  4. Viessmann Heizung über Modbus steuern

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.6k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.1k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    2.8k

Viessmann Heizung über Modbus steuern

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
35 Beiträge 6 Kommentatoren 8.3k Aufrufe 6 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • S Sascha127

    @homoran
    Ahja ok gecheckt und auf eingestellt.
    Die Registernummern haben sich auch geändert, die Verbindung bleibt auch bestehen.
    Aber ich bekomme immer noch keine Werte in den Objekten.

    IOBroker_Eingangsregister.png IOBroker_Aliases.png

    HomoranH Nicht stören
    HomoranH Nicht stören
    Homoran
    Global Moderator Administrators
    schrieb am zuletzt editiert von Homoran
    #11

    @sascha127 sagte in Viessmann Heizung über Modbus steuern:

    Aber ich bekomme immer noch keine Werte in den Objekten.

    bitte noch mal zeigen
    noch besser:
    die modbus instanz auf Logstufe debug stellen , neu starten und das debug-log zeigen

    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

    S HomoranH 2 Antworten Letzte Antwort
    0
    • HomoranH Homoran

      @sascha127 sagte in Viessmann Heizung über Modbus steuern:

      Aber ich bekomme immer noch keine Werte in den Objekten.

      bitte noch mal zeigen
      noch besser:
      die modbus instanz auf Logstufe debug stellen , neu starten und das debug-log zeigen

      S Offline
      S Offline
      Sascha127
      schrieb am zuletzt editiert von
      #12

      @homoran

      IOBroker_Objekte_Modbus2.png

      1 Antwort Letzte Antwort
      0
      • HomoranH Homoran

        @sascha127 sagte in Viessmann Heizung über Modbus steuern:

        Aber ich bekomme immer noch keine Werte in den Objekten.

        bitte noch mal zeigen
        noch besser:
        die modbus instanz auf Logstufe debug stellen , neu starten und das debug-log zeigen

        HomoranH Nicht stören
        HomoranH Nicht stören
        Homoran
        Global Moderator Administrators
        schrieb am zuletzt editiert von
        #13

        @homoran sagte in Viessmann Heizung über Modbus steuern:

        die modbus instanz auf Logstufe debug stellen , neu starten und das debug-log zeigen

        @Sascha127 bitte das noch

        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

        S 1 Antwort Letzte Antwort
        0
        • S Sascha127

          @sascha127 said in Viessmann Heizung über Modbus steuern:

          Hallo Zusammen,
          ich klinke mich hier mal ein.
          Ich Versuche auch verzweifelt über Modbus meine Heizung auszulesen und im besten Fall zu steuern.
          Zu meiner Hardware:
          Heizung: Vitocal 200
          Heizwasserpufferspecher: VitoCell 100-E
          Wärmepumpe: Vitocal 222-A AWOT-E-AC 221.A16
          VitoConnet OPT02 zur Verbindung in die Cloud, damit die App läuft.
          LON Modul auf X24 angeschlossen
          VitoGate300 mit LON Modul verbunden und auf beiden Seiten einen Abschlusswiederstand.

          In der Anlage auch das LON Modul aktiviert.
          Auf der WebOberfläche vom Vitogate sehe ich auch den Teilnehmer und kann auch alle Objekte vom Modbus auswählen.
          Ich bekomm auch eine Verbindung mit dem IOBroker zum VitoGate über ModBus TCP hin.

          Dummerweise zeigen alle Objekte den Wert 0 an.

          Hat jemand eine Idee warum das so ist?
          Würde mich über jede kleine Hilfe sehr freuen.

          Danke im voraus.

          Gruß Sascha

          Objekte_Modbus.png IOBroker_Objekte.png IOBroker_Eingangsrgister.png Inputregister.png Datenzugriff.png

          Noch zu erwähnen:
          Wenn ich wie in der Anleitung von Viessmann das Analoge Input Register bei 30001 anfangen lasse, bekomme ich keine Verbindung zum Vitogate. Daher hab ich der Warmwasser-Solltemp. das Register 4 und nicht 30004 oder 30005 gegeben.

          HomoranH Nicht stören
          HomoranH Nicht stören
          Homoran
          Global Moderator Administrators
          schrieb am zuletzt editiert von
          #14

          @sascha127 sh ist signed hundreds.
          aber warum hast du da little Endian?

          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

          S 1 Antwort Letzte Antwort
          0
          • HomoranH Homoran

            @homoran sagte in Viessmann Heizung über Modbus steuern:

            die modbus instanz auf Logstufe debug stellen , neu starten und das debug-log zeigen

            @Sascha127 bitte das noch

            S Offline
            S Offline
            Sascha127
            schrieb am zuletzt editiert von
            #15

            @homoran
            Modbus2.log

            HomoranH 1 Antwort Letzte Antwort
            0
            • S Sascha127

              @homoran
              Modbus2.log

              HomoranH Nicht stören
              HomoranH Nicht stören
              Homoran
              Global Moderator Administrators
              schrieb am zuletzt editiert von
              #16

              @sascha127 nutzt mir am Handy nix!
              bitte immer als Text in code-tags posten

              kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

              der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

              S 1 Antwort Letzte Antwort
              0
              • HomoranH Homoran

                @sascha127 sh ist signed hundreds.
                aber warum hast du da little Endian?

                S Offline
                S Offline
                Sascha127
                schrieb am zuletzt editiert von
                #17

                @homoran
                Das war nur ein Test bei Big Endian ist auch der Wert 0

                HomoranH 1 Antwort Letzte Antwort
                0
                • S Sascha127

                  @homoran
                  Das war nur ein Test bei Big Endian ist auch der Wert 0

                  HomoranH Nicht stören
                  HomoranH Nicht stören
                  Homoran
                  Global Moderator Administrators
                  schrieb am zuletzt editiert von
                  #18

                  @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                  @homoran
                  Das war nur ein Test bei Big Endian ist auch der Wert 0

                  auch beim arbeiten ohne Aliases?

                  stimmt geräte ID 1?

                  kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                  der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                  S 1 Antwort Letzte Antwort
                  0
                  • HomoranH Homoran

                    @sascha127 nutzt mir am Handy nix!
                    bitte immer als Text in code-tags posten

                    S Offline
                    S Offline
                    Sascha127
                    schrieb am zuletzt editiert von
                    #19

                    @homoran

                    2023-09-18 13:23:46.454 - info: admin.0 (15455) ==> Connected system.user.admin from ::ffff:192.168.5.57
                    2023-09-18 13:23:46.878 - info: smartmeter.0 (15506) Received 10 values, 1 updated
                    2023-09-18 13:23:53.111 - info: host.iobroker stopInstance system.adapter.modbus.2 (force=false, process=true)
                    2023-09-18 13:23:53.117 - info: modbus.2 (10830) Got terminate signal TERMINATE_YOURSELF
                    2023-09-18 13:23:53.120 - info: modbus.2 (10830) terminating
                    2023-09-18 13:23:53.122 - info: modbus.2 (10830) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                    2023-09-18 13:23:53.159 - info: host.iobroker stopInstance system.adapter.modbus.2 send kill signal
                    2023-09-18 13:23:53.624 - info: modbus.2 (10830) terminating
                    2023-09-18 13:23:53.675 - info: host.iobroker instance system.adapter.modbus.2 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                    2023-09-18 13:23:55.750 - info: smartmeter.0 (15506) Received 10 values, 1 updated
                    2023-09-18 13:23:56.197 - info: host.iobroker instance system.adapter.modbus.2 started with pid 10909
                    2023-09-18 13:23:56.565 - info: host.iobroker stopInstance system.adapter.modbus.2 (force=false, process=true)
                    2023-09-18 13:23:56.611 - info: host.iobroker stopInstance system.adapter.modbus.2 send kill signal
                    2023-09-18 13:23:57.612 - info: host.iobroker stopInstance system.adapter.modbus.2 killing pid 10909
                    2023-09-18 13:23:57.641 - warn: host.iobroker instance system.adapter.modbus.2 terminated due to SIGTERM
                    2023-09-18 13:23:57.641 - info: host.iobroker instance system.adapter.modbus.2 terminated with code null ()
                    2023-09-18 13:23:59.663 - info: host.iobroker instance system.adapter.modbus.2 started with pid 10920
                    2023-09-18 13:23:59.975 - info: admin.0 (15455) <== Disconnect system.user.admin from ::ffff:192.168.5.57 modbus
                    2023-09-18 13:24:01.272 - debug: modbus.2 (10920) Redis Objects: Use Redis connection: 127.0.0.1:9001
                    2023-09-18 13:24:01.318 - debug: modbus.2 (10920) Objects client ready ... initialize now
                    2023-09-18 13:24:01.320 - debug: modbus.2 (10920) Objects create System PubSub Client
                    2023-09-18 13:24:01.322 - debug: modbus.2 (10920) Objects create User PubSub Client
                    2023-09-18 13:24:01.343 - debug: modbus.2 (10920) Objects client initialize lua scripts
                    2023-09-18 13:24:01.353 - debug: modbus.2 (10920) Objects connected to redis: 127.0.0.1:9001
                    2023-09-18 13:24:01.375 - debug: modbus.2 (10920) Redis States: Use Redis connection: 127.0.0.1:9000
                    2023-09-18 13:24:01.384 - debug: modbus.2 (10920) States create System PubSub Client
                    2023-09-18 13:24:01.385 - debug: modbus.2 (10920) States create User PubSub Client
                    2023-09-18 13:24:01.440 - debug: modbus.2 (10920) States connected to redis: 127.0.0.1:9000
                    2023-09-18 13:24:01.480 - debug: modbus.2 (10920) Plugin sentry Initialize Plugin (enabled=true)
                    2023-09-18 13:24:01.899 - info: modbus.2 (10920) starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.5.1, js-controller: 5.0.12
                    2023-09-18 13:24:02.035 - debug: modbus.2 (10920) Initialize Objects for disInputs: [{"_address":10001,"name":"","description":"","formula":"","role":"level","room":"","cw":"","isScale":"","address":0,"deviceId":1,"id":"discreteInputs.10001","len":1}]
                    2023-09-18 13:24:02.036 - debug: modbus.2 (10920) Add discreteInputs.10001: {"_id":"discreteInputs.10001","type":"state","common":{"name":"","role":"level","type":"boolean","read":true,"write":false,"def":false},"native":{"regType":"disInputs","address":0,"deviceId":1}}
                    2023-09-18 13:24:02.038 - debug: modbus.2 (10920) Initialize Objects for coils: []
                    2023-09-18 13:24:02.039 - debug: modbus.2 (10920) Initialize Objects for inputRegs: [{"_address":30005,"name":"1.1 Effektive Warmwasser-Solltemperatur","description":"Warmwasser-Solltemperatur","unit":"°C","type":"int16le","len":1,"factor":100,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":4,"id":"inputRegisters.30005_1_1_Effektive_Warmwasser-Solltemperatur"},{"_address":30047,"name":"1.1 Anzahl Einschalt. Verdichter","description":"Anzahl_Einschalt.Verdichter","unit":"","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":46,"id":"inputRegisters.30047_1_1_Anzahl_Einschalt__Verdichter"},{"_address":30071,"name":"1.1 Warmwassertemperatur-Sollwert","description":"Warmwassertemperatur-Sollwert","unit":"°C","type":"uint16be","len":1,"factor":10,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":70,"id":"inputRegisters.30071_1_1_Warmwassertemperatur-Sollwert"},{"_address":30090,"name":"1.1 Außentemperatur","description":"Außentemperatur","unit":"°C","type":"int16be","len":1,"factor":10,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":89,"id":"inputRegisters.30090_1_1_Außentemperatur"}]
                    2023-09-18 13:24:02.040 - debug: modbus.2 (10920) Add inputRegisters.30005_1_1_Effektive_Warmwasser-Solltemperatur: {"_id":"inputRegisters.30005_1_1_Effektive_Warmwasser-Solltemperatur","type":"state","common":{"name":"Warmwasser-Solltemperatur","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":4,"deviceId":1,"type":"int16le","len":1,"offset":0,"factor":100}}
                    2023-09-18 13:24:02.041 - debug: modbus.2 (10920) Add inputRegisters.30047_1_1_Anzahl_Einschalt__Verdichter: {"_id":"inputRegisters.30047_1_1_Anzahl_Einschalt__Verdichter","type":"state","common":{"name":"Anzahl_Einschalt.Verdichter","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":46,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1}}
                    2023-09-18 13:24:02.041 - debug: modbus.2 (10920) Add inputRegisters.30071_1_1_Warmwassertemperatur-Sollwert: {"_id":"inputRegisters.30071_1_1_Warmwassertemperatur-Sollwert","type":"state","common":{"name":"Warmwassertemperatur-Sollwert","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":70,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":10}}
                    2023-09-18 13:24:02.042 - debug: modbus.2 (10920) Add inputRegisters.30090_1_1_Außentemperatur: {"_id":"inputRegisters.30090_1_1_Außentemperatur","type":"state","common":{"name":"Außentemperatur","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"°C"},"native":{"regType":"inputRegs","address":89,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":10}}
                    2023-09-18 13:24:02.043 - debug: modbus.2 (10920) Initialize Objects for holdingRegs: []
                    2023-09-18 13:24:02.370 - info: modbus.2 (10920) Connected to slave 192.168.5.155
                    2023-09-18 13:24:02.371 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:02.372 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:02.390 - debug: modbus.2 (10920) Initialization of scale factors done!
                    2023-09-18 13:24:02.391 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:02.400 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:02.403 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:02.409 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:02.411 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:02.417 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:02.420 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:02.428 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:03.483 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:03.484 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:03.489 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:03.494 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:03.495 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:03.501 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:03.502 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:03.507 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:03.508 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:03.513 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:04.564 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:04.565 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:04.569 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:04.574 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:04.575 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:04.580 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:04.581 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:04.585 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:04.586 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:04.590 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:04.634 - info: smartmeter.0 (15506) Received 10 values, 1 updated
                    2023-09-18 13:24:05.642 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:05.643 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:05.647 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:05.655 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:05.656 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:05.660 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:05.661 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:05.666 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:05.667 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:05.671 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:06.722 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:06.723 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:06.728 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:06.732 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:06.733 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:06.737 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:06.738 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:06.743 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:06.743 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:06.748 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:07.802 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:07.803 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:07.808 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:07.812 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:07.813 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:07.819 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:07.820 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:07.824 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:07.825 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:07.829 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:08.882 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:08.883 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:08.889 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:08.893 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:08.894 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:08.898 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:08.899 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:08.907 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:08.908 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:08.913 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:09.964 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:09.965 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:09.969 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:09.974 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:09.975 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:09.979 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:09.980 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:09.984 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:09.985 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:09.989 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:11.041 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:11.042 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:11.046 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:11.050 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:11.051 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:11.059 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:11.060 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:11.065 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:11.067 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:11.072 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:12.124 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:12.125 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:12.129 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:12.134 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:12.135 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:12.139 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:12.140 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:12.145 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:12.146 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:12.150 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:13.201 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:13.202 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:13.206 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:13.212 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:13.213 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:13.217 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:13.218 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:13.224 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:13.225 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:13.231 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:13.496 - info: smartmeter.0 (15506) Received 10 values, 1 updated
                    2023-09-18 13:24:14.282 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:14.283 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:14.287 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:14.292 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:14.293 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:14.297 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:14.298 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:14.302 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:14.302 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:14.307 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:15.358 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:15.359 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:15.363 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:15.368 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:15.368 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:15.373 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:15.374 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:15.382 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:15.383 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:15.388 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:16.439 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:16.441 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:16.447 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:16.453 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:16.455 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:16.461 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:16.464 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:16.471 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:16.473 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:16.480 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:17.543 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:17.544 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:17.549 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:17.555 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:17.556 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:17.560 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:17.561 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:17.565 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:17.566 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:17.571 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:18.623 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:18.625 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:18.629 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:18.634 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:18.635 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:18.639 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:18.640 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:18.644 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:18.645 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:18.649 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:19.703 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:19.704 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:19.709 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:19.713 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:19.714 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:19.718 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:19.719 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:19.723 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:19.724 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:19.729 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:20.781 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:20.782 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:20.787 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:20.791 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:20.792 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:20.797 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:20.798 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:20.802 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:20.803 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:20.809 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:21.861 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:21.863 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:21.869 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:21.875 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:21.877 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:21.883 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:21.885 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:21.892 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:21.893 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:21.899 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:22.366 - info: smartmeter.0 (15506) Received 10 values, 1 updated
                    2023-09-18 13:24:22.951 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:22.952 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:22.957 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:22.962 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:22.963 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:22.968 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:22.969 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:22.974 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:22.975 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:22.980 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:24.032 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:24.033 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:24.038 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:24.042 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:24.043 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:24.047 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:24.050 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:24.055 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:24.055 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:24.061 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:25.113 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:25.113 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:25.117 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:25.122 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:25.123 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:25.127 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:25.128 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:25.133 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:25.134 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:25.139 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:26.190 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:26.191 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:26.195 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:26.199 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:26.200 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:26.206 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:26.207 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:26.211 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:26.212 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:26.217 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:27.268 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:27.269 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:27.274 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:27.283 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:27.285 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:27.294 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:27.296 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:27.301 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:27.302 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:27.310 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:28.362 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:28.363 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:28.367 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:28.371 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:28.372 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:28.376 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:28.377 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:28.381 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:28.382 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:28.386 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:29.438 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:29.438 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:29.446 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:29.450 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:29.451 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:29.455 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:29.456 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:29.460 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:29.460 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:29.465 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:30.517 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:30.517 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:30.523 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:30.527 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:30.528 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:30.535 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:30.536 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:30.540 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:30.541 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:30.545 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:30.694 - info: smartmeter.0 (15506) Received 10 values, 3 updated
                    2023-09-18 13:24:31.597 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:31.598 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:31.602 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:31.606 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:31.607 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:31.611 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:31.612 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:31.616 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:31.617 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:31.621 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:32.674 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:32.675 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:32.680 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:32.687 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:32.689 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:32.694 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:32.696 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:32.702 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:32.703 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:32.708 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:33.761 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:33.762 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:33.766 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:33.770 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:33.771 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:33.776 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:33.776 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:33.781 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:33.782 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:33.786 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:34.839 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:34.840 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:34.844 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:34.847 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:34.849 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:34.853 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:34.854 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:34.858 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:34.859 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:34.864 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    2023-09-18 13:24:35.916 - debug: modbus.2 (10920) [DevID_1] Poll start ---------------------
                    2023-09-18 13:24:35.917 - debug: modbus.2 (10920) [DevID_1/disInputs] Poll address 0 - 16 bits
                    2023-09-18 13:24:35.921 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 - 1 registers
                    2023-09-18 13:24:35.925 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 4 DONE
                    2023-09-18 13:24:35.926 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 - 1 registers
                    2023-09-18 13:24:35.930 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 46 DONE
                    2023-09-18 13:24:35.931 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 - 1 registers
                    2023-09-18 13:24:35.935 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 70 DONE
                    2023-09-18 13:24:35.937 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 - 1 registers
                    2023-09-18 13:24:35.942 - debug: modbus.2 (10920) [DevID_1/inputRegs] Poll address 89 DONE
                    
                    1 Antwort Letzte Antwort
                    0
                    • HomoranH Homoran

                      @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                      @homoran
                      Das war nur ein Test bei Big Endian ist auch der Wert 0

                      auch beim arbeiten ohne Aliases?

                      stimmt geräte ID 1?

                      S Offline
                      S Offline
                      Sascha127
                      schrieb am zuletzt editiert von
                      #20

                      @homoran
                      Jepp auch beim Arbeiten ohne Aliases.
                      Ja die ID beim Vitogate ist die 1.

                      Vitogate300_Modbus_konfig.png

                      HomoranH 1 Antwort Letzte Antwort
                      0
                      • S Sascha127

                        @homoran
                        Jepp auch beim Arbeiten ohne Aliases.
                        Ja die ID beim Vitogate ist die 1.

                        Vitogate300_Modbus_konfig.png

                        HomoranH Nicht stören
                        HomoranH Nicht stören
                        Homoran
                        Global Moderator Administrators
                        schrieb am zuletzt editiert von Homoran
                        #21

                        @sascha127 dann arbeite erst einmal nur mit einem einzigen input Register, nichts anderes

                        wenn das läuft kann man ausbauen.

                        laut log pollt er jede Sekunde mehrere Werte

                        edit:
                        mach mal den Haken bei direkte werte verwenden weg

                        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                        S 1 Antwort Letzte Antwort
                        0
                        • HomoranH Homoran

                          @sascha127 dann arbeite erst einmal nur mit einem einzigen input Register, nichts anderes

                          wenn das läuft kann man ausbauen.

                          laut log pollt er jede Sekunde mehrere Werte

                          edit:
                          mach mal den Haken bei direkte werte verwenden weg

                          S Offline
                          S Offline
                          Sascha127
                          schrieb am zuletzt editiert von
                          #22

                          @homoran
                          Ok, Haken ist raus.
                          Hab jetzt auch nur einen Wert, den ich auslesen möchte.
                          modbus.2.inputRegisters.30005_1_1_Effektive_Warmwasser-Solltemperatur

                          IOBroker_Haken_entfernt.png

                          Wert ist immer noch 0.

                          HomoranH 1 Antwort Letzte Antwort
                          0
                          • S Sascha127

                            @homoran
                            Ok, Haken ist raus.
                            Hab jetzt auch nur einen Wert, den ich auslesen möchte.
                            modbus.2.inputRegisters.30005_1_1_Effektive_Warmwasser-Solltemperatur

                            IOBroker_Haken_entfernt.png

                            Wert ist immer noch 0.

                            HomoranH Nicht stören
                            HomoranH Nicht stören
                            Homoran
                            Global Moderator Administrators
                            schrieb am zuletzt editiert von Homoran
                            #23

                            @sascha127 Wenn die Ursache nicht an der Konfiguration vom Vitogate liegt weiss ich auch nicht mehr.

                            in der Anleitung steht du sollst input register 30001-xxxx nehmen mit int16 und Faktor
                            der offset von 30001 (??) würde aus 4 eine 30005 machen.

                            Mach mal spaßeshalber 30004 und 30006

                            was ist denn im moment deine Solltemperatur?

                            kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                            der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                            S 1 Antwort Letzte Antwort
                            0
                            • HomoranH Homoran

                              @sascha127 Wenn die Ursache nicht an der Konfiguration vom Vitogate liegt weiss ich auch nicht mehr.

                              in der Anleitung steht du sollst input register 30001-xxxx nehmen mit int16 und Faktor
                              der offset von 30001 (??) würde aus 4 eine 30005 machen.

                              Mach mal spaßeshalber 30004 und 30006

                              was ist denn im moment deine Solltemperatur?

                              S Offline
                              S Offline
                              Sascha127
                              schrieb am zuletzt editiert von
                              #24

                              @homoran

                              Also ich würde mal sagen, dass dieses Register 4 bzw. 30004 1.1 Effektive Warmwasser-Solltemperatur nichts ausgibt.
                              Ich habe jetzt das Register 70 bzw. 30070 1.1 Warmwassertemperatur-Sollwert eingetragen siehe Bilder. Faktor 10 ergab dann denn wert 4000, deshalb hab ich jetzt Faktor 0.1 gewählt.
                              Und siehe da, 40°C zeigt das Objekt an.
                              Habe dann mal mit der App die Sollwerttemp. auf 41 gestellt und dann ist auch der Wert im Objekt auf 41°C gestiegen.
                              Ich glaube, es läuft jetzt. Ich muss eben nur herausfinden, welches Register wirklich den Wert beinhaltet.

                              Vielen lieben Dank für die Hilfe.

                              Warmwassersoll.png

                              Warmwassersoll_IOBroker.png

                              IOBroker_Objekt.png

                              HomoranH 1 Antwort Letzte Antwort
                              0
                              • S Sascha127

                                @homoran

                                Also ich würde mal sagen, dass dieses Register 4 bzw. 30004 1.1 Effektive Warmwasser-Solltemperatur nichts ausgibt.
                                Ich habe jetzt das Register 70 bzw. 30070 1.1 Warmwassertemperatur-Sollwert eingetragen siehe Bilder. Faktor 10 ergab dann denn wert 4000, deshalb hab ich jetzt Faktor 0.1 gewählt.
                                Und siehe da, 40°C zeigt das Objekt an.
                                Habe dann mal mit der App die Sollwerttemp. auf 41 gestellt und dann ist auch der Wert im Objekt auf 41°C gestiegen.
                                Ich glaube, es läuft jetzt. Ich muss eben nur herausfinden, welches Register wirklich den Wert beinhaltet.

                                Vielen lieben Dank für die Hilfe.

                                Warmwassersoll.png

                                Warmwassersoll_IOBroker.png

                                IOBroker_Objekt.png

                                HomoranH Nicht stören
                                HomoranH Nicht stören
                                Homoran
                                Global Moderator Administrators
                                schrieb am zuletzt editiert von Homoran
                                #25

                                @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                                Faktor 10 ergab dann denn wert 4000, deshalb hab ich jetzt Faktor 0.1 gewählt.

                                und Faktor 0.01 statt 100 bei 30005 (30004)?

                                kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                S 1 Antwort Letzte Antwort
                                1
                                • HomoranH Homoran

                                  @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                                  Faktor 10 ergab dann denn wert 4000, deshalb hab ich jetzt Faktor 0.1 gewählt.

                                  und Faktor 0.01 statt 100 bei 30005 (30004)?

                                  S Offline
                                  S Offline
                                  Sascha127
                                  schrieb am zuletzt editiert von
                                  #26

                                  @homoran
                                  Stimmt es lag am Faktor, auch das Register 30004 gibt mit Faktor 0.01 jetzt 40°C aus.
                                  Spielt die Länge bei dem Register eine Rolle? Hab mal mit 1 und 2 probiert, kommt bei beiden 40 raus.

                                  IOBroker_Faktor.png

                                  HomoranH 1 Antwort Letzte Antwort
                                  0
                                  • S Sascha127

                                    @homoran
                                    Stimmt es lag am Faktor, auch das Register 30004 gibt mit Faktor 0.01 jetzt 40°C aus.
                                    Spielt die Länge bei dem Register eine Rolle? Hab mal mit 1 und 2 probiert, kommt bei beiden 40 raus.

                                    IOBroker_Faktor.png

                                    HomoranH Nicht stören
                                    HomoranH Nicht stören
                                    Homoran
                                    Global Moderator Administrators
                                    schrieb am zuletzt editiert von
                                    #27

                                    @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                                    Spielt die Länge bei dem Register eine Rolle?

                                    ja, natürlich!
                                    Wird aber automatisch gesetzt!


                                    wieso hast du noch coils Datenpunkte?

                                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                    S 1 Antwort Letzte Antwort
                                    0
                                    • HomoranH Homoran

                                      @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                                      Spielt die Länge bei dem Register eine Rolle?

                                      ja, natürlich!
                                      Wird aber automatisch gesetzt!


                                      wieso hast du noch coils Datenpunkte?

                                      S Offline
                                      S Offline
                                      Sascha127
                                      schrieb am zuletzt editiert von
                                      #28

                                      @homoran
                                      Ok ich importiere die Register immer, vorher baue ich diese mit Notepad++ zusammen da kann ich eben die Länge angeben.

                                      Coils hab ich auch noch.

                                      Warum mach ich den ganzen Stress überhaupt?!?
                                      Ich möchte meine Wärmepumpe erst dann einschalten, wenn mein Akku der PV 100% geladen ist, damit ich nichts vom Netz ziehen muss.
                                      Wenn dann die WP läuft soll sie das Warmwasser auf 60°C aufheizen, da ja genug Energie da ist.
                                      Praktisch wäre auch dass die WP nur einmal am Tag angeht, und der Rest kann ja der Heizstab im Pufferspeicher erledigen. Kostet natürlich sau viel Strom aber wenn die Sonne ballert ist mir das ja lieber ich verbrauche den Strom, wie dass ich für ein Apfel und ein Ei einspeise.
                                      Zudem hält dann vllt. auch die WP länger wenn ich die Einschaltzyklen minimiere.
                                      Ist natürlich alles im Sommer easy zu realisieren, im Winter schau ma mal... Hab die PV erst seit Juni 23.

                                      Ich hoffe ich konnte ein wenig für Klarheit sorgen 😊

                                      Coils.png

                                      HomoranH 1 Antwort Letzte Antwort
                                      0
                                      • S Sascha127

                                        @homoran
                                        Ok ich importiere die Register immer, vorher baue ich diese mit Notepad++ zusammen da kann ich eben die Länge angeben.

                                        Coils hab ich auch noch.

                                        Warum mach ich den ganzen Stress überhaupt?!?
                                        Ich möchte meine Wärmepumpe erst dann einschalten, wenn mein Akku der PV 100% geladen ist, damit ich nichts vom Netz ziehen muss.
                                        Wenn dann die WP läuft soll sie das Warmwasser auf 60°C aufheizen, da ja genug Energie da ist.
                                        Praktisch wäre auch dass die WP nur einmal am Tag angeht, und der Rest kann ja der Heizstab im Pufferspeicher erledigen. Kostet natürlich sau viel Strom aber wenn die Sonne ballert ist mir das ja lieber ich verbrauche den Strom, wie dass ich für ein Apfel und ein Ei einspeise.
                                        Zudem hält dann vllt. auch die WP länger wenn ich die Einschaltzyklen minimiere.
                                        Ist natürlich alles im Sommer easy zu realisieren, im Winter schau ma mal... Hab die PV erst seit Juni 23.

                                        Ich hoffe ich konnte ein wenig für Klarheit sorgen 😊

                                        Coils.png

                                        HomoranH Nicht stören
                                        HomoranH Nicht stören
                                        Homoran
                                        Global Moderator Administrators
                                        schrieb am zuletzt editiert von Homoran
                                        #29

                                        @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                                        Coils hab ich auch noch.

                                        wenn ich die Anleitung richtig verstanden habe ist das eine Alternative statt Register.

                                        Außerdem solltest du ja alles bis auf einen Eintrag entfernt haben.

                                        @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                                        Warum mach ich den ganzen Stress überhaupt?!?

                                        ist mir schon klar. Will ich im Winter ähnlich machen, habe aber Heating only.
                                        Hab daher nur wenige Register
                                        Screenshot_20230918-145512_Firefox.jpg
                                        mit jetzt nur "fake" Werten

                                        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                        S 1 Antwort Letzte Antwort
                                        0
                                        • HomoranH Homoran

                                          @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                                          Coils hab ich auch noch.

                                          wenn ich die Anleitung richtig verstanden habe ist das eine Alternative statt Register.

                                          Außerdem solltest du ja alles bis auf einen Eintrag entfernt haben.

                                          @sascha127 sagte in Viessmann Heizung über Modbus steuern:

                                          Warum mach ich den ganzen Stress überhaupt?!?

                                          ist mir schon klar. Will ich im Winter ähnlich machen, habe aber Heating only.
                                          Hab daher nur wenige Register
                                          Screenshot_20230918-145512_Firefox.jpg
                                          mit jetzt nur "fake" Werten

                                          S Offline
                                          S Offline
                                          Sascha127
                                          schrieb am zuletzt editiert von Sascha127
                                          #30

                                          @homoran

                                          Ok, ich hab das so verstanden mit den coils, wenn ich den wert auf 1 setze bei Reg. 17 dann schaltet er die einmalige Warmwasseraufbereitung an.
                                          Was er aktuell machen könne, da mein Akku 100% und die PV um die 8KW produziert.

                                          Naja mittlerweile habe ich wieder mehrere Einträge drin, hat ja mit einem Wert funktioniert 😉

                                          Ich bin immer wieder fasziniert, was ihr alle so für cooles Visualisierungen habt.
                                          Ich sammele im Moment nur Werte und versuche da etwas smartes daraus zu basteln.

                                          Edit: Das hat mal funktioniert mit dem "Register" 17 den Wert auf 1 setzen.
                                          Er hat dann die einmalige Warmwasseraufbereitung gestartet und mir in der App angezeigt.

                                          Warmwassersolltemp. ist auf 60°C gegangen und der Verdichter hat dann auch eingeschaltet.

                                          Jetzt nur die Frage: Wie kann ich einstellen, dass er nicht den Verdichter einschaltet sondern den Heizstab?

                                          Naja wird es auch ein Register geben, welches ich auf 1 setzen kann und dann den Verdichter auf 0 oder so in der Art...

                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          816

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe