@rene_hm
Ok, dann versuche ich das mal so gut wie ich kann zu beschreiben:
Objekt-ID aktuelle Temperatur = Homematic valveActualTemperature
Objekt-ID Zieltemperatur = Homematic setPointTemperature
Objekt-ID zusätzlicher Sensor = Zigebee temperature
Profil für das Arbeitszimmer, sollte jetzt 19.5°C sein

Temperatur am Regler 21,6°C
Temperatur am Raumsensor 18,4°C
Gesetzte Temperatur 14°C
2021-02-07 17:45:15.171 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":17.4,"ack":true,"ts":1612716315167,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716315167} in auto
2021-02-07 17:45:15.172 - [34mdebug[39m: heatingcontrol.0 (21224) calculate temp offset for Arbeitszimmer old value is -4.5, got value {"val":17.4,"ack":true,"ts":1612716315167,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716315167}
2021-02-07 17:45:15.174 - [34mdebug[39m: heatingcontrol.0 (21224) got 23.7 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
2021-02-07 17:45:15.175 - [34mdebug[39m: heatingcontrol.0 (21224) tempdiff: 17.4 - 23.7 = -6.300000000000001
2021-02-07 17:45:15.175 - [34mdebug[39m: heatingcontrol.0 (21224) TempOffset Arbeitszimmer
2021-02-07 17:45:15.177 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) Ist-Temperatur am Thermostat 23.7
2021-02-07 17:45:15.178 - [34mdebug[39m: heatingcontrol.0 (21224) Ist-Temperatur am zusätzl. Sensor 17.4
2021-02-07 17:45:15.178 - [34mdebug[39m: heatingcontrol.0 (21224) tempDiff -6.300000000000001
2021-02-07 17:45:15.179 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) TempOffset -5.5
2021-02-07 17:45:15.190 - [34mdebug[39m: heatingcontrol.0 (21224) new temp offset for Arbeitszimmer is -5.5
2021-02-07 17:45:15.191 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:47:02.796 - [34mdebug[39m: heatingcontrol.0 (21224) Change Status current temperature in Arbeitszimmer to 21.9
2021-02-07 17:47:02.796 - [34mdebug[39m: heatingcontrol.0 (21224) HandleActors for Arbeitszimmer auto
2021-02-07 17:47:02.796 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:47:02.811 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612716422809,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 17:47:02.812 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 17:47:02.818 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto WindowOpen 12.5°C
2021-02-07 17:47:02.873 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612716422870,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716120447}
2021-02-07 17:47:02.873 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:47:16.306 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":16.4,"ack":true,"ts":1612716436298,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716436298} in auto
2021-02-07 17:47:16.306 - [34mdebug[39m: heatingcontrol.0 (21224) calculate temp offset for Arbeitszimmer old value is -5.5, got value {"val":16.4,"ack":true,"ts":1612716436298,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716436298}
2021-02-07 17:47:16.308 - [34mdebug[39m: heatingcontrol.0 (21224) got 21.9 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
2021-02-07 17:47:16.309 - [34mdebug[39m: heatingcontrol.0 (21224) tempdiff: 16.4 - 21.9 = -5.5
2021-02-07 17:47:16.309 - [34mdebug[39m: heatingcontrol.0 (21224) TempOffset Arbeitszimmer
2021-02-07 17:47:16.310 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) Ist-Temperatur am Thermostat 21.9
2021-02-07 17:47:16.310 - [34mdebug[39m: heatingcontrol.0 (21224) Ist-Temperatur am zusätzl. Sensor 16.4
2021-02-07 17:47:16.311 - [34mdebug[39m: heatingcontrol.0 (21224) tempDiff -5.5
2021-02-07 17:47:16.311 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) TempOffset -5.5
2021-02-07 17:47:16.319 - [34mdebug[39m: heatingcontrol.0 (21224) new temp offset for Arbeitszimmer is -5.5
2021-02-07 17:47:16.320 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:47:16.345 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612716436341,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 17:47:16.346 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 17:47:16.359 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto WindowOpen 12.5°C
2021-02-07 17:47:16.425 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612716436422,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716120447}
2021-02-07 17:47:16.426 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:47:33.432 - [34mdebug[39m: heatingcontrol.0 (21224) Badezimmer ### ChangeStatus AddTempSensor to {"val":20.9,"ack":true,"ts":1612716453426,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716453426} in auto
2021-02-07 17:48:06.269 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:48:16.877 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":15.8,"ack":true,"ts":1612716496874,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716496874} in auto
2021-02-07 17:48:16.878 - [34mdebug[39m: heatingcontrol.0 (21224) calculate temp offset for Arbeitszimmer old value is -5.5, got value {"val":15.8,"ack":true,"ts":1612716496874,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716496874}
2021-02-07 17:48:16.879 - [34mdebug[39m: heatingcontrol.0 (21224) got 21.9 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
2021-02-07 17:48:16.880 - [34mdebug[39m: heatingcontrol.0 (21224) tempdiff: 15.8 - 21.9 = -6.099999999999998
2021-02-07 17:48:16.880 - [34mdebug[39m: heatingcontrol.0 (21224) TempOffset Arbeitszimmer
2021-02-07 17:48:16.881 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) Ist-Temperatur am Thermostat 21.9
2021-02-07 17:48:16.881 - [34mdebug[39m: heatingcontrol.0 (21224) Ist-Temperatur am zusätzl. Sensor 15.8
2021-02-07 17:48:16.881 - [34mdebug[39m: heatingcontrol.0 (21224) tempDiff -6.099999999999998
2021-02-07 17:48:16.882 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) TempOffset -6
2021-02-07 17:48:16.888 - [34mdebug[39m: heatingcontrol.0 (21224) new temp offset for Arbeitszimmer is -6
2021-02-07 17:48:16.889 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:48:16.907 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612716496904,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 17:48:16.908 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 17:48:16.917 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 17:48:16.975 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612716496972,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 17:48:16.976 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:48:25.288 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus Thermostats_Target to {"val":14,"ack":true,"ts":1612716505217,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612716468439} in auto
2021-02-07 17:48:25.289 - [34mdebug[39m: heatingcontrol.0 (21224) Change Status target temperature in Arbeitszimmer to 14 (profile 19.5) in auto
2021-02-07 17:48:25.290 - [34mdebug[39m: heatingcontrol.0 (21224) CheckManualMode Arbeitszimmer
2021-02-07 17:48:25.290 - [34mdebug[39m: heatingcontrol.0 (21224) CheckStartManualMode Arbeitszimmer
2021-02-07 17:48:25.291 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:48:25.294 - [34mdebug[39m: heatingcontrol.0 (21224) ChangeStatus called, while already changing, push to list Arbeitszimmer Thermostats_Current {"val":21.4,"ack":true,"ts":1612716505218,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612716505218} (1)
2021-02-07 17:48:25.331 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612716505328,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 17:48:25.331 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 17:48:25.338 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 17:48:25.406 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612716505404,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 17:48:25.407 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:48:25.414 - [34mdebug[39m: heatingcontrol.0 (21224) ChangeStatus recall cmd from list Arbeitszimmer Thermostats_Current {"val":21.4,"ack":true,"ts":1612716505218,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612716505218} (0)
2021-02-07 17:48:25.414 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus Thermostats_Current to {"val":21.4,"ack":true,"ts":1612716505218,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612716505218} in auto
2021-02-07 17:48:25.414 - [34mdebug[39m: heatingcontrol.0 (21224) Change Status current temperature in Arbeitszimmer to 21.4
2021-02-07 17:48:25.415 - [34mdebug[39m: heatingcontrol.0 (21224) HandleActors for Arbeitszimmer auto
2021-02-07 17:48:25.415 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:48:25.430 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612716505427,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 17:48:25.430 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 17:48:25.436 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 17:48:25.448 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612716505445,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 17:48:25.448 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:48:32.858 - [34mdebug[39m: heatingcontrol.0 (21224) Wohnzimmer ### ChangeStatus AddTempSensor to {"val":21.4,"ack":true,"ts":1612716512795,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612710917340} in auto
2021-02-07 17:49:14.629 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:49:17.462 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":16.1,"ack":true,"ts":1612716557457,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716557457} in auto
2021-02-07 17:49:17.463 - [34mdebug[39m: heatingcontrol.0 (21224) calculate temp offset for Arbeitszimmer old value is -6, got value {"val":16.1,"ack":true,"ts":1612716557457,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716557457}
2021-02-07 17:49:17.465 - [34mdebug[39m: heatingcontrol.0 (21224) got 21.4 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
2021-02-07 17:49:17.465 - [34mdebug[39m: heatingcontrol.0 (21224) tempdiff: 16.1 - 21.4 = -5.299999999999997
2021-02-07 17:49:17.466 - [34mdebug[39m: heatingcontrol.0 (21224) TempOffset Arbeitszimmer
2021-02-07 17:49:17.466 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) Ist-Temperatur am Thermostat 21.4
2021-02-07 17:49:17.467 - [34mdebug[39m: heatingcontrol.0 (21224) Ist-Temperatur am zusätzl. Sensor 16.1
2021-02-07 17:49:17.467 - [34mdebug[39m: heatingcontrol.0 (21224) tempDiff -5.299999999999997
2021-02-07 17:49:17.468 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) TempOffset -5.5
2021-02-07 17:49:17.476 - [34mdebug[39m: heatingcontrol.0 (21224) new temp offset for Arbeitszimmer is -5.5
2021-02-07 17:49:17.477 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:49:17.505 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612716557499,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 17:49:17.506 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 17:49:17.520 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 17:49:17.585 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612716557582,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 17:49:17.586 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:49:36.673 - [34mdebug[39m: heatingcontrol.0 (21224) Küche ### ChangeStatus Thermostats_Target to {"val":18.5,"ack":true,"ts":1612716576619,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612716009234} in auto
2021-02-07 17:50:07.052 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:50:18.039 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":16.3,"ack":true,"ts":1612716618031,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716618031} in auto
2021-02-07 17:50:18.040 - [34mdebug[39m: heatingcontrol.0 (21224) calculate temp offset for Arbeitszimmer old value is -5.5, got value {"val":16.3,"ack":true,"ts":1612716618031,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716618031}
2021-02-07 17:50:18.042 - [34mdebug[39m: heatingcontrol.0 (21224) got 21.4 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
2021-02-07 17:50:18.042 - [34mdebug[39m: heatingcontrol.0 (21224) tempdiff: 16.3 - 21.4 = -5.099999999999998
2021-02-07 17:50:18.043 - [34mdebug[39m: heatingcontrol.0 (21224) TempOffset Arbeitszimmer
2021-02-07 17:50:18.043 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) Ist-Temperatur am Thermostat 21.4
2021-02-07 17:50:18.044 - [34mdebug[39m: heatingcontrol.0 (21224) Ist-Temperatur am zusätzl. Sensor 16.3
2021-02-07 17:50:18.044 - [34mdebug[39m: heatingcontrol.0 (21224) tempDiff -5.099999999999998
2021-02-07 17:50:18.044 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) TempOffset -5.5
2021-02-07 17:50:18.052 - [34mdebug[39m: heatingcontrol.0 (21224) new temp offset for Arbeitszimmer is -5.5
2021-02-07 17:50:18.053 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:50:18.073 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612716618069,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 17:50:18.074 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 17:50:18.085 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 17:50:18.140 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612716618136,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 17:50:18.141 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:54:06.579 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 17:54:20.331 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":17,"ack":true,"ts":1612716860324,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716860324} in auto
2021-02-07 17:54:20.332 - [34mdebug[39m: heatingcontrol.0 (21224) calculate temp offset for Arbeitszimmer old value is -5.5, got value {"val":17,"ack":true,"ts":1612716860324,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612716860324}
2021-02-07 17:54:20.334 - [34mdebug[39m: heatingcontrol.0 (21224) got 20.6 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
2021-02-07 17:54:20.335 - [34mdebug[39m: heatingcontrol.0 (21224) tempdiff: 17 - 20.6 = -3.6000000000000014
2021-02-07 17:54:20.335 - [34mdebug[39m: heatingcontrol.0 (21224) TempOffset Arbeitszimmer
2021-02-07 17:54:20.336 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) Ist-Temperatur am Thermostat 20.6
2021-02-07 17:54:20.336 - [34mdebug[39m: heatingcontrol.0 (21224) Ist-Temperatur am zusätzl. Sensor 17
2021-02-07 17:54:20.337 - [34mdebug[39m: heatingcontrol.0 (21224) tempDiff -3.6000000000000014
2021-02-07 17:54:20.345 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) TempOffset -4.5
2021-02-07 17:54:20.355 - [34mdebug[39m: heatingcontrol.0 (21224) new temp offset for Arbeitszimmer is -4.5
2021-02-07 17:54:20.356 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 17:54:20.384 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612716860379,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 17:54:20.385 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 17:54:20.395 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 17:54:20.454 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612716860452,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 17:54:20.455 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 18:00:16.803 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus Thermostats_Target to {"val":14,"ack":true,"ts":1612717216737,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612716468439} in auto
2021-02-07 18:00:16.803 - [34mdebug[39m: heatingcontrol.0 (21224) Change Status target temperature in Arbeitszimmer to 14 (profile 19.5) in auto
2021-02-07 18:00:16.804 - [34mdebug[39m: heatingcontrol.0 (21224) CheckManualMode Arbeitszimmer
2021-02-07 18:00:16.804 - [34mdebug[39m: heatingcontrol.0 (21224) CheckStartManualMode Arbeitszimmer
2021-02-07 18:00:16.805 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 18:00:16.807 - [34mdebug[39m: heatingcontrol.0 (21224) ChangeStatus called, while already changing, push to list Arbeitszimmer Thermostats_Current {"val":20.9,"ack":true,"ts":1612717216737,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612717216737} (1)
2021-02-07 18:00:16.877 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612717216875,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 18:00:16.877 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 18:00:16.883 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 18:00:16.932 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612717216930,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 18:00:16.933 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 18:00:16.938 - [34mdebug[39m: heatingcontrol.0 (21224) ChangeStatus recall cmd from list Arbeitszimmer Thermostats_Current {"val":20.9,"ack":true,"ts":1612717216737,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612717216737} (0)
2021-02-07 18:00:16.939 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus Thermostats_Current to {"val":20.9,"ack":true,"ts":1612717216737,"q":0,"from":"system.adapter.hmip.0","user":"system.user.admin","lc":1612717216737} in auto
2021-02-07 18:00:16.939 - [34mdebug[39m: heatingcontrol.0 (21224) Change Status current temperature in Arbeitszimmer to 20.9
2021-02-07 18:00:16.939 - [34mdebug[39m: heatingcontrol.0 (21224) HandleActors for Arbeitszimmer auto
2021-02-07 18:00:16.940 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 18:00:16.953 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612717216951,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 18:00:16.954 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 18:00:16.960 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 18:00:17.012 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612717217010,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 18:00:17.013 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 18:00:23.749 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":17.7,"ack":true,"ts":1612717223747,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612717223747} in auto
2021-02-07 18:00:23.750 - [34mdebug[39m: heatingcontrol.0 (21224) calculate temp offset for Arbeitszimmer old value is -4.5, got value {"val":17.7,"ack":true,"ts":1612717223747,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612717223747}
2021-02-07 18:00:23.751 - [34mdebug[39m: heatingcontrol.0 (21224) got 20.9 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
2021-02-07 18:00:23.752 - [34mdebug[39m: heatingcontrol.0 (21224) tempdiff: 17.7 - 20.9 = -3.1999999999999993
2021-02-07 18:00:23.752 - [34mdebug[39m: heatingcontrol.0 (21224) TempOffset Arbeitszimmer
2021-02-07 18:00:23.752 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) Ist-Temperatur am Thermostat 20.9
2021-02-07 18:00:23.753 - [34mdebug[39m: heatingcontrol.0 (21224) Ist-Temperatur am zusätzl. Sensor 17.7
2021-02-07 18:00:23.753 - [34mdebug[39m: heatingcontrol.0 (21224) tempDiff -3.1999999999999993
2021-02-07 18:00:23.753 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) TempOffset -4
2021-02-07 18:00:23.770 - [34mdebug[39m: heatingcontrol.0 (21224) new temp offset for Arbeitszimmer is -4
2021-02-07 18:00:23.770 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 18:00:23.783 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612717223781,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 18:00:23.784 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 18:00:23.790 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 18:00:23.844 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612717223842,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 18:00:23.845 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 18:11:04.996 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
2021-02-07 18:11:30.036 - [34mdebug[39m: heatingcontrol.0 (21224) Arbeitszimmer ### ChangeStatus AddTempSensor to {"val":18.4,"ack":true,"ts":1612717890030,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612717890030} in auto
2021-02-07 18:11:30.037 - [34mdebug[39m: heatingcontrol.0 (21224) calculate temp offset for Arbeitszimmer old value is -4, got value {"val":18.4,"ack":true,"ts":1612717890030,"q":0,"from":"system.adapter.zigbee.0","user":"system.user.admin","lc":1612717890030}
2021-02-07 18:11:30.038 - [34mdebug[39m: heatingcontrol.0 (21224) got 21.3 from hmip.0.devices.3014F711A0000A1BE99B884C.channels.1.valveActualTemperature
2021-02-07 18:11:30.039 - [34mdebug[39m: heatingcontrol.0 (21224) tempdiff: 18.4 - 21.3 = -2.900000000000002
2021-02-07 18:11:30.039 - [34mdebug[39m: heatingcontrol.0 (21224) TempOffset Arbeitszimmer
2021-02-07 18:11:30.039 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) Ist-Temperatur am Thermostat 21.3
2021-02-07 18:11:30.040 - [34mdebug[39m: heatingcontrol.0 (21224) Ist-Temperatur am zusätzl. Sensor 18.4
2021-02-07 18:11:30.040 - [34mdebug[39m: heatingcontrol.0 (21224) tempDiff -2.900000000000002
2021-02-07 18:11:30.040 - [34mdebug[39m: heatingcontrol.0 (21224) (avg) TempOffset -3.5
2021-02-07 18:11:30.046 - [34mdebug[39m: heatingcontrol.0 (21224) new temp offset for Arbeitszimmer is -3.5
2021-02-07 18:11:30.047 - [34mdebug[39m: heatingcontrol.0 (21224) UpdateDPs for Arbeitszimmer auto
2021-02-07 18:11:30.066 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.CurrentTimePeriod {"val":9,"ack":false,"ts":1612717890062,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716008312}
2021-02-07 18:11:30.066 - [34mdebug[39m: heatingcontrol.0 (21224) HandleStateChanges CurrentTimePeriod 9
2021-02-07 18:11:30.076 - [34mdebug[39m: heatingcontrol.0 (21224) AddStatusToLog skip Arbeitszimmer auto 14°C
2021-02-07 18:11:30.135 - [34mdebug[39m: heatingcontrol.0 (21224) ### handle state change heatingcontrol.0.Rooms.Arbeitszimmer.StatusLog {"val":" 07.02.2021 17:47:48 auto 14°C <br> 07.02.2021 17:42:00 auto WindowOpen 12.5°C <br> 07.02.2021 17:40:08 auto 18.5°C <br> 07.02.2021 17:40:04 starting 19.5°C <br> 07.02.2021 17:40:03 starting <br>","ack":false,"ts":1612717890132,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1612716468524}
2021-02-07 18:11:30.136 - [34mdebug[39m: heatingcontrol.0 (21224) Reaching SetStatusLog for Rooms.Arbeitszimmer.StatusLog
Das habe ich in den Logs gefunden zwischen 17:45 und 18:15, ich hoffe da ist alles drin was du brauchst.