  4. [Frage] Realisierung Adapter UDP Keba Wallbox

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.6k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.1k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    2.9k

[Frage] Realisierung Adapter UDP Keba Wallbox

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
1.3k Beiträge 70 Kommentatoren 448.0k Aufrufe 54 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • S Sneak-L8

    @hardl Was zeigt den der State "curr" und "surplus" an zu diesem Zeitpunkt? Und was feed(in/out)?

    H Offline
    H Offline
    hardl
    schrieb am zuletzt editiert von hardl
    #437

    @sneak-l8 Bildschirmfoto 2021-12-10 um 10.56.33.png Bildschirmfoto 2021-12-10 um 10.57.56.png
    feed um die 2kW

    S 1 Antwort Letzte Antwort
    0
    • H hardl

      @sneak-l8 Bildschirmfoto 2021-12-10 um 10.56.33.png Bildschirmfoto 2021-12-10 um 10.57.56.png
      feed um die 2kW

      S Offline
      S Offline
      Sneak-L8
      schrieb am zuletzt editiert von
      #438

      @hardl Leider fehlt der state "curr", der verutlich zwischen den beiden Screenshots liegt.
      Wie gesagt, der Adapter kann die Ladeleistung des Autos nur schätzen, weil es kein EnergyMeter gibt. Der feed vom SolarLog hilft auch nicht, weil der Adapter nicht wissen kann, was außer dem Auto noch Strom zieht.
      Daher nimmt der Adapter immer an Ladeleistung in W = 230V * State "charging phaes" * curr / 1000.
      Da charging phases bei null ist, wird eine Phase angenommen (beim EQA müsste aber m.E. in der Konfiguration 3 eingestellt werden - geht bisher nur in den states "calcPhases", macht aber evtl. auch als einstellung in der Instanz Sinn).
      Wenn das Auto aber mit mehr oder weniger Leistung als die nach der oben angegebenen Vorschrift ermittelten Leistung lädt, dann ergibt "surplus" ein falsches Bild, weil aus feed eine falsche Leistung für die Wallbox herausgerechnet wird.
      Eigentlich sollte feed - Leistung Wallbox = surplus sein.

      Wenn das Auto als mehr (z.B. mehr Phasen als kalkuliert) oder weniger (z.B. 16 A freigegeben ,aber auto lädt nur mit 10A) kommt es dann natrlich zu einer falschen Berechnung der freizugebenen Stromstärke (curr): curr in mA = feed - aktuell "vermutete" Ladeleistung der Wallbox / calcPhases / 230 * 1000.
      Dadurch passiert es, dass bei jeder Neuberechnung (ale 30 Sekunden) die Ladeleistung weiter erhöht/vermindert wird und bei Überschreiten gewisser Grenzen anfängt zu pendeln.
      Das ist leider alles dem fehlenden EnergyMeter der D-Edition geschuldet....

      H 1 Antwort Letzte Antwort
      0
      • S Sneak-L8

        @hardl Leider fehlt der state "curr", der verutlich zwischen den beiden Screenshots liegt.
        Wie gesagt, der Adapter kann die Ladeleistung des Autos nur schätzen, weil es kein EnergyMeter gibt. Der feed vom SolarLog hilft auch nicht, weil der Adapter nicht wissen kann, was außer dem Auto noch Strom zieht.
        Daher nimmt der Adapter immer an Ladeleistung in W = 230V * State "charging phaes" * curr / 1000.
        Da charging phases bei null ist, wird eine Phase angenommen (beim EQA müsste aber m.E. in der Konfiguration 3 eingestellt werden - geht bisher nur in den states "calcPhases", macht aber evtl. auch als einstellung in der Instanz Sinn).
        Wenn das Auto aber mit mehr oder weniger Leistung als die nach der oben angegebenen Vorschrift ermittelten Leistung lädt, dann ergibt "surplus" ein falsches Bild, weil aus feed eine falsche Leistung für die Wallbox herausgerechnet wird.
        Eigentlich sollte feed - Leistung Wallbox = surplus sein.

        Wenn das Auto als mehr (z.B. mehr Phasen als kalkuliert) oder weniger (z.B. 16 A freigegeben ,aber auto lädt nur mit 10A) kommt es dann natrlich zu einer falschen Berechnung der freizugebenen Stromstärke (curr): curr in mA = feed - aktuell "vermutete" Ladeleistung der Wallbox / calcPhases / 230 * 1000.
        Dadurch passiert es, dass bei jeder Neuberechnung (ale 30 Sekunden) die Ladeleistung weiter erhöht/vermindert wird und bei Überschreiten gewisser Grenzen anfängt zu pendeln.
        Das ist leider alles dem fehlenden EnergyMeter der D-Edition geschuldet....

        H Offline
        H Offline
        hardl
        schrieb am zuletzt editiert von hardl
        #439

        @sneak-l8 Wie blöd von mir, dass beim Screenshot genau die curr-Daten fehlen.
        Soweit ich mich erinnere, waren zu Beginn des Laden`s currentHardware, currentTimer und currentUser bei 16000mA.
        Das mit Solarlog und feed stimmt so nicht, da ich einen Zähler für meinen Gesamtstrom-Verbrauch installiert habe und der Solarlog die Verbrauchswerte abzieht. Die Wallbox wird nicht beim Verbrauch mitgerechnet.
        873E1273-0C03-49A8-AEC9-CDE6AAF65217.png
        Den state von calcPhases hatte ich vor dem Ladevorgang auf 3 eingestellt, aber das wurde irgendwann scheinbar von der Box überschrieben.
        Nach Deiner obigen Rechnung muß er aber mit 3 Phasen gerechnet haben, da nur so die 11kW erreicht werden können.

        S 1 Antwort Letzte Antwort
        0
        • H hardl

          @sneak-l8 Wie blöd von mir, dass beim Screenshot genau die curr-Daten fehlen.
          Soweit ich mich erinnere, waren zu Beginn des Laden`s currentHardware, currentTimer und currentUser bei 16000mA.
          Das mit Solarlog und feed stimmt so nicht, da ich einen Zähler für meinen Gesamtstrom-Verbrauch installiert habe und der Solarlog die Verbrauchswerte abzieht. Die Wallbox wird nicht beim Verbrauch mitgerechnet.
          873E1273-0C03-49A8-AEC9-CDE6AAF65217.png
          Den state von calcPhases hatte ich vor dem Ladevorgang auf 3 eingestellt, aber das wurde irgendwann scheinbar von der Box überschrieben.
          Nach Deiner obigen Rechnung muß er aber mit 3 Phasen gerechnet haben, da nur so die 11kW erreicht werden können.

          S Offline
          S Offline
          Sneak-L8
          schrieb am zuletzt editiert von
          #440

          @hardl Also der Adapter ändern calcPhases nicht, nur statistics.chargingPhases.
          Hm, also wenn feed den Verbrauch ohne Walbox enthält, dann wird der Adapter durcheinander kommen. Bisher geht der Adapter davon aus, dass seine eigene Leistung auch immer enthalten ist.
          Ich könnte aber eine neue Option einbauen, ob dem so ist oder nicht. Dann würde das die Ungenauigkeit der D-Edtion ersetzen.
          Zuerst kann Du aber mal anstelle feed den aktuellen Gesamt-Verbrauch inkl. Wallbox einstellen. Dann sollte die Box auch korrekt mit dem Überschuss arbeiten.

          H 1 Antwort Letzte Antwort
          0
          • S Sneak-L8

            @hardl Also der Adapter ändern calcPhases nicht, nur statistics.chargingPhases.
            Hm, also wenn feed den Verbrauch ohne Walbox enthält, dann wird der Adapter durcheinander kommen. Bisher geht der Adapter davon aus, dass seine eigene Leistung auch immer enthalten ist.
            Ich könnte aber eine neue Option einbauen, ob dem so ist oder nicht. Dann würde das die Ungenauigkeit der D-Edtion ersetzen.
            Zuerst kann Du aber mal anstelle feed den aktuellen Gesamt-Verbrauch inkl. Wallbox einstellen. Dann sollte die Box auch korrekt mit dem Überschuss arbeiten.

            H Offline
            H Offline
            hardl
            schrieb am zuletzt editiert von
            #441

            @sneak-l8 Dann weiß ich nicht, wieso wieder 0 im state calcPhases steht.
            Es gibt auch gerade, ohne Ladevorgang 2 Ungereimtheiten: feed = -0,1 kW, surplus -3,506 kW, diese beiden Werte waren sonst, ohne Ladevorgang gleich und currentUser 63 A.
            Bildschirmfoto 2021-12-11 um 13.33.00.png

            Den Verbrauch mit Wallbox kann ich aktuell nicht einstellen, da müsste der Elektriker umklemmen. Die Installation des Verbrauchszählers existiert schon ein paar Jahre und wurde bei der Installation der Wallbox nicht berücksichtigt.

            S 1 Antwort Letzte Antwort
            0
            • H hardl

              @sneak-l8 Dann weiß ich nicht, wieso wieder 0 im state calcPhases steht.
              Es gibt auch gerade, ohne Ladevorgang 2 Ungereimtheiten: feed = -0,1 kW, surplus -3,506 kW, diese beiden Werte waren sonst, ohne Ladevorgang gleich und currentUser 63 A.
              Bildschirmfoto 2021-12-11 um 13.33.00.png

              Den Verbrauch mit Wallbox kann ich aktuell nicht einstellen, da müsste der Elektriker umklemmen. Die Installation des Verbrauchszählers existiert schon ein paar Jahre und wurde bei der Installation der Wallbox nicht berücksichtigt.

              S Offline
              S Offline
              Sneak-L8
              schrieb am zuletzt editiert von
              #442

              @hardl Ok, dann baue ich mal eine neue Version mit der Option, dass die Wallbox in der Berechnung nicht enthalten ist. Weiß abern icht, wie schnell cih das hinbekomme.

              H 1 Antwort Letzte Antwort
              0
              • S Sneak-L8

                @hardl Ok, dann baue ich mal eine neue Version mit der Option, dass die Wallbox in der Berechnung nicht enthalten ist. Weiß abern icht, wie schnell cih das hinbekomme.

                H Offline
                H Offline
                hardl
                schrieb am zuletzt editiert von
                #443

                @sneak-l8 Das ist sehr nett von Dir!
                Macht nichts wenn es dauert, viel Überschuss gibts momentan eh nicht.

                S 1 Antwort Letzte Antwort
                0
                • H hardl

                  @sneak-l8 Das ist sehr nett von Dir!
                  Macht nichts wenn es dauert, viel Überschuss gibts momentan eh nicht.

                  S Offline
                  S Offline
                  Sneak-L8
                  schrieb am zuletzt editiert von
                  #444

                  @hardl Jetzt gibg's doch schneller. Bitte mal von github testen. Es gibt ne neue Option nach surplus und regard. Da den Haken einfach mal entfernen, weil bei Dir die Wallbox nicht mitgerechnet wird.
                  Das ist für die D-Edition übrigens wohl die beste Lösung. Denn dann kommt es nie zu fehlerhaften Berechnungen.
                  Ich bin gespannt, was Du sagen wirst.

                  H 3 Antworten Letzte Antwort
                  0
                  • S Sneak-L8

                    @hardl Jetzt gibg's doch schneller. Bitte mal von github testen. Es gibt ne neue Option nach surplus und regard. Da den Haken einfach mal entfernen, weil bei Dir die Wallbox nicht mitgerechnet wird.
                    Das ist für die D-Edition übrigens wohl die beste Lösung. Denn dann kommt es nie zu fehlerhaften Berechnungen.
                    Ich bin gespannt, was Du sagen wirst.

                    H Offline
                    H Offline
                    hardl
                    schrieb am zuletzt editiert von
                    #445

                    @sneak-l8 Hast Du Nachtschicht eingelegt, vielen Dank !!!!!!
                    Ich habe die V1.3.3 laufen.
                    Hier einmal die Screenshots vor dem Anstecken und in Aktion.
                    Vorher:
                    Bildschirmfoto 2021-12-12 um 10.11.41.png
                    Bildschirmfoto 2021-12-12 um 10.06.42.png
                    Bildschirmfoto 2021-12-12 um 10.07.04.png
                    Angesteckt:
                    Bildschirmfoto 2021-12-12 um 10.11.41.png
                    Bildschirmfoto 2021-12-12 um 10.11.58.png
                    Bildschirmfoto 2021-12-12 um 10.12.16.png

                    Das Auto meldet Ladeunterbrechung, da der Strom nicht ausreicht und nach ein paar Minuten Ladefehler.
                    Die surplus-Anzeige ist jetzt aber identisch mit feed vom Solarlog.

                    Wie bekomme ich die roten "0" wieder weg? Die hatte ich gestern mal geändert.
                    Leider ist es jetzt wieder total bewölkt.

                    1 Antwort Letzte Antwort
                    0
                    • S Sneak-L8

                      @hardl Jetzt gibg's doch schneller. Bitte mal von github testen. Es gibt ne neue Option nach surplus und regard. Da den Haken einfach mal entfernen, weil bei Dir die Wallbox nicht mitgerechnet wird.
                      Das ist für die D-Edition übrigens wohl die beste Lösung. Denn dann kommt es nie zu fehlerhaften Berechnungen.
                      Ich bin gespannt, was Du sagen wirst.

                      H Offline
                      H Offline
                      hardl
                      schrieb am zuletzt editiert von
                      #446

                      @sneak-l8 Der Ladefehler ist jetzt wieder weg und steht wieder auf Ladeunterbrechung, aber die Reisedaten sind jetzt total verkehrt.
                      Bis vor dem Ladefehler stand dort Verbrauch nach Start oder Reset auf 22-24kWh/100km, jetzt sind alle Werte auf 99,9kWh/100km. Sicher ein Fehler in der Mercedes-Software nach Ladefehler.

                      1 Antwort Letzte Antwort
                      0
                      • S Sneak-L8

                        @hardl Jetzt gibg's doch schneller. Bitte mal von github testen. Es gibt ne neue Option nach surplus und regard. Da den Haken einfach mal entfernen, weil bei Dir die Wallbox nicht mitgerechnet wird.
                        Das ist für die D-Edition übrigens wohl die beste Lösung. Denn dann kommt es nie zu fehlerhaften Berechnungen.
                        Ich bin gespannt, was Du sagen wirst.

                        H Offline
                        H Offline
                        hardl
                        schrieb am zuletzt editiert von
                        #447

                        @sneak-l8 Hier noch das Protokoll:

                        contact.0
                        2021-12-12 10:26:48.820	info	stop charging
                        
                        kecontact.0
                        2021-12-12 10:26:18.817	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:25:48.818	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:25:18.813	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:24:48.810	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:24:18.810	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:23:48.812	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:23:18.810	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:22:48.807	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:22:18.807	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:21:48.809	info	minimum regard time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:20:48.807	info	minimum charge time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:20:18.807	info	minimum charge time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:19:48.809	info	regulate wallbox from 8500 to 6000mA
                        
                        kecontact.0
                        2021-12-12 10:19:48.808	info	minimum charge time of 300sec not reached, continuing charging session
                        
                        kecontact.0
                        2021-12-12 10:17:48.802	info	regulate wallbox from 8000 to 8500mA
                        
                        kecontact.0
                        2021-12-12 10:17:18.803	info	regulate wallbox from 7500 to 8000mA
                        
                        kecontact.0
                        2021-12-12 10:16:18.800	info	vehicle (re)starts to charge
                        
                        kecontact.0
                        2021-12-12 10:15:48.800	info	(re)start charging
                        
                        kecontact.0
                        2021-12-12 10:08:20.212	info	vehicle plugged to wallbox
                        
                        kecontact.0
                        2021-12-12 09:54:04.434	info	Keba firmware check: latest firmware installed
                        
                        kecontact.0
                        2021-12-12 09:54:04.430	warn	Keba KeContact P30 Deutschland-Edition detected. Regulation may be inaccurate.
                        
                        kecontact.0
                        2021-12-12 09:54:03.182	info	config wallboxNotIncluded: true
                        
                        kecontact.0
                        2021-12-12 09:54:03.182	info	config stateEnergyMeter3:
                        
                        kecontact.0
                        2021-12-12 09:54:03.180	info	config stateEnergyMeter2:
                        
                        kecontact.0
                        2021-12-12 09:54:03.180	info	config stateEnergyMeter1:
                        
                        kecontact.0
                        2021-12-12 09:54:03.180	info	config maxPower: 11000
                        
                        kecontact.0
                        2021-12-12 09:54:03.179	info	config regardTime: 300
                        
                        kecontact.0
                        2021-12-12 09:54:03.179	info	config minTime: 300
                        
                        kecontact.0
                        2021-12-12 09:54:03.179	info	config underusage: 500
                        
                        kecontact.0
                        2021-12-12 09:54:03.178	info	config delta: 500
                        
                        kecontact.0
                        2021-12-12 09:54:03.177	info	config addPower: 0
                        
                        kecontact.0
                        2021-12-12 09:54:03.177	info	config minAmperage: 6000
                        
                        kecontact.0
                        2021-12-12 09:54:03.177	info	config statesIncludeWallbox: false
                        
                        kecontact.0
                        2021-12-12 09:54:03.176	info	config stateSurplus: solarlog.0.status.feed
                        
                        kecontact.0
                        2021-12-12 09:54:03.176	info	config stateRegard:
                        
                        kecontact.0
                        2021-12-12 09:54:03.176	info	config useX1forAutomatic: false
                        
                        kecontact.0
                        2021-12-12 09:54:03.175	info	config loadChargingSessions: true
                        
                        kecontact.0
                        2021-12-12 09:54:03.175	info	config pollInterval: 30
                        
                        kecontact.0
                        2021-12-12 09:54:03.175	info	config passiveMode: false
                        
                        kecontact.0
                        2021-12-12 09:54:03.174	info	config host: 192.168.x.x
                        
                        kecontact.0
                        2021-12-12 09:53:58.682	error	no energy meters defined - power limitation deactivated
                        
                        kecontact.0
                        2021-12-12 09:53:58.679	info	starting charging station in active mode
                        
                        kecontact.0
                        2021-12-12 09:53:58.609	info	starting. Version 1.3.3 in /opt/iobroker/node_modules/iobroker.kecontact, node: v12.22.2, js-controller: 3.3.21
                        
                        kecontact.0
                        2021-12-12 09:53:49.940	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                        
                        kecontact.0
                        2021-12-12 09:53:49.930	info	terminating
                        
                        kecontact.0
                        2021-12-12 09:53:49.924	info	Got terminate signal TERMINATE_YOURSELF
                        
                        kecontact.0
                        2021-12-12 09:52:54.399	info	Keba firmware check: latest firmware installed
                        
                        kecontact.0
                        2021-12-12 09:52:54.394	warn	Keba KeContact P30 Deutschland-Edition detected. Regulation may be inaccurate.
                        
                        kecontact.0
                        2021-12-12 09:52:53.063	info	config wallboxNotIncluded: true
                        
                        kecontact.0
                        2021-12-12 09:52:53.062	info	config stateEnergyMeter3:
                        
                        kecontact.0
                        2021-12-12 09:52:53.062	info	config stateEnergyMeter2:
                        
                        kecontact.0
                        2021-12-12 09:52:53.062	info	config stateEnergyMeter1:
                        
                        kecontact.0
                        2021-12-12 09:52:53.061	info	config maxPower: 11000
                        
                        kecontact.0
                        2021-12-12 09:52:53.061	info	config regardTime: 300
                        
                        kecontact.0
                        2021-12-12 09:52:53.061	info	config minTime: 300
                        
                        kecontact.0
                        2021-12-12 09:52:53.060	info	config underusage: 500
                        
                        kecontact.0
                        2021-12-12 09:52:53.060	info	config delta: 500
                        
                        kecontact.0
                        2021-12-12 09:52:53.059	info	config addPower: 0
                        
                        kecontact.0
                        2021-12-12 09:52:53.057	info	config minAmperage: 6000
                        
                        kecontact.0
                        2021-12-12 09:52:53.055	info	config statesIncludeWallbox: true
                        
                        kecontact.0
                        2021-12-12 09:52:53.055	info	config stateSurplus: solarlog.0.status.feed
                        
                        kecontact.0
                        2021-12-12 09:52:53.055	info	config stateRegard:
                        
                        kecontact.0
                        2021-12-12 09:52:53.054	info	config useX1forAutomatic: false
                        
                        kecontact.0
                        2021-12-12 09:52:53.052	info	config loadChargingSessions: true
                        
                        kecontact.0
                        2021-12-12 09:52:53.052	info	config pollInterval: 30
                        
                        kecontact.0
                        2021-12-12 09:52:53.051	info	config passiveMode: false
                        
                        kecontact.0
                        2021-12-12 09:52:53.048	info	config host: 192.168.x.x
                        
                        kecontact.0
                        2021-12-12 09:52:49.851	error	no energy meters defined - power limitation deactivated
                        
                        kecontact.0
                        2021-12-12 09:52:49.848	info	starting charging station in active mode
                        
                        kecontact.0
                        2021-12-12 09:52:49.801	info	starting. Version 1.3.3 in /opt/iobroker/node_modules/iobroker.kecontact, node: v12.22.2, js-controller: 3.3.21
                        
                        S 1 Antwort Letzte Antwort
                        0
                        • H hardl

                          @sneak-l8 Hier noch das Protokoll:

                          contact.0
                          2021-12-12 10:26:48.820	info	stop charging
                          
                          kecontact.0
                          2021-12-12 10:26:18.817	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:25:48.818	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:25:18.813	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:24:48.810	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:24:18.810	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:23:48.812	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:23:18.810	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:22:48.807	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:22:18.807	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:21:48.809	info	minimum regard time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:20:48.807	info	minimum charge time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:20:18.807	info	minimum charge time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:19:48.809	info	regulate wallbox from 8500 to 6000mA
                          
                          kecontact.0
                          2021-12-12 10:19:48.808	info	minimum charge time of 300sec not reached, continuing charging session
                          
                          kecontact.0
                          2021-12-12 10:17:48.802	info	regulate wallbox from 8000 to 8500mA
                          
                          kecontact.0
                          2021-12-12 10:17:18.803	info	regulate wallbox from 7500 to 8000mA
                          
                          kecontact.0
                          2021-12-12 10:16:18.800	info	vehicle (re)starts to charge
                          
                          kecontact.0
                          2021-12-12 10:15:48.800	info	(re)start charging
                          
                          kecontact.0
                          2021-12-12 10:08:20.212	info	vehicle plugged to wallbox
                          
                          kecontact.0
                          2021-12-12 09:54:04.434	info	Keba firmware check: latest firmware installed
                          
                          kecontact.0
                          2021-12-12 09:54:04.430	warn	Keba KeContact P30 Deutschland-Edition detected. Regulation may be inaccurate.
                          
                          kecontact.0
                          2021-12-12 09:54:03.182	info	config wallboxNotIncluded: true
                          
                          kecontact.0
                          2021-12-12 09:54:03.182	info	config stateEnergyMeter3:
                          
                          kecontact.0
                          2021-12-12 09:54:03.180	info	config stateEnergyMeter2:
                          
                          kecontact.0
                          2021-12-12 09:54:03.180	info	config stateEnergyMeter1:
                          
                          kecontact.0
                          2021-12-12 09:54:03.180	info	config maxPower: 11000
                          
                          kecontact.0
                          2021-12-12 09:54:03.179	info	config regardTime: 300
                          
                          kecontact.0
                          2021-12-12 09:54:03.179	info	config minTime: 300
                          
                          kecontact.0
                          2021-12-12 09:54:03.179	info	config underusage: 500
                          
                          kecontact.0
                          2021-12-12 09:54:03.178	info	config delta: 500
                          
                          kecontact.0
                          2021-12-12 09:54:03.177	info	config addPower: 0
                          
                          kecontact.0
                          2021-12-12 09:54:03.177	info	config minAmperage: 6000
                          
                          kecontact.0
                          2021-12-12 09:54:03.177	info	config statesIncludeWallbox: false
                          
                          kecontact.0
                          2021-12-12 09:54:03.176	info	config stateSurplus: solarlog.0.status.feed
                          
                          kecontact.0
                          2021-12-12 09:54:03.176	info	config stateRegard:
                          
                          kecontact.0
                          2021-12-12 09:54:03.176	info	config useX1forAutomatic: false
                          
                          kecontact.0
                          2021-12-12 09:54:03.175	info	config loadChargingSessions: true
                          
                          kecontact.0
                          2021-12-12 09:54:03.175	info	config pollInterval: 30
                          
                          kecontact.0
                          2021-12-12 09:54:03.175	info	config passiveMode: false
                          
                          kecontact.0
                          2021-12-12 09:54:03.174	info	config host: 192.168.x.x
                          
                          kecontact.0
                          2021-12-12 09:53:58.682	error	no energy meters defined - power limitation deactivated
                          
                          kecontact.0
                          2021-12-12 09:53:58.679	info	starting charging station in active mode
                          
                          kecontact.0
                          2021-12-12 09:53:58.609	info	starting. Version 1.3.3 in /opt/iobroker/node_modules/iobroker.kecontact, node: v12.22.2, js-controller: 3.3.21
                          
                          kecontact.0
                          2021-12-12 09:53:49.940	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                          
                          kecontact.0
                          2021-12-12 09:53:49.930	info	terminating
                          
                          kecontact.0
                          2021-12-12 09:53:49.924	info	Got terminate signal TERMINATE_YOURSELF
                          
                          kecontact.0
                          2021-12-12 09:52:54.399	info	Keba firmware check: latest firmware installed
                          
                          kecontact.0
                          2021-12-12 09:52:54.394	warn	Keba KeContact P30 Deutschland-Edition detected. Regulation may be inaccurate.
                          
                          kecontact.0
                          2021-12-12 09:52:53.063	info	config wallboxNotIncluded: true
                          
                          kecontact.0
                          2021-12-12 09:52:53.062	info	config stateEnergyMeter3:
                          
                          kecontact.0
                          2021-12-12 09:52:53.062	info	config stateEnergyMeter2:
                          
                          kecontact.0
                          2021-12-12 09:52:53.062	info	config stateEnergyMeter1:
                          
                          kecontact.0
                          2021-12-12 09:52:53.061	info	config maxPower: 11000
                          
                          kecontact.0
                          2021-12-12 09:52:53.061	info	config regardTime: 300
                          
                          kecontact.0
                          2021-12-12 09:52:53.061	info	config minTime: 300
                          
                          kecontact.0
                          2021-12-12 09:52:53.060	info	config underusage: 500
                          
                          kecontact.0
                          2021-12-12 09:52:53.060	info	config delta: 500
                          
                          kecontact.0
                          2021-12-12 09:52:53.059	info	config addPower: 0
                          
                          kecontact.0
                          2021-12-12 09:52:53.057	info	config minAmperage: 6000
                          
                          kecontact.0
                          2021-12-12 09:52:53.055	info	config statesIncludeWallbox: true
                          
                          kecontact.0
                          2021-12-12 09:52:53.055	info	config stateSurplus: solarlog.0.status.feed
                          
                          kecontact.0
                          2021-12-12 09:52:53.055	info	config stateRegard:
                          
                          kecontact.0
                          2021-12-12 09:52:53.054	info	config useX1forAutomatic: false
                          
                          kecontact.0
                          2021-12-12 09:52:53.052	info	config loadChargingSessions: true
                          
                          kecontact.0
                          2021-12-12 09:52:53.052	info	config pollInterval: 30
                          
                          kecontact.0
                          2021-12-12 09:52:53.051	info	config passiveMode: false
                          
                          kecontact.0
                          2021-12-12 09:52:53.048	info	config host: 192.168.x.x
                          
                          kecontact.0
                          2021-12-12 09:52:49.851	error	no energy meters defined - power limitation deactivated
                          
                          kecontact.0
                          2021-12-12 09:52:49.848	info	starting charging station in active mode
                          
                          kecontact.0
                          2021-12-12 09:52:49.801	info	starting. Version 1.3.3 in /opt/iobroker/node_modules/iobroker.kecontact, node: v12.22.2, js-controller: 3.3.21
                          
                          S Offline
                          S Offline
                          Sneak-L8
                          schrieb am zuletzt editiert von
                          #448

                          @hardl Sieht soweit eigentlich alles gut aus.
                          Solange das Auto nicht lädt, bleibt auch chargingPhases auf null. Das ist ja nur eine Info, mit was der Adapter gerade versucht zu laden. calcPhases hast Du korrekt auf 3 gesetzt.
                          Was das Auto da an Fehlern meldet, kenne ich von meinem ID.3. Der meldet meist auch Ladefehler, aber auch mal Ladebereitschaft. Ich glaube, das liegt nicht am Adapter sondern wie das Auto das eingesteckte Kabel interpretiert, von dem aber kein Strom kommt...
                          "maxPower" ist auch null, das wird aber nur benötigt, bei Lastbegrenzung (der unterste Abschnitt in der Konfig).
                          Soweit erkenne ich jetzt nichts Falsches.

                          H 1 Antwort Letzte Antwort
                          0
                          • S Sneak-L8

                            @hardl Sieht soweit eigentlich alles gut aus.
                            Solange das Auto nicht lädt, bleibt auch chargingPhases auf null. Das ist ja nur eine Info, mit was der Adapter gerade versucht zu laden. calcPhases hast Du korrekt auf 3 gesetzt.
                            Was das Auto da an Fehlern meldet, kenne ich von meinem ID.3. Der meldet meist auch Ladefehler, aber auch mal Ladebereitschaft. Ich glaube, das liegt nicht am Adapter sondern wie das Auto das eingesteckte Kabel interpretiert, von dem aber kein Strom kommt...
                            "maxPower" ist auch null, das wird aber nur benötigt, bei Lastbegrenzung (der unterste Abschnitt in der Konfig).
                            Soweit erkenne ich jetzt nichts Falsches.

                            H Offline
                            H Offline
                            hardl
                            schrieb am zuletzt editiert von
                            #449

                            @sneak-l8 Ich weiß zwar nicht woher im Protokoll die 8,5 A kommen, aber ich werde das weiter beobachten.
                            Jetzt müsste doch bei einem surplus von >1,4 kW der Ladevorgang starten?

                            Die Sonne spielt aber momentan nicht mit.

                            S 1 Antwort Letzte Antwort
                            0
                            • H hardl

                              @sneak-l8 Ich weiß zwar nicht woher im Protokoll die 8,5 A kommen, aber ich werde das weiter beobachten.
                              Jetzt müsste doch bei einem surplus von >1,4 kW der Ladevorgang starten?

                              Die Sonne spielt aber momentan nicht mit.

                              S Offline
                              S Offline
                              Sneak-L8
                              schrieb am zuletzt editiert von
                              #450

                              @hardl Surplus muss schon 3 x 230V * 6A = 4,14kW haben, damit der Ladevorgang startet. Du hast ja drei Phasen angegeben.
                              BTW: solange kein Fahrzeug angesteckt ist, wird auch surplus nicht aktualisiert. Sollte man auch am Zeitstemepl des States sehen.

                              H 1 Antwort Letzte Antwort
                              0
                              • S Sneak-L8

                                @hardl Surplus muss schon 3 x 230V * 6A = 4,14kW haben, damit der Ladevorgang startet. Du hast ja drei Phasen angegeben.
                                BTW: solange kein Fahrzeug angesteckt ist, wird auch surplus nicht aktualisiert. Sollte man auch am Zeitstemepl des States sehen.

                                H Offline
                                H Offline
                                hardl
                                schrieb am zuletzt editiert von
                                #451

                                @sneak-l8 So langsam verstehe ich auch, warum man (im Winter) zusätzlichen Netzbezug freigeben sollte.
                                Bei meiner PV mit 8,9 kWp ist ja um diese Zeit ein feed von > 4 kW eher selten.
                                Könnte man z.B. ein Skript erstellen, das von surplus 1,4-2,8 kW den state der Phasen auf 1, bei 2,8-4,2 kW auf 2 und bei >4,2 auf 3 Phasen stellt oder lässt das die Software vom Auto nicht zu?

                                S 1 Antwort Letzte Antwort
                                0
                                • H hardl

                                  @sneak-l8 So langsam verstehe ich auch, warum man (im Winter) zusätzlichen Netzbezug freigeben sollte.
                                  Bei meiner PV mit 8,9 kWp ist ja um diese Zeit ein feed von > 4 kW eher selten.
                                  Könnte man z.B. ein Skript erstellen, das von surplus 1,4-2,8 kW den state der Phasen auf 1, bei 2,8-4,2 kW auf 2 und bei >4,2 auf 3 Phasen stellt oder lässt das die Software vom Auto nicht zu?

                                  S Offline
                                  S Offline
                                  Sneak-L8
                                  schrieb am zuletzt editiert von
                                  #452

                                  @hardl Natürlich kannst Du die calcPhases per Skript umstellen. Allerdings stellst du damit nur ein mit wievielen Phasen der Adapter die Ladeleistung kalkuliert. Damit wird nicht geregelt mit wievielen Phasen geladen wird. Das entscheidet allein Auto und Wallbox untereinander und nehmen dabei das maximal mögliche.
                                  Dann müsstest Du schon vor einem Ladevorgang mache Phasen abschalten, um z.B. ein einphasiges Laden zu ermöglichen. Die Box kann das nicht. Sie lädt imemr mit allen Phasen die angeschlossen sind.

                                  Aber einen zusätzlichen Netzbezug kannst Du natürlich skriptgesteuert für die Wintermonate aktivieren und in den Sommermonaten wieder auf null zurückfahren.

                                  1 Antwort Letzte Antwort
                                  0
                                  • H Offline
                                    H Offline
                                    hardl
                                    schrieb am zuletzt editiert von
                                    #453

                                    @sneak-l8 Kannst Du mir bitte noch sagen, was sich hinter currentTimer, currentUser, maxCurrent und maxPercent verbirgt oder gibt es irgendwo eine Erklärung?

                                    S 1 Antwort Letzte Antwort
                                    0
                                    • H hardl

                                      @sneak-l8 Kannst Du mir bitte noch sagen, was sich hinter currentTimer, currentUser, maxCurrent und maxPercent verbirgt oder gibt es irgendwo eine Erklärung?

                                      S Offline
                                      S Offline
                                      Sneak-L8
                                      schrieb am zuletzt editiert von
                                      #454

                                      @hardl mit currentTimer kann glaub ich eine Dauer der Stromstärke angegeben werden. Die Details findest du im UDP-Handbuch von Keba zum Download unter: https://www.keba.com/de/emobility/service-support/downloads/downloads.
                                      Werden vom Adapter aber nicht aktiv genutzt.

                                      H 1 Antwort Letzte Antwort
                                      0
                                      • S Sneak-L8

                                        @hardl mit currentTimer kann glaub ich eine Dauer der Stromstärke angegeben werden. Die Details findest du im UDP-Handbuch von Keba zum Download unter: https://www.keba.com/de/emobility/service-support/downloads/downloads.
                                        Werden vom Adapter aber nicht aktiv genutzt.

                                        H Offline
                                        H Offline
                                        hardl
                                        schrieb am zuletzt editiert von
                                        #455

                                        @sneak-l8 Ich muss Dich leider nochmal belästigen, sorry.
                                        Heute ist endlich mal mehr Sonne und surplus bewegt sich zwischen 3 und 5 kW.
                                        Bei addPower 0 bricht der Vorgang immer wieder ab, wenn der Stromverbrauch im Haus steigt oder eine Wolke kommt.
                                        Ich habe das mal auf 1000 gesetzt. Müsste jetzt surplus+ 1000 oder nur surplus als Lademenge kommen und die 1000 erst bei Unterschreitung von 4,14 kW?
                                        Ich hänge mal die Screenshots an.
                                        Bildschirmfoto 2021-12-20 um 14.02.00.png Bildschirmfoto 2021-12-20 um 14.02.34.png Bildschirmfoto 2021-12-20 um 14.02.56.png Bildschirmfoto 2021-12-20 um 14.03.19.png

                                        S 1 Antwort Letzte Antwort
                                        0
                                        • J Offline
                                          J Offline
                                          JamesB
                                          schrieb am zuletzt editiert von
                                          #456

                                          Servus, gleich vorweg, ich habe noch nicht sehr viel Erfahrung mit ioBroker. Er ist über Docker Compose installiert und scheint gut zu laufen.

                                          Ich erhalte jedoch keine saubere Verbindung zu Keba. Hat das mit diesen Infos zu tun?

                                          kecontact.0
                                          	2021-12-21 08:39:42.117	info	config pollInterval: 300
                                          kecontact.0
                                          	2021-12-21 08:39:42.116	info	config passiveMode: true
                                          kecontact.0
                                          	2021-12-21 08:39:42.116	info	config host: 192.168.188.80
                                          kecontact.0
                                          	2021-12-21 08:39:41.480	info	starting charging station in passive mode
                                          kecontact.0
                                          	2021-12-21 08:39:41.444	info	starting. Version 1.3.2 in /opt/iobroker/node_modules/iobroker.kecontact, node: v14.18.2, js-controller: 3.3.21
                                          kecontact.0
                                          	2021-12-21 08:39:35.631	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                          kecontact.0
                                          	2021-12-21 08:39:35.628	info	terminating
                                          kecontact.0
                                          	2021-12-21 08:39:35.623	info	Got terminate signal TERMINATE_YOURSELF
                                          

                                          Der Port 7090 ist in docker-compose eingetragen: "7090:7090/udp"

                                          Wenn ich mit einem ähnlichen FHEM Modul (auch über Docker) teste, funktioniert das einlesen der Daten problemlos.

                                          Lauf Log findet die Instaz auch schon viele Informationen:

                                          kecontact.0
                                          	2021-12-21 08:43:04.802	debug	UDP datagram from 172.20.0.1:53634: '{ "ID": "1", "Product": "KC-P30-EC240122-E00", "Serial": "21293217", "Firmware":"P30 v 3.10.16 (200708-201734)", "COM-module": 0, "Backend": 0, "timeQ": 3, "DIP-Sw1": "0x20", "DIP-Sw2": "0x00", "Sec": 4385857 } '
                                          

                                          Es werden aber keine Datenpunkte erzeugt. Hat jemand eine Idee wie ich hier weiter kommen könnte?

                                          S 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          639

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe