  5. [Gelöst] MODBUS.0 Adapter fehlt Master/Slave möglichkeit?

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.9k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.3k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.6k

[Gelöst] MODBUS.0 Adapter fehlt Master/Slave möglichkeit?

Geplant Angeheftet Gesperrt Verschoben Automatisierung
master slavemodbustyp
33 Beiträge 4 Kommentatoren 2.8k Aufrufe 2 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • wendy2702W wendy2702

    7e6f6f66-0e45-41b8-a849-37f458f09c3a-grafik.png

    michael.puschM Offline
    michael.puschM Offline
    michael.pusch
    schrieb am zuletzt editiert von
    #22

    @wendy2702

    modbus.0
    	2023-01-25 21:24:26.494	debug	Cleaning up request fifo.
    modbus.0
    	2023-01-25 21:24:26.493	debug	Clearing timeout of the current request.
    modbus.0
    	2023-01-25 21:24:26.487	info	Disconnected from slave
    modbus.0
    	2023-01-25 21:24:26.036	warn	Poll error count: 1 code: "App Timeout"
    modbus.0
    	2023-01-25 21:24:25.484	error	Cannot write single register [38407]: {"err":"timeout","timeout":5000}
    modbus.0
    	2023-01-25 21:24:25.483	error	Request timed out.
    modbus.0
    	2023-01-25 21:24:25.482	warn	Error: undefined
    modbus.0
    	2023-01-25 21:24:20.836	debug	[DevID_10/inputRegs] Poll address 13568 - 21 registers
    modbus.0
    	2023-01-25 21:24:20.836	debug	[DevID_10] Poll start ---------------------
    modbus.0
    	2023-01-25 21:24:20.585	error	Error response: Function code received in the query is not recognized or allowed by slave
    modbus.0
    	2023-01-25 21:24:20.584	error	Error response for FCx6: Illegal Function
    modbus.0
    	2023-01-25 21:24:20.473	debug	state Changed ack=false: modbus.0.holdingRegisters.38407_PV_System_LadeStatus: {"val":1,"ack":false,"ts":1674678260467,"q":0,"from":"system.adapter.admin.0","user":"system.user.admin","lc":1674678260467}
    modbus.0
    	2023-01-25 21:24:19.783	debug	[DevID_10/holdingRegs] Poll address 38407 DONE
    modbus.0
    	2023-01-25 21:24:19.697	debug	[DevID_10/holdingRegs] Poll address 38407 - 1 registers
    modbus.0
    	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Calculation result = 0.84, type = number
    modbus.0
    	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Formula = x / 100
    modbus.0
    	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Input Value = 84
    modbus.0
    	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Calculation result = 56.87, type = number
    modbus.0
    	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Formula = x / 100
    modbus.0
    	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Input Value = 5687
    modbus.0
    	2023-01-25 21:24:19.687	debug	[DevID_10/inputRegs] Poll address 13696 DONE
    modbus.0
    	2023-01-25 21:24:19.599	debug	[DevID_10/inputRegs] Poll address 13696 - 7 registers
    modbus.0
    	2023-01-25 21:24:19.595	debug	[DevID_10/inputRegs/13655] Calculation result = 211.15, type = number
    modbus.0
    	2023-01-25 21:24:19.592	debug	[DevID_10/inputRegs/13655] Formula = x / 100
    modbus.0
    	2023-01-25 21:24:19.592	debug	[DevID_10/inputRegs/13655] Input Value = 21115
    modbus.0
    	2023-01-25 21:24:19.591	debug	[DevID_10/inputRegs] Poll address 13655 DONE
    modbus.0
    	2023-01-25 21:24:19.501	debug	[DevID_10/inputRegs] Poll address 13655 - 1 registers
    modbus.0
    	2023-01-25 21:24:19.499	debug	[DevID_10/inputRegs/13643] Calculation result = 0, type = number
    modbus.0
    	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13643] Formula = x / 100
    modbus.0
    	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13643] Input Value = 0
    modbus.0
    	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13642] Calculation result = 0, type = number
    modbus.0
    	2023-01-25 21:24:19.497	debug	[DevID_10/inputRegs/13642] Formula = x / 100
    

    Gradeaus ---------->

    wendy2702W 1 Antwort Letzte Antwort
    0
    • wendy2702W wendy2702

      @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

      Function code received in the query is not recognized or allowed by slave

      Da steht aber das dein WR den Function Code nicht akzeptiert.

      Also entweder register falsch, kein Holding, oder falsche Register Parameter.

      michael.puschM Offline
      michael.puschM Offline
      michael.pusch
      schrieb am zuletzt editiert von
      #23

      @wendy2702 sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

      @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

      Function code received in the query is not recognized or allowed by slave

      Da steht aber das dein WR den Function Code nicht akzeptiert.

      Also entweder register falsch, kein Holding, oder falsche Register Parameter.

      Screenshot 2023-01-25 194703.png

      Laut Hex müsste die Adresse dann 38407 lauten...

      es geht um die Zeile C8

      Gradeaus ---------->

      GlasfaserG 1 Antwort Letzte Antwort
      0
      • michael.puschM michael.pusch

        @wendy2702

        modbus.0
        	2023-01-25 21:24:26.494	debug	Cleaning up request fifo.
        modbus.0
        	2023-01-25 21:24:26.493	debug	Clearing timeout of the current request.
        modbus.0
        	2023-01-25 21:24:26.487	info	Disconnected from slave
        modbus.0
        	2023-01-25 21:24:26.036	warn	Poll error count: 1 code: "App Timeout"
        modbus.0
        	2023-01-25 21:24:25.484	error	Cannot write single register [38407]: {"err":"timeout","timeout":5000}
        modbus.0
        	2023-01-25 21:24:25.483	error	Request timed out.
        modbus.0
        	2023-01-25 21:24:25.482	warn	Error: undefined
        modbus.0
        	2023-01-25 21:24:20.836	debug	[DevID_10/inputRegs] Poll address 13568 - 21 registers
        modbus.0
        	2023-01-25 21:24:20.836	debug	[DevID_10] Poll start ---------------------
        modbus.0
        	2023-01-25 21:24:20.585	error	Error response: Function code received in the query is not recognized or allowed by slave
        modbus.0
        	2023-01-25 21:24:20.584	error	Error response for FCx6: Illegal Function
        modbus.0
        	2023-01-25 21:24:20.473	debug	state Changed ack=false: modbus.0.holdingRegisters.38407_PV_System_LadeStatus: {"val":1,"ack":false,"ts":1674678260467,"q":0,"from":"system.adapter.admin.0","user":"system.user.admin","lc":1674678260467}
        modbus.0
        	2023-01-25 21:24:19.783	debug	[DevID_10/holdingRegs] Poll address 38407 DONE
        modbus.0
        	2023-01-25 21:24:19.697	debug	[DevID_10/holdingRegs] Poll address 38407 - 1 registers
        modbus.0
        	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Calculation result = 0.84, type = number
        modbus.0
        	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Formula = x / 100
        modbus.0
        	2023-01-25 21:24:19.689	debug	[DevID_10/inputRegs/13697] Input Value = 84
        modbus.0
        	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Calculation result = 56.87, type = number
        modbus.0
        	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Formula = x / 100
        modbus.0
        	2023-01-25 21:24:19.688	debug	[DevID_10/inputRegs/13696] Input Value = 5687
        modbus.0
        	2023-01-25 21:24:19.687	debug	[DevID_10/inputRegs] Poll address 13696 DONE
        modbus.0
        	2023-01-25 21:24:19.599	debug	[DevID_10/inputRegs] Poll address 13696 - 7 registers
        modbus.0
        	2023-01-25 21:24:19.595	debug	[DevID_10/inputRegs/13655] Calculation result = 211.15, type = number
        modbus.0
        	2023-01-25 21:24:19.592	debug	[DevID_10/inputRegs/13655] Formula = x / 100
        modbus.0
        	2023-01-25 21:24:19.592	debug	[DevID_10/inputRegs/13655] Input Value = 21115
        modbus.0
        	2023-01-25 21:24:19.591	debug	[DevID_10/inputRegs] Poll address 13655 DONE
        modbus.0
        	2023-01-25 21:24:19.501	debug	[DevID_10/inputRegs] Poll address 13655 - 1 registers
        modbus.0
        	2023-01-25 21:24:19.499	debug	[DevID_10/inputRegs/13643] Calculation result = 0, type = number
        modbus.0
        	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13643] Formula = x / 100
        modbus.0
        	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13643] Input Value = 0
        modbus.0
        	2023-01-25 21:24:19.498	debug	[DevID_10/inputRegs/13642] Calculation result = 0, type = number
        modbus.0
        	2023-01-25 21:24:19.497	debug	[DevID_10/inputRegs/13642] Formula = x / 100
        
        wendy2702W Online
        wendy2702W Online
        wendy2702
        schrieb am zuletzt editiert von
        #24

        @wendy2702 sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

        @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

        Function code received in the query is not recognized or allowed by slave

        Da steht aber das dein WR den Function Code nicht akzeptiert.

        Also entweder register falsch, kein Holding, oder falsche Register Parameter.

        Ich zitiere mich selber.

        Bitte keine Fragen per PN, die gehören ins Forum!

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        1 Antwort Letzte Antwort
        0
        • michael.puschM michael.pusch

          @wendy2702 sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

          @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

          Function code received in the query is not recognized or allowed by slave

          Da steht aber das dein WR den Function Code nicht akzeptiert.

          Also entweder register falsch, kein Holding, oder falsche Register Parameter.

          Screenshot 2023-01-25 194703.png

          Laut Hex müsste die Adresse dann 38407 lauten...

          es geht um die Zeile C8

          GlasfaserG Offline
          GlasfaserG Offline
          Glasfaser
          schrieb am zuletzt editiert von
          #25

          @michael-pusch

          Write ist Holding Register

          eefae957-57b1-4558-9d99-1074a0376b4e-grafik.png

          Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

          michael.puschM 1 Antwort Letzte Antwort
          0
          • GlasfaserG Glasfaser

            @michael-pusch

            Write ist Holding Register

            eefae957-57b1-4558-9d99-1074a0376b4e-grafik.png

            michael.puschM Offline
            michael.puschM Offline
            michael.pusch
            schrieb am zuletzt editiert von
            #26

            @glasfaser

            Screenshot 2023-01-25 210738.png

            liegt ja dort

            Gradeaus ---------->

            GlasfaserG 1 Antwort Letzte Antwort
            0
            • wendy2702W Online
              wendy2702W Online
              wendy2702
              schrieb am zuletzt editiert von wendy2702
              #27

              0x10 ist Function Code 16

              [FC16](Link Adresse)

              Setze mal den haken

              818d93c5-9167-4c26-97e7-995e0357a512-grafik.png

              Bitte keine Fragen per PN, die gehören ins Forum!

              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

              1 Antwort Letzte Antwort
              0
              • michael.puschM michael.pusch

                @glasfaser

                Screenshot 2023-01-25 210738.png

                liegt ja dort

                GlasfaserG Offline
                GlasfaserG Offline
                Glasfaser
                schrieb am zuletzt editiert von Glasfaser
                #28

                @michael-pusch

                dann gehe ein Register am ende +1 / oder -1

                Was ist dann

                38408
                38406

                Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                1 Antwort Letzte Antwort
                0
                • michael.puschM Offline
                  michael.puschM Offline
                  michael.pusch
                  schrieb am zuletzt editiert von michael.pusch
                  #29

                  @wendy2702 sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                  Function Code 16

                  Setze mal den haken

                  Ich "glaube" es funktioniert jetzt... Hakerl gesetzt, obwohl ich das hakerl setzen in anderen versuchen definitiv zwar schon mal gemacht hatte, aber jetzt dürfte es funktionieren. Hat sicher auch mit der "Mehrere ID´s" problematik zu tun gehabt...

                  Wenn ich am Datenpunkt manuell nun 2 eingebe soll er PV bevorzugen, wenn das nicht reicht soll er mit EVU, also Netz nachschiessen.
                  Wenn ich das eingebe, springt der Accu auf Standby da er voll ist und der Strom aus dem EVU Netz wird verwendet.

                  Wenn ich den Datenpunkt jetzt mit 1 belege, soll er nur PV nehmen... da das jetzt in der Nacht natürlich nicht reicht, springt der Accu an und geht von Standby auf Entladend.. sprich, er spricht mir den Datenpunkt im Hybridwechselrichter anscheinend definitv an und stellt mir diesen um!

                  Ich darf nur nicht "Bestätigt" anhängen, dann kommt und passiert auch nix !

                  Leute DANKE DANKE DANKE... !!!

                  Gradeaus ---------->

                  wendy2702W 1 Antwort Letzte Antwort
                  0
                  • michael.puschM michael.pusch

                    @wendy2702 sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                    Function Code 16

                    Setze mal den haken

                    Ich "glaube" es funktioniert jetzt... Hakerl gesetzt, obwohl ich das hakerl setzen in anderen versuchen definitiv zwar schon mal gemacht hatte, aber jetzt dürfte es funktionieren. Hat sicher auch mit der "Mehrere ID´s" problematik zu tun gehabt...

                    Wenn ich am Datenpunkt manuell nun 2 eingebe soll er PV bevorzugen, wenn das nicht reicht soll er mit EVU, also Netz nachschiessen.
                    Wenn ich das eingebe, springt der Accu auf Standby da er voll ist und der Strom aus dem EVU Netz wird verwendet.

                    Wenn ich den Datenpunkt jetzt mit 1 belege, soll er nur PV nehmen... da das jetzt in der Nacht natürlich nicht reicht, springt der Accu an und geht von Standby auf Entladend.. sprich, er spricht mir den Datenpunkt im Hybridwechselrichter anscheinend definitv an und stellt mir diesen um!

                    Ich darf nur nicht "Bestätigt" anhängen, dann kommt und passiert auch nix !

                    Leute DANKE DANKE DANKE... !!!

                    wendy2702W Online
                    wendy2702W Online
                    wendy2702
                    schrieb am zuletzt editiert von
                    #30

                    @michael-pusch Was kommt denn im Debug log wenn du den Wert schreibst?

                    Und wenn es funktioniert, bitte den ersten Beitrag editieren und ein [Gelöst] vor den Titel setzen

                    Bitte keine Fragen per PN, die gehören ins Forum!

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    michael.puschM 1 Antwort Letzte Antwort
                    0
                    • wendy2702W wendy2702

                      @michael-pusch Was kommt denn im Debug log wenn du den Wert schreibst?

                      Und wenn es funktioniert, bitte den ersten Beitrag editieren und ein [Gelöst] vor den Titel setzen

                      michael.puschM Offline
                      michael.puschM Offline
                      michael.pusch
                      schrieb am zuletzt editiert von
                      #31

                      @wendy2702

                      modbus.0
                      	2023-01-25 22:05:31.032	debug	[DevID_10/holdingRegs] Poll address 38407 DONE
                      modbus.0
                      	2023-01-25 22:05:30.939	debug	[DevID_10/holdingRegs] Poll address 38407 - 1 registers
                      modbus.0
                      	2023-01-25 22:05:30.938	debug	[DevID_10/inputRegs/13697] Calculation result = 0.56, type = number
                      modbus.0
                      	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13697] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13697] Input Value = 56
                      modbus.0
                      	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13696] Calculation result = 56.91, type = number
                      modbus.0
                      	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13696] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13696] Input Value = 5691
                      modbus.0
                      	2023-01-25 22:05:30.936	debug	[DevID_10/inputRegs] Poll address 13696 DONE
                      modbus.0
                      	2023-01-25 22:05:30.843	debug	[DevID_10/inputRegs] Poll address 13696 - 7 registers
                      modbus.0
                      	2023-01-25 22:05:30.841	debug	[DevID_10/inputRegs/13655] Calculation result = 211.15, type = number
                      modbus.0
                      	2023-01-25 22:05:30.841	debug	[DevID_10/inputRegs/13655] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.841	debug	[DevID_10/inputRegs/13655] Input Value = 21115
                      modbus.0
                      	2023-01-25 22:05:30.840	debug	[DevID_10/inputRegs] Poll address 13655 DONE
                      modbus.0
                      	2023-01-25 22:05:30.746	debug	[DevID_10/inputRegs] Poll address 13655 - 1 registers
                      modbus.0
                      	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13643] Calculation result = 0, type = number
                      modbus.0
                      	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13643] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13643] Input Value = 0
                      modbus.0
                      	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13642] Calculation result = 0, type = number
                      modbus.0
                      	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13642] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13642] Input Value = 0
                      modbus.0
                      	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13641] Calculation result = 0, type = number
                      modbus.0
                      	2023-01-25 22:05:30.744	debug	[DevID_10/inputRegs/13641] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.744	debug	[DevID_10/inputRegs/13641] Input Value = 0
                      modbus.0
                      	2023-01-25 22:05:30.744	debug	[DevID_10/inputRegs] Poll address 13641 DONE
                      modbus.0
                      	2023-01-25 22:05:30.634	debug	[DevID_10/inputRegs] Poll address 13641 - 3 registers
                      modbus.0
                      	2023-01-25 22:05:30.633	debug	[DevID_10/inputRegs/13616] Calculation result = -302.46, type = number
                      modbus.0
                      	2023-01-25 22:05:30.633	debug	[DevID_10/inputRegs/13616] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.633	debug	[DevID_10/inputRegs/13616] Input Value = -30246
                      modbus.0
                      	2023-01-25 22:05:30.632	debug	[DevID_10/inputRegs] Poll address 13616 DONE
                      modbus.0
                      	2023-01-25 22:05:30.538	debug	[DevID_10/inputRegs] Poll address 13616 - 1 registers
                      modbus.0
                      	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13602] Calculation result = 0.36, type = number
                      modbus.0
                      	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13602] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13602] Input Value = 36
                      modbus.0
                      	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13601] Calculation result = 232.41, type = number
                      modbus.0
                      	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13601] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.536	debug	[DevID_10/inputRegs/13601] Input Value = 23241
                      modbus.0
                      	2023-01-25 22:05:30.536	debug	[DevID_10/inputRegs] Poll address 13601 DONE
                      modbus.0
                      	2023-01-25 22:05:30.447	debug	[DevID_10/inputRegs] Poll address 13601 - 2 registers
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13588] Calculation result = 26, type = number
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13588] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13588] Input Value = 2600
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13587] Calculation result = 24, type = number
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13587] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13587] Input Value = 2400
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13586] Calculation result = 12, type = number
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13586] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13586] Input Value = 1200
                      modbus.0
                      	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13583] Calculation result = 120.34, type = number
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13583] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13583] Input Value = 12034
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13572] Calculation result = 50, type = number
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13572] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13572] Input Value = 5000
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13570] Calculation result = 31.86, type = number
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13570] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13570] Input Value = 3186
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13568] Calculation result = 232.41, type = number
                      modbus.0
                      	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13568] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:30.440	debug	[DevID_10/inputRegs/13568] Input Value = 23241
                      modbus.0
                      	2023-01-25 22:05:30.440	debug	[DevID_10/inputRegs] Poll address 13568 DONE
                      modbus.0
                      	2023-01-25 22:05:30.388	debug	[DevID_10/inputRegs] Poll address 13568 - 21 registers
                      modbus.0
                      	2023-01-25 22:05:30.388	debug	[DevID_10] Poll start ---------------------
                      modbus.0
                      	2023-01-25 22:05:29.337	debug	[DevID_10/holdingRegs] Poll address 38407 DONE
                      modbus.0
                      	2023-01-25 22:05:29.242	debug	[DevID_10/holdingRegs] Poll address 38407 - 1 registers
                      modbus.0
                      	2023-01-25 22:05:29.241	debug	[DevID_10/inputRegs/13697] Calculation result = 0.56, type = number
                      modbus.0
                      	2023-01-25 22:05:29.241	debug	[DevID_10/inputRegs/13697] Formula = x / 100
                      modbus.0
                      	2023-01-25 22:05:29.241	debug	[DevID_10/inputRegs/13697] Input Value = 56
                      

                      muss man suchen, 38407

                      Gradeaus ---------->

                      wendy2702W 1 Antwort Letzte Antwort
                      0
                      • michael.puschM michael.pusch

                        @wendy2702

                        modbus.0
                        	2023-01-25 22:05:31.032	debug	[DevID_10/holdingRegs] Poll address 38407 DONE
                        modbus.0
                        	2023-01-25 22:05:30.939	debug	[DevID_10/holdingRegs] Poll address 38407 - 1 registers
                        modbus.0
                        	2023-01-25 22:05:30.938	debug	[DevID_10/inputRegs/13697] Calculation result = 0.56, type = number
                        modbus.0
                        	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13697] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13697] Input Value = 56
                        modbus.0
                        	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13696] Calculation result = 56.91, type = number
                        modbus.0
                        	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13696] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.937	debug	[DevID_10/inputRegs/13696] Input Value = 5691
                        modbus.0
                        	2023-01-25 22:05:30.936	debug	[DevID_10/inputRegs] Poll address 13696 DONE
                        modbus.0
                        	2023-01-25 22:05:30.843	debug	[DevID_10/inputRegs] Poll address 13696 - 7 registers
                        modbus.0
                        	2023-01-25 22:05:30.841	debug	[DevID_10/inputRegs/13655] Calculation result = 211.15, type = number
                        modbus.0
                        	2023-01-25 22:05:30.841	debug	[DevID_10/inputRegs/13655] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.841	debug	[DevID_10/inputRegs/13655] Input Value = 21115
                        modbus.0
                        	2023-01-25 22:05:30.840	debug	[DevID_10/inputRegs] Poll address 13655 DONE
                        modbus.0
                        	2023-01-25 22:05:30.746	debug	[DevID_10/inputRegs] Poll address 13655 - 1 registers
                        modbus.0
                        	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13643] Calculation result = 0, type = number
                        modbus.0
                        	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13643] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13643] Input Value = 0
                        modbus.0
                        	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13642] Calculation result = 0, type = number
                        modbus.0
                        	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13642] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13642] Input Value = 0
                        modbus.0
                        	2023-01-25 22:05:30.745	debug	[DevID_10/inputRegs/13641] Calculation result = 0, type = number
                        modbus.0
                        	2023-01-25 22:05:30.744	debug	[DevID_10/inputRegs/13641] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.744	debug	[DevID_10/inputRegs/13641] Input Value = 0
                        modbus.0
                        	2023-01-25 22:05:30.744	debug	[DevID_10/inputRegs] Poll address 13641 DONE
                        modbus.0
                        	2023-01-25 22:05:30.634	debug	[DevID_10/inputRegs] Poll address 13641 - 3 registers
                        modbus.0
                        	2023-01-25 22:05:30.633	debug	[DevID_10/inputRegs/13616] Calculation result = -302.46, type = number
                        modbus.0
                        	2023-01-25 22:05:30.633	debug	[DevID_10/inputRegs/13616] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.633	debug	[DevID_10/inputRegs/13616] Input Value = -30246
                        modbus.0
                        	2023-01-25 22:05:30.632	debug	[DevID_10/inputRegs] Poll address 13616 DONE
                        modbus.0
                        	2023-01-25 22:05:30.538	debug	[DevID_10/inputRegs] Poll address 13616 - 1 registers
                        modbus.0
                        	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13602] Calculation result = 0.36, type = number
                        modbus.0
                        	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13602] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13602] Input Value = 36
                        modbus.0
                        	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13601] Calculation result = 232.41, type = number
                        modbus.0
                        	2023-01-25 22:05:30.537	debug	[DevID_10/inputRegs/13601] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.536	debug	[DevID_10/inputRegs/13601] Input Value = 23241
                        modbus.0
                        	2023-01-25 22:05:30.536	debug	[DevID_10/inputRegs] Poll address 13601 DONE
                        modbus.0
                        	2023-01-25 22:05:30.447	debug	[DevID_10/inputRegs] Poll address 13601 - 2 registers
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13588] Calculation result = 26, type = number
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13588] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13588] Input Value = 2600
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13587] Calculation result = 24, type = number
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13587] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13587] Input Value = 2400
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13586] Calculation result = 12, type = number
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13586] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13586] Input Value = 1200
                        modbus.0
                        	2023-01-25 22:05:30.442	debug	[DevID_10/inputRegs/13583] Calculation result = 120.34, type = number
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13583] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13583] Input Value = 12034
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13572] Calculation result = 50, type = number
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13572] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13572] Input Value = 5000
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13570] Calculation result = 31.86, type = number
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13570] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13570] Input Value = 3186
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13568] Calculation result = 232.41, type = number
                        modbus.0
                        	2023-01-25 22:05:30.441	debug	[DevID_10/inputRegs/13568] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:30.440	debug	[DevID_10/inputRegs/13568] Input Value = 23241
                        modbus.0
                        	2023-01-25 22:05:30.440	debug	[DevID_10/inputRegs] Poll address 13568 DONE
                        modbus.0
                        	2023-01-25 22:05:30.388	debug	[DevID_10/inputRegs] Poll address 13568 - 21 registers
                        modbus.0
                        	2023-01-25 22:05:30.388	debug	[DevID_10] Poll start ---------------------
                        modbus.0
                        	2023-01-25 22:05:29.337	debug	[DevID_10/holdingRegs] Poll address 38407 DONE
                        modbus.0
                        	2023-01-25 22:05:29.242	debug	[DevID_10/holdingRegs] Poll address 38407 - 1 registers
                        modbus.0
                        	2023-01-25 22:05:29.241	debug	[DevID_10/inputRegs/13697] Calculation result = 0.56, type = number
                        modbus.0
                        	2023-01-25 22:05:29.241	debug	[DevID_10/inputRegs/13697] Formula = x / 100
                        modbus.0
                        	2023-01-25 22:05:29.241	debug	[DevID_10/inputRegs/13697] Input Value = 56
                        

                        muss man suchen, 38407

                        wendy2702W Online
                        wendy2702W Online
                        wendy2702
                        schrieb am zuletzt editiert von
                        #32

                        @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                        2023-01-25 22:05:31.032 debug [DevID_10/holdingRegs] Poll address 38407 DONE

                        Zumindest kein Reject.

                        Sieht also erst mal gut aus.

                        Bitte keine Fragen per PN, die gehören ins Forum!

                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                        michael.puschM 1 Antwort Letzte Antwort
                        1
                        • wendy2702W wendy2702

                          @michael-pusch sagte in MODBUS.0 Adapter fehlt Master/Slave möglichkeit?:

                          2023-01-25 22:05:31.032 debug [DevID_10/holdingRegs] Poll address 38407 DONE

                          Zumindest kein Reject.

                          Sieht also erst mal gut aus.

                          michael.puschM Offline
                          michael.puschM Offline
                          michael.pusch
                          schrieb am zuletzt editiert von michael.pusch
                          #33

                          @wendy2702
                          @Glasfaser
                          @Homoran

                          Danke !

                          Werd das im Auge behalten, ist aber dermassen MÄCHTIG die gesamte ioBroker umgebung und die meisten User wissen das garnicht zu schätzen was ich hier immer wieder lesen muss...!
                          Und ihr steckt da so viel Zeit, Geld und Nerven trotzdem noch immer in das Projekt...

                          Danke nochmals und Hut ab !!!!

                          Gradeaus ---------->

                          1 Antwort Letzte Antwort
                          1
                          Antworten
                          • In einem neuen Thema antworten
                          Anmelden zum Antworten
                          • Älteste zuerst
                          • Neuste zuerst
                          • Meiste Stimmen


                          Support us

                          ioBroker
                          Community Adapters
                          Donate

                          723

                          Online

                          32.5k

                          Benutzer

                          81.6k

                          Themen

                          1.3m

                          Beiträge
                          Community
                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                          ioBroker Community 2014-2025
                          logo
                          • Anmelden

                          • Du hast noch kein Konto? Registrieren

                          • Anmelden oder registrieren, um zu suchen
                          • Erster Beitrag
                            Letzter Beitrag
                          0
                          • Home
                          • Aktuell
                          • Tags
                          • Ungelesen 0
                          • Kategorien
                          • Unreplied
                          • Beliebt
                          • GitHub
                          • Docu
                          • Hilfe