  4. ESPHome: Wandfeuchte messen-Schimmel vermeiden+Anwendungen
122 Beiträge 6 Kommentatoren 27.1k Aufrufe 4 Beobachtet
  • K klassisch
    So, verstehe diese Form von embedded JS nicht wirklich und habe es jetzt mal mäßig quick aber sehr dirty umgeschrieben
    Edit: Quelle des Algo: http://www.TH80.de/
    /*  Calculate Humidity and moisture data **********************
     Calculations of Humidity and water content in air
     modifications of http://www.TH80.de/
    Purpose:
    * Input values:
      ** Temp: temperaure of air
      ** Hrel: humidity in air at the same location (measured by the same sensor) SHT35 or SHT85 recommende for precise data
      ** T_wall: wall temperature. measured e.g. by a contact thermometer. To minimize calculation errors, it is reommended, to locate the T/H sensor close to the wall and contact T-sensor
    * Output data:
      **  TH70 Air: temperature to acieve a relative humidity of 70%
      **  TH80 Air: temperature to acieve a relative humidity of 80%
      **  TH90 Air: temperature to acieve a relative humidity of 90%
      **  T_dew Air: temperature to achieve a relative humidity of 100% (dew point, TH100)
      **  H_abs Mass: of water in grams in 1 m³ of air
      **  H_standard: Value of the relative humidity @20°C (standardized humidity)
      **  P_vaporSatur: Current water vapor saturation pressure in Pa
      **  P_vapor: Current water vapor pressure in Pa
      **  H_wall: Current wall moisture: relative humidty @ T-wall.
      **  P_vaporSaturWall: vapor saturation pressure at T_wall
    const debugLogOn = true;
    const nameOfThisScript = name.split('.')[name.split('.').length - 1];
    // test Variables
    var Temp = 14;
    var Hrel = 8;
    var T_wall = 12;
    //=20.13°C humidity=56.55%
    // temperature=20.52°C humidity=55.44%
    // end test variables
    var Hrel = Hrel
    var P_vaporSatur;
    var P_vaporSaturWall;
    var P_vapor;
    var T_dew;
    var TH70;
    var TH80;
    var TH90;
    var H_abs;
    var H_standard;
    var H_wall;
    var P_vaporSaturRound;
    var P_vaporRound;
    var T_dewRound;
    var TH70Round;
    var	TH80Round;
    var	TH90Round;
    var H_absRound;
    var H_standardRound;
    var H_wallRound;
    function calculateHumidityValues() {
    		P_vaporSatur = 611*Math.pow(10,7.5*Temp/(237.3+Temp));
    		P_vaporSaturWall = 611*Math.pow(10,7.5*T_wall/(237.3+T_wall));
    		P_vapor = Hrel/100*P_vaporSatur;
    		T_dew = 237.3*Math.log(P_vapor/610.78)/Math.log(10)/(7.5-Math.log(P_vapor/610.78)/Math.log(10));
    		TH70 = 237.3*Math.log(P_vapor/(610.78*0.7))/Math.log(10)/(7.5-Math.log(P_vapor/(610.78*0.7))/Math.log(10));
    		TH80 = 237.3*Math.log(P_vapor/(610.78*0.8))/Math.log(10)/(7.5-Math.log(P_vapor/(610.78*0.8))/Math.log(10));
    		TH90 = 237.3*Math.log(P_vapor/(610.78*0.9))/Math.log(10)/(7.5-Math.log(P_vapor/(610.78*0.9))/Math.log(10));
    		H_abs = 1000*18.016/8314.3*P_vapor/(Temp+273.15);
    		H_standard = P_vaporSatur*Hrel/2340;
    		H_wall = (P_vapor / P_vaporSaturWall)*100;
    		P_vaporSaturRound = Math.round(P_vaporSatur);
    		P_vaporRound = Math.round(P_vapor);
    		T_dewRound = Math.round(T_dew*100)/100;
    		TH70Round = Math.round(TH70*100)/100;
    		TH80Round = Math.round(TH80*100)/100;
    		TH90Round = Math.round(TH90*100)/100;
    		H_absRound = Math.round(H_abs*100)/100;
    		H_standardRound = Math.round(H_standard*100)/100;
       		H_wallRound = Math.round(H_wall*100)/100;
    // start calculation using the predefined data
       calculateHumidityValues();
    // output
       if(debugLogOn)console.log('Temp: ' +Temp+';  Hrel: ' + Hrel + ';  T_wall: ' + T_wall);
       if(debugLogOn)console.log('T bei 70% ' + TH70Round);
       if(debugLogOn)console.log('T bei 80% ' + TH80Round);
       if(debugLogOn)console.log('T bei 90% ' + TH90Round);
       if(debugLogOn)console.log('T_dewRound: ' + T_dewRound);
       if(debugLogOn)console.log('Habs: ' + H_absRound);
       if(debugLogOn)console.log('H_standard ' + H_standardRound);
       if(debugLogOn)console.log('Saettigungsdampfdruck: ' + P_vaporSaturRound);
       if(debugLogOn)console.log('Partialdruck: ' + P_vaporRound);
       if(debugLogOn)console.log('H_wall: ' + H_wallRound);
    //end script
    Schätze mal, daß der PWM Dimmer um 100Hz hat.
    @klassisch sagte in ESPHome: Wandfeuchte messen - Schimmel vermeiden:
    Danke erstmal dafür, setze ich nachher mal um
    @opensourcenomad sagte in ESPHome: Wandfeuchte messen - Schimmel vermeiden:
    damit das Sterben zu verlangsamen finde ich sehr altruistisch
    so bin ich halt.
    Habe davon zuviel im Fachhandel erlebt, wo es inzwischen nur noch sehr schwer ist Händler zu finden.
    Herrn Bezos möchte ich nicht unbedingt unterstützen.
    der Homematic PWM-Dimmer hat eine Ausgangsfrequenz von ca. 400 Hz
    Danke dafür!
    • OpenSourceNomadO OpenSourceNomad
      @homoran said in ESPHome: Wandfeuchte messen - Schimmel vermeiden:
      bestellen mache ich aus Prinzip nur hier
      Wenn du bereits bist ein vielfaches zu zahlen damit das (immer) in fern Ost produzierte Teil einen extra Zwischenstopp in Bayern einlegt kannst du hier ein mosfet board (ohne esp!) für 5€ erstehen. 💰
      Zum Vergleich direkt aus dem Erzeugerland:
      Deine Konsequenz die (noch) existieren Zwischenhändler zu subventionieren und damit das Sterben zu verlangsamen finde ich sehr altruistisch.
      Ich habe nie Verstanden welchen Mehrwert ich habe von einem Zwischenhändler für das identische (⚠) Produkt mehr zu zahlen. Wenn irgendwie Möglich kaufe ich immer direkt vom Produzenten.
      Ist der hier
      https://de.elv.com/homematic-led-funk-dimmer-1-fach-12-24v-pwm-hm-lc-dim1pwm-cv-fuer-smart-home-hausautomation-099444
      Habe da keine Frequenz gefunden
      Im Forum berichtet ein Kunde von einem erkennbaren 200Hz flimmern
      ELV selber dazu:
      der Homematic PWM-Dimmer hat eine Ausgangsfrequenz von ca. 400 Hz. Dieses reicht in der Regel völlig aus, da Flimmern ab 200 Hz vom Menschen normalerweise nicht mehr wahrgenommen werden kann.
      Von den 60 Euronen für das Gerät waren wohl nach Personalkosten (und Gewinn) nur noch 2,5€ pro Stück über um die Hardware aus China einzukaufen (vorausgesetzt die Geräte werden überhaupt in DE zusammengeschraubt) 😬
      Werden sie, und zwar von mir
      • K klassisch
        Purpose:
        * Input values:
        * Output data:
        // test Variables
        var Temp = 14;
        var Hrel = 8;
        var T_wall = 12;
        var Hrel = Hrel
        var P_vaporSatur;
        var P_vapor;
        var T_dew;
        var TH70;
        var TH80;
        var TH90;
        var H_abs;
        var H_standard;
        var H_wall;
        var P_vaporRound;
        var T_dewRound;
        var TH70Round;
        var	TH80Round;
        var	TH90Round;
        var H_absRound;
        var H_wallRound;
        // output
        //end script
        ich hab es versucht noch dirtier zu machen:
        muss da bei der ID noch irgendwo ein .val oder so rein?
          K
          K
          klassisch
          @homoran var Temp = getState('DeineID').val;
          • K klassisch
            getState
            Danke - läuft!
            19:35:07.082	info	javascript.1 (6588) script.js.Wetter_und_Klima.Werkstatt_TP80: Taupunkt: 10.548477384785869
            19:35:07.083	info	javascript.1 (6588) script.js.Wetter_und_Klima.Werkstatt_TP80: Saettigungsdampfdruck: 2090.4541817975487
            19:35:07.083	info	javascript.1 (6588) script.js.Wetter_und_Klima.Werkstatt_TP80: Partialdruck: 1275.1770508965046
            19:35:07.083	info	javascript.1 (6588) script.js.Wetter_und_Klima.Werkstatt_TP80: Habs: 9.484498607491766
            19:35:07.083	info	javascript.1 (6588) script.js.Wetter_und_Klima.Werkstatt_TP80: T bei 80% 14.182271687551786
            19:35:07.083	info	javascript.1 (6588) script.js.Wetter_und_Klima.Werkstatt_TP80: T bei 70% 16.064102027198793
            dann will ich mal sehen, ob ich damit noch etwas meine js-Kenntnisse aufbessern kann. (z.B. DP anlegen und befüllen)
              getState
              Danke - läuft!
              K
              K
              klassisch
              @homoran Anlegen erst mal manuell über Admin. Beschreiben via
              setState('DeineId',variable);
              • K klassisch
                @klassisch wollte ich doch machen 😢
                DANKE!
                was ist denn habs?
                die Werte, die dabei rauskommen passen nicht zum Raumklima Skript.
                kann es z.B. sein, dass hier g/Cubicmeter und nicht g/kg gerechnet wird
                hier kommt 9,48 heraus, beim Lüftungsskript 7,6
                  DANKE!
                  was ist denn habs?
                  K
                  K
                  klassisch
                  @homoran Habs ist die Absolute Feuchte in g/m³. Die bevorzugte Einheit, weil man da den Luftdruck nicht braucht.
                  • K klassisch
                    @klassisch
                    Nochmals Danke für deine Unterstützung.
                    Hab es jetzt implementiert bekommen und hoffentlich auch den Trigger korrekt gesetzt.
                    Datenpunkte werden korrekt gefüllt und den offset des Raumsensors ("kalibriert" mit den neuen Senosren) hab ich auch drin. Werte passen jetzt mit dem Raumklima übereinander.
                    Jetzt wird es langsam unübersichtlich
                    Ausschnitt Werkstatt:
                    Der aw 70 liegt aber verdammt dicht an der Wandtemperatur.
                    Da muss ich mal mein Entfeuchter/Heizprogramm nochmal durchdenken.
                    EDIT:
                    @klassisch
                    hier mein Machwerk:
                    // Luftfeuchteberechnungen
                    // modifiziert nach https://www.pb-schilling.de/baubiologie/luftfeuchte-rechner/
                    // Testvariablen
                    var Temp = getState('hm-rpc.0.JEQ0046663.1.TEMPERATURE').val/*Klima Werkstatt:1 TEMPERATURE*/;
                    var Hrel = (getState('hm-rpc.0.JEQ0046663.1.HUMIDITY').val)-2.5/*Klima Werkstatt:1 HUMIDITY*/;
                    // end Testvariablen
                    Luftfeuchteberechnungen(Temp,Hrel);
                    function Luftfeuchteberechnungen(myTemp,myHrel){
                      Luftfeuchtevorbereitung(myTemp, myHrel);
                      taupunktTemperatur();
                      //if(debugLogOn)console.log('Taupunkt: ' + taupunktTemperatur());
                      wasserdampfSaettingungsdruck();
                      //if(debugLogOn)console.log('Saettigungsdampfdruck: ' + wasserdampfSaettingungsdruck());
                      wasserdampfTeildruck();
                      //if(debugLogOn)console.log('Partialdruck: ' + wasserdampfTeildruck());
                      wassergehaltLuft();
                      //if(debugLogOn)console.log('Habs: ' + wassergehaltLuft());
                      awWert80();
                      //if(debugLogOn)console.log('T bei 80% ' + awWert80());
                      awWert70();
                      //if(debugLogOn)console.log('T bei 70% ' + awWert70());
                       function Luftfeuchtevorbereitung( theta, phi) {
                         this.theta = theta;
                         this.phi = phi;
                         if (this.phi > 1) {
                           this.phi = this.phi / 100;
                         if (this.phi > 1) {
                           this.phi = 1;
                       function taupunktTemperatur() {
                         return Math.pow(this.phi, 0.1247) * (109.8 + this.theta) - 109.8;
                       function wasserdampfSaettingungsdruck() {
                         if (this.theta > 0) {
                           return 288.68 * Math.pow(1.098 + this.theta / 100, 8.02);
                         } else {
                           return 4.689 * Math.pow(1.486 + this.theta / 100, 12.3);
                       function wasserdampfTeildruck() {
                         return this.phi * wasserdampfSaettingungsdruck();
                       function wassergehaltLuft() {
                         return 216.7 * wasserdampfTeildruck() * 0.01 / (this.theta + 273.15);
                       function awWert80() {
                         var oben, unten;
                         oben = 237.3 * Math.log(611 * Math.pow(10, 7.5 * this.theta / (237.3 + this.theta) * this.phi) / 488.62) / Math.LN10;
                         unten = 7.5 - Math.log(611 * Math.pow(10, 7.5 * this.theta / (237.3 + this.theta) * this.phi) / 488.62) / Math.LN10;
                         return oben / unten;
                       function awWert70() {
                         var oben, unten;
                         oben = 237.8 * Math.log(wasserdampfTeildruck() / (610.78 * 0.7)) / Math.LN10;
                         unten = 7.5 - Math.log(wasserdampfTeildruck() / (610.78 * 0.7)) / Math.LN10;
                    setState('javascript.1.Raumklima.Raum.Werkstatt.DETAILS.aw70',Math.round(awWert70()*10)/10, true);
                    setState('javascript.1.Raumklima.Raum.Werkstatt.DETAILS.aw80',Math.round(awWert80()*10)/10, true);
                    on('javascript.1.Raumklima.Raum.Werkstatt.Taupunkt',Luftfeuchteberechnungen); // triggert bei Wertänderung;
                    //end script
                    • HomoranH
                      @klassisch
                      ich brauche doch nochmal deine Hilfe.
                      Entweder ich habe den Trigger nicht richtig gesetzt, oder da ist noch was falsch.
                      beim Scriptstart klappt alles, aber entweder die Triggersyntax passt nicht, was mich nicht wundern würde, oder ich rufe die falsche Funktion auf, oder in der Funktion fehlt was (vobereitung()).
                        @klassisch
                        K
                        K
                        klassisch
                        @homoran ich sehe nichts
                        • K klassisch
                          keinen Fehler oder nicht das Skript im Spoiler?
                            K
                            K
                            klassisch
                            schrieb am zuletzt editiert von klassisch
                            @homoran So, habe jetzt den Spoiler gefunden
                            on({id: 'javascript.1.Raumklima.Raum.Werkstatt.Taupunkt', change: "any"}, function() { // löst bei jeder Aktualisierung aus
                             Hrel = getState('hm-rpc.0.JEQ0046663.1.HUMIDITY').val - 2.5/*Klima Werkstatt:1 HUMIDITY*/;
                            • K klassisch
                              @klassisch danke!
                              und ich dachte ich hätte etwas mehr js gelernt 😢
                                @klassisch danke!
                                K
                                K
                                klassisch
                                @homoran Ich kratze da auch nur an der Oberfläche. Und gewisse Dinge plappere ich nach wie ein Papagei, ohne mich mal grundegend mit der Struktur beschäftigt zu haben. Das Triggern durch "on" gehört dazu
                                Warum triggerst Du eigentlich auf den Taupunkt, der ja bereits ein verarbeiteter Wert ist und nicht auf einen direkten Sensorwert wie z.B.
                                • K klassisch
                                  weil ich faul bin.
                                  die Änderung des Taupunktes beinhalter mögliche Änderungen von Temperatur und/oder Feuchte.
                                  Damit erschlage ich beides (denke ich zumindest)
                                  Das mit dem Papagei ist genau mein Thema. Aber ich muss es verstanden haben um nicht immer wieder irgendwo nachsehen zu müssen.
                                  Deswegen arbeite ich mit Blockly, weil ich nichtmal die Syntax hinbekomme.
                                  Inzwischen hat sich der Wert zumindest einmal geändert und getriggert!
                                    weil ich faul bin.
                                    K
                                    K
                                    klassisch
                                    @homoran sagte in ESPHome: Wandfeuchte messen - Schimmel vermeiden:
                                    Der HM-Sensor wird wohl eh beides gleichzeitig einliefern, vermute ich.
                                    Den Anspruch habe ich nicht an mich. Habe mir einen Spickzettel in Notepad++ aufgemacht, wo die häufigsten Dinge als Beispiele drin stehen und ein paar Links zur Doku.
                                    Für Grobschlosser-Programmierung braucht man gar nicht sooo viel.
                                    Und bei den recht seltenen und langsamen Brechnungen muß ich nicht wirklich optimieren. Habe ja nicht den Anspruch, Adapter-Entwickler zu sein.
                                    Habe mir auch deshalb ein i5-6300U Notebook, der nebenbei auch ioBroker macht, für 160 EUR incl. Windows gegönnt.
                                    Ich bekomme mit "Rules" gar nichts hin. Nicht gleich kapiert, sofort verworfen.
                                    Blockly hat den Spickzettel eingebaut. Das ist praktisch. Aber ich komme mit dem graphischen Zeug immer an die Grenzen. Das wird bei mir recht schnell unübersichtlich.
                                    Deshalb habe ich mich auf JS festgelegt. Da findet man auch viele Beispiele bei selfhtml und mediaevent.de
                                    Das sieht doch nach einem Erfolg aus! Glückwunsch!
                                    Man kann ja mit dem console.log notfalls mitverfolgen, was er tut.
                                    Dazu habe ich die constante debugLogOn eingeführt. Während der Entwicklung setze ich die auf true und wenn alles läuft auf false.
                                    • K klassisch
                                      ist großteils deine Leistung. ich hab nur die Rundung und die states eingebaut.
                                      Das mit dem Trigger ärgert mich jetzt.
                                      also entweder alles notwendige in einer Funktion (z.B. main()) und diese im Trigger aufrufen, oder im Zrigger innerhalb einer eigenen Funktion (??) alle notwendigen Schritte abarbeiten? Wobei ich diese Syntax nicht auf Anhieb zusammenbekomme.
                                      Irgendwann in diesem Leben will ich js können, so!
                                      und ich Idiot kommentiere sie aus, weil ich das nicht erkannt habe.
                                        K
                                        K
                                        klassisch
                                        @homoran Das on hat halt obrflächlich betrachtet eine blöde Syntax (für mich, der ich nach dem Papageienprinzip arbeite. Wenn man das richtig durchdringt, sieht das vielleicht anders aus. Aber lohnt sich dieser Einarbeitungsaufwand für die paar Zeilen Code, die ich schreibe?)
                                        Man könnte irgendwo ausserhalb des on Blocks eine Funktion definieren, die die Daten holt, die Umrechnung aufruft und dann die neuen Daten schreibt. Also alles, was jetzt im on Block steht in eine Funktion packen und dann im On-Block nur diese Funktion aufrufen. Vielleicht eleganter.
                                        Da es aber nur ein paar Zeilen sind, kann man es auch zwischen die {} des on Blocks schreiben. Das habe ich hier teils aus Bequemlichkeit gemacht teils um die Veränderung genauer zu zeigen.
                                        Könnte also auch so aussehen:
                                        function LuftfeuchteProzessierung(){
                                        on({id: 'hm-rpc.0.JEQ0046663.1.TEMPERATURE', change: "any"}, function() { // löst bei jeder Aktualisierung aus
                                          LuftfeuchteProzessierung();
                                        Viel wichtiger wäre es mir aber, Ids in Constante zu verfrachten, also zu abstrahieren, und aus dem Code wegzubekommen. Denn dadurch hat man weniger Geschäft, wenn man z.B. einen Sensor wechselt oder das Programm für einen anderen Raum modifiziert.
                                        Also in etwa so:
                                        const temperatureSensorId = 'hm-rpc.0.JEQ0046663.1.TEMPERATURE';
                                        on({id: temperatureSensorId, change: "any"}, function() { // löst bei jeder Aktualisierung aus
                                        • michl75M
                                          michl75M
                                          michl75
                                          schrieb am zuletzt editiert von michl75
                                          Guten Morgen, habe nur eben kurz drübergelesen da Zeitdruck habe... aber letzten Endes gehts hier doch um feuchte in und auf der Mauer sowie Luft und dementsprechende Ablagerung auf kalte Bauteiloberflächen.
                                          kurz zur Berechnung - schaut euch das mal an... das ist Bauphysik und danach machen:
                                          https://building-physics.net/webfm_send/439
                                          und vorallem das:
                                          https://building-physics.net/webfm_send/767
                                          (Dies als Beispiel, gibt viele andere Ausarbeitungen von TU's)
                                          Wie gesagt, eben nur drübergeflogen... aber mal den Link der PDF's anschauen
                                          Viel Erfolg
                                          84.1k