  4. Test Adapter HeatingControl v2.12.x

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.6k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.1k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    2.9k

Test Adapter HeatingControl v2.12.x

Geplant Angeheftet Gesperrt Verschoben Tester
heating
3.2k Beiträge 236 Kommentatoren 2.0m Aufrufe 205 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • Rene_HMR Rene_HM

    @borio85 sagte in Test Adapter HeatingControl v2.1.x:

    Nein, ich verwende absichtlich die Funktion von Homematic nicht, da ich im Arbeitszimmer Zigbee nutze und mit der Funktion Thermostat behandelt "Fenster ist offen" wurde zwar erkannt das das Fenster auf ist aber die Temperatur wurde nicht gesenkt. Um das zu umgehen habe die die Homematic Sensoren nur für Alarm konfiguriert und senke die Temperatur über den Adapter, es Funktionierte bis vorhin eigentlich sehr gut.

    Laut log ist da etwas seltsam... Man sieht auch in deinem screen shot, dass nachdem das Fenster geschlossen wurde, eine Zieltemperatur von 16°C geschrieben wird. 3 Minuten später kommt vom Thermostat aber eine Zieltemperatur von 15°C zurück. Das führt dann zum manual Mode. Im manual Mode wird dann wieder 3,5°C TemperaturOffset abgezogen, das führt dann zu 11°C und so weiter.
    Ich werde in der 2.1.1 den Offset im manual nicht mehr verwenden. Woher aber die 15°C kommen, die urspünglich zum manual geführt haben, kann ich nicht erklären...

    Die 2.1.1 ist im github verfügbar

    B Offline
    B Offline
    Borio85
    schrieb am zuletzt editiert von
    #2134

    @rene_hm said in Test Adapter HeatingControl v2.1.x:

    Die 2.1.1 ist im github verfügbar

    Vielen Dank, lade ich mir jetzt und teste mal.

    1 Antwort Letzte Antwort
    0
    • Rene_HMR Rene_HM

      @borio85 sagte in Test Adapter HeatingControl v2.1.x:

      Nein, ich verwende absichtlich die Funktion von Homematic nicht, da ich im Arbeitszimmer Zigbee nutze und mit der Funktion Thermostat behandelt "Fenster ist offen" wurde zwar erkannt das das Fenster auf ist aber die Temperatur wurde nicht gesenkt. Um das zu umgehen habe die die Homematic Sensoren nur für Alarm konfiguriert und senke die Temperatur über den Adapter, es Funktionierte bis vorhin eigentlich sehr gut.

      Laut log ist da etwas seltsam... Man sieht auch in deinem screen shot, dass nachdem das Fenster geschlossen wurde, eine Zieltemperatur von 16°C geschrieben wird. 3 Minuten später kommt vom Thermostat aber eine Zieltemperatur von 15°C zurück. Das führt dann zum manual Mode. Im manual Mode wird dann wieder 3,5°C TemperaturOffset abgezogen, das führt dann zu 11°C und so weiter.
      Ich werde in der 2.1.1 den Offset im manual nicht mehr verwenden. Woher aber die 15°C kommen, die urspünglich zum manual geführt haben, kann ich nicht erklären...

      Die 2.1.1 ist im github verfügbar

      B Offline
      B Offline
      Borio85
      schrieb am zuletzt editiert von
      #2135

      @rene_hm said in Test Adapter HeatingControl v2.1.x:

      3 Minuten später kommt vom Thermostat aber eine Zieltemperatur von 15°C zurück.

      Ich glaube das ist die Temperatursturzerkennung des Thermostats, in der Homematic App ist 15C als Fenster offen Temperatur eingetragen. Ich muss gucken wie ich das deaktivieren kann.
      Dann kannst du dieses Problem ignorieren, wird wahrscheinlich an meinem setup liegen.

      P 1 Antwort Letzte Antwort
      0
      • B Borio85

        @rene_hm said in Test Adapter HeatingControl v2.1.x:

        3 Minuten später kommt vom Thermostat aber eine Zieltemperatur von 15°C zurück.

        Ich glaube das ist die Temperatursturzerkennung des Thermostats, in der Homematic App ist 15C als Fenster offen Temperatur eingetragen. Ich muss gucken wie ich das deaktivieren kann.
        Dann kannst du dieses Problem ignorieren, wird wahrscheinlich an meinem setup liegen.

        P Offline
        P Offline
        Pittini
        Developer
        schrieb am zuletzt editiert von
        #2136

        @borio85 Inked2021-02-08 19_50_42-Microsoft Store_LI.jpg

        B 1 Antwort Letzte Antwort
        0
        • P Pittini

          @borio85 Inked2021-02-08 19_50_42-Microsoft Store_LI.jpg

          B Offline
          B Offline
          Borio85
          schrieb am zuletzt editiert von
          #2137

          @pittini Vielen Dank, leider habe ich keine CCU, nutze „nur“ den AccessPoint. Ich glaube das wird als nächstes kommen...

          1 Antwort Letzte Antwort
          0
          • B Offline
            B Offline
            Borio85
            schrieb am zuletzt editiert von Borio85
            #2138

            @Rene_HM Die V2.1.1. läuft seit gestern ziemlich sauber und der Offset wird auf die Soll-Temp addiert.
            Follgendes ist mir aufgefallen, wenn der nächste Profilzeitpunkt niedirger ist als vorher z.b. von 20,5 auf 18,5 bleibt die SetTempertrue höher als die nidrigere Soll

            Log beim Profilzeipunkt mit 20,5°C

            2021-02-09 11:52:42.332  - debug: heatingcontrol.0 (4989) calculate temp offset for Arbeitszimmer old value is 4.5, got value {"val":21.6,"ack":true,"ts":1612867962326,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612867417332}
            2021-02-09 11:52:42.334  - debug: heatingcontrol.0 (4989) got 27.2 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
            2021-02-09 11:52:42.336  - debug: heatingcontrol.0 (4989) tempdiff: 27.2 - 21.6 = 5.599999999999998
            2021-02-09 11:52:42.336  - debug: heatingcontrol.0 (4989) TempOffset Arbeitszimmer
            2021-02-09 11:52:42.337  - debug: heatingcontrol.0 (4989) (avg) Ist-Temperatur am Thermostat 27.2
            2021-02-09 11:52:42.337  - debug: heatingcontrol.0 (4989) Ist-Temperatur am zusätzl. Sensor 21.6
            2021-02-09 11:52:42.337  - debug: heatingcontrol.0 (4989) tempDiff 5.599999999999998
            2021-02-09 11:52:42.338  - debug: heatingcontrol.0 (4989) (avg) TempOffset 5
            2021-02-09 11:52:42.357  - debug: heatingcontrol.0 (4989) new temp offset for Arbeitszimmer is 5
            2021-02-09 11:52:42.357  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
            2021-02-09 11:52:42.426  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":2,"ack":false,"ts":1612867962422,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612852120952}
            

            LOG bei Profilwechsel zu 18,5°C

            2021-02-09 12:00:00.015  - debug: heatingcontrol.0 (4989) ChangeStatus fired with [{"room":"Arbeitszimmer","target":18.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"12:00","CurrentTimePeriodFull":"Period 3 12:00"},{"room":"Schlafzimmer","target":17.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"12:00","CurrentTimePeriodFull":"Period 3 12:00"}]
            2021-02-09 12:00:00.016  - debug: heatingcontrol.0 (4989) Arbeitszimmer ### ChangeStatus ProfilPoint to {"room":"Arbeitszimmer","target":18.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"12:00","CurrentTimePeriodFull":"Period 3 12:00"} in manual
            2021-02-09 12:00:00.016  - debug: heatingcontrol.0 (4989) reset manual mode to auto
            2021-02-09 12:00:00.016  - debug: heatingcontrol.0 (4989) ChangeStatus by cron Profilepoint in Arbeitszimmer target 18.5
            2021-02-09 12:00:00.017  - debug: heatingcontrol.0 (4989) CalculateRoomTemperature for Arbeitszimmer auto
            2021-02-09 12:00:00.017  - debug: heatingcontrol.0 (4989) Arbeitszimmer auto mode: target 18.5
            2021-02-09 12:00:00.017  - debug: heatingcontrol.0 (4989) Arbeitszimmer auto mode (incl. reduced): target 18.5
            2021-02-09 12:00:00.018  - debug: heatingcontrol.0 (4989) SetRoomTemperature started for Arbeitszimmer target 18.5 with offset 8
            2021-02-09 12:00:00.051  - debug: heatingcontrol.0 (4989) unsubscribe hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.setPointTemperature
            2021-02-09 12:00:00.052  - debug: heatingcontrol.0 (4989) Arbeitszimmer set thermostat target hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.setPointTemperature to 26.5
            2021-02-09 12:00:00.118  - info: host.raspberrypi4-ioB instance system.adapter.coronavirus-statistics.0 started with pid 18989
            2021-02-09 12:00:00.129  - debug: heatingcontrol.0 (4989) HandleActors for Arbeitszimmer auto
            2021-02-09 12:00:00.129  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
            2021-02-09 12:00:00.128  - info: hmip.0 (11951) state change - setPointTemperature - id 69b2e9b4-e7fa-4376-aab5-2e55b666df91 - value 26.5
            

            Log Offsetberechnung mit 18.5°C

            2021-02-09 12:02:19.579  - debug: heatingcontrol.0 (4989) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
            2021-02-09 12:02:22.971  - debug: heatingcontrol.0 (4989) Arbeitszimmer ### ChangeStatus Thermostats_Target to {"val":26.5,"ack":true,"ts":1612868542913,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612868400124} in auto
            2021-02-09 12:02:22.972  - debug: heatingcontrol.0 (4989) Change Status target temperature in Arbeitszimmer to 26.5 (profile 18.5) in auto
            2021-02-09 12:02:22.972  - debug: heatingcontrol.0 (4989) CheckManualMode Arbeitszimmer
            2021-02-09 12:02:22.973  - debug: heatingcontrol.0 (4989) CheckStartManualMode Arbeitszimmer
            2021-02-09 12:02:22.973  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
            2021-02-09 12:02:22.975  - debug: heatingcontrol.0 (4989) ChangeStatus called, while already changing, push to list Arbeitszimmer Thermostats_Current {"val":24,"ack":true,"ts":1612868542914,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612868405927} (1)
            2021-02-09 12:02:23.081  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":3,"ack":false,"ts":1612868543077,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400223}
            2021-02-09 12:02:23.081  - debug: heatingcontrol.0 (4989) HandleStateChanges CurrentTimePeriod 3
            2021-02-09 12:02:23.131  - debug: heatingcontrol.0 (4989) AddStatusToLog skip Arbeitszimmer auto 26.5°C
            2021-02-09 12:02:23.145  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 09.02.2021 12:00:00 auto 26.5°C <br> 09.02.2021 11:56:04 manual 15°C <br> 09.02.2021 11:56:03 manual WindowOpen 9°C <br> 09.02.2021 11:52:05 auto WindowOpen 19°C <br> 09.02.2021 10:45:53 auto 25°C <br> 09.02.2021 10:45:31 auto WindowOpen 19°C <br> 09.02.2021 09:10:02 auto 25°C <br> 09.02.2021 09:09:41 auto WindowOpen 19°C <br> 09.02.2021 09:05:29 auto 25°C <br> 09.02.2021 08:18:07 auto 25.5°C <br> 09.02.2021 07:56:17 auto 28°C <br> 09.02.2021 07:56:03 manual 15°C <br> 09.02.2021 07:51:20 auto 26°C <br> 09.02.2021 07:48:42 auto WindowOpen 18.5°C <br> 09.02.2021 07:28:41 auto 25.5°C <br> 09.02.2021 07:28:36 starting 20.5°C <br> 09.02.2021 07:28:35 starting <br>","ack":false,"ts":1612868543142,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400371}
            2021-02-09 12:02:23.145  - debug: heatingcontrol.0 (4989) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
            2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) ChangeStatus recall cmd from list Arbeitszimmer Thermostats_Current {"val":24,"ack":true,"ts":1612868542914,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612868405927} (0)
            2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) Arbeitszimmer ### ChangeStatus Thermostats_Current to {"val":24,"ack":true,"ts":1612868542914,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612868405927} in auto
            2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) Change Status current temperature in Arbeitszimmer to 24
            2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) HandleActors for Arbeitszimmer auto
            2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
            2021-02-09 12:02:23.215  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":3,"ack":false,"ts":1612868543212,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400223}
            2021-02-09 12:02:23.215  - debug: heatingcontrol.0 (4989) HandleStateChanges CurrentTimePeriod 3
            2021-02-09 12:02:23.223  - debug: heatingcontrol.0 (4989) AddStatusToLog skip Arbeitszimmer auto 26.5°C
            2021-02-09 12:02:23.237  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 09.02.2021 12:00:00 auto 26.5°C <br> 09.02.2021 11:56:04 manual 15°C <br> 09.02.2021 11:56:03 manual WindowOpen 9°C <br> 09.02.2021 11:52:05 auto WindowOpen 19°C <br> 09.02.2021 10:45:53 auto 25°C <br> 09.02.2021 10:45:31 auto WindowOpen 19°C <br> 09.02.2021 09:10:02 auto 25°C <br> 09.02.2021 09:09:41 auto WindowOpen 19°C <br> 09.02.2021 09:05:29 auto 25°C <br> 09.02.2021 08:18:07 auto 25.5°C <br> 09.02.2021 07:56:17 auto 28°C <br> 09.02.2021 07:56:03 manual 15°C <br> 09.02.2021 07:51:20 auto 26°C <br> 09.02.2021 07:48:42 auto WindowOpen 18.5°C <br> 09.02.2021 07:28:41 auto 25.5°C <br> 09.02.2021 07:28:36 starting 20.5°C <br> 09.02.2021 07:28:35 starting <br>","ack":false,"ts":1612868543234,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400371}
            2021-02-09 12:02:23.237  - debug: heatingcontrol.0 (4989) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
            2021-02-09 12:02:47.986  - debug: heatingcontrol.0 (4989) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":18.5,"ack":true,"ts":1612868567984,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612868567984} in auto
            2021-02-09 12:02:47.986  - debug: heatingcontrol.0 (4989) calculate temp offset for Arbeitszimmer old value is 8, got value {"val":18.5,"ack":true,"ts":1612868567984,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612868567984}
            2021-02-09 12:02:47.989  - debug: heatingcontrol.0 (4989) got 24 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
            2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) tempdiff: 24 - 18.5 = 5.5
            2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) TempOffset Arbeitszimmer
            2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) (avg) Ist-Temperatur am Thermostat 24
            2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) Ist-Temperatur am zusätzl. Sensor 18.5
            2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) tempDiff 5.5
            2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) (avg) TempOffset 7
            2021-02-09 12:02:47.999  - debug: heatingcontrol.0 (4989) new temp offset for Arbeitszimmer is 7
            2021-02-09 12:02:48.000  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
            2021-02-09 12:02:48.015  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":3,"ack":false,"ts":1612868568013,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400223}
            2021-02-09 12:02:48.016  - debug: heatingcontrol.0 (4989) HandleStateChanges CurrentTimePeriod 3
            2021-02-09 12:02:48.023  - debug: heatingcontrol.0 (4989) AddStatusToLog skip Arbeitszimmer auto 26.5°C
            2021-02-09 12:02:48.085  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 09.02.2021 12:00:00 auto 26.5°C <br> 09.02.2021 11:56:04 manual 15°C <br> 09.02.2021 11:56:03 manual WindowOpen 9°C <br> 09.02.2021 11:52:05 auto WindowOpen 19°C <br> 09.02.2021 10:45:53 auto 25°C <br> 09.02.2021 10:45:31 auto WindowOpen 19°C <br> 09.02.2021 09:10:02 auto 25°C <br> 09.02.2021 09:09:41 auto WindowOpen 19°C <br> 09.02.2021 09:05:29 auto 25°C <br> 09.02.2021 08:18:07 auto 25.5°C <br> 09.02.2021 07:56:17 auto 28°C <br> 09.02.2021 07:56:03 manual 15°C <br> 09.02.2021 07:51:20 auto 26°C <br> 09.02.2021 07:48:42 auto WindowOpen 18.5°C <br> 09.02.2021 07:28:41 auto 25.5°C <br> 09.02.2021 07:28:36 starting 20.5°C <br> 09.02.2021 07:28:35 starting <br>","ack":false,"ts":1612868568082,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400371}
            2021-02-09 12:02:48.086  - debug: heatingcontrol.0 (4989) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
            

            Evtl. verstehe ich das auch falsch, sollte die SetTemperatur nicht annähernd die SollTemperatur vom Zeitpunkt haben? So heitzt doch die Heizung wenn die Temperatur unter 26.5°C fällt? Die Temperaturschwankung des zusätzlichen Senors ist durch Lüften entstanden um 11:52 habe ich die Balkontür aufgemacht.
            Ich habe jetzt ein Ist von 22,8 bei einem soll von 18.5

            PS: Das Problem mit dem ManuMode und der Temperatursturzerkennung habe ich mit einem Blockly gelöst, wenn das Fenster geschlossen wurde, setze heatingcontrol.0.Rooms.Arbeitszimmer.ResetManual nach 5min auf wahr.

            Rene_HMR 1 Antwort Letzte Antwort
            0
            • B Borio85

              @Rene_HM Die V2.1.1. läuft seit gestern ziemlich sauber und der Offset wird auf die Soll-Temp addiert.
              Follgendes ist mir aufgefallen, wenn der nächste Profilzeitpunkt niedirger ist als vorher z.b. von 20,5 auf 18,5 bleibt die SetTempertrue höher als die nidrigere Soll

              Log beim Profilzeipunkt mit 20,5°C

              2021-02-09 11:52:42.332  - debug: heatingcontrol.0 (4989) calculate temp offset for Arbeitszimmer old value is 4.5, got value {"val":21.6,"ack":true,"ts":1612867962326,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612867417332}
              2021-02-09 11:52:42.334  - debug: heatingcontrol.0 (4989) got 27.2 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
              2021-02-09 11:52:42.336  - debug: heatingcontrol.0 (4989) tempdiff: 27.2 - 21.6 = 5.599999999999998
              2021-02-09 11:52:42.336  - debug: heatingcontrol.0 (4989) TempOffset Arbeitszimmer
              2021-02-09 11:52:42.337  - debug: heatingcontrol.0 (4989) (avg) Ist-Temperatur am Thermostat 27.2
              2021-02-09 11:52:42.337  - debug: heatingcontrol.0 (4989) Ist-Temperatur am zusätzl. Sensor 21.6
              2021-02-09 11:52:42.337  - debug: heatingcontrol.0 (4989) tempDiff 5.599999999999998
              2021-02-09 11:52:42.338  - debug: heatingcontrol.0 (4989) (avg) TempOffset 5
              2021-02-09 11:52:42.357  - debug: heatingcontrol.0 (4989) new temp offset for Arbeitszimmer is 5
              2021-02-09 11:52:42.357  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
              2021-02-09 11:52:42.426  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":2,"ack":false,"ts":1612867962422,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612852120952}
              

              LOG bei Profilwechsel zu 18,5°C

              2021-02-09 12:00:00.015  - debug: heatingcontrol.0 (4989) ChangeStatus fired with [{"room":"Arbeitszimmer","target":18.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"12:00","CurrentTimePeriodFull":"Period 3 12:00"},{"room":"Schlafzimmer","target":17.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"12:00","CurrentTimePeriodFull":"Period 3 12:00"}]
              2021-02-09 12:00:00.016  - debug: heatingcontrol.0 (4989) Arbeitszimmer ### ChangeStatus ProfilPoint to {"room":"Arbeitszimmer","target":18.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"12:00","CurrentTimePeriodFull":"Period 3 12:00"} in manual
              2021-02-09 12:00:00.016  - debug: heatingcontrol.0 (4989) reset manual mode to auto
              2021-02-09 12:00:00.016  - debug: heatingcontrol.0 (4989) ChangeStatus by cron Profilepoint in Arbeitszimmer target 18.5
              2021-02-09 12:00:00.017  - debug: heatingcontrol.0 (4989) CalculateRoomTemperature for Arbeitszimmer auto
              2021-02-09 12:00:00.017  - debug: heatingcontrol.0 (4989) Arbeitszimmer auto mode: target 18.5
              2021-02-09 12:00:00.017  - debug: heatingcontrol.0 (4989) Arbeitszimmer auto mode (incl. reduced): target 18.5
              2021-02-09 12:00:00.018  - debug: heatingcontrol.0 (4989) SetRoomTemperature started for Arbeitszimmer target 18.5 with offset 8
              2021-02-09 12:00:00.051  - debug: heatingcontrol.0 (4989) unsubscribe hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.setPointTemperature
              2021-02-09 12:00:00.052  - debug: heatingcontrol.0 (4989) Arbeitszimmer set thermostat target hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.setPointTemperature to 26.5
              2021-02-09 12:00:00.118  - info: host.raspberrypi4-ioB instance system.adapter.coronavirus-statistics.0 started with pid 18989
              2021-02-09 12:00:00.129  - debug: heatingcontrol.0 (4989) HandleActors for Arbeitszimmer auto
              2021-02-09 12:00:00.129  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
              2021-02-09 12:00:00.128  - info: hmip.0 (11951) state change - setPointTemperature - id 69b2e9b4-e7fa-4376-aab5-2e55b666df91 - value 26.5
              

              Log Offsetberechnung mit 18.5°C

              2021-02-09 12:02:19.579  - debug: heatingcontrol.0 (4989) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
              2021-02-09 12:02:22.971  - debug: heatingcontrol.0 (4989) Arbeitszimmer ### ChangeStatus Thermostats_Target to {"val":26.5,"ack":true,"ts":1612868542913,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612868400124} in auto
              2021-02-09 12:02:22.972  - debug: heatingcontrol.0 (4989) Change Status target temperature in Arbeitszimmer to 26.5 (profile 18.5) in auto
              2021-02-09 12:02:22.972  - debug: heatingcontrol.0 (4989) CheckManualMode Arbeitszimmer
              2021-02-09 12:02:22.973  - debug: heatingcontrol.0 (4989) CheckStartManualMode Arbeitszimmer
              2021-02-09 12:02:22.973  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
              2021-02-09 12:02:22.975  - debug: heatingcontrol.0 (4989) ChangeStatus called, while already changing, push to list Arbeitszimmer Thermostats_Current {"val":24,"ack":true,"ts":1612868542914,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612868405927} (1)
              2021-02-09 12:02:23.081  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":3,"ack":false,"ts":1612868543077,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400223}
              2021-02-09 12:02:23.081  - debug: heatingcontrol.0 (4989) HandleStateChanges CurrentTimePeriod 3
              2021-02-09 12:02:23.131  - debug: heatingcontrol.0 (4989) AddStatusToLog skip Arbeitszimmer auto 26.5°C
              2021-02-09 12:02:23.145  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 09.02.2021 12:00:00 auto 26.5°C <br> 09.02.2021 11:56:04 manual 15°C <br> 09.02.2021 11:56:03 manual WindowOpen 9°C <br> 09.02.2021 11:52:05 auto WindowOpen 19°C <br> 09.02.2021 10:45:53 auto 25°C <br> 09.02.2021 10:45:31 auto WindowOpen 19°C <br> 09.02.2021 09:10:02 auto 25°C <br> 09.02.2021 09:09:41 auto WindowOpen 19°C <br> 09.02.2021 09:05:29 auto 25°C <br> 09.02.2021 08:18:07 auto 25.5°C <br> 09.02.2021 07:56:17 auto 28°C <br> 09.02.2021 07:56:03 manual 15°C <br> 09.02.2021 07:51:20 auto 26°C <br> 09.02.2021 07:48:42 auto WindowOpen 18.5°C <br> 09.02.2021 07:28:41 auto 25.5°C <br> 09.02.2021 07:28:36 starting 20.5°C <br> 09.02.2021 07:28:35 starting <br>","ack":false,"ts":1612868543142,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400371}
              2021-02-09 12:02:23.145  - debug: heatingcontrol.0 (4989) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
              2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) ChangeStatus recall cmd from list Arbeitszimmer Thermostats_Current {"val":24,"ack":true,"ts":1612868542914,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612868405927} (0)
              2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) Arbeitszimmer ### ChangeStatus Thermostats_Current to {"val":24,"ack":true,"ts":1612868542914,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612868405927} in auto
              2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) Change Status current temperature in Arbeitszimmer to 24
              2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) HandleActors for Arbeitszimmer auto
              2021-02-09 12:02:23.153  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
              2021-02-09 12:02:23.215  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":3,"ack":false,"ts":1612868543212,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400223}
              2021-02-09 12:02:23.215  - debug: heatingcontrol.0 (4989) HandleStateChanges CurrentTimePeriod 3
              2021-02-09 12:02:23.223  - debug: heatingcontrol.0 (4989) AddStatusToLog skip Arbeitszimmer auto 26.5°C
              2021-02-09 12:02:23.237  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 09.02.2021 12:00:00 auto 26.5°C <br> 09.02.2021 11:56:04 manual 15°C <br> 09.02.2021 11:56:03 manual WindowOpen 9°C <br> 09.02.2021 11:52:05 auto WindowOpen 19°C <br> 09.02.2021 10:45:53 auto 25°C <br> 09.02.2021 10:45:31 auto WindowOpen 19°C <br> 09.02.2021 09:10:02 auto 25°C <br> 09.02.2021 09:09:41 auto WindowOpen 19°C <br> 09.02.2021 09:05:29 auto 25°C <br> 09.02.2021 08:18:07 auto 25.5°C <br> 09.02.2021 07:56:17 auto 28°C <br> 09.02.2021 07:56:03 manual 15°C <br> 09.02.2021 07:51:20 auto 26°C <br> 09.02.2021 07:48:42 auto WindowOpen 18.5°C <br> 09.02.2021 07:28:41 auto 25.5°C <br> 09.02.2021 07:28:36 starting 20.5°C <br> 09.02.2021 07:28:35 starting <br>","ack":false,"ts":1612868543234,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400371}
              2021-02-09 12:02:23.237  - debug: heatingcontrol.0 (4989) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
              2021-02-09 12:02:47.986  - debug: heatingcontrol.0 (4989) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":18.5,"ack":true,"ts":1612868567984,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612868567984} in auto
              2021-02-09 12:02:47.986  - debug: heatingcontrol.0 (4989) calculate temp offset for Arbeitszimmer old value is 8, got value {"val":18.5,"ack":true,"ts":1612868567984,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612868567984}
              2021-02-09 12:02:47.989  - debug: heatingcontrol.0 (4989) got 24 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
              2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) tempdiff: 24 - 18.5 = 5.5
              2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) TempOffset Arbeitszimmer
              2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) (avg) Ist-Temperatur am Thermostat 24
              2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) Ist-Temperatur am zusätzl. Sensor 18.5
              2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) tempDiff 5.5
              2021-02-09 12:02:47.990  - debug: heatingcontrol.0 (4989) (avg) TempOffset 7
              2021-02-09 12:02:47.999  - debug: heatingcontrol.0 (4989) new temp offset for Arbeitszimmer is 7
              2021-02-09 12:02:48.000  - debug: heatingcontrol.0 (4989) UpdateDPs  for Arbeitszimmer auto
              2021-02-09 12:02:48.015  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":3,"ack":false,"ts":1612868568013,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400223}
              2021-02-09 12:02:48.016  - debug: heatingcontrol.0 (4989) HandleStateChanges CurrentTimePeriod 3
              2021-02-09 12:02:48.023  - debug: heatingcontrol.0 (4989) AddStatusToLog skip Arbeitszimmer auto 26.5°C
              2021-02-09 12:02:48.085  - debug: heatingcontrol.0 (4989) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 09.02.2021 12:00:00 auto 26.5°C <br> 09.02.2021 11:56:04 manual 15°C <br> 09.02.2021 11:56:03 manual WindowOpen 9°C <br> 09.02.2021 11:52:05 auto WindowOpen 19°C <br> 09.02.2021 10:45:53 auto 25°C <br> 09.02.2021 10:45:31 auto WindowOpen 19°C <br> 09.02.2021 09:10:02 auto 25°C <br> 09.02.2021 09:09:41 auto WindowOpen 19°C <br> 09.02.2021 09:05:29 auto 25°C <br> 09.02.2021 08:18:07 auto 25.5°C <br> 09.02.2021 07:56:17 auto 28°C <br> 09.02.2021 07:56:03 manual 15°C <br> 09.02.2021 07:51:20 auto 26°C <br> 09.02.2021 07:48:42 auto WindowOpen 18.5°C <br> 09.02.2021 07:28:41 auto 25.5°C <br> 09.02.2021 07:28:36 starting 20.5°C <br> 09.02.2021 07:28:35 starting <br>","ack":false,"ts":1612868568082,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612868400371}
              2021-02-09 12:02:48.086  - debug: heatingcontrol.0 (4989) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
              

              Evtl. verstehe ich das auch falsch, sollte die SetTemperatur nicht annähernd die SollTemperatur vom Zeitpunkt haben? So heitzt doch die Heizung wenn die Temperatur unter 26.5°C fällt? Die Temperaturschwankung des zusätzlichen Senors ist durch Lüften entstanden um 11:52 habe ich die Balkontür aufgemacht.
              Ich habe jetzt ein Ist von 22,8 bei einem soll von 18.5

              PS: Das Problem mit dem ManuMode und der Temperatursturzerkennung habe ich mit einem Blockly gelöst, wenn das Fenster geschlossen wurde, setze heatingcontrol.0.Rooms.Arbeitszimmer.ResetManual nach 5min auf wahr.

              Rene_HMR Offline
              Rene_HMR Offline
              Rene_HM
              Developer
              schrieb am zuletzt editiert von
              #2139

              @borio85 sagte in Test Adapter HeatingControl v2.1.x:

              Evtl. verstehe ich das auch falsch, sollte die SetTemperatur nicht annähernd die SollTemperatur vom Zeitpunkt haben?

              wie im oben verlinkten Ticket auf github geschrieben, addiere ich einfach den Offset (also die Differenz zwischen Ist am Thermostat und Ist am zusätzlichen Sensor) auf die Soll-Temperatur.
              Die Idee dahinter ist, dass der Sensor am Thermostat einen relativ konstanten Offset zum Sensor im Raum hat. Eigentlich müsste das Thermostat in dem Fall einfach nur nach dem zusätzlichen Sensor regeln, das bekomme ich mit dem Adapter aber nicht hin, weil ich die Temperatur vom zusätzlichen Sensor nicht dem Thermostat mitteilen kann.

              B ChaotC 2 Antworten Letzte Antwort
              0
              • Rene_HMR Rene_HM

                @borio85 sagte in Test Adapter HeatingControl v2.1.x:

                Evtl. verstehe ich das auch falsch, sollte die SetTemperatur nicht annähernd die SollTemperatur vom Zeitpunkt haben?

                wie im oben verlinkten Ticket auf github geschrieben, addiere ich einfach den Offset (also die Differenz zwischen Ist am Thermostat und Ist am zusätzlichen Sensor) auf die Soll-Temperatur.
                Die Idee dahinter ist, dass der Sensor am Thermostat einen relativ konstanten Offset zum Sensor im Raum hat. Eigentlich müsste das Thermostat in dem Fall einfach nur nach dem zusätzlichen Sensor regeln, das bekomme ich mit dem Adapter aber nicht hin, weil ich die Temperatur vom zusätzlichen Sensor nicht dem Thermostat mitteilen kann.

                B Offline
                B Offline
                Borio85
                schrieb am zuletzt editiert von
                #2140

                @rene_hm
                Ist schon gut, ich glaube ich hatte einen Denkfehler. Der Offset sollte ja annähernd gleich sein egal ob bei 15C oder 25C.

                1 Antwort Letzte Antwort
                0
                • Rene_HMR Rene_HM

                  @borio85 sagte in Test Adapter HeatingControl v2.1.x:

                  Evtl. verstehe ich das auch falsch, sollte die SetTemperatur nicht annähernd die SollTemperatur vom Zeitpunkt haben?

                  wie im oben verlinkten Ticket auf github geschrieben, addiere ich einfach den Offset (also die Differenz zwischen Ist am Thermostat und Ist am zusätzlichen Sensor) auf die Soll-Temperatur.
                  Die Idee dahinter ist, dass der Sensor am Thermostat einen relativ konstanten Offset zum Sensor im Raum hat. Eigentlich müsste das Thermostat in dem Fall einfach nur nach dem zusätzlichen Sensor regeln, das bekomme ich mit dem Adapter aber nicht hin, weil ich die Temperatur vom zusätzlichen Sensor nicht dem Thermostat mitteilen kann.

                  ChaotC Offline
                  ChaotC Offline
                  Chaot
                  schrieb am zuletzt editiert von
                  #2141

                  @rene_hm Äh, das ist mir etwas peinlich das ich das jetzt erst bemerke.
                  Hast du die Boost Funktion wieder rausgenommen?
                  Ich hatte da ein Thermostat das ich per Button und Script auf "ein" gesetzt habe und für 1 Stunde alle Einstellungen übergangen habe.

                  ioBroker auf NUC unter Proxmox; VIS: 12" Touchscreen und 17" Touch; Lichtsteuerung, Thermometer und Sensoren: Tasmota (39); Ambiente Beleuchtung: WLED (9); Heizung: DECT Thermostate (9) an Fritz 6690; EMS-ESP; 1 Echo V2; 3 Echo DOT; 1 Echo Connect; 2 Echo Show 5; Unifi Ap-Ac Lite.

                  Rene_HMR 1 Antwort Letzte Antwort
                  0
                  • B Offline
                    B Offline
                    Belgarion1977
                    schrieb am zuletzt editiert von
                    #2142

                    Hallo Zusammen,

                    ich habe da drei Fragen. :-)

                    Gibt es einen "einfachen" Weg Einstellungen zu setzen die für alle Räume gleich sein sollen.
                    Also z,B Boost Einstellungen, min/max Temp, decal Funktion

                    Gibt es einen Weg ein bestehendes Profil auf andere Räume zu "kopieren" um es dann anzupassen bzw. mehrere Räume dem selben Profil zuzuordnen?

                    Gibt es eine Übersicht der schon bestehenden Visualisierungen?

                    Danke euch und frohes Heizen!

                    :-)

                    Rene_HMR 1 Antwort Letzte Antwort
                    0
                    • ChaotC Chaot

                      @rene_hm Äh, das ist mir etwas peinlich das ich das jetzt erst bemerke.
                      Hast du die Boost Funktion wieder rausgenommen?
                      Ich hatte da ein Thermostat das ich per Button und Script auf "ein" gesetzt habe und für 1 Stunde alle Einstellungen übergangen habe.

                      Rene_HMR Offline
                      Rene_HMR Offline
                      Rene_HM
                      Developer
                      schrieb am zuletzt editiert von
                      #2143

                      @chaot sagte in Test Adapter HeatingControl v2.1.x:

                      Hast du die Boost Funktion wieder rausgenommen?

                      Bin mir da nicht sicher, welches Feature du da konkret meinst, Du meinst nicht das hier?
                      https://github.com/rg-engineering/ioBroker.heatingcontrol/issues/156

                      Du schreibst per script direkt auf das Thermostat, richtig? und was passiert, oder passiert nicht?

                      ChaotC 1 Antwort Letzte Antwort
                      1
                      • B Belgarion1977

                        Hallo Zusammen,

                        ich habe da drei Fragen. :-)

                        Gibt es einen "einfachen" Weg Einstellungen zu setzen die für alle Räume gleich sein sollen.
                        Also z,B Boost Einstellungen, min/max Temp, decal Funktion

                        Gibt es einen Weg ein bestehendes Profil auf andere Räume zu "kopieren" um es dann anzupassen bzw. mehrere Räume dem selben Profil zuzuordnen?

                        Gibt es eine Übersicht der schon bestehenden Visualisierungen?

                        Danke euch und frohes Heizen!

                        :-)

                        Rene_HMR Offline
                        Rene_HMR Offline
                        Rene_HM
                        Developer
                        schrieb am zuletzt editiert von
                        #2144

                        @belgarion1977 sagte in Test Adapter HeatingControl v2.1.x:

                        Gibt es einen "einfachen" Weg Einstellungen zu setzen die für alle Räume gleich sein sollen.
                        Also z,B Boost Einstellungen, min/max Temp, decal Funktion

                        nicht direkt. aber indirekt über Download Profil, manuelles Ädern des json-Files und dann wieder upload,,

                        Gibt es einen Weg ein bestehendes Profil auf andere Räume zu "kopieren" um es dann anzupassen bzw. mehrere Räume dem selben Profil zuzuordnen?

                        nein. Du kannst für einen Raum das Profil auf ein nächstes Profil kopieren (also z.Bsp. für Wohnzimmer von Profil 1 auf 2). Aber auch kannst du durch manuelles Editieren der json Datei das selbst machen...

                        Gibt es eine Übersicht der schon bestehenden Visualisierungen?

                        Ich empfehle die vis von Pittini...

                        1 Antwort Letzte Antwort
                        0
                        • Rene_HMR Rene_HM

                          @chaot sagte in Test Adapter HeatingControl v2.1.x:

                          Hast du die Boost Funktion wieder rausgenommen?

                          Bin mir da nicht sicher, welches Feature du da konkret meinst, Du meinst nicht das hier?
                          https://github.com/rg-engineering/ioBroker.heatingcontrol/issues/156

                          Du schreibst per script direkt auf das Thermostat, richtig? und was passiert, oder passiert nicht?

                          ChaotC Offline
                          ChaotC Offline
                          Chaot
                          schrieb am zuletzt editiert von Chaot
                          #2145

                          @rene_hm Ich denke mal das ich das auch anders lösen kann.
                          Im alten Adapter gab es in den Objekten einen Datenpunkt "boost" der als Schalter von mir genutzt wurde. Das ausführende Script hat auf den Schalter reagiert und den Modus am Thermostat von Automatik auf Ein gesetzt.
                          Ich habe heute gesehen das ich den Override scheinbar auch dafür nutzen kann. Zumindest ging der Thermostat auf Ein als ich 30 °C ausgewählt habe. Ich muss mir nur noch überlegen wie ich den per "one Button" schalte.

                          Ich nutze das im Badezimmer. Das läuft normalerweise auf etwas über 20°C. Wenn ich meine Kleine aber zum Baden oder Duschen schicke ist das zu kühl. Also setze ich vorher für ca. 1h das Bad auf volle Leistung. Dann ist es warm und danach greift wieder die normale Regelung.
                          Da dafür aber keine festen Zeiten machbar sind habe ich eben den Button in der VIS der das spontan auslösen kann. Erfahrungsgemäß habe ich (bzw. meine Frau) die benötigte halbe Stunde Vorlaufzeit um das Bad auf Temperatur zu bringen.

                          Edit: Sehe ich irgendwo die Restlaufzeit vom Timer?

                          ioBroker auf NUC unter Proxmox; VIS: 12" Touchscreen und 17" Touch; Lichtsteuerung, Thermometer und Sensoren: Tasmota (39); Ambiente Beleuchtung: WLED (9); Heizung: DECT Thermostate (9) an Fritz 6690; EMS-ESP; 1 Echo V2; 3 Echo DOT; 1 Echo Connect; 2 Echo Show 5; Unifi Ap-Ac Lite.

                          Rene_HMR 2 Antworten Letzte Antwort
                          0
                          • ChaotC Chaot

                            @rene_hm Ich denke mal das ich das auch anders lösen kann.
                            Im alten Adapter gab es in den Objekten einen Datenpunkt "boost" der als Schalter von mir genutzt wurde. Das ausführende Script hat auf den Schalter reagiert und den Modus am Thermostat von Automatik auf Ein gesetzt.
                            Ich habe heute gesehen das ich den Override scheinbar auch dafür nutzen kann. Zumindest ging der Thermostat auf Ein als ich 30 °C ausgewählt habe. Ich muss mir nur noch überlegen wie ich den per "one Button" schalte.

                            Ich nutze das im Badezimmer. Das läuft normalerweise auf etwas über 20°C. Wenn ich meine Kleine aber zum Baden oder Duschen schicke ist das zu kühl. Also setze ich vorher für ca. 1h das Bad auf volle Leistung. Dann ist es warm und danach greift wieder die normale Regelung.
                            Da dafür aber keine festen Zeiten machbar sind habe ich eben den Button in der VIS der das spontan auslösen kann. Erfahrungsgemäß habe ich (bzw. meine Frau) die benötigte halbe Stunde Vorlaufzeit um das Bad auf Temperatur zu bringen.

                            Edit: Sehe ich irgendwo die Restlaufzeit vom Timer?

                            Rene_HMR Offline
                            Rene_HMR Offline
                            Rene_HM
                            Developer
                            schrieb am zuletzt editiert von
                            #2146

                            @chaot sagte in Test Adapter HeatingControl v2.1.x:

                            Im alten Adapter gab es in den Objekten einen Datenpunkt "boost" der als Schalter von mir genutzt wurde

                            Was ist bei dir "alter Adapter"? Version 1.x?

                            Aber richtig: die Funktion, die du hier benötigst ist "Override". Per script einfach Override und OverrideTime setzen..

                            ChaotC 1 Antwort Letzte Antwort
                            0
                            • ChaotC Chaot

                              @rene_hm Ich denke mal das ich das auch anders lösen kann.
                              Im alten Adapter gab es in den Objekten einen Datenpunkt "boost" der als Schalter von mir genutzt wurde. Das ausführende Script hat auf den Schalter reagiert und den Modus am Thermostat von Automatik auf Ein gesetzt.
                              Ich habe heute gesehen das ich den Override scheinbar auch dafür nutzen kann. Zumindest ging der Thermostat auf Ein als ich 30 °C ausgewählt habe. Ich muss mir nur noch überlegen wie ich den per "one Button" schalte.

                              Ich nutze das im Badezimmer. Das läuft normalerweise auf etwas über 20°C. Wenn ich meine Kleine aber zum Baden oder Duschen schicke ist das zu kühl. Also setze ich vorher für ca. 1h das Bad auf volle Leistung. Dann ist es warm und danach greift wieder die normale Regelung.
                              Da dafür aber keine festen Zeiten machbar sind habe ich eben den Button in der VIS der das spontan auslösen kann. Erfahrungsgemäß habe ich (bzw. meine Frau) die benötigte halbe Stunde Vorlaufzeit um das Bad auf Temperatur zu bringen.

                              Edit: Sehe ich irgendwo die Restlaufzeit vom Timer?

                              Rene_HMR Offline
                              Rene_HMR Offline
                              Rene_HM
                              Developer
                              schrieb am zuletzt editiert von
                              #2147

                              @chaot sagte in Test Adapter HeatingControl v2.1.x:

                              Edit: Sehe ich irgendwo die Restlaufzeit vom Timer?

                              siehe https://github.com/rg-engineering/ioBroker.heatingcontrol/issues/187

                              D.h. Issue ist da, aber noch nicht umgesetzt...

                              1 Antwort Letzte Antwort
                              1
                              • Rene_HMR Rene_HM

                                @chaot sagte in Test Adapter HeatingControl v2.1.x:

                                Im alten Adapter gab es in den Objekten einen Datenpunkt "boost" der als Schalter von mir genutzt wurde

                                Was ist bei dir "alter Adapter"? Version 1.x?

                                Aber richtig: die Funktion, die du hier benötigst ist "Override". Per script einfach Override und OverrideTime setzen..

                                ChaotC Offline
                                ChaotC Offline
                                Chaot
                                schrieb am zuletzt editiert von
                                #2148

                                @rene_hm Ja, das war in der Version 1.x
                                Klappt jetzt erst mal ohne Restlaufzeit. Mal schauen wie ich das optisch so umsetze das es bei der Buttonlösung bleibt. Gefällt mir noch nicht so, aber das wird schon.

                                ioBroker auf NUC unter Proxmox; VIS: 12" Touchscreen und 17" Touch; Lichtsteuerung, Thermometer und Sensoren: Tasmota (39); Ambiente Beleuchtung: WLED (9); Heizung: DECT Thermostate (9) an Fritz 6690; EMS-ESP; 1 Echo V2; 3 Echo DOT; 1 Echo Connect; 2 Echo Show 5; Unifi Ap-Ac Lite.

                                Rene_HMR O 2 Antworten Letzte Antwort
                                0
                                • ChaotC Chaot

                                  @rene_hm Ja, das war in der Version 1.x
                                  Klappt jetzt erst mal ohne Restlaufzeit. Mal schauen wie ich das optisch so umsetze das es bei der Buttonlösung bleibt. Gefällt mir noch nicht so, aber das wird schon.

                                  Rene_HMR Offline
                                  Rene_HMR Offline
                                  Rene_HM
                                  Developer
                                  schrieb am zuletzt editiert von
                                  #2149

                                  @chaot es gibt auch eine Option, dass der Override verlängert (also quasi neu gestartet) wird, wenn man die Temperatur neu setzt.... andernfalls kann man die Temperatur während der Laufzeit des override ändern, es wird aber zurück auf auto geschaltet, sobald die Laufzeit nach dem ersten Start abgelaufen ist...

                                  1 Antwort Letzte Antwort
                                  0
                                  • ChaotC Chaot

                                    @rene_hm Ja, das war in der Version 1.x
                                    Klappt jetzt erst mal ohne Restlaufzeit. Mal schauen wie ich das optisch so umsetze das es bei der Buttonlösung bleibt. Gefällt mir noch nicht so, aber das wird schon.

                                    O Online
                                    O Online
                                    Oli
                                    schrieb am zuletzt editiert von
                                    #2150

                                    @chaot

                                    das mit der Restlaufzeit würde mich auch interessieren, wäre cool, wenn du das teilen könntest, sobald du eine Lösung gefunden hast

                                    Gruß
                                    Oliver

                                    Rene_HMR 1 Antwort Letzte Antwort
                                    0
                                    • O Oli

                                      @chaot

                                      das mit der Restlaufzeit würde mich auch interessieren, wäre cool, wenn du das teilen könntest, sobald du eine Lösung gefunden hast

                                      Rene_HMR Offline
                                      Rene_HMR Offline
                                      Rene_HM
                                      Developer
                                      schrieb am zuletzt editiert von
                                      #2151

                                      @oli das muss im Adapter gemacht werden... habe ich nur noch nicht geschafft...

                                      O 1 Antwort Letzte Antwort
                                      0
                                      • Rene_HMR Rene_HM

                                        @oli das muss im Adapter gemacht werden... habe ich nur noch nicht geschafft...

                                        O Online
                                        O Online
                                        Oli
                                        schrieb am zuletzt editiert von
                                        #2152

                                        @rene_hm

                                        danke für die Info

                                        Gruß
                                        Oliver

                                        1 Antwort Letzte Antwort
                                        0
                                        • E Offline
                                          E Offline
                                          eviltrooper
                                          schrieb am zuletzt editiert von
                                          #2153

                                          Hallo,
                                          Kann mir jemand helfen, wie oder was stelle ich das mit der Anwesenheit ein?
                                          Ich überwache das mit dem TR-064 für mich und die Frau.

                                          Was stell ich den da um ein. Und welches Profil Nutzt Heatingcontrol denn wenn wir „abwesend sind?

                                          B 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          837

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe