  4. IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.8k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.2k

IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
idmwärmepumpe modbuswärmepumpe
64 Beiträge 16 Kommentatoren 15.7k Aufrufe 13 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • B bastiaux91

    Ich bekomme beim Modbus Adapter beim Einbinden einer IDM Aero SLM ständig flogendes im Log:

    modbus.0
    	2024-03-08 15:22:06.461	info	Connected to slave 192.168.178.45
    modbus.0
    	2024-03-08 15:21:06.458	info	Disconnected from slave 192.168.178.45
    modbus.0
    	2024-03-08 15:15:18.051	info	Connected to slave 192.168.178.45
    modbus.0
    	2024-03-08 15:14:18.048	info	Disconnected from slave 192.168.178.45
    modbus.0
    	2024-03-08 15:13:33.013	info	Connected to slave 192.168.178.45
    modbus.0
    	2024-03-08 15:12:33.011	info	Disconnected from slave 192.168.178.45
    modbus.0
    	2024-03-08 15:11:58.765	info	Connected to slave 192.168.178.45
    modbus.0
    	2024-03-08 15:10:58.763	info	Disconnected from slave 192.168.178.45
    modbus.0
    	2024-03-08 14:59:35.864	info	Connected to slave 192.168.178.45
    modbus.0
    	2024-03-08 14:58:35.861	info	Disconnected from slave 192.168.178.45
    modbus.0
    	2024-03-08 14:58:01.603	info	Connected to slave 192.168.178.45
    modbus.0
    	2024-03-08 14:57:01.601	info	Disconnected from slave 192.168.178.45
    modbus.0
    	2024-03-08 14:56:27.340	info	Connected to slave 192.168.178.45
    modbus.0
    	2024-03-08 14:55:27.337	info	Disconnected from slave 192.168.178.45
    modbus.0
    	2024-03-08 14:54:53.080	info	Connected to slave 192.168.178.45
    modbus.0
    	2024-03-08 14:53:53.078	info	Disconnected from slave 192.168.178.45
    

    Das sind meine Einstellungen im Adapter:
    ca4b8408-434a-40a6-9226-98a5dbdc4033-grafik.png

    Wenn connected funktioniert alles lesend und schreibend soweit.
    Hat jemand eine Idee was hier noch nicht passt?

    WinniW Offline
    WinniW Offline
    Winni
    schrieb am zuletzt editiert von Winni
    #38

    @bastiaux91 ich habe andere Einstellungen, funktioniert aber einwandfrei.
    2024_03_08_16.08.27.jpg
    2024_03_08_16.07.44.jpg
    Ich habe eine AERO ALM 6-15

    Es gibt nicht Gutes. Außer man tut es. Erich Kästner

    B 1 Antwort Letzte Antwort
    0
    • WinniW Winni

      @bastiaux91 ich habe andere Einstellungen, funktioniert aber einwandfrei.
      2024_03_08_16.08.27.jpg
      2024_03_08_16.07.44.jpg
      Ich habe eine AERO ALM 6-15

      B Offline
      B Offline
      bastiaux91
      schrieb am zuletzt editiert von
      #39

      @winni Danke für die Infos.
      Ich habe nun mal noch die Wartezeit lesend ebenfalls auf 10000ms gestellt, aber das brachte auch keine Änderung.
      Habe zwischenzeitlich auch die IDM mal neu gestartet.
      Ein Ping auf die IDM liefert konstant 3ms ohne irgendwelche Abbrüche.

      Anbei auch mal meine Eingangs- und Holdingregister:
      2024-04-04 17_58_39-instances - iobroker – Mozilla Firefox.png

      2024-04-04 18_01_09-instances - iobroker – Mozilla Firefox.png

      2024-04-04 18_03_01-logs - iobroker – Mozilla Firefox.png

      1 Antwort Letzte Antwort
      0
      • R Offline
        R Offline
        Roli01
        schrieb am zuletzt editiert von
        #40

        Hallo!
        Hat von euch wer eine Aktuelles Register als Tab export für mich bitte?
        Die aus dem Post funktioniert nur bedingt mit dem Modbus TCP Navigator 2.0 von IDM!

        Danke

        Roli

        1 Antwort Letzte Antwort
        0
        • B Offline
          B Offline
          bastiaux91
          schrieb am zuletzt editiert von
          #41

          Hat jemand schonmal erfolgreich die WP mit den Adressen 1710 Anforderung Heizen, 1711 Anforderung Kühlen und 1712 Anforderung WW Ladung bzw. 1713 einmalige WW Ladung steuern können?
          Ich habe diese Adressen als Holding-Register, Unsigned 16 bit (Big Endian), Rolle: Switch, Haken bei Abrage, mit und ohne Haken bei CW getestet.

          Hier habe ich 1713 einmalige WW Ladung über ein blockly gesteuert, dies hat manchmal, aber nicht immer funktioniert.
          2024-09-09 14_30_05-javascript - iobroker – Mozilla Firefox.png

          Dieses blockly wollte ich zum vorzeitigen deaktivieren des Kühlens verwenden, aber es passiert gar nichts.
          372ce159-856b-4466-aeb6-520bc051ad51-grafik.png

          Wenn ich z.B. bei 1711 Anforderung Kühlen händisch eine "0" oder "1" eintrage passiert
          gar nichts, auch ändert sich der Zeitstempel des Objekts nicht.
          Weiß jemand, was ich hier noch falsch machen?

          1 Antwort Letzte Antwort
          0
          • C Offline
            C Offline
            ck_coke
            schrieb am zuletzt editiert von
            #42

            Beim Abfragen von Register 1008 (Wärmespeichertemperatur) bekomme ich immer den Fehler "ILLEGAL DATA ADDRESS".

            Über Modbus Poll kann ich das Register jedoch ohne Probleme abfragen.
            Scheint bei anderen Registern auch der Fall zu sein. Hatte das schon mal jemand?

            WinniW 1 Antwort Letzte Antwort
            0
            • C ck_coke

              Beim Abfragen von Register 1008 (Wärmespeichertemperatur) bekomme ich immer den Fehler "ILLEGAL DATA ADDRESS".

              Über Modbus Poll kann ich das Register jedoch ohne Probleme abfragen.
              Scheint bei anderen Registern auch der Fall zu sein. Hatte das schon mal jemand?

              WinniW Offline
              WinniW Offline
              Winni
              schrieb am zuletzt editiert von
              #43

              @ck_coke nein, funktioniert bei mir ohne Fehlermeldung.
              2025_02_18_13.33.06~2.jpg

              Es gibt nicht Gutes. Außer man tut es. Erich Kästner

              1 Antwort Letzte Antwort
              0
              • C Offline
                C Offline
                ck_coke
                schrieb am zuletzt editiert von
                #44

                @Bluefox Irgendeine Idee woran das liegen kann?

                HomoranH 1 Antwort Letzte Antwort
                0
                • C ck_coke

                  @Bluefox Irgendeine Idee woran das liegen kann?

                  HomoranH Nicht stören
                  HomoranH Nicht stören
                  Homoran
                  Global Moderator Administrators
                  schrieb am zuletzt editiert von
                  #45

                  @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                  @Bluefox Irgendeine Idee woran das liegen kann?

                  Da brauchst du Bluefox nicht zu fragen.
                  Ohne mehr Informationen über dein System kann der auch nichts sagen

                  kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                  der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                  C 1 Antwort Letzte Antwort
                  0
                  • HomoranH Homoran

                    @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                    @Bluefox Irgendeine Idee woran das liegen kann?

                    Da brauchst du Bluefox nicht zu fragen.
                    Ohne mehr Informationen über dein System kann der auch nichts sagen

                    C Offline
                    C Offline
                    ck_coke
                    schrieb am zuletzt editiert von ck_coke
                    #46

                    @homoran
                    Welche Infos werden denn benötigt?

                    Die Debug Meldungen aus dem Adapter geben folgendes zurück:

                    
                    modbus.54
                    2025-02-19 08:05:13.691	warn	[DevID_1] Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                    
                    modbus.54
                    2025-02-19 08:05:13.691	debug	Received pdu describes an error.
                    
                    modbus.54
                    2025-02-19 08:05:13.689	debug	[DevID_1/holdingRegs] Poll address 1000 - 10 registers
                    
                    modbus.54
                    2025-02-19 08:05:13.688	debug	[DevID_1] Poll start ---------------------
                    
                    HomoranH 1 Antwort Letzte Antwort
                    0
                    • C ck_coke

                      @homoran
                      Welche Infos werden denn benötigt?

                      Die Debug Meldungen aus dem Adapter geben folgendes zurück:

                      
                      modbus.54
                      2025-02-19 08:05:13.691	warn	[DevID_1] Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                      
                      modbus.54
                      2025-02-19 08:05:13.691	debug	Received pdu describes an error.
                      
                      modbus.54
                      2025-02-19 08:05:13.689	debug	[DevID_1/holdingRegs] Poll address 1000 - 10 registers
                      
                      modbus.54
                      2025-02-19 08:05:13.688	debug	[DevID_1] Poll start ---------------------
                      
                      HomoranH Nicht stören
                      HomoranH Nicht stören
                      Homoran
                      Global Moderator Administrators
                      schrieb am zuletzt editiert von
                      #47

                      @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                      Die Debug Meldungen

                      und die Einstellungen?

                      @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                      Poll address 1000 - 10 registers

                      mag das Gerät das?

                      kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                      der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                      C S 2 Antworten Letzte Antwort
                      0
                      • HomoranH Homoran

                        @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                        Die Debug Meldungen

                        und die Einstellungen?

                        @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                        Poll address 1000 - 10 registers

                        mag das Gerät das?

                        C Offline
                        C Offline
                        ck_coke
                        schrieb am zuletzt editiert von
                        #48

                        @homoran
                        Danke! Das war der richtige Hinweis.
                        Mit maximal 7 Registern (Float) funktioniert es.

                        S 1 Antwort Letzte Antwort
                        0
                        • C ck_coke

                          @homoran
                          Danke! Das war der richtige Hinweis.
                          Mit maximal 7 Registern (Float) funktioniert es.

                          S Offline
                          S Offline
                          Snopy_16
                          schrieb am zuletzt editiert von
                          #49

                          @ck_coke Wie hast du das gelöst. Ich habe das selbe problem.

                          Man kann nicht alle Probleme lösen, aber wenigstens verursachen.

                          LenovoThinkCentre M900 Tiny | i5-T6500 | 16 GB | 256 SSD
                          iobroker auf Proxmox VM
                          Node.js: v22.18.0 - NPM: 10.9.3 - js-controller: 7.0.6 - admin: v7.7.2
                          FritzBox-7530TX hinter Glasfasermodem, WiFi mit Unifi

                          HomoranH 1 Antwort Letzte Antwort
                          0
                          • HomoranH Homoran

                            @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                            Die Debug Meldungen

                            und die Einstellungen?

                            @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                            Poll address 1000 - 10 registers

                            mag das Gerät das?

                            S Offline
                            S Offline
                            Snopy_16
                            schrieb am zuletzt editiert von
                            #50

                            @homoran Ich habe das selbe Problem, was muss ich da jetzt ändern?

                            Man kann nicht alle Probleme lösen, aber wenigstens verursachen.

                            LenovoThinkCentre M900 Tiny | i5-T6500 | 16 GB | 256 SSD
                            iobroker auf Proxmox VM
                            Node.js: v22.18.0 - NPM: 10.9.3 - js-controller: 7.0.6 - admin: v7.7.2
                            FritzBox-7530TX hinter Glasfasermodem, WiFi mit Unifi

                            1 Antwort Letzte Antwort
                            0
                            • S Snopy_16

                              @ck_coke Wie hast du das gelöst. Ich habe das selbe problem.

                              HomoranH Nicht stören
                              HomoranH Nicht stören
                              Homoran
                              Global Moderator Administrators
                              schrieb am zuletzt editiert von
                              #51

                              @snopy_16 sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                              Wie hast du das gelöst. Ich habe das selbe problem.

                              @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                              Mit maximal 7 Registern (Float) funktioniert es.

                              Screenshot_20250930-190412_Firefox.jpg

                              kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                              der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                              S 1 Antwort Letzte Antwort
                              0
                              • HomoranH Homoran

                                @snopy_16 sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                                Wie hast du das gelöst. Ich habe das selbe problem.

                                @ck_coke sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                                Mit maximal 7 Registern (Float) funktioniert es.

                                Screenshot_20250930-190412_Firefox.jpg

                                S Offline
                                S Offline
                                Snopy_16
                                schrieb am zuletzt editiert von
                                #52

                                @homoran Sorry, funktioniert nicht

                                
                                modbus.0
                                2025-09-30 19:09:05.662	info	Disconnected from slave 192.168.178.8
                                
                                modbus.0
                                2025-09-30 19:09:05.560	warn	[DevID_1] Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                
                                modbus.0
                                2025-09-30 19:08:55.206	warn	[DevID_1] Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                
                                modbus.0
                                2025-09-30 19:08:44.851	warn	[DevID_1] Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                
                                modbus.0
                                2025-09-30 19:08:34.495	warn	[DevID_1] Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                
                                modbus.0
                                2025-09-30 19:08:24.140	warn	[DevID_1] Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                
                                modbus.0
                                2025-09-30 19:08:13.785	warn	[DevID_1] Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                
                                modbus.0
                                2025-09-30 19:08:13.484	info	Connected to slave 192.168.178.8
                                

                                Alle Register, die ich probiert habe funktionieren einwandfrei, nur Register 1008, 1012 machen diese Zicken. Es sind alles Temperaturen. Habe auch schon Holding Register probiert.

                                Man kann nicht alle Probleme lösen, aber wenigstens verursachen.

                                LenovoThinkCentre M900 Tiny | i5-T6500 | 16 GB | 256 SSD
                                iobroker auf Proxmox VM
                                Node.js: v22.18.0 - NPM: 10.9.3 - js-controller: 7.0.6 - admin: v7.7.2
                                FritzBox-7530TX hinter Glasfasermodem, WiFi mit Unifi

                                WinniW HomoranH 2 Antworten Letzte Antwort
                                0
                                • S Snopy_16

                                  @homoran Sorry, funktioniert nicht

                                  
                                  modbus.0
                                  2025-09-30 19:09:05.662	info	Disconnected from slave 192.168.178.8
                                  
                                  modbus.0
                                  2025-09-30 19:09:05.560	warn	[DevID_1] Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                  
                                  modbus.0
                                  2025-09-30 19:08:55.206	warn	[DevID_1] Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                  
                                  modbus.0
                                  2025-09-30 19:08:44.851	warn	[DevID_1] Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                  
                                  modbus.0
                                  2025-09-30 19:08:34.495	warn	[DevID_1] Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                  
                                  modbus.0
                                  2025-09-30 19:08:24.140	warn	[DevID_1] Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                  
                                  modbus.0
                                  2025-09-30 19:08:13.785	warn	[DevID_1] Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                  
                                  modbus.0
                                  2025-09-30 19:08:13.484	info	Connected to slave 192.168.178.8
                                  

                                  Alle Register, die ich probiert habe funktionieren einwandfrei, nur Register 1008, 1012 machen diese Zicken. Es sind alles Temperaturen. Habe auch schon Holding Register probiert.

                                  WinniW Offline
                                  WinniW Offline
                                  Winni
                                  schrieb am zuletzt editiert von Winni
                                  #53

                                  @snopy_16 Wie sind denn deine Einstellungen für diese Register?
                                  Bei mir funktionieren sie problemlos mit diesen Einstellungen:
                                  2025_09_30_19.29.47.jpg

                                  Edit: habe eine IDM AERO ALM 6-15

                                  Es gibt nicht Gutes. Außer man tut es. Erich Kästner

                                  S 1 Antwort Letzte Antwort
                                  0
                                  • S Snopy_16

                                    @homoran Sorry, funktioniert nicht

                                    
                                    modbus.0
                                    2025-09-30 19:09:05.662	info	Disconnected from slave 192.168.178.8
                                    
                                    modbus.0
                                    2025-09-30 19:09:05.560	warn	[DevID_1] Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    
                                    modbus.0
                                    2025-09-30 19:08:55.206	warn	[DevID_1] Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    
                                    modbus.0
                                    2025-09-30 19:08:44.851	warn	[DevID_1] Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    
                                    modbus.0
                                    2025-09-30 19:08:34.495	warn	[DevID_1] Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    
                                    modbus.0
                                    2025-09-30 19:08:24.140	warn	[DevID_1] Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    
                                    modbus.0
                                    2025-09-30 19:08:13.785	warn	[DevID_1] Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    
                                    modbus.0
                                    2025-09-30 19:08:13.484	info	Connected to slave 192.168.178.8
                                    

                                    Alle Register, die ich probiert habe funktionieren einwandfrei, nur Register 1008, 1012 machen diese Zicken. Es sind alles Temperaturen. Habe auch schon Holding Register probiert.

                                    HomoranH Nicht stören
                                    HomoranH Nicht stören
                                    Homoran
                                    Global Moderator Administrators
                                    schrieb am zuletzt editiert von Homoran
                                    #54

                                    @snopy_16 sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                                    Sorry, funktioniert nicht

                                    dann hast du nicht

                                    @snopy_16 sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                                    das selbe Problem,

                                    bitte debug-log vom Instanzenstart

                                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                    S 1 Antwort Letzte Antwort
                                    0
                                    • WinniW Winni

                                      @snopy_16 Wie sind denn deine Einstellungen für diese Register?
                                      Bei mir funktionieren sie problemlos mit diesen Einstellungen:
                                      2025_09_30_19.29.47.jpg

                                      Edit: habe eine IDM AERO ALM 6-15

                                      S Offline
                                      S Offline
                                      Snopy_16
                                      schrieb am zuletzt editiert von
                                      #55

                                      @winni Ich habe dieselbe Aero Alm 6-15. Und auch dieselbe Einstellung.
                                      Nur die Register 1008 und 1012 funktionieren nicht. Alle weiteren Temperaturabfragen funktionieren tadellos.

                                      Man kann nicht alle Probleme lösen, aber wenigstens verursachen.

                                      LenovoThinkCentre M900 Tiny | i5-T6500 | 16 GB | 256 SSD
                                      iobroker auf Proxmox VM
                                      Node.js: v22.18.0 - NPM: 10.9.3 - js-controller: 7.0.6 - admin: v7.7.2
                                      FritzBox-7530TX hinter Glasfasermodem, WiFi mit Unifi

                                      WinniW 1 Antwort Letzte Antwort
                                      0
                                      • HomoranH Homoran

                                        @snopy_16 sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                                        Sorry, funktioniert nicht

                                        dann hast du nicht

                                        @snopy_16 sagte in IDM Luftwärmepumpe per Modbus anbinden klappt nicht :( Tipps?:

                                        das selbe Problem,

                                        bitte debug-log vom Instanzenstart

                                        S Offline
                                        S Offline
                                        Snopy_16
                                        schrieb am zuletzt editiert von
                                        #56

                                        @homoran Hier mein Log

                                        
                                        modbus.0
                                        2025-09-30 19:43:12.703	info	Disconnected from slave 192.168.178.8
                                        
                                        modbus.0
                                        2025-09-30 19:43:12.602	warn	[DevID_1] Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                        
                                        modbus.0
                                        2025-09-30 19:43:02.248	warn	[DevID_1] Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                        
                                        modbus.0
                                        2025-09-30 19:42:51.893	warn	[DevID_1] Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                        
                                        modbus.0
                                        2025-09-30 19:42:41.539	warn	[DevID_1] Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                        
                                        modbus.0
                                        2025-09-30 19:42:31.182	warn	[DevID_1] Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                        
                                        modbus.0
                                        2025-09-30 19:42:20.827	warn	[DevID_1] Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                        
                                        modbus.0
                                        2025-09-30 19:42:20.526	info	Connected to slave 192.168.178.8
                                        

                                        Man kann nicht alle Probleme lösen, aber wenigstens verursachen.

                                        LenovoThinkCentre M900 Tiny | i5-T6500 | 16 GB | 256 SSD
                                        iobroker auf Proxmox VM
                                        Node.js: v22.18.0 - NPM: 10.9.3 - js-controller: 7.0.6 - admin: v7.7.2
                                        FritzBox-7530TX hinter Glasfasermodem, WiFi mit Unifi

                                        HomoranH 1 Antwort Letzte Antwort
                                        0
                                        • S Snopy_16

                                          @winni Ich habe dieselbe Aero Alm 6-15. Und auch dieselbe Einstellung.
                                          Nur die Register 1008 und 1012 funktionieren nicht. Alle weiteren Temperaturabfragen funktionieren tadellos.

                                          WinniW Offline
                                          WinniW Offline
                                          Winni
                                          schrieb am zuletzt editiert von
                                          #57

                                          @snopy_16 probier mal den Datenabfrageintervall zu verlängern. Sonst fällt mir leider nichts ein.

                                          Es gibt nicht Gutes. Außer man tut es. Erich Kästner

                                          HomoranH 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          544

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe