    4. [Adapter] NUT Adapter (USV/UPS auslesen per NUT)

    NEWS

    • Neuer Blog: Fotos und Eindrücke aus Solingen

    • ioBroker@Smart Living Forum Solingen, 14.06. - Agenda added

    • ioBroker goes Matter ... Matter Adapter in Stable

    [Adapter] NUT Adapter (USV/UPS auslesen per NUT)

    This topic has been deleted. Only users with topic management privileges can see it.
    • Homoran
      Homoran Global Moderator Administrators @e-i-k-e last edited by

      @e-i-k-e
      Kennst du den hervorragenden thread von @klassisch ?

      https://forum.iobroker.net/topic/23688/howto-usv-nut-server-auf-sbc-installieren

      oberfragger 1 Reply Last reply Reply Quote 0
      • oberfragger
        oberfragger @Homoran last edited by oberfragger

        @ChristianF Danke für die Qnap-Settings.
        Der besseren Auffindbarkeit halber noch einmal wiederholt.

        Ich habe die EATON 5p 1150i via USB-Kabel an mein Qnap 212-P geschlossen und folgendes aktiviert:

        1ef244aa-b5ff-4589-a0db-f86827b5c868-image.png

        Dann den Nut-Adapter installiert und folgende Einstellungen gewählt:
        691357ae-72ad-463f-981f-c65c52a73227-image.png
        IP der Qnap
        Passwort ist 123456

        Das wars dann schon. Leider habe ich die "Uptime" nioch nicht in den Objekten gefunden. Mal weitersuchen. Ansonsten natürlich den geposteten Link von @Homoran ansehen. Gerade dazugelernt dass meine Lösung, die mit Haken ist 😉

        1 Reply Last reply Reply Quote 0
        • K
          klassisch Most Active last edited by klassisch

          @apollon77 Wie geht der TCP-Eingang mit eventuell im NUT Server gepufferten Daten um? Werden diese gequeued oder werde die alten Werte verwofen und immer nur der neueste Wert genommen, wie das mittlerweile im smartmeter Adapter der Fall ist, siehe https://forum.iobroker.net/topic/36851/solved-smartmeter-buffering-dateneingang-via-tcp ?

          1 Reply Last reply Reply Quote 0
          • Holger Etzel
            Holger Etzel last edited by

            Hallo,

            ich habe den NUT-Adapter im iobroker am laufen. Die USV hängt an einer Synology,
            Soweit funktioniert alles soweit.

            Meine Frage:
            Angeblich liefert meine USV (APC) auch Werte wie Akku-Temperatur und Entladestrom.
            Diese Datenpunkte fehlen bei mir.

            Besteht die Möglichkeit diese Daten trotzdem abzurufen? Entweder über den NUT-Adapter oder über snmp?

            im voraus schon mal danke.

            Homoran 1 Reply Last reply Reply Quote 0
            • Homoran
              Homoran Global Moderator Administrators @Holger Etzel last edited by

              @holger-etzel sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

              Besteht die Möglichkeit diese Daten trotzdem abzurufen? Entweder über den NUT-Adapter oder über snmp?

              wenn die Daten tatsächlich zur Verfügung gestellt werden, dann ja

              @holger-etzel sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

              Angeblich liefert meine USV (APC) auch Werte wie Akku-Temperatur und Entladestrom.

              Welche APC und woher diese Info?
              Und wie sehen deine Datenpunkte aus?

              Homoran 1 Reply Last reply Reply Quote 0
              • Holger Etzel
                Holger Etzel last edited by

                @homoran

                habe das gefunden auf: https://www.opsview.com/resources/monitoring/blog/apc-ups-monitoring-useful-oids

                Da werden verschieden oid´s angegeben. Weis aber nicht genau ob es wirklich funktioniert, da meine USV keine eigene IP hat.

                Battery Information
                Battery capacity .1.3.6.1.4.1.318.1.1.1.2.2.1.0
                Battery capacity as % of total
                Battery temperature .1.3.6.1.4.1.318.1.1.1.2.2.2.0
                Battery temperature in Celcius of Farenheit - depending on how UPS is configured
                Battery runtime remain .1.3.6.1.4.1.318.1.1.1.2.2.3.0
                Total battery runtime available based on current load.
                Battery replace .1.3.6.1.4.1.318.1.1.1.2.2.4.0

                UPS Output
                Output voltage .1.3.6.1.4.1.318.1.1.1.4.2.1.0
                Output voltage from the UPS
                Output frequency .1.3.6.1.4.1.318.1.1.1.4.2.2.0
                Output frequency in Hz
                Output load .1.3.6.1.4.1.318.1.1.1.4.2.3.0
                Output load expressed as % of capacity
                Output current .1.3.6.1.4.1.318.1.1.1.4.2.4.0
                Output current in Amps

                1 Reply Last reply Reply Quote 0
                • Homoran
                  Homoran Global Moderator Administrators @Homoran last edited by Homoran

                  @homoran sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

                  Welche APC

                  bleibt leider offen 😞

                  @homoran sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

                  wie sehen deine Datenpunkte aus?

                  Hier wäre es auch zu sehen gewesen.

                  @holger-etzel sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

                  habe das gefunden auf:

                  ist auch keine gerätespezifische Info.
                  Verschiedene APC haben unterschiedlich umfangreiche Infos

                  @holger-etzel sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

                  Weis aber nicht genau ob es wirklich funktioniert, da meine USV keine eigene IP hat.

                  so ist es.
                  Da sie nicht im Netz, sondern an der Syno hängt, kommst du da zumindest so einfach nicht ran.
                  Ob deine unbekannte APC diese Infos unterstützt, und der NUT-Server auf der Syno die unterschlägt musst du selber herausbekommen

                  Holger Etzel 1 Reply Last reply Reply Quote 0
                  • Holger Etzel
                    Holger Etzel @Homoran last edited by

                    @homoran nut.PNG

                    so sieht das bei mir aus

                    Homoran 1 Reply Last reply Reply Quote 0
                    • Homoran
                      Homoran Global Moderator Administrators @Holger Etzel last edited by

                      @holger-etzel sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

                      so sieht das bei mir aus

                      Danke für den Typ deiner APC!

                      Deine Back-UPS BX kann ich hier nicht finden:
                      https://networkupstools.org/stable-hcl.html

                      Holger Etzel 1 Reply Last reply Reply Quote 0
                      • Holger Etzel
                        Holger Etzel @Homoran last edited by

                        @homoran

                        scheint so, das meine Datenpunkte alle vorhanden sind was der Treiber her gibt.
                        Trotzdem schon mal danke.

                        1 Reply Last reply Reply Quote 0
                        • Holger Etzel
                          Holger Etzel last edited by

                          Hallo,

                          ich habe mal noch eine Frage.
                          Ich benutze noch eine Eaton USV vom Typ 3S mit dem Treiber "usbhid-ups".
                          Hier sind die Datenpunkte für laden und entladen etc. immer auf false gesetzt. Ist das überhaupt dann der richtige Treiber?
                          Oder gibt es einen anderen Treiber der die Datenpunkte liefert?

                          Im voraus schon mal danke.

                          K 1 Reply Last reply Reply Quote 0
                          • K
                            klassisch Most Active @Holger Etzel last edited by klassisch

                            @holger-etzel schwer zu sagen, ob diese Eaton mehr liefern würde. Die USV sind unterschiedlich gesprächig. Wahrscheinlich verrät die 3S diese Daten gar nicht.
                            jedenfalls setzen die typischen Treffer der Suchmaschine diesen Treiber auch ein; Beispiel 1, Beispiel 2, Beispiel 3

                            Und auch die NUT-Seite listet den usbhid-ups für Eaton S3, Siehe dort

                            1 Reply Last reply Reply Quote 0
                            • N
                              nerg last edited by

                              Ich kriege leider nur noch "Error happend: Error: connect ECONNREFUSED 192.168.178.47:3493" 😞

                              USV hängt am Synology NAS. Dort habe ich die IP vom iobroker eingetragen unter "zugelassene Diskstation-Geräte" und den Port in der DSM-Firewall ebenfalls freigegeben. Im Adapter ist der Name "ups" und bei User und Passwort weiß ich nicht, was ich noch eintragen könnte. hab alles durchprobiert 😞

                              Wo könnte mein Fehler sein?

                              K 1 Reply Last reply Reply Quote 0
                              • K
                                klassisch Most Active @nerg last edited by klassisch

                                @nerg Schau mal dort
                                https://forum.iobroker.net/post/81243

                                Versuche es mal mit user ups und secret als Passwort.
                                Manchmal liest man auch user monuser und secret als PWD

                                Wenn das auch nicht hilft, dann den Adapter auf loglevel debug stellen und den nächsten Anmeldeversuch mitprotokolliern.

                                N 1 Reply Last reply Reply Quote 0
                                • N
                                  nerg @klassisch last edited by

                                  @klassisch "ups" als user kannte ich nicht, klappt aber leider nicht. "monuser" hatte ich sogar auch schon gefunden 😞

                                  Debug/Silly liefern da leider auch keine zusätzlichen Infos:

                                  nut.0	2021-04-08 13:48:55.280	warn	(28230) State "nut.0.status.severity" has no existing object, this might lead to an error in future versions
                                  nut.0	2021-04-08 13:48:55.279	debug	(28230) Set State status.severity = 4
                                  nut.0	2021-04-08 13:48:55.277	debug	(28230) Set State status.shutdown = false
                                  nut.0	2021-04-08 13:48:55.277	debug	(28230) Create State status.shutdown
                                  nut.0	2021-04-08 13:48:55.275	debug	(28230) Set State status.boosting = false
                                  nut.0	2021-04-08 13:48:55.274	debug	(28230) Create State status.boosting
                                  nut.0	2021-04-08 13:48:55.273	debug	(28230) Set State status.trimming = false
                                  nut.0	2021-04-08 13:48:55.272	debug	(28230) Create State status.trimming
                                  nut.0	2021-04-08 13:48:55.270	debug	(28230) Set State status.overload = false
                                  nut.0	2021-04-08 13:48:55.270	debug	(28230) Create State status.overload
                                  nut.0	2021-04-08 13:48:55.268	debug	(28230) Set State status.offline = false
                                  nut.0	2021-04-08 13:48:55.267	debug	(28230) Create State status.offline
                                  nut.0	2021-04-08 13:48:55.265	debug	(28230) Set State status.calibration = false
                                  nut.0	2021-04-08 13:48:55.265	debug	(28230) Create State status.calibration
                                  nut.0	2021-04-08 13:48:55.263	debug	(28230) Set State status.bypass = false
                                  nut.0	2021-04-08 13:48:55.262	debug	(28230) Create State status.bypass
                                  nut.0	2021-04-08 13:48:55.261	debug	(28230) Set State status.discharging = false
                                  nut.0	2021-04-08 13:48:55.260	debug	(28230) Create State status.discharging
                                  nut.0	2021-04-08 13:48:55.258	debug	(28230) Set State status.charging = false
                                  nut.0	2021-04-08 13:48:55.257	debug	(28230) Create State status.charging
                                  nut.0	2021-04-08 13:48:55.256	debug	(28230) Set State status.replacebattery = false
                                  nut.0	2021-04-08 13:48:55.255	debug	(28230) Create State status.replacebattery
                                  nut.0	2021-04-08 13:48:55.253	debug	(28230) Set State status.highbattery = false
                                  nut.0	2021-04-08 13:48:55.253	debug	(28230) Create State status.highbattery
                                  nut.0	2021-04-08 13:48:55.251	debug	(28230) Set State status.lowbattery = false
                                  nut.0	2021-04-08 13:48:55.250	debug	(28230) Create State status.lowbattery
                                  nut.0	2021-04-08 13:48:55.249	debug	(28230) Set State status.onbattery = false
                                  nut.0	2021-04-08 13:48:55.248	debug	(28230) Create State status.onbattery
                                  nut.0	2021-04-08 13:48:55.245	debug	(28230) Set State status.online = false
                                  nut.0	2021-04-08 13:48:55.245	debug	(28230) Create State status.online
                                  nut.0	2021-04-08 13:48:55.243	debug	(28230) NUT Connection closed. Done.
                                  nut.0	2021-04-08 13:48:55.243	error	(28230) Error happend: Error: connect ECONNREFUSED 192.168.178.47:3493
                                  nut.0	2021-04-08 13:48:55.196	silly	(28230) States system redis pmessage system.adapter.nut.0.logLevel/system.adapter.nut.0.logLevel:{"val":"silly","ack":true,"ts":1617882535192,"q":0,"from":"system.adapter.nut.0","lc":1617882535192}
                                  nut.0	2021-04-08 13:48:55.182	info	(28230) starting. Version 1.4.3 in /opt/iobroker/node_modules/iobroker.nut, node: v12.22.0, js-controller: 3.2.16
                                  nut.0	2021-04-08 13:48:55.122	debug	(28230) Plugin sentry Initialize Plugin (enabled=true)
                                  nut.0	2021-04-08 13:48:51.608	info	(28217) Got terminate signal TERMINATE_YOURSELF
                                  nut.0	2021-04-08 13:48:51.607	silly	(28217) States system redis pmessage system.adapter.nut.0.sigKill/system.adapter.nut.0.sigKill:{"val":-1,"ack":false,"ts":1617882531606,"q":0,"from":"system.host.iobroker.ruping","lc":1617882531606}
                                  nut.0	2021-04-08 13:48:51.383	warn	(28217) Terminated (NO_ADAPTER_CONFIG_FOUND): Without reason
                                  
                                  K 1 Reply Last reply Reply Quote 0
                                  • K
                                    klassisch Most Active @nerg last edited by

                                    @nerg login upsmon PWD secret auch schon getestet?

                                    N 1 Reply Last reply Reply Quote 0
                                    • N
                                      nerg @klassisch last edited by

                                      @klassisch Ich habs grad lösen können. Es ist traurig und es tut mir ein wenig leid vorher hier geschrieben zu haben 😞 😄

                                      Ich habe den USV Server der Synology DS nochmal aus und wieder an gemacht...... 😄

                                      1 Reply Last reply Reply Quote 0
                                      • Homoran
                                        Homoran Global Moderator Administrators last edited by

                                        @nerg
                                        @klassisch

                                        ich habe gerade festgestellt dass ich auch die ECONNREFUSED Fehlermeldung seit 2 Tagen habe.
                                        Danke fpr den Tipp mit dem Neustarten des Nut servers.
                                        werde ich morgen mal testen

                                        K 1 Reply Last reply Reply Quote 0
                                        • K
                                          klassisch Most Active @Homoran last edited by klassisch

                                          @homoran Welche Konfiguration fährst Du gerade? Syno als NUT Server oder SBC als NUT Server wie dort beschrieben oder gar Container, VM LX? unter Docker?
                                          Bei mir scheint noch alles zu funktionieren. Kein (related) Error im log letztee Datenupdates wenige Minuten alt.
                                          Adapter Version 1.4.3. Mit stable wird mir auch nichts Neueres angeboten und laut Änderungshistory gibt es auch nichts Neueres und die letzte Neuerung war "Enhance the port check", vorletzte "(Apollon77) Check configured port before using it (Sentry IOBROKER-NUT-3)" .
                                          Mein NUT tragender SBC ist ein OrangePi Plus 2e. An dem ich seit Einrichtung NICHTS mehr gemacht habe - schon gar kein Update.
                                          Nach der armbian Neuinstallation anläßlich der Umwidmung von ioBroker auf NUT-Server hatte der OPi nur noch 1 MByte statt 2 MByte RAM.

                                          Auf meinem NUT-Rechner läuft

                                          Welcome to ARMBIAN 5.85 stable Debian GNU/Linux 9 (stretch) 4.19.38-sunxi
                                          System load:   0.00 0.00 0.00   Up time:       648 days
                                          Memory usage:  9 % of 999MB     IP:            192.168.1.85
                                          CPU temp:      22°C
                                          Usage of /:    8% of 15G
                                          
                                          

                                          Ja, die reine Verschwendung, völliger Luxus. Aber läuft - bisher.

                                          Homoran 1 Reply Last reply Reply Quote 0
                                          • Homoran
                                            Homoran Global Moderator Administrators @klassisch last edited by Homoran

                                            @klassisch sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

                                            Welche Konfiguration fährst Du gerade? Syno als NUT Server oder SBC als NUT Server wie dort beschrieben

                                            beides!
                                            Habe 2 APC700, eine im Hamsterkäfig an der Syno mit der Meldung und eine bei meinen SBC über den Cubie ohne Probleme

                                            @klassisch sagte in [Adapter] NUT Adapter (USV/UPS auslesen per NUT):

                                            Bei mir scheint noch alles zu funktionieren.

                                            deswegen tippe ich auf ein "Problem" bei der Synology.
                                            zumal @nerg anscheinend zur gleichen Zeit das Problem hatte
                                            07.04. um 05:37 ist meine letzte Aktualisierung der Daten

                                            Leider finde ich gerade keine Möglichkeit nur den NUT-Server auf der Syno neu zu starten

                                            EDIT:
                                            Bin aber auch blöd 😞
                                            Netzwerk UPS Server aktivieren abhaken - speichern - wieder anhaken und IP vom ioBroker neu eingeben - läuft wieder!

                                            K Nashra 2 Replies Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate
                                            FAQ Cloud / IOT
                                            HowTo: Node.js-Update
                                            HowTo: Backup/Restore
                                            Downloads
                                            BLOG

                                            679
                                            Online

                                            31.8k
                                            Users

                                            79.9k
                                            Topics

                                            1.3m
                                            Posts

                                            22
                                            76
                                            16280
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo