  1. ioBroker Community Home
  2. Deutsch
  3. Skripten / Logik
  4. JavaScript
  5. E3DC Hauskraftwerk steuern

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.6k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.1k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    2.9k

E3DC Hauskraftwerk steuern

Geplant Angeheftet Gesperrt Verschoben JavaScript
3.5k Beiträge 70 Kommentatoren 1.6m Aufrufe 61 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • A ArnoD

    @psrelax sagte in E3DC Hauskraftwerk steuern:

    Theoretisch sollte ja dann bei Aktivierung von "PV Module schneefrei" auch bei meinem Hochnebel funktionieren, oder? Wie wird dann die Ladezeit berechnet?

    Ja, ist nur ein Schalter, mit dem die PV-Prognose ignoriert wird.
    An der Berechnung der Ladezeit ändert sich nichts dadurch, es wird nur nicht mehr geprüft, ob eventuell die PV-Leistung ausreichen würde, um die Batterie zu laden.

    P Online
    P Online
    psrelax
    schrieb am zuletzt editiert von
    #2945

    @arnod
    Ich habe gerade gesehen, dass die neue Version meine Entladesperre setzt, da der Batteriepreis höher ist, als der Tibber Preis.

    Der Sinn dahinter erschließt sich mir nicht.
    Nach meinem Verständnis sollte jetzt bei 0,34€ noch aus dem Speicher gezogen werden und bei 0,30€ kann dann wieder günstiger nachgeladen werden.
    Wenn ich den Haken (Batteriepreis berücksichtigen) entferne, dann ist der Batteriepreis um 0,04€ niedriger und die Entladesperre ist weg.
    Stimmt denn dann die Formel überhaupt noch? Damit würde ich auf 0,38€ kommen, wenn ich mich nicht verrechnet habe.
    Screenshot 2024-11-05 214428.jpg

    A 1 Antwort Letzte Antwort
    0
    • P psrelax

      @arnod
      Ich habe gerade gesehen, dass die neue Version meine Entladesperre setzt, da der Batteriepreis höher ist, als der Tibber Preis.

      Der Sinn dahinter erschließt sich mir nicht.
      Nach meinem Verständnis sollte jetzt bei 0,34€ noch aus dem Speicher gezogen werden und bei 0,30€ kann dann wieder günstiger nachgeladen werden.
      Wenn ich den Haken (Batteriepreis berücksichtigen) entferne, dann ist der Batteriepreis um 0,04€ niedriger und die Entladesperre ist weg.
      Stimmt denn dann die Formel überhaupt noch? Damit würde ich auf 0,38€ kommen, wenn ich mich nicht verrechnet habe.
      Screenshot 2024-11-05 214428.jpg

      A Online
      A Online
      ArnoD
      schrieb am zuletzt editiert von
      #2946

      @psrelax
      Dann rechnen wir mal 😊
      Wenn die Batterie aus dem Netz auf 1 kWh geladen wird zu einem Preis von 0,30€ bei einem Systemwirkungsgrad inkl. Batterie von 88% (12% Verlust) würde die Rechnung so aussehen:
      Für 1 kWh Hausverbrauch muss die Batterie 1 kWh +12% aus dem Netzt Strom beziehen = 1,12 kWh
      1,12 kWh kosten bei 0,30 € = 0,336 €
      Somit kostet 1 kWh aus der Batterie 0,336 €
      Im Skript ist die Formel strompreisBatterie * (1 / (systemwirkungsgrad / 100))
      strompreisBatterie = 0,30 € um beim gleichen Beispiel zu bleiben.
      Systemwirkungsgrad = 88%
      0,30 * (1/(88/100) = 0,340 Batteriepreis

      P 1 Antwort Letzte Antwort
      0
      • D Offline
        D Offline
        dataeasy
        schrieb am zuletzt editiert von dataeasy
        #2947

        Hi in die Runde ich verzeifel gerade ein wenig.. bis dato klappte das LAden via selbst gebautem Skript gesteuert via Tibber preis immer in die ich die s.u. Datenpunkte des E3Dc via e3dc-escp getriggert habe ohne Probleme... Jetzt wollte ich mal E3DC Controll ausprobieren und seid dem klappt mein einfaches Script nicht mehr wo ist mein Ich habe die E3dc Controll Programmanteile alle deaktiviert aber es geht nicht mehr !!! dann alles gelöscht klappt auch nicht !!

        Folgende Trigger setze ich... den Set_POWER_MODE auf Grid_Charge (4)
        2f58319e-38eb-4793-b86a-947bccc03cdf-grafik.png

        mit folgenden Programmzeilen !

        2b91d720-ce3d-4d67-8194-1f0d0d2f20fb-grafik.png

        bis dato klappe immer alles jetzt leider nicht mehr hat einer ggf eine Tip ?

        Wie ist das aktuelle Verhalten..... er fängt kurz an zu laden aus dem Netz hört dann aber wieder auf...

        Danke und Grüße

        A 1 Antwort Letzte Antwort
        0
        • A Online
          A Online
          ArnoD
          schrieb am zuletzt editiert von
          #2948

          Tibber Skript,
          Version: 1.2.3 auf Github hochgeladen.

          Änderungen:

          • Fehler behoben, dass die Entladesperre ständig ein und aus geschaltet wurde, wenn Batterie SOC reicht, um nächste Peak Phase zu überbrücken
          1 Antwort Letzte Antwort
          0
          • D dataeasy

            Hi in die Runde ich verzeifel gerade ein wenig.. bis dato klappte das LAden via selbst gebautem Skript gesteuert via Tibber preis immer in die ich die s.u. Datenpunkte des E3Dc via e3dc-escp getriggert habe ohne Probleme... Jetzt wollte ich mal E3DC Controll ausprobieren und seid dem klappt mein einfaches Script nicht mehr wo ist mein Ich habe die E3dc Controll Programmanteile alle deaktiviert aber es geht nicht mehr !!! dann alles gelöscht klappt auch nicht !!

            Folgende Trigger setze ich... den Set_POWER_MODE auf Grid_Charge (4)
            2f58319e-38eb-4793-b86a-947bccc03cdf-grafik.png

            mit folgenden Programmzeilen !

            2b91d720-ce3d-4d67-8194-1f0d0d2f20fb-grafik.png

            bis dato klappe immer alles jetzt leider nicht mehr hat einer ggf eine Tip ?

            Wie ist das aktuelle Verhalten..... er fängt kurz an zu laden aus dem Netz hört dann aber wieder auf...

            Danke und Grüße

            A Online
            A Online
            ArnoD
            schrieb am zuletzt editiert von
            #2949

            @dataeasy
            Welche der beiden Objekt ID's setzt du denn SET_POWER_MODE?
            Du musst SET_POWER_VALUE mindestens alle 4 sek. neu setzen, damit E3DC nicht wieder die Steuerung übernimmt.

            Leider kann ich dir bei Blockly nicht helfen, ist so gar nicht mein Ding :-)

            D 1 Antwort Letzte Antwort
            0
            • A ArnoD

              @psrelax
              Dann rechnen wir mal 😊
              Wenn die Batterie aus dem Netz auf 1 kWh geladen wird zu einem Preis von 0,30€ bei einem Systemwirkungsgrad inkl. Batterie von 88% (12% Verlust) würde die Rechnung so aussehen:
              Für 1 kWh Hausverbrauch muss die Batterie 1 kWh +12% aus dem Netzt Strom beziehen = 1,12 kWh
              1,12 kWh kosten bei 0,30 € = 0,336 €
              Somit kostet 1 kWh aus der Batterie 0,336 €
              Im Skript ist die Formel strompreisBatterie * (1 / (systemwirkungsgrad / 100))
              strompreisBatterie = 0,30 € um beim gleichen Beispiel zu bleiben.
              Systemwirkungsgrad = 88%
              0,30 * (1/(88/100) = 0,340 Batteriepreis

              P Online
              P Online
              psrelax
              schrieb am zuletzt editiert von
              #2950

              @arnod sagte in E3DC Hauskraftwerk steuern:

              Dann rechnen wir mal

              Ich seh schon. Ein Mathekurs in der VHS wäre nötig :joy:

              Heute war ja super zum testen.
              Folgende Einstellung und Ladecharakteristik hat sich heute ergeben.
              89a194d1-922b-415e-bf54-d1af53a44b72-image.png
              Theoretisch funktioniert das.
              Ich habe "Schneebedekt" angehakt, da meine Prognose aktuell überhaupt nicht hin kommt. Wir haben den ganzen Tag Nebel.
              07ed7311-4aee-40ae-b26d-58281355acc7-image.png
              Für diese Einstellung, wurde für meinen Geschmack aber auch viel zu kurz geladen, da ich gerade so mit Mühe und Not hin komme mit der Ladung.
              c5104fdf-5468-422b-82cc-4fb886f290dc-image.png

              2024-11-06 11:00:00.286  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Charge_Control: -==== Tibber output signal BatterieLaden wurde in true geändert ====-
              2024-11-06 11:00:01.311  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
              2024-11-06 11:00:01.311  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 586425281,593236836
              2024-11-06 11:00:01.311  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-06T07:00:00.000Z","2024-11-06T11:00:00.631Z"]
              2024-11-06 11:00:01.311  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Auto","Laden"]
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.2997
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 23
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 201
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = -35
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 1
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 660:00 h / 2:11 h
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.2868
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.3259
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3327
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].endLocale = 6.11.2024, 20:00:00
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].startLocale = 6.11.2024, 16:00:00
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].Type = peak
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].endLocale = 6.11.2024, 16:00:00
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].startLocale = 6.11.2024, 15:00:00
              2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].Type = high
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.endLocale = 6.11.2024, 15:00:00
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.startLocale = 6.11.2024, 08:00:00
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.Type = normal
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert Spitzenstrompreis = 0.5682
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert hoher Strompreis = 
              0.50	
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert niedriger Strompreis = 
              0.10	
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** schneeBedeckt = true
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung heute = 28.089600000000004 kWh
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung morgen = 28.089600000000004 kWh
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** pvLeistungAusreichend = false
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** eAutoLaden = true
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieEntladenSperren = false
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieLaden = true
              2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Status = Batteriepreis = 0.2868 Laden von 11:00 Uhr bis 12:00 Uhr (aktive Phase: normal)
              2024-11-06 11:00:01.313  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** ProgrammAblauf = 27,1,18,18/1,21,31,19,11,13,29,29,31, 
              
              2024-11-06 11:51:00.507  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: *******************  Debug LOG Tibber Skript Version 1.2.2 *******************
              2024-11-06 11:52:00.386  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
              2024-11-06 11:52:00.386  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 586425281,595325392
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-06T07:00:00.000Z","2024-11-06T11:52:00.273Z"]
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Auto","Laden"]
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.2997
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 67
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 7938
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 8261
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 1
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 7:57 h / 7:57 h
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.321
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.3648
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3327
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].endLocale = 6.11.2024, 20:00:00
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].startLocale = 6.11.2024, 16:00:00
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].Type = peak
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].endLocale = 6.11.2024, 16:00:00
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].startLocale = 6.11.2024, 15:00:00
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].Type = high
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.endLocale = 6.11.2024, 15:00:00
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.startLocale = 6.11.2024, 08:00:00
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.Type = normal
              2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert Spitzenstrompreis = 0.5682
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert hoher Strompreis = 
              0.50	
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert niedriger Strompreis = 
              0.10	
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** schneeBedeckt = true
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung heute = 28.089600000000004 kWh
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung morgen = 28.089600000000004 kWh
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** pvLeistungAusreichend = false
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** eAutoLaden = true
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieEntladenSperren = false
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieLaden = true
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Status = Batteriepreis = 0.321 Laden von 11:00 Uhr bis 12:52 Uhr (aktive Phase: normal)
              2024-11-06 11:52:00.388  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** ProgrammAblauf = 27,1,18,18/1,21,31,19,11,13,29,29,31, 
              2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: *******************  Debug LOG Tibber Skript Version 1.2.2 *******************
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 586425281,595365581
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-06T07:00:00.000Z","2024-11-06T11:53:00.147Z"]
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Auto","Laden"]
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.2997
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 68
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 7902
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 8327
              2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 1
              2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 8:03 h / 8:03 h
              2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
              2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.3212
              2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.365
              2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3327
              2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].endLocale = 6.11.2024, 20:00:00
              2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].startLocale = 6.11.2024, 16:00:00
              2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].Type = peak
              2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].endLocale = 6.11.2024, 16:00:00
              2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].startLocale = 6.11.2024, 15:00:00
              2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].Type = high
              2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.endLocale = 6.11.2024, 15:00:00
              2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.startLocale = 6.11.2024, 08:00:00
              2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.Type = normal
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert Spitzenstrompreis = 0.5682
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert hoher Strompreis = 
              0.50	
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert niedriger Strompreis = 
              0.10	
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** schneeBedeckt = true
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung heute = 28.089600000000004 kWh
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung morgen = 28.089600000000004 kWh
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** pvLeistungAusreichend = false
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** eAutoLaden = true
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieEntladenSperren = false
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieLaden = true
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Status = Batteriepreis = 0.3212 Laden von 11:00 Uhr bis 12:53 Uhr (aktive Phase: normal)
              2024-11-06 11:53:00.249  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** ProgrammAblauf = 27,1,18,18/1,21,31,19,11,13,29,29,31, 
              2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: *******************  Debug LOG Tibber Skript Version 1.2.2 *******************
              2024-11-06 11:54:00.392  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Charge_Control: -==== Tibber output signal BatterieLaden wurde in false geändert ====-
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 586425281,595406185,595406299
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-06T07:00:00.000Z","2024-11-06T19:00:00.000Z","2024-11-06T23:00:00.000Z"]
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,true,false]
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Auto","Laden","Laden"]
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.2997
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 69
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 7890
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 8304
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 1
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 8:11 h / 8:11 h
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.3214
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.3652
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3327
              2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].endLocale = 6.11.2024, 20:00:00
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].startLocale = 6.11.2024, 16:00:00
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].Type = peak
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].endLocale = 6.11.2024, 16:00:00
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].startLocale = 6.11.2024, 15:00:00
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].Type = high
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.endLocale = 6.11.2024, 15:00:00
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.startLocale = 6.11.2024, 08:00:00
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.Type = normal
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert Spitzenstrompreis = 0.5682
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert hoher Strompreis = 
              0.50	
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert niedriger Strompreis = 
              0.10	
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** schneeBedeckt = true
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung heute = 28.089600000000004 kWh
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung morgen = 28.089600000000004 kWh
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** pvLeistungAusreichend = false
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** eAutoLaden = true
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieEntladenSperren = false
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieLaden = false
              2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Status = warte auf niedrigere Preise von 20:00 Uhr bis 00:00 Uhr  (aktive Phase: normal)
              2024-11-06 11:54:00.592  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** ProgrammAblauf = 27,1,18,18/1,21,31,19,11,12,29,29, 
              
              A 1 Antwort Letzte Antwort
              0
              • A ArnoD

                @dataeasy
                Welche der beiden Objekt ID's setzt du denn SET_POWER_MODE?
                Du musst SET_POWER_VALUE mindestens alle 4 sek. neu setzen, damit E3DC nicht wieder die Steuerung übernimmt.

                Leider kann ich dir bei Blockly nicht helfen, ist so gar nicht mein Ding :-)

                D Offline
                D Offline
                dataeasy
                schrieb am zuletzt editiert von dataeasy
                #2951

                @arnod ne musste ich bis dato nicht... hat alles geklappt ohne den 4 SEC Trigger ... Ich setzte bei Objekt SET_POWER_MODE entwender "0" für Normal bzw. "4" für Grid_Charge udn dann noch die Ladeleistung "z.b 9000 Watt mehr nicht.
                Wobei es jetzt wieder läuft nachdem ich E3DC_rscp und mein Blocky wieder neu installiert habe sehr komisch.. Ich hatte im Zuge des ausprobierens deines Scriptes auch die Abfrageintervallwerte angepasst nach deinen Vorgaben ggf war das das Problem.... Danke trotzdem.. wie gesagt bei mir klappt das ohne den 4 SEC Trigger schon seid über einem Jahr !!! frag mich aber bitte nicht warum.

                Hatte dazu ja auch mal eine Anleitung hier ins Forum gepostet ....
                E3DC Hauskraftwerk via Tibber laden

                A 1 Antwort Letzte Antwort
                0
                • D dataeasy

                  @arnod ne musste ich bis dato nicht... hat alles geklappt ohne den 4 SEC Trigger ... Ich setzte bei Objekt SET_POWER_MODE entwender "0" für Normal bzw. "4" für Grid_Charge udn dann noch die Ladeleistung "z.b 9000 Watt mehr nicht.
                  Wobei es jetzt wieder läuft nachdem ich E3DC_rscp und mein Blocky wieder neu installiert habe sehr komisch.. Ich hatte im Zuge des ausprobierens deines Scriptes auch die Abfrageintervallwerte angepasst nach deinen Vorgaben ggf war das das Problem.... Danke trotzdem.. wie gesagt bei mir klappt das ohne den 4 SEC Trigger schon seid über einem Jahr !!! frag mich aber bitte nicht warum.

                  Hatte dazu ja auch mal eine Anleitung hier ins Forum gepostet ....
                  E3DC Hauskraftwerk via Tibber laden

                  A Online
                  A Online
                  ArnoD
                  schrieb am zuletzt editiert von ArnoD
                  #2952

                  @dataeasy sagte in E3DC Hauskraftwerk steuern:

                  wie gesagt bei mir klappt das ohne den 4 SEC Trigger schon seid über einem Jahr !!! frag mich aber bitte nicht warum.

                  Warum ist schon klar, weil beim Adapter e3dc-rscp in der Standardeinstellung bei SET_POWER Wiederholintervall 5 sek. eingestellt sind. Somit wiederholt der Adapter deinen Wert alle 5 sek.
                  Dir muss nur bewusst sein, dass es zu unerwünschten Verhalten kommen kann, wenn dein Blockly mal nicht mehr reagiert. Dann wird die letzte Einstellung ewig wiederholt, obwohl du das eventuell gar nicht mehr beabsichtigst.
                  Würde bedeuten die Batterie wird immer geladen oder entladen je nachdem, was zuletzt eingestellt war.

                  1 Antwort Letzte Antwort
                  0
                  • P psrelax

                    @arnod sagte in E3DC Hauskraftwerk steuern:

                    Dann rechnen wir mal

                    Ich seh schon. Ein Mathekurs in der VHS wäre nötig :joy:

                    Heute war ja super zum testen.
                    Folgende Einstellung und Ladecharakteristik hat sich heute ergeben.
                    89a194d1-922b-415e-bf54-d1af53a44b72-image.png
                    Theoretisch funktioniert das.
                    Ich habe "Schneebedekt" angehakt, da meine Prognose aktuell überhaupt nicht hin kommt. Wir haben den ganzen Tag Nebel.
                    07ed7311-4aee-40ae-b26d-58281355acc7-image.png
                    Für diese Einstellung, wurde für meinen Geschmack aber auch viel zu kurz geladen, da ich gerade so mit Mühe und Not hin komme mit der Ladung.
                    c5104fdf-5468-422b-82cc-4fb886f290dc-image.png

                    2024-11-06 11:00:00.286  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Charge_Control: -==== Tibber output signal BatterieLaden wurde in true geändert ====-
                    2024-11-06 11:00:01.311  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                    2024-11-06 11:00:01.311  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 586425281,593236836
                    2024-11-06 11:00:01.311  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-06T07:00:00.000Z","2024-11-06T11:00:00.631Z"]
                    2024-11-06 11:00:01.311  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Auto","Laden"]
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.2997
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 23
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 201
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = -35
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 1
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 660:00 h / 2:11 h
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.2868
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.3259
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3327
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].endLocale = 6.11.2024, 20:00:00
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].startLocale = 6.11.2024, 16:00:00
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].Type = peak
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].endLocale = 6.11.2024, 16:00:00
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].startLocale = 6.11.2024, 15:00:00
                    2024-11-06 11:00:01.312  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].Type = high
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.endLocale = 6.11.2024, 15:00:00
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.startLocale = 6.11.2024, 08:00:00
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.Type = normal
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert Spitzenstrompreis = 0.5682
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert hoher Strompreis = 
                    0.50	
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert niedriger Strompreis = 
                    0.10	
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** schneeBedeckt = true
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung heute = 28.089600000000004 kWh
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung morgen = 28.089600000000004 kWh
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** pvLeistungAusreichend = false
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** eAutoLaden = true
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieEntladenSperren = false
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieLaden = true
                    2024-11-06 11:00:01.313  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Status = Batteriepreis = 0.2868 Laden von 11:00 Uhr bis 12:00 Uhr (aktive Phase: normal)
                    2024-11-06 11:00:01.313  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** ProgrammAblauf = 27,1,18,18/1,21,31,19,11,13,29,29,31, 
                    
                    2024-11-06 11:51:00.507  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: *******************  Debug LOG Tibber Skript Version 1.2.2 *******************
                    2024-11-06 11:52:00.386  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                    2024-11-06 11:52:00.386  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 586425281,595325392
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-06T07:00:00.000Z","2024-11-06T11:52:00.273Z"]
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Auto","Laden"]
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.2997
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 67
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 7938
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 8261
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 1
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 7:57 h / 7:57 h
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.321
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.3648
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3327
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].endLocale = 6.11.2024, 20:00:00
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].startLocale = 6.11.2024, 16:00:00
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].Type = peak
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].endLocale = 6.11.2024, 16:00:00
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].startLocale = 6.11.2024, 15:00:00
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].Type = high
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.endLocale = 6.11.2024, 15:00:00
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.startLocale = 6.11.2024, 08:00:00
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.Type = normal
                    2024-11-06 11:52:00.387  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert Spitzenstrompreis = 0.5682
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert hoher Strompreis = 
                    0.50	
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert niedriger Strompreis = 
                    0.10	
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** schneeBedeckt = true
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung heute = 28.089600000000004 kWh
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung morgen = 28.089600000000004 kWh
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** pvLeistungAusreichend = false
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** eAutoLaden = true
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieEntladenSperren = false
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieLaden = true
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Status = Batteriepreis = 0.321 Laden von 11:00 Uhr bis 12:52 Uhr (aktive Phase: normal)
                    2024-11-06 11:52:00.388  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** ProgrammAblauf = 27,1,18,18/1,21,31,19,11,13,29,29,31, 
                    2024-11-06 11:52:00.388  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: *******************  Debug LOG Tibber Skript Version 1.2.2 *******************
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 586425281,595365581
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-06T07:00:00.000Z","2024-11-06T11:53:00.147Z"]
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Auto","Laden"]
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.2997
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 68
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 7902
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 8327
                    2024-11-06 11:53:00.246  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 1
                    2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 8:03 h / 8:03 h
                    2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                    2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.3212
                    2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.365
                    2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3327
                    2024-11-06 11:53:00.247  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].endLocale = 6.11.2024, 20:00:00
                    2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].startLocale = 6.11.2024, 16:00:00
                    2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].Type = peak
                    2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].endLocale = 6.11.2024, 16:00:00
                    2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].startLocale = 6.11.2024, 15:00:00
                    2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].Type = high
                    2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.endLocale = 6.11.2024, 15:00:00
                    2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.startLocale = 6.11.2024, 08:00:00
                    2024-11-06 11:53:00.248  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.Type = normal
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert Spitzenstrompreis = 0.5682
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert hoher Strompreis = 
                    0.50	
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert niedriger Strompreis = 
                    0.10	
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** schneeBedeckt = true
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung heute = 28.089600000000004 kWh
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung morgen = 28.089600000000004 kWh
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** pvLeistungAusreichend = false
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** eAutoLaden = true
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieEntladenSperren = false
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieLaden = true
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Status = Batteriepreis = 0.3212 Laden von 11:00 Uhr bis 12:53 Uhr (aktive Phase: normal)
                    2024-11-06 11:53:00.249  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** ProgrammAblauf = 27,1,18,18/1,21,31,19,11,13,29,29,31, 
                    2024-11-06 11:53:00.249  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: *******************  Debug LOG Tibber Skript Version 1.2.2 *******************
                    2024-11-06 11:54:00.392  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Charge_Control: -==== Tibber output signal BatterieLaden wurde in false geändert ====-
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 586425281,595406185,595406299
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-06T07:00:00.000Z","2024-11-06T19:00:00.000Z","2024-11-06T23:00:00.000Z"]
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,true,false]
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Auto","Laden","Laden"]
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.2997
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 69
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 7890
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 8304
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 1
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 8:11 h / 8:11 h
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.3214
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.3652
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3327
                    2024-11-06 11:54:00.591  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].endLocale = 6.11.2024, 20:00:00
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].startLocale = 6.11.2024, 16:00:00
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[1].Type = peak
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].endLocale = 6.11.2024, 16:00:00
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].startLocale = 6.11.2024, 15:00:00
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** naechstePhasen[0].Type = high
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.endLocale = 6.11.2024, 15:00:00
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.startLocale = 6.11.2024, 08:00:00
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** aktivePhase.Type = normal
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert Spitzenstrompreis = 0.5682
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert hoher Strompreis = 
                    0.50	
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Schwellwert niedriger Strompreis = 
                    0.10	
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** schneeBedeckt = true
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung heute = 28.089600000000004 kWh
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Prognose PV-Leistung morgen = 28.089600000000004 kWh
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** pvLeistungAusreichend = false
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** eAutoLaden = true
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieEntladenSperren = false
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** BatterieLaden = false
                    2024-11-06 11:54:00.592  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Status = warte auf niedrigere Preise von 20:00 Uhr bis 00:00 Uhr  (aktive Phase: normal)
                    2024-11-06 11:54:00.592  - warn: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** ProgrammAblauf = 27,1,18,18/1,21,31,19,11,12,29,29, 
                    
                    A Online
                    A Online
                    ArnoD
                    schrieb am zuletzt editiert von ArnoD
                    #2953

                    @psrelax
                    Ok, das ist jetzt nicht normal.
                    Da muss ich mir die Funktion für die Aufteilung der Phasen noch mal ansehen.
                    Um 11:54 Uhr wurde für 20:00 Uhr ein niedriger Strompreis erkannt, was ja nicht richtig ist.
                    Da ist noch ein Fehler drin.
                    Danke für dein LOG File.

                    Nachtrag:
                    OK, Fehler gefunden, es wird die falsche Phase gesucht. Es sollte nur abgebrochen werden, wenn der Schwellwert niedriger Strompreis innerhalb der Batteriereichweite unterschritten wird ( lowPhase ) und nicht der Schwellwert hoher Strompreis (normalPhase). Werde ich gleich korrigieren.

                    1 Antwort Letzte Antwort
                    0
                    • A Online
                      A Online
                      ArnoD
                      schrieb am zuletzt editiert von
                      #2954

                      Tibber Skript,
                      Version: 1.2.4 auf Github hochgeladen.

                      Änderungen:

                      • Fehler behoben, dass normalPhases anstatt lowPhases abgefragt wurde und dadurch das Laden der Batterie frühzeitig beendet wurde.
                      P 1 Antwort Letzte Antwort
                      0
                      • bluebeanB Offline
                        bluebeanB Offline
                        bluebean
                        schrieb am zuletzt editiert von bluebean
                        #2955

                        @ArnoD
                        Ich muss hier einfach mal wieder meinen großen Dank an Dich ausdrücken - selten habe ich Maintainer mit einem derart stetigen und sachkundigen Engagement erlebt, der selbst in schwierigen Situationen mit einer derart großen Ruhe und Energie an dem Projekt dran bleibt!!

                        A 1 Antwort Letzte Antwort
                        1
                        • bluebeanB bluebean

                          @ArnoD
                          Ich muss hier einfach mal wieder meinen großen Dank an Dich ausdrücken - selten habe ich Maintainer mit einem derart stetigen und sachkundigen Engagement erlebt, der selbst in schwierigen Situationen mit einer derart großen Ruhe und Energie an dem Projekt dran bleibt!!

                          A Online
                          A Online
                          ArnoD
                          schrieb am zuletzt editiert von
                          #2956

                          @bluebean
                          Danke, mache ich gerne, lerne schließlich so immer mehr dazu.

                          1 Antwort Letzte Antwort
                          0
                          • A ArnoD

                            Tibber Skript,
                            Version: 1.2.4 auf Github hochgeladen.

                            Änderungen:

                            • Fehler behoben, dass normalPhases anstatt lowPhases abgefragt wurde und dadurch das Laden der Batterie frühzeitig beendet wurde.
                            P Online
                            P Online
                            psrelax
                            schrieb am zuletzt editiert von
                            #2957

                            @arnod
                            Ich bekomm jetzt einen Fehler.

                            2024-11-07 21:05:01.848  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: -==== Tibber Skript Version 1.2.4 ====-
                            2024-11-07 21:05:01.853  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: registered 6 subscriptions, 1 schedule, 0 messages, 0 logs and 0 file subscriptions
                            2024-11-07 21:05:01.853  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: -==== alle Objekt ID's angelegt ====-
                            2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                            2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 667754469,667754482
                            2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-08T02:00:00.000Z","2024-11-08T04:00:00.000Z"]
                            2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                            2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Laden","Laden"]
                            2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.3048
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 9
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 0
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 2756
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 2
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 0:48 h / 0:48 h
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.1057
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.1057
                            2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3217
                            2024-11-07 21:05:02.184  - error: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: Fehler in Funktion tibberSteuerungHauskraftwerk: Cannot read properties of undefined (reading 'endLocale')
                            2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                            2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 667787455,667787468
                            2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-08T02:00:00.000Z","2024-11-08T04:00:00.000Z"]
                            2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                            2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Laden","Laden"]
                            2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.3048
                            2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                            2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 9
                            2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 0
                            2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 2754
                            2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 2
                            2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 0:48 h / 0:48 h
                            2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                            2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.1057
                            2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.1057
                            2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3217
                            2024-11-07 21:06:00.202  - error: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: Fehler in Funktion tibberSteuerungHauskraftwerk: Cannot read properties of undefined (reading 'endLocale')
                            2024-11-07 21:06:17.771  - info: admin.0 (264) ==> Connected system.user.admin from ::ffff:192.168.2.164
                            
                            A 2 Antworten Letzte Antwort
                            0
                            • P psrelax

                              @arnod
                              Ich bekomm jetzt einen Fehler.

                              2024-11-07 21:05:01.848  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: -==== Tibber Skript Version 1.2.4 ====-
                              2024-11-07 21:05:01.853  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: registered 6 subscriptions, 1 schedule, 0 messages, 0 logs and 0 file subscriptions
                              2024-11-07 21:05:01.853  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: -==== alle Objekt ID's angelegt ====-
                              2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                              2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 667754469,667754482
                              2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-08T02:00:00.000Z","2024-11-08T04:00:00.000Z"]
                              2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                              2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Laden","Laden"]
                              2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.3048
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 9
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 0
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 2756
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 2
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 0:48 h / 0:48 h
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.1057
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.1057
                              2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3217
                              2024-11-07 21:05:02.184  - error: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: Fehler in Funktion tibberSteuerungHauskraftwerk: Cannot read properties of undefined (reading 'endLocale')
                              2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                              2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 667787455,667787468
                              2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-08T02:00:00.000Z","2024-11-08T04:00:00.000Z"]
                              2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                              2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Laden","Laden"]
                              2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.3048
                              2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                              2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 9
                              2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 0
                              2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 2754
                              2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 2
                              2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 0:48 h / 0:48 h
                              2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                              2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.1057
                              2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.1057
                              2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3217
                              2024-11-07 21:06:00.202  - error: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: Fehler in Funktion tibberSteuerungHauskraftwerk: Cannot read properties of undefined (reading 'endLocale')
                              2024-11-07 21:06:17.771  - info: admin.0 (264) ==> Connected system.user.admin from ::ffff:192.168.2.164
                              
                              A Online
                              A Online
                              ArnoD
                              schrieb am zuletzt editiert von
                              #2958

                              @psrelax
                              komisch, den hattest du schon mal und ist dann von alleine wieder weggegangen.
                              Ich kann das bei mir nicht nachstellen.
                              endLocale wird eigentlich nur die lokale Zeit mit endTime.toLocaleString() eingetragen.
                              Der Fehler "Cannot read properties of undefined (reading 'endLocale')" tritt auf, wenn versucht wird, auf eine Eigenschaft (endLocale) eines Objekts zuzugreifen, das undefined ist.
                              Da ich nur im Debug LOG darauf zugreife, werde ich es dort mal abfangen.

                              1 Antwort Letzte Antwort
                              0
                              • P psrelax

                                @arnod
                                Ich bekomm jetzt einen Fehler.

                                2024-11-07 21:05:01.848  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: -==== Tibber Skript Version 1.2.4 ====-
                                2024-11-07 21:05:01.853  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: registered 6 subscriptions, 1 schedule, 0 messages, 0 logs and 0 file subscriptions
                                2024-11-07 21:05:01.853  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: -==== alle Objekt ID's angelegt ====-
                                2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                                2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 667754469,667754482
                                2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-08T02:00:00.000Z","2024-11-08T04:00:00.000Z"]
                                2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                                2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Laden","Laden"]
                                2024-11-07 21:05:02.183  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.3048
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 9
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 0
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 2756
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 2
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 0:48 h / 0:48 h
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.1057
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.1057
                                2024-11-07 21:05:02.184  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3217
                                2024-11-07 21:05:02.184  - error: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: Fehler in Funktion tibberSteuerungHauskraftwerk: Cannot read properties of undefined (reading 'endLocale')
                                2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ************************************************************************************
                                2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerIds = 667787455,667787468
                                2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerTarget = ["2024-11-08T02:00:00.000Z","2024-11-08T04:00:00.000Z"]
                                2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerState = [true,false]
                                2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** timerObjektID = ["Laden","Laden"]
                                2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** minStrompreis_48h = 0.3048
                                2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batterieKapazitaet_kWh = 15
                                2024-11-07 21:06:00.201  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Batterie_SOC = 9
                                2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Bat_W = 0
                                2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Power_Grid = 2754
                                2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** prognoseLadezeitBatterie = 2
                                2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** reichweiteBatterie = 0:48 h / 0:48 h
                                2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** batteriepreisAktiv = false
                                2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** strompreisBatterie = 0.1057
                                2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** bruttoPreisBatterie = 0.1057
                                2024-11-07 21:06:00.202  - info: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: ** Aktueller Preis Tibber = 0.3217
                                2024-11-07 21:06:00.202  - error: javascript.0 (271) script.js.E3DC_ChargeControl.Tibber: Fehler in Funktion tibberSteuerungHauskraftwerk: Cannot read properties of undefined (reading 'endLocale')
                                2024-11-07 21:06:17.771  - info: admin.0 (264) ==> Connected system.user.admin from ::ffff:192.168.2.164
                                
                                A Online
                                A Online
                                ArnoD
                                schrieb am zuletzt editiert von
                                #2959

                                @psrelax
                                Ich habe mal die Änderung auf Github hochgeladen, mit der gleichen Versionsnummer.
                                Kannst du die mal testen.

                                P 1 Antwort Letzte Antwort
                                0
                                • A ArnoD

                                  @psrelax
                                  Ich habe mal die Änderung auf Github hochgeladen, mit der gleichen Versionsnummer.
                                  Kannst du die mal testen.

                                  P Online
                                  P Online
                                  psrelax
                                  schrieb am zuletzt editiert von
                                  #2960

                                  @arnod
                                  Keine Änderung.
                                  Hab zwischenzeitlich auch Javascript neu gestartet aber auch ohne Erfolg.

                                  A 1 Antwort Letzte Antwort
                                  0
                                  • P psrelax

                                    @arnod
                                    Keine Änderung.
                                    Hab zwischenzeitlich auch Javascript neu gestartet aber auch ohne Erfolg.

                                    A Online
                                    A Online
                                    ArnoD
                                    schrieb am zuletzt editiert von ArnoD
                                    #2961

                                    @psrelax
                                    Der Tibberlink Adapter hat aber im Json Preisdaten für heute und morgen ?
                                    tibberlink.0.Homes.xxxxxxxxxxxxx.PricesToday.json

                                    Versuch mal das du diese Zeilen in der function DebugLog ab Zeile 1093 so auskommentierts:

                                    //if (DebugAusgabeDetail){log(`** naechstePhasen[1].endLocale = ${ergebnis.naechstePhasen[1]?.endLocale}`)}
                                    //if (DebugAusgabeDetail){log(`** naechstePhasen[1].startLocale = ${ergebnis.naechstePhasen[1].startLocale}`)} if (DebugAusgabeDetail){log(`** naechstePhasen[1].Type = ${ergebnis.naechstePhasen[1].type}`)}
                                    //if (DebugAusgabeDetail){log(`** naechstePhasen[0].endLocale = ${ergebnis.naechstePhasen[0]?.endLocale}`)}
                                    //if (DebugAusgabeDetail){log(`** naechstePhasen[0].startLocale = ${ergebnis.naechstePhasen[0].startLocale}`)}
                                    if (DebugAusgabeDetail){log(`** naechstePhasen[0].Type = ${ergebnis.naechstePhasen[0].type}`)}
                                    //if (DebugAusgabeDetail){log(`** aktivePhase.endLocale = ${ergebnis.aktivePhase?.endLocale}`)}
                                    //if (DebugAusgabeDetail){log(`** aktivePhase.startLocale = ${ergebnis.aktivePhase?.startLocale}`)}
                                    
                                    P 1 Antwort Letzte Antwort
                                    0
                                    • A ArnoD

                                      @psrelax
                                      Der Tibberlink Adapter hat aber im Json Preisdaten für heute und morgen ?
                                      tibberlink.0.Homes.xxxxxxxxxxxxx.PricesToday.json

                                      Versuch mal das du diese Zeilen in der function DebugLog ab Zeile 1093 so auskommentierts:

                                      //if (DebugAusgabeDetail){log(`** naechstePhasen[1].endLocale = ${ergebnis.naechstePhasen[1]?.endLocale}`)}
                                      //if (DebugAusgabeDetail){log(`** naechstePhasen[1].startLocale = ${ergebnis.naechstePhasen[1].startLocale}`)} if (DebugAusgabeDetail){log(`** naechstePhasen[1].Type = ${ergebnis.naechstePhasen[1].type}`)}
                                      //if (DebugAusgabeDetail){log(`** naechstePhasen[0].endLocale = ${ergebnis.naechstePhasen[0]?.endLocale}`)}
                                      //if (DebugAusgabeDetail){log(`** naechstePhasen[0].startLocale = ${ergebnis.naechstePhasen[0].startLocale}`)}
                                      if (DebugAusgabeDetail){log(`** naechstePhasen[0].Type = ${ergebnis.naechstePhasen[0].type}`)}
                                      //if (DebugAusgabeDetail){log(`** aktivePhase.endLocale = ${ergebnis.aktivePhase?.endLocale}`)}
                                      //if (DebugAusgabeDetail){log(`** aktivePhase.startLocale = ${ergebnis.aktivePhase?.startLocale}`)}
                                      
                                      P Online
                                      P Online
                                      psrelax
                                      schrieb am zuletzt editiert von
                                      #2962

                                      @arnod
                                      Die json ist vorhanden.
                                      Auskommentieren bringt nichts. Kommt trotzdem.

                                      P 1 Antwort Letzte Antwort
                                      0
                                      • P psrelax

                                        @arnod
                                        Die json ist vorhanden.
                                        Auskommentieren bringt nichts. Kommt trotzdem.

                                        P Online
                                        P Online
                                        psrelax
                                        schrieb am zuletzt editiert von psrelax
                                        #2963

                                        @psrelax

                                        Korrektur.
                                        Ich bekomme jetzt den Fehler:

                                        javascript.0	22:22:00.271	error	script.js.E3DC_ChargeControl.Tibber: Fehler in Funktion tibberSteuerungHauskraftwerk: Cannot read properties of undefined (reading 'type')
                                        

                                        Ok, Type Debugs auskommentiert und jetzt kommt kein Fehler mehr.

                                        Nachfolgende sind jetzt auskommentiert. Das funktioniert.

                                            //if (DebugAusgabeDetail){log(`** naechstePhasen[1].endLocale = ${ergebnis.naechstePhasen[1]?.endLocale}`)}
                                            //if (DebugAusgabeDetail){log(`** naechstePhasen[1].startLocale = ${ergebnis.naechstePhasen[1].startLocale}`)}
                                            //if (DebugAusgabeDetail){log(`** naechstePhasen[1].Type = ${ergebnis.naechstePhasen[1].type}`)}
                                            //if (DebugAusgabeDetail){log(`** naechstePhasen[0].endLocale = ${ergebnis.naechstePhasen[0]?.endLocale}`)}
                                            //if (DebugAusgabeDetail){log(`** naechstePhasen[0].startLocale = ${ergebnis.naechstePhasen[0].startLocale}`)}
                                            //if (DebugAusgabeDetail){log(`** naechstePhasen[0].Type = ${ergebnis.naechstePhasen[0].type}`)}
                                            //if (DebugAusgabeDetail){log(`** aktivePhase.endLocale = ${ergebnis.aktivePhase?.endLocale}`)}
                                            //if (DebugAusgabeDetail){log(`** aktivePhase.startLocale = ${ergebnis.aktivePhase?.startLocale}`)}
                                        
                                        A 2 Antworten Letzte Antwort
                                        0
                                        • P psrelax

                                          @psrelax

                                          Korrektur.
                                          Ich bekomme jetzt den Fehler:

                                          javascript.0	22:22:00.271	error	script.js.E3DC_ChargeControl.Tibber: Fehler in Funktion tibberSteuerungHauskraftwerk: Cannot read properties of undefined (reading 'type')
                                          

                                          Ok, Type Debugs auskommentiert und jetzt kommt kein Fehler mehr.

                                          Nachfolgende sind jetzt auskommentiert. Das funktioniert.

                                              //if (DebugAusgabeDetail){log(`** naechstePhasen[1].endLocale = ${ergebnis.naechstePhasen[1]?.endLocale}`)}
                                              //if (DebugAusgabeDetail){log(`** naechstePhasen[1].startLocale = ${ergebnis.naechstePhasen[1].startLocale}`)}
                                              //if (DebugAusgabeDetail){log(`** naechstePhasen[1].Type = ${ergebnis.naechstePhasen[1].type}`)}
                                              //if (DebugAusgabeDetail){log(`** naechstePhasen[0].endLocale = ${ergebnis.naechstePhasen[0]?.endLocale}`)}
                                              //if (DebugAusgabeDetail){log(`** naechstePhasen[0].startLocale = ${ergebnis.naechstePhasen[0].startLocale}`)}
                                              //if (DebugAusgabeDetail){log(`** naechstePhasen[0].Type = ${ergebnis.naechstePhasen[0].type}`)}
                                              //if (DebugAusgabeDetail){log(`** aktivePhase.endLocale = ${ergebnis.aktivePhase?.endLocale}`)}
                                              //if (DebugAusgabeDetail){log(`** aktivePhase.startLocale = ${ergebnis.aktivePhase?.startLocale}`)}
                                          
                                          A Online
                                          A Online
                                          ArnoD
                                          schrieb am zuletzt editiert von
                                          #2964

                                          @psrelax
                                          Ok, dann muss ich mal prüfen, wie ich diesen Fehler abfangen kann.
                                          Ich vermute das die Tibber Daten vom Adapter nicht vorhanden sind oder eventuell noch nicht eingelesen sind.

                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          841

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe