  4. ModBus RTU auf ModBus TCP über DR302

NEWS

  • Neuer Blogbeitrag: Monatsrückblick - Dezember 2025 🎄
    BluefoxB
    Bluefox
    11
    1
    387

  • Weihnachtsangebot 2025! 🎄
    BluefoxB
    Bluefox
    24
    1
    1.6k

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    9.5k

ModBus RTU auf ModBus TCP über DR302

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
37 Beiträge 7 Kommentatoren 4.7k Aufrufe 6 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • wendy2702W Online
    wendy2702W Online
    wendy2702
    schrieb am zuletzt editiert von
    #3

    Adapter wird auch erst grün wenn mindestes 1 register eingetragen und ausgelesen werden kann.

    Bitte keine Fragen per PN, die gehören ins Forum!

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    P 1 Antwort Letzte Antwort
    0
    • wendy2702W wendy2702

      Adapter wird auch erst grün wenn mindestes 1 register eingetragen und ausgelesen werden kann.

      P Offline
      P Offline
      Pep
      schrieb am zuletzt editiert von
      #4

      @wendy2702 DANKE - dann teste ich das jetzt mal :-)

      P 1 Antwort Letzte Antwort
      0
      • P Pep

        @wendy2702 DANKE - dann teste ich das jetzt mal :-)

        P Offline
        P Offline
        Pep
        schrieb am zuletzt editiert von
        #5

        Jetzt bekomme ich kurz beim Start eine Verbindung - werde aber gleich wieder getrennt:

        250a8218-3175-4002-8805-0becaad2deae-image.png

        Sieht mir so aus, als ob er keine ModBus daten abfragen kann oder?

        HomoranH wendy2702W 2 Antworten Letzte Antwort
        0
        • P Pep

          Jetzt bekomme ich kurz beim Start eine Verbindung - werde aber gleich wieder getrennt:

          250a8218-3175-4002-8805-0becaad2deae-image.png

          Sieht mir so aus, als ob er keine ModBus daten abfragen kann oder?

          HomoranH Nicht stören
          HomoranH Nicht stören
          Homoran
          Global Moderator Administrators
          schrieb am zuletzt editiert von
          #6

          @pep sagte in ModBus RTU auf ModBus TCP über DR302:

          Jetzt bekomme ich kurz beim Start eine Verbindung - werde aber gleich wieder getrennt:

          250a8218-3175-4002-8805-0becaad2deae-image.png

          Sieht mir so aus, als ob er keine ModBus daten abfragen kann oder?

          bitte als text in code-tags, dann kann man auch zitieren

          https://forum.iobroker.net/topic/51555/hinweise-für-gute-forenbeiträge/1

          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

          1 Antwort Letzte Antwort
          0
          • P Pep

            Jetzt bekomme ich kurz beim Start eine Verbindung - werde aber gleich wieder getrennt:

            250a8218-3175-4002-8805-0becaad2deae-image.png

            Sieht mir so aus, als ob er keine ModBus daten abfragen kann oder?

            wendy2702W Online
            wendy2702W Online
            wendy2702
            schrieb am zuletzt editiert von
            #7

            @pep stelle das loggen auf Debug

            5163B687-06A0-492C-B9A5-5086EE1AF30E.jpeg

            Und poste das log als Text in Code Tags

            1B9183A0-0A84-4D8F-9952-F6847AB72AF3.jpeg

            Bitte keine Fragen per PN, die gehören ins Forum!

            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

            P 1 Antwort Letzte Antwort
            0
            • wendy2702W wendy2702

              @pep stelle das loggen auf Debug

              5163B687-06A0-492C-B9A5-5086EE1AF30E.jpeg

              Und poste das log als Text in Code Tags

              1B9183A0-0A84-4D8F-9952-F6847AB72AF3.jpeg

              P Offline
              P Offline
              Pep
              schrieb am zuletzt editiert von
              #8

              @wendy2702
              2a7073a9-ddf4-4133-ba23-5da95d659460-image.png

              sieht aus, als ob er das ModBus Gerät nicht findet oder?

              HomoranH 1 Antwort Letzte Antwort
              0
              • P Pep

                @wendy2702
                2a7073a9-ddf4-4133-ba23-5da95d659460-image.png

                sieht aus, als ob er das ModBus Gerät nicht findet oder?

                HomoranH Nicht stören
                HomoranH Nicht stören
                Homoran
                Global Moderator Administrators
                schrieb am zuletzt editiert von
                #9

                @pep bitte text, dann zitier ich's

                kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                P 1 Antwort Letzte Antwort
                0
                • HomoranH Homoran

                  @pep bitte text, dann zitier ich's

                  P Offline
                  P Offline
                  Pep
                  schrieb am zuletzt editiert von
                  #10

                  @homoran
                  aber gern doch

                  modbus.1 2023-03-13 17:15:28.705	info	Disconnected from slave 192.168.178.33
                  modbus.1 2023-03-13 17:15:28.704	debug	Closing client on purpose.
                  modbus.1 2023-03-13 17:15:27.705	debug	Cleaning up request fifo.
                  modbus.1 2023-03-13 17:15:27.705	debug	Clearing timeout of the current request.
                  modbus.1 2023-03-13 17:15:27.704	debug	Socket closed with error
                  modbus.1 2023-03-13 17:15:27.702	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
                  modbus.1 2023-03-13 17:15:27.701	error	Client in error state.
                  modbus.1 2023-03-13 17:15:27.701	error	Request timed out.
                  modbus.1 2023-03-13 17:15:27.701	warn	Error: undefined
                  modbus.1 2023-03-13 17:15:22.697	debug	Sending pdu to the socket.
                  modbus.1 2023-03-13 17:15:22.696	debug	[DevID_1/inputRegs] Poll address 3001 - 1 registers
                  modbus.1 2023-03-13 17:15:22.695	debug	Initialization of scale factors done!
                  modbus.1 2023-03-13 17:15:22.694	debug	[DevID_1] Poll start ---------------------
                  modbus.1 2023-03-13 17:15:22.693	info	Connected to slave
                  modbus.1 2023-03-13 17:15:22.406	debug	Initialize Objects for holdingRegs: []
                  modbus.1 2023-03-13 17:15:22.406	debug	Add inputRegisters.3001_Inverter_Status: {"_id":"inputRegisters.3001_Inverter_Status","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":3001,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1}}
                  modbus.1 2023-03-13 17:15:22.405	debug	Initialize Objects for inputRegs: [{"_address":"3001","name":"Inverter Status","description":"","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":"","isScale":"","address":3001,"deviceId":1,"id":"inputRegisters.3001_Inverter_Status"}]
                  modbus.1 2023-03-13 17:15:22.405	debug	Initialize Objects for coils: []
                  modbus.1 2023-03-13 17:15:22.404	debug	Initialize Objects for disInputs: []
                  modbus.1 2023-03-13 17:15:22.201	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
                  modbus.1 2023-03-13 17:15:21.884	debug	Plugin sentry Initialize Plugin (enabled=true)
                  modbus.1 2023-03-13 17:15:21.749	debug	States connected to redis: 0.0.0.0:9000
                  modbus.1 2023-03-13 17:15:21.655	debug	States create User PubSub Client
                  modbus.1 2023-03-13 17:15:21.654	debug	States create System PubSub Client
                  modbus.1 2023-03-13 17:15:21.588	debug	Redis States: Use Redis connection: 0.0.0.0:9000
                  modbus.1 2023-03-13 17:15:21.555	debug	Objects connected to redis: 0.0.0.0:9001
                  modbus.1 2023-03-13 17:15:21.550	debug	Objects client initialize lua scripts
                  modbus.1 2023-03-13 17:15:21.478	debug	Objects create User PubSub Client
                  modbus.1 2023-03-13 17:15:21.477	debug	Objects create System PubSub Client
                  modbus.1 2023-03-13 17:15:21.381	debug	Objects client ready ... initialize now
                  modbus.1 2023-03-13 17:15:21.262	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
                  
                  wendy2702W HomoranH 2 Antworten Letzte Antwort
                  0
                  • P Pep

                    @homoran
                    aber gern doch

                    modbus.1 2023-03-13 17:15:28.705	info	Disconnected from slave 192.168.178.33
                    modbus.1 2023-03-13 17:15:28.704	debug	Closing client on purpose.
                    modbus.1 2023-03-13 17:15:27.705	debug	Cleaning up request fifo.
                    modbus.1 2023-03-13 17:15:27.705	debug	Clearing timeout of the current request.
                    modbus.1 2023-03-13 17:15:27.704	debug	Socket closed with error
                    modbus.1 2023-03-13 17:15:27.702	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
                    modbus.1 2023-03-13 17:15:27.701	error	Client in error state.
                    modbus.1 2023-03-13 17:15:27.701	error	Request timed out.
                    modbus.1 2023-03-13 17:15:27.701	warn	Error: undefined
                    modbus.1 2023-03-13 17:15:22.697	debug	Sending pdu to the socket.
                    modbus.1 2023-03-13 17:15:22.696	debug	[DevID_1/inputRegs] Poll address 3001 - 1 registers
                    modbus.1 2023-03-13 17:15:22.695	debug	Initialization of scale factors done!
                    modbus.1 2023-03-13 17:15:22.694	debug	[DevID_1] Poll start ---------------------
                    modbus.1 2023-03-13 17:15:22.693	info	Connected to slave
                    modbus.1 2023-03-13 17:15:22.406	debug	Initialize Objects for holdingRegs: []
                    modbus.1 2023-03-13 17:15:22.406	debug	Add inputRegisters.3001_Inverter_Status: {"_id":"inputRegisters.3001_Inverter_Status","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":3001,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1}}
                    modbus.1 2023-03-13 17:15:22.405	debug	Initialize Objects for inputRegs: [{"_address":"3001","name":"Inverter Status","description":"","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":"","isScale":"","address":3001,"deviceId":1,"id":"inputRegisters.3001_Inverter_Status"}]
                    modbus.1 2023-03-13 17:15:22.405	debug	Initialize Objects for coils: []
                    modbus.1 2023-03-13 17:15:22.404	debug	Initialize Objects for disInputs: []
                    modbus.1 2023-03-13 17:15:22.201	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
                    modbus.1 2023-03-13 17:15:21.884	debug	Plugin sentry Initialize Plugin (enabled=true)
                    modbus.1 2023-03-13 17:15:21.749	debug	States connected to redis: 0.0.0.0:9000
                    modbus.1 2023-03-13 17:15:21.655	debug	States create User PubSub Client
                    modbus.1 2023-03-13 17:15:21.654	debug	States create System PubSub Client
                    modbus.1 2023-03-13 17:15:21.588	debug	Redis States: Use Redis connection: 0.0.0.0:9000
                    modbus.1 2023-03-13 17:15:21.555	debug	Objects connected to redis: 0.0.0.0:9001
                    modbus.1 2023-03-13 17:15:21.550	debug	Objects client initialize lua scripts
                    modbus.1 2023-03-13 17:15:21.478	debug	Objects create User PubSub Client
                    modbus.1 2023-03-13 17:15:21.477	debug	Objects create System PubSub Client
                    modbus.1 2023-03-13 17:15:21.381	debug	Objects client ready ... initialize now
                    modbus.1 2023-03-13 17:15:21.262	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
                    
                    wendy2702W Online
                    wendy2702W Online
                    wendy2702
                    schrieb am zuletzt editiert von
                    #11

                    @pep sagte in ModBus RTU auf ModBus TCP über DR302:

                    Poll address 3001 - 1 registers

                    Gibt es das Register? Ich meine mich aus dem anderen Thread an Zahlen mit 4xxxx zu erinnern. Auch sollten es Holding sein meine ich.

                    Bitte keine Fragen per PN, die gehören ins Forum!

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    1 Antwort Letzte Antwort
                    0
                    • K Offline
                      K Offline
                      klassisch
                      Most Active
                      schrieb am zuletzt editiert von klassisch
                      #12

                      Register 30001: Ist "alias" angehakt?

                      input register oder holding register?

                      Stimmen die Modbus Adresse des Wechselrichters?

                      Ich empfehle generell immer "mehrere Geräte Ids" anzuhaken. Die Adresse ist dann auf der Registerseite einzutragen.
                      Falls irgendwann ein zweiter Modbus Teilnehmer dazukommt, geht das besser.

                      1 Antwort Letzte Antwort
                      0
                      • P Pep

                        @homoran
                        aber gern doch

                        modbus.1 2023-03-13 17:15:28.705	info	Disconnected from slave 192.168.178.33
                        modbus.1 2023-03-13 17:15:28.704	debug	Closing client on purpose.
                        modbus.1 2023-03-13 17:15:27.705	debug	Cleaning up request fifo.
                        modbus.1 2023-03-13 17:15:27.705	debug	Clearing timeout of the current request.
                        modbus.1 2023-03-13 17:15:27.704	debug	Socket closed with error
                        modbus.1 2023-03-13 17:15:27.702	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
                        modbus.1 2023-03-13 17:15:27.701	error	Client in error state.
                        modbus.1 2023-03-13 17:15:27.701	error	Request timed out.
                        modbus.1 2023-03-13 17:15:27.701	warn	Error: undefined
                        modbus.1 2023-03-13 17:15:22.697	debug	Sending pdu to the socket.
                        modbus.1 2023-03-13 17:15:22.696	debug	[DevID_1/inputRegs] Poll address 3001 - 1 registers
                        modbus.1 2023-03-13 17:15:22.695	debug	Initialization of scale factors done!
                        modbus.1 2023-03-13 17:15:22.694	debug	[DevID_1] Poll start ---------------------
                        modbus.1 2023-03-13 17:15:22.693	info	Connected to slave
                        modbus.1 2023-03-13 17:15:22.406	debug	Initialize Objects for holdingRegs: []
                        modbus.1 2023-03-13 17:15:22.406	debug	Add inputRegisters.3001_Inverter_Status: {"_id":"inputRegisters.3001_Inverter_Status","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":3001,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1}}
                        modbus.1 2023-03-13 17:15:22.405	debug	Initialize Objects for inputRegs: [{"_address":"3001","name":"Inverter Status","description":"","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":"","isScale":"","address":3001,"deviceId":1,"id":"inputRegisters.3001_Inverter_Status"}]
                        modbus.1 2023-03-13 17:15:22.405	debug	Initialize Objects for coils: []
                        modbus.1 2023-03-13 17:15:22.404	debug	Initialize Objects for disInputs: []
                        modbus.1 2023-03-13 17:15:22.201	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
                        modbus.1 2023-03-13 17:15:21.884	debug	Plugin sentry Initialize Plugin (enabled=true)
                        modbus.1 2023-03-13 17:15:21.749	debug	States connected to redis: 0.0.0.0:9000
                        modbus.1 2023-03-13 17:15:21.655	debug	States create User PubSub Client
                        modbus.1 2023-03-13 17:15:21.654	debug	States create System PubSub Client
                        modbus.1 2023-03-13 17:15:21.588	debug	Redis States: Use Redis connection: 0.0.0.0:9000
                        modbus.1 2023-03-13 17:15:21.555	debug	Objects connected to redis: 0.0.0.0:9001
                        modbus.1 2023-03-13 17:15:21.550	debug	Objects client initialize lua scripts
                        modbus.1 2023-03-13 17:15:21.478	debug	Objects create User PubSub Client
                        modbus.1 2023-03-13 17:15:21.477	debug	Objects create System PubSub Client
                        modbus.1 2023-03-13 17:15:21.381	debug	Objects client ready ... initialize now
                        modbus.1 2023-03-13 17:15:21.262	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
                        
                        HomoranH Nicht stören
                        HomoranH Nicht stören
                        Homoran
                        Global Moderator Administrators
                        schrieb am zuletzt editiert von
                        #13

                        @pep sagte in ModBus RTU auf ModBus TCP über DR302:

                        Client in error state.

                        hast du den immer noch auf Master stehen?
                        wie geschrieben

                        @homoran sagte in ModBus RTU auf ModBus TCP über DR302:

                        @pep work mode tcp server??
                        muss das nicht ein client sein?

                        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                        K 1 Antwort Letzte Antwort
                        0
                        • HomoranH Homoran

                          @pep sagte in ModBus RTU auf ModBus TCP über DR302:

                          Client in error state.

                          hast du den immer noch auf Master stehen?
                          wie geschrieben

                          @homoran sagte in ModBus RTU auf ModBus TCP über DR302:

                          @pep work mode tcp server??
                          muss das nicht ein client sein?

                          K Offline
                          K Offline
                          klassisch
                          Most Active
                          schrieb am zuletzt editiert von
                          #14

                          @homoran der usriot ist ein TCP server
                          Bei dem klopfen die clients (z.B iobroker) an und holen daten

                          K HomoranH 2 Antworten Letzte Antwort
                          1
                          • K klassisch

                            @homoran der usriot ist ein TCP server
                            Bei dem klopfen die clients (z.B iobroker) an und holen daten

                            K Offline
                            K Offline
                            klassisch
                            Most Active
                            schrieb am zuletzt editiert von
                            #15

                            @klassisch sagte in ModBus RTU auf ModBus TCP über DR302:

                            @homoran der usriot ist ein TCP server
                            Bei dem klopfen die clients (z.B iobroker) an und holen daten

                            K 1 Antwort Letzte Antwort
                            0
                            • K klassisch

                              @homoran der usriot ist ein TCP server
                              Bei dem klopfen die clients (z.B iobroker) an und holen daten

                              HomoranH Nicht stören
                              HomoranH Nicht stören
                              Homoran
                              Global Moderator Administrators
                              schrieb am zuletzt editiert von
                              #16

                              @klassisch dann muss iobroker als client eingestellt sein.
                              (ist bei mir ein master!)

                              kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                              der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                              K 1 Antwort Letzte Antwort
                              0
                              • K klassisch

                                @klassisch sagte in ModBus RTU auf ModBus TCP über DR302:

                                @homoran der usriot ist ein TCP server
                                Bei dem klopfen die clients (z.B iobroker) an und holen daten

                                K Offline
                                K Offline
                                klassisch
                                Most Active
                                schrieb am zuletzt editiert von
                                #17

                                Client in Error state kommt wenn die Verbindung zum Usriot steht, aber das Endgerät nicht oder nicht richtig antwortet

                                Immer erst mit einem Register anfangen
                                Jeder Fehler führt zum Abbruch mit unspezifischer Fehlermeldung
                                A B Leitungen probeweise kreuzen
                                Ist beim Endgerät Modbus überhaupt aktiviert?

                                P 1 Antwort Letzte Antwort
                                1
                                • HomoranH Homoran

                                  @klassisch dann muss iobroker als client eingestellt sein.
                                  (ist bei mir ein master!)

                                  K Offline
                                  K Offline
                                  klassisch
                                  Most Active
                                  schrieb am zuletzt editiert von klassisch
                                  #18

                                  @homoran master im Modbus aber client im TCP

                                  Du hast ja USB Karte und damit entfällt bei Dir der TCP Pfad.
                                  Damit siehst Du nur den Modbus RS485. Da ist der ioBroker Adapter der Master und Deine Endgeräte die Slaves. Der Master fragt die reihum ab.

                                  Bei Mudbus über TCP ist die TCP Strecke zwischengeschaltet. Der Mudbus wird sozusagen Huckepack über TCP transportiert.
                                  Und bei TCP ist der USRIOT der Server, bei dem die Clients anfragen. Der Server bedient dann die Clients und liefert Ergebnisse zurück. Das können mehrere Clients sein, die fragen.
                                  Bei meinen Implementierungen von RFLInk über TCP (virtueller COM) und smartmeter (RS485 vom Hager Lesekopf) über TCP habe ich das schon so gemacht.

                                  1 Antwort Letzte Antwort
                                  1
                                  • K klassisch

                                    Client in Error state kommt wenn die Verbindung zum Usriot steht, aber das Endgerät nicht oder nicht richtig antwortet

                                    Immer erst mit einem Register anfangen
                                    Jeder Fehler führt zum Abbruch mit unspezifischer Fehlermeldung
                                    A B Leitungen probeweise kreuzen
                                    Ist beim Endgerät Modbus überhaupt aktiviert?

                                    P Offline
                                    P Offline
                                    Pep
                                    schrieb am zuletzt editiert von
                                    #19

                                    @klassisch said in ModBus RTU auf ModBus TCP über DR302:

                                    t beim Endgerät Modbu

                                    Ich denke, dass an dem Growatt WR irgendwas mit dem ModBus noch nicht hinhaut - ich teste mal bissel rum. Sobald ich eine Lösung habe, gebe ich hier bescheid.

                                    DANKE schonmal, für die vielen Rückmeldungen

                                    S 1 Antwort Letzte Antwort
                                    0
                                    • P Pep

                                      @klassisch said in ModBus RTU auf ModBus TCP über DR302:

                                      t beim Endgerät Modbu

                                      Ich denke, dass an dem Growatt WR irgendwas mit dem ModBus noch nicht hinhaut - ich teste mal bissel rum. Sobald ich eine Lösung habe, gebe ich hier bescheid.

                                      DANKE schonmal, für die vielen Rückmeldungen

                                      S Offline
                                      S Offline
                                      Sneida
                                      schrieb am zuletzt editiert von
                                      #20

                                      @pep ich bin momentan an derselben Stelle. Ich versuche einen GROWATT MIC tl-x 2500 auszulesen. Ich bekomme mich auch auf den Waveshare RS485 - ETH Adapter verbunden, aber bekomme keine Daten aus dem WR. Konntest du dein Problem mittlerweile lösen?

                                      HomoranH 1 Antwort Letzte Antwort
                                      0
                                      • S Sneida

                                        @pep ich bin momentan an derselben Stelle. Ich versuche einen GROWATT MIC tl-x 2500 auszulesen. Ich bekomme mich auch auf den Waveshare RS485 - ETH Adapter verbunden, aber bekomme keine Daten aus dem WR. Konntest du dein Problem mittlerweile lösen?

                                        HomoranH Nicht stören
                                        HomoranH Nicht stören
                                        Homoran
                                        Global Moderator Administrators
                                        schrieb am zuletzt editiert von
                                        #21

                                        @sneida sagte in ModBus RTU auf ModBus TCP über DR302:

                                        aber bekomme keine Daten aus dem WR

                                        und keine Meldungen im debug-log?

                                        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                        S 1 Antwort Letzte Antwort
                                        0
                                        • HomoranH Homoran

                                          @sneida sagte in ModBus RTU auf ModBus TCP über DR302:

                                          aber bekomme keine Daten aus dem WR

                                          und keine Meldungen im debug-log?

                                          S Offline
                                          S Offline
                                          Sneida
                                          schrieb am zuletzt editiert von
                                          #22

                                          @homoran

                                          Hier mal meine Settings

                                          01.PNG

                                          02.PNG

                                          03.PNG

                                          2023-04-27 14:10:30.395	info	Disconnected from slave 192.168.0.6 modbus.0
                                          2023-04-27 14:10:29.594	warn	Poll error count: 5 code: "App Timeout" modbus.0
                                          2023-04-27 14:10:29.395	error	Client in error state. modbus.0
                                          2023-04-27 14:10:29.394	error	Request timed out. modbus.0
                                          2023-04-27 14:10:29.394	warn	Error: undefined modbus.0
                                          2023-04-27 14:10:25.295	warn	Poll error count: 4 code: "App Timeout" modbus.0
                                          2023-04-27 14:10:24.393	info	Connected to slave 192.168.0.6
                                          
                                          HomoranH 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          771

                                          Online

                                          32.5k

                                          Benutzer

                                          81.8k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe