:00.096	debug	[DevID_1/inputRegs/39] Calculation result = 34.5, type = number
                
                modbus.1
                2023-01-14 19:02:00.096	debug	[DevID_1/inputRegs/39] Formula = x / 10
                
                modbus.1
                2023-01-14 19:02:00.096	debug	[DevID_1/inputRegs/39] Input Value = 345
                
                modbus.1
                2023-01-14 19:02:00.096	debug	[DevID_1/inputRegs] Poll address 39 DONE
                
                modbus.1
                2023-01-14 19:02:00.065	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
                
                modbus.1
                2023-01-14 19:02:00.064	debug	[DevID_1/inputRegs/4] Calculation result = 29.3, type = number
                
                modbus.1
                2023-01-14 19:02:00.064	debug	[DevID_1/inputRegs/4] Formula = x / 10
                
                modbus.1
                2023-01-14 19:02:00.064	debug	[DevID_1/inputRegs/4] Input Value = 293
                
                modbus.1
                2023-01-14 19:02:00.064	debug	[DevID_1/inputRegs] Poll address 4 DONE
                
                modbus.1
                2023-01-14 19:02:00.024	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
                
                modbus.1
                2023-01-14 19:02:00.024	debug	[DevID_1] Poll start ---------------------
                
                modbus.1
                2023-01-14 19:01:58.973	warn	Poll error count: 2 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                
                modbus.1
                2023-01-14 19:01:58.972	debug	Received pdu describes an error.
                
                modbus.1
                2023-01-14 19:01:58.924	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
                
                modbus.1
                2023-01-14 19:01:58.923	debug	[DevID_1/inputRegs/39] Calculation result = 34.5, type = number
                
                modbus.1
                2023-01-14 19:01:58.923	debug	[DevID_1/inputRegs/39] Formula = x / 10
                
                modbus.1
                2023-01-14 19:01:58.923	debug	[DevID_1/inputRegs/39] Input Value = 345
                
                modbus.1
                2023-01-14 19:01:58.923	debug	[DevID_1/inputRegs] Poll address 39 DONE
                
                modbus.1
                2023-01-14 19:01:58.890	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
                
                modbus.1
                2023-01-14 19:01:58.890	debug	[DevID_1/inputRegs/4] Calculation result = 29.3, type = number
                
                modbus.1
                2023-01-14 19:01:58.890	debug	[DevID_1/inputRegs/4] Formula = x / 10
                
                modbus.1
                2023-01-14 19:01:58.889	debug	[DevID_1/inputRegs/4] Input Value = 293
                
                modbus.1
                2023-01-14 19:01:58.889	debug	[DevID_1/inputRegs] Poll address 4 DONE
                
                modbus.1
                2023-01-14 19:01:58.857	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
                
                modbus.1
                2023-01-14 19:01:58.856	debug	[DevID_1] Poll start ---------------------
                
                modbus.1
                2023-01-14 19:01:57.804	warn	Poll error count: 1 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                
                modbus.1
                2023-01-14 19:01:57.803	debug	Received pdu describes an error.
                
                modbus.1
                2023-01-14 19:01:57.804	warn	Poll error count: 1 code: {"errorCode":132,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
                
                modbus.1
                2023-01-14 19:01:57.803	debug	Received pdu describes an error.
                
                modbus.1
                2023-01-14 19:01:57.744	debug	[DevID_1/inputRegs] Poll address 77 - 12 registers
                
                modbus.1
                2023-01-14 19:01:57.743	debug	[DevID_1/inputRegs/39] Calculation result = 34.5, type = number
                
                modbus.1
                2023-01-14 19:01:57.743	debug	[DevID_1/inputRegs/39] Formula = x / 10
                
                modbus.1
                2023-01-14 19:01:57.743	debug	[DevID_1/inputRegs/39] Input Value = 345
                
                modbus.1
                2023-01-14 19:01:57.742	debug	[DevID_1/inputRegs] Poll address 39 DONE
                
                modbus.1
                2023-01-14 19:01:57.711	debug	[DevID_1/inputRegs] Poll address 39 - 1 registers
                
                modbus.1
                2023-01-14 19:01:57.711	debug	[DevID_1/inputRegs/4] Calculation result = 29.3, type = number
                
                modbus.1
                2023-01-14 19:01:57.711	debug	[DevID_1/inputRegs/4] Formula = x / 10
                
                modbus.1
                2023-01-14 19:01:57.710	debug	[DevID_1/inputRegs/4] Input Value = 293
                
                modbus.1
                2023-01-14 19:01:57.710	debug	[DevID_1/inputRegs] Poll address 4 DONE
                
                modbus.1
                2023-01-14 19:01:57.673	debug	[DevID_1/inputRegs] Poll address 4 - 1 registers
                
                modbus.1
                2023-01-14 19:01:57.673	debug	Initialization of scale factors done!
                
                modbus.1
                2023-01-14 19:01:57.673	debug	[DevID_1] Poll start ---------------------
                
                modbus.1
                2023-01-14 19:01:57.672	info	Connected to slave 192.168.0.56
                
                modbus.1
                2023-01-14 19:01:57.541	debug	Initialize Objects for holdingRegs: []
                
                modbus.1
                2023-01-14 19:01:57.540	debug	Add inputRegisters.88_Rücklauf_oben: {"_id":"inputRegisters.88_Rücklauf_oben","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":88,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
                
                modbus.1
                2023-01-14 19:01:57.540	debug	Add inputRegisters.77_Rücklauf_unten: {"_id":"inputRegisters.77_Rücklauf_unten","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":77,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
                
                modbus.1
                2023-01-14 19:01:57.540	debug	Add inputRegisters.39_Vorlauf__oben: {"_id":"inputRegisters.39_Vorlauf__oben","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":39,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
                
                modbus.1
                2023-01-14 19:01:57.540	debug	Add inputRegisters.4_Vorlauf_unten: {"_id":"inputRegisters.4_Vorlauf_unten","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":4,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
                
                modbus.1
                2023-01-14 19:01:57.540	debug	Initialize Objects for inputRegs: [{"_address":4,"name":"Vorlauf unten","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"x / 10","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":4,"id":"inputRegisters.4_Vorlauf_unten"},{"_address":39,"name":"Vorlauf oben","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"x / 10","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":39,"id":"inputRegisters.39_Vorlauf__oben"},{"_address":77,"name":"Rücklauf unten","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":77,"id":"inputRegisters.77_Rücklauf_unten"},{"_address":88,"name":"Rücklauf oben","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":88,"id":"inputRegisters.88_Rücklauf_oben"}]
                
                modbus.1
                2023-01-14 19:01:57.539	debug	Initialize Objects for coils: []
                
                modbus.1
                2023-01-14 19:01:57.539	debug	Initialize Objects for disInputs: []
                
                modbus.1
                2023-01-14 19:01:57.479	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v14.17.0, js-controller: 4.0.24
                
                modbus.1
                2023-01-14 19:01:57.375	debug	Plugin sentry Initialize Plugin (enabled=true)
                
                modbus.1
                2023-01-14 19:01:57.324	debug	States connected to redis: 127.0.0.1:9000
                
                modbus.1
                2023-01-14 19:01:57.267	debug	States create User PubSub Client
                
                modbus.1
                2023-01-14 19:01:57.266	debug	States create System PubSub Client
                
                modbus.1
                2023-01-14 19:01:57.259	debug	Redis States: Use Redis connection: 127.0.0.1:9000
                
                modbus.1
                2023-01-14 19:01:57.246	debug	Objects connected to redis: 127.0.0.1:9001
                
                modbus.1
                2023-01-14 19:01:57.244	debug	Objects client initialize lua scripts
                
                modbus.1
                2023-01-14 19:01:57.223	debug	Objects create User PubSub Client
                
                modbus.1
                2023-01-14 19:01:57.223	debug	Objects create System PubSub Client
                
                modbus.1
                2023-01-14 19:01:57.222	debug	Objects client ready ... initialize now
                
                modbus.1
                2023-01-14 19:01:57.204	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
                
                1 Antwort Letzte Antwort
                0
                • O Offline
                  O Offline
                  oxident
                  schrieb am zuletzt editiert von oxident
                  #22

                  Ich muss mich hier auch mal einhängen. Versuche verzweifelt, mein Victron-System per Modbus auszulesen. Fehlermeldung ist ähnlich wie hier oben:

                  
                  modbus.2 2023-01-15 09:28:45.667	debug	[DevID_100/inputRegs] Poll address 840 - 21 registers
                  modbus.2 2023-01-15 09:28:45.666	debug	[DevID_100/inputRegs] Poll address 820 DONE
                  modbus.2 2023-01-15 09:28:45.663	debug	[DevID_100/inputRegs] Poll address 820 - 3 registers
                  modbus.2 2023-01-15 09:28:45.662	debug	[DevID_100] Poll start ---------------------
                  

                  Das abzufragende Gerät liefert mir eine Erklärung:
                  916322ab-6773-4428-bcd8-d620ffb00280-image.png
                  Demnach hat der Modbus-Adapter versucht, ab Adresse 840 direkt 21 Bytes/Adressen (?) abzufragen. Dies scheiterte dann daran, dass es Adresse 847 nicht gibt, was auch stimmt. Er sollte diese Adresse auch gar nicht abfragen:
                  e790613b-7d0f-4e65-9f6d-588b9a297541-image.png

                  Ich habe jedoch in den Einstellungen des Adapters keine Option gefunden, in der man das Auslesen ganzer Blöcke deaktivieren könnte.

                  Oder bin ich da komplett auf dem Holzweg?

                  K 1 Antwort Letzte Antwort
                  0
                  • O oxident

                    Ich muss mich hier auch mal einhängen. Versuche verzweifelt, mein Victron-System per Modbus auszulesen. Fehlermeldung ist ähnlich wie hier oben:

                    
                    modbus.2 2023-01-15 09:28:45.667	debug	[DevID_100/inputRegs] Poll address 840 - 21 registers
                    modbus.2 2023-01-15 09:28:45.666	debug	[DevID_100/inputRegs] Poll address 820 DONE
                    modbus.2 2023-01-15 09:28:45.663	debug	[DevID_100/inputRegs] Poll address 820 - 3 registers
                    modbus.2 2023-01-15 09:28:45.662	debug	[DevID_100] Poll start ---------------------
                    

                    Das abzufragende Gerät liefert mir eine Erklärung:
                    916322ab-6773-4428-bcd8-d620ffb00280-image.png
                    Demnach hat der Modbus-Adapter versucht, ab Adresse 840 direkt 21 Bytes/Adressen (?) abzufragen. Dies scheiterte dann daran, dass es Adresse 847 nicht gibt, was auch stimmt. Er sollte diese Adresse auch gar nicht abfragen:
                    e790613b-7d0f-4e65-9f6d-588b9a297541-image.png

                    Ich habe jedoch in den Einstellungen des Adapters keine Option gefunden, in der man das Auslesen ganzer Blöcke deaktivieren könnte.

                    Oder bin ich da komplett auf dem Holzweg?

                    K Offline
                    K Offline
                    klassisch
                    Most Active
                    schrieb am zuletzt editiert von klassisch
                    #23

                    @oxident Ich frage auch 840 holding register des Gerätes 100 ab und bekomme keine Fehlermeldung.Ich habe 840 bis 846 eingetragen
                    Ich habe allerdings nur einen kleinen single phase 800VA MP 1.
                    Venus V2.80 29
                    Modbus Adapter 5.0.11, gestern update, war aber auch vorher gut.
                    Wie sehen Deine allgemeinen Einstellungen aus?

                    O 1 Antwort Letzte Antwort
                    0
                    • K klassisch

                      @oxident Ich frage auch 840 holding register des Gerätes 100 ab und bekomme keine Fehlermeldung.Ich habe 840 bis 846 eingetragen
                      Ich habe allerdings nur einen kleinen single phase 800VA MP 1.
                      Venus V2.80 29
                      Modbus Adapter 5.0.11, gestern update, war aber auch vorher gut.
                      Wie sehen Deine allgemeinen Einstellungen aus?

                      O Offline
                      O Offline
                      oxident
                      schrieb am zuletzt editiert von
                      #24

                      @klassisch Ich dachte mir schon dass es bestimmt Nutzer gibt, die damit Ihr Victron-System bedienen.

                      Ich glaube, ich habe das Problem gefunden. In den Instanz-Einstellung war hinterlegt, dass er 10 Werte in einem Durchgang liest. Daran lag's wohl:

                      c3d8d277-e81d-4f7d-88e8-1715be51087b-image.png

                      B 1 Antwort Letzte Antwort
                      1
                      • O oxident

                        @klassisch Ich dachte mir schon dass es bestimmt Nutzer gibt, die damit Ihr Victron-System bedienen.

                        Ich glaube, ich habe das Problem gefunden. In den Instanz-Einstellung war hinterlegt, dass er 10 Werte in einem Durchgang liest. Daran lag's wohl:

                        c3d8d277-e81d-4f7d-88e8-1715be51087b-image.png

                        B Offline
                        B Offline
                        bytec
                        schrieb am zuletzt editiert von
                        #25

                        @oxident

                        Super das war es jetzt geht es auch bei mir.

                        1 Antwort Letzte Antwort
                        0
                        • K Offline
                          K Offline
                          klassisch
                          Most Active
                          schrieb am zuletzt editiert von
                          #26

                          Freut mich, daß es jetzt auch bei Euch geht. Hab aber nicht verstanden, woran es lag.

                          Bei mir sieht es so aus:
                          deeeda45-3379-4f7d-ac8d-c548dc441b73-grafik.png

                          B 1 Antwort Letzte Antwort
                          0
                          • K klassisch

                            Freut mich, daß es jetzt auch bei Euch geht. Hab aber nicht verstanden, woran es lag.

                            Bei mir sieht es so aus:
                            deeeda45-3379-4f7d-ac8d-c548dc441b73-grafik.png

                            B Offline
                            B Offline
                            bytec
                            schrieb am zuletzt editiert von bytec
                            #27

                            @klassisch

                            Also ich habe bei mir jetzt unter Max Leseanforderungslänge eine 1 bei Float und Integer eingetragen und seitdem werden alle Register in einer Instanz sauber ausgelesen.

                            Wahrscheinlich hat sich vorher wenn die Register nah beieinander waren etwas überlappt beim auslesen.

                            K 1 Antwort Letzte Antwort
                            0
                            • B bytec

                              @klassisch

                              Also ich habe bei mir jetzt unter Max Leseanforderungslänge eine 1 bei Float und Integer eingetragen und seitdem werden alle Register in einer Instanz sauber ausgelesen.

                              Wahrscheinlich hat sich vorher wenn die Register nah beieinander waren etwas überlappt beim auslesen.

                              K Offline
                              K Offline
                              klassisch
                              Most Active
                              schrieb am zuletzt editiert von
                              #28

                              @bytec Also da, wo bei mir 100 (Float) und 128 (Integer) steht, steht bei Euch jetzt zwingend 1?
                              Aber bei mir scheint es zu gehen. Keine Fehlermeldung etc.
                              Man muß nicht alles verstehen, Hauptsache es läuft bei Euch jetzt.

                              B 1 Antwort Letzte Antwort
                              0
                              • K klassisch

                                @bytec Also da, wo bei mir 100 (Float) und 128 (Integer) steht, steht bei Euch jetzt zwingend 1?
                                Aber bei mir scheint es zu gehen. Keine Fehlermeldung etc.
                                Man muß nicht alles verstehen, Hauptsache es läuft bei Euch jetzt.

                                B Offline
                                B Offline
                                bytec
                                schrieb am zuletzt editiert von
                                #29

                                @klassisch

                                ja genau da habe ich bei beiden eine 1 eingetragen so wie Oxident das vorgschlagen hat.

                                1 Antwort Letzte Antwort
                                1
                                • O Offline
                                  O Offline
                                  oxident
                                  schrieb am zuletzt editiert von
                                  #30

                                  @klassisch @bytec Ja, das war in der Tat das Problem. Ich fänd es ja auch sinniger, wenn der Adapter "in einem Rutsch" mehr lesen könnte, aber das scheint bei uns nicht zu klappen...

                                  K 1 Antwort Letzte Antwort
                                  0
                                  • O oxident

                                    @klassisch @bytec Ja, das war in der Tat das Problem. Ich fänd es ja auch sinniger, wenn der Adapter "in einem Rutsch" mehr lesen könnte, aber das scheint bei uns nicht zu klappen...

                                    K Offline
                                    K Offline
                                    klassisch
                                    Most Active
                                    schrieb am zuletzt editiert von
                                    #31

                                    @oxident Habt Ihr Venus oder Cerbo GX? Bei mir läuft Venus auf einem alten Raspi. Reicht ja bei meinem Minimalsystem.

                                    B O 2 Antworten Letzte Antwort
                                    0
                                    • K klassisch

                                      @oxident Habt Ihr Venus oder Cerbo GX? Bei mir läuft Venus auf einem alten Raspi. Reicht ja bei meinem Minimalsystem.

                                      B Offline
                                      B Offline
                                      bytec
                                      schrieb am zuletzt editiert von
                                      #32

                                      @klassisch

                                      Ich weder noch. Wir haben eine Nibe Anlage aber das hat glaube nicht wirklich mit der Anlage Ansich zu tun sondern wie der Adapter die Register ausliest und wenn er sie jetzt einzeln ausliest scheint das zu funktionieren.

                                      1 Antwort Letzte Antwort
                                      0
                                      • K klassisch

                                        @oxident Habt Ihr Venus oder Cerbo GX? Bei mir läuft Venus auf einem alten Raspi. Reicht ja bei meinem Minimalsystem.

                                        O Offline
                                        O Offline
                                        oxident
                                        schrieb am zuletzt editiert von
                                        #33

                                        @klassisch Cerbo ... weil ich den RS485-Adapter zum Akku beim Raspi nicht zum Laufen gebracht habe. Aber dort gab es die Probleme mit dem Bulkread auch.

                                        Da das Problem von mir und @bytec irgendwie logisch erscheint frage ich mich echt, was bei Dir anders läuft. Mal blöd gefragt: Die Werte werden aber bei Dir auch regelmäßig aktualisiert und in der Venus-Console werden im Modbus-Bereich auch keine Fehler angezeigt?

                                        K 1 Antwort Letzte Antwort
                                        0
                                        • O oxident

                                          @klassisch Cerbo ... weil ich den RS485-Adapter zum Akku beim Raspi nicht zum Laufen gebracht habe. Aber dort gab es die Probleme mit dem Bulkread auch.

                                          Da das Problem von mir und @bytec irgendwie logisch erscheint frage ich mich echt, was bei Dir anders läuft. Mal blöd gefragt: Die Werte werden aber bei Dir auch regelmäßig aktualisiert und in der Venus-Console werden im Modbus-Bereich auch keine Fehler angezeigt?

                                          K Offline
                                          K Offline
                                          klassisch
                                          Most Active
                                          schrieb am zuletzt editiert von klassisch
                                          #34

                                          @oxident
                                          Bei mir sind keine Modbus Fehler hinterlegt
                                          ea59d14e-b8b8-403f-a86b-4dd6e510e8c8-grafik.png

                                          3015ef1a-27b4-42b6-906f-19fe0f02bd9a-grafik.png

                                          Und ja, die Daten werden in ioBroker aktualisiert.
                                          Habe gerade testweise das Laden des Akkus angestoßen und ich sehe, daß sich der Akkustrom ändert. 840 Spannung wird noch dauern (Edit, hat sich gerade geändert). Darf auch nicht zu lange laden. Der Netzbetreiber hat für heute ab 17:00 eine Strommangelwarnung "rot, Verbrauch reduzieren" ausgegeben.

                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          453

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe