  4. [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.7k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.1k

[Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana

Geplant Angeheftet Gesperrt Verschoben Praktische Anwendungen (Showcase)
solaredgemodbusgrafana
606 Beiträge 91 Kommentatoren 208.9k Aufrufe 99 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • B bitwicht

    Frage zur Berechnung.

    ID 40083 ist doch die aktuelle Leitung der PVA.
    ID 40084 ist der Scling Faktor

    Den Wert lasse ich dann über das Script umrechnen.

    function convertValue(value, factor) {
       if (value === null) return;
       if (factor === null) factor = 0;
       setState('PV.Wechselrichter.SE-10KRWS-PVLeistungAktuell', value * Math.pow(10, factor), true);
    }  
     
    createState('PV.Wechselrichter.SE-10KRWS-PVLeistungAktuell', {
    	name: 'PV-WR-SE-10KRWS-PVLeistungAktuell',
    	unit: 'W',
    	min:  0,
    	type: 'number',
    	role: 'value.energy'
    }, function () {
    	on('modbus.0.holdingRegisters.1.40083_I_AC_Power'/*AC-Leistungswert*/, function(obj) {
    		var timeout = setTimeout(function () {
    			clearTimeout(timeout);
    			var factorState = getState('modbus.0.holdingRegisters.1.40084_I_AC_Power_SF'/*AC-Leistung Skalierungsfaktor*/);
    			convertValue(obj.state.val, factorState ? factorState.val : 0);
    		}, 100); 
    	});
    	var factorState = getState('modbus.0.holdingRegisters.1.40084_I_AC_Power_SF'/*AC-Leistung Skalierungsfaktor*/);
    	var valueState = getState('modbus.0.holdingRegisters.1.40083_I_AC_Power'/*AC-Leistungswert*/);
    	convertValue(valueState ? valueState.val : null, factorState ? factorState.val : 0); 
    });
    

    Den Datenpunkt aus dem Script, zeichne ich mit dem Sourceanalytics Adapter auf.

    Hier die Config:
    PV-B2.JPG

    Somit müsste ich doch am Ende des Tages die am Tag erzeugte Energie haben.

    Der Wert passt aber leider überhaupt nicht (viel zu hoch).

    Haben ich einen Denkfehler?

    @hennerich müsste das so passen, kannst du das bei dir kontrollieren?

    D Offline
    D Offline
    docf
    schrieb am zuletzt editiert von
    #504

    @bitwicht

    Ja ist bei mir auch zu hoch in der Nacht zeigt mir die I AC Power ca 500 Watt an ?
    Habe da auch noch keine Lösung gefunden

    1 Antwort Letzte Antwort
    0
    • B Offline
      B Offline
      bitwicht
      schrieb am zuletzt editiert von
      #505

      @docf

      Das kann ich bestätigen. Bei mir kommen aus dem Modbus Adapter auch ca. 500 Watt, aber nur bei dem Hybrid-WR. Ich glaube ich habe mal im PV Forum gelesen, dass der Hybrid WR nie "aus" geht wegen der Akku Minimal Ladung.
      Aber er dürfte ja bei Produktion nichts anzeigen.

      Interessant ist auch das die Werte der SE-API nicht zu SE-App und auch nicht zur SE-Webportal Export CSV passen.
      Gibt es auch minimale Abweichungen.

      Verstehe ich nicht was die Hersteller da für Mist machen.

      Ich hatte bei SE schon 5 Tickets offen aber es heißt immer das alles passt.

      U 1 Antwort Letzte Antwort
      0
      • B bitwicht

        @docf

        Das kann ich bestätigen. Bei mir kommen aus dem Modbus Adapter auch ca. 500 Watt, aber nur bei dem Hybrid-WR. Ich glaube ich habe mal im PV Forum gelesen, dass der Hybrid WR nie "aus" geht wegen der Akku Minimal Ladung.
        Aber er dürfte ja bei Produktion nichts anzeigen.

        Interessant ist auch das die Werte der SE-API nicht zu SE-App und auch nicht zur SE-Webportal Export CSV passen.
        Gibt es auch minimale Abweichungen.

        Verstehe ich nicht was die Hersteller da für Mist machen.

        Ich hatte bei SE schon 5 Tickets offen aber es heißt immer das alles passt.

        U Offline
        U Offline
        Uwe96
        schrieb am zuletzt editiert von
        #506

        @bitwicht
        Ja, hatte ich ja auch schon mal geschrieben. Sehe das auf meinem Grafana ab und zu steigt Production und Verbrauch um 500 W an. Damit stimmt dann natürlich alles nicht mehr. Komischer Weise ist das ja beim Monitoring nicht so.Nutzt SolarEdge da andere Register?

        1 Antwort Letzte Antwort
        0
        • B Offline
          B Offline
          bitwicht
          schrieb am zuletzt editiert von
          #507

          @Uwe96

          ich weiß es leider nicht da SE mir keine vernünftige Antwort gibt.

          Komisch finde ich schon das die Daten SE-App vs SE-Web-CSV vs SE-API nicht übereinstimmen.

          Vielleicht berechnet SE die Daten anhand des Smart-Meter und nicht anhand der Register.

          1 Antwort Letzte Antwort
          0
          • L lisalisa

            @bitwicht Wenn hier sonst keiner antwortet...
            Teste mal meine 100.000er, sind für einen BYD-Akku.```

             _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
            101697	CommitSettings	Commit Power Control Settings		uint16be	1	1	0		level		true	false	false	false
            101701	ReactivePwrConfig	ReactivePwrConfig		uint32sw	2	1	0		level		true	false	false	false
            101763	AdvancedPwrControlEn	AdvancedPwrControlEn		uint32sw	2	1	0		level		true	false	false	false
            102787	Batt Rated Energy	Batt Rated Energy	Wh	floatsw	2	1	0		level		true	false	false	false
            102829	Batt1_Avg_T	Batterie 1 Average Temperature °C	°C	floatsw	2	1	0		level		true	false	false	false
            102837	Speicher_Ladung	Speicher Ladeleistung	W	floatsw	2	1	0		level		true	false	false	false
            102851	Speicher_SoH	Batterie alterung	%	floatsw	2	1	0		level		true	false	false	false
            102853	Speicher_SoC	Battrieladung	%	floatsw	2	1	0		level		true	false	false	false
            102855	Speicher_Betriebszustand	1 Aus 3: Laden 4: Entladen 6: Erhaltungsladen		uint32sw	2	1	0		level		true	false	false	false
            103237	Str	Storage control mode		uint16be	1	1	0		level		true	false	false	false
            103238	Storage_AC_Charge_Policy_RW	0 – Disable, 1 – Always allowed , 2 – Fixed Energy Limit –		uint16be	1	1	0		level		true	false	false	false
            103241	Storage_Backup_Reserved_Setting_RW			floatsw	2	1	0		level		true	false	false	false
            103243	StChDisChMode	Storage Charge/Discharge Mode		uint16be	1	1	0		level		true	false	false	false
            103244	Timeout	Timout	sec	uint32sw	2	1	0		level		true	false	false	false
            103247	Remote Control Charge Limit	Remote Control Charge Limit	W	floatsw	2	1	0		level		true	false	false	false
            W Online
            W Online
            wrod
            schrieb am zuletzt editiert von wrod
            #508

            @lisalisa
            Danke. Die gehen gut.
            Aber: 102829 ist die "Durchschnittstemperatur" der Batterie. Weißt du, wovon der Durchschnitt genommen wird?, etwa

            • von mehreren Batteriemodulen (so dass es eine zeitlich punktuelle Temperaturmessung ist). Wenn so: Kann man die Temperaturen der einzelnen Module auslesen?
            • über Zeit? Dann: von welchem Zeitraum? Auch hier: Gibt es Register, die den aktuellen Temperaturwert ausgeben (vorhanden sein müsste er dann ja).

            Woher hast Du diese Registerangaben?

            Kennst Du (oder jemand anders hier) eine Dokumentation, wo auch angegeben ist, was die schreibbaren Steuer-Register konkret bewirken, wo also die Logik der Steuerung angegeben ist?

            Dank im Voraus
            W

            L 1 Antwort Letzte Antwort
            0
            • W wrod

              @lisalisa
              Danke. Die gehen gut.
              Aber: 102829 ist die "Durchschnittstemperatur" der Batterie. Weißt du, wovon der Durchschnitt genommen wird?, etwa

              • von mehreren Batteriemodulen (so dass es eine zeitlich punktuelle Temperaturmessung ist). Wenn so: Kann man die Temperaturen der einzelnen Module auslesen?
              • über Zeit? Dann: von welchem Zeitraum? Auch hier: Gibt es Register, die den aktuellen Temperaturwert ausgeben (vorhanden sein müsste er dann ja).

              Woher hast Du diese Registerangaben?

              Kennst Du (oder jemand anders hier) eine Dokumentation, wo auch angegeben ist, was die schreibbaren Steuer-Register konkret bewirken, wo also die Logik der Steuerung angegeben ist?

              Dank im Voraus
              W

              L Offline
              L Offline
              lisalisa
              schrieb am zuletzt editiert von lisalisa
              #509

              @wrod
              Bitte schön, habe aber gerade keinen Plan welchen Beitrag du meinst.

              Irgendwelche Registerangaben und Infos habe ich hier aus dem Forum und aus PDFs.
              Google mal nach "SunSpec-Protokoll in SolarEdge Wechselrichtern" oder "Open Protocol for SolarEdge Inverters"

              In dieser PDF z.B. stehen Register
              https://www.photovoltaikforum.com/core/attachment/88445-power-control-open-protocol-for-solaredge-inverters-pdf/

              von dieser PDF:
              ......
              E16C (F56C) 2 R Battery 1 Average Temperature Float32 °C
              E16E (F56E) 2 R Battery 1 Max Temperature Float32 °C
              .....

              Bei mir ist zu beachten meine Adressen sind immer plus 1:
              holdingRegisters.102829 Batterie 1 Average Temperature °C
              z.B. Adresse 102.829 - 40.000 = dezimal 62.829 = hexadezimal F56D (=Adresse plus 1)

              W 1 Antwort Letzte Antwort
              0
              • L lisalisa

                @wrod
                Bitte schön, habe aber gerade keinen Plan welchen Beitrag du meinst.

                Irgendwelche Registerangaben und Infos habe ich hier aus dem Forum und aus PDFs.
                Google mal nach "SunSpec-Protokoll in SolarEdge Wechselrichtern" oder "Open Protocol for SolarEdge Inverters"

                In dieser PDF z.B. stehen Register
                https://www.photovoltaikforum.com/core/attachment/88445-power-control-open-protocol-for-solaredge-inverters-pdf/

                von dieser PDF:
                ......
                E16C (F56C) 2 R Battery 1 Average Temperature Float32 °C
                E16E (F56E) 2 R Battery 1 Max Temperature Float32 °C
                .....

                Bei mir ist zu beachten meine Adressen sind immer plus 1:
                holdingRegisters.102829 Batterie 1 Average Temperature °C
                z.B. Adresse 102.829 - 40.000 = dezimal 62.829 = hexadezimal F56D (=Adresse plus 1)

                W Online
                W Online
                wrod
                schrieb am zuletzt editiert von
                #510

                @lisalisa
                Danke. Ich meine diesen hier: https://forum.iobroker.net/post/975915.

                In dem von Dir verlinkten Dokument und in Deiner letzten Mail sind Adressen in ganz anderem Format. in dem oben genannten Post hattest Du für BYD Register mit 100000er Adressen. Dafür bräuchte ich eine Dokumentation.

                L 1 Antwort Letzte Antwort
                0
                • W wrod

                  @lisalisa
                  Danke. Ich meine diesen hier: https://forum.iobroker.net/post/975915.

                  In dem von Dir verlinkten Dokument und in Deiner letzten Mail sind Adressen in ganz anderem Format. in dem oben genannten Post hattest Du für BYD Register mit 100000er Adressen. Dafür bräuchte ich eine Dokumentation.

                  L Offline
                  L Offline
                  lisalisa
                  schrieb am zuletzt editiert von lisalisa
                  #511

                  @wrod sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                  In dem von Dir verlinkten Dokument und in Deiner letzten Mail sind Adressen in ganz anderem Format. in dem oben genannten Post hattest Du für BYD Register mit 100000er Adressen. Dafür bräuchte ich eine Dokumentation.

                  Einfach die 100000er Adressen ausrechnen
                  z.B. Adresse 102.829 - 40.000 = dezimal 62.829 = hexadezimal F56D (=Adresse plus 1)

                  3177b5c1-8156-4085-92b3-6d9d6c9fa64e-image.png

                  L 1 Antwort Letzte Antwort
                  0
                  • L lisalisa

                    @wrod sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                    In dem von Dir verlinkten Dokument und in Deiner letzten Mail sind Adressen in ganz anderem Format. in dem oben genannten Post hattest Du für BYD Register mit 100000er Adressen. Dafür bräuchte ich eine Dokumentation.

                    Einfach die 100000er Adressen ausrechnen
                    z.B. Adresse 102.829 - 40.000 = dezimal 62.829 = hexadezimal F56D (=Adresse plus 1)

                    3177b5c1-8156-4085-92b3-6d9d6c9fa64e-image.png

                    L Offline
                    L Offline
                    lisalisa
                    schrieb am zuletzt editiert von lisalisa
                    #512

                    Habe mal meine Adressen umgerechnet...

                    6b593c50-148d-45d1-95f1-aef4e068b654-image.png

                    W 1 Antwort Letzte Antwort
                    0
                    • L lisalisa

                      Habe mal meine Adressen umgerechnet...

                      6b593c50-148d-45d1-95f1-aef4e068b654-image.png

                      W Online
                      W Online
                      wrod
                      schrieb am zuletzt editiert von
                      #513

                      @lisalisa Danke! Das hilft weiter.
                      Ich kann sie einrichten, aber einige (10072x) geben leider noch keine Werte. Vielleicht doch nicht für genau mein Modell geeignet (obwohl andere (1028xx) funktionieren).

                      L 1 Antwort Letzte Antwort
                      0
                      • W wrod

                        @lisalisa Danke! Das hilft weiter.
                        Ich kann sie einrichten, aber einige (10072x) geben leider noch keine Werte. Vielleicht doch nicht für genau mein Modell geeignet (obwohl andere (1028xx) funktionieren).

                        L Offline
                        L Offline
                        lisalisa
                        schrieb am zuletzt editiert von lisalisa
                        #514

                        @wrod die ersten Adresse in der PDF E16C (F56C) funktioniert übrigens auch, die 2. ist nur gespiegelt
                        Wenn was nicht funktioniert immer mal Adresse plus oder minus 1 ausprobieren.

                        Mit "Radzio Modbus Master Simulator" kann man auch mal die Register zum Test auslesen (dazu dann aber IOBroker Modbus Zugriff deaktivieren)
                        https://en.radzio.dxp.pl/modbus-master-simulator/

                        pasted-from-clipboard.png

                        1 Antwort Letzte Antwort
                        0
                        • H hennerich

                          Teil2 – Werte umrechnen und in Grafana anzeigen

                          Jetzt haben wir also die Werte im ioBroker. Wie gehts nun damit weiter?

                          Zuerst einmal muss jeder für sich selbst entscheiden, welche Werte für ihn von Interesse sind. Ich für meinen Teil verwende die folgenden Werte:
                          Wechselrichter

                          • 40084: AC-Leistungswert in W (aktuelle PV Produktion)
                          • 40093: AC Gesamt-Energieproduktion in Wh (also alles, was eure Anlage bisher erzeugt hat)
                          • 40103: Kühlkörpertemperatur vom Wechselrichter in °C (man weiß ja nie)

                          Energiezähler

                          • 40206: Total Real Power (aktueller Netzbezug bzw. Einspeisung)
                          • 40226: Total Exported Real Energy (was ihr heute erzeugt habt)
                          • 40234: Total Imported Real Energy (was ihr heute aus dem Netz bezogen habt)

                          Aus den letzten beiden Werte kann man den Eigenverbrauch heute berechnen.

                          Dann müssen wir verstehen, dass SolarEdge für viele Werte noch Skalierungsfaktoren mitliefert. Auch das ist etwas, dass nur in der englischen Doku auftaucht. Dort steht nämlich:


                          As an alternative to floating point format, values are represented by Integer values with a signed scale factor applied. The scale factor explicitly shifts the decimal point to left (negative value) or to the right (positive value).

                          For example, a value “Value” may have an associated value “Value_SF”
                          Value = “Value” * 10^ Value_SF for example:

                          • For “Value” = 2071 and “Value_SF” = -2 Value = 2071*10^-2 = 20.71
                          • For “Value” = 2071 and “Value_SF” = 2 Value = 2071*10^2 = 2071

                          Man muss die Werte die man möchte also erst noch umrechnen. Und sie müssen unmittelbar zusammen ausgelsesen werden, sonst passen sie nicht zusammen. Dazu geht mein Dank an inkoFa aus dem PV Forum, der mir mit seiner Lösung dazu sehr weitergeholfen hat.

                          Für den Wert 40084: AC-Leistungswert legt ihr folgendes JS Script an:

                          function convertValue(value, factor) {
                             if (value === null) return;
                             if (factor === null) factor = 0;
                             setState('Solar.Wechselrichter.PVLeistungAktuell', value * Math.pow(10, factor), true);
                          }  
                           
                          createState('Solar.Wechselrichter.PVLeistungAktuell', {
                          	name: 'PVLeistungAktuell',
                          	unit: 'W',
                          	min:  0,
                          	type: 'number',
                          	role: 'value.energy'
                          }, function () {
                          	on('modbus.1.holdingRegisters.40083_I_AC_Leistung'/*AC-Leistungswert*/, function(obj) {
                          		var timeout = setTimeout(function () {
                          			clearTimeout(timeout);
                          			var factorState = getState('modbus.1.holdingRegisters.40084_I_AC_Leistung_SF'/*AC-Leistung Skalierungsfaktor*/);
                          			convertValue(obj.state.val, factorState ? factorState.val : 0);
                          		}, 100); 
                          	});
                          	var factorState = getState('modbus.1.holdingRegisters.40084_I_AC_Leistung_SF'/*AC-Leistung Skalierungsfaktor*/);
                          	var valueState = getState('modbus.1.holdingRegisters.40083_I_AC_Leistung'/*AC-Leistungswert*/);
                          	convertValue(valueState ? valueState.val : null, factorState ? factorState.val : 0); 
                          });
                          

                          Für den Wert 40206: Total Real Power legt ihr folgendes JS Script an:

                          function convertValue(value, factor) {
                             if (value === null) return;
                             if (factor === null) factor = 0;
                             setState('Solar.Wechselrichter.ACTotalRealPower', value * Math.pow(10, factor), true);
                          }  
                           
                          createState('Solar.Wechselrichter.ACTotalRealPower', {
                          	name: 'ACTotalRealPower',
                          	unit: 'W',
                          	min:  -999999,
                          	type: 'number',
                          	role: 'value.energy'
                          }, function () {
                          	on('modbus.1.holdingRegisters.40206_M_AC_Power'/*Total Real Power (sum of active phases)*/, function(obj) {
                          		var timeout = setTimeout(function () {
                          			clearTimeout(timeout);
                          			var factorState = getState('modbus.1.holdingRegisters.40210_M_AC_Power_SF'/*AC Real Power Scale Factor*/);
                          			convertValue(obj.state.val, factorState ? factorState.val : 0);
                          		}, 100); 
                          	});
                          	var factorState = getState('modbus.1.holdingRegisters.40210_M_AC_Power_SF'/*AC Real Power Scale Factor*/);
                          	var valueState = getState('modbus.1.holdingRegisters.40206_M_AC_Power'/*Total Real Power (sum of active phases)*/);
                          	convertValue(valueState ? valueState.val : null, factorState ? factorState.val : 0); 
                          });
                          

                          Und für den Wert 40103: Kühlkörpertemperatur legt ihr folgendes JS Script an:

                          function convertValue(value, factor) {
                             if (value === null) return;
                             if (factor === null) factor = 0;
                             setState('Solar.Wechselrichter.TempWechselrichter', value * Math.pow(10, factor), true);
                          }  
                           
                          createState('Solar.Wechselrichter.TempWechselrichter', {
                          	name: 'TempWechselrichter',
                          	unit: '°C',
                          	min:  -999999,
                          	type: 'number',
                          	role: 'value.energy'
                          }, function () {
                          	on('modbus.1.holdingRegisters.40103_I_Temp_Kühler'/*Kühlkörpertemperatur*/, function(obj) {
                          		var timeout = setTimeout(function () {
                          			clearTimeout(timeout);
                          			var factorState = getState('modbus.1.holdingRegisters.40106_I_Temp_SF'/*Kühlkörpertemperatur Skalierungsfaktor*/);
                          			convertValue(obj.state.val, factorState ? factorState.val : 0);
                          		}, 100); 
                          	});
                          	var factorState = getState('modbus.1.holdingRegisters.40106_I_Temp_SF'/*Kühlkörpertemperatur Skalierungsfaktor*/);
                          	var valueState = getState('modbus.1.holdingRegisters.40103_I_Temp_Kühler'/*Kühlkörpertemperatur*/);
                          	convertValue(valueState ? valueState.val : null, factorState ? factorState.val : 0); 
                          });
                          

                          Jetzt könnt ihr mit den Umrechnungen die entsprechenden Objekte befüllen. Ich hab also ein Blockly Script Hausverbrauch angelegt:
                          518582a6-ed9e-4ee9-a2da-a2d184bda8f4-grafik.png
                          Importiert gerne folgendes:

                          <xml xmlns="https://developers.google.com/blockly/xml">
                           <block type="on" id="YYeTFl5=+RUFGKp!fwS8" x="-937" y="63">
                             <field name="OID">javascript.0.Solar.Wechselrichter.ACTotalRealPower</field>
                             <field name="CONDITION">ne</field>
                             <field name="ACK_CONDITION"></field>
                             <statement name="STATEMENT">
                               <block type="update" id="{8c)~K%7n5#35[IVg*CU">
                                 <mutation xmlns="http://www.w3.org/1999/xhtml" delay_input="false"></mutation>
                                 <field name="OID">javascript.0.Solar.Wechselrichter.Hausverbrauch</field>
                                 <field name="WITH_DELAY">FALSE</field>
                                 <value name="VALUE">
                                   <block type="math_arithmetic" id="N5XZnoEUm{3Kzm-/]B@/">
                                     <field name="OP">MINUS</field>
                                     <value name="A">
                                       <shadow xmlns="http://www.w3.org/1999/xhtml" type="math_number" id="!{7/(]DX3lGP@Il`Y=E1">
                                         <field name="NUM">1</field>
                                       </shadow>
                                       <block type="get_value" id="_;teC|IbrE2JD_fEN~js">
                                         <field name="ATTR">val</field>
                                         <field name="OID">javascript.0.Solar.Wechselrichter.PVLeistungAktuell</field>
                                       </block>
                                     </value>
                                     <value name="B">
                                       <shadow xmlns="http://www.w3.org/1999/xhtml" type="math_number" id="M:s(2P888iDd:XzoTo4p">
                                         <field name="NUM">1</field>
                                       </shadow>
                                       <block type="get_value" id="|gkz@RnPUVcfP6F8mj]p">
                                         <field name="ATTR">val</field>
                                         <field name="OID">javascript.0.Solar.Wechselrichter.ACTotalRealPower</field>
                                       </block>
                                     </value>
                                   </block>
                                 </value>
                               </block>
                             </statement>
                           </block>
                          </xml>
                          

                          Und das schreibt ihr z.B. in die InfluxDB, um den Wert im Grafana anzuzeigen:
                          21df3f32-6689-48ea-93e1-65740130c347-grafik.png

                          Ich versuche mal nach und nach noch Sachen hier zu ergänzen. Und eure Meinung dazu interessiert mich natürlich auch brennend. Habt ihr andere Dinge umgesetzt? Leitet ihr Infos aus anderen Werten ab, die ich noch gar nicht auf dem Schirm habe? Wie sehen eure (PV) Dashboards aus, die ihr umgesetzt habt?

                          C Offline
                          C Offline
                          cainam
                          schrieb am zuletzt editiert von
                          #515

                          @hennerich said in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                          Man muss die Werte die man möchte also erst noch umrechnen. Und sie müssen unmittelbar zusammen ausgelsesen werden, sonst passen sie nicht zusammen. Dazu geht mein Dank an inkoFa aus dem PV Forum, der mir mit seiner Lösung dazu sehr weitergeholfen hat.

                          Hallo zusammen

                          Kann mir hier jemand helfen

                          Bei mir sind die ScaleFactoren riiiisig. Dh mit value * 10 ^ SF. ist das nicht lösbar

                          zB
                          modbus.0.holdingRegisters.40083_I_AC_Leistung ist 64535
                          modbus.0.holdingRegisters.40084_I_AC_Leistung_SF ist zwischen 0 und ca 8000

                          auch ist mir aufgefallen, dass bei mir eigentlich nur die SF sich ändern...

                          L 1 Antwort Letzte Antwort
                          0
                          • C cainam

                            @hennerich said in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                            Man muss die Werte die man möchte also erst noch umrechnen. Und sie müssen unmittelbar zusammen ausgelsesen werden, sonst passen sie nicht zusammen. Dazu geht mein Dank an inkoFa aus dem PV Forum, der mir mit seiner Lösung dazu sehr weitergeholfen hat.

                            Hallo zusammen

                            Kann mir hier jemand helfen

                            Bei mir sind die ScaleFactoren riiiisig. Dh mit value * 10 ^ SF. ist das nicht lösbar

                            zB
                            modbus.0.holdingRegisters.40083_I_AC_Leistung ist 64535
                            modbus.0.holdingRegisters.40084_I_AC_Leistung_SF ist zwischen 0 und ca 8000

                            auch ist mir aufgefallen, dass bei mir eigentlich nur die SF sich ändern...

                            L Offline
                            L Offline
                            lisalisa
                            schrieb am zuletzt editiert von
                            #516

                            @cainam sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                            modbus.0.holdingRegisters.40083_I_AC_Leistung ist 64535
                            modbus.0.holdingRegisters.40084_I_AC_Leistung_SF ist zwischen 0 und ca 8000

                            einfach mal Adresse Plus 1 testen (wurde hier auch schon paarmal geschrieben...)
                            modbus.0.holdingRegisters.40084_I_AC_Leistung
                            modbus.0.holdingRegisters.40085_I_AC_Leistung_SF

                            C 1 Antwort Letzte Antwort
                            0
                            • L lisalisa

                              @cainam sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                              modbus.0.holdingRegisters.40083_I_AC_Leistung ist 64535
                              modbus.0.holdingRegisters.40084_I_AC_Leistung_SF ist zwischen 0 und ca 8000

                              einfach mal Adresse Plus 1 testen (wurde hier auch schon paarmal geschrieben...)
                              modbus.0.holdingRegisters.40084_I_AC_Leistung
                              modbus.0.holdingRegisters.40085_I_AC_Leistung_SF

                              C Offline
                              C Offline
                              cainam
                              schrieb am zuletzt editiert von
                              #517

                              @lisalisa

                              Top Danke, das wars

                              1 Antwort Letzte Antwort
                              0
                              • W Online
                                W Online
                                wrod
                                schrieb am zuletzt editiert von
                                #518

                                @lisalisa
                                DANKE:
                                gerade 102855 funktioniert leider gar nicht bzw. liefert nur "0". 102854 und 102856 führen hingegen zu Fehlern.

                                1 Antwort Letzte Antwort
                                0
                                • C Offline
                                  C Offline
                                  cainam
                                  schrieb am zuletzt editiert von
                                  #519

                                  In dem Ersparnis skript gibt es eine Variable " alteVerguetunginEuro"... diese wird aber auf 0 gesetzt und dann mE nicht mehr verwendet... was ist das?

                                  1 Antwort Letzte Antwort
                                  0
                                  • D danielos

                                    Hallo zusammen

                                    Zuerst einmal herzlichen Dank für euren Effort. Ich habe dank diesem Beitrag zumindest schon etwas zum Laufen gebracht. Leider aber noch nicht ganz das, was ich gerne möchte.

                                    objects_-_raspberrypi.png

                                    Der 40207 funktioniert bestens. Er zeigt an, wieviel Watt ich aktuell vom Stromanbieter beziehen (wenn es eine negative Zahl ist), oder aber ins Netz speise (wenn es eine positive Zahl ist).

                                    Auch scheint die 40094 einigermassen zu passen und gibt die Gesamtproduktion seit Beginn an. Die Zahl ist zwar nicht ganz stimmig mit der aus dem App, aber so einigermassen passt's.

                                    Ich kann es aber drehen und wenden wie ich will. Was ich nicht schaffe, ist da auch die Watt rauszukriegen, welche ich aktuell für das Haus beziehe oder aber auch die PV-Anlage produziert. Ich habe mit der 40207 nur immer die Summe aus beiden.

                                    Dies ist die Spezifikation meines Wechselrichters und egal welche ich nebst der 40207 mit den gleichen Einstellungen auslese, ich kriege keine sinnvollen Resultate.

                                    https://www.dropbox.com/s/j5ye5cj86kaxhcn/sunspec-implementation-technical-note.pdf?dl=0

                                    Vermutlich suche ich da viel zu weit....herzlichen Dank für eure Hilfe!!!

                                    W Online
                                    W Online
                                    wrod
                                    schrieb am zuletzt editiert von
                                    #520

                                    @danielos Danke. Welches Register gibt denn die Werte der Einspeisung aus?

                                    1 Antwort Letzte Antwort
                                    0
                                    • W Online
                                      W Online
                                      wrod
                                      schrieb am zuletzt editiert von
                                      #521

                                      @lisalisa
                                      Danke.
                                      Gibt es irgendwo eine Tabelle für die Register für den Wechselrichter SE8K?
                                      In der Dokue steht etwas von 0xF142 als "AdvancedPwrControlEn". Den bekomme ich nicht hin. Ich habe aber aus Deiner Tabelle "103237_Storage_Control_Mode_RW". Ist das das gleiche oder ist letzterer für die BYD (habe eine LV 3x 3,5 kWh) und ersterer für den WR?

                                      Zudem habe ich seit zwei Tagen Probleme mit "102853_Batterieladestand". Der hat einige Tage lang vernünftige Werte ausgegeben. Nun gibt er zuweilen Stundenlang 0 bzw. Minuswerte aus. Hier der Verlauf aus der influx.db-Diagramm-Darstellung:
                                      50689357-1e85-46f2-8ce0-bb3a4b0eecc7-grafik.png

                                      L 1 Antwort Letzte Antwort
                                      0
                                      • W wrod

                                        @lisalisa
                                        Danke.
                                        Gibt es irgendwo eine Tabelle für die Register für den Wechselrichter SE8K?
                                        In der Dokue steht etwas von 0xF142 als "AdvancedPwrControlEn". Den bekomme ich nicht hin. Ich habe aber aus Deiner Tabelle "103237_Storage_Control_Mode_RW". Ist das das gleiche oder ist letzterer für die BYD (habe eine LV 3x 3,5 kWh) und ersterer für den WR?

                                        Zudem habe ich seit zwei Tagen Probleme mit "102853_Batterieladestand". Der hat einige Tage lang vernünftige Werte ausgegeben. Nun gibt er zuweilen Stundenlang 0 bzw. Minuswerte aus. Hier der Verlauf aus der influx.db-Diagramm-Darstellung:
                                        50689357-1e85-46f2-8ce0-bb3a4b0eecc7-grafik.png

                                        L Offline
                                        L Offline
                                        lisalisa
                                        schrieb am zuletzt editiert von
                                        #522

                                        @wrod sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                                        ...Gibt es irgendwo eine Tabelle für die Register für den Wechselrichter SE8K?...

                                        Google mal nach "SunSpec-Protokoll in SolarEdge Wechselrichtern" oder "Open Protocol for SolarEdge Inverters"

                                        dann findest du jede Menge PDF

                                        @wrod sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                                        ... In der Dokue steht etwas von 0xF142 als "AdvancedPwrControlEn".
                                        Ich habe aber aus Deiner Tabelle "103237_Storage_Control_Mode_RW". Ist das das gleiche...

                                        Nein, ist nicht das gleiche.

                                        Du solltest mal ein paar Beiträge weiter hinten lesen wie die Adressen ausgerechnet werden (HEX nach dezimal +40.000 usw.) und Googel ist dein Freund und will dir helfen, mußt ihm nur eine Chance geben.

                                        1 Antwort Letzte Antwort
                                        0
                                        • L lisalisa

                                          Hallo, ich bin Anfänger und habe versucht mit den Infos hier meinen Solaredge SE8K und meine BYD-LVS8 einzurichten.
                                          Irgend wie komme ich nicht mehr weiter, die Werte für ACTotalRealPower, Hausverbrauch, TempWechselrichter passen, aber alles andere nicht.

                                          Habe jetzt gerade festgestellt das PVLeistungAktuell aktuell auch nicht richtig ist, es zeigt auch PV-Leistung an wenn von der Batterie eingespeist wird.

                                          Vielleicht weiß hier jemand was ich falsch mache ?
                                          Bin für jede Hilfe dankbar

                                          Scripte_wechselrichter.JPG

                                          W Online
                                          W Online
                                          wrod
                                          schrieb am zuletzt editiert von wrod
                                          #523

                                          @lisalisa Du hast hier https://forum.iobroker.net/post/699727 unter anderem Register für PV Exportiert Aktuell etc angegeben - leider ohne Adresse. Ich habe auch enen SE8K. Kannst Du die Adressen posten?

                                          Danke

                                          L 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          948

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe