Skip to content
  • Home
  • Aktuell
  • Tags
  • 0 Ungelesen 0
  • Kategorien
  • Unreplied
  • Beliebt
  • GitHub
  • Docu
  • Hilfe
Skins
  • Light
  • Brite
  • Cerulean
  • Cosmo
  • Flatly
  • Journal
  • Litera
  • Lumen
  • Lux
  • Materia
  • Minty
  • Morph
  • Pulse
  • Sandstone
  • Simplex
  • Sketchy
  • Spacelab
  • United
  • Yeti
  • Zephyr
  • Dark
  • Cyborg
  • Darkly
  • Quartz
  • Slate
  • Solar
  • Superhero
  • Vapor

  • Standard: (Kein Skin)
  • Kein Skin
Einklappen
ioBroker Logo

Community Forum

donate donate
  1. ioBroker Community Home
  2. Deutsch
  3. Einsteigerfragen
  4. Einbindung von Geräten
  5. Deye Wechselrichter Modbus Register beschreiben

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.9k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.3k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.6k

Deye Wechselrichter Modbus Register beschreiben

Geplant Angeheftet Gesperrt Verschoben Einbindung von Geräten
230 Beiträge 27 Kommentatoren 59.6k Aufrufe 26 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • S shipper

    @etzeste13
    du hast mich gerettet. Wenn ich die Werte in den Objekten setze, werden die register erfolgreich beschrieben. Wenn ich in blockly die Funktion "aktualisiere Object " nehme dann nicht. Mit "steuere object" geht es dann.
    Da konnte ich lange suchen, nichts gefunden, weil sonst nichts zu finden war.

    E Online
    E Online
    etzeste13
    schrieb am zuletzt editiert von
    #142

    @shipper freut mich das es funktioniert und ich mal wem helfen konnte....:-)
    vG

    1 Antwort Letzte Antwort
    0
    • miaelM Offline
      miaelM Offline
      miael
      schrieb am zuletzt editiert von
      #143

      Hallo,
      kann mir einer sagen was ich da im Register eintragen muss um eine vernünftige Temperatur zu bekommmen?
      Unbenannt.JPG

      Danke
      michael

      W 1 Antwort Letzte Antwort
      0
      • miaelM miael

        Hallo,
        kann mir einer sagen was ich da im Register eintragen muss um eine vernünftige Temperatur zu bekommmen?
        Unbenannt.JPG

        Danke
        michael

        W Offline
        W Offline
        warp735
        schrieb am zuletzt editiert von
        #144

        @miael
        AC ist Faktor 0,1 und bei Offset -100. Dann hast den richtigen Wert. Beim DC Wert genau so, bekommst aber nur Daten wenn nen DC Batt Tempfühler angeschlossen hast. Sonst steht der immer auf 25°

        Schreiben geht bei mir übrigens problemlos.

        miaelM 1 Antwort Letzte Antwort
        0
        • W warp735

          @miael
          AC ist Faktor 0,1 und bei Offset -100. Dann hast den richtigen Wert. Beim DC Wert genau so, bekommst aber nur Daten wenn nen DC Batt Tempfühler angeschlossen hast. Sonst steht der immer auf 25°

          Schreiben geht bei mir übrigens problemlos.

          miaelM Offline
          miaelM Offline
          miael
          schrieb am zuletzt editiert von
          #145

          @warp735
          Besten dank!
          Der Hinweis mit den 25°C war es. Bin jetzt auf "Heat sink temperatur" gewechselt und funktioniert.

          W 1 Antwort Letzte Antwort
          0
          • miaelM miael

            @warp735
            Besten dank!
            Der Hinweis mit den 25°C war es. Bin jetzt auf "Heat sink temperatur" gewechselt und funktioniert.

            W Offline
            W Offline
            warp735
            schrieb am zuletzt editiert von
            #146

            @miael
            Ja, das ist AC, bzw die interne WR Temp, nach der er selbst auch regelt

            1 Antwort Letzte Antwort
            0
            • W Offline
              W Offline
              warp735
              schrieb am zuletzt editiert von warp735
              #147

              Weiß jemand wie die "Tägliche Erzeugung" gerechnet wird? Ist da der Micro inkludiert oder nicht? Bei der oberen prozentualen Anzeige "Produktion" interessiert er auf jedenfall nicht. Bei diesem Beispiel müssten es ja 55% sein und nicht 41%

              Find nämlich auch kein Register für die kwh vom Microinverter :-(

              Snag_44ef76.png

              1 Antwort Letzte Antwort
              0
              • R Offline
                R Offline
                Ronny81
                schrieb am zuletzt editiert von
                #148

                Servus zusammen,

                ich bin neu hier und hoffe ihr könnt mir helfen.
                Ich muss ganz dringen ein Register am Deye setzen und zwar die ID bzw. Seriennummer.
                Leider hat mein Deye nach dem letzten Firmware Update seine ID verloren.
                Ich habe es schon über die RS232 versucht, aber der WR will nicht antworten.
                Kann man die ID über die RS485 ändern?
                Die ID müsste die Register 3,4,5,6 und 7 haben.
                Register 7, ID(SN), Stelle 2 + 1 ASCII
                Register 6, ID(SN), Stelle 4 + 3 ASCII
                Register 5, ID(SN), Stelle 6 + 5 ASCII
                Register 4, ID(SN), Stelle 8 + 7 ASCII
                Register 3, ID(SN), Stelle 10 + 9 ASCII
                Ich hoffe Ihr könnt mir helfen. Danke schon mal.
                Anbei noch ein Foto des Display ohne ID.

                Gruß Ronny

                20240406_174924.jpg 20240407_155125.jpg

                1 Antwort Letzte Antwort
                0
                • wendy2702W Offline
                  wendy2702W Offline
                  wendy2702
                  schrieb am zuletzt editiert von
                  #149

                  Hi,

                  ich schaffe es aktuell nicht meinen Deye SUN-12K-SG04LP3-EU pe Waveshare auszulesen.

                  ich verwende diesen Waveshare:

                  15a56c0a-df08-4f36-b038-41bcf06e6805-grafik.png

                  mit diesen Einstellungen:

                  ad83f715-b7d6-4abb-adb5-613b814a6e75-grafik.png

                  636dd362-e0c0-47b0-98c1-4b4ca03fc7ec-grafik.png

                  Wenn ich mit CAS Modbus Scanner per USB RS485 Adapter einen Test mache funktioniert die Verbindung:

                  50611fe6-b361-4ec5-b918-04fb5d121f7e-grafik.png :

                  Und mit Modbus Poll kann ich register auslesen.

                  Iob ist so konfiguriert:

                  49401faa-1116-48a2-8c29-861e6cc774ba-grafik.png

                  Register aus dem Github Modbus Template von @TheBam

                  9f3695a3-2a67-4fd6-baea-7a6977a7ea52-grafik.png

                  Debug log hilft mir aktuell nicht weiter: (Gekürzt wegen Payload.)

                  2024-05-24 10:49:09.547  - info: host.iobroker "system.adapter.modbus.4" enabled
                  2024-05-24 10:49:10.972  - info: host.iobroker instance system.adapter.modbus.4 started with pid 213280
                  2024-05-24 10:49:12.811  - debug: modbus.4 (213280) Redis Objects: Use Redis connection: 0.0.0.0:9001
                  2024-05-24 10:49:12.924  - debug: modbus.4 (213280) Objects client ready ... initialize now
                  2024-05-24 10:49:13.001  - debug: modbus.4 (213280) Objects create System PubSub Client
                  2024-05-24 10:49:13.002  - debug: modbus.4 (213280) Objects create User PubSub Client
                  2024-05-24 10:49:13.308  - debug: modbus.4 (213280) Objects client initialize lua scripts
                  2024-05-24 10:49:13.332  - debug: modbus.4 (213280) Objects connected to redis: 0.0.0.0:9001
                  2024-05-24 10:49:13.551  - debug: modbus.4 (213280) Redis States: Use Redis connection: 0.0.0.0:9000
                  2024-05-24 10:49:13.669  - debug: modbus.4 (213280) States create System PubSub Client
                  2024-05-24 10:49:13.670  - debug: modbus.4 (213280) States create User PubSub Client
                  2024-05-24 10:49:13.848  - debug: modbus.4 (213280) States connected to redis: 0.0.0.0:9000
                  2024-05-24 10:49:14.085  - debug: modbus.4 (213280) Plugin sentry Do not initialize Plugin (enabled=false)
                  2024-05-24 10:49:14.141  - debug: modbus.4 (213280) Plugin sentry destroyed because not initialized correctly
                  2024-05-24 10:49:14.599  - info: modbus.4 (213280) starting. Version 6.2.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                  2024-05-24 10:49:15.614  - debug: modbus.4 (213280) Initialize Objects for disInputs: []
                  2024-05-24 10:49:15.616  - debug: modbus.4 (213280) Initialize Objects for coils: []
                  2024-05-24 10:49:15.617  - debug: modbus.4 (213280) Initialize Objects for inputRegs: []
                  2024-05-24 10:49:15.626  - debug: modbus.4 (213280) Initialize Objects for holdingRegs: [{"_address":40001,"name":"Device type","description":"Gerätetyp","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40001,"id":"holdingRegisters.40001_Device_type"},Gesamtscheinleistung","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40609,"id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power"},{"_address":40610,"name":"Grid-side frequency","description":"Grid Seite Frequenz","unit":"Hz","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40610,"id":"holdingRegisters.40610_Grid-side_frequency"},{"_address":40611,"name":"grid side inner current L1","description":"netzseitiger Innenstrom 1","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40678,"id":"holdingRegisters.40678_Dc_current_1"},{"_address":40679,"name":"Dc voltage 2","description":"Gleichspannung 2","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40679,"id":"holdingRegisters.40679_Dc_voltage_2"},{"_address":40680,"name":"Dc current 2","description":"Gleichstrom 2","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40680,"id":"holdingRegisters.40680_Dc_current_2"}]
                  2024-05-24 10:49:15.633  - debug: modbus.4 (213280) Add holdingRegisters.40001_Device_type: {"_id":"holdingRegisters.40001_Device_type","type":"state","common":{"name":"Gerätetyp","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40001,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.636  - debug: modbus.4 (213280) Add holdingRegisters.40004_Seriennummer: {"_id":"holdingRegisters.40004_Seriennummer","type":"state","common":{"name":"Seriennummer","role":"state","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":40004,"deviceId":4,"type":"string","len":5,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.637  - debug: modbus.4 (213280) Add holdingRegisters.40061_Fernsperre: {"_id":"holdingRegisters.40061_Fernsperre","type":"state","common":{"name":"Fernsperre","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40061,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40081_SchalterModus: {"_id":"holdingRegisters.40081_SchalterModus","type":"state","common":{"name":"SchalterModus","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40081,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.639  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40109_Max_A_Charge: {"_id":"holdingRegisters.40109_Max_A_Charge","type":"state","common":{"name":"Maximaler Ladestrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40109,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40110_Max_A_discharge: {"_id":"holdingRegisters.40110_Max_A_discharge","type":"state","common":{"name":"Max A Entladung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40110,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40116_ShutDown_battery_capacity_ShutDown: {"_id":"holdingRegisters.40116_ShutDown_battery_capacity_ShutDown","type":"state","common":{"name":"Abschalten Batteriekapazität Herunterfahren","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40116,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40117_Restart_battery_capacityRestart: {"_id":"holdingRegisters.40117_Restart_battery_capacityRestart","type":"state","common":{"name":"Neu starten BatteriekapazitätNeustart","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40117,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40118_LowBatt_battery_capacityLowBatt: {"_id":"holdingRegisters.40118_LowBatt_battery_capacityLowBatt","type":"state","common":{"name":"Low Batterie Anzeige zum Abschalten der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40118,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40130_Generator_is_charged_to_enable: {"_id":"holdingRegisters.40130_Generator_is_charged_to_enable","type":"state","common":{"name":"Generator is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40130,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40131_Grid_is_charged_to_enable: {"_id":"holdingRegisters.40131_Grid_is_charged_to_enable","type":"state","common":{"name":"Grid is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40131,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection: {"_id":"holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection","type":"state","common":{"name":"Begrenzen Sie die maximale Ausgangsleistung des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40144,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40145_External_current_sensor_clamp_phase: {"_id":"holdingRegisters.40145_External_current_sensor_clamp_phase","type":"state","common":{"name":"Klemmphase des externen Stromsensors","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40145,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40146_Solar_sell: {"_id":"holdingRegisters.40146_Solar_sell","type":"state","common":{"name":"  Verkauf von Solar","role":"switch","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40146,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40149_Sell_mode_time_point_1: {"_id":"holdingRegisters.40149_Sell_mode_time_point_1","type":"state","common":{"name":"Sell mode time point 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40149,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40150_Sell_mode_time_point_2: {"_id":"holdingRegisters.40150_Sell_mode_time_point_2","type":"state","common":{"name":"Sell mode time point 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40150,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40151_Sell_mode_time_point_3: {"_id":"holdingRegisters.40151_Sell_mode_time_point_3","type":"state","common":{"name":"Sell mode time point 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40151,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40152_Sell_mode_time_point_4: {"_id":"holdingRegisters.40152_Sell_mode_time_point_4","type":"state","common":{"name":"Sell mode time point 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40152,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40153_Sell_mode_time_point_5: {"_id":"holdingRegisters.40153_Sell_mode_time_point_5","type":"state","common":{"name":"Sell mode time point 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40153,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40154_Sell_mode_time_point_6: {"_id":"holdingRegisters.40154_Sell_mode_time_point_6","type":"state","common":{"name":"Sell mode time point 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40154,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40155_Sell_mode_Watt_time_1: {"_id":"holdingRegisters.40155_Sell_mode_Watt_time_1","type":"state","common":{"name":"Sell mode Watt time 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40155,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40156_Sell_mode_Watt_time_2: {"_id":"holdingRegisters.40156_Sell_mode_Watt_time_2","type":"state","common":{"name":"Sell mode Watt time 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40156,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40157_Sell_mode_Watt_time_3: {"_id":"holdingRegisters.40157_Sell_mode_Watt_time_3","type":"state","common":{"name":"Sell mode Watt time 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40157,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40158_Sell_mode_Watt_time_4: {"_id":"holdingRegisters.40158_Sell_mode_Watt_time_4","type":"state","common":{"name":"Sell mode Watt time 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40158,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40159_Sell_mode_Watt_time_5: {"_id":"holdingRegisters.40159_Sell_mode_Watt_time_5","type":"state","common":{"name":"Sell mode Watt time 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40159,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40160_Sell_mode_Watt_time_6: {"_id":"holdingRegisters.40160_Sell_mode_Watt_time_6","type":"state","common":{"name":"Sell mode Watt time 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40160,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40167_TOF_Cell_SOC_1: {"_id":"holdingRegisters.40167_TOF_Cell_SOC_1","type":"state","common":{"name":"TOF_Cell SOC 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40167,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40168_TOF_Cell_SOC_2: {"_id":"holdingRegisters.40168_TOF_Cell_SOC_2","type":"state","common":{"name":"TOF_Cell SOC 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40168,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40169_TOF_Cell_SOC_3: {"_id":"holdingRegisters.40169_TOF_Cell_SOC_3","type":"state","common":{"name":"TOF_Cell SOC 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40169,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40170_TOF_Cell_SOC_4: {"_id":"holdingRegisters.40170_TOF_Cell_SOC_4","type":"state","common":{"name":"TOF_Cell SOC 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40170,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40171_TOF_Cell_SOC_5: {"_id":"holdingRegisters.40171_TOF_Cell_SOC_5","type":"state","common":{"name":"TOF_Cell SOC 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40171,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40172_TOF_Cell_SOC_6: {"_id":"holdingRegisters.40172_TOF_Cell_SOC_6","type":"state","common":{"name":"TOF_Cell SOC 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40172,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40173_Time_point_1_charge_enable: {"_id":"holdingRegisters.40173_Time_point_1_charge_enable","type":"state","common":{"name":"Time point 1 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40173,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40174_Time_point_2_charge_enable: {"_id":"holdingRegisters.40174_Time_point_2_charge_enable","type":"state","common":{"name":"Time point 2 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40174,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40175_Time_point_3_charge_enable: {"_id":"holdingRegisters.40175_Time_point_3_charge_enable","type":"state","common":{"name":"Time point 3 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40175,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40176_Time_point_4_charge_enable: {"_id":"holdingRegisters.40176_Time_point_4_charge_enable","type":"state","common":{"name":"Time point 4 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40176,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40177_Time_point_5_charge_enable: {"_id":"holdingRegisters.40177_Time_point_5_charge_enable","type":"state","common":{"name":"Time point 5 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40177,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40178_Time_point_6_charge_enable: {"_id":"holdingRegisters.40178_Time_point_6_charge_enable","type":"state","common":{"name":"Time point 6 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40178,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei null einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40501_Status: {"_id":"holdingRegisters.40501_Status","type":"state","common":{"name":"Status (Standby, check, norm, altert, fault)","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40501,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40521_Day_Grid_Buy_Power_Wh: {"_id":"holdingRegisters.40521_Day_Grid_Buy_Power_Wh","type":"state","common":{"name":"Tag Netzabnahme Strom Wh","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40521,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40522_Day_GridSell_Power_Wh: {"_id":"holdingRegisters.40522_Day_GridSell_Power_Wh","type":"state","common":{"name":"Tages Verkaufs leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40522,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40530_Day_PV_Power_Wh: {"_id":"holdingRegisters.40530_Day_PV_Power_Wh","type":"state","common":{"name":"Tagesproduzierte leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40530,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40535_Total_PV_power_Wh_low_word: {"_id":"holdingRegisters.40535_Total_PV_power_Wh_low_word","type":"state","common":{"name":"Gesamt-PV-Leistung Wh niedriges Wort","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40535,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_AC_Relay: {"_id":"holdingRegisters.40553_AC_Relay","type":"state","common":{"name":"AC relay","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_Ac_relay_2: {"_id":"holdingRegisters.40553_Ac_relay_2","type":"state","common":{"name":"AC relay2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40587_battery_temperature: {"_id":"holdingRegisters.40587_battery_temperature","type":"state","common":{"name":"Batterietemperatur","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":40587,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40588_battery_voltage: {"_id":"holdingRegisters.40588_battery_voltage","type":"state","common":{"name":"Batteriespannung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40588,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40589_battery_capacity: {"_id":"holdingRegisters.40589_battery_capacity","type":"state","common":{"name":"Batteriekapazität","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40589,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40591_Battery_output_power: {"_id":"holdingRegisters.40591_Battery_output_power","type":"state","common":{"name":"Ausgangsleistung der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40591,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40592_Battery_output_current: {"_id":"holdingRegisters.40592_Battery_output_current","type":"state","common":{"name":"Ausgangsstrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40592,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40593_Corrected_AH: {"_id":"holdingRegisters.40593_Corrected_AH","type":"state","common":{"name":"AH korrigiert","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"AH"},"native":{"regType":"holdingRegs","address":40593,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40599_Grid_phase_voltage_A: {"_id":"holdingRegisters.40599_Grid_phase_voltage_A","type":"state","common":{"name":"Netzphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40599,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40600_Grid_phase_voltage_B: {"_id":"holdingRegisters.40600_Grid_phase_voltage_B","type":"state","common":{"name":"Netzphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40600,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40601_Grid_phase_voltage_C: {"_id":"holdingRegisters.40601_Grid_phase_voltage_C","type":"state","common":{"name":"Netzphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40601,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L1 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40605,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L2 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40606,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L3 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40607,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40608_active_power_from_side_to_side_of_the_grid: {"_id":"holdingRegisters.40608_active_power_from_side_to_side_of_the_grid","type":"state","common":{"name":"Wirkleistung von Seite zu Seite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40608,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40609_Grid_side_-_inside_total_apparent_power: {"_id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power","type":"state","common":{"name":"Netzseite – innere Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40609,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40610_Grid-side_frequency: {"_id":"holdingRegisters.40610_Grid-side_frequency","type":"state","common":{"name":"Grid Seite Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40610,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40611_grid_side_inner_current_L1: {"_id":"holdingRegisters.40611_grid_side_inner_current_L1","type":"state","common":{"name":"netzseitiger Innenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40611,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40612_grid_side_inner_current_L2: {"_id":"holdingRegisters.40612_grid_side_inner_current_L2","type":"state","common":{"name":"netzseitiger Innenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40612,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40613_grid_side_inner_current_L3: {"_id":"holdingRegisters.40613_grid_side_inner_current_L3","type":"state","common":{"name":"netzseitiger Innenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40613,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40614_Out-of-grid_-_current_L1: {"_id":"holdingRegisters.40614_Out-of-grid_-_current_L1","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40614,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40615_Out-of-grid_-_current_L2: {"_id":"holdingRegisters.40615_Out-of-grid_-_current_L2","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40615,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40616_Out-of-grid_-_current_L3: {"_id":"holdingRegisters.40616_Out-of-grid_-_current_L3","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40616,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40617_A_Out-of-grid_-power_L1: {"_id":"holdingRegisters.40617_A_Out-of-grid_-power_L1","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40617,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40618_A_Out-of-grid_-power_L2: {"_id":"holdingRegisters.40618_A_Out-of-grid_-power_L2","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40618,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40619_A_Out-of-grid_-power_L3: {"_id":"holdingRegisters.40619_A_Out-of-grid_-power_L3","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40619,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40620_Out-of-grid_–total_power: {"_id":"holdingRegisters.40620_Out-of-grid_–total_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40620,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40621_Out-of-grid_–total_apparent_power: {"_id":"holdingRegisters.40621_Out-of-grid_–total_apparent_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40621,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40622_Grid-connected_power_factor_PF: {"_id":"holdingRegisters.40622_Grid-connected_power_factor_PF","type":"state","common":{"name":"Netzgekoppelter Leistungsfaktor PF","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40622,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40623_Grid_side_A-phase_power: {"_id":"holdingRegisters.40623_Grid_side_A-phase_power","type":"state","common":{"name":"Netzseitiger L1-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40623,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40624_Grid_side_B-phase_power: {"_id":"holdingRegisters.40624_Grid_side_B-phase_power","type":"state","common":{"name":"Netzseitiger L2-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40624,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40625_Grid_side_C-phase_power: {"_id":"holdingRegisters.40625_Grid_side_C-phase_power","type":"state","common":{"name":"Netzseitiger L3-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40625,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40626_Grid_side_total_power: {"_id":"holdingRegisters.40626_Grid_side_total_power","type":"state","common":{"name":"Netzseitige Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40626,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40628_Inverter_output_phase_voltage_A: {"_id":"holdingRegisters.40628_Inverter_output_phase_voltage_A","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40628,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40629_Inverter_output_phase_voltage_B: {"_id":"holdingRegisters.40629_Inverter_output_phase_voltage_B","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40629,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40630_Inverter_output_phase_voltage_C: {"_id":"holdingRegisters.40630_Inverter_output_phase_voltage_C","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40630,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40631_Inverter_output_phase_current_A: {"_id":"holdingRegisters.40631_Inverter_output_phase_current_A","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40631,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40632_Inverter_output_phase_current_B: {"_id":"holdingRegisters.40632_Inverter_output_phase_current_B","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40632,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.657  - debug: modbus.4 (213280) Add holdingRegisters.40633_Inverter_output_phase_current_C: {"_id":"holdingRegisters.40633_Inverter_output_phase_current_C","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40633,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.659  - debug: modbus.4 (213280) Add holdingRegisters.40634_Inverter_output_phase_power_A: {"_id":"holdingRegisters.40634_Inverter_output_phase_power_A","type":"state","common":{"name":"  Ausgangsphase des Wechselrichters Macht L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40634,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.660  - debug: modbus.4 (213280) Add holdingRegisters.40635_Inverter_output_phase_power_B: {"_id":"holdingRegisters.40635_Inverter_output_phase_power_B","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Macht L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40635,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40636_Inverter_output_phase_power_C: {"_id":"holdingRegisters.40636_Inverter_output_phase_power_C","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40636,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40637_Inverter_output_total_power: {"_id":"holdingRegisters.40637_Inverter_output_total_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40637,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40638_Inverter_output_total_apparent_power: {"_id":"holdingRegisters.40638_Inverter_output_total_apparent_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Scheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40638,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40639_Inverter_frequency: {"_id":"holdingRegisters.40639_Inverter_frequency","type":"state","common":{"name":"Wechselrichter frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40639,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40641_UPS_load-side_phase_power_A: {"_id":"holdingRegisters.40641_UPS_load-side_phase_power_A","type":"state","common":{"name":"USV-lastseitige Phasenleistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40641,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40642_UPS_load-side_phase_power_B: {"_id":"holdingRegisters.40642_UPS_load-side_phase_power_B","type":"state","common":{"name":"USV-lastseitige Phasenleistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40642,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40643_UPS_load-side_phase_power_C: {"_id":"holdingRegisters.40643_UPS_load-side_phase_power_C","type":"state","common":{"name":"USV-lastseitige Phasenleistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40643,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40644_UPS_load-sidetotal_power: {"_id":"holdingRegisters.40644_UPS_load-sidetotal_power","type":"state","common":{"name":"Lastseitige Gesamtleistung der USV","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40644,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40645_Load_phase_voltage_A: {"_id":"holdingRegisters.40645_Load_phase_voltage_A","type":"state","common":{"name":"Load phasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40645,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40646_Load_phase_voltage_B: {"_id":"holdingRegisters.40646_Load_phase_voltage_B","type":"state","common":{"name":"Load phasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40646,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40647_Load_phase_voltage_C: {"_id":"holdingRegisters.40647_Load_phase_voltage_C","type":"state","common":{"name":"Load phasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40647,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40648_Load_phase_current_A: {"_id":"holdingRegisters.40648_Load_phase_current_A","type":"state","common":{"name":"Load phasenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40648,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40649_Load_phase_current_B: {"_id":"holdingRegisters.40649_Load_phase_current_B","type":"state","common":{"name":"Load phasenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40649,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40650_Load_phase_current_C: {"_id":"holdingRegisters.40650_Load_phase_current_C","type":"state","common":{"name":"Load phasenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40650,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                  2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40651_Load_phase_power_A: {"_id":"holdingRegisters.40651_Load_phase_power_A","type":"state","common":{"name":"Load phase Leistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40651,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40652_Load_phase_power_B: {"_id":"holdingRegisters.40652_Load_phase_power_B","type":"state","common":{"name":"Load phase Leistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40652,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40653_Load_phase_power_C: {"_id":"holdingRegisters.40653_Load_phase_power_C","type":"state","common":{"name":"Load phase Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40653,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40654_Load_totalpower: {"_id":"holdingRegisters.40654_Load_totalpower","type":"state","common":{"name":"Load Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40654,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40655_Load_phase_apparent_power: {"_id":"holdingRegisters.40655_Load_phase_apparent_power","type":"state","common":{"name":"Scheinleistung der Lastphase","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40655,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40656_Load_frequency: {"_id":"holdingRegisters.40656_Load_frequency","type":"state","common":{"name":"Load Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40656,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40662_Phase_voltage_of_Gen_port_A: {"_id":"holdingRegisters.40662_Phase_voltage_of_Gen_port_A","type":"state","common":{"name":"Phasenspannung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40662,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40663_Phase_voltage_of_Gen_port_B: {"_id":"holdingRegisters.40663_Phase_voltage_of_Gen_port_B","type":"state","common":{"name":"Phasenspannung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40663,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40664_Phase_voltage_of_Gen_port_C: {"_id":"holdingRegisters.40664_Phase_voltage_of_Gen_port_C","type":"state","common":{"name":"Phasenspannung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40664,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40665_Phase_power_of_Gen_port_A: {"_id":"holdingRegisters.40665_Phase_power_of_Gen_port_A","type":"state","common":{"name":"Phasenleistung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40665,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40666_Phase_power_of_Gen_port_B: {"_id":"holdingRegisters.40666_Phase_power_of_Gen_port_B","type":"state","common":{"name":"Phasenleistung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40666,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40667_Phase_power_of_Gen_port_C: {"_id":"holdingRegisters.40667_Phase_power_of_Gen_port_C","type":"state","common":{"name":"Phasenleistung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40667,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40668_total_power_of_Gen_port: {"_id":"holdingRegisters.40668_total_power_of_Gen_port","type":"state","common":{"name":"Gesamtleistung des Gen-Ports","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40668,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40673_PV1_input_power: {"_id":"holdingRegisters.40673_PV1_input_power","type":"state","common":{"name":"PV1 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40673,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40674_PV2_input_power: {"_id":"holdingRegisters.40674_PV2_input_power","type":"state","common":{"name":"PV2 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40674,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                  2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40677_Dc_voltage_1: {"_id":"holdingRegisters.40677_Dc_voltage_1","type":"state","common":{"name":"Gleichspannung 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40677,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40678_Dc_current_1: {"_id":"holdingRegisters.40678_Dc_current_1","type":"state","common":{"name":"Gleichstrom 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40678,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40679_Dc_voltage_2: {"_id":"holdingRegisters.40679_Dc_voltage_2","type":"state","common":{"name":"Gleichspannung 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40679,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40680_Dc_current_2: {"_id":"holdingRegisters.40680_Dc_current_2","type":"state","common":{"name":"Gleichstrom 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40680,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                  2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40620_Out-of-grid__total_power
                  2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
                  2024-05-24 10:49:18.765  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40620_Out-of-grid_–total_power changed to modbus.4.holdingRegisters.40620_Out-of-grid__total_power
                  2024-05-24 10:49:18.777  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40621_Out-of-grid_–total_apparent_power changed to modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
                  2024-05-24 10:49:22.213  - info: modbus.4 (213280) Connected to slave 192.168.178.238
                  2024-05-24 10:49:22.214  - debug: modbus.4 (213280) [DevID_4] Poll start ---------------------
                  2024-05-24 10:49:22.215  - debug: modbus.4 (213280) Initialization of scale factors done!
                  2024-05-24 10:49:22.215  - debug: modbus.4 (213280) [DevID_4/holdingRegs] Poll address 40001 - 8 registers
                  2024-05-24 10:49:27.221  - warn: modbus.4 (213280) Error: undefined
                  2024-05-24 10:49:27.222  - error: modbus.4 (213280) Request timed out.
                  2024-05-24 10:49:27.222  - error: modbus.4 (213280) Client in error state.
                  2024-05-24 10:49:27.222  - warn: modbus.4 (213280) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                  2024-05-24 10:49:27.223  - debug: modbus.4 (213280) Socket closed with error
                  2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Clearing timeout of the current request.
                  2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Cleaning up request fifo.
                  2024-05-24 10:49:28.222  - debug: modbus.4 (213280) Closing client on purpose.
                  2024-05-24 10:49:28.223  - info: modbus.4 (213280) Disconnected from slave 192.168.178.238
                  
                  

                  Angeschlossen am Deye Modbus Ausgang mit Firmware:
                  d1a96c7e-2622-4aa6-bb76-06240a571d6a-grafik.png

                  Der Waveshare funktioniert an einem anderen Modbus Device einwandfrei.

                  Jemand noch eine Idee wo das Problem liegen könnte?

                  Bitte keine Fragen per PN, die gehören ins Forum!

                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                  W 1 Antwort Letzte Antwort
                  0
                  • wendy2702W wendy2702

                    Hi,

                    ich schaffe es aktuell nicht meinen Deye SUN-12K-SG04LP3-EU pe Waveshare auszulesen.

                    ich verwende diesen Waveshare:

                    15a56c0a-df08-4f36-b038-41bcf06e6805-grafik.png

                    mit diesen Einstellungen:

                    ad83f715-b7d6-4abb-adb5-613b814a6e75-grafik.png

                    636dd362-e0c0-47b0-98c1-4b4ca03fc7ec-grafik.png

                    Wenn ich mit CAS Modbus Scanner per USB RS485 Adapter einen Test mache funktioniert die Verbindung:

                    50611fe6-b361-4ec5-b918-04fb5d121f7e-grafik.png :

                    Und mit Modbus Poll kann ich register auslesen.

                    Iob ist so konfiguriert:

                    49401faa-1116-48a2-8c29-861e6cc774ba-grafik.png

                    Register aus dem Github Modbus Template von @TheBam

                    9f3695a3-2a67-4fd6-baea-7a6977a7ea52-grafik.png

                    Debug log hilft mir aktuell nicht weiter: (Gekürzt wegen Payload.)

                    2024-05-24 10:49:09.547  - info: host.iobroker "system.adapter.modbus.4" enabled
                    2024-05-24 10:49:10.972  - info: host.iobroker instance system.adapter.modbus.4 started with pid 213280
                    2024-05-24 10:49:12.811  - debug: modbus.4 (213280) Redis Objects: Use Redis connection: 0.0.0.0:9001
                    2024-05-24 10:49:12.924  - debug: modbus.4 (213280) Objects client ready ... initialize now
                    2024-05-24 10:49:13.001  - debug: modbus.4 (213280) Objects create System PubSub Client
                    2024-05-24 10:49:13.002  - debug: modbus.4 (213280) Objects create User PubSub Client
                    2024-05-24 10:49:13.308  - debug: modbus.4 (213280) Objects client initialize lua scripts
                    2024-05-24 10:49:13.332  - debug: modbus.4 (213280) Objects connected to redis: 0.0.0.0:9001
                    2024-05-24 10:49:13.551  - debug: modbus.4 (213280) Redis States: Use Redis connection: 0.0.0.0:9000
                    2024-05-24 10:49:13.669  - debug: modbus.4 (213280) States create System PubSub Client
                    2024-05-24 10:49:13.670  - debug: modbus.4 (213280) States create User PubSub Client
                    2024-05-24 10:49:13.848  - debug: modbus.4 (213280) States connected to redis: 0.0.0.0:9000
                    2024-05-24 10:49:14.085  - debug: modbus.4 (213280) Plugin sentry Do not initialize Plugin (enabled=false)
                    2024-05-24 10:49:14.141  - debug: modbus.4 (213280) Plugin sentry destroyed because not initialized correctly
                    2024-05-24 10:49:14.599  - info: modbus.4 (213280) starting. Version 6.2.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                    2024-05-24 10:49:15.614  - debug: modbus.4 (213280) Initialize Objects for disInputs: []
                    2024-05-24 10:49:15.616  - debug: modbus.4 (213280) Initialize Objects for coils: []
                    2024-05-24 10:49:15.617  - debug: modbus.4 (213280) Initialize Objects for inputRegs: []
                    2024-05-24 10:49:15.626  - debug: modbus.4 (213280) Initialize Objects for holdingRegs: [{"_address":40001,"name":"Device type","description":"Gerätetyp","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40001,"id":"holdingRegisters.40001_Device_type"},Gesamtscheinleistung","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40609,"id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power"},{"_address":40610,"name":"Grid-side frequency","description":"Grid Seite Frequenz","unit":"Hz","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40610,"id":"holdingRegisters.40610_Grid-side_frequency"},{"_address":40611,"name":"grid side inner current L1","description":"netzseitiger Innenstrom 1","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40678,"id":"holdingRegisters.40678_Dc_current_1"},{"_address":40679,"name":"Dc voltage 2","description":"Gleichspannung 2","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40679,"id":"holdingRegisters.40679_Dc_voltage_2"},{"_address":40680,"name":"Dc current 2","description":"Gleichstrom 2","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40680,"id":"holdingRegisters.40680_Dc_current_2"}]
                    2024-05-24 10:49:15.633  - debug: modbus.4 (213280) Add holdingRegisters.40001_Device_type: {"_id":"holdingRegisters.40001_Device_type","type":"state","common":{"name":"Gerätetyp","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40001,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.636  - debug: modbus.4 (213280) Add holdingRegisters.40004_Seriennummer: {"_id":"holdingRegisters.40004_Seriennummer","type":"state","common":{"name":"Seriennummer","role":"state","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":40004,"deviceId":4,"type":"string","len":5,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.637  - debug: modbus.4 (213280) Add holdingRegisters.40061_Fernsperre: {"_id":"holdingRegisters.40061_Fernsperre","type":"state","common":{"name":"Fernsperre","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40061,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40081_SchalterModus: {"_id":"holdingRegisters.40081_SchalterModus","type":"state","common":{"name":"SchalterModus","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40081,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.639  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40109_Max_A_Charge: {"_id":"holdingRegisters.40109_Max_A_Charge","type":"state","common":{"name":"Maximaler Ladestrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40109,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40110_Max_A_discharge: {"_id":"holdingRegisters.40110_Max_A_discharge","type":"state","common":{"name":"Max A Entladung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40110,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40116_ShutDown_battery_capacity_ShutDown: {"_id":"holdingRegisters.40116_ShutDown_battery_capacity_ShutDown","type":"state","common":{"name":"Abschalten Batteriekapazität Herunterfahren","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40116,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40117_Restart_battery_capacityRestart: {"_id":"holdingRegisters.40117_Restart_battery_capacityRestart","type":"state","common":{"name":"Neu starten BatteriekapazitätNeustart","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40117,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40118_LowBatt_battery_capacityLowBatt: {"_id":"holdingRegisters.40118_LowBatt_battery_capacityLowBatt","type":"state","common":{"name":"Low Batterie Anzeige zum Abschalten der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40118,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40130_Generator_is_charged_to_enable: {"_id":"holdingRegisters.40130_Generator_is_charged_to_enable","type":"state","common":{"name":"Generator is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40130,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40131_Grid_is_charged_to_enable: {"_id":"holdingRegisters.40131_Grid_is_charged_to_enable","type":"state","common":{"name":"Grid is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40131,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection: {"_id":"holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection","type":"state","common":{"name":"Begrenzen Sie die maximale Ausgangsleistung des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40144,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40145_External_current_sensor_clamp_phase: {"_id":"holdingRegisters.40145_External_current_sensor_clamp_phase","type":"state","common":{"name":"Klemmphase des externen Stromsensors","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40145,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40146_Solar_sell: {"_id":"holdingRegisters.40146_Solar_sell","type":"state","common":{"name":"  Verkauf von Solar","role":"switch","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40146,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40149_Sell_mode_time_point_1: {"_id":"holdingRegisters.40149_Sell_mode_time_point_1","type":"state","common":{"name":"Sell mode time point 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40149,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40150_Sell_mode_time_point_2: {"_id":"holdingRegisters.40150_Sell_mode_time_point_2","type":"state","common":{"name":"Sell mode time point 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40150,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40151_Sell_mode_time_point_3: {"_id":"holdingRegisters.40151_Sell_mode_time_point_3","type":"state","common":{"name":"Sell mode time point 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40151,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40152_Sell_mode_time_point_4: {"_id":"holdingRegisters.40152_Sell_mode_time_point_4","type":"state","common":{"name":"Sell mode time point 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40152,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40153_Sell_mode_time_point_5: {"_id":"holdingRegisters.40153_Sell_mode_time_point_5","type":"state","common":{"name":"Sell mode time point 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40153,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40154_Sell_mode_time_point_6: {"_id":"holdingRegisters.40154_Sell_mode_time_point_6","type":"state","common":{"name":"Sell mode time point 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40154,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40155_Sell_mode_Watt_time_1: {"_id":"holdingRegisters.40155_Sell_mode_Watt_time_1","type":"state","common":{"name":"Sell mode Watt time 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40155,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40156_Sell_mode_Watt_time_2: {"_id":"holdingRegisters.40156_Sell_mode_Watt_time_2","type":"state","common":{"name":"Sell mode Watt time 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40156,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40157_Sell_mode_Watt_time_3: {"_id":"holdingRegisters.40157_Sell_mode_Watt_time_3","type":"state","common":{"name":"Sell mode Watt time 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40157,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40158_Sell_mode_Watt_time_4: {"_id":"holdingRegisters.40158_Sell_mode_Watt_time_4","type":"state","common":{"name":"Sell mode Watt time 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40158,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40159_Sell_mode_Watt_time_5: {"_id":"holdingRegisters.40159_Sell_mode_Watt_time_5","type":"state","common":{"name":"Sell mode Watt time 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40159,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40160_Sell_mode_Watt_time_6: {"_id":"holdingRegisters.40160_Sell_mode_Watt_time_6","type":"state","common":{"name":"Sell mode Watt time 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40160,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40167_TOF_Cell_SOC_1: {"_id":"holdingRegisters.40167_TOF_Cell_SOC_1","type":"state","common":{"name":"TOF_Cell SOC 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40167,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40168_TOF_Cell_SOC_2: {"_id":"holdingRegisters.40168_TOF_Cell_SOC_2","type":"state","common":{"name":"TOF_Cell SOC 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40168,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40169_TOF_Cell_SOC_3: {"_id":"holdingRegisters.40169_TOF_Cell_SOC_3","type":"state","common":{"name":"TOF_Cell SOC 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40169,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40170_TOF_Cell_SOC_4: {"_id":"holdingRegisters.40170_TOF_Cell_SOC_4","type":"state","common":{"name":"TOF_Cell SOC 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40170,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40171_TOF_Cell_SOC_5: {"_id":"holdingRegisters.40171_TOF_Cell_SOC_5","type":"state","common":{"name":"TOF_Cell SOC 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40171,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40172_TOF_Cell_SOC_6: {"_id":"holdingRegisters.40172_TOF_Cell_SOC_6","type":"state","common":{"name":"TOF_Cell SOC 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40172,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40173_Time_point_1_charge_enable: {"_id":"holdingRegisters.40173_Time_point_1_charge_enable","type":"state","common":{"name":"Time point 1 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40173,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40174_Time_point_2_charge_enable: {"_id":"holdingRegisters.40174_Time_point_2_charge_enable","type":"state","common":{"name":"Time point 2 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40174,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40175_Time_point_3_charge_enable: {"_id":"holdingRegisters.40175_Time_point_3_charge_enable","type":"state","common":{"name":"Time point 3 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40175,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40176_Time_point_4_charge_enable: {"_id":"holdingRegisters.40176_Time_point_4_charge_enable","type":"state","common":{"name":"Time point 4 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40176,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40177_Time_point_5_charge_enable: {"_id":"holdingRegisters.40177_Time_point_5_charge_enable","type":"state","common":{"name":"Time point 5 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40177,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40178_Time_point_6_charge_enable: {"_id":"holdingRegisters.40178_Time_point_6_charge_enable","type":"state","common":{"name":"Time point 6 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40178,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei null einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40501_Status: {"_id":"holdingRegisters.40501_Status","type":"state","common":{"name":"Status (Standby, check, norm, altert, fault)","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40501,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40521_Day_Grid_Buy_Power_Wh: {"_id":"holdingRegisters.40521_Day_Grid_Buy_Power_Wh","type":"state","common":{"name":"Tag Netzabnahme Strom Wh","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40521,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40522_Day_GridSell_Power_Wh: {"_id":"holdingRegisters.40522_Day_GridSell_Power_Wh","type":"state","common":{"name":"Tages Verkaufs leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40522,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40530_Day_PV_Power_Wh: {"_id":"holdingRegisters.40530_Day_PV_Power_Wh","type":"state","common":{"name":"Tagesproduzierte leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40530,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40535_Total_PV_power_Wh_low_word: {"_id":"holdingRegisters.40535_Total_PV_power_Wh_low_word","type":"state","common":{"name":"Gesamt-PV-Leistung Wh niedriges Wort","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40535,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_AC_Relay: {"_id":"holdingRegisters.40553_AC_Relay","type":"state","common":{"name":"AC relay","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_Ac_relay_2: {"_id":"holdingRegisters.40553_Ac_relay_2","type":"state","common":{"name":"AC relay2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40587_battery_temperature: {"_id":"holdingRegisters.40587_battery_temperature","type":"state","common":{"name":"Batterietemperatur","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":40587,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40588_battery_voltage: {"_id":"holdingRegisters.40588_battery_voltage","type":"state","common":{"name":"Batteriespannung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40588,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40589_battery_capacity: {"_id":"holdingRegisters.40589_battery_capacity","type":"state","common":{"name":"Batteriekapazität","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40589,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40591_Battery_output_power: {"_id":"holdingRegisters.40591_Battery_output_power","type":"state","common":{"name":"Ausgangsleistung der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40591,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40592_Battery_output_current: {"_id":"holdingRegisters.40592_Battery_output_current","type":"state","common":{"name":"Ausgangsstrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40592,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40593_Corrected_AH: {"_id":"holdingRegisters.40593_Corrected_AH","type":"state","common":{"name":"AH korrigiert","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"AH"},"native":{"regType":"holdingRegs","address":40593,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40599_Grid_phase_voltage_A: {"_id":"holdingRegisters.40599_Grid_phase_voltage_A","type":"state","common":{"name":"Netzphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40599,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40600_Grid_phase_voltage_B: {"_id":"holdingRegisters.40600_Grid_phase_voltage_B","type":"state","common":{"name":"Netzphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40600,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40601_Grid_phase_voltage_C: {"_id":"holdingRegisters.40601_Grid_phase_voltage_C","type":"state","common":{"name":"Netzphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40601,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L1 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40605,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L2 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40606,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L3 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40607,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40608_active_power_from_side_to_side_of_the_grid: {"_id":"holdingRegisters.40608_active_power_from_side_to_side_of_the_grid","type":"state","common":{"name":"Wirkleistung von Seite zu Seite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40608,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40609_Grid_side_-_inside_total_apparent_power: {"_id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power","type":"state","common":{"name":"Netzseite – innere Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40609,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40610_Grid-side_frequency: {"_id":"holdingRegisters.40610_Grid-side_frequency","type":"state","common":{"name":"Grid Seite Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40610,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40611_grid_side_inner_current_L1: {"_id":"holdingRegisters.40611_grid_side_inner_current_L1","type":"state","common":{"name":"netzseitiger Innenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40611,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40612_grid_side_inner_current_L2: {"_id":"holdingRegisters.40612_grid_side_inner_current_L2","type":"state","common":{"name":"netzseitiger Innenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40612,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40613_grid_side_inner_current_L3: {"_id":"holdingRegisters.40613_grid_side_inner_current_L3","type":"state","common":{"name":"netzseitiger Innenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40613,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40614_Out-of-grid_-_current_L1: {"_id":"holdingRegisters.40614_Out-of-grid_-_current_L1","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40614,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40615_Out-of-grid_-_current_L2: {"_id":"holdingRegisters.40615_Out-of-grid_-_current_L2","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40615,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40616_Out-of-grid_-_current_L3: {"_id":"holdingRegisters.40616_Out-of-grid_-_current_L3","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40616,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40617_A_Out-of-grid_-power_L1: {"_id":"holdingRegisters.40617_A_Out-of-grid_-power_L1","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40617,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40618_A_Out-of-grid_-power_L2: {"_id":"holdingRegisters.40618_A_Out-of-grid_-power_L2","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40618,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40619_A_Out-of-grid_-power_L3: {"_id":"holdingRegisters.40619_A_Out-of-grid_-power_L3","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40619,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40620_Out-of-grid_–total_power: {"_id":"holdingRegisters.40620_Out-of-grid_–total_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40620,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40621_Out-of-grid_–total_apparent_power: {"_id":"holdingRegisters.40621_Out-of-grid_–total_apparent_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40621,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40622_Grid-connected_power_factor_PF: {"_id":"holdingRegisters.40622_Grid-connected_power_factor_PF","type":"state","common":{"name":"Netzgekoppelter Leistungsfaktor PF","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40622,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40623_Grid_side_A-phase_power: {"_id":"holdingRegisters.40623_Grid_side_A-phase_power","type":"state","common":{"name":"Netzseitiger L1-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40623,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40624_Grid_side_B-phase_power: {"_id":"holdingRegisters.40624_Grid_side_B-phase_power","type":"state","common":{"name":"Netzseitiger L2-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40624,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40625_Grid_side_C-phase_power: {"_id":"holdingRegisters.40625_Grid_side_C-phase_power","type":"state","common":{"name":"Netzseitiger L3-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40625,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40626_Grid_side_total_power: {"_id":"holdingRegisters.40626_Grid_side_total_power","type":"state","common":{"name":"Netzseitige Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40626,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40628_Inverter_output_phase_voltage_A: {"_id":"holdingRegisters.40628_Inverter_output_phase_voltage_A","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40628,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40629_Inverter_output_phase_voltage_B: {"_id":"holdingRegisters.40629_Inverter_output_phase_voltage_B","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40629,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40630_Inverter_output_phase_voltage_C: {"_id":"holdingRegisters.40630_Inverter_output_phase_voltage_C","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40630,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40631_Inverter_output_phase_current_A: {"_id":"holdingRegisters.40631_Inverter_output_phase_current_A","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40631,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40632_Inverter_output_phase_current_B: {"_id":"holdingRegisters.40632_Inverter_output_phase_current_B","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40632,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.657  - debug: modbus.4 (213280) Add holdingRegisters.40633_Inverter_output_phase_current_C: {"_id":"holdingRegisters.40633_Inverter_output_phase_current_C","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40633,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.659  - debug: modbus.4 (213280) Add holdingRegisters.40634_Inverter_output_phase_power_A: {"_id":"holdingRegisters.40634_Inverter_output_phase_power_A","type":"state","common":{"name":"  Ausgangsphase des Wechselrichters Macht L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40634,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.660  - debug: modbus.4 (213280) Add holdingRegisters.40635_Inverter_output_phase_power_B: {"_id":"holdingRegisters.40635_Inverter_output_phase_power_B","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Macht L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40635,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40636_Inverter_output_phase_power_C: {"_id":"holdingRegisters.40636_Inverter_output_phase_power_C","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40636,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40637_Inverter_output_total_power: {"_id":"holdingRegisters.40637_Inverter_output_total_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40637,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40638_Inverter_output_total_apparent_power: {"_id":"holdingRegisters.40638_Inverter_output_total_apparent_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Scheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40638,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40639_Inverter_frequency: {"_id":"holdingRegisters.40639_Inverter_frequency","type":"state","common":{"name":"Wechselrichter frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40639,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40641_UPS_load-side_phase_power_A: {"_id":"holdingRegisters.40641_UPS_load-side_phase_power_A","type":"state","common":{"name":"USV-lastseitige Phasenleistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40641,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40642_UPS_load-side_phase_power_B: {"_id":"holdingRegisters.40642_UPS_load-side_phase_power_B","type":"state","common":{"name":"USV-lastseitige Phasenleistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40642,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40643_UPS_load-side_phase_power_C: {"_id":"holdingRegisters.40643_UPS_load-side_phase_power_C","type":"state","common":{"name":"USV-lastseitige Phasenleistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40643,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40644_UPS_load-sidetotal_power: {"_id":"holdingRegisters.40644_UPS_load-sidetotal_power","type":"state","common":{"name":"Lastseitige Gesamtleistung der USV","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40644,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40645_Load_phase_voltage_A: {"_id":"holdingRegisters.40645_Load_phase_voltage_A","type":"state","common":{"name":"Load phasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40645,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40646_Load_phase_voltage_B: {"_id":"holdingRegisters.40646_Load_phase_voltage_B","type":"state","common":{"name":"Load phasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40646,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40647_Load_phase_voltage_C: {"_id":"holdingRegisters.40647_Load_phase_voltage_C","type":"state","common":{"name":"Load phasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40647,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40648_Load_phase_current_A: {"_id":"holdingRegisters.40648_Load_phase_current_A","type":"state","common":{"name":"Load phasenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40648,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40649_Load_phase_current_B: {"_id":"holdingRegisters.40649_Load_phase_current_B","type":"state","common":{"name":"Load phasenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40649,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40650_Load_phase_current_C: {"_id":"holdingRegisters.40650_Load_phase_current_C","type":"state","common":{"name":"Load phasenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40650,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                    2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40651_Load_phase_power_A: {"_id":"holdingRegisters.40651_Load_phase_power_A","type":"state","common":{"name":"Load phase Leistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40651,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40652_Load_phase_power_B: {"_id":"holdingRegisters.40652_Load_phase_power_B","type":"state","common":{"name":"Load phase Leistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40652,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40653_Load_phase_power_C: {"_id":"holdingRegisters.40653_Load_phase_power_C","type":"state","common":{"name":"Load phase Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40653,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40654_Load_totalpower: {"_id":"holdingRegisters.40654_Load_totalpower","type":"state","common":{"name":"Load Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40654,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40655_Load_phase_apparent_power: {"_id":"holdingRegisters.40655_Load_phase_apparent_power","type":"state","common":{"name":"Scheinleistung der Lastphase","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40655,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40656_Load_frequency: {"_id":"holdingRegisters.40656_Load_frequency","type":"state","common":{"name":"Load Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40656,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40662_Phase_voltage_of_Gen_port_A: {"_id":"holdingRegisters.40662_Phase_voltage_of_Gen_port_A","type":"state","common":{"name":"Phasenspannung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40662,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40663_Phase_voltage_of_Gen_port_B: {"_id":"holdingRegisters.40663_Phase_voltage_of_Gen_port_B","type":"state","common":{"name":"Phasenspannung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40663,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40664_Phase_voltage_of_Gen_port_C: {"_id":"holdingRegisters.40664_Phase_voltage_of_Gen_port_C","type":"state","common":{"name":"Phasenspannung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40664,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40665_Phase_power_of_Gen_port_A: {"_id":"holdingRegisters.40665_Phase_power_of_Gen_port_A","type":"state","common":{"name":"Phasenleistung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40665,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40666_Phase_power_of_Gen_port_B: {"_id":"holdingRegisters.40666_Phase_power_of_Gen_port_B","type":"state","common":{"name":"Phasenleistung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40666,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40667_Phase_power_of_Gen_port_C: {"_id":"holdingRegisters.40667_Phase_power_of_Gen_port_C","type":"state","common":{"name":"Phasenleistung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40667,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40668_total_power_of_Gen_port: {"_id":"holdingRegisters.40668_total_power_of_Gen_port","type":"state","common":{"name":"Gesamtleistung des Gen-Ports","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40668,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40673_PV1_input_power: {"_id":"holdingRegisters.40673_PV1_input_power","type":"state","common":{"name":"PV1 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40673,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40674_PV2_input_power: {"_id":"holdingRegisters.40674_PV2_input_power","type":"state","common":{"name":"PV2 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40674,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                    2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40677_Dc_voltage_1: {"_id":"holdingRegisters.40677_Dc_voltage_1","type":"state","common":{"name":"Gleichspannung 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40677,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40678_Dc_current_1: {"_id":"holdingRegisters.40678_Dc_current_1","type":"state","common":{"name":"Gleichstrom 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40678,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40679_Dc_voltage_2: {"_id":"holdingRegisters.40679_Dc_voltage_2","type":"state","common":{"name":"Gleichspannung 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40679,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40680_Dc_current_2: {"_id":"holdingRegisters.40680_Dc_current_2","type":"state","common":{"name":"Gleichstrom 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40680,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                    2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40620_Out-of-grid__total_power
                    2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
                    2024-05-24 10:49:18.765  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40620_Out-of-grid_–total_power changed to modbus.4.holdingRegisters.40620_Out-of-grid__total_power
                    2024-05-24 10:49:18.777  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40621_Out-of-grid_–total_apparent_power changed to modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
                    2024-05-24 10:49:22.213  - info: modbus.4 (213280) Connected to slave 192.168.178.238
                    2024-05-24 10:49:22.214  - debug: modbus.4 (213280) [DevID_4] Poll start ---------------------
                    2024-05-24 10:49:22.215  - debug: modbus.4 (213280) Initialization of scale factors done!
                    2024-05-24 10:49:22.215  - debug: modbus.4 (213280) [DevID_4/holdingRegs] Poll address 40001 - 8 registers
                    2024-05-24 10:49:27.221  - warn: modbus.4 (213280) Error: undefined
                    2024-05-24 10:49:27.222  - error: modbus.4 (213280) Request timed out.
                    2024-05-24 10:49:27.222  - error: modbus.4 (213280) Client in error state.
                    2024-05-24 10:49:27.222  - warn: modbus.4 (213280) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                    2024-05-24 10:49:27.223  - debug: modbus.4 (213280) Socket closed with error
                    2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Clearing timeout of the current request.
                    2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Cleaning up request fifo.
                    2024-05-24 10:49:28.222  - debug: modbus.4 (213280) Closing client on purpose.
                    2024-05-24 10:49:28.223  - info: modbus.4 (213280) Disconnected from slave 192.168.178.238
                    
                    

                    Angeschlossen am Deye Modbus Ausgang mit Firmware:
                    d1a96c7e-2622-4aa6-bb76-06240a571d6a-grafik.png

                    Der Waveshare funktioniert an einem anderen Modbus Device einwandfrei.

                    Jemand noch eine Idee wo das Problem liegen könnte?

                    W Offline
                    W Offline
                    warp735
                    schrieb am zuletzt editiert von warp735
                    #150

                    @wendy2702
                    Testen immer nur mit EINEM Datenpunkt... Woher diese komplett falsch konfigurierten Register kommen, ist mir immer noch schleierhaft. Man sollte diesen Thread auch lesen ;-)
                    Ich hab ALLE Register auf Signed 16 bit

                    PS: du hast RTU over TCP, oder?

                    Snag_1040fdd.png

                    wendy2702W 1 Antwort Letzte Antwort
                    0
                    • W warp735

                      @wendy2702
                      Testen immer nur mit EINEM Datenpunkt... Woher diese komplett falsch konfigurierten Register kommen, ist mir immer noch schleierhaft. Man sollte diesen Thread auch lesen ;-)
                      Ich hab ALLE Register auf Signed 16 bit

                      PS: du hast RTU over TCP, oder?

                      Snag_1040fdd.png

                      wendy2702W Offline
                      wendy2702W Offline
                      wendy2702
                      schrieb am zuletzt editiert von wendy2702
                      #151

                      @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                      Man sollte diesen Thread auch lesen

                      Den habe ich gelesen und hier stehen soviele verschiedene "Register" das ich mir am Ende das aud der Github Sammlung genommen habe.

                      @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                      @wendy2702
                      Testen immer nur mit EINEM Datenpunkt...

                      Auch das habe ich schon hinter mir.

                      @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                      PS: du hast RTU over TCP, oder?

                      Ja, macht der Waveshare

                      Wenn du eine dreistellige Register Adresse verwendest kann ich nur Raten das du den Haken bei "benutze Aliase" an hast ?

                      Bitte keine Fragen per PN, die gehören ins Forum!

                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                      W 1 Antwort Letzte Antwort
                      0
                      • wendy2702W wendy2702

                        @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                        Man sollte diesen Thread auch lesen

                        Den habe ich gelesen und hier stehen soviele verschiedene "Register" das ich mir am Ende das aud der Github Sammlung genommen habe.

                        @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                        @wendy2702
                        Testen immer nur mit EINEM Datenpunkt...

                        Auch das habe ich schon hinter mir.

                        @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                        PS: du hast RTU over TCP, oder?

                        Ja, macht der Waveshare

                        Wenn du eine dreistellige Register Adresse verwendest kann ich nur Raten das du den Haken bei "benutze Aliase" an hast ?

                        W Offline
                        W Offline
                        warp735
                        schrieb am zuletzt editiert von warp735
                        #152

                        @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                        Ja, macht der Waveshare

                        Und warum stellst denn bei iob was anderes ein?

                        @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                        kann ich nur Raten das du den Haken bei "benutze Aliase" an hast ?

                        Nope:
                        Snag_111c2c3.png

                        wendy2702W 1 Antwort Letzte Antwort
                        0
                        • W warp735

                          @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                          Ja, macht der Waveshare

                          Und warum stellst denn bei iob was anderes ein?

                          @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                          kann ich nur Raten das du den Haken bei "benutze Aliase" an hast ?

                          Nope:
                          Snag_111c2c3.png

                          wendy2702W Offline
                          wendy2702W Offline
                          wendy2702
                          schrieb am zuletzt editiert von wendy2702
                          #153

                          @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                          Und warum stellst denn bei iob was anderes ein?

                          Weil eigentlich nur einer Umwandelt, iob oder Waveshare. Zumindest ist das bei meinen anderen Waveshare Modbus sachen so.

                          Dein Register 598 lässt sich zumindest per iob und Serieller Verbindung auslesen.

                          Gibt es hier irgendwo einen Export deiner Register?

                          EDIT: @warp735 es läuft. Die 5 Stelligen Register sind nicht "falsch", man muss dann nur den Haken bei "Benutze Aliase" setzen. Dann werden im Hintergrund die 3 stelligen verwendet.

                          So sind jetzt meine Einstellungen im Waveshare:

                          b4e6562c-277a-4fa4-afd0-5bb98ccb3034-grafik.png

                          und so in IOB:

                          7bbff636-a3fd-4aa5-b937-d151941aea27-grafik.png

                          258034e9-596e-48d1-87cd-5a90f51f6dd4-grafik.png

                          Hier nochmal der Export der Register welche aber exact der Liste von @TheBam entsprechen:

                          _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                          40001	Device type	Gerätetyp		uint16be	1	0	0		level		true	false	false	false
                          40004	Seriennummer	Seriennummer		string	5	0	0		state		true	false	false	false
                          40061	Fernsperre	Fernsperre		uint16be	1	0	0		level		true	false	false	false
                          40081	SchalterModus	SchalterModus		uint16be	1	0	0		level		true	false	false	false
                          40105	ZeroExport power	ZeroExport-Leistung	W	int16be	1	0	0		level		true	false	false	false
                          40105	ZeroExport power	ZeroExport-Leistung		floatbe	2	0	0		level		true	false	false	false
                          40109	Max A Charge	Maximaler Ladestrom der Batterie	A	uint16be	1	0	0		level		true	false	false	false
                          40110	Max A discharge	Max A Entladung	A	uint16be	1	0	0		level		true	false	false	false
                          40116	ShutDown battery capacity ShutDown	Abschalten Batteriekapazität Herunterfahren	%	uint16be	1	1	0		level		true	false	false	false
                          40117	Restart battery capacityRestart	Neu starten BatteriekapazitätNeustart	%	uint16be	1	1	0		level		true	false	false	false
                          40118	LowBatt battery capacityLowBatt	Low Batterie Anzeige zum Abschalten der Batterie	%	uint16be	1	1	0		level		true	false	false	false
                          40130	Generator is charged to enable	Generator is charged to enable		int16be	1	0	0		level		true	false	false	false
                          40131	Grid is charged to enable	Grid is charged to enable		int16be	1	0	0		level		true	false	false	false
                          40144	Max Limit Power Output Grid Connection	Begrenzen Sie die maximale Ausgangsleistung des Netzes	W	uint16be	1	0	0		level		true	false	false	false
                          40145	"External	current	sensor clamp phase"	Klemmphase des externen Stromsensors	W	uint16be	1	0	0		level		true	false	false	false
                          40146	Solar sell	  Verkauf von Solar		floatbe	2	0	0		switch		true	false	false	false
                          40149	Sell mode time point 1	Sell mode time point 1		int16be	1	0	0		level		true	false	false	false
                          40150	Sell mode time point 2	Sell mode time point 2		int16be	1	0	0		level		true	false	false	false
                          40151	Sell mode time point 3	Sell mode time point 3		int16be	1	0	0		level		true	false	false	false
                          40152	Sell mode time point 4	Sell mode time point 4		int16be	1	0	0		level		true	false	false	false
                          40153	Sell mode time point 5	Sell mode time point 5		int16be	1	0	0		level		true	false	false	false
                          40154	Sell mode time point 6	Sell mode time point 6		int16be	1	0	0		level		true	false	false	false
                          40155	Sell mode Watt time 1	Sell mode Watt time 1		int16be	1	0	0		level		true	false	false	false
                          40156	Sell mode Watt time 2	Sell mode Watt time 2		int16be	1	0	0		level		true	false	false	false
                          40157	Sell mode Watt time 3	Sell mode Watt time 3		int16be	1	0	0		level		true	false	false	false
                          40158	Sell mode Watt time 4	Sell mode Watt time 4		int16be	1	0	0		level		true	false	false	false
                          40159	Sell mode Watt time 5	Sell mode Watt time 5		int16be	1	0	0		level		true	false	false	false
                          40160	Sell mode Watt time 6	Sell mode Watt time 6		int16be	1	0	0		level		true	false	false	false
                          40167	TOF_Cell SOC 1	TOF_Cell SOC 1	%	int16be	1	0	0		level		true	false	false	false
                          40168	TOF_Cell SOC 2	TOF_Cell SOC 2	%	int16be	1	0	0		level		true	false	false	false
                          40169	TOF_Cell SOC 3	TOF_Cell SOC 3	%	int16be	1	0	0		level		true	false	false	false
                          40170	TOF_Cell SOC 4	TOF_Cell SOC 4	%	int16be	1	0	0		level		true	false	false	false
                          40171	TOF_Cell SOC 5	TOF_Cell SOC 5	%	int16be	1	0	0		level		true	false	false	false
                          40172	TOF_Cell SOC 6	TOF_Cell SOC 6	%	int16be	1	0	0		level		true	false	false	false
                          40173	Time point 1 charge enable	Time point 1 charge enable		int16be	1	0	0		level		true	false	false	false
                          40174	Time point 2 charge enable	Time point 2 charge enable		int16be	1	0	0		level		true	false	false	false
                          40175	Time point 3 charge enable	Time point 3 charge enable		int16be	1	0	0		level		true	false	false	false
                          40176	Time point 4 charge enable	Time point 4 charge enable		int16be	1	0	0		level		true	false	false	false
                          40177	Time point 5 charge enable	Time point 5 charge enable		int16be	1	0	0		level		true	false	false	false
                          40178	Time point 6 charge enable	Time point 6 charge enable		int16be	1	0	0		level		true	false	false	false
                          40341	Max Solar Sell Power at Zero grid	Maximale Solarverkaufsleistung bei null einspeisung	W	uint16be	1	0	0		level		true	false	false	false
                          40341	Max Solar Sell Power by full in	Maximale Solarverkaufsleistung bei einspeisung	W	uint16be	1	0	0		level		true	false	false	false
                          40501	Status	Status (Standby, check, norm, altert, fault)		int16be	1	0	0		level		true	false	false	false
                          40521	Day Grid Buy Power Wh	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                          40522	Day_GridSell_Power Wh	Tages Verkaufs leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                          40530	Day_PV_Power Wh	Tagesproduzierte leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                          40535	Total PV power Wh low word	Gesamt-PV-Leistung Wh niedriges Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
                          40553	AC Relay	AC relay		uint16be	1	0	0	x < 2? 0:1	level		true	false	false	false
                          40553	Ac relay 2	AC relay2		uint16be	1		0		level		true	false	false	false
                          40587	battery temperature	Batterietemperatur	°C	uint16be	1	0,01	0		level		true	false	false	false
                          40588	battery voltage	Batteriespannung	V	uint16be	1	0,01	0		level		true	false	false	false
                          40589	battery capacity	Batteriekapazität	%	uint16be	1	1	0		level		true	false	false	false
                          40591	Battery output power	Ausgangsleistung der Batterie	W	int16be	1	1	0		level		true	false	false	false
                          40592	Battery output current	Ausgangsstrom der Batterie	A	uint16be	1	0,01	0		level		true	false	false	false
                          40593	Corrected AH	AH korrigiert	AH	uint16be	1	1	0		level		true	false	false	false
                          40599	Grid phase voltage A	Netzphasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                          40600	Grid phase voltage B	Netzphasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                          40601	Grid phase voltage C	Netzphasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                          40605	L1 phase power on the inner side of the grid	L1 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                          40606	L2 phase power on the inner side of the grid	L2 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                          40607	L3 phase power on the inner side of the grid	L3 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                          40608	active power from side to side of the grid	Wirkleistung von Seite zu Seite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                          40609	Grid side - inside total apparent power	Netzseite – innere Gesamtscheinleistung	W	uint16be	1	1	0		level		true	false	false	false
                          40610	Grid-side frequency	Grid Seite Frequenz	Hz	uint16be	1	1	0		level		true	false	false	false
                          40611	grid side inner current L1	netzseitiger Innenstrom L1	A	uint16be	1	0,01	0		level		true	false	false	false
                          40612	grid side inner current L2	netzseitiger Innenstrom L2	A	uint16be	1	0,01	0		level		true	false	false	false
                          40613	grid side inner current L3	netzseitiger Innenstrom L3	A	uint16be	1	0,01	0		level		true	false	false	false
                          40614	Out-of-grid - current L1	Außerhalb des Netzes – aktuelles L1	A	uint16be	1	0,01	0		level		true	false	false	false
                          40615	Out-of-grid - current L2	Außerhalb des Netzes – aktuelles L2	A	uint16be	1	0,01	0		level		true	false	false	false
                          40616	Out-of-grid - current L3	Außerhalb des Netzes – aktuelles L3	A	uint16be	1	0,01	0		level		true	false	false	false
                          40617	A Out-of-grid -power L1	A Außerhalb des Netzes - Strom L1	W	uint16be	1	1	0		level		true	false	false	false
                          40618	A Out-of-grid -power L2	A Außerhalb des Netzes - Strom L2	W	uint16be	1	1	0		level		true	false	false	false
                          40619	A Out-of-grid -power L3	A Außerhalb des Netzes - Strom L3	W	uint16be	1	1	0		level		true	false	false	false
                          40620	Out-of-grid -total power	Außerhalb des Netzes - Gesamtleistung	W	uint16be	1	1	0		level		true	false	false	false
                          40621	Out-of-grid - total apparent power	Außerhalb des Netzes - Gesamtscheinleistung	VA	uint16be	1	1	0		level		true	false	false	false
                          40622	Grid-connected power factor PF	Netzgekoppelter Leistungsfaktor PF		uint16be	1	1	0		level		true	false	false	false
                          40623	Grid side A-phase power	Netzseitiger L1-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                          40624	Grid side B-phase power	Netzseitiger L2-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                          40625	Grid side C-phase power	Netzseitiger L3-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                          40626	Grid side total power	Netzseitige Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                          40628	Inverter output phase voltage A	Wechselrichter-Ausgangsphasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                          40629	Inverter output phase voltage B	Wechselrichter-Ausgangsphasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                          40630	Inverter output phase voltage C	Wechselrichter-Ausgangsphasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                          40631	Inverter output phase current A	Ausgangsphasenstrom des Wechselrichters L1	A	uint16be	1	0,01	0		level		true	false	false	false
                          40632	Inverter output phase current B	Ausgangsphasenstrom des Wechselrichters L2	A	uint16be	1	0,01	0		level		true	false	false	false
                          40633	Inverter output phase current C	Ausgangsphasenstrom des Wechselrichters L3	A	uint16be	1	0,01	0		level		true	false	false	false
                          40634	Inverter output phase power A	  Ausgangsphase des Wechselrichters Macht L1	W	uint16be	1	0	0		level		true	false	false	false
                          40635	Inverter output phase power B	Ausgangsphase des Wechselrichters Macht L2	W	uint16be	1	0	0		level		true	false	false	false
                          40636	Inverter output phase power C	Ausgangsphase des Wechselrichters Leistung L3	W	uint16be	1	0	0		level		true	false	false	false
                          40637	Inverter output total power	Gesamtleistung des Wechselrichters Leistung	W	uint16be	1	0	0		level		true	false	false	false
                          40638	Inverter output total apparent power	Gesamtleistung des Wechselrichters Scheinleistung	W	uint16be	1	0	0		level		true	false	false	false
                          40639	Inverter frequency	Wechselrichter frequenz	Hz	uint16be	1	0,01	0		level		true	false	false	false
                          40641	UPS load-side phase power A	USV-lastseitige Phasenleistung L1	W	uint16be	1	1	0		level		true	false	false	false
                          40642	UPS load-side phase power B	USV-lastseitige Phasenleistung L2	W	uint16be	1	1	0		level		true	false	false	false
                          40643	UPS load-side phase power C	USV-lastseitige Phasenleistung L3	W	uint16be	1	1	0		level		true	false	false	false
                          40644	UPS load-sidetotal power	Lastseitige Gesamtleistung der USV	W	uint16be	1	1	0		level		true	false	false	false
                          40645	Load phase voltage A	Load phasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                          40646	Load phase voltage B	Load phasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                          40647	Load phase voltage C	Load phasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                          40648	Load phase current A	Load phasenstrom L1	A	uint16be	1	0,01	0		level		true	false	false	false
                          40649	Load phase current B	Load phasenstrom L2	A	uint16be	1	0,01	0		level		true	false	false	false
                          40650	Load phase current C	Load phasenstrom L3	A	uint16be	1	0,01	0		level		true	false	false	false
                          40651	Load phase power A	Load phase Leistung L1	W	uint16be	1	1	0		level		true	false	false	false
                          40652	Load phase power B	Load phase Leistung L2	W	uint16be	1	1	0		level		true	false	false	false
                          40653	Load phase power C	Load phase Leistung L3	W	uint16be	1	1	0		level		true	false	false	false
                          40654	Load totalpower	Load Gesamtleistung	W	uint16be	1	1	0		level		true	false	false	false
                          40655	Load phase apparent power	Scheinleistung der Lastphase	VA	uint16be	1	1	0		level		true	false	false	false
                          40656	Load frequency	Load Frequenz	Hz	uint16be	1	1	0		level		true	false	false	false
                          40662	Phase voltage of Gen port A	Phasenspannung von Gen-Port L1	V	uint16be	1	0,1	0		level		true	false	false	false
                          40663	Phase voltage of Gen port B	Phasenspannung von Gen-Port L2	V	uint16be	1	0,1	0		level		true	false	false	false
                          40664	Phase voltage of Gen port C	Phasenspannung von Gen-Port L3	V	uint16be	1	0,1	0		level		true	false	false	false
                          40665	Phase power of Gen port A	Phasenleistung von Gen-Port L1	W	uint16be	1	1	0		level		true	false	false	false
                          40666	Phase power of Gen port B	Phasenleistung von Gen-Port L2	W	uint16be	1	1	0		level		true	false	false	false
                          40667	Phase power of Gen port C	Phasenleistung von Gen-Port L3	W	uint16be	1	1	0		level		true	false	false	false
                          40668	total power of Gen port	Gesamtleistung des Gen-Ports	W	uint16be	1	1	0		level		true	false	false	false
                          40673	PV1 input power	PV1 Eingangsleistung	W	uint16be	1	1	0		level		true	false	false	false
                          40674	PV2 input power	PV2 Eingangsleistung	W	uint16be	1	1	0		level		true	false	false	false
                          40677	Dc voltage 1	Gleichspannung 1	V	uint16be	1	0,1	0		level		true	false	false	false
                          40678	Dc current 1	Gleichstrom 1	A	uint16be	1	0,1	0		level		true	false	false	false
                          40679	Dc voltage 2	Gleichspannung 2	V	uint16be	1	0,1	0		level		true	false	false	false
                          40680	Dc current 2	Gleichstrom 2	A	uint16be	1	0,1	0		level		true	false	false	false
                          

                          Bitte keine Fragen per PN, die gehören ins Forum!

                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                          W T 2 Antworten Letzte Antwort
                          0
                          • wendy2702W wendy2702

                            @warp735 sagte in Deye Wechselrichter Modbus Register beschreiben:

                            Und warum stellst denn bei iob was anderes ein?

                            Weil eigentlich nur einer Umwandelt, iob oder Waveshare. Zumindest ist das bei meinen anderen Waveshare Modbus sachen so.

                            Dein Register 598 lässt sich zumindest per iob und Serieller Verbindung auslesen.

                            Gibt es hier irgendwo einen Export deiner Register?

                            EDIT: @warp735 es läuft. Die 5 Stelligen Register sind nicht "falsch", man muss dann nur den Haken bei "Benutze Aliase" setzen. Dann werden im Hintergrund die 3 stelligen verwendet.

                            So sind jetzt meine Einstellungen im Waveshare:

                            b4e6562c-277a-4fa4-afd0-5bb98ccb3034-grafik.png

                            und so in IOB:

                            7bbff636-a3fd-4aa5-b937-d151941aea27-grafik.png

                            258034e9-596e-48d1-87cd-5a90f51f6dd4-grafik.png

                            Hier nochmal der Export der Register welche aber exact der Liste von @TheBam entsprechen:

                            _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                            40001	Device type	Gerätetyp		uint16be	1	0	0		level		true	false	false	false
                            40004	Seriennummer	Seriennummer		string	5	0	0		state		true	false	false	false
                            40061	Fernsperre	Fernsperre		uint16be	1	0	0		level		true	false	false	false
                            40081	SchalterModus	SchalterModus		uint16be	1	0	0		level		true	false	false	false
                            40105	ZeroExport power	ZeroExport-Leistung	W	int16be	1	0	0		level		true	false	false	false
                            40105	ZeroExport power	ZeroExport-Leistung		floatbe	2	0	0		level		true	false	false	false
                            40109	Max A Charge	Maximaler Ladestrom der Batterie	A	uint16be	1	0	0		level		true	false	false	false
                            40110	Max A discharge	Max A Entladung	A	uint16be	1	0	0		level		true	false	false	false
                            40116	ShutDown battery capacity ShutDown	Abschalten Batteriekapazität Herunterfahren	%	uint16be	1	1	0		level		true	false	false	false
                            40117	Restart battery capacityRestart	Neu starten BatteriekapazitätNeustart	%	uint16be	1	1	0		level		true	false	false	false
                            40118	LowBatt battery capacityLowBatt	Low Batterie Anzeige zum Abschalten der Batterie	%	uint16be	1	1	0		level		true	false	false	false
                            40130	Generator is charged to enable	Generator is charged to enable		int16be	1	0	0		level		true	false	false	false
                            40131	Grid is charged to enable	Grid is charged to enable		int16be	1	0	0		level		true	false	false	false
                            40144	Max Limit Power Output Grid Connection	Begrenzen Sie die maximale Ausgangsleistung des Netzes	W	uint16be	1	0	0		level		true	false	false	false
                            40145	"External	current	sensor clamp phase"	Klemmphase des externen Stromsensors	W	uint16be	1	0	0		level		true	false	false	false
                            40146	Solar sell	  Verkauf von Solar		floatbe	2	0	0		switch		true	false	false	false
                            40149	Sell mode time point 1	Sell mode time point 1		int16be	1	0	0		level		true	false	false	false
                            40150	Sell mode time point 2	Sell mode time point 2		int16be	1	0	0		level		true	false	false	false
                            40151	Sell mode time point 3	Sell mode time point 3		int16be	1	0	0		level		true	false	false	false
                            40152	Sell mode time point 4	Sell mode time point 4		int16be	1	0	0		level		true	false	false	false
                            40153	Sell mode time point 5	Sell mode time point 5		int16be	1	0	0		level		true	false	false	false
                            40154	Sell mode time point 6	Sell mode time point 6		int16be	1	0	0		level		true	false	false	false
                            40155	Sell mode Watt time 1	Sell mode Watt time 1		int16be	1	0	0		level		true	false	false	false
                            40156	Sell mode Watt time 2	Sell mode Watt time 2		int16be	1	0	0		level		true	false	false	false
                            40157	Sell mode Watt time 3	Sell mode Watt time 3		int16be	1	0	0		level		true	false	false	false
                            40158	Sell mode Watt time 4	Sell mode Watt time 4		int16be	1	0	0		level		true	false	false	false
                            40159	Sell mode Watt time 5	Sell mode Watt time 5		int16be	1	0	0		level		true	false	false	false
                            40160	Sell mode Watt time 6	Sell mode Watt time 6		int16be	1	0	0		level		true	false	false	false
                            40167	TOF_Cell SOC 1	TOF_Cell SOC 1	%	int16be	1	0	0		level		true	false	false	false
                            40168	TOF_Cell SOC 2	TOF_Cell SOC 2	%	int16be	1	0	0		level		true	false	false	false
                            40169	TOF_Cell SOC 3	TOF_Cell SOC 3	%	int16be	1	0	0		level		true	false	false	false
                            40170	TOF_Cell SOC 4	TOF_Cell SOC 4	%	int16be	1	0	0		level		true	false	false	false
                            40171	TOF_Cell SOC 5	TOF_Cell SOC 5	%	int16be	1	0	0		level		true	false	false	false
                            40172	TOF_Cell SOC 6	TOF_Cell SOC 6	%	int16be	1	0	0		level		true	false	false	false
                            40173	Time point 1 charge enable	Time point 1 charge enable		int16be	1	0	0		level		true	false	false	false
                            40174	Time point 2 charge enable	Time point 2 charge enable		int16be	1	0	0		level		true	false	false	false
                            40175	Time point 3 charge enable	Time point 3 charge enable		int16be	1	0	0		level		true	false	false	false
                            40176	Time point 4 charge enable	Time point 4 charge enable		int16be	1	0	0		level		true	false	false	false
                            40177	Time point 5 charge enable	Time point 5 charge enable		int16be	1	0	0		level		true	false	false	false
                            40178	Time point 6 charge enable	Time point 6 charge enable		int16be	1	0	0		level		true	false	false	false
                            40341	Max Solar Sell Power at Zero grid	Maximale Solarverkaufsleistung bei null einspeisung	W	uint16be	1	0	0		level		true	false	false	false
                            40341	Max Solar Sell Power by full in	Maximale Solarverkaufsleistung bei einspeisung	W	uint16be	1	0	0		level		true	false	false	false
                            40501	Status	Status (Standby, check, norm, altert, fault)		int16be	1	0	0		level		true	false	false	false
                            40521	Day Grid Buy Power Wh	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                            40522	Day_GridSell_Power Wh	Tages Verkaufs leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                            40530	Day_PV_Power Wh	Tagesproduzierte leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                            40535	Total PV power Wh low word	Gesamt-PV-Leistung Wh niedriges Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
                            40553	AC Relay	AC relay		uint16be	1	0	0	x < 2? 0:1	level		true	false	false	false
                            40553	Ac relay 2	AC relay2		uint16be	1		0		level		true	false	false	false
                            40587	battery temperature	Batterietemperatur	°C	uint16be	1	0,01	0		level		true	false	false	false
                            40588	battery voltage	Batteriespannung	V	uint16be	1	0,01	0		level		true	false	false	false
                            40589	battery capacity	Batteriekapazität	%	uint16be	1	1	0		level		true	false	false	false
                            40591	Battery output power	Ausgangsleistung der Batterie	W	int16be	1	1	0		level		true	false	false	false
                            40592	Battery output current	Ausgangsstrom der Batterie	A	uint16be	1	0,01	0		level		true	false	false	false
                            40593	Corrected AH	AH korrigiert	AH	uint16be	1	1	0		level		true	false	false	false
                            40599	Grid phase voltage A	Netzphasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                            40600	Grid phase voltage B	Netzphasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                            40601	Grid phase voltage C	Netzphasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                            40605	L1 phase power on the inner side of the grid	L1 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                            40606	L2 phase power on the inner side of the grid	L2 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                            40607	L3 phase power on the inner side of the grid	L3 Phasenleistung auf der Innenseite des Netzes	W	uint16be	1	1	0		level		true	false	false	false
                            40608	active power from side to side of the grid	Wirkleistung von Seite zu Seite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                            40609	Grid side - inside total apparent power	Netzseite – innere Gesamtscheinleistung	W	uint16be	1	1	0		level		true	false	false	false
                            40610	Grid-side frequency	Grid Seite Frequenz	Hz	uint16be	1	1	0		level		true	false	false	false
                            40611	grid side inner current L1	netzseitiger Innenstrom L1	A	uint16be	1	0,01	0		level		true	false	false	false
                            40612	grid side inner current L2	netzseitiger Innenstrom L2	A	uint16be	1	0,01	0		level		true	false	false	false
                            40613	grid side inner current L3	netzseitiger Innenstrom L3	A	uint16be	1	0,01	0		level		true	false	false	false
                            40614	Out-of-grid - current L1	Außerhalb des Netzes – aktuelles L1	A	uint16be	1	0,01	0		level		true	false	false	false
                            40615	Out-of-grid - current L2	Außerhalb des Netzes – aktuelles L2	A	uint16be	1	0,01	0		level		true	false	false	false
                            40616	Out-of-grid - current L3	Außerhalb des Netzes – aktuelles L3	A	uint16be	1	0,01	0		level		true	false	false	false
                            40617	A Out-of-grid -power L1	A Außerhalb des Netzes - Strom L1	W	uint16be	1	1	0		level		true	false	false	false
                            40618	A Out-of-grid -power L2	A Außerhalb des Netzes - Strom L2	W	uint16be	1	1	0		level		true	false	false	false
                            40619	A Out-of-grid -power L3	A Außerhalb des Netzes - Strom L3	W	uint16be	1	1	0		level		true	false	false	false
                            40620	Out-of-grid -total power	Außerhalb des Netzes - Gesamtleistung	W	uint16be	1	1	0		level		true	false	false	false
                            40621	Out-of-grid - total apparent power	Außerhalb des Netzes - Gesamtscheinleistung	VA	uint16be	1	1	0		level		true	false	false	false
                            40622	Grid-connected power factor PF	Netzgekoppelter Leistungsfaktor PF		uint16be	1	1	0		level		true	false	false	false
                            40623	Grid side A-phase power	Netzseitiger L1-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                            40624	Grid side B-phase power	Netzseitiger L2-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                            40625	Grid side C-phase power	Netzseitiger L3-Phasen-Strom	W	uint16be	1	1	0		level		true	false	false	false
                            40626	Grid side total power	Netzseitige Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                            40628	Inverter output phase voltage A	Wechselrichter-Ausgangsphasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                            40629	Inverter output phase voltage B	Wechselrichter-Ausgangsphasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                            40630	Inverter output phase voltage C	Wechselrichter-Ausgangsphasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                            40631	Inverter output phase current A	Ausgangsphasenstrom des Wechselrichters L1	A	uint16be	1	0,01	0		level		true	false	false	false
                            40632	Inverter output phase current B	Ausgangsphasenstrom des Wechselrichters L2	A	uint16be	1	0,01	0		level		true	false	false	false
                            40633	Inverter output phase current C	Ausgangsphasenstrom des Wechselrichters L3	A	uint16be	1	0,01	0		level		true	false	false	false
                            40634	Inverter output phase power A	  Ausgangsphase des Wechselrichters Macht L1	W	uint16be	1	0	0		level		true	false	false	false
                            40635	Inverter output phase power B	Ausgangsphase des Wechselrichters Macht L2	W	uint16be	1	0	0		level		true	false	false	false
                            40636	Inverter output phase power C	Ausgangsphase des Wechselrichters Leistung L3	W	uint16be	1	0	0		level		true	false	false	false
                            40637	Inverter output total power	Gesamtleistung des Wechselrichters Leistung	W	uint16be	1	0	0		level		true	false	false	false
                            40638	Inverter output total apparent power	Gesamtleistung des Wechselrichters Scheinleistung	W	uint16be	1	0	0		level		true	false	false	false
                            40639	Inverter frequency	Wechselrichter frequenz	Hz	uint16be	1	0,01	0		level		true	false	false	false
                            40641	UPS load-side phase power A	USV-lastseitige Phasenleistung L1	W	uint16be	1	1	0		level		true	false	false	false
                            40642	UPS load-side phase power B	USV-lastseitige Phasenleistung L2	W	uint16be	1	1	0		level		true	false	false	false
                            40643	UPS load-side phase power C	USV-lastseitige Phasenleistung L3	W	uint16be	1	1	0		level		true	false	false	false
                            40644	UPS load-sidetotal power	Lastseitige Gesamtleistung der USV	W	uint16be	1	1	0		level		true	false	false	false
                            40645	Load phase voltage A	Load phasenspannung L1	V	uint16be	1	0,1	0		level		true	false	false	false
                            40646	Load phase voltage B	Load phasenspannung L2	V	uint16be	1	0,1	0		level		true	false	false	false
                            40647	Load phase voltage C	Load phasenspannung L3	V	uint16be	1	0,1	0		level		true	false	false	false
                            40648	Load phase current A	Load phasenstrom L1	A	uint16be	1	0,01	0		level		true	false	false	false
                            40649	Load phase current B	Load phasenstrom L2	A	uint16be	1	0,01	0		level		true	false	false	false
                            40650	Load phase current C	Load phasenstrom L3	A	uint16be	1	0,01	0		level		true	false	false	false
                            40651	Load phase power A	Load phase Leistung L1	W	uint16be	1	1	0		level		true	false	false	false
                            40652	Load phase power B	Load phase Leistung L2	W	uint16be	1	1	0		level		true	false	false	false
                            40653	Load phase power C	Load phase Leistung L3	W	uint16be	1	1	0		level		true	false	false	false
                            40654	Load totalpower	Load Gesamtleistung	W	uint16be	1	1	0		level		true	false	false	false
                            40655	Load phase apparent power	Scheinleistung der Lastphase	VA	uint16be	1	1	0		level		true	false	false	false
                            40656	Load frequency	Load Frequenz	Hz	uint16be	1	1	0		level		true	false	false	false
                            40662	Phase voltage of Gen port A	Phasenspannung von Gen-Port L1	V	uint16be	1	0,1	0		level		true	false	false	false
                            40663	Phase voltage of Gen port B	Phasenspannung von Gen-Port L2	V	uint16be	1	0,1	0		level		true	false	false	false
                            40664	Phase voltage of Gen port C	Phasenspannung von Gen-Port L3	V	uint16be	1	0,1	0		level		true	false	false	false
                            40665	Phase power of Gen port A	Phasenleistung von Gen-Port L1	W	uint16be	1	1	0		level		true	false	false	false
                            40666	Phase power of Gen port B	Phasenleistung von Gen-Port L2	W	uint16be	1	1	0		level		true	false	false	false
                            40667	Phase power of Gen port C	Phasenleistung von Gen-Port L3	W	uint16be	1	1	0		level		true	false	false	false
                            40668	total power of Gen port	Gesamtleistung des Gen-Ports	W	uint16be	1	1	0		level		true	false	false	false
                            40673	PV1 input power	PV1 Eingangsleistung	W	uint16be	1	1	0		level		true	false	false	false
                            40674	PV2 input power	PV2 Eingangsleistung	W	uint16be	1	1	0		level		true	false	false	false
                            40677	Dc voltage 1	Gleichspannung 1	V	uint16be	1	0,1	0		level		true	false	false	false
                            40678	Dc current 1	Gleichstrom 1	A	uint16be	1	0,1	0		level		true	false	false	false
                            40679	Dc voltage 2	Gleichspannung 2	V	uint16be	1	0,1	0		level		true	false	false	false
                            40680	Dc current 2	Gleichstrom 2	A	uint16be	1	0,1	0		level		true	false	false	false
                            
                            W Offline
                            W Offline
                            warp735
                            schrieb am zuletzt editiert von
                            #154

                            @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                            man muss dann nur den Haken bei "Benutze Aliase" setzen

                            Das war schon immer so ;-)

                            Wenn die Register bei dir so funktionieren, ist ja in Ordnung. Ich habs wie gesagt anders eingestellt.

                            wendy2702W 1 Antwort Letzte Antwort
                            0
                            • W warp735

                              @wendy2702 sagte in Deye Wechselrichter Modbus Register beschreiben:

                              man muss dann nur den Haken bei "Benutze Aliase" setzen

                              Das war schon immer so ;-)

                              Wenn die Register bei dir so funktionieren, ist ja in Ordnung. Ich habs wie gesagt anders eingestellt.

                              wendy2702W Offline
                              wendy2702W Offline
                              wendy2702
                              schrieb am zuletzt editiert von
                              #155

                              @warp735 Gerade mal über längere Zeit beobachtet. Da kommen schonmal merkwürdige Werte raus.

                              Kannst du mal bitte einen Export deiner Register einstellen?

                              Bitte keine Fragen per PN, die gehören ins Forum!

                              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                              W 1 Antwort Letzte Antwort
                              0
                              • wendy2702W wendy2702

                                @warp735 Gerade mal über längere Zeit beobachtet. Da kommen schonmal merkwürdige Werte raus.

                                Kannst du mal bitte einen Export deiner Register einstellen?

                                W Offline
                                W Offline
                                warp735
                                schrieb am zuletzt editiert von
                                #156

                                @wendy2702
                                Ausnahmslos alle Werte so:

                                Snag_13f8b67.png

                                wendy2702W 1 Antwort Letzte Antwort
                                0
                                • W warp735

                                  @wendy2702
                                  Ausnahmslos alle Werte so:

                                  Snag_13f8b67.png

                                  wendy2702W Offline
                                  wendy2702W Offline
                                  wendy2702
                                  schrieb am zuletzt editiert von
                                  #157

                                  @warp735 Hm,

                                  das hilft bei der Frage nach einem Export der Register leider nicht weiter.

                                  Bitte keine Fragen per PN, die gehören ins Forum!

                                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                  W 1 Antwort Letzte Antwort
                                  0
                                  • wendy2702W wendy2702

                                    @warp735 Hm,

                                    das hilft bei der Frage nach einem Export der Register leider nicht weiter.

                                    W Offline
                                    W Offline
                                    warp735
                                    schrieb am zuletzt editiert von
                                    #158

                                    @wendy2702
                                    Dann stell halt schnell selbst um. Bin am Handy und gibt kein Export

                                    wendy2702W 1 Antwort Letzte Antwort
                                    0
                                    • W warp735

                                      @wendy2702
                                      Dann stell halt schnell selbst um. Bin am Handy und gibt kein Export

                                      wendy2702W Offline
                                      wendy2702W Offline
                                      wendy2702
                                      schrieb am zuletzt editiert von
                                      #159

                                      @warp735 Mir wäre es eher um den Vergleich gegangen welche Register du nutzt und was alles in der Liste steht die ich importiert habe.

                                      Das du am Handy bist kann ich ja nicht wissen.

                                      Bitte keine Fragen per PN, die gehören ins Forum!

                                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                      W 1 Antwort Letzte Antwort
                                      0
                                      • wendy2702W wendy2702

                                        @warp735 Mir wäre es eher um den Vergleich gegangen welche Register du nutzt und was alles in der Liste steht die ich importiert habe.

                                        Das du am Handy bist kann ich ja nicht wissen.

                                        W Offline
                                        W Offline
                                        warp735
                                        schrieb am zuletzt editiert von
                                        #160

                                        @wendy2702
                                        Glaub das Register pdf hab ich hier auch mal reingestellt. Da kannst dir ja das was du benötigst raussuchen.

                                        wendy2702W 1 Antwort Letzte Antwort
                                        0
                                        • W warp735

                                          @wendy2702
                                          Glaub das Register pdf hab ich hier auch mal reingestellt. Da kannst dir ja das was du benötigst raussuchen.

                                          wendy2702W Offline
                                          wendy2702W Offline
                                          wendy2702
                                          schrieb am zuletzt editiert von
                                          #161

                                          @warp735 OK. Muss ich mal suchen.

                                          Habe aktuell dieses Merkwürdige Verhalten nachdem ich alles umgestellt habe:

                                          5aacb763-4db9-4c3f-a8c2-17b7924b47e0-E0C990AE-DF3E-4A05-9F92-93602C49858B.GIF

                                          Bitte keine Fragen per PN, die gehören ins Forum!

                                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                          W W 2 Antworten Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          817

                                          Online

                                          32.5k

                                          Benutzer

                                          81.6k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe