    Deye Wechselrichter Modbus Register beschreiben

    This topic has been deleted. Only users with topic management privileges can see it.
    • W
      warp735 last edited by warp735

      Weiß jemand wie die "Tägliche Erzeugung" gerechnet wird? Ist da der Micro inkludiert oder nicht? Bei der oberen prozentualen Anzeige "Produktion" interessiert er auf jedenfall nicht. Bei diesem Beispiel müssten es ja 55% sein und nicht 41%

      Find nämlich auch kein Register für die kwh vom Microinverter 😞

      Snag_44ef76.png

      1 Reply Last reply Reply Quote 0
      • R
        Ronny81 last edited by

        Servus zusammen,

        ich bin neu hier und hoffe ihr könnt mir helfen.
        Ich muss ganz dringen ein Register am Deye setzen und zwar die ID bzw. Seriennummer.
        Leider hat mein Deye nach dem letzten Firmware Update seine ID verloren.
        Ich habe es schon über die RS232 versucht, aber der WR will nicht antworten.
        Kann man die ID über die RS485 ändern?
        Die ID müsste die Register 3,4,5,6 und 7 haben.
        Register 7, ID(SN), Stelle 2 + 1 ASCII
        Register 6, ID(SN), Stelle 4 + 3 ASCII
        Register 5, ID(SN), Stelle 6 + 5 ASCII
        Register 4, ID(SN), Stelle 8 + 7 ASCII
        Register 3, ID(SN), Stelle 10 + 9 ASCII
        Ich hoffe Ihr könnt mir helfen. Danke schon mal.
        Anbei noch ein Foto des Display ohne ID.

        Gruß Ronny

        20240406_174924.jpg 20240407_155125.jpg

        1 Reply Last reply Reply Quote 0
        • wendy2702
          wendy2702 last edited by

          Hi,

          ich schaffe es aktuell nicht meinen Deye SUN-12K-SG04LP3-EU pe Waveshare auszulesen.

          ich verwende diesen Waveshare:

          15a56c0a-df08-4f36-b038-41bcf06e6805-grafik.png

          mit diesen Einstellungen:

          ad83f715-b7d6-4abb-adb5-613b814a6e75-grafik.png

          636dd362-e0c0-47b0-98c1-4b4ca03fc7ec-grafik.png

          Wenn ich mit CAS Modbus Scanner per USB RS485 Adapter einen Test mache funktioniert die Verbindung:

          50611fe6-b361-4ec5-b918-04fb5d121f7e-grafik.png :

          Und mit Modbus Poll kann ich register auslesen.

          Iob ist so konfiguriert:

          49401faa-1116-48a2-8c29-861e6cc774ba-grafik.png

          Register aus dem Github Modbus Template von @TheBam

          9f3695a3-2a67-4fd6-baea-7a6977a7ea52-grafik.png

          Debug log hilft mir aktuell nicht weiter: (Gekürzt wegen Payload.)

          2024-05-24 10:49:09.547  - info: host.iobroker "system.adapter.modbus.4" enabled
          2024-05-24 10:49:10.972  - info: host.iobroker instance system.adapter.modbus.4 started with pid 213280
          2024-05-24 10:49:12.811  - debug: modbus.4 (213280) Redis Objects: Use Redis connection: 0.0.0.0:9001
          2024-05-24 10:49:12.924  - debug: modbus.4 (213280) Objects client ready ... initialize now
          2024-05-24 10:49:13.001  - debug: modbus.4 (213280) Objects create System PubSub Client
          2024-05-24 10:49:13.002  - debug: modbus.4 (213280) Objects create User PubSub Client
          2024-05-24 10:49:13.308  - debug: modbus.4 (213280) Objects client initialize lua scripts
          2024-05-24 10:49:13.332  - debug: modbus.4 (213280) Objects connected to redis: 0.0.0.0:9001
          2024-05-24 10:49:13.551  - debug: modbus.4 (213280) Redis States: Use Redis connection: 0.0.0.0:9000
          2024-05-24 10:49:13.669  - debug: modbus.4 (213280) States create System PubSub Client
          2024-05-24 10:49:13.670  - debug: modbus.4 (213280) States create User PubSub Client
          2024-05-24 10:49:13.848  - debug: modbus.4 (213280) States connected to redis: 0.0.0.0:9000
          2024-05-24 10:49:14.085  - debug: modbus.4 (213280) Plugin sentry Do not initialize Plugin (enabled=false)
          2024-05-24 10:49:14.141  - debug: modbus.4 (213280) Plugin sentry destroyed because not initialized correctly
          2024-05-24 10:49:14.599  - info: modbus.4 (213280) starting. Version 6.2.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
          2024-05-24 10:49:15.614  - debug: modbus.4 (213280) Initialize Objects for disInputs: []
          2024-05-24 10:49:15.616  - debug: modbus.4 (213280) Initialize Objects for coils: []
          2024-05-24 10:49:15.617  - debug: modbus.4 (213280) Initialize Objects for inputRegs: []
          2024-05-24 10:49:15.626  - debug: modbus.4 (213280) Initialize Objects for holdingRegs: [{"_address":40001,"name":"Device type","description":"Gerätetyp","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40001,"id":"holdingRegisters.40001_Device_type"},Gesamtscheinleistung","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40609,"id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power"},{"_address":40610,"name":"Grid-side frequency","description":"Grid Seite Frequenz","unit":"Hz","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40610,"id":"holdingRegisters.40610_Grid-side_frequency"},{"_address":40611,"name":"grid side inner current L1","description":"netzseitiger Innenstrom 1","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40678,"id":"holdingRegisters.40678_Dc_current_1"},{"_address":40679,"name":"Dc voltage 2","description":"Gleichspannung 2","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40679,"id":"holdingRegisters.40679_Dc_voltage_2"},{"_address":40680,"name":"Dc current 2","description":"Gleichstrom 2","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40680,"id":"holdingRegisters.40680_Dc_current_2"}]
          2024-05-24 10:49:15.633  - debug: modbus.4 (213280) Add holdingRegisters.40001_Device_type: {"_id":"holdingRegisters.40001_Device_type","type":"state","common":{"name":"Gerätetyp","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40001,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.636  - debug: modbus.4 (213280) Add holdingRegisters.40004_Seriennummer: {"_id":"holdingRegisters.40004_Seriennummer","type":"state","common":{"name":"Seriennummer","role":"state","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":40004,"deviceId":4,"type":"string","len":5,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.637  - debug: modbus.4 (213280) Add holdingRegisters.40061_Fernsperre: {"_id":"holdingRegisters.40061_Fernsperre","type":"state","common":{"name":"Fernsperre","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40061,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40081_SchalterModus: {"_id":"holdingRegisters.40081_SchalterModus","type":"state","common":{"name":"SchalterModus","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40081,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.639  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40109_Max_A_Charge: {"_id":"holdingRegisters.40109_Max_A_Charge","type":"state","common":{"name":"Maximaler Ladestrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40109,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40110_Max_A_discharge: {"_id":"holdingRegisters.40110_Max_A_discharge","type":"state","common":{"name":"Max A Entladung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40110,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40116_ShutDown_battery_capacity_ShutDown: {"_id":"holdingRegisters.40116_ShutDown_battery_capacity_ShutDown","type":"state","common":{"name":"Abschalten Batteriekapazität Herunterfahren","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40116,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40117_Restart_battery_capacityRestart: {"_id":"holdingRegisters.40117_Restart_battery_capacityRestart","type":"state","common":{"name":"Neu starten BatteriekapazitätNeustart","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40117,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40118_LowBatt_battery_capacityLowBatt: {"_id":"holdingRegisters.40118_LowBatt_battery_capacityLowBatt","type":"state","common":{"name":"Low Batterie Anzeige zum Abschalten der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40118,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40130_Generator_is_charged_to_enable: {"_id":"holdingRegisters.40130_Generator_is_charged_to_enable","type":"state","common":{"name":"Generator is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40130,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40131_Grid_is_charged_to_enable: {"_id":"holdingRegisters.40131_Grid_is_charged_to_enable","type":"state","common":{"name":"Grid is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40131,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection: {"_id":"holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection","type":"state","common":{"name":"Begrenzen Sie die maximale Ausgangsleistung des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40144,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40145_External_current_sensor_clamp_phase: {"_id":"holdingRegisters.40145_External_current_sensor_clamp_phase","type":"state","common":{"name":"Klemmphase des externen Stromsensors","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40145,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40146_Solar_sell: {"_id":"holdingRegisters.40146_Solar_sell","type":"state","common":{"name":"  Verkauf von Solar","role":"switch","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40146,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40149_Sell_mode_time_point_1: {"_id":"holdingRegisters.40149_Sell_mode_time_point_1","type":"state","common":{"name":"Sell mode time point 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40149,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40150_Sell_mode_time_point_2: {"_id":"holdingRegisters.40150_Sell_mode_time_point_2","type":"state","common":{"name":"Sell mode time point 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40150,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40151_Sell_mode_time_point_3: {"_id":"holdingRegisters.40151_Sell_mode_time_point_3","type":"state","common":{"name":"Sell mode time point 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40151,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40152_Sell_mode_time_point_4: {"_id":"holdingRegisters.40152_Sell_mode_time_point_4","type":"state","common":{"name":"Sell mode time point 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40152,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40153_Sell_mode_time_point_5: {"_id":"holdingRegisters.40153_Sell_mode_time_point_5","type":"state","common":{"name":"Sell mode time point 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40153,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40154_Sell_mode_time_point_6: {"_id":"holdingRegisters.40154_Sell_mode_time_point_6","type":"state","common":{"name":"Sell mode time point 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40154,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40155_Sell_mode_Watt_time_1: {"_id":"holdingRegisters.40155_Sell_mode_Watt_time_1","type":"state","common":{"name":"Sell mode Watt time 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40155,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40156_Sell_mode_Watt_time_2: {"_id":"holdingRegisters.40156_Sell_mode_Watt_time_2","type":"state","common":{"name":"Sell mode Watt time 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40156,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40157_Sell_mode_Watt_time_3: {"_id":"holdingRegisters.40157_Sell_mode_Watt_time_3","type":"state","common":{"name":"Sell mode Watt time 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40157,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40158_Sell_mode_Watt_time_4: {"_id":"holdingRegisters.40158_Sell_mode_Watt_time_4","type":"state","common":{"name":"Sell mode Watt time 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40158,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40159_Sell_mode_Watt_time_5: {"_id":"holdingRegisters.40159_Sell_mode_Watt_time_5","type":"state","common":{"name":"Sell mode Watt time 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40159,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40160_Sell_mode_Watt_time_6: {"_id":"holdingRegisters.40160_Sell_mode_Watt_time_6","type":"state","common":{"name":"Sell mode Watt time 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40160,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40167_TOF_Cell_SOC_1: {"_id":"holdingRegisters.40167_TOF_Cell_SOC_1","type":"state","common":{"name":"TOF_Cell SOC 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40167,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40168_TOF_Cell_SOC_2: {"_id":"holdingRegisters.40168_TOF_Cell_SOC_2","type":"state","common":{"name":"TOF_Cell SOC 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40168,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40169_TOF_Cell_SOC_3: {"_id":"holdingRegisters.40169_TOF_Cell_SOC_3","type":"state","common":{"name":"TOF_Cell SOC 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40169,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40170_TOF_Cell_SOC_4: {"_id":"holdingRegisters.40170_TOF_Cell_SOC_4","type":"state","common":{"name":"TOF_Cell SOC 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40170,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40171_TOF_Cell_SOC_5: {"_id":"holdingRegisters.40171_TOF_Cell_SOC_5","type":"state","common":{"name":"TOF_Cell SOC 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40171,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40172_TOF_Cell_SOC_6: {"_id":"holdingRegisters.40172_TOF_Cell_SOC_6","type":"state","common":{"name":"TOF_Cell SOC 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40172,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40173_Time_point_1_charge_enable: {"_id":"holdingRegisters.40173_Time_point_1_charge_enable","type":"state","common":{"name":"Time point 1 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40173,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40174_Time_point_2_charge_enable: {"_id":"holdingRegisters.40174_Time_point_2_charge_enable","type":"state","common":{"name":"Time point 2 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40174,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40175_Time_point_3_charge_enable: {"_id":"holdingRegisters.40175_Time_point_3_charge_enable","type":"state","common":{"name":"Time point 3 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40175,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40176_Time_point_4_charge_enable: {"_id":"holdingRegisters.40176_Time_point_4_charge_enable","type":"state","common":{"name":"Time point 4 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40176,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40177_Time_point_5_charge_enable: {"_id":"holdingRegisters.40177_Time_point_5_charge_enable","type":"state","common":{"name":"Time point 5 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40177,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40178_Time_point_6_charge_enable: {"_id":"holdingRegisters.40178_Time_point_6_charge_enable","type":"state","common":{"name":"Time point 6 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40178,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei null einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40501_Status: {"_id":"holdingRegisters.40501_Status","type":"state","common":{"name":"Status (Standby, check, norm, altert, fault)","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40501,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40521_Day_Grid_Buy_Power_Wh: {"_id":"holdingRegisters.40521_Day_Grid_Buy_Power_Wh","type":"state","common":{"name":"Tag Netzabnahme Strom Wh","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40521,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40522_Day_GridSell_Power_Wh: {"_id":"holdingRegisters.40522_Day_GridSell_Power_Wh","type":"state","common":{"name":"Tages Verkaufs leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40522,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40530_Day_PV_Power_Wh: {"_id":"holdingRegisters.40530_Day_PV_Power_Wh","type":"state","common":{"name":"Tagesproduzierte leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40530,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40535_Total_PV_power_Wh_low_word: {"_id":"holdingRegisters.40535_Total_PV_power_Wh_low_word","type":"state","common":{"name":"Gesamt-PV-Leistung Wh niedriges Wort","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40535,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_AC_Relay: {"_id":"holdingRegisters.40553_AC_Relay","type":"state","common":{"name":"AC relay","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_Ac_relay_2: {"_id":"holdingRegisters.40553_Ac_relay_2","type":"state","common":{"name":"AC relay2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40587_battery_temperature: {"_id":"holdingRegisters.40587_battery_temperature","type":"state","common":{"name":"Batterietemperatur","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":40587,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40588_battery_voltage: {"_id":"holdingRegisters.40588_battery_voltage","type":"state","common":{"name":"Batteriespannung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40588,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40589_battery_capacity: {"_id":"holdingRegisters.40589_battery_capacity","type":"state","common":{"name":"Batteriekapazität","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40589,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40591_Battery_output_power: {"_id":"holdingRegisters.40591_Battery_output_power","type":"state","common":{"name":"Ausgangsleistung der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40591,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40592_Battery_output_current: {"_id":"holdingRegisters.40592_Battery_output_current","type":"state","common":{"name":"Ausgangsstrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40592,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40593_Corrected_AH: {"_id":"holdingRegisters.40593_Corrected_AH","type":"state","common":{"name":"AH korrigiert","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"AH"},"native":{"regType":"holdingRegs","address":40593,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40599_Grid_phase_voltage_A: {"_id":"holdingRegisters.40599_Grid_phase_voltage_A","type":"state","common":{"name":"Netzphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40599,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40600_Grid_phase_voltage_B: {"_id":"holdingRegisters.40600_Grid_phase_voltage_B","type":"state","common":{"name":"Netzphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40600,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40601_Grid_phase_voltage_C: {"_id":"holdingRegisters.40601_Grid_phase_voltage_C","type":"state","common":{"name":"Netzphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40601,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L1 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40605,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L2 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40606,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L3 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40607,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40608_active_power_from_side_to_side_of_the_grid: {"_id":"holdingRegisters.40608_active_power_from_side_to_side_of_the_grid","type":"state","common":{"name":"Wirkleistung von Seite zu Seite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40608,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40609_Grid_side_-_inside_total_apparent_power: {"_id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power","type":"state","common":{"name":"Netzseite – innere Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40609,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40610_Grid-side_frequency: {"_id":"holdingRegisters.40610_Grid-side_frequency","type":"state","common":{"name":"Grid Seite Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40610,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40611_grid_side_inner_current_L1: {"_id":"holdingRegisters.40611_grid_side_inner_current_L1","type":"state","common":{"name":"netzseitiger Innenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40611,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40612_grid_side_inner_current_L2: {"_id":"holdingRegisters.40612_grid_side_inner_current_L2","type":"state","common":{"name":"netzseitiger Innenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40612,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40613_grid_side_inner_current_L3: {"_id":"holdingRegisters.40613_grid_side_inner_current_L3","type":"state","common":{"name":"netzseitiger Innenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40613,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40614_Out-of-grid_-_current_L1: {"_id":"holdingRegisters.40614_Out-of-grid_-_current_L1","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40614,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40615_Out-of-grid_-_current_L2: {"_id":"holdingRegisters.40615_Out-of-grid_-_current_L2","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40615,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40616_Out-of-grid_-_current_L3: {"_id":"holdingRegisters.40616_Out-of-grid_-_current_L3","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40616,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40617_A_Out-of-grid_-power_L1: {"_id":"holdingRegisters.40617_A_Out-of-grid_-power_L1","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40617,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40618_A_Out-of-grid_-power_L2: {"_id":"holdingRegisters.40618_A_Out-of-grid_-power_L2","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40618,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40619_A_Out-of-grid_-power_L3: {"_id":"holdingRegisters.40619_A_Out-of-grid_-power_L3","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40619,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40620_Out-of-grid_–total_power: {"_id":"holdingRegisters.40620_Out-of-grid_–total_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40620,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40621_Out-of-grid_–total_apparent_power: {"_id":"holdingRegisters.40621_Out-of-grid_–total_apparent_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40621,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40622_Grid-connected_power_factor_PF: {"_id":"holdingRegisters.40622_Grid-connected_power_factor_PF","type":"state","common":{"name":"Netzgekoppelter Leistungsfaktor PF","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40622,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40623_Grid_side_A-phase_power: {"_id":"holdingRegisters.40623_Grid_side_A-phase_power","type":"state","common":{"name":"Netzseitiger L1-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40623,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40624_Grid_side_B-phase_power: {"_id":"holdingRegisters.40624_Grid_side_B-phase_power","type":"state","common":{"name":"Netzseitiger L2-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40624,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40625_Grid_side_C-phase_power: {"_id":"holdingRegisters.40625_Grid_side_C-phase_power","type":"state","common":{"name":"Netzseitiger L3-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40625,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40626_Grid_side_total_power: {"_id":"holdingRegisters.40626_Grid_side_total_power","type":"state","common":{"name":"Netzseitige Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40626,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40628_Inverter_output_phase_voltage_A: {"_id":"holdingRegisters.40628_Inverter_output_phase_voltage_A","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40628,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40629_Inverter_output_phase_voltage_B: {"_id":"holdingRegisters.40629_Inverter_output_phase_voltage_B","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40629,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40630_Inverter_output_phase_voltage_C: {"_id":"holdingRegisters.40630_Inverter_output_phase_voltage_C","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40630,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40631_Inverter_output_phase_current_A: {"_id":"holdingRegisters.40631_Inverter_output_phase_current_A","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40631,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40632_Inverter_output_phase_current_B: {"_id":"holdingRegisters.40632_Inverter_output_phase_current_B","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40632,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.657  - debug: modbus.4 (213280) Add holdingRegisters.40633_Inverter_output_phase_current_C: {"_id":"holdingRegisters.40633_Inverter_output_phase_current_C","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40633,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.659  - debug: modbus.4 (213280) Add holdingRegisters.40634_Inverter_output_phase_power_A: {"_id":"holdingRegisters.40634_Inverter_output_phase_power_A","type":"state","common":{"name":"  Ausgangsphase des Wechselrichters Macht L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40634,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.660  - debug: modbus.4 (213280) Add holdingRegisters.40635_Inverter_output_phase_power_B: {"_id":"holdingRegisters.40635_Inverter_output_phase_power_B","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Macht L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40635,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40636_Inverter_output_phase_power_C: {"_id":"holdingRegisters.40636_Inverter_output_phase_power_C","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40636,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40637_Inverter_output_total_power: {"_id":"holdingRegisters.40637_Inverter_output_total_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40637,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40638_Inverter_output_total_apparent_power: {"_id":"holdingRegisters.40638_Inverter_output_total_apparent_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Scheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40638,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40639_Inverter_frequency: {"_id":"holdingRegisters.40639_Inverter_frequency","type":"state","common":{"name":"Wechselrichter frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40639,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40641_UPS_load-side_phase_power_A: {"_id":"holdingRegisters.40641_UPS_load-side_phase_power_A","type":"state","common":{"name":"USV-lastseitige Phasenleistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40641,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40642_UPS_load-side_phase_power_B: {"_id":"holdingRegisters.40642_UPS_load-side_phase_power_B","type":"state","common":{"name":"USV-lastseitige Phasenleistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40642,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40643_UPS_load-side_phase_power_C: {"_id":"holdingRegisters.40643_UPS_load-side_phase_power_C","type":"state","common":{"name":"USV-lastseitige Phasenleistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40643,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40644_UPS_load-sidetotal_power: {"_id":"holdingRegisters.40644_UPS_load-sidetotal_power","type":"state","common":{"name":"Lastseitige Gesamtleistung der USV","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40644,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40645_Load_phase_voltage_A: {"_id":"holdingRegisters.40645_Load_phase_voltage_A","type":"state","common":{"name":"Load phasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40645,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40646_Load_phase_voltage_B: {"_id":"holdingRegisters.40646_Load_phase_voltage_B","type":"state","common":{"name":"Load phasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40646,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40647_Load_phase_voltage_C: {"_id":"holdingRegisters.40647_Load_phase_voltage_C","type":"state","common":{"name":"Load phasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40647,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40648_Load_phase_current_A: {"_id":"holdingRegisters.40648_Load_phase_current_A","type":"state","common":{"name":"Load phasenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40648,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40649_Load_phase_current_B: {"_id":"holdingRegisters.40649_Load_phase_current_B","type":"state","common":{"name":"Load phasenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40649,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40650_Load_phase_current_C: {"_id":"holdingRegisters.40650_Load_phase_current_C","type":"state","common":{"name":"Load phasenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40650,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40651_Load_phase_power_A: {"_id":"holdingRegisters.40651_Load_phase_power_A","type":"state","common":{"name":"Load phase Leistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40651,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40652_Load_phase_power_B: {"_id":"holdingRegisters.40652_Load_phase_power_B","type":"state","common":{"name":"Load phase Leistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40652,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40653_Load_phase_power_C: {"_id":"holdingRegisters.40653_Load_phase_power_C","type":"state","common":{"name":"Load phase Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40653,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40654_Load_totalpower: {"_id":"holdingRegisters.40654_Load_totalpower","type":"state","common":{"name":"Load Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40654,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40655_Load_phase_apparent_power: {"_id":"holdingRegisters.40655_Load_phase_apparent_power","type":"state","common":{"name":"Scheinleistung der Lastphase","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40655,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40656_Load_frequency: {"_id":"holdingRegisters.40656_Load_frequency","type":"state","common":{"name":"Load Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40656,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40662_Phase_voltage_of_Gen_port_A: {"_id":"holdingRegisters.40662_Phase_voltage_of_Gen_port_A","type":"state","common":{"name":"Phasenspannung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40662,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40663_Phase_voltage_of_Gen_port_B: {"_id":"holdingRegisters.40663_Phase_voltage_of_Gen_port_B","type":"state","common":{"name":"Phasenspannung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40663,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40664_Phase_voltage_of_Gen_port_C: {"_id":"holdingRegisters.40664_Phase_voltage_of_Gen_port_C","type":"state","common":{"name":"Phasenspannung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40664,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40665_Phase_power_of_Gen_port_A: {"_id":"holdingRegisters.40665_Phase_power_of_Gen_port_A","type":"state","common":{"name":"Phasenleistung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40665,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40666_Phase_power_of_Gen_port_B: {"_id":"holdingRegisters.40666_Phase_power_of_Gen_port_B","type":"state","common":{"name":"Phasenleistung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40666,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40667_Phase_power_of_Gen_port_C: {"_id":"holdingRegisters.40667_Phase_power_of_Gen_port_C","type":"state","common":{"name":"Phasenleistung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40667,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40668_total_power_of_Gen_port: {"_id":"holdingRegisters.40668_total_power_of_Gen_port","type":"state","common":{"name":"Gesamtleistung des Gen-Ports","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40668,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40673_PV1_input_power: {"_id":"holdingRegisters.40673_PV1_input_power","type":"state","common":{"name":"PV1 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40673,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40674_PV2_input_power: {"_id":"holdingRegisters.40674_PV2_input_power","type":"state","common":{"name":"PV2 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40674,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40677_Dc_voltage_1: {"_id":"holdingRegisters.40677_Dc_voltage_1","type":"state","common":{"name":"Gleichspannung 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40677,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40678_Dc_current_1: {"_id":"holdingRegisters.40678_Dc_current_1","type":"state","common":{"name":"Gleichstrom 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40678,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40679_Dc_voltage_2: {"_id":"holdingRegisters.40679_Dc_voltage_2","type":"state","common":{"name":"Gleichspannung 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40679,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40680_Dc_current_2: {"_id":"holdingRegisters.40680_Dc_current_2","type":"state","common":{"name":"Gleichstrom 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40680,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
          2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40620_Out-of-grid__total_power
          2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
          2024-05-24 10:49:18.765  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40620_Out-of-grid_–total_power changed to modbus.4.holdingRegisters.40620_Out-of-grid__total_power
          2024-05-24 10:49:18.777  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40621_Out-of-grid_–total_apparent_power changed to modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
          2024-05-24 10:49:22.213  - info: modbus.4 (213280) Connected to slave 192.168.178.238
          2024-05-24 10:49:22.214  - debug: modbus.4 (213280) [DevID_4] Poll start ---------------------
          2024-05-24 10:49:22.215  - debug: modbus.4 (213280) Initialization of scale factors done!
          2024-05-24 10:49:22.215  - debug: modbus.4 (213280) [DevID_4/holdingRegs] Poll address 40001 - 8 registers
          2024-05-24 10:49:27.221  - warn: modbus.4 (213280) Error: undefined
          2024-05-24 10:49:27.222  - error: modbus.4 (213280) Request timed out.
          2024-05-24 10:49:27.222  - error: modbus.4 (213280) Client in error state.
          2024-05-24 10:49:27.222  - warn: modbus.4 (213280) Poll error count: 1 code: {"err":"timeout","timeout":5000}
          2024-05-24 10:49:27.223  - debug: modbus.4 (213280) Socket closed with error
          2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Clearing timeout of the current request.
          2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Cleaning up request fifo.
          2024-05-24 10:49:28.222  - debug: modbus.4 (213280) Closing client on purpose.
          2024-05-24 10:49:28.223  - info: modbus.4 (213280) Disconnected from slave 192.168.178.238
          
          

          Angeschlossen am Deye Modbus Ausgang mit Firmware:
          d1a96c7e-2622-4aa6-bb76-06240a571d6a-grafik.png

          Der Waveshare funktioniert an einem anderen Modbus Device einwandfrei.

          Jemand noch eine Idee wo das Problem liegen könnte?

          W 1 Reply Last reply Reply Quote 0
          • W
            warp735 @wendy2702 last edited by warp735

            @wendy2702
            Testen immer nur mit EINEM Datenpunkt... Woher diese komplett falsch konfigurierten Register kommen, ist mir immer noch schleierhaft. Man sollte diesen Thread auch lesen 😉
            Ich hab ALLE Register auf Signed 16 bit

            PS: du hast RTU over TCP, oder?

            Snag_1040fdd.png

            wendy2702 1 Reply Last reply Reply Quote 0
            • wendy2702
              wendy2702 @warp735 last edited by wendy2702

              @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

              Man sollte diesen Thread auch lesen

              Den habe ich gelesen und hier stehen soviele verschiedene "Register" das ich mir am Ende das aud der Github Sammlung genommen habe.

              @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

              @wendy2702
              Testen immer nur mit EINEM Datenpunkt...

              Auch das habe ich schon hinter mir.

              @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

              PS: du hast RTU over TCP, oder?

              Ja, macht der Waveshare

              Wenn du eine dreistellige Register Adresse verwendest kann ich nur Raten das du den Haken bei "benutze Aliase" an hast ?

              W 1 Reply Last reply Reply Quote 0
              • W
                warp735 @wendy2702 last edited by warp735

                @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                Ja, macht der Waveshare

                Und warum stellst denn bei iob was anderes ein?

                @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                kann ich nur Raten das du den Haken bei "benutze Aliase" an hast ?

                Nope:
                Snag_111c2c3.png

                wendy2702 1 Reply Last reply Reply Quote 0
                • wendy2702
                  wendy2702 @warp735 last edited by wendy2702

                  @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                  Und warum stellst denn bei iob was anderes ein?

                  Weil eigentlich nur einer Umwandelt, iob oder Waveshare. Zumindest ist das bei meinen anderen Waveshare Modbus sachen so.

                  Dein Register 598 lässt sich zumindest per iob und Serieller Verbindung auslesen.

                  Gibt es hier irgendwo einen Export deiner Register?

                  EDIT: @warp735 es läuft. Die 5 Stelligen Register sind nicht "falsch", man muss dann nur den Haken bei "Benutze Aliase" setzen. Dann werden im Hintergrund die 3 stelligen verwendet.

                  So sind jetzt meine Einstellungen im Waveshare:

                  b4e6562c-277a-4fa4-afd0-5bb98ccb3034-grafik.png

                  und so in IOB:

                  7bbff636-a3fd-4aa5-b937-d151941aea27-grafik.png

                  258034e9-596e-48d1-87cd-5a90f51f6dd4-grafik.png

                  Hier nochmal der Export der Register welche aber exact der Liste von @TheBam entsprechen:

                  _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                  40001	Device type	Gerätetyp		uint16be	1	0	0		level		true	false	false	false
                  40004	Seriennummer	Seriennummer		string	5	0	0		state		true	false	false	false
                  40061	Fernsperre	Fernsperre		uint16be	1	0	0		level		true	false	false	false
                  40081	SchalterModus	SchalterModus		uint16be	1	0	0		level		true	false	false	false
                  40105	ZeroExport power	ZeroExport-Leistung	W	int16be	1	0	0		level		true	false	false	false
                  40105	ZeroExport power	ZeroExport-Leistung		floatbe	2	0	0		level		true	false	false	false
                  40109	Max A Charge	Maximaler Ladestrom der Batterie	A	uint16be	1	0	0		level		true	false	false	false
                  40110	Max A discharge	Max A Entladung	A	uint16be	1	0	0		level		true	false	false	false
                  40116	ShutDown battery capacity ShutDown	Abschalten Batteriekapazität Herunterfahren	%	uint16be	1	1	0		level		true	false	false	false
                  40117	Restart battery capacityRestart	Neu starten BatteriekapazitätNeustart	%	uint16be	1	1	0		level		true	false	false	false
                  40118	LowBatt battery capacityLowBatt	Low Batterie Anzeige zum Abschalten der Batterie	%	uint16be	1	1	0		level		true	false	false	false
                  40130	Generator is charged to enable	Generator is charged to enable		int16be	1	0	0		level		true	false	false	false
                  40131	Grid is charged to enable	Grid is charged to enable		int16be	1	0	0		level		true	false	false	false
                  40144	Max Limit Power Output Grid Connection	Begrenzen Sie die maximale Ausgangsleistung des Netzes	W	uint16be	1	0	0		level		true	false	false	false
                  40145	"External	current	sensor clamp phase"	Klemmphase des externen Stromsensors	W	uint16be	1	0	0		level		true	false	false	false
                  40146	Solar sell	  Verkauf von Solar		floatbe	2	0	0		switch		true	false	false	false
                  40149	Sell mode time point 1	Sell mode time point 1		int16be	1	0	0		level		true	false	false	false
                  40150	Sell mode time point 2	Sell mode time point 2		int16be	1	0	0		level		true	false	false	false
                  40151	Sell mode time point 3	Sell mode time point 3		int16be	1	0	0		level		true	false	false	false
                  40152	Sell mode time point 4	Sell mode time point 4		int16be	1	0	0		level		true	false	false	false
                  40153	Sell mode time point 5	Sell mode time point 5		int16be	1	0	0		level		true	false	false	false
                  40154	Sell mode time point 6	Sell mode time point 6		int16be	1	0	0		level		true	false	false	false
                  40155	Sell mode Watt time 1	Sell mode Watt time 1		int16be	1	0	0		level		true	false	false	false
                  40156	Sell mode Watt time 2	Sell mode Watt time 2		int16be	1	0	0		level		true	false	false	false
                  40157	Sell mode Watt time 3	Sell mode Watt time 3		int16be	1	0	0		level		true	false	false	false
                  40158	Sell mode Watt time 4	Sell mode Watt time 4		int16be	1	0	0		level		true	false	false	false
                  40159	Sell mode Watt time 5	Sell mode Watt time 5		int16be	1	0	0		level		true	false	false	false
                  40160	Sell mode Watt time 6	Sell mode Watt time 6		int16be	1	0	0		level		true	false	false	false
                  40167	TOF_Cell SOC 1	TOF_Cell SOC 1	%	int16be	1	0	0		level		true	false	false	false
                  40168	TOF_Cell SOC 2	TOF_Cell SOC 2	%	int16be	1	0	0		level		true	false	false	false
                  40169	TOF_Cell SOC 3	TOF_Cell SOC 3	%	int16be	1	0	0		level		true	false	false	false
                  40170	TOF_Cell SOC 4	TOF_Cell SOC 4	%	int16be	1	0	0		level		true	false	false	false
                  40171	TOF_Cell SOC 5	TOF_Cell SOC 5	%	int16be	1	0	0		level		true	false	false	false
                  40172	TOF_Cell SOC 6	TOF_Cell SOC 6	%	int16be	1	0	0		level		true	false	false	false
                  40173	Time point 1 charge enable	Time point 1 charge enable		int16be	1	0	0		level		true	false	false	false
                  40174	Time point 2 charge enable	Time point 2 charge enable		int16be	1	0	0		level		true	false	false	false
                  40175	Time point 3 charge enable	Time point 3 charge enable		int16be	1	0	0		level		true	false	false	false
                  40176	Time point 4 charge enable	Time point 4 charge enable		int16be	1	0	0		level		true	false	false	false
                  40177	Time point 5 charge enable	Time point 5 charge enable		int16be	1	0	0		level		true	false	false	false
                  40178	Time point 6 charge enable	Time point 6 charge enable		int16be	1	0	0		level		true	false	false	false
                  40341	Max Solar Sell Power at Zero grid	Maximale Solarverkaufsleistung bei null einspeisung	W	uint16be	1	0	0		level		true	false	false	false
                  40341	Max Solar Sell Power by full in	Maximale Solarverkaufsleistung bei einspeisung	W	uint16be	1	0	0		level		true	false	false	false
                  40501	Status	Status (Standby, check, norm, altert, fault)		int16be	1	0	0		level		true	false	false	false
                  40521	Day Grid Buy Power Wh	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                  40522	Day_GridSell_Power Wh	Tages Verkaufs leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                  40530	Day_PV_Power Wh	Tagesproduzierte leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                  40535	Total PV power Wh low word	Gesamt-PV-Leistung Wh niedriges Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
                  40553	AC Relay	AC relay		uint16be	1	0	0	x < 2? 0:1	level		true	false	false	false
                  40553	Ac relay 2	AC relay2		uint16be	1		0		level		true	false	false	false
                  40587	battery temperature	Batterietemperatur	°C	uint16be	1	0,01	0		level		true	false	false	false
                  40588	battery voltage	Batteriespannung	V	uint16be	1	0,01	0		level		true	false	false	false
                  40589	battery capacity	Batteriekapazität	%	uint16be	1	1	0		level		true	false	false	false
                  40591	Battery output power	Ausgangsleistung der Batterie	W	int16be	1	1	0		level		true	false	false	false
                  40592	Battery output current	Ausgangsstrom der Batterie	A	uint16be	1	0,01	0		level		true	false	false	false
                  40593	Corrected AH	AH korrigiert	AH	uint16be	1	1	0		level		true	false	false	false
                  40599	Grid phase voltage A	Netzphasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                  40600	Grid phase voltage B	Netzphasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                  40601	Grid phase voltage C	Netzphasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                  40605	L1 phase power on the inner side of the grid	L1 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                  40606	L2 phase power on the inner side of the grid	L2 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                  40607	L3 phase power on the inner side of the grid	L3 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                  40608	active power from side to side of the grid	Wirkleistung von Seite zu Seite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                  40609	Grid side - inside total apparent power	Netzseite – innere Gesamtscheinleistung	W	uint16be	1	1	0		level		true	false	false	false
                  40610	Grid-side frequency	Grid Seite Frequenz	Hz	uint16be	1	1	0		level		true	false	false	false
                  40611	grid side inner current L1	netzseitiger Innenstrom L1	A	uint16be	1	0,01	0		level		true	false	false	false
                  40612	grid side inner current L2	netzseitiger Innenstrom L2	A	uint16be	1	0,01	0		level		true	false	false	false
                  40613	grid side inner current L3	netzseitiger Innenstrom L3	A	uint16be	1	0,01	0		level		true	false	false	false
                  40614	Out-of-grid - current L1	Außerhalb des Netzes – aktuelles L1	A	uint16be	1	0,01	0		level		true	false	false	false
                  40615	Out-of-grid - current L2	Außerhalb des Netzes – aktuelles L2	A	uint16be	1	0,01	0		level		true	false	false	false
                  40616	Out-of-grid - current L3	Außerhalb des Netzes – aktuelles L3	A	uint16be	1	0,01	0		level		true	false	false	false
                  40617	A Out-of-grid -power L1	A Außerhalb des Netzes - Strom L1	W	uint16be	1	1	0		level		true	false	false	false
                  40618	A Out-of-grid -power L2	A Außerhalb des Netzes - Strom L2	W	uint16be	1	1	0		level		true	false	false	false
                  40619	A Out-of-grid -power L3	A Außerhalb des Netzes - Strom L3	W	uint16be	1	1	0		level		true	false	false	false
                  40620	Out-of-grid -total power	Außerhalb des Netzes - Gesamtleistung	W	uint16be	1	1	0		level		true	false	false	false
                  40621	Out-of-grid - total apparent power	Außerhalb des Netzes - Gesamtscheinleistung	VA	uint16be	1	1	0		level		true	false	false	false
                  40622	Grid-connected power factor PF	Netzgekoppelter Leistungsfaktor PF		uint16be	1	1	0		level		true	false	false	false
                  40623	Grid side A-phase power	Netzseitiger L1-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                  40624	Grid side B-phase power	Netzseitiger L2-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                  40625	Grid side C-phase power	Netzseitiger L3-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                  40626	Grid side total power	Netzseitige Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                  40628	Inverter output phase voltage A	Wechselrichter-Ausgangsphasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                  40629	Inverter output phase voltage B	Wechselrichter-Ausgangsphasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                  40630	Inverter output phase voltage C	Wechselrichter-Ausgangsphasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                  40631	Inverter output phase current A	Ausgangsphasenstrom des Wechselrichters L1	A	uint16be	1	0,01	0		level		true	false	false	false
                  40632	Inverter output phase current B	Ausgangsphasenstrom des Wechselrichters L2	A	uint16be	1	0,01	0		level		true	false	false	false
                  40633	Inverter output phase current C	Ausgangsphasenstrom des Wechselrichters L3	A	uint16be	1	0,01	0		level		true	false	false	false
                  40634	Inverter output phase power A	  Ausgangsphase des Wechselrichters Macht L1	W	uint16be	1	0	0		level		true	false	false	false
                  40635	Inverter output phase power B	Ausgangsphase des Wechselrichters Macht L2	W	uint16be	1	0	0		level		true	false	false	false
                  40636	Inverter output phase power C	Ausgangsphase des Wechselrichters Leistung L3	W	uint16be	1	0	0		level		true	false	false	false
                  40637	Inverter output total power	Gesamtleistung des Wechselrichters Leistung	W	uint16be	1	0	0		level		true	false	false	false
                  40638	Inverter output total apparent power	Gesamtleistung des Wechselrichters Scheinleistung	W	uint16be	1	0	0		level		true	false	false	false
                  40639	Inverter frequency	Wechselrichter frequenz	Hz	uint16be	1	0,01	0		level		true	false	false	false
                  40641	UPS load-side phase power A	USV-lastseitige Phasenleistung L1	W	uint16be	1	1	0		level		true	false	false	false
                  40642	UPS load-side phase power B	USV-lastseitige Phasenleistung L2	W	uint16be	1	1	0		level		true	false	false	false
                  40643	UPS load-side phase power C	USV-lastseitige Phasenleistung L3	W	uint16be	1	1	0		level		true	false	false	false
                  40644	UPS load-sidetotal power	Lastseitige Gesamtleistung der USV	W	uint16be	1	1	0		level		true	false	false	false
                  40645	Load phase voltage A	Load phasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                  40646	Load phase voltage B	Load phasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                  40647	Load phase voltage C	Load phasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                  40648	Load phase current A	Load phasenstrom L1	A	uint16be	1	0,01	0		level		true	false	false	false
                  40649	Load phase current B	Load phasenstrom L2	A	uint16be	1	0,01	0		level		true	false	false	false
                  40650	Load phase current C	Load phasenstrom L3	A	uint16be	1	0,01	0		level		true	false	false	false
                  40651	Load phase power A	Load phase Leistung L1	W	uint16be	1	1	0		level		true	false	false	false
                  40652	Load phase power B	Load phase Leistung L2	W	uint16be	1	1	0		level		true	false	false	false
                  40653	Load phase power C	Load phase Leistung L3	W	uint16be	1	1	0		level		true	false	false	false
                  40654	Load totalpower	Load Gesamtleistung	W	uint16be	1	1	0		level		true	false	false	false
                  40655	Load phase apparent power	Scheinleistung der Lastphase	VA	uint16be	1	1	0		level		true	false	false	false
                  40656	Load frequency	Load Frequenz	Hz	uint16be	1	1	0		level		true	false	false	false
                  40662	Phase voltage of Gen port A	Phasenspannung von Gen-Port L1	V	uint16be	1	0,1	0		level		true	false	false	false
                  40663	Phase voltage of Gen port B	Phasenspannung von Gen-Port L2	V	uint16be	1	0,1	0		level		true	false	false	false
                  40664	Phase voltage of Gen port C	Phasenspannung von Gen-Port L3	V	uint16be	1	0,1	0		level		true	false	false	false
                  40665	Phase power of Gen port A	Phasenleistung von Gen-Port L1	W	uint16be	1	1	0		level		true	false	false	false
                  40666	Phase power of Gen port B	Phasenleistung von Gen-Port L2	W	uint16be	1	1	0		level		true	false	false	false
                  40667	Phase power of Gen port C	Phasenleistung von Gen-Port L3	W	uint16be	1	1	0		level		true	false	false	false
                  40668	total power of Gen port	Gesamtleistung des Gen-Ports	W	uint16be	1	1	0		level		true	false	false	false
                  40673	PV1 input power	PV1 Eingangsleistung	W	uint16be	1	1	0		level		true	false	false	false
                  40674	PV2 input power	PV2 Eingangsleistung	W	uint16be	1	1	0		level		true	false	false	false
                  40677	Dc voltage 1	Gleichspannung 1	V	uint16be	1	0,1	0		level		true	false	false	false
                  40678	Dc current 1	Gleichstrom 1	A	uint16be	1	0,1	0		level		true	false	false	false
                  40679	Dc voltage 2	Gleichspannung 2	V	uint16be	1	0,1	0		level		true	false	false	false
                  40680	Dc current 2	Gleichstrom 2	A	uint16be	1	0,1	0		level		true	false	false	false
                  
                  W 1 Reply Last reply Reply Quote 0
                  • W
                    warp735 @wendy2702 last edited by

                    @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                    man muss dann nur den Haken bei "Benutze Aliase" setzen

                    Das war schon immer so 😉

                    Wenn die Register bei dir so funktionieren, ist ja in Ordnung. Ich habs wie gesagt anders eingestellt.

                    wendy2702 1 Reply Last reply Reply Quote 0
                    • wendy2702
                      wendy2702 @warp735 last edited by

                      @warp735 Gerade mal über längere Zeit beobachtet. Da kommen schonmal merkwürdige Werte raus.

                      Kannst du mal bitte einen Export deiner Register einstellen?

                      W 1 Reply Last reply Reply Quote 0
                      • W
                        warp735 @wendy2702 last edited by

                        @wendy2702
                        Ausnahmslos alle Werte so:

                        Snag_13f8b67.png

                        wendy2702 1 Reply Last reply Reply Quote 0
                        • wendy2702
                          wendy2702 @warp735 last edited by

                          @warp735 Hm,

                          das hilft bei der Frage nach einem Export der Register leider nicht weiter.

                          W 1 Reply Last reply Reply Quote 0
                          • W
                            warp735 @wendy2702 last edited by

                            @wendy2702
                            Dann stell halt schnell selbst um. Bin am Handy und gibt kein Export

                            wendy2702 1 Reply Last reply Reply Quote 0
                            • wendy2702
                              wendy2702 @warp735 last edited by

                              @warp735 Mir wäre es eher um den Vergleich gegangen welche Register du nutzt und was alles in der Liste steht die ich importiert habe.

                              Das du am Handy bist kann ich ja nicht wissen.

                              W 1 Reply Last reply Reply Quote 0
                              • W
                                warp735 @wendy2702 last edited by

                                @wendy2702
                                Glaub das Register pdf hab ich hier auch mal reingestellt. Da kannst dir ja das was du benötigst raussuchen.

                                wendy2702 1 Reply Last reply Reply Quote 0
                                • wendy2702
                                  wendy2702 @warp735 last edited by

                                  @warp735 OK. Muss ich mal suchen.

                                  Habe aktuell dieses Merkwürdige Verhalten nachdem ich alles umgestellt habe:

                                  5aacb763-4db9-4c3f-a8c2-17b7924b47e0-E0C990AE-DF3E-4A05-9F92-93602C49858B.GIF

                                  W W 2 Replies Last reply Reply Quote 0
                                  • W
                                    warp735 @wendy2702 last edited by warp735

                                    @wendy2702
                                    Um Himmels Willen, was hast denn da für nen Intervall? Bist überhaupt noch über der Polltime?
                                    Aber wenn der wert sich nicht ändert ist das so..

                                    1 Reply Last reply Reply Quote 0
                                    • W
                                      Waly_de @wendy2702 last edited by

                                      @wendy2702

                                      _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                                      40001	1	Device type	Gerätetyp		uint16be	1	0	0		level		true	false	false	false
                                      40002	1	ModbusAdress	ModbusAdress		uint16be	1	0	0		level		true	false	false	false
                                      40003	1	ComProtVersion	ComProtVersion		uint16be	1	0	0		level		true	false	false	false
                                      40004	1	Seriennummer	Seriennummer		string	5	0	0		state		true	false	false	false
                                      40012	1	AssistProgVersion	AssistProgVersion		uint16be	1	0	0		level		true	false	false	false
                                      40015	1	ControlPanelFirmware-2	ControlPanelFirmware-1		uint16be	1	0	0		level		true	false	false	false
                                      40016	1	ControlPanelFirmware-master	ControlPanelFirmware-master		uint16be	1	0	0		level		true	false	false	false
                                      40017	1	CommPanelFirmware-1	CommPanelFirmware0		uint16be	1	0	0		level		true	false	false	false
                                      40018	1	CommPanelFirmware-2	CommPanelFirmware-1		uint16be	1	0	0		level		true	false	false	false
                                      40019	1	CommPanelFirmware-master	CommPanelFirmware-master		uint16be	1	0	0		level		true	false	false	false
                                      40061	1	Fernsperre	Fernsperre		uint16be	1	0	0		level		true	false	false	false
                                      40081	1	SchalterModus	SchalterModus		uint16be	1	0	0		level		true	false	false	false
                                      40105	1	ZeroExport power	ZeroExport-Leistung	W	int16be	1	0	0		level		true	false	false	false
                                      40106	1	EqualizationDayCycle	EqualizationDayCycle	Day	int16be	1	0	0		level		true	false	false	false
                                      40107	1	EqualizationTime	EqualizationTime	0.5h	int16be	1	0	0		level		true	false	false	false
                                      40108	1	TEMPCO	TEMPCO	mV/C	int16be	1	0	0		level		true	false	false	false
                                      40109	1	Max A Charge	Maximaler Ladestrom der Batterie	A	int16be	1	0	0		level		true	false	false	false
                                      40110	1	Max A discharge	Max A Entladung	A	int16be	1	0	0		level		true	false	false	false
                                      40112	1	BatOpMode	battery operates according to voltage or capacity 		int16be	1	0	0		level		true	false	false	false
                                      40113	1	BatWakeBit	Lithium battery wake up sign bit 		int16be	1	0	0		level		true	false	false	false
                                      40114	1	BatResistVal	battery resistance value 	mOhm	int16be	1	0	0		level		true	false	false	false
                                      40115	1	BatChargeEfficiency	Battery charging efficiency	0.1%	int16be	1	0	0		level		true	false	false	false
                                      40116	1	BatCapacityShutDown	battery capacity ShutDown	%	int16be	1	0	0		level		true	false	false	false
                                      40117	1	BatCapacityRestart	battery capacity Restart	%	int16be	1	0	0		level		true	false	false	false
                                      40118	1	BatCapacityLowBatt	battery capacityLowBatt	%	int16be	1	0	0		level		true	false	false	false
                                      40119	1	BatVoltageShutDown	battery voltageShutDown	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40120	1	BatVoltageRestart	battery voltage Restart	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40121	1	BatVoltageLowBatt	battery voltageLowBatt	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40122	1	Max-Gen-Time	Max-Gen-Time	h	int16be	1	0,1	0		level		true	false	false	false
                                      40123	1	Gen-Cool-Time	Gen-Cool-Time	h	int16be	1	0,1	0		level		true	false	false	false
                                      40124	1	Gen-Start-Volt	Gen-Start-Volt	V	int16be	1	0,01	0		level		true	false	false	false
                                      40125	1	Gen-Start-Proz	Gen-Start-Proz	%	int16be	1	0	0		level		true	false	false	false
                                      40126	1	Gen-Charge-Current	Gen-Charge-Current	A	int16be	1	0	0		level		true	false	false	false
                                      40127	1	Grid-Start-Volt	Grid-Start-Volt	V	int16be	1	0,01	0		level		true	false	false	false
                                      40128	1	Grid-Start-Proz	Grid-Start-Proz	%	int16be	1	0	0		level		true	false	false	false
                                      40129	1	Grid-Charge-Current	Grid-Charge-Current	A	int16be	1	0	0		level		true	false	false	false
                                      40130	1	Gen-Charge-Enable	Gen-Charge-Enable		uint16be	1	0	0		level		true	false	false	false
                                      40131	1	Grid-Charge-Enable	Grid-Charge-Enable		uint16be	1	0	0		level		true	false	false	false
                                      40132	1	AC-Frequency-Cap	AC couplefrequency cap setting		int16be	1	0	0		level		true	false	false	false
                                      40133	1	Force-On-Generator-As-Load	Force on generator as load function		int16be	1	0	0		level		true	false	false	false
                                      40134	1	Generator-Input-Is-Load-Output	generator input is enabled as the load output		int16be	1	0	0		level		true	false	false	false
                                      40135	1	SmartLoadOffBattVoltage	SmartLoad OFF batt Voltage	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40136	1	SmartLoadOffBattProz	SmartLoad OFF batt Proz	%	int16be	1	0	0		level		true	false	false	false
                                      40137	1	SmartLoadOnBattVoltage	SmartLoad ON batt Voltage	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40138	1	SmartLoadOnBattProz	SmartLoad ON batt Proz	%	int16be	1	0	0		level		true	false	false	false
                                      40139	1	OutputVoltageLevel	"0 express220V means 220V
1 express230V means 230V
                                      2 express240V means 240V
                                      3 express120V means 120V
                                      4 133VAC"		int16be	1	0	0		level		true	false	false	false
                                      40140	1	MinPvStartGen	minimum solar power required to start a generator	W	int16be	1	0	0		level		true	false	false	false
                                      40141	1	Gen_Grid_Signal On			int16be	1	0	0		level		true	false	false	false
                                      40142	1	EnergyManagementMode	"Bit0-1 Indicates the passive grid-connected power balance function
                                      10 battery first mode
                                      11 load first mode
                                      Bit2-3 Represents passive grid-connected power balance function
                                      10 not open / colse
                                      11 turn on / open
                                      Bit4-5 Represents active grid-connection power balance function
                                      10 not open /close 
                                      11 turn on / open"	Bits	int16be	1	0	0		level		true	false	false	false
                                      40143	1	LimitControlFunction	"0x00 sell electricity enabled
                                      0x01 built-in enabled 
                                      0x02 extraposition enabled"		int16be	1	0	0		level		true	false	false	false
                                      40144	1	MaxLimitPowerOutputGridConnection	Begrenzen Sie die maximale Ausgangsleistung des Netzes	W	int16be	1	0	0		level		true	false	false	false
                                      40145	1	ExternalCurrentSensorClampPhase	Klemmphase des externen Stromsensors	W	int16be	1	0	0		level		true	false	false	false
                                      40146	1	SolarSell	Verkauf von Solar		uint8be	1	0	0		value		true	false	false	false
                                      40147	1	TOUBits	TOUBits	Bits	uint8be	1	0	0		value		true	false	false	false
                                      40149	1	Sell mode time point 1	Sell mode time point 1		int16be	1	0	0		level		true	false	false	false
                                      40150	1	Sell mode time point 2	Sell mode time point 2		int16be	1	0	0		level		true	false	false	false
                                      40151	1	Sell mode time point 3	Sell mode time point 3		int16be	1	0	0		level		true	false	false	false
                                      40152	1	Sell mode time point 4	Sell mode time point 4		int16be	1	0	0		level		true	false	false	false
                                      40153	1	Sell mode time point 5	Sell mode time point 5		int16be	1	0	0		level		true	false	false	false
                                      40154	1	Sell mode time point 6	Sell mode time point 6		int16be	1	0	0		level		true	false	false	false
                                      40155	1	BatMaxPower1	BatMaxPower1	W	int16be	1	0	0		level		true	false	false	false
                                      40156	1	BatMaxPower2	BatMaxPower2	W	int16be	1	0	0		level		true	false	false	false
                                      40157	1	BatMaxPower3	BatMaxPower3	W	int16be	1	0	0		level		true	false	false	false
                                      40158	1	BatMaxPower4	BatMaxPower4	W	int16be	1	0	0		level		true	false	false	false
                                      40159	1	BatMaxPower5	BatMaxPower5	W	int16be	1	0	0		level		true	false	false	false
                                      40160	1	BatMaxPower6	BatMaxPower6	W	int16be	1	0	0		level		true	false	false	false
                                      40161	1	BatVolt1	BatVolt1	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40162	1	BatVolt2	BatVolt2	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40163	1	BatVolt3	BatVolt3	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40164	1	BatVolt4	BatVolt4	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40165	1	BatVolt5	BatVolt5	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40166	1	BatVolt6	BatVolt6	0.01V	int16be	1	0	0		level		true	false	false	false
                                      40167	1	BatProz1	BatProz1	%	int16be	1	0	0		level		true	false	false	false
                                      40168	1	BatProz2	BatProz2	%	int16be	1	0	0		level		true	false	false	false
                                      40169	1	BatProz3	BatProz3	%	int16be	1	0	0		level		true	false	false	false
                                      40170	1	BatProz4	BatProz4	%	int16be	1	0	0		level		true	false	false	false
                                      40171	1	BatProz5	BatProz5	%	int16be	1	0	0		level		true	false	false	false
                                      40172	1	BatProz6	BatProz6	%	int16be	1	0	0		level		true	false	false	false
                                      40173	1	GridGenEn1	GridGenEn1	Bits	int16be	1	0	0		level		true	false	false	false
                                      40174	1	GridGenEn2	GridGenEn2	Bits	int16be	1	0	0		level		true	false	false	false
                                      40175	1	GridGenEn3	GridGenEn3	Bits	int16be	1	0	0		level		true	false	false	false
                                      40176	1	GridGenEn4	GridGenEn4	Bits	int16be	1	0	0		level		true	false	false	false
                                      40177	1	GridGenEn5	GridGenEn5	Bits	int16be	1	0	0		level		true	false	false	false
                                      40178	1	GridGenEn6	GridGenEn6	Bits	int16be	1	0	0		level		true	false	false	false
                                      40341	1	Max Solar Sell Power at Zero grid	Maximale Solarverkaufsleistung bei null einspeisung	W	int16be	1	0	0		level		true	false	false	false
                                      40341	1	Max Solar Sell Power by full in	Maximale Solarverkaufsleistung bei einspeisung	W	int16be	1	0	0		level		true	false	false	false
                                      40501	1	Status	Status (Standby, check, norm, altert, fault)		int16be	1	0	0		level		true	false	false	false
                                      40502	1	active power generation of today	active power generation of today	kwh	int16be	1	0,1	0		level		true	false	false	false
                                      40503	1	reactive power generation of today	reactive power generation of today	kwh	int16be	1	0,1	0		level		true	false	false	false
                                      40504	1	Grid connection time of today	Grid connection time of today	s	uint16be	1	1	0		level		true	false	false	false
                                      40515	1	Today charge of the battery 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40516	1	Today discharge of the battery 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40517	1	Total charge of the battery low byte 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40518	1	Total charge of the battery high byte	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40519	1	Total discharge of the battery low byte 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40520	1	Total discharge of the battery high byte	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40521	1	Day Grid Buy Power kWh	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40522	1	Day_GridSell_Power kWh	Tages Verkaufs leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40523	1	Total_GridBuy_Power kWh_low word	Total_GridBuy_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40524	1	Total_GridBuy_Power kWh_high word	Total_GridBuy_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40525	1	Total_GridSell_Power kWh_low word	Total_GridSell_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40526	1	Total_GridSell_Power kWh_high word	Total_GridSell_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40527	1	Day_Load_Power kWH	Day_Load_Power kWH	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40528	1	Total_Load_Power kWh_low word	Total_Load_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40529	1	Total_Load_Power kWh_high word	Total_Load_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40530	1	Day_PV_Power kWh	Tagesproduzierte leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40531	1	Day_PV-1_Power kWh	Day_PV-1_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40532	1	Day_PV-2_Power kWh	Day_PV-2_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40533	1	Day_PV-3_Power kWh	Day_PV-3_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40534	1	Day_PV-4_Power kWh	Day_PV-4_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40535	1	Total PV power Wh low word	Gesamt-PV-Leistung Wh niedriges Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40536	1	Total PV power Wh high word	Gesamt-PV-Leistung Wh hohes Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                      40554	1	Warning message word 1	Warning message word 1		uint16be	1	1	0		level		true	false	false	false
                                      40555	1	Warning message word 2	Warning message word 2		uint16be	1	1	0		level		true	false	false	false
                                      40556	1	Fault information word 1	Fault information word 1		uint16be	1	1	0		level		true	false	false	false
                                      40557	1	Fault information word 2	Fault information word 2		uint16be	1	1	0		level		true	false	false	false
                                      40558	1	Fault information word 3	Fault information word 3		uint16be	1	1	0		level		true	false	false	false
                                      40559	1	Fault information word 4	Fault information word 4		uint16be	1	1	0		level		true	false	false	false
                                      40587	1	battery temperature	Batterietemperatur	°C	int16be	1	0,01	10		level		true	false	false	false
                                      40588	1	battery voltage	Batteriespannung	V	int16be	1	0,01	0		level		true	false	false	false
                                      40589	1	battery capacity	Batteriekapazität	%	int16be	1	1	0		level		true	false	false	false
                                      40591	1	Battery output power	Ausgangsleistung der Batterie	W	int16be	1	1	0		level		true	false	false	false
                                      40592	1	Battery output current	Ausgangsstrom der Batterie	A	int16be	1	0,01	0		level		true	false	false	false
                                      40593	1	Corrected AH	AH korrigiert	AH	int16be	1	1	0		level		true	false	false	false
                                      40599	1	Grid phase voltage A	Netzphasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
                                      40600	1	Grid phase voltage B	Netzphasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
                                      40601	1	Grid phase voltage C	Netzphasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
                                      40602	1	Grid line voltage AB	Netzphasenspannung L1-L2	V	int16be	1	0,1	0		level		true	false	false	false
                                      40603	1	Grid line voltage BC	Netzphasenspannung L2-L3	V	int16be	1	0,1	0		level		true	false	false	false
                                      40604	1	Grid line voltage CA	Netzphasenspannung L3-L1	V	int16be	1	0,1	0		level		true	false	false	false
                                      40605	1	L1 phase power on the inner side of the grid	L1 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                      40606	1	L2 phase power on the inner side of the grid	L2 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                      40607	1	L3 phase power on the inner side of the grid	L3 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                      40608	1	active power from side to side of the grid	Wirkleistung von Seite zu Seite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                      40609	1	Grid side - inside total apparent power	Netzseite – innere Gesamtscheinleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40610	1	Grid-side frequency	Grid Seite Frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
                                      40611	1	grid side inner current L1	netzseitiger Innenstrom L1	A	int16be	1	0,01	0		level		true	false	false	false
                                      40612	1	grid side inner current L2	netzseitiger Innenstrom L2	A	int16be	1	0,01	0		level		true	false	false	false
                                      40613	1	grid side inner current L3	netzseitiger Innenstrom L3	A	int16be	1	0,01	0		level		true	false	false	false
                                      40614	1	Out-of-grid - current L1	Außerhalb des Netzes – aktuelles L1	A	int16be	1	0,01	0		level		true	false	false	false
                                      40615	1	Out-of-grid - current L2	Außerhalb des Netzes – aktuelles L2	A	int16be	1	0,01	0		level		true	false	false	false
                                      40616	1	Out-of-grid - current L3	Außerhalb des Netzes – aktuelles L3	A	int16be	1	0,01	0		level		true	false	false	false
                                      40617	1	A Out-of-grid -power L1	A Außerhalb des Netzes - Strom L1	W	int16be	1	1	0		level		true	false	false	false
                                      40618	1	A Out-of-grid -power L2	A Außerhalb des Netzes - Strom L2	W	int16be	1	1	0		level		true	false	false	false
                                      40619	1	A Out-of-grid -power L3	A Außerhalb des Netzes - Strom L3	W	int16be	1	1	0		level		true	false	false	false
                                      40620	1	Out-of-grid-total-power	Außerhalb des Netzes - Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40621	1	Out-of-grid-total-apparent-power	Außerhalb des Netzes - Gesamtscheinleistung	VA	uint16le	1	1	0		level		true	false	false	false
                                      40622	1	Grid-connected power factor PF	Netzgekoppelter Leistungsfaktor PF		int16be	1	1	0		level		true	false	false	false
                                      40623	1	Grid side A-phase power	Netzseitiger L1-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
                                      40624	1	Grid side B-phase power	Netzseitiger L2-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
                                      40625	1	Grid side C-phase power	Netzseitiger L3-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
                                      40626	1	Grid side total power	Netzseitige Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40628	1	Inverter output phase voltage A	Wechselrichter-Ausgangsphasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
                                      40629	1	Inverter output phase voltage B	Wechselrichter-Ausgangsphasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
                                      40630	1	Inverter output phase voltage C	Wechselrichter-Ausgangsphasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
                                      40631	1	Inverter output phase current A	Ausgangsphasenstrom des Wechselrichters L1	A	int16be	1	0,01	0		level		true	false	false	false
                                      40632	1	Inverter output phase current B	Ausgangsphasenstrom des Wechselrichters L2	A	int16be	1	0,01	0		level		true	false	false	false
                                      40633	1	Inverter output phase current C	Ausgangsphasenstrom des Wechselrichters L3	A	int16be	1	0,01	0		level		true	false	false	false
                                      40634	1	Inverter output phase power A	Ausgangsphase des Wechselrichters Macht L1	W	int16be	1	1	0		level		true	false	false	false
                                      40635	1	Inverter output phase power B	Ausgangsphase des Wechselrichters Macht L2	W	int16be	1	1	0		level		true	false	false	false
                                      40636	1	Inverter output phase power C	Ausgangsphase des Wechselrichters Leistung L3	W	int16be	1	1	0		level		true	false	false	false
                                      40637	1	Inverter output total power	Gesamtleistung des Wechselrichters Leistung	W	int16be	1	1	0		level		true	false	false	false
                                      40638	1	Inverter output total apparent power	Gesamtleistung des Wechselrichters Scheinleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40639	1	Inverter frequency	Wechselrichter frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
                                      40641	1	UPS load-side phase power A	USV-lastseitige Phasenleistung L1	W	int16be	1	1	0		level		true	false	false	false
                                      40642	1	UPS load-side phase power B	USV-lastseitige Phasenleistung L2	W	int16be	1	1	0		level		true	false	false	false
                                      40643	1	UPS load-side phase power C	USV-lastseitige Phasenleistung L3	W	int16be	1	1	0		level		true	false	false	false
                                      40644	1	UPS load-sidetotal power	Lastseitige Gesamtleistung der USV	W	int16be	1	1	0		level		true	false	false	false
                                      40645	1	Load phase voltage A	Load phasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
                                      40646	1	Load phase voltage B	Load phasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
                                      40647	1	Load phase voltage C	Load phasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
                                      40648	1	Load phase current A	Load phasenstrom L1	A	int16be	1	0,01	0		level		true	false	false	false
                                      40649	1	Load phase current B	Load phasenstrom L2	A	int16be	1	0,01	0		level		true	false	false	false
                                      40650	1	Load phase current C	Load phasenstrom L3	A	int16be	1	0,01	0		level		true	false	false	false
                                      40651	1	Load phase power A	Load phase Leistung L1	W	int16be	1	1	0		level		true	false	false	false
                                      40652	1	Load phase power B	Load phase Leistung L2	W	int16be	1	1	0		level		true	false	false	false
                                      40653	1	Load phase power C	Load phase Leistung L3	W	int16be	1	1	0		level		true	false	false	false
                                      40654	1	Load totalpower	Load Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40655	1	Load phase apparent power	Scheinleistung der Lastphase	VA	int16be	1	1	0		level		true	false	false	false
                                      40656	1	Load frequency	Load Frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
                                      40662	1	Phase voltage of Gen port A	Phasenspannung von Gen-Port L1	V	int16be	1	0,1	0		level		true	false	false	false
                                      40663	1	Phase voltage of Gen port B	Phasenspannung von Gen-Port L2	V	int16be	1	0,1	0		level		true	false	false	false
                                      40664	1	Phase voltage of Gen port C	Phasenspannung von Gen-Port L3	V	int16be	1	0,1	0		level		true	false	false	false
                                      40665	1	Phase power of Gen port A	Phasenleistung von Gen-Port L1	W	int16be	1	1	0		level		true	false	false	false
                                      40666	1	Phase power of Gen port B	Phasenleistung von Gen-Port L2	W	int16be	1	1	0		level		true	false	false	false
                                      40667	1	Phase power of Gen port C	Phasenleistung von Gen-Port L3	W	int16be	1	1	0		level		true	false	false	false
                                      40668	1	total power of Gen port	Gesamtleistung des Gen-Ports	W	int16be	1	1	0		level		true	false	false	false
                                      40673	1	PV1 input power	PV1 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40674	1	PV2 input power	PV2 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40675	1	PV3 input power	PV3 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40676	1	PV4 input power	PV4 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
                                      40677	1	Dc voltage 1	Gleichspannung 1	V	int16be	1	0,1	0		level		true	false	false	false
                                      40678	1	Dc current 1	Gleichstrom 1	A	int16be	1	0,1	0		level		true	false	false	false
                                      40679	1	Dc voltage 2	Gleichspannung 2	V	int16be	1	0,1	0		level		true	false	false	false
                                      40680	1	Dc current 2	Gleichstrom 2	A	int16be	1	0,1	0		level		true	false	false	false
                                      40681	1	Dc voltage 3	Gleichspannung 3	V	int16be	1	0,1	0		level		true	false	false	false
                                      40682	1	Dc current 3	Gleichstrom 3	A	int16be	1	0,1	0		level		true	false	false	false
                                      40683	1	Dc voltage 4	Gleichspannung 4	V	int16be	1	0,1	0		level		true	false	false	false
                                      40684	1	Dc current 4	Gleichstrom 4	A	int16be	1	0,1	0		level		true	false	false	false
                                      
                                      

                                      hier mal mein Export... vielleicht hilft es ja 🙂

                                      wendy2702 W 2 Replies Last reply Reply Quote 0
                                      • wendy2702
                                        wendy2702 @Waly_de last edited by

                                        @waly_de Danke. Werde ich testen.

                                        Welches Abfrage Intervall nutzt ihr denn so?

                                        Alleine hier in dem Thread findet man mindestens 4 Verschiedene.

                                        Hatte den default mit 1sek, jetzt mal auf 5 gestellt.

                                        1 Reply Last reply Reply Quote 0
                                        • W
                                          warp735 @Waly_de last edited by warp735

                                          @wendy2702
                                          Was sollen den sekündliche Werte bringen? Ich hatte zum testen 15s und im Normalbetrieb 30s. Alles andere ist in meinen Augen "Wahnsinn"

                                          W wendy2702 2 Replies Last reply Reply Quote 0
                                          • W
                                            Waly_de @warp735 last edited by

                                            @warp735 tut mir leid, ich hab im Moment wenig Zeit wenn du etwas von mir möchtest, dann wiederhol doch bitte die Frage noch einmal

                                            1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            852
                                            Online

                                            31.9k
                                            Users

                                            80.2k
                                            Topics

                                            1.3m
                                            Posts

                                            26
                                            229
                                            44183
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo