  3. Einsteigerfragen
  4. Einbindung von Geräten
  5. JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.
    2.8k
    4.8k
    4.1k
111 Beiträge 8 Kommentatoren 17.9k Aufrufe 5 Beobachtet
  • Elektroniker86E Elektroniker86
    Ich komme nicht weiter, hier die logs:
    modbus.5
    2025-03-06 16:23:30.302	info	Disconnected from slave 192.168.1.123
    modbus.5
    2025-03-06 16:23:29.302	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
    modbus.5
    2025-03-06 16:23:29.302	error	Client in error state.
    modbus.5
    2025-03-06 16:23:29.302	error	Request timed out.
    modbus.5
    2025-03-06 16:23:29.301	warn	Error: undefined
    modbus.5
    2025-03-06 16:23:23.250	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
    modbus.5
    2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
    modbus.5
    wendy2702W Offline
    wendy2702W Offline
    wendy2702
    #22
    @elektroniker86 Da müssen wir auch die Einstellungen zu sehen.
    Elektroniker86E 1 Antwort Letzte Antwort
      modbus.5
      modbus.5
      modbus.5
      modbus.5
      modbus.5
      modbus.5
      modbus.5
      modbus.5
      #23
      @elektroniker86 stell mal bitte auf debug
      Ansonsten
      @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:
      @wendy2702 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:
      Function Code 03H wären zum Lesen Holding Register
      • wendy2702W wendy2702
        Elektroniker86E Offline
        Elektroniker86
        #24
        @wendy2702
        Moment da hat sich was überschnitten Das ist jetzt aktuell.
        Screenshot 2025-03-06 170913.png Screenshot 2025-03-06 170846.png Screenshot 2025-03-06 170813.png
        modbus.5
        2025-03-06 17:10:00.444	info	Disconnected from slave 192.168.1.123
        modbus.5
        2025-03-06 17:09:59.443	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
        modbus.5
        2025-03-06 17:09:59.443	error	Client in error state.
        modbus.5
        2025-03-06 17:09:59.443	error	Request timed out.
        modbus.5
        2025-03-06 17:09:59.442	warn	Error: undefined
        modbus.5
        2025-03-06 17:09:53.391	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
        modbus.5
        2025-03-06 17:09:53.390	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
        modbus.5
        modbus.5
        2025-03-06 17:09:48.990	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
        modbus.5
        2025-03-06 17:09:43.902	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
        modbus.5
        2025-03-06 17:09:43.788	info	Connected to slave 192.168.1.123
        modbus.5
        2025-03-06 17:09:43.634	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
        modbus.5
        2025-03-06 17:09:39.643	info	terminating
        modbus.5
        2025-03-06 17:09:39.159	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
        modbus.5
        2025-03-06 17:09:39.158	info	terminating
        modbus.5
        2025-03-06 17:09:39.142	info	Got terminate signal TERMINATE_YOURSELF
          @wendy2702
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          modbus.5
          #25
          bitte erst einmal nur ein Register abrufen.
          Input <-> Holding gilt immer noch
            Elektroniker86
            #26
            So, ein Register und Debug:
            modbus.5
            2025-03-06 17:14:13.892	info	Disconnected from slave 192.168.1.123
            modbus.5
            2025-03-06 17:14:13.892	debug	Closing client on purpose.
            modbus.5
            2025-03-06 17:14:12.892	debug	Cleaning up request fifo.
            modbus.5
            2025-03-06 17:14:12.892	debug	Clearing timeout of the current request.
            modbus.5
            2025-03-06 17:14:12.892	debug	Socket closed with error
            modbus.5
            2025-03-06 17:14:12.891	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
            modbus.5
            2025-03-06 17:14:12.891	error	Client in error state.
            modbus.5
            2025-03-06 17:14:12.891	error	Request timed out.
            modbus.5
            2025-03-06 17:14:12.891	warn	Error: undefined
            modbus.5
            2025-03-06 17:14:07.890	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
            modbus.5
            2025-03-06 17:14:07.889	debug	[DevID_1] Poll start ---------------------
            modbus.5
            2025-03-06 17:14:06.839	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
            modbus.5
            2025-03-06 17:14:04.028	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
            modbus.5
            2025-03-06 17:14:04.028	debug	[DevID_1] Poll start ---------------------
            modbus.5
            2025-03-06 17:14:02.975	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
            modbus.5
            2025-03-06 17:13:57.793	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
            modbus.5
            2025-03-06 17:13:57.776	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
            modbus.5
            2025-03-06 17:13:57.776	debug	Initialization of scale factors done!
            modbus.5
            2025-03-06 17:13:57.775	debug	[DevID_1] Poll start ---------------------
            modbus.5
            2025-03-06 17:13:57.775	info	Connected to slave 192.168.1.123
            modbus.5
            2025-03-06 17:13:57.721	debug	Remove old object modbus.5.inputRegisters.4774_soc
            modbus.5
            2025-03-06 17:13:57.677	debug	Initialize Objects for holdingRegs: []
            modbus.5
            2025-03-06 17:13:57.677	debug	Add inputRegisters.4752_Total_Battery_Voltage: {"_id":"inputRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"mV"},"native":{"regType":"inputRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1}}
            modbus.5
            2025-03-06 17:13:57.677	debug	Initialize Objects for inputRegs: [{"_address":4752,"deviceId":1,"name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":4752,"id":"inputRegisters.4752_Total_Battery_Voltage"}]
            modbus.5
            2025-03-06 17:13:57.676	debug	Initialize Objects for coils: []
            modbus.5
            2025-03-06 17:13:57.676	debug	Initialize Objects for disInputs: []
            modbus.5
            2025-03-06 17:13:57.621	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
            modbus.5
            2025-03-06 17:13:57.502	debug	Plugin sentry Initialize Plugin (enabled=true)
            modbus.5
            2025-03-06 17:13:57.487	debug	States connected to redis: 0.0.0.0:9000
            modbus.5
            2025-03-06 17:13:57.433	debug	States create User PubSub Client
            modbus.5
            2025-03-06 17:13:57.433	debug	States create System PubSub Client
            modbus.5
            2025-03-06 17:13:57.424	debug	Redis States: Use Redis connection: 0.0.0.0:9000
            modbus.5
            2025-03-06 17:13:57.406	debug	Objects connected to redis: 0.0.0.0:9001
            modbus.5
            2025-03-06 17:13:57.405	debug	Objects client initialize lua scripts
            modbus.5
            2025-03-06 17:13:57.376	debug	Objects create User PubSub Client
            modbus.5
            2025-03-06 17:13:57.376	debug	Objects create System PubSub Client
            modbus.5
            2025-03-06 17:13:57.375	debug	Objects client ready ... initialize now
            modbus.5
            2025-03-06 17:13:57.358	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
            modbus.5
            2025-03-06 17:13:53.655	info	terminating
            modbus.5
            2025-03-06 17:13:53.169	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
            modbus.5
            2025-03-06 17:13:53.169	debug	Plugin sentry destroyed
            modbus.5
            2025-03-06 17:13:53.169	info	terminating
            modbus.5
            2025-03-06 17:13:53.154	debug	Closing client on purpose.
            modbus.5
            2025-03-06 17:13:53.154	info	Got terminate signal TERMINATE_YOURSELF
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              modbus.5
              #27
              Add inputRegisters
              bitte Holdingregister nehmen
              wendy2702W Elektroniker86E 2 Antworten Letzte Antwort
                Add inputRegisters
                wendy2702W Offline
                wendy2702W Offline
                wendy2702
                #28
                @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:
                Add inputRegisters
                Und besser beim Port 502 bleiben.
                @Elektroniker86 : gibt es bei dem Konverter noch ein erweitertes Menu oder kann man da wo TCP Server steht was anderes auswählen?
                  Add inputRegisters
                  Elektroniker86
                  #29
                  Ich habe jetzt das Register beim Reiter Holding eingetragen. und bei eingang rausgelöscht. Hoffe das ist richtig so?
                  modbus.5
                  2025-03-06 17:28:01.562	info	Disconnected from slave 192.168.1.123
                  modbus.5
                  2025-03-06 17:28:01.562	debug	Closing client on purpose.
                  modbus.5
                  2025-03-06 17:28:00.563	debug	Cleaning up request fifo.
                  modbus.5
                  2025-03-06 17:28:00.563	debug	Clearing timeout of the current request.
                  modbus.5
                  2025-03-06 17:28:00.563	debug	Socket closed with error
                  modbus.5
                  2025-03-06 17:28:00.562	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                  modbus.5
                  2025-03-06 17:28:00.562	error	Client in error state.
                  modbus.5
                  2025-03-06 17:28:00.562	error	Request timed out.
                  modbus.5
                  2025-03-06 17:28:00.561	warn	Error: undefined
                  modbus.5
                  2025-03-06 17:27:55.560	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                  modbus.5
                  2025-03-06 17:27:55.560	debug	[DevID_1] Poll start ---------------------
                  modbus.5
                  2025-03-06 17:27:54.510	warn	[DevID_1] Poll error count: 2 code: "ReadHoldingRegisters: Invalid FC 32"
                  modbus.5
                  2025-03-06 17:27:54.428	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                  modbus.5
                  2025-03-06 17:27:54.427	debug	[DevID_1] Poll start ---------------------
                  modbus.5
                  2025-03-06 17:27:53.377	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                  modbus.5
                  2025-03-06 17:27:48.324	warn	Error in handler for 3: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                  modbus.5
                  2025-03-06 17:27:48.178	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                  modbus.5
                  2025-03-06 17:27:48.178	debug	Initialization of scale factors done!
                  modbus.5
                  2025-03-06 17:27:48.177	debug	[DevID_1] Poll start ---------------------
                  modbus.5
                  2025-03-06 17:27:48.177	info	Connected to slave 192.168.1.123
                  modbus.5
                  2025-03-06 17:27:48.083	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  modbus.5
                  2025-03-06 17:27:48.083	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                  modbus.5
                  2025-03-06 17:27:48.083	debug	Initialize Objects for inputRegs: []
                  modbus.5
                  2025-03-06 17:27:48.083	debug	Initialize Objects for coils: []
                  modbus.5
                  2025-03-06 17:27:48.083	debug	Initialize Objects for disInputs: []
                  modbus.5
                  2025-03-06 17:27:48.025	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                  modbus.5
                  2025-03-06 17:27:47.911	debug	Plugin sentry Initialize Plugin (enabled=true)
                  modbus.5
                  2025-03-06 17:27:47.897	debug	States connected to redis: 0.0.0.0:9000
                  modbus.5
                  2025-03-06 17:27:47.844	debug	States create User PubSub Client
                  modbus.5
                  2025-03-06 17:27:47.843	debug	States create System PubSub Client
                  modbus.5
                  2025-03-06 17:27:47.795	debug	Redis States: Use Redis connection: 0.0.0.0:9000
                  modbus.5
                  2025-03-06 17:27:47.770	debug	Objects connected to redis: 0.0.0.0:9001
                  modbus.5
                  2025-03-06 17:27:47.768	debug	Objects client initialize lua scripts
                  modbus.5
                  2025-03-06 17:27:47.736	debug	Objects create User PubSub Client
                  modbus.5
                  2025-03-06 17:27:47.736	debug	Objects create System PubSub Client
                  modbus.5
                  2025-03-06 17:27:47.736	debug	Objects client ready ... initialize now
                  modbus.5
                  2025-03-06 17:27:47.719	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
                  modbus.5
                  2025-03-06 17:27:43.961	info	terminating
                  modbus.5
                  2025-03-06 17:27:43.476	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                  modbus.5
                  2025-03-06 17:27:43.476	debug	Plugin sentry destroyed
                  modbus.5
                  2025-03-06 17:27:43.476	info	terminating
                  modbus.5
                  2025-03-06 17:27:43.460	debug	Closing client on purpose.
                  modbus.5
                  2025-03-06 17:27:43.459	info	Got terminate signal TERMINATE_YOURSELF
                    Add inputRegisters
                    Elektroniker86
                    schrieb am zuletzt editiert von Elektroniker86
                    #30
                    @wendy2702
                    Port stell ich um und probiere nochmal aus.
                    Mehr gibts nicht einzustellen bei dem adapter
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      modbus.5
                      wendy2702W Offline
                      wendy2702W Offline
                      wendy2702
                      #31
                      Das sieht für mich so aus als wenn die Antwort zu lang ist und der reservierte Buffer nicht reicht.
                      In deinem Link aus dem JSON steht für länge 0, hilft uns aber auch nicht weiter.
                      Software zum testen:
                      ModbusPoll
                      GmodbusMaster
                      RMMS (Radzio Modbus Master Simulator
                      HomoranH Elektroniker86E 2 Antworten Letzte Antwort
                        ModbusPoll
                        GmodbusMaster
                        #32
                        @Elektroniker86
                        auch wenn (oder gerade weil) du nur ein Register haben willst, stell mal in den Grundeinstellungen die Anzahl gepollte Register auf einen niedrigen Wert.
                        und Abfrage angehakt?
                          @Elektroniker86
                          Elektroniker86
                          #33
                          Ja, habe ich angehakt:
                          Probiere ich aus.
                            @Elektroniker86
                            Elektroniker86
                            #34
                            Habe ich auch getestet habe die Werte auf die Hälfte eingestellt.
                            modbus.5
                            2025-03-07 10:01:01.501	debug	Closing client on purpose.
                            modbus.5
                            2025-03-07 10:01:00.499	debug	Cleaning up request fifo.
                            modbus.5
                            2025-03-07 10:01:00.499	debug	Clearing timeout of the current request.
                            modbus.5
                            2025-03-07 10:01:00.499	debug	Socket closed with error
                            modbus.5
                            2025-03-07 10:01:00.491	info	Disconnected from slave 192.168.1.146
                            modbus.5
                            2025-03-07 10:01:00.491	debug	Closing client on purpose.
                            modbus.5
                            2025-03-07 10:01:00.441	warn	[DevID_1] Poll error count: 6 code: "App Timeout"
                            modbus.5
                            2025-03-07 10:00:55.314	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                            modbus.5
                            2025-03-07 10:00:55.241	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                            modbus.5
                            2025-03-07 10:00:55.241	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            2025-03-07 10:00:54.189	warn	[DevID_1] Poll error count: 5 code: "App Timeout"
                            modbus.5
                            2025-03-07 10:00:49.053	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                            modbus.5
                            2025-03-07 10:00:48.988	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                            modbus.5
                            2025-03-07 10:00:48.988	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            2025-03-07 10:00:47.938	warn	[DevID_1] Poll error count: 4 code: "App Timeout"
                            modbus.5
                            2025-03-07 10:00:42.840	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                            modbus.5
                            2025-03-07 10:00:42.737	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                            modbus.5
                            2025-03-07 10:00:42.737	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            2025-03-07 10:00:41.686	warn	[DevID_1] Poll error count: 3 code: "App Timeout"
                            modbus.5
                            2025-03-07 10:00:36.577	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                            modbus.5
                            2025-03-07 10:00:36.485	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                            modbus.5
                            2025-03-07 10:00:36.485	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            2025-03-07 10:00:35.434	warn	[DevID_1] Poll error count: 2 code: "App Timeout"
                            modbus.5
                            2025-03-07 10:00:30.313	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                            modbus.5
                            2025-03-07 10:00:30.233	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                            modbus.5
                            2025-03-07 10:00:30.233	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            2025-03-07 10:00:29.182	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                            modbus.5
                            2025-03-07 10:00:24.100	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                            modbus.5
                            2025-03-07 10:00:23.981	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                            modbus.5
                            2025-03-07 10:00:23.981	debug	Initialization of scale factors done!
                            modbus.5
                            2025-03-07 10:00:23.981	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            2025-03-07 10:00:23.980	info	Connected to slave 192.168.1.146
                            modbus.5
                            2025-03-07 10:00:23.886	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                            modbus.5
                            2025-03-07 10:00:23.885	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                            modbus.5
                            2025-03-07 10:00:23.885	debug	Initialize Objects for inputRegs: []
                            modbus.5
                            2025-03-07 10:00:23.885	debug	Initialize Objects for coils: []
                            modbus.5
                            2025-03-07 10:00:23.885	debug	Initialize Objects for disInputs: []
                            modbus.5
                            2025-03-07 10:00:23.828	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                            modbus.5
                            2025-03-07 10:00:23.711	debug	Plugin sentry Initialize Plugin (enabled=true)
                            modbus.5
                            2025-03-07 10:00:19.818	info	terminating
                            modbus.5
                            2025-03-07 10:00:19.332	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                            modbus.5
                            2025-03-07 10:00:19.332	debug	Plugin sentry destroyed
                            modbus.5
                            2025-03-07 10:00:19.332	info	terminating
                            modbus.5
                            2025-03-07 10:00:19.317	debug	Closing client on purpose.
                            modbus.5
                            2025-03-07 10:00:19.316	info	Got terminate signal TERMINATE_YOURSELF
                            modbus.5
                            2025-03-07 10:00:12.413	debug	Closing client on purpose.
                            modbus.5
                            2025-03-07 10:00:11.412	debug	Cleaning up request fifo.
                            modbus.5
                            2025-03-07 10:00:11.412	debug	Clearing timeout of the current request.
                            modbus.5
                            2025-03-07 10:00:11.412	debug	Socket closed with error
                            modbus.5
                            2025-03-07 10:00:11.404	info	Disconnected from slave 192.168.1.146
                            modbus.5
                            2025-03-07 10:00:11.404	debug	Closing client on purpose.
                            modbus.5
                            2025-03-07 10:00:11.353	warn	[DevID_1] Poll error count: 10 code: "App Timeout"
                            modbus.5
                            2025-03-07 10:00:06.266	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                            modbus.5
                            2025-03-07 10:00:06.153	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                            modbus.5
                            2025-03-07 10:00:06.153	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            2025-03-07 10:00:06.153	info	Connected to slave 192.168.1.146
                            modbus.5
                            2025-03-07 09:59:07.158	debug	Closing client on purpose.
                            modbus.5
                            2025-03-07 09:59:06.158	debug	Cleaning up request fifo.
                            modbus.5
                            2025-03-07 09:59:06.158	debug	Clearing timeout of the current request.
                            modbus.5
                            2025-03-07 09:59:06.158	debug	Socket closed with error
                            modbus.5
                            2025-03-07 09:59:06.151	info	Disconnected from slave 192.168.1.146
                            modbus.5
                            2025-03-07 09:59:06.151	debug	Closing client on purpose.
                            modbus.5
                            2025-03-07 09:59:06.100	warn	[DevID_1] Poll error count: 9 code: "App Timeout"
                            modbus.5
                            2025-03-07 09:59:00.997	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                            modbus.5
                            2025-03-07 09:59:00.901	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                            modbus.5
                            2025-03-07 09:59:00.900	debug	[DevID_1] Poll start ---------------------
                            modbus.5
                            2025-03-07 09:59:00.900	info	Connected to slave 192.168.1.146
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              modbus.5
                              #35
                              bitte auf 1 oder 2 stellen
                              es gibt Geräte die sich sonst aufhängen.
                              Muss nicht die Ursache sein, würde ich gerne ausschließen
                              wo steht der Parameter denn?
                              Hier
                              steht 0, nicht 4
                                Hier
                                steht 0, nicht 4
                                Elektroniker86
                                #36
                                modbus.5
                                2025-03-07 10:16:18.537	debug	Closing client on purpose.
                                modbus.5
                                2025-03-07 10:16:17.536	debug	Cleaning up request fifo.
                                modbus.5
                                2025-03-07 10:16:17.536	debug	Clearing timeout of the current request.
                                modbus.5
                                2025-03-07 10:16:17.536	debug	Socket closed with error
                                modbus.5
                                2025-03-07 10:16:17.531	info	Disconnected from slave 192.168.1.146
                                modbus.5
                                2025-03-07 10:16:17.531	debug	Closing client on purpose.
                                modbus.5
                                2025-03-07 10:16:17.480	warn	[DevID_1] Poll error count: 6 code: "App Timeout"
                                modbus.5
                                2025-03-07 10:16:12.369	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                modbus.5
                                2025-03-07 10:16:12.279	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                modbus.5
                                2025-03-07 10:16:12.279	debug	[DevID_1] Poll start ---------------------
                                modbus.5
                                2025-03-07 10:16:11.228	warn	[DevID_1] Poll error count: 5 code: "App Timeout"
                                modbus.5
                                2025-03-07 10:16:06.105	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                modbus.5
                                2025-03-07 10:16:06.027	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                modbus.5
                                2025-03-07 10:16:06.027	debug	[DevID_1] Poll start ---------------------
                                modbus.5
                                2025-03-07 10:16:04.975	warn	[DevID_1] Poll error count: 4 code: "App Timeout"
                                modbus.5
                                2025-03-07 10:15:59.843	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                modbus.5
                                2025-03-07 10:15:59.775	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                modbus.5
                                2025-03-07 10:15:59.775	debug	[DevID_1] Poll start ---------------------
                                modbus.5
                                2025-03-07 10:15:58.724	warn	[DevID_1] Poll error count: 3 code: "App Timeout"
                                modbus.5
                                2025-03-07 10:15:53.629	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                modbus.5
                                2025-03-07 10:15:53.523	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                modbus.5
                                2025-03-07 10:15:53.523	debug	[DevID_1] Poll start ---------------------
                                modbus.5
                                2025-03-07 10:15:52.471	warn	[DevID_1] Poll error count: 2 code: "App Timeout"
                                modbus.5
                                2025-03-07 10:15:47.365	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                modbus.5
                                2025-03-07 10:15:47.270	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                modbus.5
                                2025-03-07 10:15:47.270	debug	[DevID_1] Poll start ---------------------
                                modbus.5
                                2025-03-07 10:15:46.219	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                                modbus.5
                                2025-03-07 10:15:41.103	warn	Error in handler for 3: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 3. Received 4
                                modbus.5
                                2025-03-07 10:15:41.019	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                modbus.5
                                2025-03-07 10:15:41.019	debug	Initialization of scale factors done!
                                modbus.5
                                2025-03-07 10:15:41.018	debug	[DevID_1] Poll start ---------------------
                                modbus.5
                                2025-03-07 10:15:41.018	info	Connected to slave 192.168.1.146
                                modbus.5
                                2025-03-07 10:15:40.927	debug	Add holdingRegisters.4752_Total_Battery_Voltage: {"_id":"holdingRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mV"},"native":{"regType":"holdingRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":4,"factor":1,"poll":true}}
                                modbus.5
                                2025-03-07 10:15:40.927	debug	Initialize Objects for holdingRegs: [{"_address":"4752","name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":4,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":4752,"id":"holdingRegisters.4752_Total_Battery_Voltage"}]
                                modbus.5
                                2025-03-07 10:15:40.927	debug	Initialize Objects for inputRegs: []
                                modbus.5
                                2025-03-07 10:15:40.927	debug	Initialize Objects for coils: []
                                modbus.5
                                2025-03-07 10:15:40.927	debug	Initialize Objects for disInputs: []
                                modbus.5
                                2025-03-07 10:15:40.874	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                                modbus.5
                                2025-03-07 10:15:40.764	debug	Plugin sentry Initialize Plugin (enabled=true)
                                modbus.5
                                2025-03-07 10:15:36.922	info	terminating
                                modbus.5
                                2025-03-07 10:15:36.437	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                modbus.5
                                2025-03-07 10:15:36.437	debug	Plugin sentry destroyed
                                modbus.5
                                2025-03-07 10:15:36.437	info	terminating
                                modbus.5
                                2025-03-07 10:15:36.422	debug	Closing client on purpose.
                                modbus.5
                                2025-03-07 10:15:36.422	info	Got terminate signal TERMINATE_YOURSELF
                                Sehr komisch alles, habe mit Modbus noch nie Probleme gehabt. Habe alle SMA Wechselrichter drin plus Energiezähler von EASTRoN und Heidelberg Ladestation die funktionieren super.
                                • Elektroniker86E Offline
                                  Elektroniker86
                                  #37
                                  Ich habe zum Test jetzt auch mal noch ein ELFIN RS485 Adapter probiert aber auch hier das selbe
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    modbus.5
                                    #38
                                    wo kommt der offset 4 her?
                                    edit!
                                    hast du den in der Zwischenzeit eingestellt?
                                    Warum?
                                    Das ist im Moment der einzige Fehler
                                      Hier
                                      steht 0, nicht 4
                                      Elektroniker86
                                      #39
                                      Hier
                                      steht 0, nicht 4
                                      Ich habe es so verstanden das ich den so einstellen soll
                                      Sorry
                                        Hier
                                        steht 0, nicht 4
                                        Sorry
                                        #40
                                        nein!
                                          nein!
                                          Elektroniker86
                                          #41
                                          Ich habe den ZLAN wieder angeschlossen und offset auf 0
                                          modbus.5
                                          2025-03-07 10:47:53.458	info	Disconnected from slave 192.168.1.123
                                          modbus.5
                                          2025-03-07 10:47:53.458	debug	Closing client on purpose.
                                          modbus.5
                                          2025-03-07 10:47:52.457	debug	Cleaning up request fifo.
                                          modbus.5
                                          2025-03-07 10:47:52.457	debug	Clearing timeout of the current request.
                                          modbus.5
                                          2025-03-07 10:47:52.457	debug	Socket closed with error
                                          modbus.5
                                          2025-03-07 10:47:52.457	warn	[DevID_1] Poll error count: 7 code: {"err":"timeout","timeout":5000}
                                          modbus.5
                                          2025-03-07 10:47:52.456	error	Client in error state.
                                          modbus.5
                                          2025-03-07 10:47:52.456	error	Request timed out.
                                          modbus.5
                                          2025-03-07 10:47:52.456	warn	Error: undefined
                                          modbus.5
                                          2025-03-07 10:47:47.456	debug	[DevID_1/holdingRegs] Poll address 4752 - 2 registers
                                          modbus.5
                                          2025-03-07 10:47:47.456	debug	[DevID_1] Poll start ---------------------
                                          modbus.5
                                          2025-03-07 10:47:47.456	info	Connected to slave 192.168.1.123