  1. ioBroker Community Home
  2. Deutsch
  3. Error/Bug
  4. Gelöst Modbus import TSV -> No field isScale in position 15

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.7k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.1k

Gelöst Modbus import TSV -> No field isScale in position 15

Geplant Angeheftet Gesperrt Verschoben Error/Bug
23 Beiträge 3 Kommentatoren 2.4k Aufrufe 3 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • wendy2702W wendy2702

    @glasfaser Das heisst beim Import markierst du die bereits existierende Zeile und überschreibst die dann.

    Klar ist das der oder ein Weg. Wenn ich aber, wie jetzt vor lauter übereifer in meinem Fall auch an unbedachte, unerfahrene User denke wundert mich das es noch keinem Aufgefallen ist.

    Wenn ich aber der einzige depp bin dem das passiert ist belassen wir es einfach dabei.

    GlasfaserG Offline
    GlasfaserG Offline
    Glasfaser
    schrieb am zuletzt editiert von
    #14

    @wendy2702 sagte in Modbus import TSV error --> No field isScale in position 15:

    Das heisst beim Import markierst du die bereits existierende Zeile und überschreibst die dann.

    richtig ... schon immer so gemacht

    unerfahrene User

    da hast du recht ... sollte man trotzdem eventuell als Issues anfragen !?

    Wenn ich aber der einzige depp bin dem das passiert ist belassen wir es einfach dabei.

    Kein Kommentar ;)

    Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

    1 Antwort Letzte Antwort
    0
    • I Offline
      I Offline
      ici-ice
      schrieb am zuletzt editiert von ici-ice
      #15

      @glasfaser: das Thema ist schon vom Januar, jedoch möchte ich hier noch einmal einhaken, weil ich exakt das gleiche Problem habe und ich auf keine Lösung komme, egal welche Variante ich ausprobiere.
      Gerade habe ich den Modbus Adapter installiert, um ihn mit meinem Sungrow WR zu verbinden.
      Die Einstellungen unter "Allgemein" habe ich so übernommen, wie oben beschrieben. Beim Importieren der TSV-Daten bekomme ich folgenden Fehler:
      Fehler Import.PNG
      das TSV-File habe ich hier downgeloaded:
      https://forum.iobroker.net/topic/38441/sungrow-wr-sgh10rt-erfolgreich-mit-modbus-eingebunden/3
      Hat jemand eine Idee, warum der Import nicht klappt?

      GlasfaserG 1 Antwort Letzte Antwort
      0
      • I ici-ice

        @glasfaser: das Thema ist schon vom Januar, jedoch möchte ich hier noch einmal einhaken, weil ich exakt das gleiche Problem habe und ich auf keine Lösung komme, egal welche Variante ich ausprobiere.
        Gerade habe ich den Modbus Adapter installiert, um ihn mit meinem Sungrow WR zu verbinden.
        Die Einstellungen unter "Allgemein" habe ich so übernommen, wie oben beschrieben. Beim Importieren der TSV-Daten bekomme ich folgenden Fehler:
        Fehler Import.PNG
        das TSV-File habe ich hier downgeloaded:
        https://forum.iobroker.net/topic/38441/sungrow-wr-sgh10rt-erfolgreich-mit-modbus-eingebunden/3
        Hat jemand eine Idee, warum der Import nicht klappt?

        GlasfaserG Offline
        GlasfaserG Offline
        Glasfaser
        schrieb am zuletzt editiert von
        #16

        @ici-ice sagte in Gelöst Modbus import TSV -> No field isScale in position 15:

        Hat jemand eine Idee, warum der Import nicht klappt?

        ja ,
        weil sich die Modus Formatierung geändert hat , dein Vorlage ist aus 2020 , die muß dann angepasst werden .

        Hier habe ich es angepasst :
        .

        _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
        4999	System Clock Year	Systemzeit Jahr		uint16be	1	1	0		value		true	false	false	false
        5000	System Clock Month	Systemzeit Monat		uint16be	1	1	0		value		true	false	false	false
        5001	System Clock Day	Systemzeit Tag		uint16be	1	1	0		value		true	false	false	false
        5002	System Clock Hour	Systemzeit Stunde		uint16be	1	1	0		value		true	false	false	false
        5003	System Clock Minute	Systemzeit Minute		uint16be	1	1	0		value		true	false	false	false
        12999	Start/Stop	Start/Stop Start(CF) Stop (CF)		uint16be	1	1	0		value		true	false	false	false
        13001	Load Adjustment mode	Energie Management Modus ON/OFF(1) / Energieoptimiert(2)		uint16be	1	1	0		value		true	false	false	false
        13002	Load 1 timing period 1: Start hour		h	uint16be	1	1	0		value		true	false	false	false
        13003	Load 1 timing period 1: Start minute		min	uint16be	1	1	0		value		true	false	false	false
        13004	Load 1 timing period 1: End hour		min	uint16be	1	1	0		value		true	false	false	false
        13005	Load 1 timing period 1: End minute		h	uint16be	1	1	0		value		true	false	false	false
        13006	Load 1 timing period 2: Start hour		h	uint16be	1	1	0		value		true	false	false	false
        13007	Load 1 timing period 2: Start minute		min	uint16be	1	1	0		value		true	false	false	false
        13008	Load 1 timing period 2: End hour		h	uint16be	1	1	0		value		true	false	false	false
        13009	Load 1 timing period 2: End minute		min	uint16be	1	1	0		value		true	false	false	false
        13010	Load 1 ON/OFF mode	Load 1 ON/OFF mode    ON(170/AA)/ OFF (85/55)		uint16be	1	1	0		value		true	false	false	false
        13011	Load 1 power optimized mode: Start hour		h	uint16be	1	1	0		value		true	false	false	false
        13012	Load 1 power optimized mode: Start minute		min	uint16be	1	1	0		value		true	false	false	false
        13013	Load 1 power optimized mode: End hour		h	uint16be	1	1	0		value		true	false	false	false
        13014	Load 1 power optimized mode: End Minute 		min	uint16be	1	1	0		value		true	false	false	false
        13015	Optimized power of load 1	Optimized power of load 1	W	uint16be	1	1	0		value		true	false	false	false
        13049	EMS mode selection 	EMS Modus		uint16be	1	1	0		value		true	false	false	false
        13050	Charge/discharge command	Ext. Sollvorgabe Laden170(AA)/ Stop187(BB)/ Entladen204(CC) 		uint16be	1	1	0		value		true	false	false	false
        13051	Charge/discharge power	Ext. Sollvorgabe Lade/Entladeleistung		uint16be	1	1	0		value		true	false	false	false
        13055	Batterie nominal Voltage	Nominal Spannung Batterie	V	uint16be	1	0.1	0		value		true	false	false	false
        13056	Battery capacity	Batteriekapazität	Ah	uint16be	1	1	0		value		true	false	false	false
        13057	Max. SOC	Max SOC	%	uint16be	1	0.1	0		value		true	false	false	false
        13058	Min. SOC	Min SOC	%	uint16be	1	0.1	0		value		true	false	false	false
        13059	Battery overvoltage threshold	Batterie Überspannungs Threshold	V	int16be	1	0.1	0		value		true	false	false	false
        13060	Battery undervoltage threshold	Batterie Unterspannungs Threshold	V	int16be	1	0.1	0		value		true	false	false	false
        13061	Battery over temperature threshold	Batterie Übertemperatur Threshold	°C	int16be	1	0.1	0		value		true	false	false	false
        13062	Battery under temperature threshold	Batterie Übertemperatur Threshold	°C	int16be	1	0.1	0		value		true	false	false	false
        13064	Terminated current of constant voltage charging		°C	int16be	1	0.001	0		value		true	false	false	false
        13065	Max. discharge current	Max. Entlade Strom	A	uint16be	1	0.001	0		value		true	false	false	false
        13066	Max. charge current	Max. Lade Strom	A	uint16be	1	0.001	0		value		true	false	false	false
        13079	External EMS heartbeat			uint16be	1	1	0		value		true	false	false	false
        13083	Start  Charging Power	u.U. Leistung, mit welcher ein Ladevorgang begonnen wird. Klärung erwünscht	W	uint16be	1	1	0		value		true	false	false	false
        13084	Start Discharging Power	u.U. Leistung, mit welcher ein Entladevorgang begonnen wird. Klärung erwünscht	W	uint16be	1	1	0		value		false	false	false	false
        13085	Meter Comm.	Kommunikation mit Energie Meter des WR	W	uint16be	1	1	0		value		true	false	false	false
        13086	Export Power Limitation	Einspeise Limitierung AN(170/AA) AUS(85/55h)		uint16be	1	1	0		value		true	false	false	false
        13099	SOC Reserve	SOC Reserve	%	uint16be	1	1	0		value		true	false	false	false
        

        Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

        I 1 Antwort Letzte Antwort
        0
        • GlasfaserG Glasfaser

          @ici-ice sagte in Gelöst Modbus import TSV -> No field isScale in position 15:

          Hat jemand eine Idee, warum der Import nicht klappt?

          ja ,
          weil sich die Modus Formatierung geändert hat , dein Vorlage ist aus 2020 , die muß dann angepasst werden .

          Hier habe ich es angepasst :
          .

          _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
          4999	System Clock Year	Systemzeit Jahr		uint16be	1	1	0		value		true	false	false	false
          5000	System Clock Month	Systemzeit Monat		uint16be	1	1	0		value		true	false	false	false
          5001	System Clock Day	Systemzeit Tag		uint16be	1	1	0		value		true	false	false	false
          5002	System Clock Hour	Systemzeit Stunde		uint16be	1	1	0		value		true	false	false	false
          5003	System Clock Minute	Systemzeit Minute		uint16be	1	1	0		value		true	false	false	false
          12999	Start/Stop	Start/Stop Start(CF) Stop (CF)		uint16be	1	1	0		value		true	false	false	false
          13001	Load Adjustment mode	Energie Management Modus ON/OFF(1) / Energieoptimiert(2)		uint16be	1	1	0		value		true	false	false	false
          13002	Load 1 timing period 1: Start hour		h	uint16be	1	1	0		value		true	false	false	false
          13003	Load 1 timing period 1: Start minute		min	uint16be	1	1	0		value		true	false	false	false
          13004	Load 1 timing period 1: End hour		min	uint16be	1	1	0		value		true	false	false	false
          13005	Load 1 timing period 1: End minute		h	uint16be	1	1	0		value		true	false	false	false
          13006	Load 1 timing period 2: Start hour		h	uint16be	1	1	0		value		true	false	false	false
          13007	Load 1 timing period 2: Start minute		min	uint16be	1	1	0		value		true	false	false	false
          13008	Load 1 timing period 2: End hour		h	uint16be	1	1	0		value		true	false	false	false
          13009	Load 1 timing period 2: End minute		min	uint16be	1	1	0		value		true	false	false	false
          13010	Load 1 ON/OFF mode	Load 1 ON/OFF mode    ON(170/AA)/ OFF (85/55)		uint16be	1	1	0		value		true	false	false	false
          13011	Load 1 power optimized mode: Start hour		h	uint16be	1	1	0		value		true	false	false	false
          13012	Load 1 power optimized mode: Start minute		min	uint16be	1	1	0		value		true	false	false	false
          13013	Load 1 power optimized mode: End hour		h	uint16be	1	1	0		value		true	false	false	false
          13014	Load 1 power optimized mode: End Minute 		min	uint16be	1	1	0		value		true	false	false	false
          13015	Optimized power of load 1	Optimized power of load 1	W	uint16be	1	1	0		value		true	false	false	false
          13049	EMS mode selection 	EMS Modus		uint16be	1	1	0		value		true	false	false	false
          13050	Charge/discharge command	Ext. Sollvorgabe Laden170(AA)/ Stop187(BB)/ Entladen204(CC) 		uint16be	1	1	0		value		true	false	false	false
          13051	Charge/discharge power	Ext. Sollvorgabe Lade/Entladeleistung		uint16be	1	1	0		value		true	false	false	false
          13055	Batterie nominal Voltage	Nominal Spannung Batterie	V	uint16be	1	0.1	0		value		true	false	false	false
          13056	Battery capacity	Batteriekapazität	Ah	uint16be	1	1	0		value		true	false	false	false
          13057	Max. SOC	Max SOC	%	uint16be	1	0.1	0		value		true	false	false	false
          13058	Min. SOC	Min SOC	%	uint16be	1	0.1	0		value		true	false	false	false
          13059	Battery overvoltage threshold	Batterie Überspannungs Threshold	V	int16be	1	0.1	0		value		true	false	false	false
          13060	Battery undervoltage threshold	Batterie Unterspannungs Threshold	V	int16be	1	0.1	0		value		true	false	false	false
          13061	Battery over temperature threshold	Batterie Übertemperatur Threshold	°C	int16be	1	0.1	0		value		true	false	false	false
          13062	Battery under temperature threshold	Batterie Übertemperatur Threshold	°C	int16be	1	0.1	0		value		true	false	false	false
          13064	Terminated current of constant voltage charging		°C	int16be	1	0.001	0		value		true	false	false	false
          13065	Max. discharge current	Max. Entlade Strom	A	uint16be	1	0.001	0		value		true	false	false	false
          13066	Max. charge current	Max. Lade Strom	A	uint16be	1	0.001	0		value		true	false	false	false
          13079	External EMS heartbeat			uint16be	1	1	0		value		true	false	false	false
          13083	Start  Charging Power	u.U. Leistung, mit welcher ein Ladevorgang begonnen wird. Klärung erwünscht	W	uint16be	1	1	0		value		true	false	false	false
          13084	Start Discharging Power	u.U. Leistung, mit welcher ein Entladevorgang begonnen wird. Klärung erwünscht	W	uint16be	1	1	0		value		false	false	false	false
          13085	Meter Comm.	Kommunikation mit Energie Meter des WR	W	uint16be	1	1	0		value		true	false	false	false
          13086	Export Power Limitation	Einspeise Limitierung AN(170/AA) AUS(85/55h)		uint16be	1	1	0		value		true	false	false	false
          13099	SOC Reserve	SOC Reserve	%	uint16be	1	1	0		value		true	false	false	false
          

          I Offline
          I Offline
          ici-ice
          schrieb am zuletzt editiert von ici-ice
          #17

          @glasfaser said in Gelöst Modbus import TSV -> No field isScale in position 15:

          _address name description unit type len factor offset formula role room poll wp cw isScale

          schon mal vielen Dank für deine Unterstützung aber ich bin wahrscheinlich zu doof für den Import. Ich habe deine Daten kopiert, in den Editor geladen, Leerzeilen gelöscht, dann kopiert und zum Import eingefügt.
          Es kommen folgende Fehler:
          Fehler Import.PNG
          Irgendwas mache ich noch falsch

          Edit: muss die Modbus-Verbindung zum Sungrow WR bereits funktionieren oder spielt das beim Import der Registerdaten keine Rolle?

          GlasfaserG 1 Antwort Letzte Antwort
          0
          • I ici-ice

            @glasfaser said in Gelöst Modbus import TSV -> No field isScale in position 15:

            _address name description unit type len factor offset formula role room poll wp cw isScale

            schon mal vielen Dank für deine Unterstützung aber ich bin wahrscheinlich zu doof für den Import. Ich habe deine Daten kopiert, in den Editor geladen, Leerzeilen gelöscht, dann kopiert und zum Import eingefügt.
            Es kommen folgende Fehler:
            Fehler Import.PNG
            Irgendwas mache ich noch falsch

            Edit: muss die Modbus-Verbindung zum Sungrow WR bereits funktionieren oder spielt das beim Import der Registerdaten keine Rolle?

            GlasfaserG Offline
            GlasfaserG Offline
            Glasfaser
            schrieb am zuletzt editiert von
            #18

            @ici-ice sagte in Gelöst Modbus import TSV -> No field isScale in position 15:

            Irgendwas mache ich noch falsch

            das kommt im Holding Register !

            Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

            I 1 Antwort Letzte Antwort
            0
            • GlasfaserG Glasfaser

              @ici-ice sagte in Gelöst Modbus import TSV -> No field isScale in position 15:

              Irgendwas mache ich noch falsch

              das kommt im Holding Register !

              I Offline
              I Offline
              ici-ice
              schrieb am zuletzt editiert von
              #19

              @glasfaser : Guten Morgen, bei Einfügen der Daten ins Holding Register kommen die gleichen Fehlermeldungen :anguished:

              GlasfaserG 1 Antwort Letzte Antwort
              0
              • I ici-ice

                @glasfaser : Guten Morgen, bei Einfügen der Daten ins Holding Register kommen die gleichen Fehlermeldungen :anguished:

                GlasfaserG Offline
                GlasfaserG Offline
                Glasfaser
                schrieb am zuletzt editiert von
                #20

                @ici-ice sagte in Gelöst Modbus import TSV -> No field isScale in position 15:

                kommen die gleichen Fehlermeldungen

                Immer ein Screenshot davon , das sagt mehr aus !

                Ich vermute das es mit einem Zeilenumbruch kopiert/importiert wird ( passiert bei Firefox ) .

                Achte auch auf die Verbindungsparameter , Keine Geräte ID !

                siehe so , die Vorlage funktioniert :
                .
                Animation.gif

                Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                I 1 Antwort Letzte Antwort
                0
                • GlasfaserG Glasfaser

                  @ici-ice sagte in Gelöst Modbus import TSV -> No field isScale in position 15:

                  kommen die gleichen Fehlermeldungen

                  Immer ein Screenshot davon , das sagt mehr aus !

                  Ich vermute das es mit einem Zeilenumbruch kopiert/importiert wird ( passiert bei Firefox ) .

                  Achte auch auf die Verbindungsparameter , Keine Geräte ID !

                  siehe so , die Vorlage funktioniert :
                  .
                  Animation.gif

                  I Offline
                  I Offline
                  ici-ice
                  schrieb am zuletzt editiert von
                  #21

                  @glasfaser : jetzt läufts! Bin ja so happy, vielen Dank!! Bin jetzt mit dem Chrome Browser rein und hab damit kopiert - hat auf Anhieb geklappt. Beim Firefox habe ich vorher tatsächlich viele Leerzeilen rauswerfen müssen. Vermutlich hat sich beim Formatieren ein Fehler eingeschlichen.
                  Noch mal: vielen Dank!

                  GlasfaserG 1 Antwort Letzte Antwort
                  0
                  • I ici-ice

                    @glasfaser : jetzt läufts! Bin ja so happy, vielen Dank!! Bin jetzt mit dem Chrome Browser rein und hab damit kopiert - hat auf Anhieb geklappt. Beim Firefox habe ich vorher tatsächlich viele Leerzeilen rauswerfen müssen. Vermutlich hat sich beim Formatieren ein Fehler eingeschlichen.
                    Noch mal: vielen Dank!

                    GlasfaserG Offline
                    GlasfaserG Offline
                    Glasfaser
                    schrieb am zuletzt editiert von
                    #22

                    @ici-ice sagte in Gelöst Modbus import TSV -> No field isScale in position 15:

                    Noch mal: vielen Dank!

                    ... sehr gerne .. ;)

                    Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                    I 1 Antwort Letzte Antwort
                    0
                    • GlasfaserG Glasfaser

                      @ici-ice sagte in Gelöst Modbus import TSV -> No field isScale in position 15:

                      Noch mal: vielen Dank!

                      ... sehr gerne .. ;)

                      I Offline
                      I Offline
                      ici-ice
                      schrieb am zuletzt editiert von
                      #23

                      @glasfaser : noch eine Frage: hast du aktuelle Daten, mit denen ich auch das Eingangsregister füllen kann?

                      1 Antwort Letzte Antwort
                      0
                      Antworten
                      • In einem neuen Thema antworten
                      Anmelden zum Antworten
                      • Älteste zuerst
                      • Neuste zuerst
                      • Meiste Stimmen


                      Support us

                      ioBroker
                      Community Adapters
                      Donate

                      947

                      Online

                      32.4k

                      Benutzer

                      81.5k

                      Themen

                      1.3m

                      Beiträge
                      Community
                      Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                      ioBroker Community 2014-2025
                      logo
                      • Anmelden

                      • Du hast noch kein Konto? Registrieren

                      • Anmelden oder registrieren, um zu suchen
                      • Erster Beitrag
                        Letzter Beitrag
                      0
                      • Home
                      • Aktuell
                      • Tags
                      • Ungelesen 0
                      • Kategorien
                      • Unreplied
                      • Beliebt
                      • GitHub
                      • Docu
                      • Hilfe