Skip to content
  • Aktuell
  • Tags
  • 0 Ungelesen 0
  • Kategorien
  • Unreplied
  • Beliebt
  • GitHub
  • Docu
  • Hilfe
Skins
  • Light
  • Brite
  • Cerulean
  • Cosmo
  • Flatly
  • Journal
  • Litera
  • Lumen
  • Lux
  • Materia
  • Minty
  • Morph
  • Pulse
  • Sandstone
  • Simplex
  • Sketchy
  • Spacelab
  • United
  • Yeti
  • Zephyr
  • Dark
  • Cyborg
  • Darkly
  • Quartz
  • Slate
  • Solar
  • Superhero
  • Vapor

  • Standard: (Kein Skin)
  • Kein Skin
Einklappen
ioBroker Logo
  1. ioBroker Community Home
  2. Deutsch
  3. ioBroker Allgemein
  4. Modbus adapter

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.1k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.9k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.1k

Modbus adapter

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
modbus adaptermodbus
978 Beiträge 140 Kommentatoren 382.1k Aufrufe 64 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • K klassisch

    @icegixxe Sieht gut aus!

    Hast Du beim 410S RTU eingestellt? Ich glaub bei dem kann man das, aber der macht das nicht stabil, wenn ich mich recht erinnere.
    Bringt ein paar Logeinträge pro Tag.
    Deshalb lieber den 410S auf TCP stellen und den ioBroker Adapter auf RTU TCP.
    Man darf immer nur bei einem der beiden Partner RTU einstellen.

    I Offline
    I Offline
    icegixxe
    schrieb am zuletzt editiert von
    #737

    @klassisch sagte in Modbus adapter:

    @icegixxe Sieht gut aus!

    Hast Du beim 410S RTU eingestellt? Ich glaub bei dem kann man das, aber der macht das nicht stabil, wenn ich mich recht erinnere.
    Bringt ein paar Logeinträge pro Tag.
    Deshalb lieber den 410S auf TCP stellen und den ioBroker Adapter auf RTU TCP.
    Man darf immer nur bei einem der beiden Partner RTU einstellen.

    Diese Einstellung finde ich nicht am Gerät und auch nicht in der Herstellerdoku.
    https://stromzähler.eu/media/pdf/93/17/d7/SDM72DM-V2.pdf

    Aber so wie es jetzt ist könnte es doch bleiben?
    Hast du eine technische Erklärung für meine Änderungen? Ich habe noch nicht verstanden, warum es jetzt mit den neuen Aliases Einstellungen klappt...

    K 1 Antwort Letzte Antwort
    0
    • K klassisch

      @icegixxe Sieht gut aus!

      Hast Du beim 410S RTU eingestellt? Ich glaub bei dem kann man das, aber der macht das nicht stabil, wenn ich mich recht erinnere.
      Bringt ein paar Logeinträge pro Tag.
      Deshalb lieber den 410S auf TCP stellen und den ioBroker Adapter auf RTU TCP.
      Man darf immer nur bei einem der beiden Partner RTU einstellen.

      I Offline
      I Offline
      icegixxe
      schrieb am zuletzt editiert von
      #738

      @klassisch sagte in Modbus adapter:

      @icegixxe Sieht gut aus!

      Hast Du beim 410S RTU eingestellt? Ich glaub bei dem kann man das, aber der macht das nicht stabil, wenn ich mich recht erinnere.
      Bringt ein paar Logeinträge pro Tag.
      Deshalb lieber den 410S auf TCP stellen und den ioBroker Adapter auf RTU TCP.
      Man darf immer nur bei einem der beiden Partner RTU einstellen.

      Sorry, du meinst natürlich das gateway.
      Das sieht aktuell so aus:

      7783ca57-f84c-45f1-88ce-4a5564dd93f6-image.png

      1 Antwort Letzte Antwort
      0
      • I icegixxe

        @klassisch sagte in Modbus adapter:

        @icegixxe Sieht gut aus!

        Hast Du beim 410S RTU eingestellt? Ich glaub bei dem kann man das, aber der macht das nicht stabil, wenn ich mich recht erinnere.
        Bringt ein paar Logeinträge pro Tag.
        Deshalb lieber den 410S auf TCP stellen und den ioBroker Adapter auf RTU TCP.
        Man darf immer nur bei einem der beiden Partner RTU einstellen.

        Diese Einstellung finde ich nicht am Gerät und auch nicht in der Herstellerdoku.
        https://stromzähler.eu/media/pdf/93/17/d7/SDM72DM-V2.pdf

        Aber so wie es jetzt ist könnte es doch bleiben?
        Hast du eine technische Erklärung für meine Änderungen? Ich habe noch nicht verstanden, warum es jetzt mit den neuen Aliases Einstellungen klappt...

        K Offline
        K Offline
        klassisch
        Most Active
        schrieb am zuletzt editiert von
        #739

        @icegixxe sagte in Modbus adapter:

        Diese Einstellung finde ich nicht am Gerät und auch nicht in der Herstellerdoku.

        Nein, das ist eine Einstellung beim USRIOT

        Aber so wie es jetzt ist könnte es doch bleiben?

        Ja, Du kannst das mal so lassen und das logfile beobachten. Ich hatte das auch mal so testweise, es gab dann allerdings ein paar Fehlereinträge pro Tag. Dann habe ich im Adapter TCP RTU eingestellt und im 410S nur TCP. Das lief dann stabiler. Man darf anscheinend immer nur auf einer Seite Mdobus RTU auswählen. Entweder im Konverter oder im ioBroker.

        Hast du eine technische Erklärung für meine Änderungen? Ich habe noch nicht verstanden, warum es jetzt mit den neuen Aliases Einstellungen klappt...

        Not really. Modbus ist eine alte Sache also die Computer RAMs noch in kByte gezählt wurden. Das ist nicht so komfortabel mit der Einstellung der Register. Und ich habe mich nicht wirklich intensiv damit beschäftigt. Ich bin immer froh, wenn es dann mal läuft. Aber wenn es läuft, dann recht stabil.

        I 1 Antwort Letzte Antwort
        0
        • K klassisch

          @icegixxe sagte in Modbus adapter:

          Diese Einstellung finde ich nicht am Gerät und auch nicht in der Herstellerdoku.

          Nein, das ist eine Einstellung beim USRIOT

          Aber so wie es jetzt ist könnte es doch bleiben?

          Ja, Du kannst das mal so lassen und das logfile beobachten. Ich hatte das auch mal so testweise, es gab dann allerdings ein paar Fehlereinträge pro Tag. Dann habe ich im Adapter TCP RTU eingestellt und im 410S nur TCP. Das lief dann stabiler. Man darf anscheinend immer nur auf einer Seite Mdobus RTU auswählen. Entweder im Konverter oder im ioBroker.

          Hast du eine technische Erklärung für meine Änderungen? Ich habe noch nicht verstanden, warum es jetzt mit den neuen Aliases Einstellungen klappt...

          Not really. Modbus ist eine alte Sache also die Computer RAMs noch in kByte gezählt wurden. Das ist nicht so komfortabel mit der Einstellung der Register. Und ich habe mich nicht wirklich intensiv damit beschäftigt. Ich bin immer froh, wenn es dann mal läuft. Aber wenn es läuft, dann recht stabil.

          I Offline
          I Offline
          icegixxe
          schrieb am zuletzt editiert von
          #740

          @klassisch sagte in Modbus adapter:

          @icegixxe sagte in Modbus adapter:

          Diese Einstellung finde ich nicht am Gerät und auch nicht in der Herstellerdoku.

          Nein, das ist eine Einstellung beim USRIOT

          Aber so wie es jetzt ist könnte es doch bleiben?

          Ja, Du kannst das mal so lassen und das logfile beobachten. Ich hatte das auch mal so testweise, es gab dann allerdings ein paar Fehlereinträge pro Tag. Dann habe ich im Adapter TCP RTU eingestellt und im 410S nur TCP. Das lief dann stabiler. Man darf anscheinend immer nur auf einer Seite Mdobus RTU auswählen. Entweder im Konverter oder im ioBroker.

          Hast du eine technische Erklärung für meine Änderungen? Ich habe noch nicht verstanden, warum es jetzt mit den neuen Aliases Einstellungen klappt...

          Not really. Modbus ist eine alte Sache also die Computer RAMs noch in kByte gezählt wurden. Das ist nicht so komfortabel mit der Einstellung der Register. Und ich habe mich nicht wirklich intensiv damit beschäftigt. Ich bin immer froh, wenn es dann mal läuft. Aber wenn es läuft, dann recht stabil.

          Hatte kurz vorher nochmal die Config aus dem 410 gepostet. Aber dort scheint die Einstellung auch nicht zu sein.

          K 1 Antwort Letzte Antwort
          0
          • I icegixxe

            @klassisch sagte in Modbus adapter:

            @icegixxe sagte in Modbus adapter:

            Diese Einstellung finde ich nicht am Gerät und auch nicht in der Herstellerdoku.

            Nein, das ist eine Einstellung beim USRIOT

            Aber so wie es jetzt ist könnte es doch bleiben?

            Ja, Du kannst das mal so lassen und das logfile beobachten. Ich hatte das auch mal so testweise, es gab dann allerdings ein paar Fehlereinträge pro Tag. Dann habe ich im Adapter TCP RTU eingestellt und im 410S nur TCP. Das lief dann stabiler. Man darf anscheinend immer nur auf einer Seite Mdobus RTU auswählen. Entweder im Konverter oder im ioBroker.

            Hast du eine technische Erklärung für meine Änderungen? Ich habe noch nicht verstanden, warum es jetzt mit den neuen Aliases Einstellungen klappt...

            Not really. Modbus ist eine alte Sache also die Computer RAMs noch in kByte gezählt wurden. Das ist nicht so komfortabel mit der Einstellung der Register. Und ich habe mich nicht wirklich intensiv damit beschäftigt. Ich bin immer froh, wenn es dann mal läuft. Aber wenn es läuft, dann recht stabil.

            Hatte kurz vorher nochmal die Config aus dem 410 gepostet. Aber dort scheint die Einstellung auch nicht zu sein.

            K Offline
            K Offline
            klassisch
            Most Active
            schrieb am zuletzt editiert von klassisch
            #741

            @icegixxe Habe gerade den 410S nicht am Laufen, weil ich meinen SDM630 gerade an einem Waveshare DIN Rail Umsetzer betreibe

            Wenn die jetzige Einstellung nicht stabil läuft bzw. ab und an Fehler ins log schreibt, dann mal
            e17f040f-d402-44b6-b85a-11f83d8af046-grafik.png
            das "Modbus TCP" auf none stellen und dafür im ioBroker Adapter "RTU over TCP" einstellen.
            875a4bc7-4c2c-4150-b8eb-206e0dde5a30-grafik.png

            I 1 Antwort Letzte Antwort
            0
            • K klassisch

              @icegixxe Habe gerade den 410S nicht am Laufen, weil ich meinen SDM630 gerade an einem Waveshare DIN Rail Umsetzer betreibe

              Wenn die jetzige Einstellung nicht stabil läuft bzw. ab und an Fehler ins log schreibt, dann mal
              e17f040f-d402-44b6-b85a-11f83d8af046-grafik.png
              das "Modbus TCP" auf none stellen und dafür im ioBroker Adapter "RTU over TCP" einstellen.
              875a4bc7-4c2c-4150-b8eb-206e0dde5a30-grafik.png

              I Offline
              I Offline
              icegixxe
              schrieb am zuletzt editiert von
              #742

              @klassisch Danke, bis jetzt läuft es sehr gut.
              Und schau mal bei deinen PNs!

              K 1 Antwort Letzte Antwort
              0
              • I icegixxe

                @klassisch Danke, bis jetzt läuft es sehr gut.
                Und schau mal bei deinen PNs!

                K Offline
                K Offline
                klassisch
                Most Active
                schrieb am zuletzt editiert von
                #743

                @icegixxe Bei mir waren es auch nur wenige Aussetzer pro Tag. Also mal einige Tage in Ruhe laufen lassen.
                Dann ein Tageslog runterladen und nach Modbus-Einträgen durchsuchen.
                0c39505b-1e57-4e4f-937b-ec1e4fdc07fd-grafik.png

                1 Antwort Letzte Antwort
                0
                • B bkuerby

                  Hallo zusammen,

                  ich versuche gerade meine Wärmepumpe (Waterkotte Ai1+ mit WPCU-Regler) über Modbus RTU einzubinden.

                  Grundsätzlich funktioniert die Verbindung sowohl über ioBroker als auch testweise über qmodbus.

                  Zum Einen erhalte ich bei jeder Anfrage die timeout Meldung zum Anderen erhalte ich eine Meldung "unknown funktion code: 132".

                  Bei der ersten Abfrage nach dem Einschalten der Instanz erscheint nur die timeout Meldung. Dabei werden die Variablenwerte auch aktualisiert. Ab der zweiten Abfrage erfolgt keine Aktualisierung mehr.

                  modbus.0	2019-02-03 14:21:00.894	info	Disconnected from slave
                  modbus.0	2019-02-03 14:20:59.884	warn	Poll error count: 12 code: {"err":"timeout"}
                  modbus.0	2019-02-03 14:20:59.883	error	Request timed out.
                  modbus.0	2019-02-03 14:20:59.883	warn	Error: undefined
                  modbus.0	2019-02-03 14:20:54.984	error	unknown function code: 132
                  modbus.0	2019-02-03 14:20:54.865	info	Connected to slave
                  modbus.0	2019-02-03 14:19:57.610	info	Disconnected from slave
                  modbus.0	2019-02-03 14:19:56.602	warn	Poll error count: 11 code: {"err":"timeout"}
                  modbus.0	2019-02-03 14:19:56.602	error	Request timed out.
                  modbus.0	2019-02-03 14:19:56.601	warn	Error: undefined
                  modbus.0	2019-02-03 14:19:51.705	error	unknown function code: 132
                  modbus.0	2019-02-03 14:19:51.595	info	Connected to slave
                  
                  

                  18988_serial.jpg
                  18988_input.jpg
                  18988_holding.jpg

                  Hat jemand eine Idee?

                  Viele Grüße

                  Bastian

                  W Offline
                  W Offline
                  worxweis
                  schrieb am zuletzt editiert von
                  #744

                  @bkuerby Hallo!

                  Funktioniert bei dir das Auslesen der WPCU mit dem Modbus adapter? Wie hast du die WPCU angeschlossen? Die hat doch einen RS232 Anschluss.

                  Ich bin schon am Verzweifeln.
                  Ich habe auch einen WPCU Regler. lt Schaltplan von Waterkotte ein RS232 Anschluss.
                  Mittels Adapter RS232-> USB verbinde ich mich zu einem Raspberry 4 auf dem Iobroker läuft.
                  Das System ist komplett frisch aufgesetzt und es läuft eigentlich nur der Modbus Adapter darauf.

                  Jedoch bekomme ich keine Verbindung mit dem Modbus Adapter.
                  Also der Adapter wird kurz grün und geht dann wieder auf gelb.

                  Folgende Meldungen kommen im log:

                  
                  modbus.0
                  2023-01-23 18:02:11.042	info	Disconnected from slave
                  
                  modbus.0
                  2023-01-23 18:02:10.040	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
                  
                  modbus.0
                  2023-01-23 18:02:10.038	error	Request timed out.
                  
                  modbus.0
                  2023-01-23 18:02:10.036	warn	Error: undefined
                  
                  modbus.0
                  2023-01-23 18:02:05.060	error	Error response: Data address of some or all the required entities are not allowed or do not exist in slave
                  
                  modbus.0
                  2023-01-23 18:02:05.059	error	Error response for FCx4: Illegal Data Address
                  
                  modbus.0
                  2023-01-23 18:02:05.025	info	Connected to slave
                  
                  modbus.0
                  2023-01-23 18:02:04.569	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
                  

                  Ich habe auch schon diverse versuche mit Eingangsregister und Holdingregister unternommen.
                  Was kann ich hier noch falsch eingestellt haben?

                  wendy2702W 1 Antwort Letzte Antwort
                  0
                  • W worxweis

                    @bkuerby Hallo!

                    Funktioniert bei dir das Auslesen der WPCU mit dem Modbus adapter? Wie hast du die WPCU angeschlossen? Die hat doch einen RS232 Anschluss.

                    Ich bin schon am Verzweifeln.
                    Ich habe auch einen WPCU Regler. lt Schaltplan von Waterkotte ein RS232 Anschluss.
                    Mittels Adapter RS232-> USB verbinde ich mich zu einem Raspberry 4 auf dem Iobroker läuft.
                    Das System ist komplett frisch aufgesetzt und es läuft eigentlich nur der Modbus Adapter darauf.

                    Jedoch bekomme ich keine Verbindung mit dem Modbus Adapter.
                    Also der Adapter wird kurz grün und geht dann wieder auf gelb.

                    Folgende Meldungen kommen im log:

                    
                    modbus.0
                    2023-01-23 18:02:11.042	info	Disconnected from slave
                    
                    modbus.0
                    2023-01-23 18:02:10.040	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
                    
                    modbus.0
                    2023-01-23 18:02:10.038	error	Request timed out.
                    
                    modbus.0
                    2023-01-23 18:02:10.036	warn	Error: undefined
                    
                    modbus.0
                    2023-01-23 18:02:05.060	error	Error response: Data address of some or all the required entities are not allowed or do not exist in slave
                    
                    modbus.0
                    2023-01-23 18:02:05.059	error	Error response for FCx4: Illegal Data Address
                    
                    modbus.0
                    2023-01-23 18:02:05.025	info	Connected to slave
                    
                    modbus.0
                    2023-01-23 18:02:04.569	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
                    

                    Ich habe auch schon diverse versuche mit Eingangsregister und Holdingregister unternommen.
                    Was kann ich hier noch falsch eingestellt haben?

                    wendy2702W Online
                    wendy2702W Online
                    wendy2702
                    schrieb am zuletzt editiert von
                    #745

                    @worxweis Sollte sich der Regler direkt per Modbus ansprechen lassen oder wie auch immer: Du benötigst ein sogenanntes "Null-Modem" Kabel. Also ein RS-232 bei dem RX-TX gekreutzt ist. Sonst gibt das nichts.

                    Bitte keine Fragen per PN, die gehören ins Forum!

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    W 1 Antwort Letzte Antwort
                    0
                    • wendy2702W wendy2702

                      @worxweis Sollte sich der Regler direkt per Modbus ansprechen lassen oder wie auch immer: Du benötigst ein sogenanntes "Null-Modem" Kabel. Also ein RS-232 bei dem RX-TX gekreutzt ist. Sonst gibt das nichts.

                      W Offline
                      W Offline
                      worxweis
                      schrieb am zuletzt editiert von
                      #746

                      @wendy2702 Ich habe ein Nullmodemkabel zwischen Adapter und Wärmepumpe.

                      1 Antwort Letzte Antwort
                      0
                      • B Offline
                        B Offline
                        blessi
                        schrieb am zuletzt editiert von
                        #747

                        Hallo Zusammen,

                        könnt Ihr mir aktuell einen Drehstromzähler (geeicht) und ein Gateway empfehlen, um die Daten in den iobroker zu bekommen?

                        Viele Grüße
                        Maic

                        K wendy2702W 2 Antworten Letzte Antwort
                        0
                        • B blessi

                          Hallo Zusammen,

                          könnt Ihr mir aktuell einen Drehstromzähler (geeicht) und ein Gateway empfehlen, um die Daten in den iobroker zu bekommen?

                          Viele Grüße
                          Maic

                          K Offline
                          K Offline
                          klassisch
                          Most Active
                          schrieb am zuletzt editiert von
                          #748

                          @blessi Hier gibt es Erfahrungen mit funktionierenden Konfigurationen: https://forum.iobroker.net/topic/55710/sdm120-sdm72-sdm630-modbus-rs485-stromzähler-w-lan-iobroker?_=1677138832377

                          B 1 Antwort Letzte Antwort
                          0
                          • B blessi

                            Hallo Zusammen,

                            könnt Ihr mir aktuell einen Drehstromzähler (geeicht) und ein Gateway empfehlen, um die Daten in den iobroker zu bekommen?

                            Viele Grüße
                            Maic

                            wendy2702W Online
                            wendy2702W Online
                            wendy2702
                            schrieb am zuletzt editiert von wendy2702
                            #749

                            @blessi sagte in Modbus adapter:

                            Hallo Zusammen,

                            könnt Ihr mir aktuell einen Drehstromzähler (geeicht) und ein Gateway empfehlen, um die Daten in den iobroker zu bekommen?

                            Viele Grüße
                            Maic

                            An wie vielen Stellen willst du noch fragen?

                            https://forum.iobroker.net/topic/63286/geeichte-drehstromzähler-zwischenzähler-für-iobroker?_=1677135057685

                            Einmal sollte doch reichen.

                            Zumal es hier eigentlich um den Modbus Adapter geht.

                            Bitte keine Fragen per PN, die gehören ins Forum!

                            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                            B 1 Antwort Letzte Antwort
                            0
                            • wendy2702W wendy2702

                              @blessi sagte in Modbus adapter:

                              Hallo Zusammen,

                              könnt Ihr mir aktuell einen Drehstromzähler (geeicht) und ein Gateway empfehlen, um die Daten in den iobroker zu bekommen?

                              Viele Grüße
                              Maic

                              An wie vielen Stellen willst du noch fragen?

                              https://forum.iobroker.net/topic/63286/geeichte-drehstromzähler-zwischenzähler-für-iobroker?_=1677135057685

                              Einmal sollte doch reichen.

                              Zumal es hier eigentlich um den Modbus Adapter geht.

                              B Offline
                              B Offline
                              blessi
                              schrieb am zuletzt editiert von
                              #750

                              @wendy2702 Kann ich nicht an 2 Stellen Fragen stellen?
                              Hier frage ich, weil ich den Adapter gefunden habe und es sich interessant anhört, nach der aktuell funktionierenden Hardware mit diesem Adapter.

                              Meine Frage unter Hardware ist komplett offen in einer möglichen Lösung.

                              Ein Forum ist dafür da, Fragen zu stellen, oder sehe ich das falsch?

                              wendy2702W HomoranH 2 Antworten Letzte Antwort
                              0
                              • B blessi

                                @wendy2702 Kann ich nicht an 2 Stellen Fragen stellen?
                                Hier frage ich, weil ich den Adapter gefunden habe und es sich interessant anhört, nach der aktuell funktionierenden Hardware mit diesem Adapter.

                                Meine Frage unter Hardware ist komplett offen in einer möglichen Lösung.

                                Ein Forum ist dafür da, Fragen zu stellen, oder sehe ich das falsch?

                                wendy2702W Online
                                wendy2702W Online
                                wendy2702
                                schrieb am zuletzt editiert von
                                #751

                                @blessi Klar ist das Forum dafür da, aber nicht um das gleiche an mehreren Stellen zu fragen.

                                Ausserdem geht es hier im Thread eigentlich um den Adapter und nicht um HW die eventuell damit funktionieren könnte.

                                Im anderen Thread hast du schon Antworten auf dein Frage bekommen.

                                Bitte keine Fragen per PN, die gehören ins Forum!

                                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                1 Antwort Letzte Antwort
                                0
                                • B blessi

                                  @wendy2702 Kann ich nicht an 2 Stellen Fragen stellen?
                                  Hier frage ich, weil ich den Adapter gefunden habe und es sich interessant anhört, nach der aktuell funktionierenden Hardware mit diesem Adapter.

                                  Meine Frage unter Hardware ist komplett offen in einer möglichen Lösung.

                                  Ein Forum ist dafür da, Fragen zu stellen, oder sehe ich das falsch?

                                  HomoranH Nicht stören
                                  HomoranH Nicht stören
                                  Homoran
                                  Global Moderator Administrators
                                  schrieb am zuletzt editiert von
                                  #752

                                  @blessi sagte in Modbus adapter:

                                  Kann ich nicht an 2 Stellen Fragen stellen?

                                  kannst du schon, hat ja geklappt!

                                  @blessi sagte in Modbus adapter:

                                  Ein Forum ist dafür da, Fragen zu stellen, oder sehe ich das falsch?

                                  ist schon richtig, aber wenn jetzt in mehreren Threads untersciedliche Antworten / Antworten von unterschiedlichen Usern kommen, wird es sehr schnell chaotisch.

                                  kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                  der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                  1 Antwort Letzte Antwort
                                  0
                                  • K klassisch

                                    @blessi Hier gibt es Erfahrungen mit funktionierenden Konfigurationen: https://forum.iobroker.net/topic/55710/sdm120-sdm72-sdm630-modbus-rs485-stromzähler-w-lan-iobroker?_=1677138832377

                                    B Offline
                                    B Offline
                                    blessi
                                    schrieb am zuletzt editiert von
                                    #753

                                    @klassisch Moin,

                                    ich habe mir jetzt den Drehstromzähler SDM720DM-V2 sowie den Wandler USR-TCP232-304 bestellt.
                                    Wenn ich es richtig verstanden habe, klemme ich zwischen Zähler und Wandler A auf A, B auf B und G auf G, richtig?

                                    An dem Wandler kann ich auch mehrere SDM 720 anschließen, oder habe ich das falsch verstanden?

                                    Brauche ich noch etwas?

                                    Ich hoffe ich komme mit der Einrichtung klar 😉

                                    K 1 Antwort Letzte Antwort
                                    0
                                    • B blessi

                                      @klassisch Moin,

                                      ich habe mir jetzt den Drehstromzähler SDM720DM-V2 sowie den Wandler USR-TCP232-304 bestellt.
                                      Wenn ich es richtig verstanden habe, klemme ich zwischen Zähler und Wandler A auf A, B auf B und G auf G, richtig?

                                      An dem Wandler kann ich auch mehrere SDM 720 anschließen, oder habe ich das falsch verstanden?

                                      Brauche ich noch etwas?

                                      Ich hoffe ich komme mit der Einrichtung klar 😉

                                      K Offline
                                      K Offline
                                      klassisch
                                      Most Active
                                      schrieb am zuletzt editiert von
                                      #754

                                      @blessi Ja, 2 Zähler gehen. Vorher manuell über die Tasten und das Display die gleiche Baudraute einstellen und unterschiedliche Adressen.
                                      Generell A nach A und B nach B. Manchmal muß man auch kreuzen, weil die Definition verschieden interpretiert wird.

                                      B 1 Antwort Letzte Antwort
                                      0
                                      • K klassisch

                                        @blessi Ja, 2 Zähler gehen. Vorher manuell über die Tasten und das Display die gleiche Baudraute einstellen und unterschiedliche Adressen.
                                        Generell A nach A und B nach B. Manchmal muß man auch kreuzen, weil die Definition verschieden interpretiert wird.

                                        B Offline
                                        B Offline
                                        blessi
                                        schrieb am zuletzt editiert von
                                        #755

                                        @klassisch Gehen an dem Gateway maximal 2 oder auch mehr Zähler?

                                        K 1 Antwort Letzte Antwort
                                        0
                                        • B blessi

                                          @klassisch Gehen an dem Gateway maximal 2 oder auch mehr Zähler?

                                          K Offline
                                          K Offline
                                          klassisch
                                          Most Active
                                          schrieb am zuletzt editiert von
                                          #756

                                          @blessi Da gehen auch mehr. Jedem seine eigene Adresse manuell einstellen. Die Baudrate hochstellen und vielleicht nicht gar zu viele Werte abfragen, damit die Daten über den Bus gehen können.

                                          K 1 Antwort Letzte Antwort
                                          1
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          764

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe