  1. ioBroker Community Home
  2. Deutsch
  3. ioBroker Allgemein
  4. Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.0k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.8k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.0k

Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe

Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe

Scheduled Pinned Locked Moved ioBroker Allgemein
modbustuyawärmepumpeelfinew11
47 Posts 5 Posters 2.9k Views 1 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • wendy2702W Online
    wendy2702W Online
    wendy2702
    wrote on last edited by
    #16

    Es ist dunkel, viele WRs liefern dann null Daten.

    Bitte testen wenn Produktion.

    @Thomas-Braun : node ist zwar nicht aktuell aber auch zu 98% nicht die Ursache

    Bitte keine Fragen per PN, die gehören ins Forum!

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    Thomas BraunT wendy2702W 2 Replies Last reply
    0
    • wendy2702W wendy2702

      Es ist dunkel, viele WRs liefern dann null Daten.

      Bitte testen wenn Produktion.

      @Thomas-Braun : node ist zwar nicht aktuell aber auch zu 98% nicht die Ursache

      Thomas BraunT Online
      Thomas BraunT Online
      Thomas Braun
      Most Active
      wrote on last edited by
      #17

      @wendy2702 sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

      @Thomas-Braun : node ist zwar nicht aktuell aber auch zu 98% nicht die Ursache

      Das ist ja wurscht. Ist unabhängig vom konkreten Problem schleunigst zu aktualisieren.
      Der Rest vom System ist dann erfahrungsgemäß auch nicht aktuell.
      Das alles trägt dann auch nicht zu einem stabilen Gesamtsystem bei.

      Linux-Werkzeugkasten:
      https://forum.iobroker.net/topic/42952/der-kleine-iobroker-linux-werkzeugkasten
      NodeJS Fixer Skript:
      https://forum.iobroker.net/topic/68035/iob-node-fix-skript
      iob_diag: curl -sLf -o diag.sh https://iobroker.net/diag.sh && bash diag.sh

      1 Reply Last reply
      0
      • wendy2702W wendy2702

        Es ist dunkel, viele WRs liefern dann null Daten.

        Bitte testen wenn Produktion.

        @Thomas-Braun : node ist zwar nicht aktuell aber auch zu 98% nicht die Ursache

        wendy2702W Online
        wendy2702W Online
        wendy2702
        wrote on last edited by
        #18

        @wendy2702 sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

        Es ist dunkel, viele WRs liefern dann null Daten.

        Bitte testen wenn Produktion.

        Hier steht an der Stelle Blödsinn.

        Hatte beim Schreiben einen Wechselrichter im kopf und keine Wärmepumpe.

        Bitte keine Fragen per PN, die gehören ins Forum!

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        H 1 Reply Last reply
        0
        • wendy2702W wendy2702

          @wendy2702 sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

          Es ist dunkel, viele WRs liefern dann null Daten.

          Bitte testen wenn Produktion.

          Hier steht an der Stelle Blödsinn.

          Hatte beim Schreiben einen Wechselrichter im kopf und keine Wärmepumpe.

          H Offline
          H Offline
          Habedere
          wrote on last edited by Habedere
          #19

          @Thomas-Braun sooo - node update ist erledigt.

          @Homoran @wendy2702
          Wärmepumpe ist eingeschaltet, jedoch nicht aktiv in Produktion. Wenn ich i diesem Stand keine Daten erhalten kann ich es gleich vergessen, da es dann sinnlos ist...

          Habe bissl rum probiert, komme jedoch nicht weiter.
          Hier 16 im Holding Register:

          c54dd46d-7d8e-4f6f-8fe5-08c15662758d-image.png

          b61e48ed-f3e3-4494-aa14-591605b8216a-image.png

          
          modbus.1
          2025-06-25 21:14:32.070	info	Connected to slave 192.168.178.67
          
          modbus.1
          2025-06-25 21:14:31.988	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.3, js-controller: 7.0.6
          
          modbus.1
          2025-06-25 21:14:28.440	info	terminating
          
          modbus.1
          2025-06-25 21:14:27.955	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
          
          modbus.1
          2025-06-25 21:14:27.955	info	terminating
          
          modbus.1
          2025-06-25 21:14:27.939	info	Got terminate signal TERMINATE_YOURSELF
          

          Zumindest bleibt der Adapter grün und ein Objekt erscheint im Baum 🙂
          Aber egal mit welchen Registern ich experimentiere - wenn überhaupt was kommt, dann immer die 0.

          HomoranH 1 Reply Last reply
          0
          • H Habedere

            @Thomas-Braun sooo - node update ist erledigt.

            @Homoran @wendy2702
            Wärmepumpe ist eingeschaltet, jedoch nicht aktiv in Produktion. Wenn ich i diesem Stand keine Daten erhalten kann ich es gleich vergessen, da es dann sinnlos ist...

            Habe bissl rum probiert, komme jedoch nicht weiter.
            Hier 16 im Holding Register:

            c54dd46d-7d8e-4f6f-8fe5-08c15662758d-image.png

            b61e48ed-f3e3-4494-aa14-591605b8216a-image.png

            
            modbus.1
            2025-06-25 21:14:32.070	info	Connected to slave 192.168.178.67
            
            modbus.1
            2025-06-25 21:14:31.988	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.3, js-controller: 7.0.6
            
            modbus.1
            2025-06-25 21:14:28.440	info	terminating
            
            modbus.1
            2025-06-25 21:14:27.955	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
            
            modbus.1
            2025-06-25 21:14:27.955	info	terminating
            
            modbus.1
            2025-06-25 21:14:27.939	info	Got terminate signal TERMINATE_YOURSELF
            

            Zumindest bleibt der Adapter grün und ein Objekt erscheint im Baum 🙂
            Aber egal mit welchen Registern ich experimentiere - wenn überhaupt was kommt, dann immer die 0.

            HomoranH Do not disturb
            HomoranH Do not disturb
            Homoran
            Global Moderator Administrators
            wrote on last edited by
            #20

            @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

            Hier 16 im Holding Register:

            der Haken bei Abfrage fehlt

            kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

            der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

            H 1 Reply Last reply
            0
            • HomoranH Homoran

              @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

              Hier 16 im Holding Register:

              der Haken bei Abfrage fehlt

              H Offline
              H Offline
              Habedere
              wrote on last edited by
              #21

              @homoran
              Habe ich auch probiert - dann gibts ne Fehlermeldung und der Adapter bleibt nicht grün:

              
              modbus.1
              2025-06-25 22:12:10.232	info	Disconnected from slave 192.168.178.67
              
              modbus.1
              2025-06-25 22:12:09.233	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":8000}
              
              modbus.1
              2025-06-25 22:12:09.232	error	Client in error state.
              
              modbus.1
              2025-06-25 22:12:09.232	error	Request timed out.
              
              modbus.1
              2025-06-25 22:12:09.232	warn	Error: undefined
              
              modbus.1
              2025-06-25 22:12:01.230	info	Connected to slave 192.168.178.67
              
              modbus.1
              2025-06-25 22:12:01.146	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.3, js-controller: 7.0.6
              
              modbus.1
              2025-06-25 22:11:57.605	info	terminating
              
              modbus.1
              2025-06-25 22:11:57.120	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
              
              modbus.1
              2025-06-25 22:11:57.120	info	terminating
              
              modbus.1
              2025-06-25 22:11:57.103	info	Got terminate signal TERMINATE_YOURSELF
              
              HomoranH 1 Reply Last reply
              0
              • H Habedere

                @homoran
                Habe ich auch probiert - dann gibts ne Fehlermeldung und der Adapter bleibt nicht grün:

                
                modbus.1
                2025-06-25 22:12:10.232	info	Disconnected from slave 192.168.178.67
                
                modbus.1
                2025-06-25 22:12:09.233	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":8000}
                
                modbus.1
                2025-06-25 22:12:09.232	error	Client in error state.
                
                modbus.1
                2025-06-25 22:12:09.232	error	Request timed out.
                
                modbus.1
                2025-06-25 22:12:09.232	warn	Error: undefined
                
                modbus.1
                2025-06-25 22:12:01.230	info	Connected to slave 192.168.178.67
                
                modbus.1
                2025-06-25 22:12:01.146	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.3, js-controller: 7.0.6
                
                modbus.1
                2025-06-25 22:11:57.605	info	terminating
                
                modbus.1
                2025-06-25 22:11:57.120	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                
                modbus.1
                2025-06-25 22:11:57.120	info	terminating
                
                modbus.1
                2025-06-25 22:11:57.103	info	Got terminate signal TERMINATE_YOURSELF
                
                HomoranH Do not disturb
                HomoranH Do not disturb
                Homoran
                Global Moderator Administrators
                wrote on last edited by Homoran
                #22

                @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                dann gibts ne Fehlermeldung

                die hab ich vermisst 😉
                da sind wir wieder bei

                @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                Error: undefined

                @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                Client in error state.

                ich kenne leider die Einstellungen für den ELFIN nicht.
                Kann man den neu starten?

                Ich vermisse aber auch die Meldung welche Daten für die Abfrage verwendet werden.
                Da kommt wohl gar keine Rückmeldung beim ersten Handshake, so dass die Abfrage gar nicht gestartet wird

                kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                HomoranH 1 Reply Last reply
                0
                • H Habedere

                  @Homoran
                  warum 30015? gute Frage 😄 ein Versuch auf Basis meiner anderer Geräte und bissl Google. Wenn ich was kürzeres eingebe - wie eben nur "15" reagiert der Adapter gleich garnicht drauf. Daher dachte ich das kann so nur falsch sein.

                  Du meinst das hier bzgl. Grundeinstellungen?
                  06cc35f1-5049-4140-9f8d-dd2a0270da85-image.png

                  debug-log muss ich checken. (wenn ich raus gefunden habe wie das geht^^)

                  @wendy2702
                  Bei Adresse 15 passiert nichts - allerdings auch im Eingangsregister.
                  Ich probiere es mal bei Holding Register.

                  Port war frei gewählt - eins kleiner ist mein WR oder WP, weiß gerade nicht. Aber der Port passt bei beiden zusammen.

                  Danke schon mal für eure Teilnahme!

                  Hier das Dokument nochmal als PDF.
                  Modbus RS-485_Sunrain_BYC-TV.pdf

                  HomoranH Do not disturb
                  HomoranH Do not disturb
                  Homoran
                  Global Moderator Administrators
                  wrote on last edited by
                  #23

                  @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                  Port war frei gewählt

                  was bedeutet das.
                  hast du dem Elfin Port 503 für modbus tcp verpasst?

                  Wie sehen denn jetztcdue Grundeinstellungen des Adapters dazu aus?

                  kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                  der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                  1 Reply Last reply
                  0
                  • HomoranH Homoran

                    @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                    dann gibts ne Fehlermeldung

                    die hab ich vermisst 😉
                    da sind wir wieder bei

                    @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                    Error: undefined

                    @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                    Client in error state.

                    ich kenne leider die Einstellungen für den ELFIN nicht.
                    Kann man den neu starten?

                    Ich vermisse aber auch die Meldung welche Daten für die Abfrage verwendet werden.
                    Da kommt wohl gar keine Rückmeldung beim ersten Handshake, so dass die Abfrage gar nicht gestartet wird

                    HomoranH Do not disturb
                    HomoranH Do not disturb
                    Homoran
                    Global Moderator Administrators
                    wrote on last edited by
                    #24

                    @homoran sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                    ich kenne leider die Einstellungen für den ELFIN nicht.

                    Screenshot_20250625-222517_Firefox.jpg

                    welche IP gilt denn jetzt?

                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                    H 2 Replies Last reply
                    0
                    • HomoranH Homoran

                      @homoran sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                      ich kenne leider die Einstellungen für den ELFIN nicht.

                      Screenshot_20250625-222517_Firefox.jpg

                      welche IP gilt denn jetzt?

                      H Offline
                      H Offline
                      Habedere
                      wrote on last edited by Habedere
                      #25

                      @homoran
                      das ist die IP des ioBroker auf meinem Proxmox.
                      Die Einstellungen des EW11 sind oben. Neustart ist durchgeführt.
                      Man sieht anhand dem Status, dass kommuniziert wird denke ich.
                      Richtung WP mehr als zu ioBroker wenn ich es richtig interpretiere.

                      Port 503 ist bei beiden eingestellt. Die Verbindung steht ja wenn der Adapter grün ist und er nicht abbricht.

                      Bzgl. Rückmeldung zum Handshake - das sollte ich wohl auch im Debug Log sehen?

                      hier nochmal die Adapter Einstellungen:
                      fe31de38-c8fd-4deb-99bc-2ae93cb38097-image.png
                      fc29944a-fc04-4699-afc5-318dc60cda83-image.png

                      1 Reply Last reply
                      0
                      • HomoranH Homoran

                        @homoran sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                        ich kenne leider die Einstellungen für den ELFIN nicht.

                        Screenshot_20250625-222517_Firefox.jpg

                        welche IP gilt denn jetzt?

                        H Offline
                        H Offline
                        Habedere
                        wrote on last edited by
                        #26

                        @homoran
                        soooo - jetzt habe ich das mit dem "Adapter in Debug versetzten" erst richtig verstanden. Sorry dafür...
                        Jetzt spuckt das log mehr aus!

                        
                        modbus.1
                        2025-06-26 08:21:12.179	info	Disconnected from slave 192.168.178.67
                        
                        modbus.1
                        2025-06-26 08:21:12.178	debug	Closing client on purpose.
                        
                        modbus.1
                        2025-06-26 08:21:11.179	debug	Cleaning up request fifo.
                        
                        modbus.1
                        2025-06-26 08:21:11.179	debug	Clearing timeout of the current request.
                        
                        modbus.1
                        2025-06-26 08:21:11.179	debug	Socket closed with error
                        
                        modbus.1
                        2025-06-26 08:21:11.178	warn	[DevID_1] Poll error count: 2 code: {"err":"timeout","timeout":8000}
                        
                        modbus.1
                        2025-06-26 08:21:11.178	error	Client in error state.
                        
                        modbus.1
                        2025-06-26 08:21:11.178	error	Request timed out.
                        
                        modbus.1
                        2025-06-26 08:21:11.178	warn	Error: undefined
                        
                        modbus.1
                        2025-06-26 08:21:03.178	debug	[DevID_1/holdingRegs] Poll address 16 - 1 registers
                        
                        modbus.1
                        2025-06-26 08:21:03.178	debug	[DevID_1] Poll start ---------------------
                        
                        modbus.1
                        2025-06-26 08:21:03.177	info	Connected to slave 192.168.178.67
                        
                        modbus.1
                        2025-06-26 08:20:48.173	info	Disconnected from slave 192.168.178.67
                        
                        modbus.1
                        2025-06-26 08:20:48.173	debug	Closing client on purpose.
                        
                        modbus.1
                        2025-06-26 08:20:47.174	debug	Cleaning up request fifo.
                        
                        modbus.1
                        2025-06-26 08:20:47.174	debug	Clearing timeout of the current request.
                        
                        modbus.1
                        2025-06-26 08:20:47.174	debug	Socket closed with error
                        
                        modbus.1
                        2025-06-26 08:20:47.173	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":8000}
                        
                        modbus.1
                        2025-06-26 08:20:47.173	error	Client in error state.
                        
                        modbus.1
                        2025-06-26 08:20:47.173	error	Request timed out.
                        
                        modbus.1
                        2025-06-26 08:20:47.172	warn	Error: undefined
                        
                        modbus.1
                        2025-06-26 08:20:39.172	debug	[DevID_1/holdingRegs] Poll address 16 - 1 registers
                        
                        modbus.1
                        2025-06-26 08:20:39.172	debug	Initialization of scale factors done!
                        
                        modbus.1
                        2025-06-26 08:20:39.172	debug	[DevID_1] Poll start ---------------------
                        
                        modbus.1
                        2025-06-26 08:20:39.171	info	Connected to slave 192.168.178.67
                        
                        modbus.1
                        2025-06-26 08:20:39.129	debug	Add holdingRegisters.16_Test: {"_id":"holdingRegisters.16_Test","type":"state","common":{"name":"Test","role":"value.temperature","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":16,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                        
                        modbus.1
                        2025-06-26 08:20:39.129	debug	Initialize Objects for holdingRegs: [{"_address":"16","name":"Test","description":"Test","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value.temperature","room":"","poll":true,"wp":"","cw":false,"isScale":"","address":16,"deviceId":1,"id":"holdingRegisters.16_Test"}]
                        
                        modbus.1
                        2025-06-26 08:20:39.129	debug	Initialize Objects for inputRegs: []
                        
                        modbus.1
                        2025-06-26 08:20:39.129	debug	Initialize Objects for coils: []
                        
                        modbus.1
                        2025-06-26 08:20:39.129	debug	Initialize Objects for disInputs: []
                        
                        modbus.1
                        2025-06-26 08:20:39.092	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.3, js-controller: 7.0.6
                        
                        modbus.1
                        2025-06-26 08:20:39.069	debug	Plugin sentry Do not initialize Plugin (enabled=false)
                        
                        modbus.1
                        2025-06-26 08:20:39.062	debug	States connected to redis: 127.0.0.1:6379
                        
                        modbus.1
                        2025-06-26 08:20:39.058	debug	States create User PubSub Client
                        
                        modbus.1
                        2025-06-26 08:20:39.058	debug	States create System PubSub Client
                        
                        modbus.1
                        2025-06-26 08:20:39.057	debug	Redis States: Use Redis connection: 127.0.0.1:6379
                        
                        modbus.1
                        2025-06-26 08:20:39.046	debug	Objects connected to redis: 127.0.0.1:9001
                        
                        modbus.1
                        2025-06-26 08:20:39.044	debug	Objects client initialize lua scripts
                        
                        modbus.1
                        2025-06-26 08:20:39.027	debug	Objects create User PubSub Client
                        
                        modbus.1
                        2025-06-26 08:20:39.027	debug	Objects create System PubSub Client
                        
                        modbus.1
                        2025-06-26 08:20:39.027	debug	Objects client ready ... initialize now
                        
                        modbus.1
                        2025-06-26 08:20:39.015	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
                        
                        HomoranH 1 Reply Last reply
                        0
                        • H Habedere

                          @homoran
                          soooo - jetzt habe ich das mit dem "Adapter in Debug versetzten" erst richtig verstanden. Sorry dafür...
                          Jetzt spuckt das log mehr aus!

                          
                          modbus.1
                          2025-06-26 08:21:12.179	info	Disconnected from slave 192.168.178.67
                          
                          modbus.1
                          2025-06-26 08:21:12.178	debug	Closing client on purpose.
                          
                          modbus.1
                          2025-06-26 08:21:11.179	debug	Cleaning up request fifo.
                          
                          modbus.1
                          2025-06-26 08:21:11.179	debug	Clearing timeout of the current request.
                          
                          modbus.1
                          2025-06-26 08:21:11.179	debug	Socket closed with error
                          
                          modbus.1
                          2025-06-26 08:21:11.178	warn	[DevID_1] Poll error count: 2 code: {"err":"timeout","timeout":8000}
                          
                          modbus.1
                          2025-06-26 08:21:11.178	error	Client in error state.
                          
                          modbus.1
                          2025-06-26 08:21:11.178	error	Request timed out.
                          
                          modbus.1
                          2025-06-26 08:21:11.178	warn	Error: undefined
                          
                          modbus.1
                          2025-06-26 08:21:03.178	debug	[DevID_1/holdingRegs] Poll address 16 - 1 registers
                          
                          modbus.1
                          2025-06-26 08:21:03.178	debug	[DevID_1] Poll start ---------------------
                          
                          modbus.1
                          2025-06-26 08:21:03.177	info	Connected to slave 192.168.178.67
                          
                          modbus.1
                          2025-06-26 08:20:48.173	info	Disconnected from slave 192.168.178.67
                          
                          modbus.1
                          2025-06-26 08:20:48.173	debug	Closing client on purpose.
                          
                          modbus.1
                          2025-06-26 08:20:47.174	debug	Cleaning up request fifo.
                          
                          modbus.1
                          2025-06-26 08:20:47.174	debug	Clearing timeout of the current request.
                          
                          modbus.1
                          2025-06-26 08:20:47.174	debug	Socket closed with error
                          
                          modbus.1
                          2025-06-26 08:20:47.173	warn	[DevID_1] Poll error count: 1 code: {"err":"timeout","timeout":8000}
                          
                          modbus.1
                          2025-06-26 08:20:47.173	error	Client in error state.
                          
                          modbus.1
                          2025-06-26 08:20:47.173	error	Request timed out.
                          
                          modbus.1
                          2025-06-26 08:20:47.172	warn	Error: undefined
                          
                          modbus.1
                          2025-06-26 08:20:39.172	debug	[DevID_1/holdingRegs] Poll address 16 - 1 registers
                          
                          modbus.1
                          2025-06-26 08:20:39.172	debug	Initialization of scale factors done!
                          
                          modbus.1
                          2025-06-26 08:20:39.172	debug	[DevID_1] Poll start ---------------------
                          
                          modbus.1
                          2025-06-26 08:20:39.171	info	Connected to slave 192.168.178.67
                          
                          modbus.1
                          2025-06-26 08:20:39.129	debug	Add holdingRegisters.16_Test: {"_id":"holdingRegisters.16_Test","type":"state","common":{"name":"Test","role":"value.temperature","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":16,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                          
                          modbus.1
                          2025-06-26 08:20:39.129	debug	Initialize Objects for holdingRegs: [{"_address":"16","name":"Test","description":"Test","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value.temperature","room":"","poll":true,"wp":"","cw":false,"isScale":"","address":16,"deviceId":1,"id":"holdingRegisters.16_Test"}]
                          
                          modbus.1
                          2025-06-26 08:20:39.129	debug	Initialize Objects for inputRegs: []
                          
                          modbus.1
                          2025-06-26 08:20:39.129	debug	Initialize Objects for coils: []
                          
                          modbus.1
                          2025-06-26 08:20:39.129	debug	Initialize Objects for disInputs: []
                          
                          modbus.1
                          2025-06-26 08:20:39.092	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.3, js-controller: 7.0.6
                          
                          modbus.1
                          2025-06-26 08:20:39.069	debug	Plugin sentry Do not initialize Plugin (enabled=false)
                          
                          modbus.1
                          2025-06-26 08:20:39.062	debug	States connected to redis: 127.0.0.1:6379
                          
                          modbus.1
                          2025-06-26 08:20:39.058	debug	States create User PubSub Client
                          
                          modbus.1
                          2025-06-26 08:20:39.058	debug	States create System PubSub Client
                          
                          modbus.1
                          2025-06-26 08:20:39.057	debug	Redis States: Use Redis connection: 127.0.0.1:6379
                          
                          modbus.1
                          2025-06-26 08:20:39.046	debug	Objects connected to redis: 127.0.0.1:9001
                          
                          modbus.1
                          2025-06-26 08:20:39.044	debug	Objects client initialize lua scripts
                          
                          modbus.1
                          2025-06-26 08:20:39.027	debug	Objects create User PubSub Client
                          
                          modbus.1
                          2025-06-26 08:20:39.027	debug	Objects create System PubSub Client
                          
                          modbus.1
                          2025-06-26 08:20:39.027	debug	Objects client ready ... initialize now
                          
                          modbus.1
                          2025-06-26 08:20:39.015	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
                          
                          HomoranH Do not disturb
                          HomoranH Do not disturb
                          Homoran
                          Global Moderator Administrators
                          wrote on last edited by
                          #27

                          @habedere da muss dir jetzt erstmal jemand helfen, der sich mit dem Elfin auskennt

                          solange

                          @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                          Error: undefined

                          und

                          @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                          Client in error state.

                          kommt geht's nicht weiter.

                          Der Adapter sieht grundsätzlich korrekt konfiguriert aus, allerdings ist deine Annahme

                          @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                          wenn überhaupt was kommt, dann immer die 0.

                          falsch.
                          Solange diese 0 gelb(orange) ist, kommt die nicht, sondern das ist der vom Adapter gesetzte Default Wert.
                          Es kommt also nie etwas

                          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                          H 1 Reply Last reply
                          0
                          • HomoranH Homoran

                            @habedere da muss dir jetzt erstmal jemand helfen, der sich mit dem Elfin auskennt

                            solange

                            @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                            Error: undefined

                            und

                            @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                            Client in error state.

                            kommt geht's nicht weiter.

                            Der Adapter sieht grundsätzlich korrekt konfiguriert aus, allerdings ist deine Annahme

                            @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                            wenn überhaupt was kommt, dann immer die 0.

                            falsch.
                            Solange diese 0 gelb(orange) ist, kommt die nicht, sondern das ist der vom Adapter gesetzte Default Wert.
                            Es kommt also nie etwas

                            H Offline
                            H Offline
                            Habedere
                            wrote on last edited by
                            #28

                            @homoran
                            okay - danke für die Hilfe.
                            Dann muss ich nochmal auf den Hersteller zugehen.

                            Aber kann man anhand des Scrennshots des Konverters eindeutig sagen, dass die Kommunikation des Konverters mit der Wärmepumpe aktiv ist und korrekt verkabelt.
                            Die Verbindung zwischen ioBroker Adapter und Konverter ist theoretisch auch nicht ganz verkehrt.
                            Also liegt es effektiv im Detail?
                            e2a9ea42-d820-41a4-b70b-5c4f81abaf0a-image.png
                            Vielleicht liegt es auch daran, dass ich das Modbus-Signal zwischen zwei Platinen abgreife... Master/Slave; ID usw...

                            HomoranH wendy2702W 2 Replies Last reply
                            0
                            • H Habedere

                              @homoran
                              okay - danke für die Hilfe.
                              Dann muss ich nochmal auf den Hersteller zugehen.

                              Aber kann man anhand des Scrennshots des Konverters eindeutig sagen, dass die Kommunikation des Konverters mit der Wärmepumpe aktiv ist und korrekt verkabelt.
                              Die Verbindung zwischen ioBroker Adapter und Konverter ist theoretisch auch nicht ganz verkehrt.
                              Also liegt es effektiv im Detail?
                              e2a9ea42-d820-41a4-b70b-5c4f81abaf0a-image.png
                              Vielleicht liegt es auch daran, dass ich das Modbus-Signal zwischen zwei Platinen abgreife... Master/Slave; ID usw...

                              HomoranH Do not disturb
                              HomoranH Do not disturb
                              Homoran
                              Global Moderator Administrators
                              wrote on last edited by
                              #29

                              @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                              Die Verbindung zwischen ioBroker Adapter und Konverter ist theoretisch auch nicht ganz verkehrt.

                              wie gesagt, kenne ich das System nicht, nur vom mitlesen.
                              Da gibt es anscheinend RTU, TCP und RTU über TCP.

                              auch andere Einstellungen könnten noch anders als bei RTU sein

                              kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                              der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                              1 Reply Last reply
                              0
                              • H Habedere

                                @homoran
                                okay - danke für die Hilfe.
                                Dann muss ich nochmal auf den Hersteller zugehen.

                                Aber kann man anhand des Scrennshots des Konverters eindeutig sagen, dass die Kommunikation des Konverters mit der Wärmepumpe aktiv ist und korrekt verkabelt.
                                Die Verbindung zwischen ioBroker Adapter und Konverter ist theoretisch auch nicht ganz verkehrt.
                                Also liegt es effektiv im Detail?
                                e2a9ea42-d820-41a4-b70b-5c4f81abaf0a-image.png
                                Vielleicht liegt es auch daran, dass ich das Modbus-Signal zwischen zwei Platinen abgreife... Master/Slave; ID usw...

                                wendy2702W Online
                                wendy2702W Online
                                wendy2702
                                wrote on last edited by
                                #30

                                @habedere Was kann man denn im Elfin einstellen wo jetzt TCP-Server steht?

                                Und welches System hat welche IP?

                                Wie sieht denn die RS485 Verkabelung zwischen Elfin und WP aus? Mal a/b getauscht zum testen?

                                Bitte keine Fragen per PN, die gehören ins Forum!

                                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                H 1 Reply Last reply
                                1
                                • wendy2702W wendy2702

                                  @habedere Was kann man denn im Elfin einstellen wo jetzt TCP-Server steht?

                                  Und welches System hat welche IP?

                                  Wie sieht denn die RS485 Verkabelung zwischen Elfin und WP aus? Mal a/b getauscht zum testen?

                                  H Offline
                                  H Offline
                                  Habedere
                                  wrote on last edited by
                                  #31

                                  @wendy2702
                                  Nachfolgend die anderen Auswahlmöglichkeiten:
                                  2c639d91-9a70-4618-acea-c4fec87c6b1c-image.png

                                  .100 ist der ioBroker.
                                  .67 der Elfin

                                  Die Verkabelung ist recht unspektakulär - bis auf dass ich mich zu einer vorhandenen Klemme hinzu geschalten habe.
                                  A/B habe ich noch nicht getauscht. Wäre eigentlich eindeutig beschriftet. Sofern ich da nichts kaputt machen bzw. stören kann an der WP, tausche ich die eben mal.

                                  HomoranH wendy2702W 2 Replies Last reply
                                  0
                                  • H Habedere

                                    @wendy2702
                                    Nachfolgend die anderen Auswahlmöglichkeiten:
                                    2c639d91-9a70-4618-acea-c4fec87c6b1c-image.png

                                    .100 ist der ioBroker.
                                    .67 der Elfin

                                    Die Verkabelung ist recht unspektakulär - bis auf dass ich mich zu einer vorhandenen Klemme hinzu geschalten habe.
                                    A/B habe ich noch nicht getauscht. Wäre eigentlich eindeutig beschriftet. Sofern ich da nichts kaputt machen bzw. stören kann an der WP, tausche ich die eben mal.

                                    HomoranH Do not disturb
                                    HomoranH Do not disturb
                                    Homoran
                                    Global Moderator Administrators
                                    wrote on last edited by
                                    #32

                                    @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                                    bis auf dass ich mich zu einer vorhandenen Klemme hinzu geschalten habe.

                                    Screenshot_20230620-171550_Firefox.jpg

                                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                    H 1 Reply Last reply
                                    0
                                    • H Habedere

                                      @wendy2702
                                      Nachfolgend die anderen Auswahlmöglichkeiten:
                                      2c639d91-9a70-4618-acea-c4fec87c6b1c-image.png

                                      .100 ist der ioBroker.
                                      .67 der Elfin

                                      Die Verkabelung ist recht unspektakulär - bis auf dass ich mich zu einer vorhandenen Klemme hinzu geschalten habe.
                                      A/B habe ich noch nicht getauscht. Wäre eigentlich eindeutig beschriftet. Sofern ich da nichts kaputt machen bzw. stören kann an der WP, tausche ich die eben mal.

                                      wendy2702W Online
                                      wendy2702W Online
                                      wendy2702
                                      wrote on last edited by
                                      #33

                                      @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                                      Die Verkabelung ist recht unspektakulär - bis auf dass ich mich zu einer vorhandenen Klemme hinzu geschalten habe.

                                      Dann wird das einer der Gründe sein. Wenn da schon eine Modbus kommunikation per RS485 zwischen 2 oder mehreren Geräten stattfindet wird das so nicht klappen.

                                      @Homoran : hat dir ja schon ein schönes Bild dazu geschickt.

                                      Bitte keine Fragen per PN, die gehören ins Forum!

                                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                      HomoranH 1 Reply Last reply
                                      0
                                      • wendy2702W wendy2702

                                        @habedere sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                                        Die Verkabelung ist recht unspektakulär - bis auf dass ich mich zu einer vorhandenen Klemme hinzu geschalten habe.

                                        Dann wird das einer der Gründe sein. Wenn da schon eine Modbus kommunikation per RS485 zwischen 2 oder mehreren Geräten stattfindet wird das so nicht klappen.

                                        @Homoran : hat dir ja schon ein schönes Bild dazu geschickt.

                                        HomoranH Do not disturb
                                        HomoranH Do not disturb
                                        Homoran
                                        Global Moderator Administrators
                                        wrote on last edited by
                                        #34

                                        @wendy2702 sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                                        per RS485 zwischen 2 oder mehreren Geräten stattfindet

                                        @Habedere
                                        haben denn alle Geräte am Bus auch eindeutige IDs?
                                        und passt die ID in der Modbus-Instanz dazu?

                                        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                        wendy2702W 1 Reply Last reply
                                        0
                                        • HomoranH Homoran

                                          @wendy2702 sagte in Modbusverbindung - Elfin EW11 / Sunrain Wärmepumpe:

                                          per RS485 zwischen 2 oder mehreren Geräten stattfindet

                                          @Habedere
                                          haben denn alle Geräte am Bus auch eindeutige IDs?
                                          und passt die ID in der Modbus-Instanz dazu?

                                          wendy2702W Online
                                          wendy2702W Online
                                          wendy2702
                                          wrote on last edited by
                                          #35

                                          @homoran Ich denke das Problem wird eher sein das es bereits einen Master gibt, dann könnte es eventuell funktionieren wenn er den Adapter als Slave konfiguriert.

                                          Bitte keine Fragen per PN, die gehören ins Forum!

                                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                          1 Reply Last reply
                                          0
                                          Reply
                                          • Reply as topic
                                          Log in to reply
                                          • Oldest to Newest
                                          • Newest to Oldest
                                          • Most Votes


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          407

                                          Online

                                          32.4k

                                          Users

                                          81.3k

                                          Topics

                                          1.3m

                                          Posts
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Login

                                          • Don't have an account? Register

                                          • Login or register to search.
                                          • First post
                                            Last post
                                          0
                                          • Recent
                                          • Tags
                                          • Unread 0
                                          • Categories
                                          • Unreplied
                                          • Popular
                                          • GitHub
                                          • Docu
                                          • Hilfe