  5. JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.1k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.8k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.1k

JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.

Scheduled Pinned Locked Moved Einbindung von Geräten
110 Posts 8 Posters 10.9k Views 7 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • Elektroniker86E Offline
    Elektroniker86E Offline
    Elektroniker86
    wrote on last edited by
    #21

    Ich komme nicht weiter, hier die logs:

    
    modbus.5
    2025-03-06 16:23:30.302	info	Disconnected from slave 192.168.1.123
    
    modbus.5
    2025-03-06 16:23:29.302	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
    
    modbus.5
    2025-03-06 16:23:29.302	error	Client in error state.
    
    modbus.5
    2025-03-06 16:23:29.302	error	Request timed out.
    
    modbus.5
    2025-03-06 16:23:29.301	warn	Error: undefined
    
    modbus.5
    2025-03-06 16:23:23.250	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
    
    modbus.5
    2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
    
    modbus.5
    2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
    
    wendy2702W HomoranH 2 Replies Last reply
    0
    • Elektroniker86E Elektroniker86

      Ich komme nicht weiter, hier die logs:

      
      modbus.5
      2025-03-06 16:23:30.302	info	Disconnected from slave 192.168.1.123
      
      modbus.5
      2025-03-06 16:23:29.302	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
      
      modbus.5
      2025-03-06 16:23:29.302	error	Client in error state.
      
      modbus.5
      2025-03-06 16:23:29.302	error	Request timed out.
      
      modbus.5
      2025-03-06 16:23:29.301	warn	Error: undefined
      
      modbus.5
      2025-03-06 16:23:23.250	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
      
      modbus.5
      2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
      
      modbus.5
      2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
      
      wendy2702W Offline
      wendy2702W Offline
      wendy2702
      wrote on last edited by
      #22

      @elektroniker86 Da müssen wir auch die Einstellungen zu sehen.

      Bitte keine Fragen per PN, die gehören ins Forum!

      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

      Elektroniker86E 1 Reply Last reply
      0
      • Elektroniker86E Elektroniker86

        Ich komme nicht weiter, hier die logs:

        
        modbus.5
        2025-03-06 16:23:30.302	info	Disconnected from slave 192.168.1.123
        
        modbus.5
        2025-03-06 16:23:29.302	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
        
        modbus.5
        2025-03-06 16:23:29.302	error	Client in error state.
        
        modbus.5
        2025-03-06 16:23:29.302	error	Request timed out.
        
        modbus.5
        2025-03-06 16:23:29.301	warn	Error: undefined
        
        modbus.5
        2025-03-06 16:23:23.250	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
        
        modbus.5
        2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
        
        modbus.5
        2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
        
        HomoranH Do not disturb
        HomoranH Do not disturb
        Homoran
        Global Moderator Administrators
        wrote on last edited by
        #23

        @elektroniker86 stell mal bitte auf debug

        Ansonsten

        @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

        "ReadInputRegisters: Invalid FC 32"

        @wendy2702 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

        Function Code 03H wären zum Lesen Holding Register

        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

        1 Reply Last reply
        0
        • wendy2702W wendy2702

          @elektroniker86 Da müssen wir auch die Einstellungen zu sehen.

          Elektroniker86E Offline
          Elektroniker86E Offline
          Elektroniker86
          wrote on last edited by
          #24

          @wendy2702

          Moment da hat sich was überschnitten Das ist jetzt aktuell.

          Screenshot 2025-03-06 170913.png Screenshot 2025-03-06 170846.png Screenshot 2025-03-06 170813.png

          
          modbus.5
          2025-03-06 17:10:00.444	info	Disconnected from slave 192.168.1.123
          
          modbus.5
          2025-03-06 17:09:59.443	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
          
          modbus.5
          2025-03-06 17:09:59.443	error	Client in error state.
          
          modbus.5
          2025-03-06 17:09:59.443	error	Request timed out.
          
          modbus.5
          2025-03-06 17:09:59.442	warn	Error: undefined
          
          modbus.5
          2025-03-06 17:09:53.391	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
          
          modbus.5
          2025-03-06 17:09:53.390	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
          
          modbus.5
          2025-03-06 17:09:53.390	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
          
          modbus.5
          2025-03-06 17:09:48.990	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
          
          modbus.5
          2025-03-06 17:09:43.902	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
          
          modbus.5
          2025-03-06 17:09:43.788	info	Connected to slave 192.168.1.123
          
          modbus.5
          2025-03-06 17:09:43.634	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
          
          modbus.5
          2025-03-06 17:09:39.643	info	terminating
          
          modbus.5
          2025-03-06 17:09:39.159	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
          
          modbus.5
          2025-03-06 17:09:39.158	info	terminating
          
          modbus.5
          2025-03-06 17:09:39.142	info	Got terminate signal TERMINATE_YOURSELF
          
          
          HomoranH 1 Reply Last reply
          0
          • Elektroniker86E Elektroniker86

            @wendy2702

            Moment da hat sich was überschnitten Das ist jetzt aktuell.

            Screenshot 2025-03-06 170913.png Screenshot 2025-03-06 170846.png Screenshot 2025-03-06 170813.png

            
            modbus.5
            2025-03-06 17:10:00.444	info	Disconnected from slave 192.168.1.123
            
            modbus.5
            2025-03-06 17:09:59.443	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
            
            modbus.5
            2025-03-06 17:09:59.443	error	Client in error state.
            
            modbus.5
            2025-03-06 17:09:59.443	error	Request timed out.
            
            modbus.5
            2025-03-06 17:09:59.442	warn	Error: undefined
            
            modbus.5
            2025-03-06 17:09:53.391	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
            
            modbus.5
            2025-03-06 17:09:53.390	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
            
            modbus.5
            2025-03-06 17:09:53.390	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
            
            modbus.5
            2025-03-06 17:09:48.990	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
            
            modbus.5
            2025-03-06 17:09:43.902	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
            
            modbus.5
            2025-03-06 17:09:43.788	info	Connected to slave 192.168.1.123
            
            modbus.5
            2025-03-06 17:09:43.634	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
            
            modbus.5
            2025-03-06 17:09:39.643	info	terminating
            
            modbus.5
            2025-03-06 17:09:39.159	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
            
            modbus.5
            2025-03-06 17:09:39.158	info	terminating
            
            modbus.5
            2025-03-06 17:09:39.142	info	Got terminate signal TERMINATE_YOURSELF
            
            
            HomoranH Do not disturb
            HomoranH Do not disturb
            Homoran
            Global Moderator Administrators
            wrote on last edited by
            #25

            @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

            Das ist jetzt aktuell.

            bitte erst einmal nur ein Register abrufen.
            Input <-> Holding gilt immer noch

            kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

            der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

            Elektroniker86E 1 Reply Last reply
            0
            • HomoranH Homoran

              @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

              Das ist jetzt aktuell.

              bitte erst einmal nur ein Register abrufen.
              Input <-> Holding gilt immer noch

              Elektroniker86E Offline
              Elektroniker86E Offline
              Elektroniker86
              wrote on last edited by
              #26

              @homoran

              So, ein Register und Debug:

              
              modbus.5
              2025-03-06 17:14:13.892	info	Disconnected from slave 192.168.1.123
              
              modbus.5
              2025-03-06 17:14:13.892	debug	Closing client on purpose.
              
              modbus.5
              2025-03-06 17:14:12.892	debug	Cleaning up request fifo.
              
              modbus.5
              2025-03-06 17:14:12.892	debug	Clearing timeout of the current request.
              
              modbus.5
              2025-03-06 17:14:12.892	debug	Socket closed with error
              
              modbus.5
              2025-03-06 17:14:12.891	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
              
              modbus.5
              2025-03-06 17:14:12.891	error	Client in error state.
              
              modbus.5
              2025-03-06 17:14:12.891	error	Request timed out.
              
              modbus.5
              2025-03-06 17:14:12.891	warn	Error: undefined
              
              modbus.5
              2025-03-06 17:14:07.890	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
              
              modbus.5
              2025-03-06 17:14:07.889	debug	[DevID_1] Poll start ---------------------
              
              modbus.5
              2025-03-06 17:14:06.839	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
              
              modbus.5
              2025-03-06 17:14:04.028	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
              
              modbus.5
              2025-03-06 17:14:04.028	debug	[DevID_1] Poll start ---------------------
              
              modbus.5
              2025-03-06 17:14:02.975	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
              
              modbus.5
              2025-03-06 17:13:57.793	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
              
              modbus.5
              2025-03-06 17:13:57.776	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
              
              modbus.5
              2025-03-06 17:13:57.776	debug	Initialization of scale factors done!
              
              modbus.5
              2025-03-06 17:13:57.775	debug	[DevID_1] Poll start ---------------------
              
              modbus.5
              2025-03-06 17:13:57.775	info	Connected to slave 192.168.1.123
              
              modbus.5
              2025-03-06 17:13:57.721	debug	Remove old object modbus.5.inputRegisters.4774_soc
              
              modbus.5
              2025-03-06 17:13:57.677	debug	Initialize Objects for holdingRegs: []
              
              modbus.5
              2025-03-06 17:13:57.677	debug	Add inputRegisters.4752_Total_Battery_Voltage: {"_id":"inputRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"mV"},"native":{"regType":"inputRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1}}
              
              modbus.5
              2025-03-06 17:13:57.677	debug	Initialize Objects for inputRegs: [{"_address":4752,"deviceId":1,"name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":4752,"id":"inputRegisters.4752_Total_Battery_Voltage"}]
              
              modbus.5
              2025-03-06 17:13:57.676	debug	Initialize Objects for coils: []
              
              modbus.5
              2025-03-06 17:13:57.676	debug	Initialize Objects for disInputs: []
              
              modbus.5
              2025-03-06 17:13:57.621	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
              
              modbus.5
              2025-03-06 17:13:57.502	debug	Plugin sentry Initialize Plugin (enabled=true)
              
              modbus.5
              2025-03-06 17:13:57.487	debug	States connected to redis: 0.0.0.0:9000
              
              modbus.5
              2025-03-06 17:13:57.433	debug	States create User PubSub Client
              
              modbus.5
              2025-03-06 17:13:57.433	debug	States create System PubSub Client
              
              modbus.5
              2025-03-06 17:13:57.424	debug	Redis States: Use Redis connection: 0.0.0.0:9000
              
              modbus.5
              2025-03-06 17:13:57.406	debug	Objects connected to redis: 0.0.0.0:9001
              
              modbus.5
              2025-03-06 17:13:57.405	debug	Objects client initialize lua scripts
              
              modbus.5
              2025-03-06 17:13:57.376	debug	Objects create User PubSub Client
              
              modbus.5
              2025-03-06 17:13:57.376	debug	Objects create System PubSub Client
              
              modbus.5
              2025-03-06 17:13:57.375	debug	Objects client ready ... initialize now
              
              modbus.5
              2025-03-06 17:13:57.358	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
              
              modbus.5
              2025-03-06 17:13:53.655	info	terminating
              
              modbus.5
              2025-03-06 17:13:53.169	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
              
              modbus.5
              2025-03-06 17:13:53.169	debug	Plugin sentry destroyed
              
              modbus.5
              2025-03-06 17:13:53.169	info	terminating
              
              modbus.5
              2025-03-06 17:13:53.154	debug	Closing client on purpose.
              
              modbus.5
              2025-03-06 17:13:53.154	info	Got terminate signal TERMINATE_YOURSELF
              
              HomoranH 1 Reply Last reply
              0
              • Elektroniker86E Elektroniker86

                @homoran

                So, ein Register und Debug:

                
                modbus.5
                2025-03-06 17:14:13.892	info	Disconnected from slave 192.168.1.123
                
                modbus.5
                2025-03-06 17:14:13.892	debug	Closing client on purpose.
                
                modbus.5
                2025-03-06 17:14:12.892	debug	Cleaning up request fifo.
                
                modbus.5
                2025-03-06 17:14:12.892	debug	Clearing timeout of the current request.
                
                modbus.5
                2025-03-06 17:14:12.892	debug	Socket closed with error
                
                modbus.5
                2025-03-06 17:14:12.891	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                
                modbus.5
                2025-03-06 17:14:12.891	error	Client in error state.
                
                modbus.5
                2025-03-06 17:14:12.891	error	Request timed out.
                
                modbus.5
                2025-03-06 17:14:12.891	warn	Error: undefined
                
                modbus.5
                2025-03-06 17:14:07.890	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
                
                modbus.5
                2025-03-06 17:14:07.889	debug	[DevID_1] Poll start ---------------------
                
                modbus.5
                2025-03-06 17:14:06.839	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
                
                modbus.5
                2025-03-06 17:14:04.028	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
                
                modbus.5
                2025-03-06 17:14:04.028	debug	[DevID_1] Poll start ---------------------
                
                modbus.5
                2025-03-06 17:14:02.975	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                
                modbus.5
                2025-03-06 17:13:57.793	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                
                modbus.5
                2025-03-06 17:13:57.776	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
                
                modbus.5
                2025-03-06 17:13:57.776	debug	Initialization of scale factors done!
                
                modbus.5
                2025-03-06 17:13:57.775	debug	[DevID_1] Poll start ---------------------
                
                modbus.5
                2025-03-06 17:13:57.775	info	Connected to slave 192.168.1.123
                
                modbus.5
                2025-03-06 17:13:57.721	debug	Remove old object modbus.5.inputRegisters.4774_soc
                
                modbus.5
                2025-03-06 17:13:57.677	debug	Initialize Objects for holdingRegs: []
                
                modbus.5
                2025-03-06 17:13:57.677	debug	Add inputRegisters.4752_Total_Battery_Voltage: {"_id":"inputRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"mV"},"native":{"regType":"inputRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1}}
                
                modbus.5
                2025-03-06 17:13:57.677	debug	Initialize Objects for inputRegs: [{"_address":4752,"deviceId":1,"name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":4752,"id":"inputRegisters.4752_Total_Battery_Voltage"}]
                
                modbus.5
                2025-03-06 17:13:57.676	debug	Initialize Objects for coils: []
                
                modbus.5
                2025-03-06 17:13:57.676	debug	Initialize Objects for disInputs: []
                
                modbus.5
                2025-03-06 17:13:57.621	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                
                modbus.5
                2025-03-06 17:13:57.502	debug	Plugin sentry Initialize Plugin (enabled=true)
                
                modbus.5
                2025-03-06 17:13:57.487	debug	States connected to redis: 0.0.0.0:9000
                
                modbus.5
                2025-03-06 17:13:57.433	debug	States create User PubSub Client
                
                modbus.5
                2025-03-06 17:13:57.433	debug	States create System PubSub Client
                
                modbus.5
                2025-03-06 17:13:57.424	debug	Redis States: Use Redis connection: 0.0.0.0:9000
                
                modbus.5
                2025-03-06 17:13:57.406	debug	Objects connected to redis: 0.0.0.0:9001
                
                modbus.5
                2025-03-06 17:13:57.405	debug	Objects client initialize lua scripts
                
                modbus.5
                2025-03-06 17:13:57.376	debug	Objects create User PubSub Client
                
                modbus.5
                2025-03-06 17:13:57.376	debug	Objects create System PubSub Client
                
                modbus.5
                2025-03-06 17:13:57.375	debug	Objects client ready ... initialize now
                
                modbus.5
                2025-03-06 17:13:57.358	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
                
                modbus.5
                2025-03-06 17:13:53.655	info	terminating
                
                modbus.5
                2025-03-06 17:13:53.169	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                
                modbus.5
                2025-03-06 17:13:53.169	debug	Plugin sentry destroyed
                
                modbus.5
                2025-03-06 17:13:53.169	info	terminating
                
                modbus.5
                2025-03-06 17:13:53.154	debug	Closing client on purpose.
                
                modbus.5
                2025-03-06 17:13:53.154	info	Got terminate signal TERMINATE_YOURSELF
                
                HomoranH Do not disturb
                HomoranH Do not disturb
                Homoran
                Global Moderator Administrators
                wrote on last edited by
                #27

                @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                Add inputRegisters

                bitte Holdingregister nehmen

                kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                wendy2702W Elektroniker86E 2 Replies Last reply
                0
                • HomoranH Homoran

                  @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                  Add inputRegisters

                  bitte Holdingregister nehmen

                  wendy2702W Offline
                  wendy2702W Offline
                  wendy2702
                  wrote on last edited by
                  #28

                  @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                  @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                  Add inputRegisters

                  bitte Holdingregister nehmen

                  Und besser beim Port 502 bleiben.

                  @Elektroniker86 : gibt es bei dem Konverter noch ein erweitertes Menu oder kann man da wo TCP Server steht was anderes auswählen?

                  Bitte keine Fragen per PN, die gehören ins Forum!

                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                  Elektroniker86E 1 Reply Last reply
                  0
                  • HomoranH Homoran

                    @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                    Add inputRegisters

                    bitte Holdingregister nehmen

                    Elektroniker86E Offline
                    Elektroniker86E Offline
                    Elektroniker86
                    wrote on last edited by
                    #29

                    @homoran

                    Ich habe jetzt das Register beim Reiter Holding eingetragen. und bei eingang rausgelöscht. Hoffe das ist richtig so?

                    modbus.5
                    2025-03-06 17:28:01.562	info	Disconnected from slave 192.168.1.123
                    
                    modbus.5
                    2025-03-06 17:28:01.562	debug	Closing client on purpose.
                    
                    modbus.5
                    2025-03-06 17:28:00.563	debug	Cleaning up request fifo.
                    
                    modbus.5
                    2025-03-06 17:28:00.563	debug	Clearing timeout of the current request.
                    
                    modbus.5
                    2025-03-06 17:28:00.563	debug	Socket closed with error
                    
                    modbus.5
                    2025-03-06 17:28:00.562	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                    
                    modbus.5
                    2025-03-06 17:28:00.562	error	Client in error state.
                    
                    modbus.5
                    2025-03-06 17:28:00.562	error	Request timed out.
                    
                    modbus.5
                    2025-03-06 17:28:00.561	warn	Error: undefined
                    
                    modbus.5
                    2025-03-06 17:27:55.560	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                    
                    modbus.5
                    2025-03-06 17:27:55.560	debug	[DevID_1] Poll start ---------------------
                    
                    modbus.5
                    2025-03-06 17:27:54.510	warn	[DevID_1] Poll error count: 2 code: "ReadHoldingRegisters: Invalid FC 32"
                    
                    modbus.5
                    2025-03-06 17:27:54.428	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                    
                    modbus.5
                    2025-03-06 17:27:54.427	debug	[DevID_1] Poll start ---------------------
                    
                    modbus.5
                    2025-03-06 17:27:53.377	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                    
                    modbus.5
                    2025-03-06 17:27:48.324	warn	Error in handler for 3: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                    
                    modbus.5
                    2025-03-06 17:27:48.178	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                    
                    modbus.5
                    2025-03-06 17:27:48.178	debug	Initialization of scale factors done!
                    
                    modbus.5
                    2025-03-06 17:27:48.177	debug	[DevID_1] Poll start ---------------------
                    
                    modbus.5
                    2025-03-06 17:27:48.177	info	Connected to slave 192.168.1.123
                    
                    modbus.5
                    2025-03-06 17:27:48.083	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                    
                    modbus.5
                    2025-03-06 17:27:48.083	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                    
                    modbus.5
                    2025-03-06 17:27:48.083	debug	Initialize Objects for inputRegs: []
                    
                    modbus.5
                    2025-03-06 17:27:48.083	debug	Initialize Objects for coils: []
                    
                    modbus.5
                    2025-03-06 17:27:48.083	debug	Initialize Objects for disInputs: []
                    
                    modbus.5
                    2025-03-06 17:27:48.025	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                    
                    modbus.5
                    2025-03-06 17:27:47.911	debug	Plugin sentry Initialize Plugin (enabled=true)
                    
                    modbus.5
                    2025-03-06 17:27:47.897	debug	States connected to redis: 0.0.0.0:9000
                    
                    modbus.5
                    2025-03-06 17:27:47.844	debug	States create User PubSub Client
                    
                    modbus.5
                    2025-03-06 17:27:47.843	debug	States create System PubSub Client
                    
                    modbus.5
                    2025-03-06 17:27:47.795	debug	Redis States: Use Redis connection: 0.0.0.0:9000
                    
                    modbus.5
                    2025-03-06 17:27:47.770	debug	Objects connected to redis: 0.0.0.0:9001
                    
                    modbus.5
                    2025-03-06 17:27:47.768	debug	Objects client initialize lua scripts
                    
                    modbus.5
                    2025-03-06 17:27:47.736	debug	Objects create User PubSub Client
                    
                    modbus.5
                    2025-03-06 17:27:47.736	debug	Objects create System PubSub Client
                    
                    modbus.5
                    2025-03-06 17:27:47.736	debug	Objects client ready ... initialize now
                    
                    modbus.5
                    2025-03-06 17:27:47.719	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
                    
                    modbus.5
                    2025-03-06 17:27:43.961	info	terminating
                    
                    modbus.5
                    2025-03-06 17:27:43.476	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                    
                    modbus.5
                    2025-03-06 17:27:43.476	debug	Plugin sentry destroyed
                    
                    modbus.5
                    2025-03-06 17:27:43.476	info	terminating
                    
                    modbus.5
                    2025-03-06 17:27:43.460	debug	Closing client on purpose.
                    
                    modbus.5
                    2025-03-06 17:27:43.459	info	Got terminate signal TERMINATE_YOURSELF
                    
                    wendy2702W 1 Reply Last reply
                    0
                    • wendy2702W wendy2702

                      @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                      @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                      Add inputRegisters

                      bitte Holdingregister nehmen

                      Und besser beim Port 502 bleiben.

                      @Elektroniker86 : gibt es bei dem Konverter noch ein erweitertes Menu oder kann man da wo TCP Server steht was anderes auswählen?

                      Elektroniker86E Offline
                      Elektroniker86E Offline
                      Elektroniker86
                      wrote on last edited by Elektroniker86
                      #30

                      @wendy2702

                      Screenshot 2025-03-06 173115.png

                      Port stell ich um und probiere nochmal aus.

                      Mehr gibts nicht einzustellen bei dem adapter

                      1 Reply Last reply
                      0
                      • Elektroniker86E Elektroniker86

                        @homoran

                        Ich habe jetzt das Register beim Reiter Holding eingetragen. und bei eingang rausgelöscht. Hoffe das ist richtig so?

                        modbus.5
                        2025-03-06 17:28:01.562	info	Disconnected from slave 192.168.1.123
                        
                        modbus.5
                        2025-03-06 17:28:01.562	debug	Closing client on purpose.
                        
                        modbus.5
                        2025-03-06 17:28:00.563	debug	Cleaning up request fifo.
                        
                        modbus.5
                        2025-03-06 17:28:00.563	debug	Clearing timeout of the current request.
                        
                        modbus.5
                        2025-03-06 17:28:00.563	debug	Socket closed with error
                        
                        modbus.5
                        2025-03-06 17:28:00.562	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                        
                        modbus.5
                        2025-03-06 17:28:00.562	error	Client in error state.
                        
                        modbus.5
                        2025-03-06 17:28:00.562	error	Request timed out.
                        
                        modbus.5
                        2025-03-06 17:28:00.561	warn	Error: undefined
                        
                        modbus.5
                        2025-03-06 17:27:55.560	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                        
                        modbus.5
                        2025-03-06 17:27:55.560	debug	[DevID_1] Poll start ---------------------
                        
                        modbus.5
                        2025-03-06 17:27:54.510	warn	[DevID_1] Poll error count: 2 code: "ReadHoldingRegisters: Invalid FC 32"
                        
                        modbus.5
                        2025-03-06 17:27:54.428	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                        
                        modbus.5
                        2025-03-06 17:27:54.427	debug	[DevID_1] Poll start ---------------------
                        
                        modbus.5
                        2025-03-06 17:27:53.377	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                        
                        modbus.5
                        2025-03-06 17:27:48.324	warn	Error in handler for 3: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                        
                        modbus.5
                        2025-03-06 17:27:48.178	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                        
                        modbus.5
                        2025-03-06 17:27:48.178	debug	Initialization of scale factors done!
                        
                        modbus.5
                        2025-03-06 17:27:48.177	debug	[DevID_1] Poll start ---------------------
                        
                        modbus.5
                        2025-03-06 17:27:48.177	info	Connected to slave 192.168.1.123
                        
                        modbus.5
                        2025-03-06 17:27:48.083	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                        
                        modbus.5
                        2025-03-06 17:27:48.083	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                        
                        modbus.5
                        2025-03-06 17:27:48.083	debug	Initialize Objects for inputRegs: []
                        
                        modbus.5
                        2025-03-06 17:27:48.083	debug	Initialize Objects for coils: []
                        
                        modbus.5
                        2025-03-06 17:27:48.083	debug	Initialize Objects for disInputs: []
                        
                        modbus.5
                        2025-03-06 17:27:48.025	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                        
                        modbus.5
                        2025-03-06 17:27:47.911	debug	Plugin sentry Initialize Plugin (enabled=true)
                        
                        modbus.5
                        2025-03-06 17:27:47.897	debug	States connected to redis: 0.0.0.0:9000
                        
                        modbus.5
                        2025-03-06 17:27:47.844	debug	States create User PubSub Client
                        
                        modbus.5
                        2025-03-06 17:27:47.843	debug	States create System PubSub Client
                        
                        modbus.5
                        2025-03-06 17:27:47.795	debug	Redis States: Use Redis connection: 0.0.0.0:9000
                        
                        modbus.5
                        2025-03-06 17:27:47.770	debug	Objects connected to redis: 0.0.0.0:9001
                        
                        modbus.5
                        2025-03-06 17:27:47.768	debug	Objects client initialize lua scripts
                        
                        modbus.5
                        2025-03-06 17:27:47.736	debug	Objects create User PubSub Client
                        
                        modbus.5
                        2025-03-06 17:27:47.736	debug	Objects create System PubSub Client
                        
                        modbus.5
                        2025-03-06 17:27:47.736	debug	Objects client ready ... initialize now
                        
                        modbus.5
                        2025-03-06 17:27:47.719	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
                        
                        modbus.5
                        2025-03-06 17:27:43.961	info	terminating
                        
                        modbus.5
                        2025-03-06 17:27:43.476	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                        
                        modbus.5
                        2025-03-06 17:27:43.476	debug	Plugin sentry destroyed
                        
                        modbus.5
                        2025-03-06 17:27:43.476	info	terminating
                        
                        modbus.5
                        2025-03-06 17:27:43.460	debug	Closing client on purpose.
                        
                        modbus.5
                        2025-03-06 17:27:43.459	info	Got terminate signal TERMINATE_YOURSELF
                        
                        wendy2702W Offline
                        wendy2702W Offline
                        wendy2702
                        wrote on last edited by
                        #31

                        @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                        ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds

                        Das sieht für mich so aus als wenn die Antwort zu lang ist und der reservierte Buffer nicht reicht.

                        In deinem Link aus dem JSON steht für länge 0, hilft uns aber auch nicht weiter.

                        Software zum testen:
                        ModbusPoll
                        GmodbusMaster
                        RMMS (Radzio Modbus Master Simulator

                        Bitte keine Fragen per PN, die gehören ins Forum!

                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                        HomoranH Elektroniker86E 2 Replies Last reply
                        0
                        • wendy2702W wendy2702

                          @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                          ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds

                          Das sieht für mich so aus als wenn die Antwort zu lang ist und der reservierte Buffer nicht reicht.

                          In deinem Link aus dem JSON steht für länge 0, hilft uns aber auch nicht weiter.

                          Software zum testen:
                          ModbusPoll
                          GmodbusMaster
                          RMMS (Radzio Modbus Master Simulator

                          HomoranH Do not disturb
                          HomoranH Do not disturb
                          Homoran
                          Global Moderator Administrators
                          wrote on last edited by
                          #32

                          @wendy2702 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                          und der reservierte Buffer nicht reicht.

                          @Elektroniker86
                          auch wenn (oder gerade weil) du nur ein Register haben willst, stell mal in den Grundeinstellungen die Anzahl gepollte Register auf einen niedrigen Wert.

                          @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                          beim Reiter Holding eingetragen

                          und Abfrage angehakt?

                          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                          Elektroniker86E 2 Replies Last reply
                          0
                          • HomoranH Homoran

                            @wendy2702 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                            und der reservierte Buffer nicht reicht.

                            @Elektroniker86
                            auch wenn (oder gerade weil) du nur ein Register haben willst, stell mal in den Grundeinstellungen die Anzahl gepollte Register auf einen niedrigen Wert.

                            @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                            beim Reiter Holding eingetragen

                            und Abfrage angehakt?

                            Elektroniker86E Offline
                            Elektroniker86E Offline
                            Elektroniker86
                            wrote on last edited by Elektroniker86
                            #33

                            @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                            und Abfrage angehakt?

                            Ja, habe ich angehakt:

                            Screenshot 2025-03-07 095828.png

                            @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                            auch wenn (oder gerade weil) du nur ein Register haben willst, stell mal in den Grundeinstellungen die Anzahl gepollte Register auf einen niedrigen Wert.

                            Probiere ich aus.

                            1 Reply Last reply
                            0
                            • HomoranH Homoran

                              @wendy2702 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                              und der reservierte Buffer nicht reicht.

                              @Elektroniker86
                              auch wenn (oder gerade weil) du nur ein Register haben willst, stell mal in den Grundeinstellungen die Anzahl gepollte Register auf einen niedrigen Wert.

                              @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                              beim Reiter Holding eingetragen

                              und Abfrage angehakt?

                              Elektroniker86E Offline
                              Elektroniker86E Offline
                              Elektroniker86
                              wrote on last edited by
                              #34

                              @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                              auch wenn (oder gerade weil) du nur ein Register haben willst, stell mal in den Grundeinstellungen die Anzahl gepollte Register auf einen niedrigen Wert.

                              Habe ich auch getestet habe die Werte auf die Hälfte eingestellt.

                              Screenshot 2025-03-07 100309.png

                              
                              modbus.5
                              2025-03-07 10:01:01.501	debug	Closing client on purpose.
                              
                              modbus.5
                              2025-03-07 10:01:00.499	debug	Cleaning up request fifo.
                              
                              modbus.5
                              2025-03-07 10:01:00.499	debug	Clearing timeout of the current request.
                              
                              modbus.5
                              2025-03-07 10:01:00.499	debug	Socket closed with error
                              
                              modbus.5
                              2025-03-07 10:01:00.491	info	Disconnected from slave 192.168.1.146
                              
                              modbus.5
                              2025-03-07 10:01:00.491	debug	Closing client on purpose.
                              
                              modbus.5
                              2025-03-07 10:01:00.441	warn	[DevID_1] Poll error count: 6 code: "App Timeout"
                              
                              modbus.5
                              2025-03-07 10:00:55.314	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                              
                              modbus.5
                              2025-03-07 10:00:55.241	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                              
                              modbus.5
                              2025-03-07 10:00:55.241	debug	[DevID_1] Poll start ---------------------
                              
                              modbus.5
                              2025-03-07 10:00:54.189	warn	[DevID_1] Poll error count: 5 code: "App Timeout"
                              
                              modbus.5
                              2025-03-07 10:00:49.053	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                              
                              modbus.5
                              2025-03-07 10:00:48.988	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                              
                              modbus.5
                              2025-03-07 10:00:48.988	debug	[DevID_1] Poll start ---------------------
                              
                              modbus.5
                              2025-03-07 10:00:47.938	warn	[DevID_1] Poll error count: 4 code: "App Timeout"
                              
                              modbus.5
                              2025-03-07 10:00:42.840	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                              
                              modbus.5
                              2025-03-07 10:00:42.737	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                              
                              modbus.5
                              2025-03-07 10:00:42.737	debug	[DevID_1] Poll start ---------------------
                              
                              modbus.5
                              2025-03-07 10:00:41.686	warn	[DevID_1] Poll error count: 3 code: "App Timeout"
                              
                              modbus.5
                              2025-03-07 10:00:36.577	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                              
                              modbus.5
                              2025-03-07 10:00:36.485	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                              
                              modbus.5
                              2025-03-07 10:00:36.485	debug	[DevID_1] Poll start ---------------------
                              
                              modbus.5
                              2025-03-07 10:00:35.434	warn	[DevID_1] Poll error count: 2 code: "App Timeout"
                              
                              modbus.5
                              2025-03-07 10:00:30.313	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                              
                              modbus.5
                              2025-03-07 10:00:30.233	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                              
                              modbus.5
                              2025-03-07 10:00:30.233	debug	[DevID_1] Poll start ---------------------
                              
                              modbus.5
                              2025-03-07 10:00:29.182	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                              
                              modbus.5
                              2025-03-07 10:00:24.100	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                              
                              modbus.5
                              2025-03-07 10:00:23.981	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                              
                              modbus.5
                              2025-03-07 10:00:23.981	debug	Initialization of scale factors done!
                              
                              modbus.5
                              2025-03-07 10:00:23.981	debug	[DevID_1] Poll start ---------------------
                              
                              modbus.5
                              2025-03-07 10:00:23.980	info	Connected to slave 192.168.1.146
                              
                              modbus.5
                              2025-03-07 10:00:23.886	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                              
                              modbus.5
                              2025-03-07 10:00:23.885	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                              
                              modbus.5
                              2025-03-07 10:00:23.885	debug	Initialize Objects for inputRegs: []
                              
                              modbus.5
                              2025-03-07 10:00:23.885	debug	Initialize Objects for coils: []
                              
                              modbus.5
                              2025-03-07 10:00:23.885	debug	Initialize Objects for disInputs: []
                              
                              modbus.5
                              2025-03-07 10:00:23.828	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                              
                              modbus.5
                              2025-03-07 10:00:23.711	debug	Plugin sentry Initialize Plugin (enabled=true)
                              
                              modbus.5
                              2025-03-07 10:00:19.818	info	terminating
                              
                              modbus.5
                              2025-03-07 10:00:19.332	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                              
                              modbus.5
                              2025-03-07 10:00:19.332	debug	Plugin sentry destroyed
                              
                              modbus.5
                              2025-03-07 10:00:19.332	info	terminating
                              
                              modbus.5
                              2025-03-07 10:00:19.317	debug	Closing client on purpose.
                              
                              modbus.5
                              2025-03-07 10:00:19.316	info	Got terminate signal TERMINATE_YOURSELF
                              
                              modbus.5
                              2025-03-07 10:00:12.413	debug	Closing client on purpose.
                              
                              modbus.5
                              2025-03-07 10:00:11.412	debug	Cleaning up request fifo.
                              
                              modbus.5
                              2025-03-07 10:00:11.412	debug	Clearing timeout of the current request.
                              
                              modbus.5
                              2025-03-07 10:00:11.412	debug	Socket closed with error
                              
                              modbus.5
                              2025-03-07 10:00:11.404	info	Disconnected from slave 192.168.1.146
                              
                              modbus.5
                              2025-03-07 10:00:11.404	debug	Closing client on purpose.
                              
                              modbus.5
                              2025-03-07 10:00:11.353	warn	[DevID_1] Poll error count: 10 code: "App Timeout"
                              
                              modbus.5
                              2025-03-07 10:00:06.266	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                              
                              modbus.5
                              2025-03-07 10:00:06.153	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                              
                              modbus.5
                              2025-03-07 10:00:06.153	debug	[DevID_1] Poll start ---------------------
                              
                              modbus.5
                              2025-03-07 10:00:06.153	info	Connected to slave 192.168.1.146
                              
                              modbus.5
                              2025-03-07 09:59:07.158	debug	Closing client on purpose.
                              
                              modbus.5
                              2025-03-07 09:59:06.158	debug	Cleaning up request fifo.
                              
                              modbus.5
                              2025-03-07 09:59:06.158	debug	Clearing timeout of the current request.
                              
                              modbus.5
                              2025-03-07 09:59:06.158	debug	Socket closed with error
                              
                              modbus.5
                              2025-03-07 09:59:06.151	info	Disconnected from slave 192.168.1.146
                              
                              modbus.5
                              2025-03-07 09:59:06.151	debug	Closing client on purpose.
                              
                              modbus.5
                              2025-03-07 09:59:06.100	warn	[DevID_1] Poll error count: 9 code: "App Timeout"
                              
                              modbus.5
                              2025-03-07 09:59:00.997	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                              
                              modbus.5
                              2025-03-07 09:59:00.901	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                              
                              modbus.5
                              2025-03-07 09:59:00.900	debug	[DevID_1] Poll start ---------------------
                              
                              modbus.5
                              2025-03-07 09:59:00.900	info	Connected to slave 192.168.1.146
                              
                              HomoranH 1 Reply Last reply
                              0
                              • Elektroniker86E Elektroniker86

                                @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                auch wenn (oder gerade weil) du nur ein Register haben willst, stell mal in den Grundeinstellungen die Anzahl gepollte Register auf einen niedrigen Wert.

                                Habe ich auch getestet habe die Werte auf die Hälfte eingestellt.

                                Screenshot 2025-03-07 100309.png

                                
                                modbus.5
                                2025-03-07 10:01:01.501	debug	Closing client on purpose.
                                
                                modbus.5
                                2025-03-07 10:01:00.499	debug	Cleaning up request fifo.
                                
                                modbus.5
                                2025-03-07 10:01:00.499	debug	Clearing timeout of the current request.
                                
                                modbus.5
                                2025-03-07 10:01:00.499	debug	Socket closed with error
                                
                                modbus.5
                                2025-03-07 10:01:00.491	info	Disconnected from slave 192.168.1.146
                                
                                modbus.5
                                2025-03-07 10:01:00.491	debug	Closing client on purpose.
                                
                                modbus.5
                                2025-03-07 10:01:00.441	warn	[DevID_1] Poll error count: 6 code: "App Timeout"
                                
                                modbus.5
                                2025-03-07 10:00:55.314	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                
                                modbus.5
                                2025-03-07 10:00:55.241	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                
                                modbus.5
                                2025-03-07 10:00:55.241	debug	[DevID_1] Poll start ---------------------
                                
                                modbus.5
                                2025-03-07 10:00:54.189	warn	[DevID_1] Poll error count: 5 code: "App Timeout"
                                
                                modbus.5
                                2025-03-07 10:00:49.053	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                
                                modbus.5
                                2025-03-07 10:00:48.988	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                
                                modbus.5
                                2025-03-07 10:00:48.988	debug	[DevID_1] Poll start ---------------------
                                
                                modbus.5
                                2025-03-07 10:00:47.938	warn	[DevID_1] Poll error count: 4 code: "App Timeout"
                                
                                modbus.5
                                2025-03-07 10:00:42.840	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                
                                modbus.5
                                2025-03-07 10:00:42.737	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                
                                modbus.5
                                2025-03-07 10:00:42.737	debug	[DevID_1] Poll start ---------------------
                                
                                modbus.5
                                2025-03-07 10:00:41.686	warn	[DevID_1] Poll error count: 3 code: "App Timeout"
                                
                                modbus.5
                                2025-03-07 10:00:36.577	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                
                                modbus.5
                                2025-03-07 10:00:36.485	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                
                                modbus.5
                                2025-03-07 10:00:36.485	debug	[DevID_1] Poll start ---------------------
                                
                                modbus.5
                                2025-03-07 10:00:35.434	warn	[DevID_1] Poll error count: 2 code: "App Timeout"
                                
                                modbus.5
                                2025-03-07 10:00:30.313	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                
                                modbus.5
                                2025-03-07 10:00:30.233	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                
                                modbus.5
                                2025-03-07 10:00:30.233	debug	[DevID_1] Poll start ---------------------
                                
                                modbus.5
                                2025-03-07 10:00:29.182	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                                
                                modbus.5
                                2025-03-07 10:00:24.100	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                
                                modbus.5
                                2025-03-07 10:00:23.981	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                
                                modbus.5
                                2025-03-07 10:00:23.981	debug	Initialization of scale factors done!
                                
                                modbus.5
                                2025-03-07 10:00:23.981	debug	[DevID_1] Poll start ---------------------
                                
                                modbus.5
                                2025-03-07 10:00:23.980	info	Connected to slave 192.168.1.146
                                
                                modbus.5
                                2025-03-07 10:00:23.886	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                                
                                modbus.5
                                2025-03-07 10:00:23.885	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                                
                                modbus.5
                                2025-03-07 10:00:23.885	debug	Initialize Objects for inputRegs: []
                                
                                modbus.5
                                2025-03-07 10:00:23.885	debug	Initialize Objects for coils: []
                                
                                modbus.5
                                2025-03-07 10:00:23.885	debug	Initialize Objects for disInputs: []
                                
                                modbus.5
                                2025-03-07 10:00:23.828	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                                
                                modbus.5
                                2025-03-07 10:00:23.711	debug	Plugin sentry Initialize Plugin (enabled=true)
                                
                                modbus.5
                                2025-03-07 10:00:19.818	info	terminating
                                
                                modbus.5
                                2025-03-07 10:00:19.332	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                
                                modbus.5
                                2025-03-07 10:00:19.332	debug	Plugin sentry destroyed
                                
                                modbus.5
                                2025-03-07 10:00:19.332	info	terminating
                                
                                modbus.5
                                2025-03-07 10:00:19.317	debug	Closing client on purpose.
                                
                                modbus.5
                                2025-03-07 10:00:19.316	info	Got terminate signal TERMINATE_YOURSELF
                                
                                modbus.5
                                2025-03-07 10:00:12.413	debug	Closing client on purpose.
                                
                                modbus.5
                                2025-03-07 10:00:11.412	debug	Cleaning up request fifo.
                                
                                modbus.5
                                2025-03-07 10:00:11.412	debug	Clearing timeout of the current request.
                                
                                modbus.5
                                2025-03-07 10:00:11.412	debug	Socket closed with error
                                
                                modbus.5
                                2025-03-07 10:00:11.404	info	Disconnected from slave 192.168.1.146
                                
                                modbus.5
                                2025-03-07 10:00:11.404	debug	Closing client on purpose.
                                
                                modbus.5
                                2025-03-07 10:00:11.353	warn	[DevID_1] Poll error count: 10 code: "App Timeout"
                                
                                modbus.5
                                2025-03-07 10:00:06.266	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                
                                modbus.5
                                2025-03-07 10:00:06.153	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                
                                modbus.5
                                2025-03-07 10:00:06.153	debug	[DevID_1] Poll start ---------------------
                                
                                modbus.5
                                2025-03-07 10:00:06.153	info	Connected to slave 192.168.1.146
                                
                                modbus.5
                                2025-03-07 09:59:07.158	debug	Closing client on purpose.
                                
                                modbus.5
                                2025-03-07 09:59:06.158	debug	Cleaning up request fifo.
                                
                                modbus.5
                                2025-03-07 09:59:06.158	debug	Clearing timeout of the current request.
                                
                                modbus.5
                                2025-03-07 09:59:06.158	debug	Socket closed with error
                                
                                modbus.5
                                2025-03-07 09:59:06.151	info	Disconnected from slave 192.168.1.146
                                
                                modbus.5
                                2025-03-07 09:59:06.151	debug	Closing client on purpose.
                                
                                modbus.5
                                2025-03-07 09:59:06.100	warn	[DevID_1] Poll error count: 9 code: "App Timeout"
                                
                                modbus.5
                                2025-03-07 09:59:00.997	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                
                                modbus.5
                                2025-03-07 09:59:00.901	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                
                                modbus.5
                                2025-03-07 09:59:00.900	debug	[DevID_1] Poll start ---------------------
                                
                                modbus.5
                                2025-03-07 09:59:00.900	info	Connected to slave 192.168.1.146
                                
                                HomoranH Do not disturb
                                HomoranH Do not disturb
                                Homoran
                                Global Moderator Administrators
                                wrote on last edited by Homoran
                                #35

                                @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                auf die Hälfte eingestellt.

                                bitte auf 1 oder 2 stellen
                                es gibt Geräte die sich sonst aufhängen.

                                Muss nicht die Ursache sein, würde ich gerne ausschließen

                                @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4

                                wo steht der Parameter denn?

                                Hier
                                Screenshot_20250307-100722_Firefox.jpg
                                steht 0, nicht 4

                                kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                Elektroniker86E 2 Replies Last reply
                                0
                                • HomoranH Homoran

                                  @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                  auf die Hälfte eingestellt.

                                  bitte auf 1 oder 2 stellen
                                  es gibt Geräte die sich sonst aufhängen.

                                  Muss nicht die Ursache sein, würde ich gerne ausschließen

                                  @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                  Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4

                                  wo steht der Parameter denn?

                                  Hier
                                  Screenshot_20250307-100722_Firefox.jpg
                                  steht 0, nicht 4

                                  Elektroniker86E Offline
                                  Elektroniker86E Offline
                                  Elektroniker86
                                  wrote on last edited by
                                  #36

                                  @homoran

                                  Screenshot 2025-03-07 101501.png

                                  Screenshot 2025-03-07 101436.png

                                  modbus.5
                                  2025-03-07 10:16:18.537	debug	Closing client on purpose.
                                  
                                  modbus.5
                                  2025-03-07 10:16:17.536	debug	Cleaning up request fifo.
                                  
                                  modbus.5
                                  2025-03-07 10:16:17.536	debug	Clearing timeout of the current request.
                                  
                                  modbus.5
                                  2025-03-07 10:16:17.536	debug	Socket closed with error
                                  
                                  modbus.5
                                  2025-03-07 10:16:17.531	info	Disconnected from slave 192.168.1.146
                                  
                                  modbus.5
                                  2025-03-07 10:16:17.531	debug	Closing client on purpose.
                                  
                                  modbus.5
                                  2025-03-07 10:16:17.480	warn	[DevID_1] Poll error count: 6 code: "App Timeout"
                                  
                                  modbus.5
                                  2025-03-07 10:16:12.369	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                  
                                  modbus.5
                                  2025-03-07 10:16:12.279	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                  
                                  modbus.5
                                  2025-03-07 10:16:12.279	debug	[DevID_1] Poll start ---------------------
                                  
                                  modbus.5
                                  2025-03-07 10:16:11.228	warn	[DevID_1] Poll error count: 5 code: "App Timeout"
                                  
                                  modbus.5
                                  2025-03-07 10:16:06.105	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                  
                                  modbus.5
                                  2025-03-07 10:16:06.027	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                  
                                  modbus.5
                                  2025-03-07 10:16:06.027	debug	[DevID_1] Poll start ---------------------
                                  
                                  modbus.5
                                  2025-03-07 10:16:04.975	warn	[DevID_1] Poll error count: 4 code: "App Timeout"
                                  
                                  modbus.5
                                  2025-03-07 10:15:59.843	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                  
                                  modbus.5
                                  2025-03-07 10:15:59.775	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                  
                                  modbus.5
                                  2025-03-07 10:15:59.775	debug	[DevID_1] Poll start ---------------------
                                  
                                  modbus.5
                                  2025-03-07 10:15:58.724	warn	[DevID_1] Poll error count: 3 code: "App Timeout"
                                  
                                  modbus.5
                                  2025-03-07 10:15:53.629	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                  
                                  modbus.5
                                  2025-03-07 10:15:53.523	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                  
                                  modbus.5
                                  2025-03-07 10:15:53.523	debug	[DevID_1] Poll start ---------------------
                                  
                                  modbus.5
                                  2025-03-07 10:15:52.471	warn	[DevID_1] Poll error count: 2 code: "App Timeout"
                                  
                                  modbus.5
                                  2025-03-07 10:15:47.365	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                  
                                  modbus.5
                                  2025-03-07 10:15:47.270	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                  
                                  modbus.5
                                  2025-03-07 10:15:47.270	debug	[DevID_1] Poll start ---------------------
                                  
                                  modbus.5
                                  2025-03-07 10:15:46.219	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                                  
                                  modbus.5
                                  2025-03-07 10:15:41.103	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                  
                                  modbus.5
                                  2025-03-07 10:15:41.019	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                  
                                  modbus.5
                                  2025-03-07 10:15:41.019	debug	Initialization of scale factors done!
                                  
                                  modbus.5
                                  2025-03-07 10:15:41.018	debug	[DevID_1] Poll start ---------------------
                                  
                                  modbus.5
                                  2025-03-07 10:15:41.018	info	Connected to slave 192.168.1.146
                                  
                                  modbus.5
                                  2025-03-07 10:15:40.927	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":4,"factor":1,"poll":true}}
                                  
                                  modbus.5
                                  2025-03-07 10:15:40.927	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":4,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                                  
                                  modbus.5
                                  2025-03-07 10:15:40.927	debug	Initialize Objects for inputRegs: []
                                  
                                  modbus.5
                                  2025-03-07 10:15:40.927	debug	Initialize Objects for coils: []
                                  
                                  modbus.5
                                  2025-03-07 10:15:40.927	debug	Initialize Objects for disInputs: []
                                  
                                  modbus.5
                                  2025-03-07 10:15:40.874	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                                  
                                  modbus.5
                                  2025-03-07 10:15:40.764	debug	Plugin sentry Initialize Plugin (enabled=true)
                                  
                                  modbus.5
                                  2025-03-07 10:15:36.922	info	terminating
                                  
                                  modbus.5
                                  2025-03-07 10:15:36.437	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                  
                                  modbus.5
                                  2025-03-07 10:15:36.437	debug	Plugin sentry destroyed
                                  
                                  modbus.5
                                  2025-03-07 10:15:36.437	info	terminating
                                  
                                  modbus.5
                                  2025-03-07 10:15:36.422	debug	Closing client on purpose.
                                  
                                  modbus.5
                                  2025-03-07 10:15:36.422	info	Got terminate signal TERMINATE_YOURSELF
                                  

                                  Sehr komisch alles, habe mit Modbus noch nie Probleme gehabt. Habe alle SMA Wechselrichter drin plus Energiezähler von EASTRoN und Heidelberg Ladestation die funktionieren super.

                                  HomoranH 1 Reply Last reply
                                  0
                                  • Elektroniker86E Offline
                                    Elektroniker86E Offline
                                    Elektroniker86
                                    wrote on last edited by
                                    #37

                                    Ich habe zum Test jetzt auch mal noch ein ELFIN RS485 Adapter probiert aber auch hier das selbe

                                    1 Reply Last reply
                                    0
                                    • Elektroniker86E Elektroniker86

                                      @homoran

                                      Screenshot 2025-03-07 101501.png

                                      Screenshot 2025-03-07 101436.png

                                      modbus.5
                                      2025-03-07 10:16:18.537	debug	Closing client on purpose.
                                      
                                      modbus.5
                                      2025-03-07 10:16:17.536	debug	Cleaning up request fifo.
                                      
                                      modbus.5
                                      2025-03-07 10:16:17.536	debug	Clearing timeout of the current request.
                                      
                                      modbus.5
                                      2025-03-07 10:16:17.536	debug	Socket closed with error
                                      
                                      modbus.5
                                      2025-03-07 10:16:17.531	info	Disconnected from slave 192.168.1.146
                                      
                                      modbus.5
                                      2025-03-07 10:16:17.531	debug	Closing client on purpose.
                                      
                                      modbus.5
                                      2025-03-07 10:16:17.480	warn	[DevID_1] Poll error count: 6 code: "App Timeout"
                                      
                                      modbus.5
                                      2025-03-07 10:16:12.369	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                      
                                      modbus.5
                                      2025-03-07 10:16:12.279	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                      
                                      modbus.5
                                      2025-03-07 10:16:12.279	debug	[DevID_1] Poll start ---------------------
                                      
                                      modbus.5
                                      2025-03-07 10:16:11.228	warn	[DevID_1] Poll error count: 5 code: "App Timeout"
                                      
                                      modbus.5
                                      2025-03-07 10:16:06.105	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                      
                                      modbus.5
                                      2025-03-07 10:16:06.027	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                      
                                      modbus.5
                                      2025-03-07 10:16:06.027	debug	[DevID_1] Poll start ---------------------
                                      
                                      modbus.5
                                      2025-03-07 10:16:04.975	warn	[DevID_1] Poll error count: 4 code: "App Timeout"
                                      
                                      modbus.5
                                      2025-03-07 10:15:59.843	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                      
                                      modbus.5
                                      2025-03-07 10:15:59.775	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                      
                                      modbus.5
                                      2025-03-07 10:15:59.775	debug	[DevID_1] Poll start ---------------------
                                      
                                      modbus.5
                                      2025-03-07 10:15:58.724	warn	[DevID_1] Poll error count: 3 code: "App Timeout"
                                      
                                      modbus.5
                                      2025-03-07 10:15:53.629	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                      
                                      modbus.5
                                      2025-03-07 10:15:53.523	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                      
                                      modbus.5
                                      2025-03-07 10:15:53.523	debug	[DevID_1] Poll start ---------------------
                                      
                                      modbus.5
                                      2025-03-07 10:15:52.471	warn	[DevID_1] Poll error count: 2 code: "App Timeout"
                                      
                                      modbus.5
                                      2025-03-07 10:15:47.365	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                      
                                      modbus.5
                                      2025-03-07 10:15:47.270	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                      
                                      modbus.5
                                      2025-03-07 10:15:47.270	debug	[DevID_1] Poll start ---------------------
                                      
                                      modbus.5
                                      2025-03-07 10:15:46.219	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                                      
                                      modbus.5
                                      2025-03-07 10:15:41.103	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                      
                                      modbus.5
                                      2025-03-07 10:15:41.019	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                      
                                      modbus.5
                                      2025-03-07 10:15:41.019	debug	Initialization of scale factors done!
                                      
                                      modbus.5
                                      2025-03-07 10:15:41.018	debug	[DevID_1] Poll start ---------------------
                                      
                                      modbus.5
                                      2025-03-07 10:15:41.018	info	Connected to slave 192.168.1.146
                                      
                                      modbus.5
                                      2025-03-07 10:15:40.927	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":4,"factor":1,"poll":true}}
                                      
                                      modbus.5
                                      2025-03-07 10:15:40.927	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":4,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                                      
                                      modbus.5
                                      2025-03-07 10:15:40.927	debug	Initialize Objects for inputRegs: []
                                      
                                      modbus.5
                                      2025-03-07 10:15:40.927	debug	Initialize Objects for coils: []
                                      
                                      modbus.5
                                      2025-03-07 10:15:40.927	debug	Initialize Objects for disInputs: []
                                      
                                      modbus.5
                                      2025-03-07 10:15:40.874	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                                      
                                      modbus.5
                                      2025-03-07 10:15:40.764	debug	Plugin sentry Initialize Plugin (enabled=true)
                                      
                                      modbus.5
                                      2025-03-07 10:15:36.922	info	terminating
                                      
                                      modbus.5
                                      2025-03-07 10:15:36.437	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                      
                                      modbus.5
                                      2025-03-07 10:15:36.437	debug	Plugin sentry destroyed
                                      
                                      modbus.5
                                      2025-03-07 10:15:36.437	info	terminating
                                      
                                      modbus.5
                                      2025-03-07 10:15:36.422	debug	Closing client on purpose.
                                      
                                      modbus.5
                                      2025-03-07 10:15:36.422	info	Got terminate signal TERMINATE_YOURSELF
                                      

                                      Sehr komisch alles, habe mit Modbus noch nie Probleme gehabt. Habe alle SMA Wechselrichter drin plus Energiezähler von EASTRoN und Heidelberg Ladestation die funktionieren super.

                                      HomoranH Do not disturb
                                      HomoranH Do not disturb
                                      Homoran
                                      Global Moderator Administrators
                                      wrote on last edited by Homoran
                                      #38

                                      @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                                              2025-03-07 10:15:40.927	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":4,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]                                                                    
                                      

                                      wo kommt der offset 4 her?

                                      edit!
                                      hast du den in der Zwischenzeit eingestellt?
                                      Warum?

                                      Das ist im Moment der einzige Fehler

                                      kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                      der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                      1 Reply Last reply
                                      0
                                      • HomoranH Homoran

                                        @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                        auf die Hälfte eingestellt.

                                        bitte auf 1 oder 2 stellen
                                        es gibt Geräte die sich sonst aufhängen.

                                        Muss nicht die Ursache sein, würde ich gerne ausschließen

                                        @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                        Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4

                                        wo steht der Parameter denn?

                                        Hier
                                        Screenshot_20250307-100722_Firefox.jpg
                                        steht 0, nicht 4

                                        Elektroniker86E Offline
                                        Elektroniker86E Offline
                                        Elektroniker86
                                        wrote on last edited by
                                        #39

                                        @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                        Hier

                                        steht 0, nicht 4

                                        Ich habe es so verstanden das ich den so einstellen soll
                                        Sorry

                                        HomoranH 1 Reply Last reply
                                        0
                                        • Elektroniker86E Elektroniker86

                                          @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                          Hier

                                          steht 0, nicht 4

                                          Ich habe es so verstanden das ich den so einstellen soll
                                          Sorry

                                          HomoranH Do not disturb
                                          HomoranH Do not disturb
                                          Homoran
                                          Global Moderator Administrators
                                          wrote on last edited by Homoran
                                          #40

                                          @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                          das ich den so einstellen soll

                                          nein!

                                          @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                          2025-03-07 10:00:55.314 warn Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4

                                          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                          Elektroniker86E 1 Reply Last reply
                                          0
                                          Reply
                                          • Reply as topic
                                          Log in to reply
                                          • Oldest to Newest
                                          • Newest to Oldest
                                          • Most Votes


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          700

                                          Online

                                          32.4k

                                          Users

                                          81.4k

                                          Topics

                                          1.3m

                                          Posts
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Login

                                          • Don't have an account? Register

                                          • Login or register to search.
                                          • First post
                                            Last post
                                          0
                                          • Recent
                                          • Tags
                                          • Unread 0
                                          • Categories
                                          • Unreplied
                                          • Popular
                                          • GitHub
                                          • Docu
                                          • Hilfe