      wendy2702 @darkblu last edited by

      @darkblu So wie ich das sehe gibt es kein Coil "48" was genau deiner Meldung im Log entsprechen würde

      8f27a559-55b2-4174-bd06-b1519fe7e13d-grafik.png

      Hier geht es bis 39 und dann erst wieder bei 56 weiter.

      K 1 Reply Last reply Reply Quote 0
      • K
        klaus131079 @wendy2702 last edited by

        @wendy2702 said in Trovis 5573-1:

        @darkblu So wie ich das sehe gibt es kein Coil "48" was genau deiner Meldung im Log entsprechen würde

        8f27a559-55b2-4174-bd06-b1519fe7e13d-grafik.png

        Hier geht es bis 39 und dann erst wieder bei 56 weiter.

        Vielen Dank für deine Hilfe, nach viel Herumprobieren habe ich es nun geschafft die Coils für meine Pumpen auszulesen. Ich verstehe folgendes nicht, ich muss z.B im Iobroker
        Coil 54 angeben, damit am trovis das Coil 56 (UP1) ausgelesen wird, oder
        Coil 51 angeben, damit am trovis das Coil 59 (SLP) ausgelesen wird.

        Warum kann man da nicht direkt Coil 56 / 59 im iobroker angeben damit auch 56 / 59 ausgelesen wird? (vielleicht fehlt noch das nötige Wissen:-))
        danke LG Klaus

        D 1 Reply Last reply Reply Quote 0
        • D
          darkblu @klaus131079 last edited by

          @klaus131079 ,
          die Coils und Register wurden ja von Tom vor einigen Jahren ausgelesen und entstammen keiner offiziellen Doku.
          Vielleicht liegt es daran, who knows.

          Aber schön, dass du das rausgefunden hast.
          Könntest du mir noch einen Screenshot deiner Modbus Instanz hier reinstellen ?
          Danke

          K 1 Reply Last reply Reply Quote 0
          • K
            klaus131079 @darkblu last edited by

            @darkblu

            Danke, die Coils/Register von Tom sind, denke ich korrekt, ich muss nur in der Modbus-instanz tricksen, damit die richtigen Adressen ausgelesen werden:
            z.B Damit Coil 4 (Sammelebenbit) ausgelesen wird, muss ich Adresse 11 angeben (?), siehe:
            7eeb0128-41c4-4594-98cc-208acb31c9c1-grafik.png

            Danke, Anbei ein paar weitere screenshots von der Modbus-Instanz:
            5adf7641-ec4d-4a91-9b68-d287a234542b-grafik.png

            1137bb50-b374-44de-a0aa-01af84c09cb2-grafik.png

            wendy2702 S 2 Replies Last reply Reply Quote 1
            • wendy2702
              wendy2702 @klaus131079 last edited by

              @klaus131079 Das liegt wahrscheinlich an dem Haken bei „Use Aliases“

              K 1 Reply Last reply Reply Quote 0
              • K
                klaus131079 @wendy2702 last edited by

                @wendy2702
                in der Tat, danke, "Use Aliases" weggenommen, und jetzt entspricht die Coil-nummer auch dem, was tatsächlich abegefragt wird. Vielen Danke. Anbei meine modbus adapter einstellungen, mit dem die Lösung jetzt gut funktioniert:
                f16c973d-37c5-42cd-bf3c-7861eb87557e-grafik.png

                D 1 Reply Last reply Reply Quote 0
                • D
                  darkblu @klaus131079 last edited by darkblu

                  @klaus131079 , @wendy2702
                  Hallo, heute ist mein Elfin EW11A angekommen und ich habe mich sofort daran gemacht den Trovis in den ioBroker zu bekommen.
                  Leider wird die Modbusinstanz nur für ca. 5 Sekunden grün, danach wieder gelb.
                  Ich habe die allgemeinen Einstellungen genauso gemacht wie @klaus131079 .
                  Folgende Fehler und Warnungen bekomme ich:
                  FundW.png

                  In den paar Sekunden wo der Adapter grün ist, kann ich sehen, dass mein Elfin mit dem ioBroker verbunden ist und auch
                  etwas empfängt, scheinbar aber nix sendet:
                  Elfin.png

                  @klaus131079 , ich kann in meiner Trovis 5573 auch gar nicht die Baudrate verändern, auch in der BA gibt es diesen Punkt gar nicht.
                  Geht das bei deiner 5573 ?
                  Darum habe ich den Elfin auf 9600 eingestellt, gut ich habe natürlich beides probiert - erfolglos.

                  Hier noch die Modbus Einstellungen:
                  mbe.png

                  Hat jemand einen Tipp für mich ?
                  Ich hatte mir das irgendwie einfacher vorgestellt 😞

                  wendy2702 1 Reply Last reply Reply Quote 0
                  • wendy2702
                    wendy2702 @darkblu last edited by

                    @darkblu sagte in Trovis 5573-1:

                    Elfin EW11A

                    Was ist das?

                    D 1 Reply Last reply Reply Quote 0
                    • D
                      darkblu @wendy2702 last edited by

                      @wendy2702

                      Serial port RS485 zu WiFi, siehe auch weiter oben (13 May 2021) von @Badwater

                      wendy2702 1 Reply Last reply Reply Quote 0
                      • wendy2702
                        wendy2702 @darkblu last edited by

                        @darkblu ok.

                        Kenne ich nicht.

                        Da sollte dann jemand helfen der die HW hat.

                        T 1 Reply Last reply Reply Quote 0
                        • T
                          The_Stig @wendy2702 last edited by

                          @wendy2702 oder jemand anders: Bin ein kompletter iobroker-Newbie und möchte auch gerne die Trovis 5573 auslesen.
                          Habe vorher das Auslesen über SmarthomeNG gemacht (Adapter und Anbindung funktioniert also).
                          Aktuell habe ich im iobroker modbus installiert und die IP des Adapters hinterlegt. Folgende Einstellungen:
                          0d4e453e-2960-4dde-8155-ebaf71f0c448-image.png
                          Im Protokoll bekomme ich:


                          admin.0
                          2024-03-08 11:42:52.996 info <== Disconnect system.user.admin from ::ffff:192.168.178.80 modbus

                          admin.0
                          2024-03-08 11:42:52.996 info <== Disconnect system.user.admin from ::ffff:192.168.178.80 modbus

                          admin.0
                          2024-03-08 11:42:18.222 info ==> Connected system.user.admin from ::ffff:192.168.178.80

                          modbus.0
                          2024-03-08 11:42:08.709 info Disconnected from slave 192.168.178.95

                          modbus.0
                          2024-03-08 11:42:07.709 warn Poll error count: 3 code: {"err":"timeout","timeout":5000}

                          modbus.0
                          2024-03-08 11:42:07.709 error Client in error state.

                          modbus.0
                          2024-03-08 11:42:07.708 error Request timed out.

                          modbus.0
                          2024-03-08 11:42:07.708 warn Error: undefined

                          modbus.0
                          2024-03-08 11:42:02.706 info Connected to slave 192.168.178.95

                          modbus.0
                          2024-03-08 11:41:02.706 info Disconnected from slave 192.168.178.95

                          Ich habe noch nicht verstanden, was genau nun die richtige Einstellung ist und wie ich dann die Holding Register auslesen kann.

                          Kann mir da den richtigen Weg zeigen? Würde mich sehr freuen.

                          D 1 Reply Last reply Reply Quote 0
                          • D
                            darkblu @The_Stig last edited by

                            @the_stig , hallo,
                            ich habe noch den Haken bei "die Adressen nicht auf 16 Bits ausrichten" gesetzt.
                            Stimmt denn auch deine Stationsadresse ? Diese muss ja in der Trovis Steuerung gesetzt werden unter PA6.
                            Bei mir z.B. 247.

                            Das hier kennst du bestimmt: klick

                            und hier sind die Register und Coils aufgelistet: klick_2

                            T 1 Reply Last reply Reply Quote 0
                            • T
                              The_Stig @darkblu last edited by

                              @darkblu danke dir erstmal für deine Antwort. Ich habe noch ein wenig rumgespielt und es geht jetzt - ich glaube, dass da parallel noch meine alte DB (SmarthomeNG) zugegriffen hat, hat für Probleme gesorgt. Aktuell läuft es. Coole Sache...

                              1 Reply Last reply Reply Quote 0
                              • P
                                poncho last edited by

                                Braucht man für den Modbus Seriel zu Wifi Gateway zwingend einen SAM HOME Gateway? Oder kann ich den Modbus Gateway direkt an die Trovis 5573 anschließen?

                                1 Reply Last reply Reply Quote 0
                                • S
                                  schorty @klaus131079 last edited by schorty

                                  @klaus131079
                                  Hallo Klaus,

                                  bei mir klappt das Auslesen bis auf die Coils.
                                  Hab mal mit SLP gestartet und bekomme:

                                  modbus.2
                                  2024-11-22 20:07:26.757 warn [DevID_247] Poll error count: 9 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}

                                  Wie bekommst Du den separaten Order Coils in der Objektabsicht?

                                  Danke & Grüße
                                  Alex

                                  Edit: Hab es doch hinbekommen... Stickwort Diskrete Ausgänge == Coils

                                  1 Reply Last reply Reply Quote 0
                                  • S
                                    schorty @katte last edited by schorty

                                    Hallo Zusammen,

                                    hat jemand schon erfolgreich Register der Trovis 5573-1 beschrieben? Möchte die Warmwasserbereitung TW ein- und ausschalten.

                                    Sind Trovis Nutzer noch da?

                                    Grüße
                                    Alex

                                    S 1 Reply Last reply Reply Quote 0
                                    • S
                                      schorty @schorty last edited by

                                      keiner mehr da zu dem Thema???

                                      1 Reply Last reply Reply Quote 0
                                      • First post
                                        Last post

                                      Support us

                                      ioBroker
                                      Community Adapters
                                      Donate
                                      FAQ Cloud / IOT
                                      HowTo: Node.js-Update
                                      HowTo: Backup/Restore
                                      Downloads
                                      BLOG

                                      1.0k
                                      Online

                                      31.7k
                                      Users

                                      79.7k
                                      Topics

                                      1.3m
                                      Posts

                                      11
                                      32
                                      3749
                                      Loading More Posts
                                      • Oldest to Newest
                                      • Newest to Oldest
                                      • Most Votes
                                      Reply
                                      • Reply as topic
                                      Log in to reply
                                      Community
                                      Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                      The ioBroker Community 2014-2023
                                      logo