      shipper @etzeste13 last edited by

      @etzeste13

      ok, wert setzen in den Objekten funktioniert, nachdem ich WP rausgenommen habe, dann wird's auch mit Skript gehen

      danke

      S 1 Reply Last reply Reply Quote 0
      • S
        shipper @shipper last edited by

        @etzeste13
        du hast mich gerettet. Wenn ich die Werte in den Objekten setze, werden die register erfolgreich beschrieben. Wenn ich in blockly die Funktion "aktualisiere Object " nehme dann nicht. Mit "steuere object" geht es dann.
        Da konnte ich lange suchen, nichts gefunden, weil sonst nichts zu finden war.

        E 1 Reply Last reply Reply Quote 1
        • E
          etzeste13 @shipper last edited by

          @shipper freut mich das es funktioniert und ich mal wem helfen konnte....:-)
          vG

          1 Reply Last reply Reply Quote 0
          • miael
            miael last edited by

            Hallo,
            kann mir einer sagen was ich da im Register eintragen muss um eine vernünftige Temperatur zu bekommmen?
            Unbenannt.JPG

            Danke
            michael

            W 1 Reply Last reply Reply Quote 0
            • W
              warp735 @miael last edited by

              @miael
              AC ist Faktor 0,1 und bei Offset -100. Dann hast den richtigen Wert. Beim DC Wert genau so, bekommst aber nur Daten wenn nen DC Batt Tempfühler angeschlossen hast. Sonst steht der immer auf 25°

              Schreiben geht bei mir übrigens problemlos.

              miael 1 Reply Last reply Reply Quote 0
              • miael
                miael @warp735 last edited by

                @warp735
                Besten dank!
                Der Hinweis mit den 25°C war es. Bin jetzt auf "Heat sink temperatur" gewechselt und funktioniert.

                W 1 Reply Last reply Reply Quote 0
                • W
                  warp735 @miael last edited by

                  @miael
                  Ja, das ist AC, bzw die interne WR Temp, nach der er selbst auch regelt

                  1 Reply Last reply Reply Quote 0
                  • W
                    warp735 last edited by warp735

                    Weiß jemand wie die "Tägliche Erzeugung" gerechnet wird? Ist da der Micro inkludiert oder nicht? Bei der oberen prozentualen Anzeige "Produktion" interessiert er auf jedenfall nicht. Bei diesem Beispiel müssten es ja 55% sein und nicht 41%

                    Find nämlich auch kein Register für die kwh vom Microinverter 😞

                    Snag_44ef76.png

                    1 Reply Last reply Reply Quote 0
                    • R
                      Ronny81 last edited by

                      Servus zusammen,

                      ich bin neu hier und hoffe ihr könnt mir helfen.
                      Ich muss ganz dringen ein Register am Deye setzen und zwar die ID bzw. Seriennummer.
                      Leider hat mein Deye nach dem letzten Firmware Update seine ID verloren.
                      Ich habe es schon über die RS232 versucht, aber der WR will nicht antworten.
                      Kann man die ID über die RS485 ändern?
                      Die ID müsste die Register 3,4,5,6 und 7 haben.
                      Register 7, ID(SN), Stelle 2 + 1 ASCII
                      Register 6, ID(SN), Stelle 4 + 3 ASCII
                      Register 5, ID(SN), Stelle 6 + 5 ASCII
                      Register 4, ID(SN), Stelle 8 + 7 ASCII
                      Register 3, ID(SN), Stelle 10 + 9 ASCII
                      Ich hoffe Ihr könnt mir helfen. Danke schon mal.
                      Anbei noch ein Foto des Display ohne ID.

                      Gruß Ronny

                      20240406_174924.jpg 20240407_155125.jpg

                      1 Reply Last reply Reply Quote 0
                      • wendy2702
                        wendy2702 last edited by

                        Hi,

                        ich schaffe es aktuell nicht meinen Deye SUN-12K-SG04LP3-EU pe Waveshare auszulesen.

                        ich verwende diesen Waveshare:

                        15a56c0a-df08-4f36-b038-41bcf06e6805-grafik.png

                        mit diesen Einstellungen:

                        ad83f715-b7d6-4abb-adb5-613b814a6e75-grafik.png

                        636dd362-e0c0-47b0-98c1-4b4ca03fc7ec-grafik.png

                        Wenn ich mit CAS Modbus Scanner per USB RS485 Adapter einen Test mache funktioniert die Verbindung:

                        50611fe6-b361-4ec5-b918-04fb5d121f7e-grafik.png :

                        Und mit Modbus Poll kann ich register auslesen.

                        Iob ist so konfiguriert:

                        49401faa-1116-48a2-8c29-861e6cc774ba-grafik.png

                        Register aus dem Github Modbus Template von @TheBam

                        9f3695a3-2a67-4fd6-baea-7a6977a7ea52-grafik.png

                        Debug log hilft mir aktuell nicht weiter: (Gekürzt wegen Payload.)

                        2024-05-24 10:49:09.547  - info: host.iobroker "system.adapter.modbus.4" enabled
                        2024-05-24 10:49:10.972  - info: host.iobroker instance system.adapter.modbus.4 started with pid 213280
                        2024-05-24 10:49:12.811  - debug: modbus.4 (213280) Redis Objects: Use Redis connection: 0.0.0.0:9001
                        2024-05-24 10:49:12.924  - debug: modbus.4 (213280) Objects client ready ... initialize now
                        2024-05-24 10:49:13.001  - debug: modbus.4 (213280) Objects create System PubSub Client
                        2024-05-24 10:49:13.002  - debug: modbus.4 (213280) Objects create User PubSub Client
                        2024-05-24 10:49:13.308  - debug: modbus.4 (213280) Objects client initialize lua scripts
                        2024-05-24 10:49:13.332  - debug: modbus.4 (213280) Objects connected to redis: 0.0.0.0:9001
                        2024-05-24 10:49:13.551  - debug: modbus.4 (213280) Redis States: Use Redis connection: 0.0.0.0:9000
                        2024-05-24 10:49:13.669  - debug: modbus.4 (213280) States create System PubSub Client
                        2024-05-24 10:49:13.670  - debug: modbus.4 (213280) States create User PubSub Client
                        2024-05-24 10:49:13.848  - debug: modbus.4 (213280) States connected to redis: 0.0.0.0:9000
                        2024-05-24 10:49:14.085  - debug: modbus.4 (213280) Plugin sentry Do not initialize Plugin (enabled=false)
                        2024-05-24 10:49:14.141  - debug: modbus.4 (213280) Plugin sentry destroyed because not initialized correctly
                        2024-05-24 10:49:14.599  - info: modbus.4 (213280) starting. Version 6.2.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                        2024-05-24 10:49:15.614  - debug: modbus.4 (213280) Initialize Objects for disInputs: []
                        2024-05-24 10:49:15.616  - debug: modbus.4 (213280) Initialize Objects for coils: []
                        2024-05-24 10:49:15.617  - debug: modbus.4 (213280) Initialize Objects for inputRegs: []
                        2024-05-24 10:49:15.626  - debug: modbus.4 (213280) Initialize Objects for holdingRegs: [{"_address":40001,"name":"Device type","description":"Gerätetyp","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40001,"id":"holdingRegisters.40001_Device_type"},Gesamtscheinleistung","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40609,"id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power"},{"_address":40610,"name":"Grid-side frequency","description":"Grid Seite Frequenz","unit":"Hz","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40610,"id":"holdingRegisters.40610_Grid-side_frequency"},{"_address":40611,"name":"grid side inner current L1","description":"netzseitiger Innenstrom 1","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40678,"id":"holdingRegisters.40678_Dc_current_1"},{"_address":40679,"name":"Dc voltage 2","description":"Gleichspannung 2","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40679,"id":"holdingRegisters.40679_Dc_voltage_2"},{"_address":40680,"name":"Dc current 2","description":"Gleichstrom 2","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40680,"id":"holdingRegisters.40680_Dc_current_2"}]
                        2024-05-24 10:49:15.633  - debug: modbus.4 (213280) Add holdingRegisters.40001_Device_type: {"_id":"holdingRegisters.40001_Device_type","type":"state","common":{"name":"Gerätetyp","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40001,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.636  - debug: modbus.4 (213280) Add holdingRegisters.40004_Seriennummer: {"_id":"holdingRegisters.40004_Seriennummer","type":"state","common":{"name":"Seriennummer","role":"state","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":40004,"deviceId":4,"type":"string","len":5,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.637  - debug: modbus.4 (213280) Add holdingRegisters.40061_Fernsperre: {"_id":"holdingRegisters.40061_Fernsperre","type":"state","common":{"name":"Fernsperre","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40061,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40081_SchalterModus: {"_id":"holdingRegisters.40081_SchalterModus","type":"state","common":{"name":"SchalterModus","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40081,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.639  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40109_Max_A_Charge: {"_id":"holdingRegisters.40109_Max_A_Charge","type":"state","common":{"name":"Maximaler Ladestrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40109,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40110_Max_A_discharge: {"_id":"holdingRegisters.40110_Max_A_discharge","type":"state","common":{"name":"Max A Entladung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40110,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40116_ShutDown_battery_capacity_ShutDown: {"_id":"holdingRegisters.40116_ShutDown_battery_capacity_ShutDown","type":"state","common":{"name":"Abschalten Batteriekapazität Herunterfahren","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40116,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40117_Restart_battery_capacityRestart: {"_id":"holdingRegisters.40117_Restart_battery_capacityRestart","type":"state","common":{"name":"Neu starten BatteriekapazitätNeustart","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40117,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40118_LowBatt_battery_capacityLowBatt: {"_id":"holdingRegisters.40118_LowBatt_battery_capacityLowBatt","type":"state","common":{"name":"Low Batterie Anzeige zum Abschalten der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40118,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40130_Generator_is_charged_to_enable: {"_id":"holdingRegisters.40130_Generator_is_charged_to_enable","type":"state","common":{"name":"Generator is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40130,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40131_Grid_is_charged_to_enable: {"_id":"holdingRegisters.40131_Grid_is_charged_to_enable","type":"state","common":{"name":"Grid is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40131,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection: {"_id":"holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection","type":"state","common":{"name":"Begrenzen Sie die maximale Ausgangsleistung des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40144,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40145_External_current_sensor_clamp_phase: {"_id":"holdingRegisters.40145_External_current_sensor_clamp_phase","type":"state","common":{"name":"Klemmphase des externen Stromsensors","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40145,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40146_Solar_sell: {"_id":"holdingRegisters.40146_Solar_sell","type":"state","common":{"name":"  Verkauf von Solar","role":"switch","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40146,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40149_Sell_mode_time_point_1: {"_id":"holdingRegisters.40149_Sell_mode_time_point_1","type":"state","common":{"name":"Sell mode time point 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40149,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40150_Sell_mode_time_point_2: {"_id":"holdingRegisters.40150_Sell_mode_time_point_2","type":"state","common":{"name":"Sell mode time point 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40150,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40151_Sell_mode_time_point_3: {"_id":"holdingRegisters.40151_Sell_mode_time_point_3","type":"state","common":{"name":"Sell mode time point 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40151,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40152_Sell_mode_time_point_4: {"_id":"holdingRegisters.40152_Sell_mode_time_point_4","type":"state","common":{"name":"Sell mode time point 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40152,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40153_Sell_mode_time_point_5: {"_id":"holdingRegisters.40153_Sell_mode_time_point_5","type":"state","common":{"name":"Sell mode time point 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40153,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40154_Sell_mode_time_point_6: {"_id":"holdingRegisters.40154_Sell_mode_time_point_6","type":"state","common":{"name":"Sell mode time point 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40154,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40155_Sell_mode_Watt_time_1: {"_id":"holdingRegisters.40155_Sell_mode_Watt_time_1","type":"state","common":{"name":"Sell mode Watt time 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40155,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40156_Sell_mode_Watt_time_2: {"_id":"holdingRegisters.40156_Sell_mode_Watt_time_2","type":"state","common":{"name":"Sell mode Watt time 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40156,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40157_Sell_mode_Watt_time_3: {"_id":"holdingRegisters.40157_Sell_mode_Watt_time_3","type":"state","common":{"name":"Sell mode Watt time 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40157,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40158_Sell_mode_Watt_time_4: {"_id":"holdingRegisters.40158_Sell_mode_Watt_time_4","type":"state","common":{"name":"Sell mode Watt time 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40158,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40159_Sell_mode_Watt_time_5: {"_id":"holdingRegisters.40159_Sell_mode_Watt_time_5","type":"state","common":{"name":"Sell mode Watt time 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40159,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40160_Sell_mode_Watt_time_6: {"_id":"holdingRegisters.40160_Sell_mode_Watt_time_6","type":"state","common":{"name":"Sell mode Watt time 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40160,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40167_TOF_Cell_SOC_1: {"_id":"holdingRegisters.40167_TOF_Cell_SOC_1","type":"state","common":{"name":"TOF_Cell SOC 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40167,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40168_TOF_Cell_SOC_2: {"_id":"holdingRegisters.40168_TOF_Cell_SOC_2","type":"state","common":{"name":"TOF_Cell SOC 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40168,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40169_TOF_Cell_SOC_3: {"_id":"holdingRegisters.40169_TOF_Cell_SOC_3","type":"state","common":{"name":"TOF_Cell SOC 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40169,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40170_TOF_Cell_SOC_4: {"_id":"holdingRegisters.40170_TOF_Cell_SOC_4","type":"state","common":{"name":"TOF_Cell SOC 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40170,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40171_TOF_Cell_SOC_5: {"_id":"holdingRegisters.40171_TOF_Cell_SOC_5","type":"state","common":{"name":"TOF_Cell SOC 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40171,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40172_TOF_Cell_SOC_6: {"_id":"holdingRegisters.40172_TOF_Cell_SOC_6","type":"state","common":{"name":"TOF_Cell SOC 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40172,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40173_Time_point_1_charge_enable: {"_id":"holdingRegisters.40173_Time_point_1_charge_enable","type":"state","common":{"name":"Time point 1 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40173,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40174_Time_point_2_charge_enable: {"_id":"holdingRegisters.40174_Time_point_2_charge_enable","type":"state","common":{"name":"Time point 2 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40174,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40175_Time_point_3_charge_enable: {"_id":"holdingRegisters.40175_Time_point_3_charge_enable","type":"state","common":{"name":"Time point 3 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40175,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40176_Time_point_4_charge_enable: {"_id":"holdingRegisters.40176_Time_point_4_charge_enable","type":"state","common":{"name":"Time point 4 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40176,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40177_Time_point_5_charge_enable: {"_id":"holdingRegisters.40177_Time_point_5_charge_enable","type":"state","common":{"name":"Time point 5 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40177,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40178_Time_point_6_charge_enable: {"_id":"holdingRegisters.40178_Time_point_6_charge_enable","type":"state","common":{"name":"Time point 6 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40178,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei null einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40501_Status: {"_id":"holdingRegisters.40501_Status","type":"state","common":{"name":"Status (Standby, check, norm, altert, fault)","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40501,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40521_Day_Grid_Buy_Power_Wh: {"_id":"holdingRegisters.40521_Day_Grid_Buy_Power_Wh","type":"state","common":{"name":"Tag Netzabnahme Strom Wh","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40521,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40522_Day_GridSell_Power_Wh: {"_id":"holdingRegisters.40522_Day_GridSell_Power_Wh","type":"state","common":{"name":"Tages Verkaufs leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40522,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40530_Day_PV_Power_Wh: {"_id":"holdingRegisters.40530_Day_PV_Power_Wh","type":"state","common":{"name":"Tagesproduzierte leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40530,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40535_Total_PV_power_Wh_low_word: {"_id":"holdingRegisters.40535_Total_PV_power_Wh_low_word","type":"state","common":{"name":"Gesamt-PV-Leistung Wh niedriges Wort","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40535,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_AC_Relay: {"_id":"holdingRegisters.40553_AC_Relay","type":"state","common":{"name":"AC relay","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_Ac_relay_2: {"_id":"holdingRegisters.40553_Ac_relay_2","type":"state","common":{"name":"AC relay2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40587_battery_temperature: {"_id":"holdingRegisters.40587_battery_temperature","type":"state","common":{"name":"Batterietemperatur","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":40587,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40588_battery_voltage: {"_id":"holdingRegisters.40588_battery_voltage","type":"state","common":{"name":"Batteriespannung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40588,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40589_battery_capacity: {"_id":"holdingRegisters.40589_battery_capacity","type":"state","common":{"name":"Batteriekapazität","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40589,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40591_Battery_output_power: {"_id":"holdingRegisters.40591_Battery_output_power","type":"state","common":{"name":"Ausgangsleistung der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40591,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40592_Battery_output_current: {"_id":"holdingRegisters.40592_Battery_output_current","type":"state","common":{"name":"Ausgangsstrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40592,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40593_Corrected_AH: {"_id":"holdingRegisters.40593_Corrected_AH","type":"state","common":{"name":"AH korrigiert","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"AH"},"native":{"regType":"holdingRegs","address":40593,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40599_Grid_phase_voltage_A: {"_id":"holdingRegisters.40599_Grid_phase_voltage_A","type":"state","common":{"name":"Netzphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40599,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40600_Grid_phase_voltage_B: {"_id":"holdingRegisters.40600_Grid_phase_voltage_B","type":"state","common":{"name":"Netzphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40600,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40601_Grid_phase_voltage_C: {"_id":"holdingRegisters.40601_Grid_phase_voltage_C","type":"state","common":{"name":"Netzphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40601,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L1 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40605,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L2 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40606,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L3 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40607,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40608_active_power_from_side_to_side_of_the_grid: {"_id":"holdingRegisters.40608_active_power_from_side_to_side_of_the_grid","type":"state","common":{"name":"Wirkleistung von Seite zu Seite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40608,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40609_Grid_side_-_inside_total_apparent_power: {"_id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power","type":"state","common":{"name":"Netzseite – innere Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40609,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40610_Grid-side_frequency: {"_id":"holdingRegisters.40610_Grid-side_frequency","type":"state","common":{"name":"Grid Seite Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40610,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40611_grid_side_inner_current_L1: {"_id":"holdingRegisters.40611_grid_side_inner_current_L1","type":"state","common":{"name":"netzseitiger Innenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40611,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40612_grid_side_inner_current_L2: {"_id":"holdingRegisters.40612_grid_side_inner_current_L2","type":"state","common":{"name":"netzseitiger Innenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40612,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40613_grid_side_inner_current_L3: {"_id":"holdingRegisters.40613_grid_side_inner_current_L3","type":"state","common":{"name":"netzseitiger Innenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40613,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40614_Out-of-grid_-_current_L1: {"_id":"holdingRegisters.40614_Out-of-grid_-_current_L1","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40614,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40615_Out-of-grid_-_current_L2: {"_id":"holdingRegisters.40615_Out-of-grid_-_current_L2","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40615,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40616_Out-of-grid_-_current_L3: {"_id":"holdingRegisters.40616_Out-of-grid_-_current_L3","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40616,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40617_A_Out-of-grid_-power_L1: {"_id":"holdingRegisters.40617_A_Out-of-grid_-power_L1","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40617,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40618_A_Out-of-grid_-power_L2: {"_id":"holdingRegisters.40618_A_Out-of-grid_-power_L2","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40618,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40619_A_Out-of-grid_-power_L3: {"_id":"holdingRegisters.40619_A_Out-of-grid_-power_L3","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40619,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40620_Out-of-grid_–total_power: {"_id":"holdingRegisters.40620_Out-of-grid_–total_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40620,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40621_Out-of-grid_–total_apparent_power: {"_id":"holdingRegisters.40621_Out-of-grid_–total_apparent_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40621,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40622_Grid-connected_power_factor_PF: {"_id":"holdingRegisters.40622_Grid-connected_power_factor_PF","type":"state","common":{"name":"Netzgekoppelter Leistungsfaktor PF","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40622,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40623_Grid_side_A-phase_power: {"_id":"holdingRegisters.40623_Grid_side_A-phase_power","type":"state","common":{"name":"Netzseitiger L1-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40623,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40624_Grid_side_B-phase_power: {"_id":"holdingRegisters.40624_Grid_side_B-phase_power","type":"state","common":{"name":"Netzseitiger L2-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40624,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40625_Grid_side_C-phase_power: {"_id":"holdingRegisters.40625_Grid_side_C-phase_power","type":"state","common":{"name":"Netzseitiger L3-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40625,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40626_Grid_side_total_power: {"_id":"holdingRegisters.40626_Grid_side_total_power","type":"state","common":{"name":"Netzseitige Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40626,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40628_Inverter_output_phase_voltage_A: {"_id":"holdingRegisters.40628_Inverter_output_phase_voltage_A","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40628,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40629_Inverter_output_phase_voltage_B: {"_id":"holdingRegisters.40629_Inverter_output_phase_voltage_B","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40629,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40630_Inverter_output_phase_voltage_C: {"_id":"holdingRegisters.40630_Inverter_output_phase_voltage_C","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40630,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40631_Inverter_output_phase_current_A: {"_id":"holdingRegisters.40631_Inverter_output_phase_current_A","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40631,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40632_Inverter_output_phase_current_B: {"_id":"holdingRegisters.40632_Inverter_output_phase_current_B","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40632,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.657  - debug: modbus.4 (213280) Add holdingRegisters.40633_Inverter_output_phase_current_C: {"_id":"holdingRegisters.40633_Inverter_output_phase_current_C","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40633,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.659  - debug: modbus.4 (213280) Add holdingRegisters.40634_Inverter_output_phase_power_A: {"_id":"holdingRegisters.40634_Inverter_output_phase_power_A","type":"state","common":{"name":"  Ausgangsphase des Wechselrichters Macht L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40634,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.660  - debug: modbus.4 (213280) Add holdingRegisters.40635_Inverter_output_phase_power_B: {"_id":"holdingRegisters.40635_Inverter_output_phase_power_B","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Macht L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40635,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40636_Inverter_output_phase_power_C: {"_id":"holdingRegisters.40636_Inverter_output_phase_power_C","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40636,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40637_Inverter_output_total_power: {"_id":"holdingRegisters.40637_Inverter_output_total_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40637,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40638_Inverter_output_total_apparent_power: {"_id":"holdingRegisters.40638_Inverter_output_total_apparent_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Scheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40638,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40639_Inverter_frequency: {"_id":"holdingRegisters.40639_Inverter_frequency","type":"state","common":{"name":"Wechselrichter frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40639,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40641_UPS_load-side_phase_power_A: {"_id":"holdingRegisters.40641_UPS_load-side_phase_power_A","type":"state","common":{"name":"USV-lastseitige Phasenleistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40641,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40642_UPS_load-side_phase_power_B: {"_id":"holdingRegisters.40642_UPS_load-side_phase_power_B","type":"state","common":{"name":"USV-lastseitige Phasenleistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40642,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40643_UPS_load-side_phase_power_C: {"_id":"holdingRegisters.40643_UPS_load-side_phase_power_C","type":"state","common":{"name":"USV-lastseitige Phasenleistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40643,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40644_UPS_load-sidetotal_power: {"_id":"holdingRegisters.40644_UPS_load-sidetotal_power","type":"state","common":{"name":"Lastseitige Gesamtleistung der USV","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40644,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40645_Load_phase_voltage_A: {"_id":"holdingRegisters.40645_Load_phase_voltage_A","type":"state","common":{"name":"Load phasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40645,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40646_Load_phase_voltage_B: {"_id":"holdingRegisters.40646_Load_phase_voltage_B","type":"state","common":{"name":"Load phasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40646,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40647_Load_phase_voltage_C: {"_id":"holdingRegisters.40647_Load_phase_voltage_C","type":"state","common":{"name":"Load phasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40647,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40648_Load_phase_current_A: {"_id":"holdingRegisters.40648_Load_phase_current_A","type":"state","common":{"name":"Load phasenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40648,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40649_Load_phase_current_B: {"_id":"holdingRegisters.40649_Load_phase_current_B","type":"state","common":{"name":"Load phasenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40649,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40650_Load_phase_current_C: {"_id":"holdingRegisters.40650_Load_phase_current_C","type":"state","common":{"name":"Load phasenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40650,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                        2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40651_Load_phase_power_A: {"_id":"holdingRegisters.40651_Load_phase_power_A","type":"state","common":{"name":"Load phase Leistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40651,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40652_Load_phase_power_B: {"_id":"holdingRegisters.40652_Load_phase_power_B","type":"state","common":{"name":"Load phase Leistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40652,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40653_Load_phase_power_C: {"_id":"holdingRegisters.40653_Load_phase_power_C","type":"state","common":{"name":"Load phase Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40653,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40654_Load_totalpower: {"_id":"holdingRegisters.40654_Load_totalpower","type":"state","common":{"name":"Load Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40654,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40655_Load_phase_apparent_power: {"_id":"holdingRegisters.40655_Load_phase_apparent_power","type":"state","common":{"name":"Scheinleistung der Lastphase","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40655,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40656_Load_frequency: {"_id":"holdingRegisters.40656_Load_frequency","type":"state","common":{"name":"Load Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40656,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40662_Phase_voltage_of_Gen_port_A: {"_id":"holdingRegisters.40662_Phase_voltage_of_Gen_port_A","type":"state","common":{"name":"Phasenspannung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40662,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40663_Phase_voltage_of_Gen_port_B: {"_id":"holdingRegisters.40663_Phase_voltage_of_Gen_port_B","type":"state","common":{"name":"Phasenspannung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40663,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40664_Phase_voltage_of_Gen_port_C: {"_id":"holdingRegisters.40664_Phase_voltage_of_Gen_port_C","type":"state","common":{"name":"Phasenspannung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40664,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40665_Phase_power_of_Gen_port_A: {"_id":"holdingRegisters.40665_Phase_power_of_Gen_port_A","type":"state","common":{"name":"Phasenleistung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40665,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40666_Phase_power_of_Gen_port_B: {"_id":"holdingRegisters.40666_Phase_power_of_Gen_port_B","type":"state","common":{"name":"Phasenleistung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40666,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40667_Phase_power_of_Gen_port_C: {"_id":"holdingRegisters.40667_Phase_power_of_Gen_port_C","type":"state","common":{"name":"Phasenleistung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40667,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40668_total_power_of_Gen_port: {"_id":"holdingRegisters.40668_total_power_of_Gen_port","type":"state","common":{"name":"Gesamtleistung des Gen-Ports","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40668,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40673_PV1_input_power: {"_id":"holdingRegisters.40673_PV1_input_power","type":"state","common":{"name":"PV1 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40673,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40674_PV2_input_power: {"_id":"holdingRegisters.40674_PV2_input_power","type":"state","common":{"name":"PV2 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40674,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40677_Dc_voltage_1: {"_id":"holdingRegisters.40677_Dc_voltage_1","type":"state","common":{"name":"Gleichspannung 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40677,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40678_Dc_current_1: {"_id":"holdingRegisters.40678_Dc_current_1","type":"state","common":{"name":"Gleichstrom 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40678,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40679_Dc_voltage_2: {"_id":"holdingRegisters.40679_Dc_voltage_2","type":"state","common":{"name":"Gleichspannung 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40679,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40680_Dc_current_2: {"_id":"holdingRegisters.40680_Dc_current_2","type":"state","common":{"name":"Gleichstrom 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40680,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                        2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40620_Out-of-grid__total_power
                        2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
                        2024-05-24 10:49:18.765  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40620_Out-of-grid_–total_power changed to modbus.4.holdingRegisters.40620_Out-of-grid__total_power
                        2024-05-24 10:49:18.777  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40621_Out-of-grid_–total_apparent_power changed to modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
                        2024-05-24 10:49:22.213  - info: modbus.4 (213280) Connected to slave 192.168.178.238
                        2024-05-24 10:49:22.214  - debug: modbus.4 (213280) [DevID_4] Poll start ---------------------
                        2024-05-24 10:49:22.215  - debug: modbus.4 (213280) Initialization of scale factors done!
                        2024-05-24 10:49:22.215  - debug: modbus.4 (213280) [DevID_4/holdingRegs] Poll address 40001 - 8 registers
                        2024-05-24 10:49:27.221  - warn: modbus.4 (213280) Error: undefined
                        2024-05-24 10:49:27.222  - error: modbus.4 (213280) Request timed out.
                        2024-05-24 10:49:27.222  - error: modbus.4 (213280) Client in error state.
                        2024-05-24 10:49:27.222  - warn: modbus.4 (213280) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                        2024-05-24 10:49:27.223  - debug: modbus.4 (213280) Socket closed with error
                        2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Clearing timeout of the current request.
                        2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Cleaning up request fifo.
                        2024-05-24 10:49:28.222  - debug: modbus.4 (213280) Closing client on purpose.
                        2024-05-24 10:49:28.223  - info: modbus.4 (213280) Disconnected from slave 192.168.178.238
                        
                        

                        Angeschlossen am Deye Modbus Ausgang mit Firmware:
                        d1a96c7e-2622-4aa6-bb76-06240a571d6a-grafik.png

                        Der Waveshare funktioniert an einem anderen Modbus Device einwandfrei.

                        Jemand noch eine Idee wo das Problem liegen könnte?

                        W 1 Reply Last reply Reply Quote 0
                        • W
                          warp735 @wendy2702 last edited by warp735

                          @wendy2702
                          Testen immer nur mit EINEM Datenpunkt... Woher diese komplett falsch konfigurierten Register kommen, ist mir immer noch schleierhaft. Man sollte diesen Thread auch lesen 😉
                          Ich hab ALLE Register auf Signed 16 bit

                          PS: du hast RTU over TCP, oder?

                          Snag_1040fdd.png

                          wendy2702 1 Reply Last reply Reply Quote 0
                          • wendy2702
                            wendy2702 @warp735 last edited by wendy2702

                            @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                            Man sollte diesen Thread auch lesen

                            Den habe ich gelesen und hier stehen soviele verschiedene "Register" das ich mir am Ende das aud der Github Sammlung genommen habe.

                            @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                            @wendy2702
                            Testen immer nur mit EINEM Datenpunkt...

                            Auch das habe ich schon hinter mir.

                            @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                            PS: du hast RTU over TCP, oder?

                            Ja, macht der Waveshare

                            Wenn du eine dreistellige Register Adresse verwendest kann ich nur Raten das du den Haken bei "benutze Aliase" an hast ?

                            W 1 Reply Last reply Reply Quote 0
                            • W
                              warp735 @wendy2702 last edited by warp735

                              @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                              Ja, macht der Waveshare

                              Und warum stellst denn bei iob was anderes ein?

                              @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                              kann ich nur Raten das du den Haken bei "benutze Aliase" an hast ?

                              Nope:
                              Snag_111c2c3.png

                              wendy2702 1 Reply Last reply Reply Quote 0
                              • wendy2702
                                wendy2702 @warp735 last edited by wendy2702

                                @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                                Und warum stellst denn bei iob was anderes ein?

                                Weil eigentlich nur einer Umwandelt, iob oder Waveshare. Zumindest ist das bei meinen anderen Waveshare Modbus sachen so.

                                Dein Register 598 lässt sich zumindest per iob und Serieller Verbindung auslesen.

                                Gibt es hier irgendwo einen Export deiner Register?

                                EDIT: @warp735 es läuft. Die 5 Stelligen Register sind nicht "falsch", man muss dann nur den Haken bei "Benutze Aliase" setzen. Dann werden im Hintergrund die 3 stelligen verwendet.

                                So sind jetzt meine Einstellungen im Waveshare:

                                b4e6562c-277a-4fa4-afd0-5bb98ccb3034-grafik.png

                                und so in IOB:

                                7bbff636-a3fd-4aa5-b937-d151941aea27-grafik.png

                                258034e9-596e-48d1-87cd-5a90f51f6dd4-grafik.png

                                Hier nochmal der Export der Register welche aber exact der Liste von @TheBam entsprechen:

                                _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                                40001	Device type	Gerätetyp		uint16be	1	0	0		level		true	false	false	false
                                40004	Seriennummer	Seriennummer		string	5	0	0		state		true	false	false	false
                                40061	Fernsperre	Fernsperre		uint16be	1	0	0		level		true	false	false	false
                                40081	SchalterModus	SchalterModus		uint16be	1	0	0		level		true	false	false	false
                                40105	ZeroExport power	ZeroExport-Leistung	W	int16be	1	0	0		level		true	false	false	false
                                40105	ZeroExport power	ZeroExport-Leistung		floatbe	2	0	0		level		true	false	false	false
                                40109	Max A Charge	Maximaler Ladestrom der Batterie	A	uint16be	1	0	0		level		true	false	false	false
                                40110	Max A discharge	Max A Entladung	A	uint16be	1	0	0		level		true	false	false	false
                                40116	ShutDown battery capacity ShutDown	Abschalten Batteriekapazität Herunterfahren	%	uint16be	1	1	0		level		true	false	false	false
                                40117	Restart battery capacityRestart	Neu starten BatteriekapazitätNeustart	%	uint16be	1	1	0		level		true	false	false	false
                                40118	LowBatt battery capacityLowBatt	Low Batterie Anzeige zum Abschalten der Batterie	%	uint16be	1	1	0		level		true	false	false	false
                                40130	Generator is charged to enable	Generator is charged to enable		int16be	1	0	0		level		true	false	false	false
                                40131	Grid is charged to enable	Grid is charged to enable		int16be	1	0	0		level		true	false	false	false
                                40144	Max Limit Power Output Grid Connection	Begrenzen Sie die maximale Ausgangsleistung des Netzes	W	uint16be	1	0	0		level		true	false	false	false
                                40145	"External	current	sensor clamp phase"	Klemmphase des externen Stromsensors	W	uint16be	1	0	0		level		true	false	false	false
                                40146	Solar sell	  Verkauf von Solar		floatbe	2	0	0		switch		true	false	false	false
                                40149	Sell mode time point 1	Sell mode time point 1		int16be	1	0	0		level		true	false	false	false
                                40150	Sell mode time point 2	Sell mode time point 2		int16be	1	0	0		level		true	false	false	false
                                40151	Sell mode time point 3	Sell mode time point 3		int16be	1	0	0		level		true	false	false	false
                                40152	Sell mode time point 4	Sell mode time point 4		int16be	1	0	0		level		true	false	false	false
                                40153	Sell mode time point 5	Sell mode time point 5		int16be	1	0	0		level		true	false	false	false
                                40154	Sell mode time point 6	Sell mode time point 6		int16be	1	0	0		level		true	false	false	false
                                40155	Sell mode Watt time 1	Sell mode Watt time 1		int16be	1	0	0		level		true	false	false	false
                                40156	Sell mode Watt time 2	Sell mode Watt time 2		int16be	1	0	0		level		true	false	false	false
                                40157	Sell mode Watt time 3	Sell mode Watt time 3		int16be	1	0	0		level		true	false	false	false
                                40158	Sell mode Watt time 4	Sell mode Watt time 4		int16be	1	0	0		level		true	false	false	false
                                40159	Sell mode Watt time 5	Sell mode Watt time 5		int16be	1	0	0		level		true	false	false	false
                                40160	Sell mode Watt time 6	Sell mode Watt time 6		int16be	1	0	0		level		true	false	false	false
                                40167	TOF_Cell SOC 1	TOF_Cell SOC 1	%	int16be	1	0	0		level		true	false	false	false
                                40168	TOF_Cell SOC 2	TOF_Cell SOC 2	%	int16be	1	0	0		level		true	false	false	false
                                40169	TOF_Cell SOC 3	TOF_Cell SOC 3	%	int16be	1	0	0		level		true	false	false	false
                                40170	TOF_Cell SOC 4	TOF_Cell SOC 4	%	int16be	1	0	0		level		true	false	false	false
                                40171	TOF_Cell SOC 5	TOF_Cell SOC 5	%	int16be	1	0	0		level		true	false	false	false
                                40172	TOF_Cell SOC 6	TOF_Cell SOC 6	%	int16be	1	0	0		level		true	false	false	false
                                40173	Time point 1 charge enable	Time point 1 charge enable		int16be	1	0	0		level		true	false	false	false
                                40174	Time point 2 charge enable	Time point 2 charge enable		int16be	1	0	0		level		true	false	false	false
                                40175	Time point 3 charge enable	Time point 3 charge enable		int16be	1	0	0		level		true	false	false	false
                                40176	Time point 4 charge enable	Time point 4 charge enable		int16be	1	0	0		level		true	false	false	false
                                40177	Time point 5 charge enable	Time point 5 charge enable		int16be	1	0	0		level		true	false	false	false
                                40178	Time point 6 charge enable	Time point 6 charge enable		int16be	1	0	0		level		true	false	false	false
                                40341	Max Solar Sell Power at Zero grid	Maximale Solarverkaufsleistung bei null einspeisung	W	uint16be	1	0	0		level		true	false	false	false
                                40341	Max Solar Sell Power by full in	Maximale Solarverkaufsleistung bei einspeisung	W	uint16be	1	0	0		level		true	false	false	false
                                40501	Status	Status (Standby, check, norm, altert, fault)		int16be	1	0	0		level		true	false	false	false
                                40521	Day Grid Buy Power Wh	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                40522	Day_GridSell_Power Wh	Tages Verkaufs leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                40530	Day_PV_Power Wh	Tagesproduzierte leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                40535	Total PV power Wh low word	Gesamt-PV-Leistung Wh niedriges Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                40553	AC Relay	AC relay		uint16be	1	0	0	x < 2? 0:1	level		true	false	false	false
                                40553	Ac relay 2	AC relay2		uint16be	1		0		level		true	false	false	false
                                40587	battery temperature	Batterietemperatur	°C	uint16be	1	0,01	0		level		true	false	false	false
                                40588	battery voltage	Batteriespannung	V	uint16be	1	0,01	0		level		true	false	false	false
                                40589	battery capacity	Batteriekapazität	%	uint16be	1	1	0		level		true	false	false	false
                                40591	Battery output power	Ausgangsleistung der Batterie	W	int16be	1	1	0		level		true	false	false	false
                                40592	Battery output current	Ausgangsstrom der Batterie	A	uint16be	1	0,01	0		level		true	false	false	false
                                40593	Corrected AH	AH korrigiert	AH	uint16be	1	1	0		level		true	false	false	false
                                40599	Grid phase voltage A	Netzphasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                                40600	Grid phase voltage B	Netzphasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                                40601	Grid phase voltage C	Netzphasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                                40605	L1 phase power on the inner side of the grid	L1 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                                40606	L2 phase power on the inner side of the grid	L2 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                                40607	L3 phase power on the inner side of the grid	L3 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                                40608	active power from side to side of the grid	Wirkleistung von Seite zu Seite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                40609	Grid side - inside total apparent power	Netzseite – innere Gesamtscheinleistung	W	uint16be	1	1	0		level		true	false	false	false
                                40610	Grid-side frequency	Grid Seite Frequenz	Hz	uint16be	1	1	0		level		true	false	false	false
                                40611	grid side inner current L1	netzseitiger Innenstrom L1	A	uint16be	1	0,01	0		level		true	false	false	false
                                40612	grid side inner current L2	netzseitiger Innenstrom L2	A	uint16be	1	0,01	0		level		true	false	false	false
                                40613	grid side inner current L3	netzseitiger Innenstrom L3	A	uint16be	1	0,01	0		level		true	false	false	false
                                40614	Out-of-grid - current L1	Außerhalb des Netzes – aktuelles L1	A	uint16be	1	0,01	0		level		true	false	false	false
                                40615	Out-of-grid - current L2	Außerhalb des Netzes – aktuelles L2	A	uint16be	1	0,01	0		level		true	false	false	false
                                40616	Out-of-grid - current L3	Außerhalb des Netzes – aktuelles L3	A	uint16be	1	0,01	0		level		true	false	false	false
                                40617	A Out-of-grid -power L1	A Außerhalb des Netzes - Strom L1	W	uint16be	1	1	0		level		true	false	false	false
                                40618	A Out-of-grid -power L2	A Außerhalb des Netzes - Strom L2	W	uint16be	1	1	0		level		true	false	false	false
                                40619	A Out-of-grid -power L3	A Außerhalb des Netzes - Strom L3	W	uint16be	1	1	0		level		true	false	false	false
                                40620	Out-of-grid -total power	Außerhalb des Netzes - Gesamtleistung	W	uint16be	1	1	0		level		true	false	false	false
                                40621	Out-of-grid - total apparent power	Außerhalb des Netzes - Gesamtscheinleistung	VA	uint16be	1	1	0		level		true	false	false	false
                                40622	Grid-connected power factor PF	Netzgekoppelter Leistungsfaktor PF		uint16be	1	1	0		level		true	false	false	false
                                40623	Grid side A-phase power	Netzseitiger L1-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                                40624	Grid side B-phase power	Netzseitiger L2-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                                40625	Grid side C-phase power	Netzseitiger L3-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                                40626	Grid side total power	Netzseitige Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                                40628	Inverter output phase voltage A	Wechselrichter-Ausgangsphasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                                40629	Inverter output phase voltage B	Wechselrichter-Ausgangsphasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                                40630	Inverter output phase voltage C	Wechselrichter-Ausgangsphasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                                40631	Inverter output phase current A	Ausgangsphasenstrom des Wechselrichters L1	A	uint16be	1	0,01	0		level		true	false	false	false
                                40632	Inverter output phase current B	Ausgangsphasenstrom des Wechselrichters L2	A	uint16be	1	0,01	0		level		true	false	false	false
                                40633	Inverter output phase current C	Ausgangsphasenstrom des Wechselrichters L3	A	uint16be	1	0,01	0		level		true	false	false	false
                                40634	Inverter output phase power A	  Ausgangsphase des Wechselrichters Macht L1	W	uint16be	1	0	0		level		true	false	false	false
                                40635	Inverter output phase power B	Ausgangsphase des Wechselrichters Macht L2	W	uint16be	1	0	0		level		true	false	false	false
                                40636	Inverter output phase power C	Ausgangsphase des Wechselrichters Leistung L3	W	uint16be	1	0	0		level		true	false	false	false
                                40637	Inverter output total power	Gesamtleistung des Wechselrichters Leistung	W	uint16be	1	0	0		level		true	false	false	false
                                40638	Inverter output total apparent power	Gesamtleistung des Wechselrichters Scheinleistung	W	uint16be	1	0	0		level		true	false	false	false
                                40639	Inverter frequency	Wechselrichter frequenz	Hz	uint16be	1	0,01	0		level		true	false	false	false
                                40641	UPS load-side phase power A	USV-lastseitige Phasenleistung L1	W	uint16be	1	1	0		level		true	false	false	false
                                40642	UPS load-side phase power B	USV-lastseitige Phasenleistung L2	W	uint16be	1	1	0		level		true	false	false	false
                                40643	UPS load-side phase power C	USV-lastseitige Phasenleistung L3	W	uint16be	1	1	0		level		true	false	false	false
                                40644	UPS load-sidetotal power	Lastseitige Gesamtleistung der USV	W	uint16be	1	1	0		level		true	false	false	false
                                40645	Load phase voltage A	Load phasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                                40646	Load phase voltage B	Load phasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                                40647	Load phase voltage C	Load phasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                                40648	Load phase current A	Load phasenstrom L1	A	uint16be	1	0,01	0		level		true	false	false	false
                                40649	Load phase current B	Load phasenstrom L2	A	uint16be	1	0,01	0		level		true	false	false	false
                                40650	Load phase current C	Load phasenstrom L3	A	uint16be	1	0,01	0		level		true	false	false	false
                                40651	Load phase power A	Load phase Leistung L1	W	uint16be	1	1	0		level		true	false	false	false
                                40652	Load phase power B	Load phase Leistung L2	W	uint16be	1	1	0		level		true	false	false	false
                                40653	Load phase power C	Load phase Leistung L3	W	uint16be	1	1	0		level		true	false	false	false
                                40654	Load totalpower	Load Gesamtleistung	W	uint16be	1	1	0		level		true	false	false	false
                                40655	Load phase apparent power	Scheinleistung der Lastphase	VA	uint16be	1	1	0		level		true	false	false	false
                                40656	Load frequency	Load Frequenz	Hz	uint16be	1	1	0		level		true	false	false	false
                                40662	Phase voltage of Gen port A	Phasenspannung von Gen-Port L1	V	uint16be	1	0,1	0		level		true	false	false	false
                                40663	Phase voltage of Gen port B	Phasenspannung von Gen-Port L2	V	uint16be	1	0,1	0		level		true	false	false	false
                                40664	Phase voltage of Gen port C	Phasenspannung von Gen-Port L3	V	uint16be	1	0,1	0		level		true	false	false	false
                                40665	Phase power of Gen port A	Phasenleistung von Gen-Port L1	W	uint16be	1	1	0		level		true	false	false	false
                                40666	Phase power of Gen port B	Phasenleistung von Gen-Port L2	W	uint16be	1	1	0		level		true	false	false	false
                                40667	Phase power of Gen port C	Phasenleistung von Gen-Port L3	W	uint16be	1	1	0		level		true	false	false	false
                                40668	total power of Gen port	Gesamtleistung des Gen-Ports	W	uint16be	1	1	0		level		true	false	false	false
                                40673	PV1 input power	PV1 Eingangsleistung	W	uint16be	1	1	0		level		true	false	false	false
                                40674	PV2 input power	PV2 Eingangsleistung	W	uint16be	1	1	0		level		true	false	false	false
                                40677	Dc voltage 1	Gleichspannung 1	V	uint16be	1	0,1	0		level		true	false	false	false
                                40678	Dc current 1	Gleichstrom 1	A	uint16be	1	0,1	0		level		true	false	false	false
                                40679	Dc voltage 2	Gleichspannung 2	V	uint16be	1	0,1	0		level		true	false	false	false
                                40680	Dc current 2	Gleichstrom 2	A	uint16be	1	0,1	0		level		true	false	false	false
                                
                                W 1 Reply Last reply Reply Quote 0
                                • W
                                  warp735 @wendy2702 last edited by

                                  @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                                  man muss dann nur den Haken bei "Benutze Aliase" setzen

                                  Das war schon immer so 😉

                                  Wenn die Register bei dir so funktionieren, ist ja in Ordnung. Ich habs wie gesagt anders eingestellt.

                                  wendy2702 1 Reply Last reply Reply Quote 0
                                  • wendy2702
                                    wendy2702 @warp735 last edited by

                                    @warp735 Gerade mal über längere Zeit beobachtet. Da kommen schonmal merkwürdige Werte raus.

                                    Kannst du mal bitte einen Export deiner Register einstellen?

                                    W 1 Reply Last reply Reply Quote 0
                                    • W
                                      warp735 @wendy2702 last edited by

                                      @wendy2702
                                      Ausnahmslos alle Werte so:

                                      Snag_13f8b67.png

                                      wendy2702 1 Reply Last reply Reply Quote 0
                                      • wendy2702
                                        wendy2702 @warp735 last edited by

                                        @warp735 Hm,

                                        das hilft bei der Frage nach einem Export der Register leider nicht weiter.

                                        W 1 Reply Last reply Reply Quote 0
                                        • W
                                          warp735 @wendy2702 last edited by

                                          @wendy2702
                                          Dann stell halt schnell selbst um. Bin am Handy und gibt kein Export

                                          wendy2702 1 Reply Last reply Reply Quote 0
                                          • wendy2702
                                            wendy2702 @warp735 last edited by

                                            @warp735 Mir wäre es eher um den Vergleich gegangen welche Register du nutzt und was alles in der Liste steht die ich importiert habe.

                                            Das du am Handy bist kann ich ja nicht wissen.

                                            W 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            837
                                            Online

                                            31.6k
                                            Users

                                            79.5k
                                            Topics

                                            1.3m
                                            Posts

                                            25
                                            228
                                            39573
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo