I'm getting this error when importing:
Ignoring Corredor.Aquecimento.PRE_COR_SWITCH_COUNTER because no DPT is assigned to 1339. The GA is not connected to a KO in ETS Ignoring Corredor.Aquecimento.PRE_COR_SWITCH_COUNTER_REACHED because no DPT is assigned to 1340. The GA is not connected to a KO in ETS Ignoring Corredor.Aquecimento.PRE_COR_SET_POINT_LOWER_HYSTERESIS because no DPT is assigned to 1342. The GA is not connected to a KO in ETS Ignoring Corredor.Aquecimento.PRE_COR_SET_POINT_UPPER_HYSTERESIS because no DPT is assigned to 1343. The GA is not connected to a KO in ETS Ignoring Corredor.Aquecimento.PRE_COR_OVERHEAT_TEMP because no DPT is assigned to 1344. The GA is not connected to a KO in ETS Ignoring Corredor.Aquecimento.PRE_COR_AVG_TEMP because no DPT is assigned to 1345. The GA is not connected to a KO in ETS Ignoring Cozinha.Luzes.IN_COZ_LUZES_FAIL_STATUS because no DPT is assigned to 2054. The GA is not connected to a KO in ETS Ignoring Cozinha.Aquecimento.PRE_COZ_ON_OFF because no DPT is assigned to 2361. The GA is not connected to a KO in ETS Ignoring Cozinha.Aquecimento.PRE_COZ_ON_OFF_STATUS because no DPT is assigned to 2364. The GA is not connected to a KO in ETS Ignoring Cozinha.Aquecimento.PRE_COZ_SWITCH_COUNTER because no DPT is assigned to 2365. The GA is not connected to a KO in ETS Ignoring Cozinha.Aquecimento.PRE_COZ_SWITCH_COUNTER_REACHED because no DPT is assigned to 2366. The GA is not connected to a KO in ETS Ignoring Cozinha.Aquecimento.PRE_COZ_RIGHT_TEMP because no DPT is assigned to 2367. The GA is not connected to a KO in ETS
Any idea what is wrong here?
Thanks
-
@wizard2010 This is not an error only a information that this GA is not used in ETS
-
@tombox Thanks your are right
I'm also getting this warning...
There is any way to see which datapoints? I'm using free datapoints instead of x/x/x.
-
@wizard2010 The adapter receive information on the bus for this address but it is not in the xml file. The Adapter cannot say the name of the datapoint
-
@tombox Maybe this datapoints are the ones that were not imported from the xml file due to that ignore error.
Do you know if it's possible to convert this "3/6/254" in openKNX in order to allow me to check if the number matches with the ones in XML file?
-
Hallo,
ich bekomme folgende Fehlemeldung bei mir im Log angezeigt:2021-12-29 12:07:47.280 - error: openknx.0 (10336) [error] "2021-12-29T11:07:47.279Z" 'DPT14: Must supply a number value'
Leider kann ich die Meldung keiner speziellen GA zuordnen da ich mehrere mit DPT14 habe. Besteht die Möglichkeit das weiter einzugrenzen?
-
@chrischros Du könntest den Adapter in Log Level Debug setzen. Einfach in Instanzen im Experten modus von info auf debug setzen. Ruhig dann auch hier posten vielleicht können wir die log information verbessern
-
@tombox
Danke für den Tipp, werde ich nachher oder heute Abend mal testen.noch eine weitere Meldung die mir aufgefallen ist:
State value to set for "openknx.0.Dimmen.Dimmen.Außen_-_Terrasse_-_Spots_-_Dimmen" has to be stringified but received type "object"
Die GA ist als DPT 3.007 Dimmer schritte in der ETS parametriert und in ioBroker sieht das Objekt wie folgt aus:
{ "_id": "openknx.0.Dimmen.Dimmen.Außen_-_Terrasse_-_Spots_-_Dimmen", "type": "state", "common": { "desc": "Basetype: 4-bit relative dimming control", "name": "Außen - Terrasse - Spots - Dimmen", "read": true, "role": "state", "type": "object", "write": true }, "native": { "address": "2/3/13", "answer_groupValueResponse": false, "autoread": true, "bitlength": 4, "dpt": "DPT3.007", "valuetype": "composite" }, "from": "system.adapter.openknx.0", "user": "system.user.admin", "ts": 1640778698317, "acl": { "object": 1636, "state": 1636, "owner": "system.user.admin", "ownerGroup": "system.group.administrator" } }
aktuell kann ich da keinen wirklichen fehler entdecken, so sind bei mir alle GAs parametriert die mit Dimmen zu tun haben.
Hat jemand ne Idee? -
@tombox
Hier mal der Auszug aus dem Log von der Sekunde in der die Fehlermeldung kam:2021-12-29 13:50:35.027 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.026 Inbound message: 0610042000150453ab002900bce011fe2450010080 2021-12-29 13:50:35.028 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.028 (idle): zzzz... 2021-12-29 13:50:35.029 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/80 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Heizung_Zündung 2021-12-29 13:50:35.114 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.113 Inbound message: 0610042000150453ac002900bce011fe2451010080 2021-12-29 13:50:35.115 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.115 (idle): zzzz... 2021-12-29 13:50:35.116 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/81 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Gebläse_Zündung 2021-12-29 13:50:35.219 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.218 Inbound message: 0610042000150453ad002900bce011fe2452010080 2021-12-29 13:50:35.220 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.219 (idle): zzzz... 2021-12-29 13:50:35.220 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/82 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Aschenaustragung_aktiv 2021-12-29 13:50:35.356 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.356 Inbound message: 0610042000150453ae002900bce011fe2453010080 2021-12-29 13:50:35.358 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.357 (idle): zzzz... 2021-12-29 13:50:35.358 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/83 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Richtung_Aschenaustragung 2021-12-29 13:50:35.429 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/0 value 471 from openknx.0.Heizung.Photovoltaik.Photovoltaik-Leistung 2021-12-29 13:50:35.431 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.431 (sendDatagram): >>>>>>> successfully sent seqnum: 1349 2021-12-29 13:50:35.431 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.431 Inbound message: 06100421000a04534500 2021-12-29 13:50:35.432 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.432 ===== datagram 69 acknowledged by IP router 2021-12-29 13:50:35.432 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.432 (idle): zzzz... 2021-12-29 13:50:35.433 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/1 value 0 from openknx.0.Heizung.Photovoltaik.Batterie-Leistung 2021-12-29 13:50:35.434 - [31merror[39m: openknx.0 (11241) [error] "2021-12-29T12:50:35.434Z" 'DPT14: Must supply a number value' 2021-12-29 13:50:35.435 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/2 value 464 from openknx.0.Heizung.Photovoltaik.Hausverbrauchs-Leistung 2021-12-29 13:50:35.436 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/3 value -7 from openknx.0.Heizung.Photovoltaik.Leistung_am_Netzübergabepunkt 2021-12-29 13:50:35.437 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/18 value 402 from openknx.0.Heizung.Photovoltaik.DC-Spannung_an_String_1 2021-12-29 13:50:35.438 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/19 value 410 from openknx.0.Heizung.Photovoltaik.DC-Spannung_an_String_2 2021-12-29 13:50:35.439 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.439 Inbound message: 0610042000150453af002900bce011fe2454010080 2021-12-29 13:50:35.440 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.440 (idle): zzzz... 2021-12-29 13:50:35.440 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/84 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Einschubschnecke_aktiv 2021-12-29 13:50:35.466 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/22 value 237 from openknx.0.Heizung.Photovoltaik.DC-Leistung_an_String_1 2021-12-29 13:50:35.468 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/23 value 234 from openknx.0.Heizung.Photovoltaik.DC-Leistung_an_String_2 2021-12-29 13:50:35.480 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.480 (sendDatagram): >>>>>>> successfully sent seqnum: 1350 2021-12-29 13:50:35.482 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.482 Inbound message: 06100421000a04534600 2021-12-29 13:50:35.482 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.482 ===== datagram 70 acknowledged by IP router 2021-12-29 13:50:35.483 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.483 (idle): zzzz... 2021-12-29 13:50:35.530 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.530 Inbound message: 0610042000150453b0002900bce011fe2455010080 2021-12-29 13:50:35.531 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.531 (idle): zzzz... 2021-12-29 13:50:35.531 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/85 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Richtung_Einschubschnecke 2021-12-29 13:50:35.533 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.533 (sendDatagram): >>>>>>> successfully sent seqnum: 1351 2021-12-29 13:50:35.534 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.534 Inbound message: 06100421000a04534700 2021-12-29 13:50:35.535 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.535 ===== datagram 71 acknowledged by IP router 2021-12-29 13:50:35.535 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.535 (idle): zzzz... 2021-12-29 13:50:35.583 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.583 (sendDatagram): >>>>>>> successfully sent seqnum: 1352 2021-12-29 13:50:35.584 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.584 Inbound message: 06100421000a04534800 2021-12-29 13:50:35.585 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.585 ===== datagram 72 acknowledged by IP router 2021-12-29 13:50:35.585 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.585 (idle): zzzz... 2021-12-29 13:50:35.599 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.599 Inbound message: 0610042000150453b1002900bce011fe2456010080 2021-12-29 13:50:35.600 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.600 (idle): zzzz... 2021-12-29 13:50:35.600 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/86 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Raumaustragung_Sauger_aktiv 2021-12-29 13:50:35.634 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.634 (sendDatagram): >>>>>>> successfully sent seqnum: 1353 2021-12-29 13:50:35.635 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.635 Inbound message: 06100421000a04534900 2021-12-29 13:50:35.635 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.635 ===== datagram 73 acknowledged by IP router 2021-12-29 13:50:35.636 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.636 (idle): zzzz... 2021-12-29 13:50:35.685 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.685 (sendDatagram): >>>>>>> successfully sent seqnum: 1354 2021-12-29 13:50:35.686 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.686 Inbound message: 06100421000a04534a00 2021-12-29 13:50:35.687 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.686 ===== datagram 74 acknowledged by IP router 2021-12-29 13:50:35.687 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.687 (idle): zzzz... 2021-12-29 13:50:35.698 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.698 Inbound message: 0610042000150453b2002900bce011fe2457010080 2021-12-29 13:50:35.699 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.699 (idle): zzzz... 2021-12-29 13:50:35.699 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/87 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Raumaustragung_aktiv 2021-12-29 13:50:35.736 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.736 (sendDatagram): >>>>>>> successfully sent seqnum: 1355 2021-12-29 13:50:35.737 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.737 Inbound message: 06100421000a04534b00 2021-12-29 13:50:35.737 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.737 ===== datagram 75 acknowledged by IP router 2021-12-29 13:50:35.737 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.737 (idle): zzzz... 2021-12-29 13:50:35.785 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.785 Inbound message: 0610042000150453b3002900bce011fe2458010080 2021-12-29 13:50:35.786 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.786 (idle): zzzz... 2021-12-29 13:50:35.786 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/88 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Richtung_Raumaustragung 2021-12-29 13:50:35.788 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.788 (sendDatagram): >>>>>>> successfully sent seqnum: 1356 2021-12-29 13:50:35.789 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.788 Inbound message: 06100421000a04534c00 2021-12-29 13:50:35.789 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.789 ===== datagram 76 acknowledged by IP router 2021-12-29 13:50:35.790 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.790 (idle): zzzz... 2021-12-29 13:50:35.848 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.848 Inbound message: 0610042000150453b4002900bce011fe245a010080 2021-12-29 13:50:35.849 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.849 (idle): zzzz... 2021-12-29 13:50:35.850 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/90 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Reinigung_aktiv 2021-12-29 13:50:35.947 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.947 Inbound message: 0610042000150453b5002900bce011fe245b010080 2021-12-29 13:50:35.949 - [34mdebug[39m: openknx.0 (11241) [debug] 2021-12-29 12:50:35.949 (idle): zzzz... 2021-12-29 13:50:35.949 - [34mdebug[39m: openknx.0 (11241) Inbound GroupValue_Write 4/4/91 val: false dpt: DPT1 to Object: openknx.0.Heizung.Hargassner_Nano_PK.Mischer_Rücklauf_Auf
Die Fehlermeldung lautet "DPT14: Must supply a number value" und wurde um 13:50:35.434 Uhr aufgezeichnet. Die Meldung vor der Fehler lautete wie folgt:
2021-12-29 13:50:35.433 - [34mdebug[39m: openknx.0 (11241) Outbound GroupValue_Write to 4/6/1 value 0 from openknx.0.Heizung.Photovoltaik.Batterie-Leistung
Das Objekt Batterie-Leistung wird per Modbus ausgelesen und per blockly auf den Bus gesendet.
Die Objektdaten von dem Modbus-Objekt lauten wie folgt:{ "_id": "modbus.0.holdingRegisters.40070_Batterie_Leistung", "type": "state", "common": { "name": "Batterie-Leistung in Watt", "role": "value", "type": "number", "read": true, "write": true, "def": 0, "unit": "W", "custom": { "mqtt-client.0": { "enabled": true, "publish": true, "pubChangesOnly": false, "pubAsObject": false, "qos": false, "retain": false, "subscribe": false, "subChangesOnly": false, "subAsObject": false, "subQos": false, "setAck": false }, "influxdb.0": { "enabled": true, "storageType": "", "aliasId": "", "changesOnly": true, "debounce": 1000, "changesRelogInterval": 60, "changesMinDelta": 0 } } }, "native": { "regType": "holdingRegs", "address": 69, "deviceId": 1, "type": "int32sw", "len": 2, "offset": 0, "factor": 1, "poll": true }, "acl": { "object": 1636, "state": 1636, "file": 1636, "owner": "system.user.admin", "ownerGroup": "system.group.administrator" }, "from": "system.adapter.modbus.0", "user": "system.user.admin", "ts": 1640759338188 }
Die Objekt-Daten von dem KNX-Objekt sehen wie folgt aus:
{ "_id": "openknx.0.Heizung.Photovoltaik.Batterie-Leistung", "type": "state", "common": { "desc": "Basetype: 32-bit floating point value", "name": "Batterie-Leistung", "read": true, "role": "state", "type": "number", "unit": "W", "write": true }, "native": { "address": "4/6/1", "answer_groupValueResponse": false, "autoread": true, "bitlength": 32, "dpt": "DPT14.056", "valuetype": "basic" }, "from": "system.adapter.openknx.0", "user": "system.user.admin", "ts": 1640778701203, "acl": { "object": 1636, "state": 1636, "owner": "system.user.admin", "ownerGroup": "system.group.administrator" } }
Wie sollte ich eurer Meinung nach der DPT für KNX Objekt aussehen?
-
@tombox
Hat sich erledigt. Es kann nichts importiert werden, weil keine DPT definiert sind. Hab für dieses Problem ja eine Lösung gefunden (verwende die bisher erzeugten Objekte weiter). Ansonsten hätte ich mir halt die Arbeit machen müssen und extra für den Import die DPTs definieren müssen. Mach ich vielleicht auch mal. Wie gesagt, das war die Arbeit einer zertifizierten Elektrikerfirma, vor 22 Jahren.Hier gab es mit dem anderen Adapter keine Probleme. Auch die ETS 5 meckert bei einem Prüflauf zwar einiges an, aber nicht die fehlenden DPTs.
-
@chrischros said in Test Adapter OpenKNX 0.1.x:
Leider kann ich die Meldung keiner speziellen GA zuordnen da ich mehrere mit DPT14 habe. Besteht die Möglichkeit das weiter einzugrenzen?
wie schreibst du den Wert mit blockly ? Es muss vom Typ number sein.
-
@chrischros said in Test Adapter OpenKNX 0.1.x:
State value to set for "openknx.0.Dimmen.Dimmen.Außen_-Terrasse-Spots-_Dimmen" has to be stringified but received type "object"
Das ist noch ein Problem vom Adapter, führt aber zu keiner Funktionsbeeinträchtigung.
-
@killroy2 sagte in Test Adapter OpenKNX 0.1.x:
Die Zuordnung zu Status GA wertet der Adapter nicht anhand der alten Konfiguration aus. Das geht jetzt seit v0.1.11 über Alias
Die Zuordnung der Status GA über Alias finde ich eine super Lösung. Ich hab das gleich mal getestet, leider findet die momentane Testversion nur 14 von meinen Status GA. Wenn dir das was bei der Entwicklung hilft kann ich dir gerne meine XML schicken.
-
@mane444 ja schick mal zu, wenn du es veröffentlichen kannst dann irgendwo hier einfügen: https://github.com/iobroker-community-adapters/ioBroker.openknx/issues
-
Hallo,
hatt zufällig jemand eine Lösung gefunden für mein Problem mit
State value to set for "openknx.0.OG.Licht.OG_-_Licht_O5_Zimmer_Eltern_O5_2_Decke_-_dimm" has to be stringified but received type "object"
danke
-
@tiego
Das ist das gleich Problem wie bei mir weiter oben und von @killroy2 bereits beantwortet.@killroy2 said in Test Adapter OpenKNX 0.1.x:
@chrischros said in Test Adapter OpenKNX 0.1.x:
State value to set for "openknx.0.Dimmen.Dimmen.Außen_-Terrasse-Spots-_Dimmen" has to be stringified but received type "object"
Das ist noch ein Problem vom Adapter, führt aber zu keiner Funktionsbeeinträchtigung.
Ist noch ein Problem im Adapter, nichts schlimmes.
-
@killroy2 aktuell sieht das bei blockly so bei mir aus:
Muss aber dazu sagen das sind meine ersten Gehversuche mit blockly. Gut möglich das ich die falsche Elemente benutze. Zumindest kann ich hier nicht sehen wo ich den Datentyp definieren kann.
-
@tombox
Was mir noch aufgefallen ist beim Erstellen der alias DP werden keine Einheiten eingetragen. z.B. bei Solltemperaturen. -
@chrischros es scheint so als würdest du keine Zahl übertragen. Ich versuche gerade ein aussagekräftige Fehlermeldung einzubauen
-
@tombox Das kuriose ist ja, dass ich trotz der Fehlermeldung Daten auf den BUS bekomme, die vorläufig iO aussehen. Auch in der ETS kann ich nicht wirklich einen Fehler in dem übermittelten Wert sehen.
Ich muss morgen oder die Tage mal schauen wenn wieder etwas Leistung in und aus der Batterie gefördert wird.