  5. [Gelöst] MODBUS.0 Adapter fehlt Master/Slave möglichkeit?

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.9k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.3k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.6k

[Gelöst] MODBUS.0 Adapter fehlt Master/Slave möglichkeit?

Geplant Angeheftet Gesperrt Verschoben Automatisierung
master slavemodbustyp
33 Beiträge 4 Kommentatoren 2.8k Aufrufe 2 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • michael.puschM michael.pusch

    @glasfaser

    Danke für deine Antwort

    Ich dachte das "ID 1" ist die Adresse des Modbus Adapters im Bus...?
    In der einen Instanz muss ich mit 115200 fahren, die andere mit nur 9600 baud weil die beiden FIXE unveränderbare Baudraten haben...

    Modbus0 ist die abzufragende Adresse 10, 115200 baud, Nur EIN Teilnehmer und eigener Bus.
    Modbus1 ist die abzufragende Adresse 2, 9600baud. Nur EIN Teilnehmer und ebenfalls eigener Bus.
    Also die beiden hängen nicht an der selben Strippe...

    Habe beide Instanzen unter "GeräteID" mit 1 tituliert da ich dachte hier wäre die Masteradresse des Adapters gemeint...

    Ich kann Daten auslesen, das funktioniert ja, jedoch nicht schreiben, da sagt mir der Adapter ich wäre SLAVE und darf nicht schreiben am Bus

    GlasfaserG Offline
    GlasfaserG Offline
    Glasfaser
    schrieb am zuletzt editiert von
    #4

    @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

    Modbus0 ist die abzufragende Adresse 10, 115200 baud, Nur EIN Teilnehmer und eigener Bus.
    Modbus1 ist die abzufragende Adresse 2, 9600baud. Nur EIN Teilnehmer und ebenfalls eigener Bus.

    dann nimm den Haken raus bei :

    41db54b3-6e03-4b80-9523-6a83b4851f5b-grafik.png

    den brauchst du dann auch nicht ...

    Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

    michael.puschM 1 Antwort Letzte Antwort
    0
    • GlasfaserG Glasfaser

      @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

      Modbus0 ist die abzufragende Adresse 10, 115200 baud, Nur EIN Teilnehmer und eigener Bus.
      Modbus1 ist die abzufragende Adresse 2, 9600baud. Nur EIN Teilnehmer und ebenfalls eigener Bus.

      dann nimm den Haken raus bei :

      41db54b3-6e03-4b80-9523-6a83b4851f5b-grafik.png

      den brauchst du dann auch nicht ...

      michael.puschM Offline
      michael.puschM Offline
      michael.pusch
      schrieb am zuletzt editiert von michael.pusch
      #5

      @glasfaser

      Bei beiden erledigt, statt 1 jetzt die Geräteadressen 10 und 2 eingetragen und KEINE Verbindung mehr :face_with_rolling_eyes:
      Drum hatte ich die nämlich SO drinnen

      aber an meinem Master Slave Problem ändert des momentan a nix

      modbus.1 2023-01-25 20:46:38.310	info	Disconnected from slave
      modbus.1 2023-01-25 20:46:37.309	warn	Poll error count: 1 code: {"err":"timeout","timeout":500}
      modbus.1 2023-01-25 20:46:37.307	error	Request timed out.
      modbus.1 2023-01-25 20:46:37.306	warn	Error: undefined
      modbus.1 2023-01-25 20:46:36.794	info    Connected to slave
      

      Gradeaus ---------->

      wendy2702W 1 Antwort Letzte Antwort
      0
      • michael.puschM michael.pusch

        @glasfaser

        Bei beiden erledigt, statt 1 jetzt die Geräteadressen 10 und 2 eingetragen und KEINE Verbindung mehr :face_with_rolling_eyes:
        Drum hatte ich die nämlich SO drinnen

        aber an meinem Master Slave Problem ändert des momentan a nix

        modbus.1 2023-01-25 20:46:38.310	info	Disconnected from slave
        modbus.1 2023-01-25 20:46:37.309	warn	Poll error count: 1 code: {"err":"timeout","timeout":500}
        modbus.1 2023-01-25 20:46:37.307	error	Request timed out.
        modbus.1 2023-01-25 20:46:37.306	warn	Error: undefined
        modbus.1 2023-01-25 20:46:36.794	info    Connected to slave
        
        wendy2702W Offline
        wendy2702W Offline
        wendy2702
        schrieb am zuletzt editiert von wendy2702
        #6

        @michael-pusch Unten steht bei RTU "Master"

        6c2f5965-0fec-417c-868c-85898af99876-grafik.png

        Wenn du "mehrere ID" raus nimmst, kontrolliere mal alle anderen Einstellungen.

        Stell das loggen mal auf Debug und poste dann das log

        Bitte keine Fragen per PN, die gehören ins Forum!

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        michael.puschM 1 Antwort Letzte Antwort
        0
        • wendy2702W wendy2702

          @michael-pusch Unten steht bei RTU "Master"

          6c2f5965-0fec-417c-868c-85898af99876-grafik.png

          Wenn du "mehrere ID" raus nimmst, kontrolliere mal alle anderen Einstellungen.

          Stell das loggen mal auf Debug und poste dann das log

          michael.puschM Offline
          michael.puschM Offline
          michael.pusch
          schrieb am zuletzt editiert von
          #7

          @wendy2702

          modbus.1
          	2023-01-25 20:56:37.028	info	Connected to slave
          modbus.1
          	2023-01-25 20:55:37.020	info	Disconnected from slave
          modbus.1
          	2023-01-25 20:55:36.021	warn	Poll error count: 1 code: {"err":"timeout","timeout":500}
          modbus.1
          	2023-01-25 20:55:36.019	error	Request timed out.
          modbus.1
          	2023-01-25 20:55:36.018	warn	Error: undefined
          modbus.1
          	2023-01-25 20:55:35.590	error	Wrong CRC for frame: 1,4,12,0,3,20,171,0,78,0,99,0,94,0,40,219,140
          modbus.1
          	2023-01-25 20:54:21.697	info	Connected to slave
          modbus.1
          	2023-01-25 20:53:21.685	info	Disconnected from slave
          modbus.1
          	2023-01-25 20:53:20.683	warn	Poll error count: 1 code: {"err":"timeout","timeout":500}
          modbus.1
          	2023-01-25 20:53:20.681	error	Request timed out.
          modbus.1
          	2023-01-25 20:53:20.679	warn	Error: undefined
          modbus.1
          	2023-01-25 20:53:20.250	error	Wrong CRC for frame: 1,4,4,0,3,20,130,0,206
          modbus.1
          	2023-01-25 20:53:00.639	info	Connected to slave
          

          jetzt hab i dauernde reconnects... :disappointed:

          Gradeaus ---------->

          wendy2702W 1 Antwort Letzte Antwort
          0
          • michael.puschM michael.pusch

            @wendy2702

            modbus.1
            	2023-01-25 20:56:37.028	info	Connected to slave
            modbus.1
            	2023-01-25 20:55:37.020	info	Disconnected from slave
            modbus.1
            	2023-01-25 20:55:36.021	warn	Poll error count: 1 code: {"err":"timeout","timeout":500}
            modbus.1
            	2023-01-25 20:55:36.019	error	Request timed out.
            modbus.1
            	2023-01-25 20:55:36.018	warn	Error: undefined
            modbus.1
            	2023-01-25 20:55:35.590	error	Wrong CRC for frame: 1,4,12,0,3,20,171,0,78,0,99,0,94,0,40,219,140
            modbus.1
            	2023-01-25 20:54:21.697	info	Connected to slave
            modbus.1
            	2023-01-25 20:53:21.685	info	Disconnected from slave
            modbus.1
            	2023-01-25 20:53:20.683	warn	Poll error count: 1 code: {"err":"timeout","timeout":500}
            modbus.1
            	2023-01-25 20:53:20.681	error	Request timed out.
            modbus.1
            	2023-01-25 20:53:20.679	warn	Error: undefined
            modbus.1
            	2023-01-25 20:53:20.250	error	Wrong CRC for frame: 1,4,4,0,3,20,130,0,206
            modbus.1
            	2023-01-25 20:53:00.639	info	Connected to slave
            

            jetzt hab i dauernde reconnects... :disappointed:

            wendy2702W Offline
            wendy2702W Offline
            wendy2702
            schrieb am zuletzt editiert von wendy2702
            #8

            @michael-pusch WIe sehen denn die Register aus?

            Funktioniert es wieder wenn du den haken wieder setzt?

            Und, das ist kein DEBUG log!!!

            Bitte keine Fragen per PN, die gehören ins Forum!

            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

            michael.puschM GlasfaserG 2 Antworten Letzte Antwort
            0
            • wendy2702W wendy2702

              @michael-pusch WIe sehen denn die Register aus?

              Funktioniert es wieder wenn du den haken wieder setzt?

              Und, das ist kein DEBUG log!!!

              michael.puschM Offline
              michael.puschM Offline
              michael.pusch
              schrieb am zuletzt editiert von michael.pusch
              #9

              @wendy2702

              hab den modbus.1 ausgewählt und auf debug gestellt...

              DAS sind die daten die ich krieg.
              Screenshot 2023-01-25 210108.png

              Screenshot 2023-01-25 210025.png

              momentan rennts... zumindest kommen daten rein... frage is nur wie lange...

              DER adpater war aber eigentlich nicht mein Problem...
              Hier les ich nur daten aus der Batterie aus.

              Modbus.0 is der Hybridwechselrichter und da möcht ich daten schreiben können. Das sollte laut Hersteller auch funktionieren.
              Unter Holdingregister kann ich den Parameter auslesen, aber ned schreiben... da krieg ich dann eben den Slave Fehler...

              Screenshot 2023-01-25 210738.png

              Gradeaus ---------->

              wendy2702W 1 Antwort Letzte Antwort
              0
              • wendy2702W wendy2702

                @michael-pusch WIe sehen denn die Register aus?

                Funktioniert es wieder wenn du den haken wieder setzt?

                Und, das ist kein DEBUG log!!!

                GlasfaserG Offline
                GlasfaserG Offline
                Glasfaser
                schrieb am zuletzt editiert von Glasfaser
                #10

                @wendy2702

                Hi .. ...
                gerade mal getestet ...

                ist mir noch gar nicht aufgefallen , da ich selber nur TCP nutze ., dort geht die Umstellung Master / Slave

                Bei Serial und RTU over TCP ist keine Auswahl möglich .

                Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                michael.puschM 1 Antwort Letzte Antwort
                0
                • michael.puschM michael.pusch

                  @wendy2702

                  hab den modbus.1 ausgewählt und auf debug gestellt...

                  DAS sind die daten die ich krieg.
                  Screenshot 2023-01-25 210108.png

                  Screenshot 2023-01-25 210025.png

                  momentan rennts... zumindest kommen daten rein... frage is nur wie lange...

                  DER adpater war aber eigentlich nicht mein Problem...
                  Hier les ich nur daten aus der Batterie aus.

                  Modbus.0 is der Hybridwechselrichter und da möcht ich daten schreiben können. Das sollte laut Hersteller auch funktionieren.
                  Unter Holdingregister kann ich den Parameter auslesen, aber ned schreiben... da krieg ich dann eben den Slave Fehler...

                  Screenshot 2023-01-25 210738.png

                  wendy2702W Offline
                  wendy2702W Offline
                  wendy2702
                  schrieb am zuletzt editiert von
                  #11

                  @michael-pusch LOgs bitte immer als Text in Code Tags </> Posten.

                  Und du bist sicher das du zum auslesen Eingangsregister verwenden musst?

                  Und greift die Instanz 1 auch noch auf den richtigen USB Port zu ?

                  Bitte keine Fragen per PN, die gehören ins Forum!

                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                  michael.puschM 1 Antwort Letzte Antwort
                  0
                  • GlasfaserG Glasfaser

                    @wendy2702

                    Hi .. ...
                    gerade mal getestet ...

                    ist mir noch gar nicht aufgefallen , da ich selber nur TCP nutze ., dort geht die Umstellung Master / Slave

                    Bei Serial und RTU over TCP ist keine Auswahl möglich .

                    michael.puschM Offline
                    michael.puschM Offline
                    michael.pusch
                    schrieb am zuletzt editiert von
                    #12

                    @glasfaser
                    @wendy2702

                    Haaa... ok ?
                    is das so gewollt? denn dann kann ich das so nicht nutzen und auch den Parameter ned ändern...

                    Gradeaus ---------->

                    1 Antwort Letzte Antwort
                    0
                    • wendy2702W wendy2702

                      @michael-pusch LOgs bitte immer als Text in Code Tags </> Posten.

                      Und du bist sicher das du zum auslesen Eingangsregister verwenden musst?

                      Und greift die Instanz 1 auch noch auf den richtigen USB Port zu ?

                      michael.puschM Offline
                      michael.puschM Offline
                      michael.pusch
                      schrieb am zuletzt editiert von michael.pusch
                      #13

                      @wendy2702 sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                      @michael-pusch LOgs bitte immer als Text in Code Tags </> Posten.

                      Und du bist sicher das du zum auslesen Eingangsregister verwenden musst?

                      Und greift die Instanz 1 auch noch auf den richtigen USB Port zu ?

                      Sorry, war a ausreisser mit dem Snapshotprogramm weil i grad andere bilder gemacht hab... die vorigen codes sind ja im editor... sorry
                      Zum auslesen sind die adressen alle im eingangsregister und das funktioniert auch... der lesend/schreibende sollte ein holdingregister sein und lesen kann ich den auch, aber schreiben ned

                      Screenshot 2023-01-25 211410.png

                      Gradeaus ---------->

                      wendy2702W 1 Antwort Letzte Antwort
                      0
                      • michael.puschM michael.pusch

                        @wendy2702 sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                        @michael-pusch LOgs bitte immer als Text in Code Tags </> Posten.

                        Und du bist sicher das du zum auslesen Eingangsregister verwenden musst?

                        Und greift die Instanz 1 auch noch auf den richtigen USB Port zu ?

                        Sorry, war a ausreisser mit dem Snapshotprogramm weil i grad andere bilder gemacht hab... die vorigen codes sind ja im editor... sorry
                        Zum auslesen sind die adressen alle im eingangsregister und das funktioniert auch... der lesend/schreibende sollte ein holdingregister sein und lesen kann ich den auch, aber schreiben ned

                        Screenshot 2023-01-25 211410.png

                        wendy2702W Offline
                        wendy2702W Offline
                        wendy2702
                        schrieb am zuletzt editiert von wendy2702
                        #14

                        @michael-pusch Was kommt denn im Debug log wenn du versuchst zu schreiben?

                        Bitte keine Fragen per PN, die gehören ins Forum!

                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                        michael.puschM 1 Antwort Letzte Antwort
                        0
                        • wendy2702W wendy2702

                          @michael-pusch Was kommt denn im Debug log wenn du versuchst zu schreiben?

                          michael.puschM Offline
                          michael.puschM Offline
                          michael.pusch
                          schrieb am zuletzt editiert von michael.pusch
                          #15

                          @wendy2702

                          modbus.0 2023-01-25 21:15:42.174	info	        Disconnected from slave
                          modbus.0 2023-01-25 21:15:41.522	warn	Poll error count: 1 code: "App Timeout"
                          modbus.0 2023-01-25 21:15:41.170	error	Cannot write single register [38407]: {"err":"timeout","timeout":5000}
                          modbus.0 2023-01-25 21:15:41.169	error	Request timed out.
                          modbus.0 2023-01-25 21:15:41.169	warn	Error: undefined
                          modbus.0 2023-01-25 21:15:36.217	error	Error response: Function code received in the query is not recognized or allowed by slave
                          modbus.0 2023-01-25 21:15:36.216	error	Error response for FCx6: Illegal Function
                          admin.0 2023-01-25 21:15:21.307	info	<== Disconnect system.user.admin from ::ffff:192.168.1.112 modbus
                          modbus.1 2023-01-25 21:11:57.222	info	        Connected to slave
                          

                          Gradeaus ---------->

                          HomoranH wendy2702W 2 Antworten Letzte Antwort
                          0
                          • michael.puschM michael.pusch

                            @wendy2702

                            modbus.0 2023-01-25 21:15:42.174	info	        Disconnected from slave
                            modbus.0 2023-01-25 21:15:41.522	warn	Poll error count: 1 code: "App Timeout"
                            modbus.0 2023-01-25 21:15:41.170	error	Cannot write single register [38407]: {"err":"timeout","timeout":5000}
                            modbus.0 2023-01-25 21:15:41.169	error	Request timed out.
                            modbus.0 2023-01-25 21:15:41.169	warn	Error: undefined
                            modbus.0 2023-01-25 21:15:36.217	error	Error response: Function code received in the query is not recognized or allowed by slave
                            modbus.0 2023-01-25 21:15:36.216	error	Error response for FCx6: Illegal Function
                            admin.0 2023-01-25 21:15:21.307	info	<== Disconnect system.user.admin from ::ffff:192.168.1.112 modbus
                            modbus.1 2023-01-25 21:11:57.222	info	        Connected to slave
                            
                            HomoranH Nicht stören
                            HomoranH Nicht stören
                            Homoran
                            Global Moderator Administrators
                            schrieb am zuletzt editiert von
                            #16

                            @michael-pusch das ist kein debug-log!

                            hast du die Instanz auf Logstufe debug gestellt?

                            kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                            der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                            michael.puschM 1 Antwort Letzte Antwort
                            0
                            • michael.puschM michael.pusch

                              @wendy2702

                              modbus.0 2023-01-25 21:15:42.174	info	        Disconnected from slave
                              modbus.0 2023-01-25 21:15:41.522	warn	Poll error count: 1 code: "App Timeout"
                              modbus.0 2023-01-25 21:15:41.170	error	Cannot write single register [38407]: {"err":"timeout","timeout":5000}
                              modbus.0 2023-01-25 21:15:41.169	error	Request timed out.
                              modbus.0 2023-01-25 21:15:41.169	warn	Error: undefined
                              modbus.0 2023-01-25 21:15:36.217	error	Error response: Function code received in the query is not recognized or allowed by slave
                              modbus.0 2023-01-25 21:15:36.216	error	Error response for FCx6: Illegal Function
                              admin.0 2023-01-25 21:15:21.307	info	<== Disconnect system.user.admin from ::ffff:192.168.1.112 modbus
                              modbus.1 2023-01-25 21:11:57.222	info	        Connected to slave
                              
                              wendy2702W Offline
                              wendy2702W Offline
                              wendy2702
                              schrieb am zuletzt editiert von
                              #17

                              @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                              Function code received in the query is not recognized or allowed by slave

                              Da steht aber das dein WR den Function Code nicht akzeptiert.

                              Also entweder register falsch, kein Holding, oder falsche Register Parameter.

                              Bitte keine Fragen per PN, die gehören ins Forum!

                              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                              michael.puschM 1 Antwort Letzte Antwort
                              0
                              • HomoranH Homoran

                                @michael-pusch das ist kein debug-log!

                                hast du die Instanz auf Logstufe debug gestellt?

                                michael.puschM Offline
                                michael.puschM Offline
                                michael.pusch
                                schrieb am zuletzt editiert von michael.pusch
                                #18

                                @homoran Screenshot 2023-01-25 211846.png

                                Screenshot 2023-01-25 212005.png

                                Gradeaus ---------->

                                wendy2702W 1 Antwort Letzte Antwort
                                0
                                • michael.puschM michael.pusch

                                  @homoran Screenshot 2023-01-25 211846.png

                                  Screenshot 2023-01-25 212005.png

                                  wendy2702W Offline
                                  wendy2702W Offline
                                  wendy2702
                                  schrieb am zuletzt editiert von
                                  #19

                                  @michael-pusch Das ist nur der Filter.

                                  Debug stellt man in der Instanz ein wo jetzt Info steht.

                                  Bitte keine Fragen per PN, die gehören ins Forum!

                                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                  michael.puschM 1 Antwort Letzte Antwort
                                  0
                                  • wendy2702W wendy2702

                                    @michael-pusch Das ist nur der Filter.

                                    Debug stellt man in der Instanz ein wo jetzt Info steht.

                                    michael.puschM Offline
                                    michael.puschM Offline
                                    michael.pusch
                                    schrieb am zuletzt editiert von
                                    #20

                                    @wendy2702

                                    thx... naja, bin mit dem ding a ned jeden tag auf du und du ;)
                                    sekunde

                                    Gradeaus ---------->

                                    1 Antwort Letzte Antwort
                                    0
                                    • wendy2702W Offline
                                      wendy2702W Offline
                                      wendy2702
                                      schrieb am zuletzt editiert von
                                      #21

                                      7e6f6f66-0e45-41b8-a849-37f458f09c3a-grafik.png

                                      Bitte keine Fragen per PN, die gehören ins Forum!

                                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                      michael.puschM 1 Antwort Letzte Antwort
                                      0
                                      • wendy2702W wendy2702

                                        7e6f6f66-0e45-41b8-a849-37f458f09c3a-grafik.png

                                        michael.puschM Offline
                                        michael.puschM Offline
                                        michael.pusch
                                        schrieb am zuletzt editiert von
                                        #22

                                        @wendy2702

                                        modbus.0
                                        	2023-01-25 21:24:26.494	debug	Cleaning up request fifo.
                                        modbus.0
                                        	2023-01-25 21:24:26.493	debug	Clearing timeout of the current request.
                                        modbus.0
                                        	2023-01-25 21:24:26.487	info	Disconnected from slave
                                        modbus.0
                                        	2023-01-25 21:24:26.036	warn	Poll error count: 1 code: "App Timeout"
                                        modbus.0
                                        	2023-01-25 21:24:25.484	error	Cannot write single register [38407]: {"err":"timeout","timeout":5000}
                                        modbus.0
                                        	2023-01-25 21:24:25.483	error	Request timed out.
                                        modbus.0
                                        	2023-01-25 21:24:25.482	warn	Error: undefined
                                        modbus.0
                                        	2023-01-25 21:24:20.836	debug	[DevID_10/inputRegs] Poll address 13568 - 21 registers
                                        modbus.0
                                        	2023-01-25 21:24:20.836	debug	[DevID_10] Poll start ---------------------
                                        modbus.0
                                        	2023-01-25 21:24:20.585	error	Error response: Function code received in the query is not recognized or allowed by slave
                                        modbus.0
                                        	2023-01-25 21:24:20.584	error	Error response for FCx6: Illegal Function
                                        modbus.0
                                        	2023-01-25 21:24:20.473	debug	state Changed ack=false: modbus.0.holdingRegisters.38407_PV_System_LadeStatus: {"val":1,"ack":false,"ts":1674678260467,"q":0,"from":"system.adapter.admin.0","user":"system.user.admin","lc":1674678260467}
                                        modbus.0
                                        	2023-01-25 21:24:19.783	debug	[DevID_10/holdingRegs] Poll address 38407 DONE
                                        modbus.0
                                        	2023-01-25 21:24:19.697	debug	[DevID_10/holdingRegs] Poll address 38407 - 1 registers
                                        modbus.0
                                        	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Calculation result = 0.84, type = number
                                        modbus.0
                                        	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Formula = x / 100
                                        modbus.0
                                        	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Input Value = 84
                                        modbus.0
                                        	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Calculation result = 56.87, type = number
                                        modbus.0
                                        	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Formula = x / 100
                                        modbus.0
                                        	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Input Value = 5687
                                        modbus.0
                                        	2023-01-25 21:24:19.687	debug	[DevID_10/inputRegs] Poll address 13696 DONE
                                        modbus.0
                                        	2023-01-25 21:24:19.599	debug	[DevID_10/inputRegs] Poll address 13696 - 7 registers
                                        modbus.0
                                        	2023-01-25 21:24:19.595	debug	[DevID_10/inputRegs/13655] Calculation result = 211.15, type = number
                                        modbus.0
                                        	2023-01-25 21:24:19.592	debug	[DevID_10/inputRegs/13655] Formula = x / 100
                                        modbus.0
                                        	2023-01-25 21:24:19.592	debug	[DevID_10/inputRegs/13655] Input Value = 21115
                                        modbus.0
                                        	2023-01-25 21:24:19.591	debug	[DevID_10/inputRegs] Poll address 13655 DONE
                                        modbus.0
                                        	2023-01-25 21:24:19.501	debug	[DevID_10/inputRegs] Poll address 13655 - 1 registers
                                        modbus.0
                                        	2023-01-25 21:24:19.499	debug	[DevID_10/inputRegs/13643] Calculation result = 0, type = number
                                        modbus.0
                                        	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13643] Formula = x / 100
                                        modbus.0
                                        	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13643] Input Value = 0
                                        modbus.0
                                        	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13642] Calculation result = 0, type = number
                                        modbus.0
                                        	2023-01-25 21:24:19.497	debug	[DevID_10/inputRegs/13642] Formula = x / 100
                                        

                                        Gradeaus ---------->

                                        wendy2702W 1 Antwort Letzte Antwort
                                        0
                                        • wendy2702W wendy2702

                                          @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                                          Function code received in the query is not recognized or allowed by slave

                                          Da steht aber das dein WR den Function Code nicht akzeptiert.

                                          Also entweder register falsch, kein Holding, oder falsche Register Parameter.

                                          michael.puschM Offline
                                          michael.puschM Offline
                                          michael.pusch
                                          schrieb am zuletzt editiert von
                                          #23

                                          @wendy2702 sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                                          @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                                          Function code received in the query is not recognized or allowed by slave

                                          Da steht aber das dein WR den Function Code nicht akzeptiert.

                                          Also entweder register falsch, kein Holding, oder falsche Register Parameter.

                                          Screenshot 2023-01-25 194703.png

                                          Laut Hex müsste die Adresse dann 38407 lauten...

                                          es geht um die Zeile C8

                                          Gradeaus ---------->

                                          GlasfaserG 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          792

                                          Online

                                          32.5k

                                          Benutzer

                                          81.6k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe