  3. Einsteigerfragen
  4. Sofar Solar HYD10 KTL Wechselrichter an modbus Adapter
    2.7k
    4.8k
    4.0k
190 Beiträge 20 Kommentatoren 35.4k Aufrufe 16 Beobachtet
  • V V8Turbo
    @glasfaser Anbei die aktuellen Werte. Der WR ist auch auf 9600 eingestellt.
    Im Holding Register ist jetzt nur ein Eintrag
    _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
    1412	Voltage_PV1		V	uint16be	1	0,1	0		state		true	false	false	false
    Aktuelles Log von gerade Ebend.
    modbus.0
    2023-01-13 07:32:40.268	debug	Cleaning up request fifo.
    modbus.0
    2023-01-13 07:32:40.267	debug	Clearing timeout of the current request.
    modbus.0
    2023-01-13 07:32:40.263	info	Disconnected from slave
    modbus.0
    2023-01-13 07:32:39.566	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:39.565	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:39.263	warn	Poll error count: 2 code: {"err":"timeout","timeout":4000}
    modbus.0
    2023-01-13 07:32:39.262	error	Request timed out.
    modbus.0
    2023-01-13 07:32:39.261	warn	Error: undefined
    modbus.0
    2023-01-13 07:32:35.291	error	Wrong CRC for frame: 255,2,3,2,4,172,254,249
    modbus.0
    2023-01-13 07:32:35.259	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:35.258	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:35.255	info	Connected to slave
    modbus.0
    2023-01-13 07:32:35.249	debug	connect to serial /dev/ttyUSB0 with 9600
    modbus.0
    2023-01-13 07:32:29.251	debug	Cleaning up request fifo.
    modbus.0
    2023-01-13 07:32:29.250	debug	Clearing timeout of the current request.
    modbus.0
    2023-01-13 07:32:29.248	info	Disconnected from slave
    modbus.0
    2023-01-13 07:32:28.550	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:28.549	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:28.248	warn	Poll error count: 1 code: {"err":"timeout","timeout":4000}
    modbus.0
    2023-01-13 07:32:28.247	error	Request timed out.
    modbus.0
    2023-01-13 07:32:28.246	warn	Error: undefined
    modbus.0
    2023-01-13 07:32:24.277	error	Wrong CRC for frame: 255,2,3,2,7,173,63,201
    modbus.0
    2023-01-13 07:32:24.244	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:24.243	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:23.740	debug	[DevID_2/holdingRegs] Poll address 1412 DONE
    modbus.0
    2023-01-13 07:32:23.707	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:23.706	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:23.704	info	Connected to slave
    modbus.0
    2023-01-13 07:32:23.695	debug	connect to serial /dev/ttyUSB0 with 9600
    modbus.0
    2023-01-13 07:32:17.697	debug	Cleaning up request fifo.
    modbus.0
    2023-01-13 07:32:17.696	debug	Clearing timeout of the current request.
    modbus.0
    2023-01-13 07:32:17.693	info	Disconnected from slave
    modbus.0
    2023-01-13 07:32:16.995	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:16.994	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:16.693	warn	Poll error count: 2 code: {"err":"timeout","timeout":4000}
    modbus.0
    2023-01-13 07:32:16.692	error	Request timed out.
    modbus.0
    2023-01-13 07:32:16.690	warn	Error: undefined
    modbus.0
    2023-01-13 07:32:12.721	error	Wrong CRC for frame: 3,2,4,250,126,199,255,2,3
    modbus.0
    2023-01-13 07:32:12.688	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:12.687	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:12.686	info	Connected to slave
    modbus.0
    2023-01-13 07:32:12.677	debug	connect to serial /dev/ttyUSB0 with 9600
    modbus.0
    2023-01-13 07:32:06.678	debug	Cleaning up request fifo.
    modbus.0
    2023-01-13 07:32:06.677	debug	Clearing timeout of the current request.
    modbus.0
    2023-01-13 07:32:06.675	info	Disconnected from slave
    modbus.0
    2023-01-13 07:32:05.976	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:05.975	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:05.673	warn	Poll error count: 1 code: {"err":"timeout","timeout":4000}
    modbus.0
    2023-01-13 07:32:05.673	error	Request timed out.
    modbus.0
    2023-01-13 07:32:05.672	warn	Error: undefined
    modbus.0
    2023-01-13 07:32:01.668	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:01.667	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:01.165	debug	[DevID_2/holdingRegs] Poll address 1412 DONE
    modbus.0
    2023-01-13 07:32:01.133	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:01.132	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:00.627	debug	[DevID_2/holdingRegs] Poll address 1412 DONE
    modbus.0
    2023-01-13 07:32:00.589	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:32:00.588	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:32:00.587	info	Connected to slave
    modbus.0
    2023-01-13 07:32:00.579	debug	connect to serial /dev/ttyUSB0 with 9600
    modbus.0
    2023-01-13 07:31:54.579	debug	Cleaning up request fifo.
    modbus.0
    2023-01-13 07:31:54.578	debug	Clearing timeout of the current request.
    modbus.0
    2023-01-13 07:31:54.576	info	Disconnected from slave
    modbus.0
    2023-01-13 07:31:53.879	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:31:53.877	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:31:53.576	warn	Poll error count: 1 code: {"err":"timeout","timeout":4000}
    modbus.0
    2023-01-13 07:31:53.573	error	Request timed out.
    modbus.0
    2023-01-13 07:31:53.572	warn	Error: undefined
    modbus.0
    2023-01-13 07:31:49.604	error	unknown function code: 0x20, 0xa0
    modbus.0
    2023-01-13 07:31:49.564	debug	[DevID_2/holdingRegs] Poll address 1412 - 1 registers
    modbus.0
    2023-01-13 07:31:49.564	debug	Initialization of scale factors done!
    modbus.0
    2023-01-13 07:31:49.562	debug	[DevID_2] Poll start ---------------------
    modbus.0
    2023-01-13 07:31:49.561	info	Connected to slave
    modbus.0
    2023-01-13 07:31:49.554	debug	connect to serial /dev/ttyUSB0 with 9600
    V Offline
    V Offline
    V8Turbo
    #21
    Achso die Werte trägt er, auch wenn alle im Holding stehen sporadisch mal ein (siehe Log oben). Also ja die Werte trägt er irgendwann wenn die Connection klappt ein und die stimmen auch.
    • wendy2702W Offline
      wendy2702W Offline
      wendy2702
      #22
      Wenn ich mir den Screenshot ansehe hast du schon einiges an den Grundeinstellungen verbogen.
      ich würde mal mit diesen Beginnen:
      Also nach Instanz Installation nur den haken bei "Aliases benutzen" raus machen.
      Sicherstellen das der WR die gleichen Kommunikationseinstellungen verwendet die im Adapter eingestellt sind. > Baudrate, Data Bits, Stop Bits, Parität, Geräte ID
      Im Holding Register nur 1 Register Eintragen bei dem das Ergebnis eindeutig ist:
      Z.B. Frequenz HEX=484 DEC=1156 Unsigned 16bit Big Endian Faktor 0.01 Einheit Hz
      Dann schauen ob was kommt.
      Wenn nicht das Register in Holding löschen und bei Eingangsregister eintragen und testen.
      Meine SMA WR haben z.B. Eingangsregister definiert.
      V 1 Antwort Letzte Antwort
      • wendy2702W wendy2702
        V Offline
        V Offline
        V8Turbo
        schrieb am zuletzt editiert von V8Turbo
        #23
        @wendy2702
        Einstellungen sind so gesetzt... Bis auf den Haken bei "Adressen nicht auf 16bit...." der muss rein. (bzw. habe es auch gerade ohne probiert passiert das gleiche)
        Sicherstellen das der WR die gleichen Kommunikationseinstellungen verwendet die im Adapter eingestellt sind. > Baudrate, Data Bits, Stop Bits, Parität, Geräte ID <- Wie soll ich das machen ? Es gibt nur eine Einstellung im WR und da kann man die BAUD eintragen. Anleitung steht auch nichts...
        Holding Register, Eingangsregister kommt die gleiche Meldung im Log (siehe unten)...
        modbus.0
        2023-01-13 08:37:42.765	debug	Plugin sentry Initialize Plugin (enabled=true)
        modbus.0
        2023-01-13 08:40:01.661	debug	Cleaning up request fifo.
        modbus.0
        2023-01-13 08:40:01.660	debug	Clearing timeout of the current request.
        modbus.0
        2023-01-13 08:40:01.657	info	Disconnected from slave
        modbus.0
        2023-01-13 08:40:00.659	warn	Poll error count: 3 code: {"err":"timeout","timeout":5000}
        modbus.0
        2023-01-13 08:40:00.656	error	Request timed out.
        modbus.0
        2023-01-13 08:40:00.655	warn	Error: undefined
        modbus.0
        2023-01-13 08:39:55.652	debug	[DevID_2/inputRegs] Poll address 1412 - 1 registers
        modbus.0
        2023-01-13 08:39:55.651	debug	[DevID_2] Poll start ---------------------
        modbus.0
        2023-01-13 08:39:55.650	info	Connected to slave
        modbus.0
        2023-01-13 08:39:55.643	debug	connect to serial /dev/ttyUSB0 with 9600
        modbus.0
        2023-01-13 08:38:55.646	debug	Cleaning up request fifo.
        modbus.0
        2023-01-13 08:38:55.644	debug	Clearing timeout of the current request.
        modbus.0
        2023-01-13 08:38:55.641	info	Disconnected from slave
        modbus.0
        2023-01-13 08:38:54.641	warn	Poll error count: 2 code: {"err":"timeout","timeout":5000}
        modbus.0
        2023-01-13 08:38:54.639	error	Request timed out.
        modbus.0
        2023-01-13 08:38:54.638	warn	Error: undefined
        modbus.0
        2023-01-13 08:38:49.634	debug	[DevID_2/inputRegs] Poll address 1412 - 1 registers
        modbus.0
        2023-01-13 08:38:49.633	debug	[DevID_2] Poll start ---------------------
        modbus.0
        2023-01-13 08:38:49.632	info	Connected to slave
        modbus.0
        2023-01-13 08:38:49.623	debug	connect to serial /dev/ttyUSB0 with 9600
        modbus.0
        2023-01-13 08:37:49.627	debug	Cleaning up request fifo.
        modbus.0
        2023-01-13 08:37:49.626	debug	Clearing timeout of the current request.
        modbus.0
        2023-01-13 08:37:49.621	info	Disconnected from slave
        modbus.0
        2023-01-13 08:37:48.620	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
        modbus.0
        2023-01-13 08:37:48.617	error	Request timed out.
        modbus.0
        2023-01-13 08:37:48.616	warn	Error: undefined
        modbus.0
        2023-01-13 08:37:43.609	debug	[DevID_2/inputRegs] Poll address 1412 - 1 registers
        modbus.0
        2023-01-13 08:37:43.608	debug	Initialization of scale factors done!
        modbus.0
        2023-01-13 08:37:43.606	debug	[DevID_2] Poll start ---------------------
        modbus.0
        2023-01-13 08:37:43.605	info	Connected to slave
        modbus.0
        2023-01-13 08:37:43.586	debug	connect to serial /dev/ttyUSB0 with 9600
        V wendy2702W 2 Antworten Letzte Antwort
        • V V8Turbo
          @wendy2702
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          V Offline
          V Offline
          V8Turbo
          #24
          Hab jetzt mal inverter Temperatur genommen statt PV Voltage... Aber ist ja das gleiche.
          OHNE Haken bei Adressen 16bit bla bla...
          modbus.0
          2023-01-13 08:46:16.526	debug	Cleaning up request fifo.
          modbus.0
          2023-01-13 08:46:16.525	debug	Clearing timeout of the current request.
          modbus.0
          2023-01-13 08:46:16.522	info	Disconnected from slave
          modbus.0
          2023-01-13 08:46:15.521	warn	Poll error count: 2 code: {"err":"timeout","timeout":5000}
          modbus.0
          2023-01-13 08:46:15.520	error	Request timed out.
          modbus.0
          2023-01-13 08:46:15.518	warn	Error: undefined
          modbus.0
          2023-01-13 08:46:10.587	error	unknown function code: 0x20, 0x20
          modbus.0
          2023-01-13 08:46:10.517	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:46:10.516	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:46:10.516	info	Connected to slave
          modbus.0
          2023-01-13 08:46:10.511	debug	connect to serial /dev/ttyUSB0 with 9600
          modbus.0
          2023-01-13 08:45:10.515	debug	Cleaning up request fifo.
          modbus.0
          2023-01-13 08:45:10.514	debug	Clearing timeout of the current request.
          modbus.0
          2023-01-13 08:45:10.509	info	Disconnected from slave
          modbus.0
          2023-01-13 08:45:09.507	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
          modbus.0
          2023-01-13 08:45:09.505	error	Request timed out.
          modbus.0
          2023-01-13 08:45:09.504	warn	Error: undefined
          modbus.0
          2023-01-13 08:45:04.567	error	Error response: 20
          modbus.0
          2023-01-13 08:45:04.500	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:45:04.499	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:45:03.444	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
          modbus.0
          2023-01-13 08:45:03.405	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:45:03.404	debug	Initialization of scale factors done!
          modbus.0
          2023-01-13 08:45:03.402	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:45:03.401	info	Connected to slave
          modbus.0
          2023-01-13 08:45:03.387	debug	connect to serial /dev/ttyUSB0 with 9600
          modbus.0
          2023-01-13 08:45:03.069	debug	Add holdingRegisters.1056_Temperature_Inv1: {"_id":"holdingRegisters.1056_Temperature_Inv1","type":"state","common":{"name":"","role":"state","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":1056,"deviceId":2,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
          modbus.0
          2023-01-13 08:45:03.068	debug	Initialize Objects for holdingRegs: [{"_address":"1056","name":"Temperature_Inv1","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"state","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":2,"address":1056,"id":"holdingRegisters.1056_Temperature_Inv1"}]
          modbus.0
          2023-01-13 08:45:03.068	debug	Initialize Objects for inputRegs: []
          modbus.0
          2023-01-13 08:45:03.067	debug	Initialize Objects for coils: []
          modbus.0
          2023-01-13 08:45:03.066	debug	Initialize Objects for disInputs: []
          modbus.0
          2023-01-13 08:45:02.924	info	starting. Version 5.0.11 (non-npm: ioBroker/ioBroker.modbus) in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
          modbus.0
          2023-01-13 08:45:02.606	debug	Plugin sentry Initialize Plugin (enabled=true)
          host.raspberrypi
          2023-01-13 08:45:01.211	info	instance system.adapter.modbus.0 started with pid 5986
          MIT Haken bei Adressen 16bit blabla...
          modbus.0
          2023-01-13 08:47:55.508	debug	Cleaning up request fifo.
          modbus.0
          2023-01-13 08:47:55.507	debug	Clearing timeout of the current request.
          modbus.0
          2023-01-13 08:47:55.504	info	Disconnected from slave
          modbus.0
          2023-01-13 08:47:54.503	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
          modbus.0
          2023-01-13 08:47:54.501	error	Request timed out.
          modbus.0
          2023-01-13 08:47:54.499	warn	Error: undefined
          modbus.0
          2023-01-13 08:47:49.530	error	unknown function code: 0x20, 0x20
          modbus.0
          2023-01-13 08:47:49.497	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:47:49.495	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:47:48.443	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
          modbus.0
          2023-01-13 08:47:48.411	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:47:48.410	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:47:47.356	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
          modbus.0
          2023-01-13 08:47:47.323	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:47:47.322	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:47:46.269	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
          modbus.0
          2023-01-13 08:47:46.165	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:47:46.163	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:47:45.109	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
          modbus.0
          2023-01-13 08:47:45.076	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:47:45.075	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:47:44.022	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
          modbus.0
          2023-01-13 08:47:43.985	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:47:43.984	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:47:42.930	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
          modbus.0
          2023-01-13 08:47:42.892	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
          modbus.0
          2023-01-13 08:47:42.891	debug	Initialization of scale factors done!
          modbus.0
          2023-01-13 08:47:42.889	debug	[DevID_2] Poll start ---------------------
          modbus.0
          2023-01-13 08:47:42.888	info	Connected to slave
          modbus.0
          2023-01-13 08:47:42.870	debug	connect to serial /dev/ttyUSB0 with 9600
          • V V8Turbo
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            host.raspberrypi
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            V Offline
            V Offline
            V8Turbo
            #25
            Und so sieht das ganze aus wenn es eine weile lief...
            modbus.0
            2023-01-13 09:14:40.917	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:14:40.916	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:14:40.910	info	Disconnected from slave
            modbus.0
            2023-01-13 09:14:39.907	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:14:39.906	error	Request timed out.
            modbus.0
            2023-01-13 09:14:39.905	warn	Error: undefined
            modbus.0
            2023-01-13 09:14:34.935	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:14:34.901	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:14:34.900	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:14:33.843	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 09:14:33.793	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:14:33.792	debug	Initialization of scale factors done!
            modbus.0
            2023-01-13 09:14:33.789	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:14:33.787	info	Connected to slave
            modbus.0
            2023-01-13 09:14:33.778	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:14:33.501	debug	Add holdingRegisters.1056_Temperature_Inv1: {"_id":"holdingRegisters.1056_Temperature_Inv1","type":"state","common":{"name":"","role":"state","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":1056,"deviceId":2,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
            modbus.0
            2023-01-13 09:14:33.501	debug	Initialize Objects for holdingRegs: [{"_address":"1056","name":"Temperature_Inv1","description":"","unit":"°C","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"state","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":2,"address":1056,"id":"holdingRegisters.1056_Temperature_Inv1"}]
            modbus.0
            2023-01-13 09:14:33.500	debug	Initialize Objects for inputRegs: []
            modbus.0
            2023-01-13 09:14:33.499	debug	Initialize Objects for coils: []
            modbus.0
            2023-01-13 09:14:33.498	debug	Initialize Objects for disInputs: []
            modbus.0
            2023-01-13 09:14:33.357	info	starting. Version 5.0.11 (non-npm: ioBroker/ioBroker.modbus) in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
            modbus.0
            2023-01-13 09:14:33.037	debug	Plugin sentry Initialize Plugin (enabled=true)
            host.raspberrypi
            2023-01-13 09:14:31.670	info	instance system.adapter.modbus.0 started with pid 6057
            host.raspberrypi
            2023-01-13 09:14:30.562	info	Restart adapter system.adapter.modbus.0 because enabled
            host.raspberrypi
            2023-01-13 09:14:30.561	info	instance system.adapter.modbus.0 terminated with code 156 (START_IMMEDIATELY_AFTER_STOP)
            modbus.0
            2023-01-13 09:14:29.937	info	Terminated (START_IMMEDIATELY_AFTER_STOP): Without reason
            modbus.0
            2023-01-13 09:14:29.936	debug	Plugin sentry destroyed
            modbus.0
            2023-01-13 09:14:29.934	error	Reconnect did not help, restart adapter
            modbus.0
            2023-01-13 09:14:29.933	warn	Poll error count: 13 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:14:29.932	error	Request timed out.
            modbus.0
            2023-01-13 09:14:29.931	warn	Error: undefined
            modbus.0
            2023-01-13 09:14:24.960	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:14:24.929	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:14:24.928	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:14:24.927	info	Connected to slave
            modbus.0
            2023-01-13 09:14:24.921	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:13:24.923	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:13:24.922	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:13:24.919	info	Disconnected from slave
            modbus.0
            2023-01-13 09:13:23.918	warn	Poll error count: 12 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:13:23.917	error	Request timed out.
            modbus.0
            2023-01-13 09:13:23.916	warn	Error: undefined
            modbus.0
            2023-01-13 09:13:18.944	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:13:18.914	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:13:18.914	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:13:18.913	info	Connected to slave
            modbus.0
            2023-01-13 09:13:18.907	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:12:18.908	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:12:18.907	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:12:18.905	info	Disconnected from slave
            modbus.0
            2023-01-13 09:12:17.904	warn	Poll error count: 11 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:12:17.904	error	Request timed out.
            modbus.0
            2023-01-13 09:12:17.903	warn	Error: undefined
            modbus.0
            2023-01-13 09:12:12.931	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:12:12.901	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:12:12.900	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:12:12.897	info	Connected to slave
            modbus.0
            2023-01-13 09:12:12.891	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:11:12.895	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:11:12.894	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:11:12.890	info	Disconnected from slave
            modbus.0
            2023-01-13 09:11:11.890	warn	Poll error count: 10 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:11:11.889	error	Request timed out.
            modbus.0
            2023-01-13 09:11:11.888	warn	Error: undefined
            modbus.0
            2023-01-13 09:11:06.919	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:11:06.885	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:11:06.885	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:11:06.883	info	Connected to slave
            modbus.0
            2023-01-13 09:11:06.876	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:10:06.877	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:10:06.876	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:10:06.873	info	Disconnected from slave
            modbus.0
            2023-01-13 09:10:05.872	warn	Poll error count: 9 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:10:05.871	error	Request timed out.
            modbus.0
            2023-01-13 09:10:05.870	warn	Error: undefined
            modbus.0
            2023-01-13 09:10:00.898	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:10:00.868	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:10:00.867	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:10:00.865	info	Connected to slave
            modbus.0
            2023-01-13 09:10:00.860	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:09:00.863	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:09:00.862	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:09:00.858	info	Disconnected from slave
            modbus.0
            2023-01-13 09:08:59.856	warn	Poll error count: 8 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:08:59.856	error	Request timed out.
            modbus.0
            2023-01-13 09:08:59.855	warn	Error: undefined
            modbus.0
            2023-01-13 09:08:54.885	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:08:54.853	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:08:54.852	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:08:54.851	info	Connected to slave
            modbus.0
            2023-01-13 09:08:54.846	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:07:54.859	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:07:54.858	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:07:54.844	info	Disconnected from slave
            modbus.0
            2023-01-13 09:07:53.843	warn	Poll error count: 7 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:07:53.842	error	Request timed out.
            modbus.0
            2023-01-13 09:07:53.841	warn	Error: undefined
            modbus.0
            2023-01-13 09:07:48.871	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:07:48.839	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:07:48.839	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:07:48.838	info	Connected to slave
            modbus.0
            2023-01-13 09:07:48.831	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:06:48.835	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:06:48.834	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:06:48.830	info	Disconnected from slave
            modbus.0
            2023-01-13 09:06:47.830	warn	Poll error count: 6 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:06:47.829	error	Request timed out.
            modbus.0
            2023-01-13 09:06:47.828	warn	Error: undefined
            modbus.0
            2023-01-13 09:06:42.855	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:06:42.826	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:06:42.826	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:06:42.825	info	Connected to slave
            modbus.0
            2023-01-13 09:06:42.820	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:05:42.824	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:05:42.822	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:05:42.819	info	Disconnected from slave
            modbus.0
            2023-01-13 09:05:41.819	warn	Poll error count: 5 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:05:41.819	error	Request timed out.
            modbus.0
            2023-01-13 09:05:41.817	warn	Error: undefined
            modbus.0
            2023-01-13 09:05:36.922	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:05:36.815	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:05:36.815	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:05:36.814	info	Connected to slave
            modbus.0
            2023-01-13 09:05:36.807	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:04:36.809	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:04:36.808	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:04:36.806	info	Disconnected from slave
            modbus.0
            2023-01-13 09:04:35.806	warn	Poll error count: 4 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:04:35.805	error	Request timed out.
            modbus.0
            2023-01-13 09:04:35.804	warn	Error: undefined
            modbus.0
            2023-01-13 09:04:30.909	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:04:30.802	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:04:30.801	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:04:30.800	info	Connected to slave
            modbus.0
            2023-01-13 09:04:30.790	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:03:30.793	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:03:30.792	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:03:30.789	info	Disconnected from slave
            modbus.0
            2023-01-13 09:03:29.789	warn	Poll error count: 3 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:03:29.788	error	Request timed out.
            modbus.0
            2023-01-13 09:03:29.787	warn	Error: undefined
            modbus.0
            2023-01-13 09:03:24.891	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:03:24.785	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:03:24.784	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:03:24.784	info	Connected to slave
            modbus.0
            2023-01-13 09:03:24.778	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:02:24.781	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:02:24.780	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:02:24.777	info	Disconnected from slave
            modbus.0
            2023-01-13 09:02:23.777	warn	Poll error count: 2 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:02:23.776	error	Request timed out.
            modbus.0
            2023-01-13 09:02:23.775	warn	Error: undefined
            modbus.0
            2023-01-13 09:02:18.874	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:02:18.772	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:02:18.771	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:02:18.770	info	Connected to slave
            modbus.0
            2023-01-13 09:02:18.761	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:01:18.764	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:01:18.763	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:01:18.759	info	Disconnected from slave
            modbus.0
            2023-01-13 09:01:17.759	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:01:17.758	error	Request timed out.
            modbus.0
            2023-01-13 09:01:17.757	warn	Error: undefined
            modbus.0
            2023-01-13 09:01:12.856	error	Wrong CRC for frame: 255,2,3,2,0,26,125,143
            modbus.0
            2023-01-13 09:01:12.756	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:01:12.752	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:01:11.699	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 09:01:11.667	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:01:11.666	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:01:11.664	info	Connected to slave
            modbus.0
            2023-01-13 09:01:11.655	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 09:00:11.657	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 09:00:11.656	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 09:00:11.653	info	Disconnected from slave
            modbus.0
            2023-01-13 09:00:10.653	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 09:00:10.652	error	Request timed out.
            modbus.0
            2023-01-13 09:00:10.651	warn	Error: undefined
            modbus.0
            2023-01-13 09:00:05.681	error	Error response: 20
            modbus.0
            2023-01-13 09:00:05.649	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:00:05.648	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:00:04.596	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 09:00:04.567	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:00:04.566	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:00:03.513	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 09:00:03.481	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:00:03.480	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:00:02.427	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 09:00:02.266	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 09:00:02.265	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 09:00:02.264	info	Connected to slave
            modbus.0
            2023-01-13 09:00:02.257	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:59:02.260	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:59:02.259	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:59:02.254	info	Disconnected from slave
            modbus.0
            2023-01-13 08:59:01.254	warn	Poll error count: 3 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:59:01.253	error	Request timed out.
            modbus.0
            2023-01-13 08:59:01.252	warn	Error: undefined
            modbus.0
            2023-01-13 08:58:56.280	error	unknown function code: 0x20, 0x20
            modbus.0
            2023-01-13 08:58:56.251	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:58:56.250	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:58:56.250	info	Connected to slave
            modbus.0
            2023-01-13 08:58:56.243	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:57:56.245	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:57:56.244	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:57:56.241	info	Disconnected from slave
            modbus.0
            2023-01-13 08:57:55.242	warn	Poll error count: 2 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:57:55.241	error	Request timed out.
            modbus.0
            2023-01-13 08:57:55.240	warn	Error: undefined
            modbus.0
            2023-01-13 08:57:50.269	error	Error response: Data address of some or all the required entities are not allowed or do not exist in slave
            modbus.0
            2023-01-13 08:57:50.268	error	Error response for FCx64: Illegal Data Address
            modbus.0
            2023-01-13 08:57:50.238	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:57:50.237	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:57:50.236	info	Connected to slave
            modbus.0
            2023-01-13 08:57:50.229	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:56:50.232	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:56:50.231	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:56:50.228	info	Disconnected from slave
            modbus.0
            2023-01-13 08:56:49.227	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:56:49.226	error	Request timed out.
            modbus.0
            2023-01-13 08:56:49.225	warn	Error: undefined
            modbus.0
            2023-01-13 08:56:44.255	error	unknown function code: 0x20, 0x20
            modbus.0
            2023-01-13 08:56:44.223	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:56:44.222	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:56:43.169	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 08:56:43.137	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:56:43.136	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:56:42.084	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 08:56:41.987	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:56:41.986	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:56:41.984	info	Connected to slave
            modbus.0
            2023-01-13 08:56:41.977	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:55:41.981	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:55:41.980	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:55:41.976	info	Disconnected from slave
            modbus.0
            2023-01-13 08:55:40.977	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:55:40.975	error	Request timed out.
            modbus.0
            2023-01-13 08:55:40.974	warn	Error: undefined
            modbus.0
            2023-01-13 08:55:36.063	error	Error response: 20
            modbus.0
            2023-01-13 08:55:35.973	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:55:35.971	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:55:34.919	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 08:55:34.887	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:55:34.885	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:55:33.832	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 08:55:33.800	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:55:33.796	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:55:32.743	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 08:55:32.709	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:55:32.708	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:55:32.707	info	Connected to slave
            modbus.0
            2023-01-13 08:55:32.700	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:54:32.703	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:54:32.701	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:54:32.698	info	Disconnected from slave
            modbus.0
            2023-01-13 08:54:31.697	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:54:31.696	error	Request timed out.
            modbus.0
            2023-01-13 08:54:31.695	warn	Error: undefined
            modbus.0
            2023-01-13 08:54:26.724	error	unknown function code: 0x20, 0x20
            modbus.0
            2023-01-13 08:54:26.693	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:54:26.691	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:54:25.638	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
            modbus.0
            2023-01-13 08:54:25.605	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:54:25.604	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:54:25.603	info	Connected to slave
            modbus.0
            2023-01-13 08:54:25.596	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:53:25.598	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:53:25.597	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:53:25.594	info	Disconnected from slave
            modbus.0
            2023-01-13 08:53:24.593	warn	Poll error count: 6 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:53:24.592	error	Request timed out.
            modbus.0
            2023-01-13 08:53:24.591	warn	Error: undefined
            modbus.0
            2023-01-13 08:53:19.618	error	unknown function code: 0x20, 0x19
            modbus.0
            2023-01-13 08:53:19.588	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:53:19.587	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:53:19.585	info	Connected to slave
            modbus.0
            2023-01-13 08:53:19.577	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:52:19.579	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:52:19.578	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:52:19.575	info	Disconnected from slave
            modbus.0
            2023-01-13 08:52:18.574	warn	Poll error count: 5 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:52:18.573	error	Request timed out.
            modbus.0
            2023-01-13 08:52:18.572	warn	Error: undefined
            modbus.0
            2023-01-13 08:52:13.602	error	Wrong CRC for frame: 3,2,0,25,61
            modbus.0
            2023-01-13 08:52:13.569	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:52:13.568	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:52:13.567	info	Connected to slave
            modbus.0
            2023-01-13 08:52:13.561	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:51:13.564	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:51:13.563	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:51:13.559	info	Disconnected from slave
            modbus.0
            2023-01-13 08:51:12.559	warn	Poll error count: 4 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:51:12.558	error	Request timed out.
            modbus.0
            2023-01-13 08:51:12.557	warn	Error: undefined
            modbus.0
            2023-01-13 08:51:07.588	error	Wrong CRC for frame: 3,2,0,25,61
            modbus.0
            2023-01-13 08:51:07.555	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:51:07.554	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:51:07.552	info	Connected to slave
            modbus.0
            2023-01-13 08:51:07.545	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:50:07.547	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:50:07.546	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:50:07.542	info	Disconnected from slave
            modbus.0
            2023-01-13 08:50:06.542	warn	Poll error count: 3 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:50:06.541	error	Request timed out.
            modbus.0
            2023-01-13 08:50:06.541	warn	Error: undefined
            modbus.0
            2023-01-13 08:50:01.569	error	Wrong CRC for frame: 6,3,2,0,25,61,142
            modbus.0
            2023-01-13 08:50:01.537	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:50:01.536	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:50:01.535	info	Connected to slave
            modbus.0
            2023-01-13 08:50:01.528	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            2023-01-13 08:49:01.528	debug	Cleaning up request fifo.
            modbus.0
            2023-01-13 08:49:01.527	debug	Clearing timeout of the current request.
            modbus.0
            2023-01-13 08:49:01.524	info	Disconnected from slave
            modbus.0
            2023-01-13 08:49:00.523	warn	Poll error count: 2 code: {"err":"timeout","timeout":5000}
            modbus.0
            2023-01-13 08:49:00.522	error	Request timed out.
            modbus.0
            2023-01-13 08:49:00.521	warn	Error: undefined
            modbus.0
            2023-01-13 08:48:55.550	error	Wrong CRC for frame: 6,3,2,0,25,61,142
            modbus.0
            2023-01-13 08:48:55.517	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
            modbus.0
            2023-01-13 08:48:55.516	debug	[DevID_2] Poll start ---------------------
            modbus.0
            2023-01-13 08:48:55.515	info	Connected to slave
            modbus.0
            2023-01-13 08:48:55.507	debug	connect to serial /dev/ttyUSB0 with 9600
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            • V V8Turbo
              @wendy2702
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              modbus.0
              wendy2702W Offline
              wendy2702W Offline
              wendy2702
              #26
              @v8turbo sagte in Sofar Solar HYD10 KTL Wechselrichter an modbus Adapter:
              Das ist schlecht. Hersteller und/oder Installateur mal kontaktiert?
              Weil wenn das nicht passt kannst du lange probieren.
              Dann wäre noch wichtig ob das Excel auch wirklich zu deiner SW Version passt.
              Hast du mal den Rat von @Glasfaser befolgt?
              @glasfaser sagte in Sofar Solar HYD10 KTL Wechselrichter an modbus Adapter:
              Mache es so , mit einem Windows Programm QModMaster , zuerst alles raussuchen :
              https://forum.iobroker.net/post/829310
                V Offline
                V Offline
                V8Turbo
                #27
                @wendy2702 nein habe ich noch nicht gemacht aber kann das nochmal mit QModMaster probieren. Die Excel passt, die ist für die aktuelle FW die ich gestern Installiert habe. Jetzt sogar mit Deutsch als Sprache :)
                Hersteller und/oder Installateur mal kontaktiert? <- Habe ich vorhin gerade, aber die Werte sind ja fast immer gleich also die sollten wohl passen. Ich denke immernoch es liegt an dem "Pausen" Problem wie in dem Thread den ich weiter oben verlinkt habe geschrieben wurde.
                https://forum.iobroker.net/topic/22126/adapter-modbus-mehrere-geräte-ids-timeout-beim-auslesen-von-mehr-als-einen-teilnehmern/17
                wendy2702W M 2 Antworten Letzte Antwort
                • V V8Turbo
                  wendy2702W Offline
                  wendy2702W Offline
                  wendy2702
                  #28
                  @v8turbo Das kann viele Ursachen haben. Möglich ist auch ein "schlechter USB-RS485" Adapter.
                  Da hatte ich zu Beginn auch immer Probleme mit.
                  Seit 2 Tagen nutze ich ein Waveshare RS485<->LAN Adapter zur Abfrage eines Modbus Gerätes und das klappt bisher ohne aussetzer.
                    V Offline
                    V Offline
                    V8Turbo
                    #29
                    @wendy2702 ```
                    [RTU]>Tx > 11:37:06:762 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:06:798 - 02 03 08 01 5A 00 91 0F 57 01 54 EE 2C
                    [RTU]>Tx > 11:37:09:763 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:09:799 - 02 03 08 01 2A 00 82 0F F6 01 49 8B C3
                    [RTU]>Tx > 11:37:12:763 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:12:799 - FF 02 03 08 01 5E 00 91
                    Sys > 11:37:13:309 - Error : Response not from requested slave
                    [RTU]>Tx > 11:37:15:764 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:15:798 - 02 03 08 01 45 00 8B 0F D0 01 4E 68 CD
                    [RTU]>Tx > 11:37:18:762 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:18:797 - FF 02 03 08 01 1C 00 7C
                    Sys > 11:37:19:302 - Error : Response not from requested slave
                    [RTU]>Tx > 11:37:21:765 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:21:877 - 02 03 08 01 52 00 90 0F 85 01 52 7A 17
                    [RTU]>Tx > 11:37:24:763 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:24:799 - FF 02 03 08 01 5F 00 90
                    Sys > 11:37:25:312 - Error : Response not from requested slave
                    [RTU]>Tx > 11:37:27:815 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:27:849 - 02 03 08 01 57 00 90 0F 60 01 54 BE E2
                    [RTU]>Tx > 11:37:30:762 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:30:796 - 02 03 08 01 27 00 80 0F FB 01 49 BF 00
                    [RTU]>Tx > 11:37:33:765 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:33:839 - 02 03 08 01 34 00 86 0F EA 01 4A 05 C5
                    [RTU]>Tx > 11:37:36:763 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:36:798 - FF 02 03 08 01 5F 00 91
                    Sys > 11:37:37:309 - Error : Response not from requested slave
                    [RTU]>Tx > 11:37:39:764 - 02 03 05 85 00 04 55 1F
                    [RTU]>Rx > 11:37:39:799 - 02 03 08 01 41 00 8A 0F BC 01 4F 11 10
                      wendy2702W Offline
                      wendy2702
                      #30
                      Wovon ist das?
                        Wovon ist das?
                        V Offline
                        V Offline
                        V8Turbo
                        #31
                        @wendy2702 QModMaster ?!
                        • V V8Turbo
                          V Offline
                          V Offline
                          V8Turbo
                          #32
                          Mit neuem Seriellen RS485 FTDI Chip auf USB...
                          modbus.0
                          	2023-01-16 20:55:36.525	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:55:36.523	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:55:36.520	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:55:35.519	warn	Poll error count: 9 code: {"err":"timeout","timeout":5000}
                          modbus.0
                          	2023-01-16 20:55:35.518	error	Request timed out.
                          modbus.0
                          	2023-01-16 20:55:35.517	warn	Error: undefined
                          admin.0
                          	2023-01-16 20:55:30.945	info	==> Connected system.user.admin from ::ffff:192.168.178.201
                          modbus.0
                          	2023-01-16 20:55:30.516	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:55:30.514	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:55:30.481	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:55:30.481	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:55:30.480	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:55:30.473	debug	connect to serial /dev/ttyUSB0 with 9600
                          modbus.0
                          	2023-01-16 20:54:30.477	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:54:30.475	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:54:30.472	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:54:29.473	warn	Poll error count: 8 code: {"err":"timeout","timeout":5000}
                          modbus.0
                          	2023-01-16 20:54:29.472	error	Request timed out.
                          modbus.0
                          	2023-01-16 20:54:29.470	warn	Error: undefined
                          modbus.0
                          	2023-01-16 20:54:24.497	error	Wrong CRC for frame: 2,3,2,128,2,3,86
                          modbus.0
                          	2023-01-16 20:54:24.468	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:54:24.466	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:54:24.426	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:54:24.425	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:54:24.424	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:54:24.415	debug	connect to serial /dev/ttyUSB0 with 9600
                          modbus.0
                          	2023-01-16 20:53:24.419	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:53:24.418	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:53:24.413	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:53:23.411	error	Request timed out.
                          modbus.0
                          	2023-01-16 20:53:23.410	warn	Error: undefined
                          modbus.0
                          	2023-01-16 20:53:23.400	warn	Poll error count: 7 code: "App Timeout"
                          modbus.0
                          	2023-01-16 20:53:18.409	debug	[DevID_2/holdingRegs] Poll address 1476 - 1 registers
                          modbus.0
                          	2023-01-16 20:53:18.407	debug	[DevID_2/holdingRegs] Poll address 1412 DONE
                          modbus.0
                          	2023-01-16 20:53:18.364	debug	[DevID_2/holdingRegs] Poll address 1412 - 6 registers
                          modbus.0
                          	2023-01-16 20:53:18.359	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                          modbus.0
                          	2023-01-16 20:53:18.234	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:53:18.231	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:53:18.198	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:53:18.197	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:53:18.196	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:53:18.187	debug	connect to serial /dev/ttyUSB0 with 9600
                          modbus.0
                          	2023-01-16 20:52:18.203	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:52:18.202	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:52:18.185	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:52:18.133	warn	Poll error count: 6 code: "App Timeout"
                          modbus.0
                          	2023-01-16 20:52:13.248	debug	[DevID_2/holdingRegs] Poll address 1544 - 3 registers
                          modbus.0
                          	2023-01-16 20:52:13.246	debug	[DevID_2/holdingRegs] Poll address 1476 DONE
                          modbus.0
                          	2023-01-16 20:52:13.217	debug	[DevID_2/holdingRegs] Poll address 1476 - 1 registers
                          modbus.0
                          	2023-01-16 20:52:13.214	debug	[DevID_2/holdingRegs] Poll address 1412 DONE
                          modbus.0
                          	2023-01-16 20:52:13.169	debug	[DevID_2/holdingRegs] Poll address 1412 - 6 registers
                          modbus.0
                          	2023-01-16 20:52:13.166	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                          modbus.0
                          	2023-01-16 20:52:13.040	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:52:13.038	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:52:12.932	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:52:12.931	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:52:12.930	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:52:12.922	debug	connect to serial /dev/ttyUSB0 with 9600
                          modbus.0
                          	2023-01-16 20:51:12.924	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:51:12.923	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:51:12.920	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:51:12.825	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:51:12.824	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:51:11.920	error	Request timed out.
                          modbus.0
                          	2023-01-16 20:51:11.919	warn	Error: undefined
                          modbus.0
                          	2023-01-16 20:51:11.772	warn	Poll error count: 5 code: "App Timeout"
                          modbus.0
                          	2023-01-16 20:51:06.918	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                          modbus.0
                          	2023-01-16 20:51:06.917	debug	[DevID_2/holdingRegs] Poll address 1640 DONE
                          modbus.0
                          	2023-01-16 20:51:06.886	debug	[DevID_2/holdingRegs] Poll address 1640 - 2 registers
                          modbus.0
                          	2023-01-16 20:51:06.885	debug	[DevID_2/holdingRegs] Poll address 1544 DONE
                          modbus.0
                          	2023-01-16 20:51:06.839	debug	[DevID_2/holdingRegs] Poll address 1544 - 3 registers
                          modbus.0
                          	2023-01-16 20:51:06.837	debug	[DevID_2/holdingRegs] Poll address 1476 DONE
                          modbus.0
                          	2023-01-16 20:51:06.792	debug	[DevID_2/holdingRegs] Poll address 1476 - 1 registers
                          modbus.0
                          	2023-01-16 20:51:06.789	debug	[DevID_2/holdingRegs] Poll address 1412 DONE
                          modbus.0
                          	2023-01-16 20:51:06.744	debug	[DevID_2/holdingRegs] Poll address 1412 - 6 registers
                          modbus.0
                          	2023-01-16 20:51:06.741	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                          modbus.0
                          	2023-01-16 20:51:06.616	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:51:06.613	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:51:06.572	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:51:06.571	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:51:06.570	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:51:06.561	debug	connect to serial /dev/ttyUSB0 with 9600
                          modbus.0
                          	2023-01-16 20:50:06.564	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:50:06.563	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:50:06.560	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:50:05.561	warn	Poll error count: 4 code: {"err":"timeout","timeout":5000}
                          modbus.0
                          	2023-01-16 20:50:05.560	error	Request timed out.
                          modbus.0
                          	2023-01-16 20:50:05.552	warn	Error: undefined
                          modbus.0
                          	2023-01-16 20:50:00.582	error	Wrong CRC for frame: 2,3,2,0,2,3,86
                          modbus.0
                          	2023-01-16 20:50:00.552	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:50:00.550	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:50:00.434	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:50:00.434	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:50:00.434	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:50:00.428	debug	connect to serial /dev/ttyUSB0 with 9600
                          javascript.0
                          	2023-01-16 20:50:00.014	info	script.js.Sonnenstand: Script Sonnenstand; Erfolgreich gelaufen, Werte akzeptiert
                          modbus.0
                          	2023-01-16 20:49:00.430	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:49:00.429	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:49:00.426	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:48:59.433	warn	Poll error count: 3 code: {"err":"timeout","timeout":5000}
                          modbus.0
                          	2023-01-16 20:48:59.426	error	Request timed out.
                          modbus.0
                          	2023-01-16 20:48:59.425	warn	Error: undefined
                          modbus.0
                          	2023-01-16 20:48:54.423	debug	[DevID_2/holdingRegs] Poll address 1412 - 6 registers
                          modbus.0
                          	2023-01-16 20:48:54.419	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                          modbus.0
                          	2023-01-16 20:48:54.293	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:48:54.291	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:48:54.258	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:48:54.257	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:48:54.256	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:48:54.248	debug	connect to serial /dev/ttyUSB0 with 9600
                          modbus.0
                          	2023-01-16 20:47:54.251	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:47:54.249	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:47:54.246	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:47:53.245	warn	Poll error count: 2 code: {"err":"timeout","timeout":5000}
                          modbus.0
                          	2023-01-16 20:47:53.244	error	Request timed out.
                          modbus.0
                          	2023-01-16 20:47:53.243	warn	Error: undefined
                          modbus.0
                          	2023-01-16 20:47:48.239	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:47:48.237	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:47:48.208	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:47:48.208	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:47:48.206	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:47:48.196	debug	connect to serial /dev/ttyUSB0 with 9600
                          modbus.0
                          	2023-01-16 20:46:48.199	debug	Cleaning up request fifo.
                          modbus.0
                          	2023-01-16 20:46:48.198	debug	Clearing timeout of the current request.
                          modbus.0
                          	2023-01-16 20:46:48.193	info	Disconnected from slave
                          modbus.0
                          	2023-01-16 20:46:48.126	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:46:48.125	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:46:47.192	error	Request timed out.
                          modbus.0
                          	2023-01-16 20:46:47.190	warn	Error: undefined
                          modbus.0
                          	2023-01-16 20:46:47.071	warn	Poll error count: 1 code: "App Timeout"
                          modbus.0
                          	2023-01-16 20:46:42.188	debug	[DevID_2/holdingRegs] Poll address 1544 - 3 registers
                          modbus.0
                          	2023-01-16 20:46:42.186	debug	[DevID_2/holdingRegs] Poll address 1476 DONE
                          modbus.0
                          	2023-01-16 20:46:42.157	debug	[DevID_2/holdingRegs] Poll address 1476 - 1 registers
                          modbus.0
                          	2023-01-16 20:46:42.154	debug	[DevID_2/holdingRegs] Poll address 1412 DONE
                          modbus.0
                          	2023-01-16 20:46:42.111	debug	[DevID_2/holdingRegs] Poll address 1412 - 6 registers
                          modbus.0
                          	2023-01-16 20:46:42.107	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                          modbus.0
                          	2023-01-16 20:46:41.919	debug	[DevID_2/holdingRegs] Poll address 1157 - 43 registers
                          modbus.0
                          	2023-01-16 20:46:41.916	debug	[DevID_2/holdingRegs] Poll address 1056 DONE
                          modbus.0
                          	2023-01-16 20:46:41.871	debug	[DevID_2/holdingRegs] Poll address 1056 - 1 registers
                          modbus.0
                          	2023-01-16 20:46:41.870	debug	Initialization of scale factors done!
                          modbus.0
                          	2023-01-16 20:46:41.869	debug	[DevID_2] Poll start ---------------------
                          modbus.0
                          	2023-01-16 20:46:41.867	info	Connected to slave
                          modbus.0
                          	2023-01-16 20:46:41.858	debug	connect to serial /dev/ttyUSB0 with 9600
                          • V V8Turbo
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            admin.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            javascript.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            modbus.0
                            V Offline
                            V Offline
                            V8Turbo
                            #33
                            Mit nur einem Holding und abfrage alle 15sec läuft es.... ?! Woran liegt das ?
                            modbus.0
                            	2023-01-16 21:15:37.511	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                            modbus.0
                            	2023-01-16 21:15:37.465	debug	[DevID_2/holdingRegs] Poll address 1157 - 1 registers
                            modbus.0
                            	2023-01-16 21:15:37.463	debug	[DevID_2] Poll start ---------------------
                            modbus.0
                            	2023-01-16 21:15:21.961	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                            modbus.0
                            	2023-01-16 21:15:21.931	debug	[DevID_2/holdingRegs] Poll address 1157 - 1 registers
                            modbus.0
                            	2023-01-16 21:15:21.931	debug	[DevID_2] Poll start ---------------------
                            modbus.0
                            	2023-01-16 21:15:06.428	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                            modbus.0
                            	2023-01-16 21:15:06.385	debug	[DevID_2/holdingRegs] Poll address 1157 - 1 registers
                            modbus.0
                            	2023-01-16 21:15:06.382	debug	[DevID_2] Poll start ---------------------
                            modbus.0
                            	2023-01-16 21:14:50.878	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                            modbus.0
                            	2023-01-16 21:14:50.838	debug	[DevID_2/holdingRegs] Poll address 1157 - 1 registers
                            modbus.0
                            	2023-01-16 21:14:50.836	debug	[DevID_2] Poll start ---------------------
                            modbus.0
                            	2023-01-16 21:14:35.331	debug	[DevID_2/holdingRegs] Poll address 1157 DONE
                            modbus.0
                            	2023-01-16 21:14:35.236	debug	[DevID_2/holdingRegs] Poll address 1157 - 1 registers
                            modbus.0
                            	2023-01-16 21:14:35.236	debug	Initialization of scale factors done!
                            modbus.0
                            	2023-01-16 21:14:35.234	debug	[DevID_2] Poll start ---------------------
                            modbus.0
                            	2023-01-16 21:14:35.233	info	Connected to slave
                            modbus.0
                            	2023-01-16 21:14:35.218	debug	connect to serial /dev/ttyUSB0 with 9600
                            • V V8Turbo
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              modbus.0
                              wendy2702W Offline
                              wendy2702W Offline
                              wendy2702
                              #34
                              @v8turbo Gab irgendwo einen anderen Thread wo die user die Register Abfrage Länge unter allgemein auf 1 für Float und Boolean gestellt haben bei einem ähnlichen Problem.
                              Probier das doch mal.
                                V Offline
                                V Offline
                                V8Turbo
                                #35
                                @wendy2702 Hilft auch nicht. Hab jetzt diese Register...
                                _address	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                                1668	PV_Generation_Today		kWh	uint32be	2	0,01	0		state		true	false	false	false
                                1672	Load_Consumption_Today		kWh	uint32be	2	0,01	0		state		true	false	false	false
                                1676	Energy_Purchase_Today		kWh	uint32be	2	0,01	0		state		true	false	false	false
                                1680	Energy_Selling_Today		kWh	uint32be	2	0,01	0		state		true	false	false	false
                                1684	Bat_Charge_Today		kWh	uint32be	2	0,01	0		state		true	false	false	false
                                1688	Bat_Discharge_Today		kWh	uint32be	2	0,01	0		state		true	false	false	false
                                Die liegen wohl alle auf 1668 (modbus.0
                                2023-01-17 10:19:05.533 debug [DevID_2/holdingRegs] Poll address 1668 - 22 registers), zumindest liest er die alle seit gestern Abend alle 15sec ohne Fehler. Sobald ich ein anderes hinzufüge geht es nicht mehr, ich denke auch es hat was mit dem Problem zutun was auch andere hatten...
                                Aber es muss doch jemand eine Lösung dafür haben ??
                                V GlasfaserG wendy2702W 3 Antworten Letzte Antwort
                                • V V8Turbo
                                  V Offline
                                  V Offline
                                  V8Turbo
                                  #36
                                  @v8turbo
                                  admin.0
                                  2023-01-17 10:19:58.552	info	<== Disconnect system.user.admin from ::ffff:192.168.178.203 modbus
                                  admin.0
                                  modbus.0
                                  2023-01-17 10:19:52.410	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  2023-01-17 10:19:52.288	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                                  modbus.0
                                  2023-01-17 10:19:52.286	debug	[DevID_2] Poll start ---------------------
                                  modbus.0
                                  2023-01-17 10:19:36.780	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  2023-01-17 10:19:36.704	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                                  modbus.0
                                  2023-01-17 10:19:36.703	debug	[DevID_2] Poll start ---------------------
                                  modbus.0
                                  2023-01-17 10:19:21.199	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  2023-01-17 10:19:21.122	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                                  modbus.0
                                  2023-01-17 10:19:21.121	debug	[DevID_2] Poll start ---------------------
                                  modbus.0
                                  2023-01-17 10:19:05.618	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  modbus.0
                                  2023-01-17 10:19:05.532	debug	[DevID_2] Poll start ---------------------
                                  modbus.0
                                  2023-01-17 10:18:50.021	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  2023-01-17 10:18:49.944	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                                  modbus.0
                                  2023-01-17 10:18:49.942	debug	[DevID_2] Poll start ---------------------
                                  modbus.0
                                  2023-01-17 10:18:34.440	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  2023-01-17 10:18:34.282	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                                  modbus.0
                                  2023-01-17 10:18:34.281	debug	[DevID_2] Poll start ---------------------
                                  modbus.0
                                  2023-01-17 10:18:18.778	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  2023-01-17 10:18:18.701	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                                  modbus.0
                                  2023-01-17 10:18:18.700	debug	[DevID_2] Poll start ---------------------
                                  modbus.0
                                  2023-01-17 10:18:03.197	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  2023-01-17 10:18:03.119	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                                  modbus.0
                                  2023-01-17 10:18:03.118	debug	[DevID_2] Poll start ---------------------
                                  modbus.0
                                  2023-01-17 10:17:47.684	info	List of port: [{"path":"/dev/ttyAMA0"},{"path":"/dev/ttyUSB0"}]
                                  modbus.0
                                  2023-01-17 10:17:47.683	info	Check /dev/ttyUSB0 : true
                                  modbus.0
                                  2023-01-17 10:17:47.683	info	Check /dev/ttyAMA0 : true
                                  modbus.0
                                  2023-01-17 10:17:47.681	info	Verify [{"path":"/dev/ttyUSB0","manufacturer":"FTDI","serialNumber":"A10NB15S","pnpId":"usb-FTDI_FT232R_USB_UART_A10NB15S-if00-port0","vendorId":"0403","productId":"6001"},{"path":"/dev/ttyAMA0"}]
                                  modbus.0
                                  2023-01-17 10:17:47.616	debug	[DevID_2/holdingRegs] Poll address 1668 DONE
                                  modbus.0
                                  2023-01-17 10:17:47.541	debug	[DevID_2/holdingRegs] Poll address 1668 - 22 registers
                                  modbus.0
                                  2023-01-17 10:17:47.540	debug	[DevID_2] Poll start ---------------------
                                  • V V8Turbo
                                    GlasfaserG Offline
                                    GlasfaserG Offline
                                    Glasfaser
                                    #37
                                    wendy2702 meint diesen Thread ... war erst die Tage :
                                    https://forum.iobroker.net/post/928897
                                    • GlasfaserG Glasfaser
                                      V Offline
                                      V Offline
                                      V8Turbo
                                      #38
                                      @glasfaser Hmm habe ich gelesen die haben aber ein anderes Problem denke ich. Wenn ich bei mir 1 Eintrage kommen wieder poll errors. Ich versteh das auch nicht mit den Registern... ?! Eine Adresse ist nicht gleich 1 Register oder ?! Also manchmal.
                                      [DevID_2/holdingRegs] Poll address 1157 - 1 registers <- Ist wohl nur 1 Register ?!
                                      [DevID_2/holdingRegs] Poll address 1668 - 22 registers <- Sind 22 Register auf einer Adresse oder wie verstehe ich das ??
                                      Also solange ich nur eine Adresse Abrufe läuft alles ohne Probleme. Bei 2 oder mehr oder auf unterschiedlichen Bit/Byte dann geht es nicht mehr.
                                      Seite 9 stehen die ganzen Daten fürs RS485. Alles standard.
                                      Remote Control Description for SOFARSOLAR Hybird Inverter HYD.pdf
                                      • V V8Turbo
                                        GlasfaserG Offline
                                        GlasfaserG Offline
                                        Glasfaser
                                        #39
                                        @v8turbo
                                        bin ich selber leider überfragt , was bei dir ist .
                                        bzw. bei ioBroker modbus ist das meistens so , das am ende der Register Adresse +1 / -1 ist .
                                        das heißt soll 1157 sein, ist aber 1156 bzw. 1158
                                        Kannst du nicht hiermit erstmal etwas auslesen !?
                                        https://forum.iobroker.net/post/749115
                                        • V V8Turbo
                                          wendy2702W Offline
                                          wendy2702W Offline
                                          wendy2702
                                          #40
                                          Woher kommen den diese Register? Im PDF sind die nicht oder bin ich blind?
                                          Und Rolle ist ein Value, kein State.