  4. Status vom Kostal Wechselrichter auslesen?

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.7k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.1k

Status vom Kostal Wechselrichter auslesen?

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
331 Beiträge 35 Kommentatoren 88.7k Aufrufe 25 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • S Offline
    S Offline
    stoepselinho
    schrieb am zuletzt editiert von
    #42

    Hallo zusammen,

    trotz Code

    (?:\s+([a-zA-Z äöüÄÖÜ]+))
    

    wird mir bei Störung immer nur St angezeigt.

    Rolle -> Wert

    Typ -> String

    Alles ander Finktioniert ohne Probleme

    hat jemand eine Idee?

    1 Antwort Letzte Antwort
    0
    • DiginixD Offline
      DiginixD Offline
      Diginix
      schrieb am zuletzt editiert von
      #43

      Kann mir hier jemand die modbus Adapter Einstellungen für ein Plenticore Plus 5.5 mit Firmware 1.30 erklären oder als Screenshot zeigen.
      Habe die IP, Port und GeräteID eingetragen, sonst noch nichts weiter. Die Instanz bleibt aber gelb. Im Log steht "Serial is not available", habe aber TCP gewählt.

      ..:: So long! Tom ::..

      NUC7i3 (Ubuntu Proxmox VM) | Echo Dots 2+3. Gen | Xiaomi Sensoren | Mi Robot 1S | Yeelight | Sonoff | Shelly | H801 RGB | Gosund SP1 | NodeMCU+ESP32 | Kostal Plenticore PV+BYD | openWB

      J 1 Antwort Letzte Antwort
      0
      • bahnuhrB bahnuhr

        Ich benutze folgendes Script:

        /* Photovoltaik: Piko 5.5 Anlage
        
        Diese Script stammt aus dem Homematic Forum. Von wem weiß ich nicht mehr.
        Lief bei mir als ccu.io.Script einwandfrei.
        
        Dieses Script habe ich nun auf iobroker umgeschrieben.
        
        @bahnuhr
        02.01.2017 Dieter Müller
        */
        
        //Variaben
        var idaktuell = 'javascript.0.Status.Photovoltaik.Leistung_aktuell';
        var idTag = 'javascript.0.Status.Photovoltaik.Tagesleistung';
        var idall = 'javascript.0.Status.Photovoltaik.Leistung_gesamt';
        var idP1 = 'javascript.0.Status.Photovoltaik.Leistung_Strang1';
        var idP2 = 'javascript.0.Status.Photovoltaik.Leistung_Strang2';
        
        var NameAnlage = 'xxx';   // Nutzername der Photovoltaik-Anlage
        var PassAnlage = 'x';   // Password der Photovoltaik-Anlage
        var IPAnlage = '192.168.xxx.xx';   // IP der Photovoltaik-Anlage
        
        var logging = false;
        
         function Piko() {
                    var cheerio = require('cheerio');
                    var request = require('request');
        
                    if (logging) log("Piko 5.5 auslesen");
                    //http://SN-Login:WGrZMkb@192.168.243.75
                    request('http://' + NameAnlage + ':' + PassAnlage +'@' + IPAnlage, function (error, response, body) {
                            $ = cheerio.load(body);
                            var d = $("td");
        
                            var pwr = parseFloat(d.eq(14).text().trim());   // Energie aktuell in W
                            var day = parseFloat(d.eq(26).text().trim());   // Tagesenergie in kWh
                            var all = parseFloat(d.eq(17).text().trim());   // Gesamtenergie in kWh
                            var v1 = d.eq(56).text().trim();   // PV Generator Nr. 1 - Spannung in V
                            var i1 = d.eq(65).text().trim();   // PV Generator Nr. 1 - Strom in A
                            var p1 = parseInt(v1 * i1);
                            var v2 = d.eq(82).text().trim();   // PV Generator Nr. 1 - Spannung in V
                            var i2 = d.eq(91).text().trim();   // PV Generator Nr. 1 - Strom in A
                            var p2 = parseInt(v2 * i2);
                            if (isNaN(pwr)) pwr = 0;
                            if (isNaN(p1)) p1 = 0;
                            if (isNaN(p2)) p2 = 0;
        
                            if (logging) log("Leistung aktuell= " + pwr);
                            if (logging) log("Tagesleistung= " + day);
                            if (logging) log("Leistung gesamt= " + all);
        					if (logging) log("Leistung Strang 1= " + p1);
        					if (logging) log("Leistung Strang 2= " + p2);
        
                            setState(idaktuell, pwr);
                            setState(idTag, day);
                            setState(idall, all);
                            setState(idP1, p1);
                            setState(idP2, p2);
                    });
            }
        
        schedule("2,7,12,17,22,27,32,37,42,47,52,57 * * * *", function () {
            log ("Auslöser: Schedule");
        	Piko();
        });
        
        schedule("3 0 * * *", function () {     // Variablen löschen um 00:03 Uhr
            setState('javascript.0.Status.Photovoltaik.Tagesleistung', 0);
        });
        
        
        • Variablen manuell anlegen

        • benutzernamen, password, ip anpassen

        • cheerio unter js eintragen.

        dann klappts.

        mfg

        Dieter

        S Offline
        S Offline
        Spooky99
        schrieb am zuletzt editiert von
        #44

        @bahnuhr
        Hallo Dieter,
        ich versuche mich grad an dem skript, bin aber noch seeeeeeeeehr neu in dem ganzen Thema.
        Was meinst du mit Cheerio unter JS eintragen?
        Und die Variablen kann ich in einen Ordner anlegen den ich z.B. Wechselrichter nenne?

        bahnuhrB 1 Antwort Letzte Antwort
        0
        • S Spooky99

          @bahnuhr
          Hallo Dieter,
          ich versuche mich grad an dem skript, bin aber noch seeeeeeeeehr neu in dem ganzen Thema.
          Was meinst du mit Cheerio unter JS eintragen?
          Und die Variablen kann ich in einen Ordner anlegen den ich z.B. Wechselrichter nenne?

          bahnuhrB Online
          bahnuhrB Online
          bahnuhr
          Forum Testing Most Active
          schrieb am zuletzt editiert von
          #45

          @Spooky99 sagte in Status vom Kostal Wechselrichter auslesen?:

          @bahnuhr
          Hallo Dieter,
          ich versuche mich grad an dem skript, bin aber noch seeeeeeeeehr neu in dem ganzen Thema.
          Was meinst du mit Cheerio unter JS eintragen?
          Und die Variablen kann ich in einen Ordner anlegen den ich z.B. Wechselrichter nenne?

          cheerio klappt nicht mehr.

          Musste das Script wie folgt ändern:

          // Photovoltaik: Piko 5.5 Anlage (alte Firmware)
          // Danke an homoran für den regex
          // @bahnuhr; 03/2019 Dieter Müller
          
          //Variaben
              var idaktuell = 'javascript.0.Status.Photovoltaik.Leistung_aktuell';
              var idTag = 'javascript.0.Status.Photovoltaik.Tagesleistung';
              var idall = 'javascript.0.Status.Photovoltaik.Leistung_gesamt';
              var idP1 = 'javascript.0.Status.Photovoltaik.Leistung_Strang1';
              var idP2 = 'javascript.0.Status.Photovoltaik.Leistung_Strang2';
          
              var NameAnlage = 'SN-Login';        // Nutzername der Photovoltaik-Anlage
              var PassAnlage = 'xxx';         // Password der Photovoltaik-Anlage
              var IPAnlage = '192.168.xxx.xxx';    // IP der Photovoltaik-Anlage
          
              var logging = false;
              var request = require('request');
          
          
           function Piko() {
              log("Piko 5.5 auslesen");
              var results = [];
              request('http://' + NameAnlage + ':' + PassAnlage +'@' + IPAnlage, function (error, response, body) {
                  var d = body.toString();
                  if (logging) log (d);
                  var reg = /#FFFFFF">[^\d]+([^<]+)/g
                  var z = reg.exec(d);
          
                  while(z != null) {
                      if (isNaN(z[1])) {
                          if (logging) log("keine Zahl= "+ z[1]);
                          z[1] = 0;
                      } else {
                          if (logging) log("Zahl= "+ z[1]);
                          parseFloat(z[1]);
                      }
                      results[results.length] = z[1];
                      z = reg.exec(d);
                  }
                  if (logging) log("results= "+ results);
          
              // Werte zuordnen
                  var pwr = results[0];           // Energie aktuell in W
                  var day = results[2];           // Tagesenergie in kWh
                  var all = results[1];           // Gesamtenergie in kWh
                  var v1 = results[3];            // PV Generator Nr. 1 - Spannung in V
                  var i1 = results[5];            // PV Generator Nr. 1 - Strom in A
                  var p1 = parseInt(v1 * i1);
                  var v2 = results[7];            // PV Generator Nr. 2 - Spannung in V
                  var i2 = results[9];            // PV Generator Nr. 2 - Strom in A
                  var p2 = parseInt(v2 * i2);
          
                  if (logging) log("Leistung aktuell= " + pwr + " W");
                  if (logging) log("Tagesleistung= " + day + " kWh");
                  if (logging) log("Leistung gesamt= " + all + " kWh");
          	    if (logging) log("Leistung Strang 1= " + p1 + " W");
              	if (logging) log("Leistung Strang 2= " + p2 + " W");
          
                  setState(idaktuell, parseFloat(pwr));
                  setState(idTag, parseFloat(day));
                  setState(idall, parseFloat(all));
                  setState(idP1, parseFloat(p1));
                  setState(idP2, parseFloat(p2));
              });
          }
          
          
          schedule("2,7,12,17,22,27,32,37,42,47,52,57 * * * *", function () {
              log ("Auslöser: Schedule");
          	Piko();
          });
          
          schedule("3 0 * * *", function () {     // Variablen löschen um 00:03 Uhr   
              setState('javascript.0.Status.Photovoltaik.Tagesleistung', 0);
          });
          
          
          

          Wenn ich helfen konnte, dann Daumen hoch (Pfeil nach oben)!
          Danke.
          gute Forenbeiträge: https://forum.iobroker.net/topic/51555/hinweise-f%C3%BCr-gute-forenbeitr%C3%A4ge
          ScreenToGif :https://www.screentogif.com/downloads.html

          S E 2 Antworten Letzte Antwort
          1
          • bahnuhrB bahnuhr

            @Spooky99 sagte in Status vom Kostal Wechselrichter auslesen?:

            @bahnuhr
            Hallo Dieter,
            ich versuche mich grad an dem skript, bin aber noch seeeeeeeeehr neu in dem ganzen Thema.
            Was meinst du mit Cheerio unter JS eintragen?
            Und die Variablen kann ich in einen Ordner anlegen den ich z.B. Wechselrichter nenne?

            cheerio klappt nicht mehr.

            Musste das Script wie folgt ändern:

            // Photovoltaik: Piko 5.5 Anlage (alte Firmware)
            // Danke an homoran für den regex
            // @bahnuhr; 03/2019 Dieter Müller
            
            //Variaben
                var idaktuell = 'javascript.0.Status.Photovoltaik.Leistung_aktuell';
                var idTag = 'javascript.0.Status.Photovoltaik.Tagesleistung';
                var idall = 'javascript.0.Status.Photovoltaik.Leistung_gesamt';
                var idP1 = 'javascript.0.Status.Photovoltaik.Leistung_Strang1';
                var idP2 = 'javascript.0.Status.Photovoltaik.Leistung_Strang2';
            
                var NameAnlage = 'SN-Login';        // Nutzername der Photovoltaik-Anlage
                var PassAnlage = 'xxx';         // Password der Photovoltaik-Anlage
                var IPAnlage = '192.168.xxx.xxx';    // IP der Photovoltaik-Anlage
            
                var logging = false;
                var request = require('request');
            
            
             function Piko() {
                log("Piko 5.5 auslesen");
                var results = [];
                request('http://' + NameAnlage + ':' + PassAnlage +'@' + IPAnlage, function (error, response, body) {
                    var d = body.toString();
                    if (logging) log (d);
                    var reg = /#FFFFFF">[^\d]+([^<]+)/g
                    var z = reg.exec(d);
            
                    while(z != null) {
                        if (isNaN(z[1])) {
                            if (logging) log("keine Zahl= "+ z[1]);
                            z[1] = 0;
                        } else {
                            if (logging) log("Zahl= "+ z[1]);
                            parseFloat(z[1]);
                        }
                        results[results.length] = z[1];
                        z = reg.exec(d);
                    }
                    if (logging) log("results= "+ results);
            
                // Werte zuordnen
                    var pwr = results[0];           // Energie aktuell in W
                    var day = results[2];           // Tagesenergie in kWh
                    var all = results[1];           // Gesamtenergie in kWh
                    var v1 = results[3];            // PV Generator Nr. 1 - Spannung in V
                    var i1 = results[5];            // PV Generator Nr. 1 - Strom in A
                    var p1 = parseInt(v1 * i1);
                    var v2 = results[7];            // PV Generator Nr. 2 - Spannung in V
                    var i2 = results[9];            // PV Generator Nr. 2 - Strom in A
                    var p2 = parseInt(v2 * i2);
            
                    if (logging) log("Leistung aktuell= " + pwr + " W");
                    if (logging) log("Tagesleistung= " + day + " kWh");
                    if (logging) log("Leistung gesamt= " + all + " kWh");
            	    if (logging) log("Leistung Strang 1= " + p1 + " W");
                	if (logging) log("Leistung Strang 2= " + p2 + " W");
            
                    setState(idaktuell, parseFloat(pwr));
                    setState(idTag, parseFloat(day));
                    setState(idall, parseFloat(all));
                    setState(idP1, parseFloat(p1));
                    setState(idP2, parseFloat(p2));
                });
            }
            
            
            schedule("2,7,12,17,22,27,32,37,42,47,52,57 * * * *", function () {
                log ("Auslöser: Schedule");
            	Piko();
            });
            
            schedule("3 0 * * *", function () {     // Variablen löschen um 00:03 Uhr   
                setState('javascript.0.Status.Photovoltaik.Tagesleistung', 0);
            });
            
            
            
            S Offline
            S Offline
            Spooky99
            schrieb am zuletzt editiert von
            #46

            @bahnuhr ok werde ich gleich mal übernehmen...
            ich tue mich noch schwer mit den Variablen anlegen, hättest du da vielleicht ein BIld wie das bei dir ausschaut? Ich bin echt unbeholfen ;-)

            bahnuhrB 1 Antwort Letzte Antwort
            0
            • S Spooky99

              @bahnuhr ok werde ich gleich mal übernehmen...
              ich tue mich noch schwer mit den Variablen anlegen, hättest du da vielleicht ein BIld wie das bei dir ausschaut? Ich bin echt unbeholfen ;-)

              bahnuhrB Online
              bahnuhrB Online
              bahnuhr
              Forum Testing Most Active
              schrieb am zuletzt editiert von
              #47

              @Spooky99 sagte in Status vom Kostal Wechselrichter auslesen?:

              Variablen anlegen,

              mit folgendem Script:

              // Photovoltaik -------------------------------------------------------------------------------------------------------------
              createState('javascript.0.Status.Photovoltaik.Leistung_aktuell', 0, {type: 'number',name: 'Leistung aktuell',min: 0,role: 'per Script'});
              createState('javascript.0.Status.Photovoltaik.Tagesleistung', 0, {type: 'number',name: 'Tagesleistung',min: 0,role: 'per Script'});
              createState('javascript.0.Status.Photovoltaik.Leistung_gesamt', 0, {type: 'number',name: 'Leistung gesamt',min: 0,role: 'per Script'});
              createState('javascript.0.Status.Photovoltaik.Leistung_Strang1', 0, {type: 'number',name: 'Leistung Strang 1',min: 0,role: 'per Script'});
              createState('javascript.0.Status.Photovoltaik.Leistung_Strang2', 0, {type: 'number',name: 'Leistung Strang 2',min: 0,role: 'value'});
              
              

              Wenn ich helfen konnte, dann Daumen hoch (Pfeil nach oben)!
              Danke.
              gute Forenbeiträge: https://forum.iobroker.net/topic/51555/hinweise-f%C3%BCr-gute-forenbeitr%C3%A4ge
              ScreenToGif :https://www.screentogif.com/downloads.html

              1 Antwort Letzte Antwort
              0
              • bahnuhrB Online
                bahnuhrB Online
                bahnuhr
                Forum Testing Most Active
                schrieb am zuletzt editiert von
                #48

                und bei den Objekten siehts dann so aus:

                75273d82-cc5d-41a4-a6e4-5a2a227c4e30-grafik.png


                Wenn ich helfen konnte, dann Daumen hoch (Pfeil nach oben)!
                Danke.
                gute Forenbeiträge: https://forum.iobroker.net/topic/51555/hinweise-f%C3%BCr-gute-forenbeitr%C3%A4ge
                ScreenToGif :https://www.screentogif.com/downloads.html

                1 Antwort Letzte Antwort
                0
                • bahnuhrB Online
                  bahnuhrB Online
                  bahnuhr
                  Forum Testing Most Active
                  schrieb am zuletzt editiert von
                  #49

                  und meine Darstellung in vis:
                  531203d8-ecc5-4537-a0c4-8684e7de2118-grafik.png


                  Wenn ich helfen konnte, dann Daumen hoch (Pfeil nach oben)!
                  Danke.
                  gute Forenbeiträge: https://forum.iobroker.net/topic/51555/hinweise-f%C3%BCr-gute-forenbeitr%C3%A4ge
                  ScreenToGif :https://www.screentogif.com/downloads.html

                  1 Antwort Letzte Antwort
                  0
                  • bahnuhrB Online
                    bahnuhrB Online
                    bahnuhr
                    Forum Testing Most Active
                    schrieb am zuletzt editiert von
                    #50

                    und die Darstellung in flot:
                    7e63ed26-5ab9-4b81-a454-f748ee144a1a-grafik.png

                    Aber das kannst du ja machen wie du möchtest.


                    Wenn ich helfen konnte, dann Daumen hoch (Pfeil nach oben)!
                    Danke.
                    gute Forenbeiträge: https://forum.iobroker.net/topic/51555/hinweise-f%C3%BCr-gute-forenbeitr%C3%A4ge
                    ScreenToGif :https://www.screentogif.com/downloads.html

                    1 Antwort Letzte Antwort
                    0
                    • S Offline
                      S Offline
                      Spooky99
                      schrieb am zuletzt editiert von
                      #51

                      ARGH WIE GEIL IST DAS DENN??????
                      Vielen vielen Dank!!! WIe ich das aufbereite muss ich mal sehen aber das ist ja der Hammer!
                      Da muss ich wohl doch noch nen Volkshochschulkurs belegen;-)

                      bahnuhrB 1 Antwort Letzte Antwort
                      0
                      • S Spooky99

                        ARGH WIE GEIL IST DAS DENN??????
                        Vielen vielen Dank!!! WIe ich das aufbereite muss ich mal sehen aber das ist ja der Hammer!
                        Da muss ich wohl doch noch nen Volkshochschulkurs belegen;-)

                        bahnuhrB Online
                        bahnuhrB Online
                        bahnuhr
                        Forum Testing Most Active
                        schrieb am zuletzt editiert von
                        #52

                        @Spooky99 sagte in Status vom Kostal Wechselrichter auslesen?:

                        ARGH WIE GEIL IST DAS DENN??????
                        Vielen vielen Dank!!! WIe ich das aufbereite muss ich mal sehen aber das ist ja der Hammer!
                        Da muss ich wohl doch noch nen Volkshochschulkurs belegen;-)

                        wenns gefällt dann positiv vooten.


                        Wenn ich helfen konnte, dann Daumen hoch (Pfeil nach oben)!
                        Danke.
                        gute Forenbeiträge: https://forum.iobroker.net/topic/51555/hinweise-f%C3%BCr-gute-forenbeitr%C3%A4ge
                        ScreenToGif :https://www.screentogif.com/downloads.html

                        1 Antwort Letzte Antwort
                        1
                        • S Offline
                          S Offline
                          Spooky99
                          schrieb am zuletzt editiert von
                          #53

                          und irgendwann hab ich auch raus wie ich in das runde Anzeigending 1000 2000 3000 usw. stehen habe irgendwie unterteilt der das noch falsch...

                          1 Antwort Letzte Antwort
                          0
                          • DiginixD Diginix

                            Kann mir hier jemand die modbus Adapter Einstellungen für ein Plenticore Plus 5.5 mit Firmware 1.30 erklären oder als Screenshot zeigen.
                            Habe die IP, Port und GeräteID eingetragen, sonst noch nichts weiter. Die Instanz bleibt aber gelb. Im Log steht "Serial is not available", habe aber TCP gewählt.

                            J Offline
                            J Offline
                            joefarm
                            schrieb am zuletzt editiert von
                            #54

                            @Diginix said in Status vom Kostal Wechselrichter auslesen?:

                            Kann mir hier jemand die modbus Adapter Einstellungen für ein Plenticore Plus 5.5 mit Firmware 1.30 erklären oder als Screenshot zeigen.
                            Habe die IP, Port und GeräteID eingetragen, sonst noch nichts weiter. Die Instanz bleibt aber gelb. Im Log steht "Serial is not available", habe aber TCP gewählt.

                            Sorry, hab die Frage gerade erst gelesen. Mein Plenticore Plus 10 ist jetzt seit gut einem Monat in Betrieb und ich hab einiges ausprobiert, um ihn auszulesen per modbus. Mit folgenden Einstellungen war ich erfolgreich:

                            address	name	description	unit	type	len	factor	offset	role	room	poll	wp
                            2	MODBUSEnable	MODBUS Enable		uint16be	1	1	0	value		false	false	
                            4	MODBUSUnit-ID	MODBUS Unit-ID		uint16be	1	1	0	value		false	false	
                            6	Inverterarticlenumber	Inverter article number		string	8	1	0	value		false	false	
                            14	Inverterserialnumber	Inverter serial number		string	8	1	0	value		false	false	
                            30	Numberofbidirectionalconverter	Number of bidirectional converter		uint16be	1	1	0	value		false	false	
                            32	NumberofACphases	Number of AC phases		uint16be	1	1	0	value		false	false	
                            34	NumberofPVstrings	Number of PV strings		uint16be	1	1	0	value		false	false	
                            36	Hardware-Version-	Hardware-Version -		uint16be	1	1	0	value		false	false	
                            38	Software-VersionMaincontroller(MC)	Software-Version Maincontroller (MC)		string	8	1	0	value		false	false	
                            46	Software-VersionIO-Controller(IOC)	Software-Version IO-Controller (IOC)		string	8	1	0	value		false	false	
                            54	Power-ID	Power-ID		uint16be	1	1	0	value		false	false	
                            56	Inverterstate2	Inverter state2		uint16be	1	1	0	value		true	false	
                            100	TotalDCpower	Total DC power	W	floatsw	2	1	0	value		true	false	
                            104	Stateofenergymanager3	State of energy manager3		floatsw	2	1	0	value		true	false	
                            106	Homeownconsumptionfrombattery	Home own consumption from battery	W	floatsw	2	1	0	value		true	false	
                            108	Homeownconsumptionfromgrid	Home own consumption from grid	W	floatsw	2	1	0	value		true	false	
                            110	TotalhomeconsumptionBattery	Total home consumption Battery	kWh	floatsw	2	0.001	0	value		true	false	
                            112	TotalhomeconsumptionGrid	Total home consumption Grid	kWh	floatsw	2	0.001	0	value		true	false	
                            114	TotalhomeconsumptionPV	Total home consumption PV	kWh	floatsw	2	0.001	0	value		true	false	
                            116	HomeownconsumptionfromPV	Home own consumption from PV	W	floatsw	2	1	0	value		true	false	
                            118	Totalhomeconsumption	Total home consumption	kWh	floatsw	2	0.001	0	value		true	false	
                            120	Isolationresistance	Isolation resistance	Ohm	floatsw	2	1	0	value		false	false	
                            122	PowerlimitfromEVU	Power limit from EVU	%	floatsw	2	1	0	value		true	false	
                            124	Totalhomeconsumptionrate	Total home consumption rate	%	floatsw	2	1	0	value		true	false	
                            144	Worktime	Worktime	s	floatsw	2	1	0	value		true	false	
                            150	Actualcosf	Actual cos f		floatsw	2	1	0	value		true	false	
                            152	Gridfrequency	Grid frequency	Hz	floatsw	2	1	0	value		true	false	
                            154	CurrentPhase1	Current Phase 1	A	floatsw	2	1	0	value		false	false	
                            156	ActivepowerPhase1	Active power Phase 1	W	floatsw	2	1	0	value		false	false	
                            158	VoltagePhase1	Voltage Phase 1	V	floatsw	2	1	0	value		false	false	
                            160	CurrentPhase2	Current Phase 2	A	floatsw	2	1	0	value		false	false	
                            162	ActivepowerPhase2	Active power Phase 2	W	floatsw	2	1	0	value		false	false	
                            164	VoltagePhase2	Voltage Phase 2	V	floatsw	2	1	0	value		false	false	
                            166	CurrentPhase3	Current Phase 3	A	floatsw	2	1	0	value		false	false	
                            168	ActivepowerPhase3	Active power Phase 3	W	floatsw	2	1	0	value		false	false	
                            170	VoltagePhase3	Voltage Phase 3	V	floatsw	2	1	0	value		false	false	
                            172	TotalACactivepower	Total AC active power	W	floatsw	2	1	0	value		true	false	
                            174	TotalACreactivepower	Total AC reactive power	Var	floatsw	2	1	0	value		false	false	
                            178	TotalACapparentpower	Total AC apparent power	VA	floatsw	2	1	0	value		false	false	
                            190	Batterychargecurrent	Battery charge current	A	floatsw	2	1	0	value		true	false	
                            194	Numberofbatterycycles	Number of battery cycles		floatsw	2	1	0	value		true	false	
                            200	Actualbatterycharge (-)/discharge(+)current	Actual battery charge (-)/ discharge(+)  current	A	floatsw	2	1	0	value		true	false	
                            202	PSSBfusestate6	PSSB fuse state6		floatsw	2	1	0	value		true	false	
                            208	Batteryreadyflag	Battery ready flag		floatsw	2	1	0	value		true	false	
                            210	Act.stateofcharge	Act. state of charge	%	floatsw	2	1	0	value		true	false	
                            212	Batterystate5	Battery state5		floatsw	2	1	0	value		false	false	
                            214	Batterytemperature	Battery temperature	°C	floatsw	2	1	0	value		true	false	
                            216	Batteryvoltage	Battery voltage	V	floatsw	2	1	0	value		true	false	
                            218	Cosf(powermeter)	Cos f (powermeter)		floatsw	2	1	0	value		true	false	
                            220	Frequency(powermeter)	Frequency (powermeter)	Hz	floatsw	2	1	0	value		true	false	
                            320	Totale Erzeugung	Totale Erzeugung	kWh	floatsw	2	0.001	0	value		true	false	
                            322	Tagesproduktion	Tagesproduktion	kWh	floatsw	2	0.001	0	value		true	false	
                            252	Totalactivepower(powermeter)	Total active power (powermeter)	W	floatsw	2	1	0	value		true	false	
                            324	Yearlyyield	Yearly yield	kWh	floatsw	2	0.001	0	value		true	false	
                            326	Monthlyyield	Monthly yield	kWh	floatsw	2	0.001	0	value		true	false	
                            512	Batterygrosscapacity5	Battery gross capacity5	Ah	uint32be	2	1	0	value		true	false	
                            514	BatteryactualSOC	Battery actual SOC	%	uint16be	1	1	0	value		true	false	
                            577	GenerationEnergy	Generation Energy	kWh	uint32be	2	0.001	0	value		true	false	
                            582	Actualbatterycharge/dischargepower	Actual battery charge/discharge power	W	int16be	1	1	0	value		true	false	
                            224	Activepowerphase1(powermeter)	Active power phase 1 (powermeter)	W	floatsw	2	1	0	value		true	false	
                            234	Activepowerphase2(powermeter)	Active power phase 2 (powermeter)	W	floatsw	2	1	0	value		true	false	
                            244	Activepowerphase3(powermeter)	Active power phase 3 (powermeter)	W	floatsw	2	1	0	value		true	false	
                            575	InverterGenerationPower(actual)	Inverter Generation Power (actual)	W	int16be	1	1	0	value		true	false	
                            260	PowerDC1	Power DC1	W	floatsw	2	1	0	value		true	false	
                            270	PowerDC2	Power DC2	W	floatsw	2	1	0	value		true	false	
                            280	PowerDC3	Power DC3	W	floatsw	2	1	0	value		true	false	
                            
                            

                            Nicht alle Einträge liefern brauchbare Werte, aber die meisten doch. Einfach ausprobieren.
                            Ich hab zusätzlich noch den Smart Energy Manager am laufen, den ich per 2. modbus Eintrag auslese:

                            address	name	description	unit	type	len	factor	offset	role	room	poll	wp
                            8218	Product Name	Product Name		string	16	1	0	value		true	false	
                            40071	M_AC_Current	AC Current (sum of active phases)	A	int16be	1	0.01	0	value		false	false	
                            40072	M_AC_Cur- rent_A	Phase A AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                            40073	M_AC_Cur- rent_B	Phase B AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                            40074	M_AC_Cur- rent_C	Phase C AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                            40076	M_AC_Vol- tage_LN	Line to Neutral AC Voltage (average of active phases)	V	int16be	1	0.01	0	value		false	false	
                            40077	M_AC_Vol- tage_AN	Phase A to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                            40078	M_AC_Vol- tage_BN	Phase B to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                            40079	M_AC_Vol- tage_CN	Phase C to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                            40080	M_AC_Vol- tage_LL	Line to Line AC Voltage (average of active phases)	V	uint16be	1	1	0	value		false	false	
                            40081	M_AC_Vol- tage_AB	Phase A to Phase B AC Voltage	V	uint16be	1	1	0	value		false	false	
                            40082	M_AC_Vol- tage_BC	Phase B to Phase C AC Voltage	V	uint16be	1	1	0	value		false	false	
                            40083	M_AC_Vol- tage_CA	Phase C to Phase A AC Voltage	V	uint16be	1	1	0	value		false	false	
                            40085	M_AC_Freq	AC Frequency	Hz	uint16be	1	0.01	0	value		true	false	
                            40087	M_AC_Power	Total Real Power (sum of active pha- ses)	kW	int16be	1	0.01	0	value		true	false	
                            40088	M_AC_Pow- er_A	Phase A AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                            40089	M_AC_Pow- er_B	Phase B AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                            40090	M_AC_Pow- er_C	Phase C AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                            40092	M_AC_VA	Total AC Apparent Power (sum of ac- tive phases)	VA	int16be	1	1	0	value		false	false	
                            40093	M_AC_VA_A	Phase A AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                            40094	M_AC_VA_B	Phase B AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                            40095	M_AC_VA_C	Phase C AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                            40097	M_AC_VAR	Total AC Reactive Power (sum of ac- tive phases)	var	uint16be	1	1	0	value		false	false	
                            40098	M_AC_VAR_A	Phase A AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                            40099	M_AC_VAR_B	Phase B AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                            40100	M_AC_VAR_C	Phase C AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                            40102	M_AC_PF	Average Power Factor (average of active phases)	%	uint16be	1	1	0	value		false	false	
                            40103	M_AC_PF_A	Phase A Power Factor	%	uint16be	1	1	0	value		false	false	
                            40104	M_AC_PF_B	Phase B Power Factor	%	uint16be	1	1	0	value		false	false	
                            40105	M_AC_PF_C	Phase C Power Factor	%	uint16be	1	1	0	value		false	false	
                            40107	M_Exported	Total Exported Re- al Energy	kWh	int32be	2	-0.001	0	value		true	false	
                            40109	M_Expor- ted_A	Phase A Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                            40111	M_Expor- ted_B	Phase B Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                            40113	M_Expor- ted_C	Phase C Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                            40115	M_Imported	Total Imported Re- al Energy	kWh	int32be	2	0.001	0	value		true	false	
                            40117	M_Imported_A	Phase A Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                            40119	M_Impor- ted_B	Phase B Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                            40121	M_Impor- ted_C	Phase C Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                            40124	M_Expor- ted_VA	Total Exported Ap- parent Energy	VAh	int32be	2	1	0	value		false	false	
                            40126	M_Expor- ted_VA_A	Phase A Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                            40128	M_Expor- ted_VA_B	Phase B Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                            40130	M_Expor- ted_VA_C	Phase C Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                            40132	M_Impor- ted_VA	Total Imported Ap- parent Energy	VAh	uint32be	2	1	0	value		false	false	
                            40134	M_Impor- ted_VA_A	Phase A Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                            40136	M_Impor- ted_VA_B	Phase B Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                            40138	M_Impor- ted_VA_C	Phase C Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                            40145	M_Import_ VARh_Q1B	Phase B – Quadrant 1: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40147	M_Import_ VARh_Q1C	Phase C – Quadrant 1: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40149	M_Import_ VARh_Q2	Quadrant 2: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40151	M_Import_ VARh_Q2A	Phase A – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40153	M_Import_ VARh_Q2B	Phase B – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40155	M_Import_ VARh_Q2C	Phase C – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40157	M_Export_ VARh_Q3	Quadrant 3: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40159	M_Export_ VARh_Q3A	Phase A – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40161	M_Export_ VARh_Q3B	Phase B – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40163	M_Export_ VARh_Q3C	Phase C – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40165	M_Export_ VARh_Q4	Quadrant 4: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40167	M_Export_ VARh_Q4A	Phase A – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40169	M_Export_ VARh_Q4B	Phase B – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            40171	M_Export_ VARh_Q4C	Phase C – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                            0	Active Power+	Active Power+	W	uint32be	2	1	0	value		false	false	
                            2	Active Power-	Active Power-	W	uint32be	2	1	0	value		false	false	
                            
                            

                            Beides jeweils in die Holding-Register importieren. Bin gerne aufgeschlossen, wer noch weitere Werte gefunden hat.

                            Das Ganze sieht dann visualisiert so aus:
                            6af9a378-fd30-4b27-a801-ff71183cf4e8-image.png

                            DiginixD Marco LaserM E 3 Antworten Letzte Antwort
                            0
                            • J joefarm

                              @Diginix said in Status vom Kostal Wechselrichter auslesen?:

                              Kann mir hier jemand die modbus Adapter Einstellungen für ein Plenticore Plus 5.5 mit Firmware 1.30 erklären oder als Screenshot zeigen.
                              Habe die IP, Port und GeräteID eingetragen, sonst noch nichts weiter. Die Instanz bleibt aber gelb. Im Log steht "Serial is not available", habe aber TCP gewählt.

                              Sorry, hab die Frage gerade erst gelesen. Mein Plenticore Plus 10 ist jetzt seit gut einem Monat in Betrieb und ich hab einiges ausprobiert, um ihn auszulesen per modbus. Mit folgenden Einstellungen war ich erfolgreich:

                              address	name	description	unit	type	len	factor	offset	role	room	poll	wp
                              2	MODBUSEnable	MODBUS Enable		uint16be	1	1	0	value		false	false	
                              4	MODBUSUnit-ID	MODBUS Unit-ID		uint16be	1	1	0	value		false	false	
                              6	Inverterarticlenumber	Inverter article number		string	8	1	0	value		false	false	
                              14	Inverterserialnumber	Inverter serial number		string	8	1	0	value		false	false	
                              30	Numberofbidirectionalconverter	Number of bidirectional converter		uint16be	1	1	0	value		false	false	
                              32	NumberofACphases	Number of AC phases		uint16be	1	1	0	value		false	false	
                              34	NumberofPVstrings	Number of PV strings		uint16be	1	1	0	value		false	false	
                              36	Hardware-Version-	Hardware-Version -		uint16be	1	1	0	value		false	false	
                              38	Software-VersionMaincontroller(MC)	Software-Version Maincontroller (MC)		string	8	1	0	value		false	false	
                              46	Software-VersionIO-Controller(IOC)	Software-Version IO-Controller (IOC)		string	8	1	0	value		false	false	
                              54	Power-ID	Power-ID		uint16be	1	1	0	value		false	false	
                              56	Inverterstate2	Inverter state2		uint16be	1	1	0	value		true	false	
                              100	TotalDCpower	Total DC power	W	floatsw	2	1	0	value		true	false	
                              104	Stateofenergymanager3	State of energy manager3		floatsw	2	1	0	value		true	false	
                              106	Homeownconsumptionfrombattery	Home own consumption from battery	W	floatsw	2	1	0	value		true	false	
                              108	Homeownconsumptionfromgrid	Home own consumption from grid	W	floatsw	2	1	0	value		true	false	
                              110	TotalhomeconsumptionBattery	Total home consumption Battery	kWh	floatsw	2	0.001	0	value		true	false	
                              112	TotalhomeconsumptionGrid	Total home consumption Grid	kWh	floatsw	2	0.001	0	value		true	false	
                              114	TotalhomeconsumptionPV	Total home consumption PV	kWh	floatsw	2	0.001	0	value		true	false	
                              116	HomeownconsumptionfromPV	Home own consumption from PV	W	floatsw	2	1	0	value		true	false	
                              118	Totalhomeconsumption	Total home consumption	kWh	floatsw	2	0.001	0	value		true	false	
                              120	Isolationresistance	Isolation resistance	Ohm	floatsw	2	1	0	value		false	false	
                              122	PowerlimitfromEVU	Power limit from EVU	%	floatsw	2	1	0	value		true	false	
                              124	Totalhomeconsumptionrate	Total home consumption rate	%	floatsw	2	1	0	value		true	false	
                              144	Worktime	Worktime	s	floatsw	2	1	0	value		true	false	
                              150	Actualcosf	Actual cos f		floatsw	2	1	0	value		true	false	
                              152	Gridfrequency	Grid frequency	Hz	floatsw	2	1	0	value		true	false	
                              154	CurrentPhase1	Current Phase 1	A	floatsw	2	1	0	value		false	false	
                              156	ActivepowerPhase1	Active power Phase 1	W	floatsw	2	1	0	value		false	false	
                              158	VoltagePhase1	Voltage Phase 1	V	floatsw	2	1	0	value		false	false	
                              160	CurrentPhase2	Current Phase 2	A	floatsw	2	1	0	value		false	false	
                              162	ActivepowerPhase2	Active power Phase 2	W	floatsw	2	1	0	value		false	false	
                              164	VoltagePhase2	Voltage Phase 2	V	floatsw	2	1	0	value		false	false	
                              166	CurrentPhase3	Current Phase 3	A	floatsw	2	1	0	value		false	false	
                              168	ActivepowerPhase3	Active power Phase 3	W	floatsw	2	1	0	value		false	false	
                              170	VoltagePhase3	Voltage Phase 3	V	floatsw	2	1	0	value		false	false	
                              172	TotalACactivepower	Total AC active power	W	floatsw	2	1	0	value		true	false	
                              174	TotalACreactivepower	Total AC reactive power	Var	floatsw	2	1	0	value		false	false	
                              178	TotalACapparentpower	Total AC apparent power	VA	floatsw	2	1	0	value		false	false	
                              190	Batterychargecurrent	Battery charge current	A	floatsw	2	1	0	value		true	false	
                              194	Numberofbatterycycles	Number of battery cycles		floatsw	2	1	0	value		true	false	
                              200	Actualbatterycharge (-)/discharge(+)current	Actual battery charge (-)/ discharge(+)  current	A	floatsw	2	1	0	value		true	false	
                              202	PSSBfusestate6	PSSB fuse state6		floatsw	2	1	0	value		true	false	
                              208	Batteryreadyflag	Battery ready flag		floatsw	2	1	0	value		true	false	
                              210	Act.stateofcharge	Act. state of charge	%	floatsw	2	1	0	value		true	false	
                              212	Batterystate5	Battery state5		floatsw	2	1	0	value		false	false	
                              214	Batterytemperature	Battery temperature	°C	floatsw	2	1	0	value		true	false	
                              216	Batteryvoltage	Battery voltage	V	floatsw	2	1	0	value		true	false	
                              218	Cosf(powermeter)	Cos f (powermeter)		floatsw	2	1	0	value		true	false	
                              220	Frequency(powermeter)	Frequency (powermeter)	Hz	floatsw	2	1	0	value		true	false	
                              320	Totale Erzeugung	Totale Erzeugung	kWh	floatsw	2	0.001	0	value		true	false	
                              322	Tagesproduktion	Tagesproduktion	kWh	floatsw	2	0.001	0	value		true	false	
                              252	Totalactivepower(powermeter)	Total active power (powermeter)	W	floatsw	2	1	0	value		true	false	
                              324	Yearlyyield	Yearly yield	kWh	floatsw	2	0.001	0	value		true	false	
                              326	Monthlyyield	Monthly yield	kWh	floatsw	2	0.001	0	value		true	false	
                              512	Batterygrosscapacity5	Battery gross capacity5	Ah	uint32be	2	1	0	value		true	false	
                              514	BatteryactualSOC	Battery actual SOC	%	uint16be	1	1	0	value		true	false	
                              577	GenerationEnergy	Generation Energy	kWh	uint32be	2	0.001	0	value		true	false	
                              582	Actualbatterycharge/dischargepower	Actual battery charge/discharge power	W	int16be	1	1	0	value		true	false	
                              224	Activepowerphase1(powermeter)	Active power phase 1 (powermeter)	W	floatsw	2	1	0	value		true	false	
                              234	Activepowerphase2(powermeter)	Active power phase 2 (powermeter)	W	floatsw	2	1	0	value		true	false	
                              244	Activepowerphase3(powermeter)	Active power phase 3 (powermeter)	W	floatsw	2	1	0	value		true	false	
                              575	InverterGenerationPower(actual)	Inverter Generation Power (actual)	W	int16be	1	1	0	value		true	false	
                              260	PowerDC1	Power DC1	W	floatsw	2	1	0	value		true	false	
                              270	PowerDC2	Power DC2	W	floatsw	2	1	0	value		true	false	
                              280	PowerDC3	Power DC3	W	floatsw	2	1	0	value		true	false	
                              
                              

                              Nicht alle Einträge liefern brauchbare Werte, aber die meisten doch. Einfach ausprobieren.
                              Ich hab zusätzlich noch den Smart Energy Manager am laufen, den ich per 2. modbus Eintrag auslese:

                              address	name	description	unit	type	len	factor	offset	role	room	poll	wp
                              8218	Product Name	Product Name		string	16	1	0	value		true	false	
                              40071	M_AC_Current	AC Current (sum of active phases)	A	int16be	1	0.01	0	value		false	false	
                              40072	M_AC_Cur- rent_A	Phase A AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                              40073	M_AC_Cur- rent_B	Phase B AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                              40074	M_AC_Cur- rent_C	Phase C AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                              40076	M_AC_Vol- tage_LN	Line to Neutral AC Voltage (average of active phases)	V	int16be	1	0.01	0	value		false	false	
                              40077	M_AC_Vol- tage_AN	Phase A to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                              40078	M_AC_Vol- tage_BN	Phase B to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                              40079	M_AC_Vol- tage_CN	Phase C to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                              40080	M_AC_Vol- tage_LL	Line to Line AC Voltage (average of active phases)	V	uint16be	1	1	0	value		false	false	
                              40081	M_AC_Vol- tage_AB	Phase A to Phase B AC Voltage	V	uint16be	1	1	0	value		false	false	
                              40082	M_AC_Vol- tage_BC	Phase B to Phase C AC Voltage	V	uint16be	1	1	0	value		false	false	
                              40083	M_AC_Vol- tage_CA	Phase C to Phase A AC Voltage	V	uint16be	1	1	0	value		false	false	
                              40085	M_AC_Freq	AC Frequency	Hz	uint16be	1	0.01	0	value		true	false	
                              40087	M_AC_Power	Total Real Power (sum of active pha- ses)	kW	int16be	1	0.01	0	value		true	false	
                              40088	M_AC_Pow- er_A	Phase A AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                              40089	M_AC_Pow- er_B	Phase B AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                              40090	M_AC_Pow- er_C	Phase C AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                              40092	M_AC_VA	Total AC Apparent Power (sum of ac- tive phases)	VA	int16be	1	1	0	value		false	false	
                              40093	M_AC_VA_A	Phase A AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                              40094	M_AC_VA_B	Phase B AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                              40095	M_AC_VA_C	Phase C AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                              40097	M_AC_VAR	Total AC Reactive Power (sum of ac- tive phases)	var	uint16be	1	1	0	value		false	false	
                              40098	M_AC_VAR_A	Phase A AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                              40099	M_AC_VAR_B	Phase B AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                              40100	M_AC_VAR_C	Phase C AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                              40102	M_AC_PF	Average Power Factor (average of active phases)	%	uint16be	1	1	0	value		false	false	
                              40103	M_AC_PF_A	Phase A Power Factor	%	uint16be	1	1	0	value		false	false	
                              40104	M_AC_PF_B	Phase B Power Factor	%	uint16be	1	1	0	value		false	false	
                              40105	M_AC_PF_C	Phase C Power Factor	%	uint16be	1	1	0	value		false	false	
                              40107	M_Exported	Total Exported Re- al Energy	kWh	int32be	2	-0.001	0	value		true	false	
                              40109	M_Expor- ted_A	Phase A Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                              40111	M_Expor- ted_B	Phase B Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                              40113	M_Expor- ted_C	Phase C Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                              40115	M_Imported	Total Imported Re- al Energy	kWh	int32be	2	0.001	0	value		true	false	
                              40117	M_Imported_A	Phase A Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                              40119	M_Impor- ted_B	Phase B Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                              40121	M_Impor- ted_C	Phase C Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                              40124	M_Expor- ted_VA	Total Exported Ap- parent Energy	VAh	int32be	2	1	0	value		false	false	
                              40126	M_Expor- ted_VA_A	Phase A Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                              40128	M_Expor- ted_VA_B	Phase B Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                              40130	M_Expor- ted_VA_C	Phase C Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                              40132	M_Impor- ted_VA	Total Imported Ap- parent Energy	VAh	uint32be	2	1	0	value		false	false	
                              40134	M_Impor- ted_VA_A	Phase A Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                              40136	M_Impor- ted_VA_B	Phase B Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                              40138	M_Impor- ted_VA_C	Phase C Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                              40145	M_Import_ VARh_Q1B	Phase B – Quadrant 1: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40147	M_Import_ VARh_Q1C	Phase C – Quadrant 1: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40149	M_Import_ VARh_Q2	Quadrant 2: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40151	M_Import_ VARh_Q2A	Phase A – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40153	M_Import_ VARh_Q2B	Phase B – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40155	M_Import_ VARh_Q2C	Phase C – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40157	M_Export_ VARh_Q3	Quadrant 3: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40159	M_Export_ VARh_Q3A	Phase A – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40161	M_Export_ VARh_Q3B	Phase B – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40163	M_Export_ VARh_Q3C	Phase C – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40165	M_Export_ VARh_Q4	Quadrant 4: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40167	M_Export_ VARh_Q4A	Phase A – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40169	M_Export_ VARh_Q4B	Phase B – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              40171	M_Export_ VARh_Q4C	Phase C – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                              0	Active Power+	Active Power+	W	uint32be	2	1	0	value		false	false	
                              2	Active Power-	Active Power-	W	uint32be	2	1	0	value		false	false	
                              
                              

                              Beides jeweils in die Holding-Register importieren. Bin gerne aufgeschlossen, wer noch weitere Werte gefunden hat.

                              Das Ganze sieht dann visualisiert so aus:
                              6af9a378-fd30-4b27-a801-ff71183cf4e8-image.png

                              DiginixD Offline
                              DiginixD Offline
                              Diginix
                              schrieb am zuletzt editiert von
                              #55

                              @joefarm
                              Danke, hatte es damals selbst gelöst bekommen.
                              Wichtig war die Adressen unter Holding Registers und mit Float (Big Endian Word Swap) anzulegen.

                              ..:: So long! Tom ::..

                              NUC7i3 (Ubuntu Proxmox VM) | Echo Dots 2+3. Gen | Xiaomi Sensoren | Mi Robot 1S | Yeelight | Sonoff | Shelly | H801 RGB | Gosund SP1 | NodeMCU+ESP32 | Kostal Plenticore PV+BYD | openWB

                              J 1 Antwort Letzte Antwort
                              0
                              • DiginixD Diginix

                                @joefarm
                                Danke, hatte es damals selbst gelöst bekommen.
                                Wichtig war die Adressen unter Holding Registers und mit Float (Big Endian Word Swap) anzulegen.

                                J Offline
                                J Offline
                                joefarm
                                schrieb am zuletzt editiert von
                                #56

                                @Diginix
                                Alles klar, freut mich wenn es geklappt hat.

                                1 Antwort Letzte Antwort
                                0
                                • bahnuhrB bahnuhr

                                  @Spooky99 sagte in Status vom Kostal Wechselrichter auslesen?:

                                  @bahnuhr
                                  Hallo Dieter,
                                  ich versuche mich grad an dem skript, bin aber noch seeeeeeeeehr neu in dem ganzen Thema.
                                  Was meinst du mit Cheerio unter JS eintragen?
                                  Und die Variablen kann ich in einen Ordner anlegen den ich z.B. Wechselrichter nenne?

                                  cheerio klappt nicht mehr.

                                  Musste das Script wie folgt ändern:

                                  // Photovoltaik: Piko 5.5 Anlage (alte Firmware)
                                  // Danke an homoran für den regex
                                  // @bahnuhr; 03/2019 Dieter Müller
                                  
                                  //Variaben
                                      var idaktuell = 'javascript.0.Status.Photovoltaik.Leistung_aktuell';
                                      var idTag = 'javascript.0.Status.Photovoltaik.Tagesleistung';
                                      var idall = 'javascript.0.Status.Photovoltaik.Leistung_gesamt';
                                      var idP1 = 'javascript.0.Status.Photovoltaik.Leistung_Strang1';
                                      var idP2 = 'javascript.0.Status.Photovoltaik.Leistung_Strang2';
                                  
                                      var NameAnlage = 'SN-Login';        // Nutzername der Photovoltaik-Anlage
                                      var PassAnlage = 'xxx';         // Password der Photovoltaik-Anlage
                                      var IPAnlage = '192.168.xxx.xxx';    // IP der Photovoltaik-Anlage
                                  
                                      var logging = false;
                                      var request = require('request');
                                  
                                  
                                   function Piko() {
                                      log("Piko 5.5 auslesen");
                                      var results = [];
                                      request('http://' + NameAnlage + ':' + PassAnlage +'@' + IPAnlage, function (error, response, body) {
                                          var d = body.toString();
                                          if (logging) log (d);
                                          var reg = /#FFFFFF">[^\d]+([^<]+)/g
                                          var z = reg.exec(d);
                                  
                                          while(z != null) {
                                              if (isNaN(z[1])) {
                                                  if (logging) log("keine Zahl= "+ z[1]);
                                                  z[1] = 0;
                                              } else {
                                                  if (logging) log("Zahl= "+ z[1]);
                                                  parseFloat(z[1]);
                                              }
                                              results[results.length] = z[1];
                                              z = reg.exec(d);
                                          }
                                          if (logging) log("results= "+ results);
                                  
                                      // Werte zuordnen
                                          var pwr = results[0];           // Energie aktuell in W
                                          var day = results[2];           // Tagesenergie in kWh
                                          var all = results[1];           // Gesamtenergie in kWh
                                          var v1 = results[3];            // PV Generator Nr. 1 - Spannung in V
                                          var i1 = results[5];            // PV Generator Nr. 1 - Strom in A
                                          var p1 = parseInt(v1 * i1);
                                          var v2 = results[7];            // PV Generator Nr. 2 - Spannung in V
                                          var i2 = results[9];            // PV Generator Nr. 2 - Strom in A
                                          var p2 = parseInt(v2 * i2);
                                  
                                          if (logging) log("Leistung aktuell= " + pwr + " W");
                                          if (logging) log("Tagesleistung= " + day + " kWh");
                                          if (logging) log("Leistung gesamt= " + all + " kWh");
                                  	    if (logging) log("Leistung Strang 1= " + p1 + " W");
                                      	if (logging) log("Leistung Strang 2= " + p2 + " W");
                                  
                                          setState(idaktuell, parseFloat(pwr));
                                          setState(idTag, parseFloat(day));
                                          setState(idall, parseFloat(all));
                                          setState(idP1, parseFloat(p1));
                                          setState(idP2, parseFloat(p2));
                                      });
                                  }
                                  
                                  
                                  schedule("2,7,12,17,22,27,32,37,42,47,52,57 * * * *", function () {
                                      log ("Auslöser: Schedule");
                                  	Piko();
                                  });
                                  
                                  schedule("3 0 * * *", function () {     // Variablen löschen um 00:03 Uhr   
                                      setState('javascript.0.Status.Photovoltaik.Tagesleistung', 0);
                                  });
                                  
                                  
                                  
                                  E Offline
                                  E Offline
                                  ee
                                  schrieb am zuletzt editiert von ee
                                  #57

                                  @bahnuhr Hi, super Beitrag! funktioniert bei mir! Wie kann ich noch die Werte vom BA anzeigen lassen?
                                  http://192.168.170.200/BA.fhtml (Hausverbrauch)
                                  Grüße!

                                  Hier noch die Seite:
                                  <!DOCTYPE html PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
                                  <html><head>
                                  <meta http-equiv="Content-Type" content="text/html; charset=ISO-8859-1">
                                  <meta name="Generator" content="ChrisB">
                                  <title>PV Webserver</title>
                                  </head>
                                  <body nof="(MB=(DefaultMasterborder, 65, 60, 150, 10), L=(HomeLayout, 700, 600))" bgcolor="#EAF7F7" text="#000000" link="#0033CC" vlink="#990099" alink="#FF0000" topmargin=0 leftmargin=0 marginwidth=0 marginheight=0>
                                  <table cellspacing="0" cellpadding="0" width="800" nof="ly">
                                  <tr valign="top" align="left">
                                  <td height="5" width="190"></td>
                                  <td></td>
                                  </tr>
                                  <tr align="left" valign="top">
                                  <td height="55"></td>
                                  <td colspan="2" width="600">
                                  <font face="Arial,Helvetica,Geneva,Sans-serif,sans-serif" size="+3">
                                  PIKO 10
                                  <br><font size="+1">
                                  Ebert (255)
                                  </font>
                                  </font>
                                  <td colspan="1" width="50"><img alt="Logo" height="42" width="130" src="KSE.gif"></td>
                                  </tr>
                                  </table>

                                  <table border="0" width="100%">
                                  <tr>
                                     <td width="150"></td>
                                     <td> <hr> </td>
                                  </tr></table>
                                  
                                  <font face="Arial,Helvetica,Geneva,Sans-serif,sans-serif">
                                  <table border="0" width="100%">
                                    <tr>
                                      <td height="30" width="150"></td>
                                      <td>
                                        <font size="+1"><U>Batterie
                                        </u></font></td>
                                    </tr><tr>
                                      <td width="150"></td>
                                      <td width="280" height="35" align="right">Ladezustand:</td>
                                      <td><b>0.0%</b></td>
                                    </tr><tr>
                                      <td width="150"></td>
                                      <td width="280" height="35" align="right">Spannung:</td>
                                      <td><b>   0V</b></td>
                                    </tr><tr>
                                      <td width="150"></td>
                                      <td width="280" height="35" align="right">Ladestrom:</td>
                                      <td><b> 0.00A</b></td>
                                    </tr><tr>
                                      <td width="150"></td>
                                      <td width="280" height="35" align="right">Temperatur:</td>
                                      <td><b> 0.0°C</b></td>
                                    </tr><tr>
                                      <td width="150"></td>
                                      <td align="right" height="35" width="280">Zyklenanzahl:</td>
                                      <td><b>0</b></td>
                                    </tr><tr>
                                      <td height="50" width="150"></td>
                                      <td>
                                        <font size="+1"><u>Hausverbrauch
                                        </u></font></td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td height="35" width="280">Deckung des Hausverbrauches aus:</td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td align="right" height="35" width="280">Solargenerator:</td>
                                      <td><b>  0.0W</b></td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td align="right" height="35" width="280">Batterie:</td>
                                      <td><b>  0.0W</b></td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td align="right" height="35" width="280">Netz:</td>
                                      <td><b>  0.0W</b></td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td height="35" width="280">Phasenselektiver Hausverbrauch:</td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td align="right" height="35" width="280">Phase 1:</td>
                                      <td><b>  0.0W</b></td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td align="right" height="35" width="280">Phase 2:</td>
                                      <td><b>  0.0W</b></td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td align="right" height="35" width="280">Phase 3:</td>
                                      <td><b>  0.0W</b></td>
                                    </tr><tr>	    
                                      <td width="150"></td>
                                      <td align="right" height="35" width="280"></td>
                                    </tr>
                                  </table>
                                  </font>
                                  <hr><br>
                                  

                                  <table align="left"><tbody><tr><td width="160">&nbsp</td><td>
                                  <font face="Arial,Helvetica,Geneva,Sans-serif">&nbsp&nbsp
                                  &nbsp<a href="index.fhtml"> Zurück zur Hauptseite </a>
                                  &nbsp
                                  </font></td></tr></tbody></table>

                                  </body></html>

                                  bahnuhrB 1 Antwort Letzte Antwort
                                  0
                                  • J joefarm

                                    @Diginix said in Status vom Kostal Wechselrichter auslesen?:

                                    Kann mir hier jemand die modbus Adapter Einstellungen für ein Plenticore Plus 5.5 mit Firmware 1.30 erklären oder als Screenshot zeigen.
                                    Habe die IP, Port und GeräteID eingetragen, sonst noch nichts weiter. Die Instanz bleibt aber gelb. Im Log steht "Serial is not available", habe aber TCP gewählt.

                                    Sorry, hab die Frage gerade erst gelesen. Mein Plenticore Plus 10 ist jetzt seit gut einem Monat in Betrieb und ich hab einiges ausprobiert, um ihn auszulesen per modbus. Mit folgenden Einstellungen war ich erfolgreich:

                                    address	name	description	unit	type	len	factor	offset	role	room	poll	wp
                                    2	MODBUSEnable	MODBUS Enable		uint16be	1	1	0	value		false	false	
                                    4	MODBUSUnit-ID	MODBUS Unit-ID		uint16be	1	1	0	value		false	false	
                                    6	Inverterarticlenumber	Inverter article number		string	8	1	0	value		false	false	
                                    14	Inverterserialnumber	Inverter serial number		string	8	1	0	value		false	false	
                                    30	Numberofbidirectionalconverter	Number of bidirectional converter		uint16be	1	1	0	value		false	false	
                                    32	NumberofACphases	Number of AC phases		uint16be	1	1	0	value		false	false	
                                    34	NumberofPVstrings	Number of PV strings		uint16be	1	1	0	value		false	false	
                                    36	Hardware-Version-	Hardware-Version -		uint16be	1	1	0	value		false	false	
                                    38	Software-VersionMaincontroller(MC)	Software-Version Maincontroller (MC)		string	8	1	0	value		false	false	
                                    46	Software-VersionIO-Controller(IOC)	Software-Version IO-Controller (IOC)		string	8	1	0	value		false	false	
                                    54	Power-ID	Power-ID		uint16be	1	1	0	value		false	false	
                                    56	Inverterstate2	Inverter state2		uint16be	1	1	0	value		true	false	
                                    100	TotalDCpower	Total DC power	W	floatsw	2	1	0	value		true	false	
                                    104	Stateofenergymanager3	State of energy manager3		floatsw	2	1	0	value		true	false	
                                    106	Homeownconsumptionfrombattery	Home own consumption from battery	W	floatsw	2	1	0	value		true	false	
                                    108	Homeownconsumptionfromgrid	Home own consumption from grid	W	floatsw	2	1	0	value		true	false	
                                    110	TotalhomeconsumptionBattery	Total home consumption Battery	kWh	floatsw	2	0.001	0	value		true	false	
                                    112	TotalhomeconsumptionGrid	Total home consumption Grid	kWh	floatsw	2	0.001	0	value		true	false	
                                    114	TotalhomeconsumptionPV	Total home consumption PV	kWh	floatsw	2	0.001	0	value		true	false	
                                    116	HomeownconsumptionfromPV	Home own consumption from PV	W	floatsw	2	1	0	value		true	false	
                                    118	Totalhomeconsumption	Total home consumption	kWh	floatsw	2	0.001	0	value		true	false	
                                    120	Isolationresistance	Isolation resistance	Ohm	floatsw	2	1	0	value		false	false	
                                    122	PowerlimitfromEVU	Power limit from EVU	%	floatsw	2	1	0	value		true	false	
                                    124	Totalhomeconsumptionrate	Total home consumption rate	%	floatsw	2	1	0	value		true	false	
                                    144	Worktime	Worktime	s	floatsw	2	1	0	value		true	false	
                                    150	Actualcosf	Actual cos f		floatsw	2	1	0	value		true	false	
                                    152	Gridfrequency	Grid frequency	Hz	floatsw	2	1	0	value		true	false	
                                    154	CurrentPhase1	Current Phase 1	A	floatsw	2	1	0	value		false	false	
                                    156	ActivepowerPhase1	Active power Phase 1	W	floatsw	2	1	0	value		false	false	
                                    158	VoltagePhase1	Voltage Phase 1	V	floatsw	2	1	0	value		false	false	
                                    160	CurrentPhase2	Current Phase 2	A	floatsw	2	1	0	value		false	false	
                                    162	ActivepowerPhase2	Active power Phase 2	W	floatsw	2	1	0	value		false	false	
                                    164	VoltagePhase2	Voltage Phase 2	V	floatsw	2	1	0	value		false	false	
                                    166	CurrentPhase3	Current Phase 3	A	floatsw	2	1	0	value		false	false	
                                    168	ActivepowerPhase3	Active power Phase 3	W	floatsw	2	1	0	value		false	false	
                                    170	VoltagePhase3	Voltage Phase 3	V	floatsw	2	1	0	value		false	false	
                                    172	TotalACactivepower	Total AC active power	W	floatsw	2	1	0	value		true	false	
                                    174	TotalACreactivepower	Total AC reactive power	Var	floatsw	2	1	0	value		false	false	
                                    178	TotalACapparentpower	Total AC apparent power	VA	floatsw	2	1	0	value		false	false	
                                    190	Batterychargecurrent	Battery charge current	A	floatsw	2	1	0	value		true	false	
                                    194	Numberofbatterycycles	Number of battery cycles		floatsw	2	1	0	value		true	false	
                                    200	Actualbatterycharge (-)/discharge(+)current	Actual battery charge (-)/ discharge(+)  current	A	floatsw	2	1	0	value		true	false	
                                    202	PSSBfusestate6	PSSB fuse state6		floatsw	2	1	0	value		true	false	
                                    208	Batteryreadyflag	Battery ready flag		floatsw	2	1	0	value		true	false	
                                    210	Act.stateofcharge	Act. state of charge	%	floatsw	2	1	0	value		true	false	
                                    212	Batterystate5	Battery state5		floatsw	2	1	0	value		false	false	
                                    214	Batterytemperature	Battery temperature	°C	floatsw	2	1	0	value		true	false	
                                    216	Batteryvoltage	Battery voltage	V	floatsw	2	1	0	value		true	false	
                                    218	Cosf(powermeter)	Cos f (powermeter)		floatsw	2	1	0	value		true	false	
                                    220	Frequency(powermeter)	Frequency (powermeter)	Hz	floatsw	2	1	0	value		true	false	
                                    320	Totale Erzeugung	Totale Erzeugung	kWh	floatsw	2	0.001	0	value		true	false	
                                    322	Tagesproduktion	Tagesproduktion	kWh	floatsw	2	0.001	0	value		true	false	
                                    252	Totalactivepower(powermeter)	Total active power (powermeter)	W	floatsw	2	1	0	value		true	false	
                                    324	Yearlyyield	Yearly yield	kWh	floatsw	2	0.001	0	value		true	false	
                                    326	Monthlyyield	Monthly yield	kWh	floatsw	2	0.001	0	value		true	false	
                                    512	Batterygrosscapacity5	Battery gross capacity5	Ah	uint32be	2	1	0	value		true	false	
                                    514	BatteryactualSOC	Battery actual SOC	%	uint16be	1	1	0	value		true	false	
                                    577	GenerationEnergy	Generation Energy	kWh	uint32be	2	0.001	0	value		true	false	
                                    582	Actualbatterycharge/dischargepower	Actual battery charge/discharge power	W	int16be	1	1	0	value		true	false	
                                    224	Activepowerphase1(powermeter)	Active power phase 1 (powermeter)	W	floatsw	2	1	0	value		true	false	
                                    234	Activepowerphase2(powermeter)	Active power phase 2 (powermeter)	W	floatsw	2	1	0	value		true	false	
                                    244	Activepowerphase3(powermeter)	Active power phase 3 (powermeter)	W	floatsw	2	1	0	value		true	false	
                                    575	InverterGenerationPower(actual)	Inverter Generation Power (actual)	W	int16be	1	1	0	value		true	false	
                                    260	PowerDC1	Power DC1	W	floatsw	2	1	0	value		true	false	
                                    270	PowerDC2	Power DC2	W	floatsw	2	1	0	value		true	false	
                                    280	PowerDC3	Power DC3	W	floatsw	2	1	0	value		true	false	
                                    
                                    

                                    Nicht alle Einträge liefern brauchbare Werte, aber die meisten doch. Einfach ausprobieren.
                                    Ich hab zusätzlich noch den Smart Energy Manager am laufen, den ich per 2. modbus Eintrag auslese:

                                    address	name	description	unit	type	len	factor	offset	role	room	poll	wp
                                    8218	Product Name	Product Name		string	16	1	0	value		true	false	
                                    40071	M_AC_Current	AC Current (sum of active phases)	A	int16be	1	0.01	0	value		false	false	
                                    40072	M_AC_Cur- rent_A	Phase A AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                                    40073	M_AC_Cur- rent_B	Phase B AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                                    40074	M_AC_Cur- rent_C	Phase C AC cur- rent	A	int16be	1	0.01	0	value		true	false	
                                    40076	M_AC_Vol- tage_LN	Line to Neutral AC Voltage (average of active phases)	V	int16be	1	0.01	0	value		false	false	
                                    40077	M_AC_Vol- tage_AN	Phase A to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                                    40078	M_AC_Vol- tage_BN	Phase B to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                                    40079	M_AC_Vol- tage_CN	Phase C to Neutral AC Voltage	V	uint16be	1	0.01	0	value		true	false	
                                    40080	M_AC_Vol- tage_LL	Line to Line AC Voltage (average of active phases)	V	uint16be	1	1	0	value		false	false	
                                    40081	M_AC_Vol- tage_AB	Phase A to Phase B AC Voltage	V	uint16be	1	1	0	value		false	false	
                                    40082	M_AC_Vol- tage_BC	Phase B to Phase C AC Voltage	V	uint16be	1	1	0	value		false	false	
                                    40083	M_AC_Vol- tage_CA	Phase C to Phase A AC Voltage	V	uint16be	1	1	0	value		false	false	
                                    40085	M_AC_Freq	AC Frequency	Hz	uint16be	1	0.01	0	value		true	false	
                                    40087	M_AC_Power	Total Real Power (sum of active pha- ses)	kW	int16be	1	0.01	0	value		true	false	
                                    40088	M_AC_Pow- er_A	Phase A AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                                    40089	M_AC_Pow- er_B	Phase B AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                                    40090	M_AC_Pow- er_C	Phase C AC Real Power	kW	int16be	1	0.01	0	value		true	false	
                                    40092	M_AC_VA	Total AC Apparent Power (sum of ac- tive phases)	VA	int16be	1	1	0	value		false	false	
                                    40093	M_AC_VA_A	Phase A AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                                    40094	M_AC_VA_B	Phase B AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                                    40095	M_AC_VA_C	Phase C AC Appa- rent Power	VA	int16be	1	1	0	value		false	false	
                                    40097	M_AC_VAR	Total AC Reactive Power (sum of ac- tive phases)	var	uint16be	1	1	0	value		false	false	
                                    40098	M_AC_VAR_A	Phase A AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                                    40099	M_AC_VAR_B	Phase B AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                                    40100	M_AC_VAR_C	Phase C AC Reac- tive Power	var	uint16be	1	1	0	value		false	false	
                                    40102	M_AC_PF	Average Power Factor (average of active phases)	%	uint16be	1	1	0	value		false	false	
                                    40103	M_AC_PF_A	Phase A Power Factor	%	uint16be	1	1	0	value		false	false	
                                    40104	M_AC_PF_B	Phase B Power Factor	%	uint16be	1	1	0	value		false	false	
                                    40105	M_AC_PF_C	Phase C Power Factor	%	uint16be	1	1	0	value		false	false	
                                    40107	M_Exported	Total Exported Re- al Energy	kWh	int32be	2	-0.001	0	value		true	false	
                                    40109	M_Expor- ted_A	Phase A Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                                    40111	M_Expor- ted_B	Phase B Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                                    40113	M_Expor- ted_C	Phase C Exported Real Energy	kWh	int32be	2	-0.001	0	value		true	false	
                                    40115	M_Imported	Total Imported Re- al Energy	kWh	int32be	2	0.001	0	value		true	false	
                                    40117	M_Imported_A	Phase A Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                                    40119	M_Impor- ted_B	Phase B Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                                    40121	M_Impor- ted_C	Phase C Imported Real Energy	kWh	int32be	2	0.001	0	value		true	false	
                                    40124	M_Expor- ted_VA	Total Exported Ap- parent Energy	VAh	int32be	2	1	0	value		false	false	
                                    40126	M_Expor- ted_VA_A	Phase A Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                                    40128	M_Expor- ted_VA_B	Phase B Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                                    40130	M_Expor- ted_VA_C	Phase C Exported Apparent Energy	VAh	int32be	2	1	0	value		false	false	
                                    40132	M_Impor- ted_VA	Total Imported Ap- parent Energy	VAh	uint32be	2	1	0	value		false	false	
                                    40134	M_Impor- ted_VA_A	Phase A Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                                    40136	M_Impor- ted_VA_B	Phase B Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                                    40138	M_Impor- ted_VA_C	Phase C Imported Apparent Energy	VAh	uint32be	2	1	0	value		false	false	
                                    40145	M_Import_ VARh_Q1B	Phase B – Quadrant 1: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40147	M_Import_ VARh_Q1C	Phase C – Quadrant 1: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40149	M_Import_ VARh_Q2	Quadrant 2: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40151	M_Import_ VARh_Q2A	Phase A – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40153	M_Import_ VARh_Q2B	Phase B – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40155	M_Import_ VARh_Q2C	Phase C – Quadrant 2: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40157	M_Export_ VARh_Q3	Quadrant 3: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40159	M_Export_ VARh_Q3A	Phase A – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40161	M_Export_ VARh_Q3B	Phase B – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40163	M_Export_ VARh_Q3C	Phase C – Quadrant 3: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40165	M_Export_ VARh_Q4	Quadrant 4: Total Imported Reactive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40167	M_Export_ VARh_Q4A	Phase A – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40169	M_Export_ VARh_Q4B	Phase B – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    40171	M_Export_ VARh_Q4C	Phase C – Quadrant 4: Imported Reac- tive Energy	VARh	uint32be	2	1	0	value		false	false	
                                    0	Active Power+	Active Power+	W	uint32be	2	1	0	value		false	false	
                                    2	Active Power-	Active Power-	W	uint32be	2	1	0	value		false	false	
                                    
                                    

                                    Beides jeweils in die Holding-Register importieren. Bin gerne aufgeschlossen, wer noch weitere Werte gefunden hat.

                                    Das Ganze sieht dann visualisiert so aus:
                                    6af9a378-fd30-4b27-a801-ff71183cf4e8-image.png

                                    Marco LaserM Offline
                                    Marco LaserM Offline
                                    Marco Laser
                                    schrieb am zuletzt editiert von
                                    #58

                                    @joefarm Moin, wäre es möglich dass du die Flot Einstellungen von dem unteren teilst? Bei mir nimmt er da immer Werte vom Vortag mit rein. Die Werte hast du mit dem SourceAnalytix Adapter aufgezeichnet oder?

                                    J 1 Antwort Letzte Antwort
                                    0
                                    • E ee

                                      @bahnuhr Hi, super Beitrag! funktioniert bei mir! Wie kann ich noch die Werte vom BA anzeigen lassen?
                                      http://192.168.170.200/BA.fhtml (Hausverbrauch)
                                      Grüße!

                                      Hier noch die Seite:
                                      <!DOCTYPE html PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
                                      <html><head>
                                      <meta http-equiv="Content-Type" content="text/html; charset=ISO-8859-1">
                                      <meta name="Generator" content="ChrisB">
                                      <title>PV Webserver</title>
                                      </head>
                                      <body nof="(MB=(DefaultMasterborder, 65, 60, 150, 10), L=(HomeLayout, 700, 600))" bgcolor="#EAF7F7" text="#000000" link="#0033CC" vlink="#990099" alink="#FF0000" topmargin=0 leftmargin=0 marginwidth=0 marginheight=0>
                                      <table cellspacing="0" cellpadding="0" width="800" nof="ly">
                                      <tr valign="top" align="left">
                                      <td height="5" width="190"></td>
                                      <td></td>
                                      </tr>
                                      <tr align="left" valign="top">
                                      <td height="55"></td>
                                      <td colspan="2" width="600">
                                      <font face="Arial,Helvetica,Geneva,Sans-serif,sans-serif" size="+3">
                                      PIKO 10
                                      <br><font size="+1">
                                      Ebert (255)
                                      </font>
                                      </font>
                                      <td colspan="1" width="50"><img alt="Logo" height="42" width="130" src="KSE.gif"></td>
                                      </tr>
                                      </table>

                                      <table border="0" width="100%">
                                      <tr>
                                         <td width="150"></td>
                                         <td> <hr> </td>
                                      </tr></table>
                                      
                                      <font face="Arial,Helvetica,Geneva,Sans-serif,sans-serif">
                                      <table border="0" width="100%">
                                        <tr>
                                          <td height="30" width="150"></td>
                                          <td>
                                            <font size="+1"><U>Batterie
                                            </u></font></td>
                                        </tr><tr>
                                          <td width="150"></td>
                                          <td width="280" height="35" align="right">Ladezustand:</td>
                                          <td><b>0.0%</b></td>
                                        </tr><tr>
                                          <td width="150"></td>
                                          <td width="280" height="35" align="right">Spannung:</td>
                                          <td><b>   0V</b></td>
                                        </tr><tr>
                                          <td width="150"></td>
                                          <td width="280" height="35" align="right">Ladestrom:</td>
                                          <td><b> 0.00A</b></td>
                                        </tr><tr>
                                          <td width="150"></td>
                                          <td width="280" height="35" align="right">Temperatur:</td>
                                          <td><b> 0.0°C</b></td>
                                        </tr><tr>
                                          <td width="150"></td>
                                          <td align="right" height="35" width="280">Zyklenanzahl:</td>
                                          <td><b>0</b></td>
                                        </tr><tr>
                                          <td height="50" width="150"></td>
                                          <td>
                                            <font size="+1"><u>Hausverbrauch
                                            </u></font></td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td height="35" width="280">Deckung des Hausverbrauches aus:</td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td align="right" height="35" width="280">Solargenerator:</td>
                                          <td><b>  0.0W</b></td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td align="right" height="35" width="280">Batterie:</td>
                                          <td><b>  0.0W</b></td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td align="right" height="35" width="280">Netz:</td>
                                          <td><b>  0.0W</b></td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td height="35" width="280">Phasenselektiver Hausverbrauch:</td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td align="right" height="35" width="280">Phase 1:</td>
                                          <td><b>  0.0W</b></td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td align="right" height="35" width="280">Phase 2:</td>
                                          <td><b>  0.0W</b></td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td align="right" height="35" width="280">Phase 3:</td>
                                          <td><b>  0.0W</b></td>
                                        </tr><tr>	    
                                          <td width="150"></td>
                                          <td align="right" height="35" width="280"></td>
                                        </tr>
                                      </table>
                                      </font>
                                      <hr><br>
                                      

                                      <table align="left"><tbody><tr><td width="160">&nbsp</td><td>
                                      <font face="Arial,Helvetica,Geneva,Sans-serif">&nbsp&nbsp
                                      &nbsp<a href="index.fhtml"> Zurück zur Hauptseite </a>
                                      &nbsp
                                      </font></td></tr></tbody></table>

                                      </body></html>

                                      bahnuhrB Online
                                      bahnuhrB Online
                                      bahnuhr
                                      Forum Testing Most Active
                                      schrieb am zuletzt editiert von
                                      #59

                                      @ee sagte in Status vom Kostal Wechselrichter auslesen?:

                                      Hi, super Beitrag! funktioniert bei mir! Wie kann ich noch die Werte vom BA anzeigen lassen?

                                      Was ist BA?

                                      Mehr Infos wären gut.


                                      Wenn ich helfen konnte, dann Daumen hoch (Pfeil nach oben)!
                                      Danke.
                                      gute Forenbeiträge: https://forum.iobroker.net/topic/51555/hinweise-f%C3%BCr-gute-forenbeitr%C3%A4ge
                                      ScreenToGif :https://www.screentogif.com/downloads.html

                                      E 1 Antwort Letzte Antwort
                                      0
                                      • bahnuhrB bahnuhr

                                        @ee sagte in Status vom Kostal Wechselrichter auslesen?:

                                        Hi, super Beitrag! funktioniert bei mir! Wie kann ich noch die Werte vom BA anzeigen lassen?

                                        Was ist BA?

                                        Mehr Infos wären gut.

                                        E Offline
                                        E Offline
                                        ee
                                        schrieb am zuletzt editiert von
                                        #60

                                        @bahnuhr Hi, der misst den Eigenverbrauch. (von Kostal https://shop.kostal-solar-electric.com/de/piko-ba-sensor.html)

                                        ich möchte die Werte weiter verarbeiten.
                                        Zb. Wenn 1000W Überschuss dann Waschmaschine einschalten.

                                        Ich habe einen Kostal Piko 10 Wechselrichter. Ich installiere gerade die neuste UI und FW auf den Wechselrichter.
                                        FW-Update_05_60
                                        PIKO-Update_UIv06.41

                                        Wie kann ich alle daten die im Webserver angezeigt werden in den IO Broker bekommen :)

                                        Sorry ich bin ein richtiger NOOB

                                        1 Antwort Letzte Antwort
                                        0
                                        • E Offline
                                          E Offline
                                          ee
                                          schrieb am zuletzt editiert von
                                          #61

                                          2edf5fa0-d4f3-43ce-8621-b9ad22a2b069-image.png

                                          So sieht die neue UI aus

                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          863

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe