  4. Modbus Adapter received answer for wrong ID 2, expected 1

NEWS

  • Jahresrückblick 2025 – unser neuer Blogbeitrag ist online! ✨
    BluefoxB
    Bluefox
    17
    1
    3.2k

  • Neuer Blogbeitrag: Monatsrückblick - Dezember 2025 🎄
    BluefoxB
    Bluefox
    13
    1
    1.1k

  • Weihnachtsangebot 2025! 🎄
    BluefoxB
    Bluefox
    25
    1
    2.4k

Modbus Adapter received answer for wrong ID 2, expected 1

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
20 Beiträge 7 Kommentatoren 165 Aufrufe 6 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • HF_SPSlerH HF_SPSler

    Hallo,

    ich habe heute den Modbus Adapter auf 7.0.6 geupdatet und ihn anschließend mit der debugausgabe gestartet. Dabei ist mir aufgefallen, dass beim Polling der Slaves zwar die Daten ordnungsgemäß abgeholt werden jedoch der Eintrag "received answer for wrong ID 2, expected 1" für fast jeden Slave mit in das log geschrieben wird.

    modbus.4 	2026-02-13 18:23:29.903	debug	[DevID_30/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:29.902	debug	received answer for wrong ID 30, expected 1
    modbus.4	2026-02-13 18:23:29.880	debug	[DevID_30/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:29.880	debug	[DevID_30] Poll start ---------------------
    modbus.4	2026-02-13 18:23:29.103	debug	[DevID_24/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:29.102	debug	received answer for wrong ID 24, expected 1
    modbus.4	2026-02-13 18:23:29.079	debug	[DevID_24/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:29.078	debug	[DevID_24] Poll start ---------------------
    modbus.4	2026-02-13 18:23:28.303	debug	[DevID_23/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:28.303	debug	received answer for wrong ID 23, expected 1
    modbus.4	2026-02-13 18:23:28.281	debug	[DevID_23/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:28.281	debug	[DevID_23] Poll start ---------------------
    modbus.4	2026-02-13 18:23:27.504	debug	[DevID_22/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:27.503	debug	received answer for wrong ID 22, expected 1
    modbus.4	2026-02-13 18:23:27.482	debug	[DevID_22/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:27.481	debug	[DevID_22] Poll start ---------------------
    modbus.4	2026-02-13 18:23:26.704	debug	[DevID_21/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:26.704	debug	received answer for wrong ID 21, expected 1
    modbus.4	2026-02-13 18:23:26.682	debug	[DevID_21/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:26.681	debug	[DevID_21] Poll start ---------------------
    modbus.4	2026-02-13 18:23:25.905	debug	[DevID_20/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:25.904	debug	received answer for wrong ID 20, expected 1
    modbus.4	2026-02-13 18:23:25.820	debug	[DevID_20/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:25.819	debug	[DevID_20] Poll start ---------------------
    modbus.4	2026-02-13 18:23:25.042	debug	[DevID_3/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:25.041	debug	received answer for wrong ID 3, expected 1
    modbus.4	2026-02-13 18:23:25.020	debug	[DevID_3/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:25.019	debug	[DevID_3] Poll start ---------------------
    modbus.4	2026-02-13 18:23:24.242	debug	[DevID_2/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:24.241	debug	received answer for wrong ID 2, expected 1
    modbus.4	2026-02-13 18:23:24.217	debug	[DevID_2/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:24.216	debug	[DevID_2] Poll start ---------------------
    modbus.4	2026-02-13 18:23:23.441	debug	[DevID_1/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:23.411	debug	[DevID_1/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:23.410	debug	[DevID_1] Poll start ---------------------
    modbus.4	2026-02-13 18:23:19.635	debug	[DevID_30/inputRegs] Poll address 0 DONE
    modbus.4	2026-02-13 18:23:19.634	debug	received answer for wrong ID 30, expected 1
    modbus.4	2026-02-13 18:23:19.611	debug	[DevID_30/inputRegs] Poll address 0 - 6 registers
    modbus.4	2026-02-13 18:23:19.611	debug	[DevID_30] Poll start ---------------------
    

    Verwendet wird Iobroker auf einem Raspi4 8GB. Der Adapter läuft in mehreren Instanzen um zum Einen via Modbus-TCP die Victron PV Anlage auszulesen und via Modbus-RTU 9 Slaves auszulesen die in verschiedenen Räumen Klimadaten aufnehmen.

    Jetzt würde mich natürlich mal interessieren, warum diese Meldung ins Log geschrieben wird?

    fuzzy1955F Online
    fuzzy1955F Online
    fuzzy1955
    schrieb am zuletzt editiert von fuzzy1955
    #2

    @HF_SPSler sagte in Modbus Adapter received answer for wrong ID 2, expected 1:

    ich habe heute den Modbus Adapter auf 7.0.6 geupdatet

    Hi,
    bei mir bringt auch das Update auf den Modbus-Adapter v7.0.6 Fehler beim Waveshare Modbus ETH 8xRelay:

    modbus.1
    2026-02-14 08:14:14.615	warn	[DevID_1] Some register types failed but continuing: 1/4 errors
    modbus.1
    2026-02-14 08:14:14.114	warn	[DevID_1/coils] Block 0-15: {}
    modbus.1
    2026-02-14 08:14:14.114	debug	Received pdu describes an error.
    modbus.1
    2026-02-14 08:14:14.107	debug	[DevID_1/coils] Poll address 0 - 16 bits
    modbus.1
    2026-02-14 08:14:14.107	debug	[DevID_1] Poll start ---------------------
    

    f6ef7ead-e3ad-437c-a9de-9538c39fb546-image.png

    Die Relais schalten korrekt, aber im Log stehen die Fehler, obwohl ich nur das Coils-Register verwenden. Was kann die Ursache dafür sein? Vorweg danke für eure Unterstützung!

    [Nachtrag]
    37b2b8de-19a4-4a3f-9758-e320eff64b44-image.png
    afc69517-bc85-41dc-a1a1-8e26725e8cfc-image.png
    bae561cb-7492-4022-baf7-cb1aa0480078-image.png
    a86f1273-c715-4701-ad9b-64cfa9a16276-image.png

    Raspberry PI5 mit Linux Debian 13, IoBroker v7.7.22, VIS-2, MariaDB (MySQL)
    Shellies: 1G4, 1MiniG3, PlusI4DC, PlusPlugS, Pro0110PM, ProSmoke. Modbus: Waveshare Relay 8 Channels, Waveshare RS485-TO-ETH.
    PV: 10 kWp Module, 2 x Deye WR SUN-10K, 3 x 10 kWh MeritSun LiFe Speicher, KEBA P30 Wallbox, Fronius Wattpilot home 11

    1 Antwort Letzte Antwort
    0
    • WinniW Offline
      WinniW Offline
      Winni
      Most Active
      schrieb am zuletzt editiert von
      #3
      modbus.1
      2026-02-14 08:14:14.615	warn	[DevID_1] Some register types failed but continuing: 1/4 errors
      

      Bei mir genauso. Ich hatte die Fehlermeldung nach dem Update auch. Nachdem das aber meine IDM AERO ALM 6-15 Wärmepumpe ist und das bisher perfekt gelaufen ist,wollte ich kein Risiko eingehen und bin nur zurück auf die 6.4.0. Damit war die Fehlermeldung wieder verschwunden. Vielleicht interessant, ich habe noch 2 weitere Instanzen laufen für SMA Wechelrichter SB4000/5000 TL-21, da kam keine Fehlermeldung.

      Es gibt nicht Gutes. Außer man tut es. Erich Kästner

      WinniW 1 Antwort Letzte Antwort
      0
      • mcm1957M Online
        mcm1957M Online
        mcm1957
        schrieb am zuletzt editiert von
        #4

        Wenn es Probleme gibt bitte ein Issue loggen.

        Entwicklung u Betreuung: envertech-pv, hoymiles-ms, ns-client, pid, snmp Adapter;
        Support Repositoryverwaltung.

        Wer Danke sagen will, kann nen Kaffee spendieren: https://paypal.me/mcm1957atiobroker

        LESEN - gute Forenbeitrage

        1 Antwort Letzte Antwort
        0
        • WinniW Winni
          modbus.1
          2026-02-14 08:14:14.615	warn	[DevID_1] Some register types failed but continuing: 1/4 errors
          

          Bei mir genauso. Ich hatte die Fehlermeldung nach dem Update auch. Nachdem das aber meine IDM AERO ALM 6-15 Wärmepumpe ist und das bisher perfekt gelaufen ist,wollte ich kein Risiko eingehen und bin nur zurück auf die 6.4.0. Damit war die Fehlermeldung wieder verschwunden. Vielleicht interessant, ich habe noch 2 weitere Instanzen laufen für SMA Wechelrichter SB4000/5000 TL-21, da kam keine Fehlermeldung.

          WinniW Offline
          WinniW Offline
          Winni
          Most Active
          schrieb am zuletzt editiert von Winni
          #5

          Ich glaube ich konnte das Problem lösen. Ich hatte einen Datenpunkt unter "Diskrete Eingänge" aktiviert ohne weitere Parameter anzugeben. War wohl irgendwann aus Versehen. Die neue Version hat das bemerkt und angemeckert, der älteren war das wohl egal. Ich habe das korrigiert und jetzt läuft der Adapter wie er soll. 😀

          Edit: Ich meine das Problem dieser Fehlermeldung:

          modbus.1
          2026-02-14 08:14:14.615	warn	[DevID_1] Some register types failed but continuing: 1/4 errors
          

          Es gibt nicht Gutes. Außer man tut es. Erich Kästner

          1 Antwort Letzte Antwort
          0
          • D Online
            D Online
            darkblu
            schrieb am zuletzt editiert von darkblu
            #6

            Ich habe die gleiche Fehlermeldung mit ebenfalls 7.0.6:

            2026-02-14 16:56:29.082	warn	[DevID_247] Some register types failed but continuing: 1/4 errors
            

            wüsste aber nicht, wo etwas falsches oder fehlendes sein soll.

            Demnach müsste ich jetzt jeden Eintrag der Reihe nach aus meinen Holding Registern und Diskreten Ausgängen löschen um zu sehen, welcher der fehlerhafte ist ?

            Die Muße habe ich gerade nicht.

            Ich komme von 6.3.2, da war auch alles i.O.

            Raspi 4, 4GB für Influxdb 1.8 und Grafana
            Raspi 5, 8 GB für ioBroker

            mcm1957M DolomitiD 2 Antworten Letzte Antwort
            0
            • D darkblu

              Ich habe die gleiche Fehlermeldung mit ebenfalls 7.0.6:

              2026-02-14 16:56:29.082	warn	[DevID_247] Some register types failed but continuing: 1/4 errors
              

              wüsste aber nicht, wo etwas falsches oder fehlendes sein soll.

              Demnach müsste ich jetzt jeden Eintrag der Reihe nach aus meinen Holding Registern und Diskreten Ausgängen löschen um zu sehen, welcher der fehlerhafte ist ?

              Die Muße habe ich gerade nicht.

              Ich komme von 6.3.2, da war auch alles i.O.

              mcm1957M Online
              mcm1957M Online
              mcm1957
              schrieb am zuletzt editiert von mcm1957
              #7

              Ich komme von 6.3.2, da war auch alles i.O.

              Wenn es die selbe Ursache ist war das in 6.x.x auch NICHT in Ordnung. Es wurde nur der Fehler nicht entdeckt. :-).

              Du kannst aber auch einfach nicht in log schaun. Dann ist ja weiter alles ok. :-):-)

              Entwicklung u Betreuung: envertech-pv, hoymiles-ms, ns-client, pid, snmp Adapter;
              Support Repositoryverwaltung.

              Wer Danke sagen will, kann nen Kaffee spendieren: https://paypal.me/mcm1957atiobroker

              LESEN - gute Forenbeitrage

              1 Antwort Letzte Antwort
              0
              • WinniW Offline
                WinniW Offline
                Winni
                Most Active
                schrieb am zuletzt editiert von
                #8

                Oder mal die Datenpunkte anschauen. Ist da einer der nicht aktualisiert ist, bzw. wo N/A drin steht?

                Es gibt nicht Gutes. Außer man tut es. Erich Kästner

                1 Antwort Letzte Antwort
                1
                • HF_SPSlerH Offline
                  HF_SPSlerH Offline
                  HF_SPSler
                  schrieb am zuletzt editiert von
                  #9

                  Jetzt haben sich ja einige mit hier an das Thema gehängt, die aber, so verstehe ich das, andere Probleme haben. Wie sieht es denn mit meinem Issue aus :-)

                  Da hänge ich immer noch bei:

                  modbus.4 	2026-02-13 18:23:29.903	debug	[DevID_30/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:29.902	debug	received answer for wrong ID 30, expected 1
                  modbus.4	2026-02-13 18:23:29.880	debug	[DevID_30/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:29.880	debug	[DevID_30] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:29.103	debug	[DevID_24/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:29.102	debug	received answer for wrong ID 24, expected 1
                  modbus.4	2026-02-13 18:23:29.079	debug	[DevID_24/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:29.078	debug	[DevID_24] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:28.303	debug	[DevID_23/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:28.303	debug	received answer for wrong ID 23, expected 1
                  modbus.4	2026-02-13 18:23:28.281	debug	[DevID_23/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:28.281	debug	[DevID_23] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:27.504	debug	[DevID_22/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:27.503	debug	received answer for wrong ID 22, expected 1
                  modbus.4	2026-02-13 18:23:27.482	debug	[DevID_22/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:27.481	debug	[DevID_22] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:26.704	debug	[DevID_21/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:26.704	debug	received answer for wrong ID 21, expected 1
                  modbus.4	2026-02-13 18:23:26.682	debug	[DevID_21/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:26.681	debug	[DevID_21] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:25.905	debug	[DevID_20/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:25.904	debug	received answer for wrong ID 20, expected 1
                  modbus.4	2026-02-13 18:23:25.820	debug	[DevID_20/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:25.819	debug	[DevID_20] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:25.042	debug	[DevID_3/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:25.041	debug	received answer for wrong ID 3, expected 1
                  modbus.4	2026-02-13 18:23:25.020	debug	[DevID_3/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:25.019	debug	[DevID_3] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:24.242	debug	[DevID_2/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:24.241	debug	received answer for wrong ID 2, expected 1
                  modbus.4	2026-02-13 18:23:24.217	debug	[DevID_2/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:24.216	debug	[DevID_2] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:23.441	debug	[DevID_1/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:23.411	debug	[DevID_1/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:23.410	debug	[DevID_1] Poll start ---------------------
                  modbus.4	2026-02-13 18:23:19.635	debug	[DevID_30/inputRegs] Poll address 0 DONE
                  modbus.4	2026-02-13 18:23:19.634	debug	received answer for wrong ID 30, expected 1
                  modbus.4	2026-02-13 18:23:19.611	debug	[DevID_30/inputRegs] Poll address 0 - 6 registers
                  modbus.4	2026-02-13 18:23:19.611	debug	[DevID_30] Poll start ---------------------
                  

                  S7 1214 (Master) + Logo!8(Slave Erdgeschoss) + Logo!8 (Slave Obergeschoss) + S7 1214 (Slave Garage/Nebengebäude)

                  HomoranH 1 Antwort Letzte Antwort
                  0
                  • HF_SPSlerH HF_SPSler

                    Jetzt haben sich ja einige mit hier an das Thema gehängt, die aber, so verstehe ich das, andere Probleme haben. Wie sieht es denn mit meinem Issue aus :-)

                    Da hänge ich immer noch bei:

                    modbus.4 	2026-02-13 18:23:29.903	debug	[DevID_30/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:29.902	debug	received answer for wrong ID 30, expected 1
                    modbus.4	2026-02-13 18:23:29.880	debug	[DevID_30/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:29.880	debug	[DevID_30] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:29.103	debug	[DevID_24/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:29.102	debug	received answer for wrong ID 24, expected 1
                    modbus.4	2026-02-13 18:23:29.079	debug	[DevID_24/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:29.078	debug	[DevID_24] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:28.303	debug	[DevID_23/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:28.303	debug	received answer for wrong ID 23, expected 1
                    modbus.4	2026-02-13 18:23:28.281	debug	[DevID_23/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:28.281	debug	[DevID_23] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:27.504	debug	[DevID_22/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:27.503	debug	received answer for wrong ID 22, expected 1
                    modbus.4	2026-02-13 18:23:27.482	debug	[DevID_22/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:27.481	debug	[DevID_22] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:26.704	debug	[DevID_21/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:26.704	debug	received answer for wrong ID 21, expected 1
                    modbus.4	2026-02-13 18:23:26.682	debug	[DevID_21/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:26.681	debug	[DevID_21] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:25.905	debug	[DevID_20/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:25.904	debug	received answer for wrong ID 20, expected 1
                    modbus.4	2026-02-13 18:23:25.820	debug	[DevID_20/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:25.819	debug	[DevID_20] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:25.042	debug	[DevID_3/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:25.041	debug	received answer for wrong ID 3, expected 1
                    modbus.4	2026-02-13 18:23:25.020	debug	[DevID_3/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:25.019	debug	[DevID_3] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:24.242	debug	[DevID_2/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:24.241	debug	received answer for wrong ID 2, expected 1
                    modbus.4	2026-02-13 18:23:24.217	debug	[DevID_2/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:24.216	debug	[DevID_2] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:23.441	debug	[DevID_1/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:23.411	debug	[DevID_1/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:23.410	debug	[DevID_1] Poll start ---------------------
                    modbus.4	2026-02-13 18:23:19.635	debug	[DevID_30/inputRegs] Poll address 0 DONE
                    modbus.4	2026-02-13 18:23:19.634	debug	received answer for wrong ID 30, expected 1
                    modbus.4	2026-02-13 18:23:19.611	debug	[DevID_30/inputRegs] Poll address 0 - 6 registers
                    modbus.4	2026-02-13 18:23:19.611	debug	[DevID_30] Poll start ---------------------
                    
                    HomoranH Nicht stören
                    HomoranH Nicht stören
                    Homoran
                    Global Moderator Administrators
                    schrieb am zuletzt editiert von
                    #10

                    @HF_SPSler sagte in Modbus Adapter received answer for wrong ID 2, expected 1:

                    Wie sieht es denn mit meinem Issue aus :-)

                    hast du ein Issue suf Github erstellt?
                    dann kommt auch da die Antwort

                    Hier hab ich noch keine (fehlerhafte) Konfiguration von dir gesehen

                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                    1 Antwort Letzte Antwort
                    0
                    • D darkblu

                      Ich habe die gleiche Fehlermeldung mit ebenfalls 7.0.6:

                      2026-02-14 16:56:29.082	warn	[DevID_247] Some register types failed but continuing: 1/4 errors
                      

                      wüsste aber nicht, wo etwas falsches oder fehlendes sein soll.

                      Demnach müsste ich jetzt jeden Eintrag der Reihe nach aus meinen Holding Registern und Diskreten Ausgängen löschen um zu sehen, welcher der fehlerhafte ist ?

                      Die Muße habe ich gerade nicht.

                      Ich komme von 6.3.2, da war auch alles i.O.

                      DolomitiD Offline
                      DolomitiD Offline
                      Dolomiti
                      schrieb am zuletzt editiert von
                      #11

                      @darkblu sagte in Modbus Adapter received answer for wrong ID 2, expected 1:

                      Ich habe die gleiche Fehlermeldung mit ebenfalls 7.0.6:

                      2026-02-14 16:56:29.082	warn	[DevID_247] Some register types failed but continuing: 1/4 errors
                      

                      wüsste aber nicht, wo etwas falsches oder fehlendes sein soll.

                      Demnach müsste ich jetzt jeden Eintrag der Reihe nach aus meinen Holding Registern und Diskreten Ausgängen löschen um zu sehen, welcher der fehlerhafte ist ?

                      Die Muße habe ich gerade nicht.

                      Ich komme von 6.3.2, da war auch alles i.O.

                      Ich habe auch das Problem. Die Warnungen gingen erste weg nachdem ich alle DI bis auf einen gelöscht habe.

                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.
                      Intel N100 (32GB,256GB SSD), Proxmox -> Debian 12 in VM (Master) + Debian 12 in CT (Test) + Debmatic, HM-Aktoren, Wago 750-880, Shelly, Zigbee

                      1 Antwort Letzte Antwort
                      0
                      • D Online
                        D Online
                        darkblu
                        schrieb am zuletzt editiert von darkblu
                        #12

                        @dolomiti ,Was sind denn DI ? 🤔

                        Raspi 4, 4GB für Influxdb 1.8 und Grafana
                        Raspi 5, 8 GB für ioBroker

                        HomoranH 1 Antwort Letzte Antwort
                        0
                        • D darkblu

                          @dolomiti ,Was sind denn DI ? 🤔

                          HomoranH Nicht stören
                          HomoranH Nicht stören
                          Homoran
                          Global Moderator Administrators
                          schrieb am zuletzt editiert von
                          #13

                          @darkblu Digital Inputs

                          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                          1 Antwort Letzte Antwort
                          0
                          • DolomitiD Offline
                            DolomitiD Offline
                            Dolomiti
                            schrieb am zuletzt editiert von
                            #14

                            @darkblu Digital Inputs

                            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.
                            Intel N100 (32GB,256GB SSD), Proxmox -> Debian 12 in VM (Master) + Debian 12 in CT (Test) + Debmatic, HM-Aktoren, Wago 750-880, Shelly, Zigbee

                            1 Antwort Letzte Antwort
                            0
                            • D Online
                              D Online
                              darkblu
                              schrieb am zuletzt editiert von
                              #15

                              Ok, Danke
                              Du hast also alle Register und/oder Coils bis auf einen gelöscht ?
                              Dann leb ich lieber erstmal mit der Fehlermeldung.

                              Raspi 4, 4GB für Influxdb 1.8 und Grafana
                              Raspi 5, 8 GB für ioBroker

                              DolomitiD 1 Antwort Letzte Antwort
                              0
                              • D darkblu

                                Ok, Danke
                                Du hast also alle Register und/oder Coils bis auf einen gelöscht ?
                                Dann leb ich lieber erstmal mit der Fehlermeldung.

                                DolomitiD Offline
                                DolomitiD Offline
                                Dolomiti
                                schrieb am zuletzt editiert von
                                #16

                                @darkblu
                                Ja, war auf meinem Testsystem zum eingrenzen des Problems. Ich bleibe erstmal auf 6.3.2 bzw. 6.4.0.
                                Mal schauen ob ich einen Wireshark-Mitschnitt mache um das Problem zu finden.

                                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.
                                Intel N100 (32GB,256GB SSD), Proxmox -> Debian 12 in VM (Master) + Debian 12 in CT (Test) + Debmatic, HM-Aktoren, Wago 750-880, Shelly, Zigbee

                                1 Antwort Letzte Antwort
                                0
                                • WinniW Offline
                                  WinniW Offline
                                  Winni
                                  Most Active
                                  schrieb am zuletzt editiert von
                                  #17

                                  @darkblu @dolomiti habt ihr die Einstellung bei der 7.0.6 gesehen?
                                  1000018120.jpg
                                  Mir ist die unter der 6.x nicht aufgefallen. Probiert doch mal aus ein Häkchen zu setzen, vielleicht ist die Fehlermeldung dann weg. Wäre dann eine Lösung bis die wirkliche Ursache gefunden ist.

                                  Es gibt nicht Gutes. Außer man tut es. Erich Kästner

                                  fuzzy1955F DolomitiD 2 Antworten Letzte Antwort
                                  0
                                  • WinniW Winni

                                    @darkblu @dolomiti habt ihr die Einstellung bei der 7.0.6 gesehen?
                                    1000018120.jpg
                                    Mir ist die unter der 6.x nicht aufgefallen. Probiert doch mal aus ein Häkchen zu setzen, vielleicht ist die Fehlermeldung dann weg. Wäre dann eine Lösung bis die wirkliche Ursache gefunden ist.

                                    fuzzy1955F Online
                                    fuzzy1955F Online
                                    fuzzy1955
                                    schrieb am zuletzt editiert von
                                    #18

                                    @Winni sagte in Modbus Adapter received answer for wrong ID 2, expected 1:

                                    Mir ist die unter der 6.x nicht aufgefallen. Probiert doch mal aus ein Häkchen zu setzen

                                    Hab ich versucht. Das hilft nichts.

                                    Raspberry PI5 mit Linux Debian 13, IoBroker v7.7.22, VIS-2, MariaDB (MySQL)
                                    Shellies: 1G4, 1MiniG3, PlusI4DC, PlusPlugS, Pro0110PM, ProSmoke. Modbus: Waveshare Relay 8 Channels, Waveshare RS485-TO-ETH.
                                    PV: 10 kWp Module, 2 x Deye WR SUN-10K, 3 x 10 kWh MeritSun LiFe Speicher, KEBA P30 Wallbox, Fronius Wattpilot home 11

                                    1 Antwort Letzte Antwort
                                    0
                                    • WinniW Winni

                                      @darkblu @dolomiti habt ihr die Einstellung bei der 7.0.6 gesehen?
                                      1000018120.jpg
                                      Mir ist die unter der 6.x nicht aufgefallen. Probiert doch mal aus ein Häkchen zu setzen, vielleicht ist die Fehlermeldung dann weg. Wäre dann eine Lösung bis die wirkliche Ursache gefunden ist.

                                      DolomitiD Offline
                                      DolomitiD Offline
                                      Dolomiti
                                      schrieb am zuletzt editiert von
                                      #19

                                      @Winni sagte in Modbus Adapter received answer for wrong ID 2, expected 1:

                                      @darkblu @dolomiti habt ihr die Einstellung bei der 7.0.6 gesehen?
                                      1000018120.jpg
                                      Mir ist die unter der 6.x nicht aufgefallen. Probiert doch mal aus ein Häkchen zu setzen, vielleicht ist die Fehlermeldung dann weg. Wäre dann eine Lösung bis die wirkliche Ursache gefunden ist.

                                      Hat bei mir auch nicht geholfen. V8.0.0 war bei mir die Lösung

                                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.
                                      Intel N100 (32GB,256GB SSD), Proxmox -> Debian 12 in VM (Master) + Debian 12 in CT (Test) + Debmatic, HM-Aktoren, Wago 750-880, Shelly, Zigbee

                                      1 Antwort Letzte Antwort
                                      1
                                      • D Online
                                        D Online
                                        darkblu
                                        schrieb am zuletzt editiert von
                                        #20

                                        Kann ich auch bestätigen, Version 8.0.0 brachte die Lösung.
                                        Seit dem keine Fehlermeldung mehr.

                                        Raspi 4, 4GB für Influxdb 1.8 und Grafana
                                        Raspi 5, 8 GB für ioBroker

                                        1 Antwort Letzte Antwort
                                        1
                                        Antworten
                                        • In einem neuen Thema antworten
                                        Anmelden zum Antworten
                                        • Älteste zuerst
                                        • Neuste zuerst
                                        • Meiste Stimmen


                                        Support us

                                        ioBroker
                                        Community Adapters
                                        Donate
                                        FAQ Cloud / IOT
                                        HowTo: Node.js-Update
                                        HowTo: Backup/Restore
                                        Downloads
                                        BLOG

                                        547

                                        Online

                                        32.7k

                                        Benutzer

                                        82.3k

                                        Themen

                                        1.3m

                                        Beiträge
                                        Community
                                        Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                        ioBroker Community 2014-2025
                                        logo
                                        • Anmelden

                                        • Du hast noch kein Konto? Registrieren

                                        • Anmelden oder registrieren, um zu suchen
                                        • Erster Beitrag
                                          Letzter Beitrag
                                        0
                                        • Home
                                        • Aktuell
                                        • Tags
                                        • Ungelesen 0
                                        • Kategorien
                                        • Unreplied
                                        • Beliebt
                                        • GitHub
                                        • Docu
                                        • Hilfe