E3DC Hauskraftwerk steuern
-
-
Hallo zusammen,
kann es sein, dass es Probleme mit Javascript 5 und Node.js 18 gibt?
Ich bekomme nachfolgenden Fehler mit der Version 1.2.12.
Vielen Dank schonmal für die Hilfe.javascript.0 2023-10-09 23:33:15.109 error at script.js.E3DC_ChargeControl.Charge_Control:1976:3 javascript.0 2023-10-09 23:33:15.109 error at script.js.E3DC_ChargeControl.Charge_Control:50:49 javascript.0 2023-10-09 23:33:15.109 error script.js.E3DC_ChargeControl.Charge_Control: TypeError: Cannot read properties of undefined (reading 'XMLHttpRequest') javascript.0 2023-10-09 23:33:15.107 info script.js.E3DC_ChargeControl.Charge_Control: registered 0 subscriptions, 0 schedules, 0 messages, 0 logs and 0 file subscriptions javascript.0 2023-10-09 23:33:15.102 error at script.js.E3DC_ChargeControl.Charge_Control:1976:3 javascript.0 2023-10-09 23:33:15.102 error at script.js.E3DC_ChargeControl.Charge_Control:50:24 javascript.0 2023-10-09 23:33:15.101 error script.js.E3DC_ChargeControl.Charge_Control: /opt/iobroker/node_modules/iobroker.javascript/node_modules/xmlhttprequest/lib/XMLHttpRequest.js:308 javascript.0 2023-10-09 23:33:15.097 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== Charge-Control Version 1.2.12 ====- "}## javascript.0 2023-10-09 23:33:15.079 info Start javascript script.js.E3DC_ChargeControl.Charge_Control javascript.0 2023-10-09 23:33:12.133 info Stop script script.js.E3DC_ChargeControl.Charge_Control
-
@psrelax sagte in E3DC Hauskraftwerk steuern:
'XMLHttpRequest'
'XMLHttpRequest' in javascript Adapter eingetragen?
-
@smartboart
xmlhttprequest war noch eingetragen.
Wider besseren Wissens, hatte ich das Modul jetzt testweise entfernt, konnte danach aber den Javascript Adapter nicht mehr starten. Auch ein hinzufügen des Moduls konnte den Adapter nicht mehr "gerade ziehen".
Ich habe das Modul dann über die Konsole nachinstalliert und konnte dann Javascript wieder einwandfrei starten.
Das hat anscheinend auch meinen zuvor geposteten Fehler behoben
Vielen Dank für die Hilfe -
@arnod sagte in E3DC Hauskraftwerk steuern:
Nur interessehalber, konntest du das Problem lösen bzw. die Ursache herausfinden?
Argh... völlig vergessen hier bescheid zu sagen. Mag auch daran liegen, dass die Ursache ziemlich peinlich ist .
Also: Ich habe die Anlage im Juni 2022 bekommen. Dann hatte ich sofort auf einem raspberry pi - auf dem auch ein, zwei weitere lokale Dienste liefen - "e3dc-control" installiert und etwas damit rumexperimentiert. Nach einiger Zeit bin ich dann mit ioBroker eingestiegen und habe dann die Steuerung mit Deinem Skript realisiert. Dafür habe ich natürlich e3dc-control auf dem pi beendet. Tja, und was soll ich sagen? Ich hatte das Skript "bootfest" gemacht. Als ich dann nach einer laaaangen Uptime-Zeit den pi nochmal neu gestartet habe, habe ich nicht geschnallt, dass der pi auch e3dc-control wieder gestartet hat. Lange Rede, kurzer Sinn: Dein Skript und e3dc-control sind sich in die Quere gekommen.
Sorry!
VG
Georg -
Ich habe seit dem letzten Update vom Adapter plötzlich wieder extreme Fehlermeldungen.
Leider finde ich die entsprechenden Einstellungen im Adapter nicht um das Polling dieser Befehle zu deaktivieren.
Das Logging möchte ich eigentlich auch nicht verringern.
Hat jemand auch das Problem?
-
@valbuz
Denke da bist du hier im falschen Forum.
Am besten bei Probleme mit dem e3dc-rscp Adapter ein Issue hier öffnen: https://github.com/git-kick/ioBroker.e3dc-rscp -
@arnod sagte in E3DC Hauskraftwerk steuern:
@valbuz
Denke da bist du hier im falschen Forum.
Am besten bei Probleme mit dem e3dc-rscp Adapter ein Issue hier öffnen: https://github.com/git-kick/ioBroker.e3dc-rscpDanke.
-
Hallo zusammen,
ich hatte heute ein komisches Phänomen.
Die Version 1.2.12 ist gelaufen.
Bei 90% SOC habe ich ein Pulsieren beim Laden gesehen. Im Sekundentakt, Wechsel zwischen 0 Ladung und 2000.
Ich habe dann die Version 1.2.12 gestoppt und die Version 1.2.11 gestartet. -> Ladung hat mit der alten jetzt neu gestarteten Version nicht gestartet, was ich für korrekt halte, da Ladeende2 noch nicht in die Nähe gekommen ist.Kann es sein, dass es mit der Version 1.2.12 noch ein Problem gibt?
Eventuell hilft der Ausschnitt der Log.javascript.0 2023-10-22 13:44:09.021 warn script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 2667 M_Power = 2667 ====-"}## javascript.0 2023-10-22 13:44:09.008 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:2667 = Math.round(((Ladeende2_Proz:99 - Batterie_SOC_Proz:90)* Speichergroesse_kWh:16 * 10 * 3600)/(tSommerladeende_milisek:1697976993064 - Zeit_aktuell_milisek:1697975049000)) ====- "}## javascript.0 2023-10-22 13:44:06.012 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== Regelung E3DC überlassen (idle). Schritt = 3 SET_POWER_MODE = 0 normal ====- "}## javascript.0 2023-10-22 13:44:06.010 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== Laderegelung wird gestoppt ====- "}## javascript.0 2023-10-22 13:44:03.020 warn script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 2658 M_Power = 2658 ====-"}## javascript.0 2023-10-22 13:44:03.007 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:2658 = Math.round(((Ladeende2_Proz:99 - Batterie_SOC_Proz:90)* Speichergroesse_kWh:16 * 10 * 3600)/(tSommerladeende_milisek:1697976993064 - Zeit_aktuell_milisek:1697975043001)) ====- "}## javascript.0 2023-10-22 13:44:00.104 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== Regelung E3DC überlassen (idle). Schritt = 3 SET_POWER_MODE = 0 normal ====- "}## javascript.0 2023-10-22 13:44:00.061 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== Laderegelung wird gestoppt ====- "}## javascript.0 2023-10-22 13:43:57.014 warn script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 2650 M_Power = 2650 ====-"}## javascript.0 2023-10-22 13:43:57.007 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:2650 = Math.round(((Ladeende2_Proz:99 - Batterie_SOC_Proz:90)* Speichergroesse_kWh:16 * 10 * 3600)/(tSommerladeende_milisek:1697976993064 - Zeit_aktuell_milisek:1697975037000)) ====- "}## javascript.0 2023-10-22 13:43:54.014 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== Regelung E3DC überlassen (idle). Schritt = 3 SET_POWER_MODE = 0 normal ====- "}## javascript.0 2023-10-22 13:43:54.011 info script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":" -==== Laderegelung wird gestoppt ====- "}## javascript.0 2023-10-22 13:43:51.016 warn script.js.E3DC_ChargeControl.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 2642 M_Power = 2642 ====-"}##
-
@psrelax
konnte bis heute mit der Version 1.2.12 bei mir kein Problem feststellen.
Aus dem Log sehe ich nur das die Berechnung eine Ladeleistung von 2642 W ergibt, um deine Batterie auf 99 % zu laden.
Dann wird aber umgeschaltet auf Leerlauf und das Laden der Batterie wird gestoppt.
Das bedeutet, dass nicht mehr genug PV-Leistung vorhanden war, um die Batterie zu laden oder der Hausverbrauch einfach höher war.
Hast du von dem Zeitraum ein Diagramm wo man erkennen kann, wie die PV-Leistung, Hausverbrauch, Einspeiseleistung usw. war. -
@arnod
Leider bin ich mit Diagrammen nicht wirklich gut aufgestellt.
Ich hoffe nachfolgende von E3DC und OpenWB helfen dir ein wenig.
Das Pulsieren kann ich allerdings in den Diagrammen nicht sehen, da sie wahrscheinlich zu träge sind.
Evtl. beim Diagramm von OpenWB. Dort ist Speicher laden und entladen zur gleichen Zeit 12:35-14:00 Uhr zu sehen. -
@psrelax
zwischen 12:35 Uhr und 14:05 Uhr. Da wird kurz aus dem Netz Leistung gezogen und das ist auch der Punkt wo das Script die Steuerung an E3DC abgibt.
Warum jetzt aber die PV-Leistung in dem Moment nicht ausgereicht hat, ist bei der Auflösung leider nicht zu erkennen. Dass es im Diagramm so aussieht, als ob Speicher laden und entladen zur gleichen Zeit stattgefunden hat, ist einfach der Auflösung geschuldet, da sowas nicht möglich ist.
Wenn da nur alle 15 min ein Wert erfasst wird, geht alles dazwischen im Diagramm verloren.
Meine Vermutung ist, dass es einfach in dem Moment bewölkt war und deswegen die PV-Leistung nicht mehr ausgereicht hat, um die Batterie zu laden und der Rest aus dem Netz gezogen wurde.
Dafür spricht auch der Einbruch in der PV-Leistung um ca. 13:15 und 13:45 Uhr. -
Neue Version Charge-Control auf GitHub hochgeladen.
Version: 1.2.13
Änderungen:- Neue Objekt-ID
0_userdata.0.Charge_Control.Allgemein.Akt_Berechnete_Ladeleistung_W
erstellt, um die berechnete Ladeleistung bis Regelende bzw. Ladeende in VIS anzuzeigen.
- Neue Objekt-ID
-
@arnod
Ok danke dir erstmal für deine Bemühungen. Ich werde das dann weiter beobachten.
Ich setze dazu dann deine heute hochgeladene Version aktiv. -
Neue Version Charge-Control auf GitHub hochgeladen.
Version: 1.2.14
Änderungen:- Fehler behoben, dass die neue Objekt-ID "0_userdata.0.Charge_Control.Allgemein.Akt_Berechnete_Ladeleistung_W" nach Ladeende nicht auf 0 gesetzt wurde. Die Ladeleistung wird jetzt auch berechnet, wenn „Automatik Laderegelung“ ausgeschaltet wird.
-
@arnod ! habe mit v.14 ziemlich unplausiblen Wert der ber.Ladeleistung
o soll das so
72dcf2ff-0381-4813-8c1d-f71f1ec6e5b1-image.png -
@as
Nein, das soll nicht so sein
Muss ich mir morgen ansehen, zurzeit bin ich tagsüber in der Arbeit und kann es somit nicht testen.Was hast du bei dir als Ladeende % und Ladeende2 % eigentlich eingestellt und welche Zeiten?
-
@arnod Hallo, muss halt nicht gleich sein: Notstromfunktion lässt die Relais ständig schalten. Wie gesagt, es eilt nicht.
nach 20 Uhr wurde der Reserverwert erreicht und da ging dann auch das Schalten los.
-
@jh537
Kann es sein, dass du noch eine alte Version von Script einsetzt?
Um ein Pulsieren zu verhindern wird nämlich der Notstrom_SOC_Proz Wert um 2% erhöht, wenn einmal der eingestellte Wert erreicht oder unterschritten wurde.
In deinem LOG Zeile 3 von unten sehe ich aber das dieser auf 21% bleibt. Dort müsste eigentlich bei Notstrom_SOC_Proz= 23 stehen.Beim Batterie SOC besteht das Problem das dieser um 1% bis 2% nach oben springt, wenn die Lade/Entladesperre eingeschalten wird.
-
@arnod Nö die Version ist aktuell, hatte ja mit den neuen Wert getestet. Es kann aber sein, dass der Schwankungswert bei meiner Batt nicht reicht und ich den wieder höher stellen musss-ich teste. Danke für deine Prüfung