NEWS
Test Adapter HeatingControl v2.12.x
-
Hey,
ich nutze deinen Adapter schon sehr lange und seit neuestem bekomme ich Warnmeldungen:heatingcontrol.0 2021-12-22 13:35:25.562 warn window sensor has no datatyp in Wohnzimmer (EG_Wohnzimmer_Terrassentür Is open), boolean used. Please check and save configuration heatingcontrol.0 2021-12-22 13:35:25.562 warn window sensor has no datatyp in Wohnzimmer (EG_Kaminzimmer_Fenster_Links Is open), boolean used. Please check and save configuration heatingcontrol.0 2021-12-22 13:35:25.562 warn window sensor has no datatyp in Wohnzimmer (EG_Kaminzimmer_Fenster_Rechts Is open), boolean used. Please check and save configuration heatingcontrol.0 2021-12-22 13:35:25.562 warn window sensor has no datatyp in Küche (EG_Küche_FensterRechts_Links Is open), boolean used. Please check and save configuration heatingcontrol.0 2021-12-22 13:35:25.561 warn window sensor has no datatyp in Küche (EG_Küche_FensterRechts_Rechts Is open), boolean used. Please check and save configuration heatingcontrol.0 2021-12-22 13:35:25.561 warn window sensor has no datatyp in Küche (EG_Küche_FensterLinks_Links Is open), boolean used. Please check and save configuration heatingcontrol.0 2021-12-22 13:35:25.561 warn window sensor has no datatyp in Küche (EG_Küche_FensterLinks_Rechts Is open), boolean used. Please check and save configuration
Ich habe die Konfiguration etc. mit anderen funktionierenden Fenstersensoren verglichen und finde keinen Unterschied in der Konfiguration und auch nicht in den Datenpunkten.
Hier ein Datenpunkt der als Warnung angezeigt wird:
Hier die Konfiguarion:
Hast du eventuell eine Idee?
-
@dominik-f sagte in Test Adapter HeatingControl v2.8.x:
Hast du eventuell eine Idee?
Die Meldung kommt, weil ich irgendwann für die Sensoren den support verschiedener Datentypen eingebaut habe und gleichzeitig die aktuelle Konfiguration kompatibel machen wollte. Eigentlich sollte es reichen, einmal im Admin die Konfiguration zu speichern...
Wenn das nicht hilft, müssen wir genauer schauen. Das letzte Bild mit der Konfiguration der Sensoren ist genau was wir brauchen. Dort kann man die Datentypen umschalten. Vielleicht muss man einfach den Datentyp kurz ändern, damit dort gespeichert wird... Ich hoffe, die Sensor-Namen sind eindeutig und nicht evtl. doppelt verwendet? -
Das ändern des Datenpunkten zu Number und wieder zurück zu Boolean hat geholfen, Fehlermeldungen sind weg. Musste das für jeden Sensor machen.
Ich danke dir
-
@rene_hm
OK, verstehe. Wie wird der Wert gemittelt?Neue Beobachtung:
Wenn ich die Temperatur bei geöffnetem Fenster auf 12°C setze, wird die Temperatur als Sollwert übernommen. Ich möchte lediglich manuelle Eingriffe am Thermostat in das Profil übernehmen. Gibt es eine Möglichkeit dies so zu konfigurieren? -
ich versuche gerade in der VIS Vorlage einen Regler einzubauen um am Handy auch ganz einfach die Temperatur einzustellen. Also wenn es jetzt doch mal was wärmer sein soll.
Mit welchem Wert Steuer ich dies am besten?
Über den Adapter ? Oder direkt am Thermostat SetTemperature ?
Oder arbeitet man hier mit offsets ?
Nutze das HQwidget dafür. -
Im github und NPM liegt die 2.8.1 zum Testen bereit.
siehe auch github
Es gibt folgende Änderungen:- im Raumstatus (html) wird nun die Temperatur vom externen Sensor und der aktuelle Offset angezeigt (siehe issue)
- der override wird nur verlängert, wenn eine geänderte Temperatur erkannt wird. Die gleiche Temperatur führt nicht mehr zu einer Verlängerung des overrides
- die verbleibende Override-Zeit wird auf 0 gesetzt, wenn der override abgebrochen wird
- das ack-Flag für geänderte Datenpunkte wird erst nach zwei Sekunden gesetzt. Das sollte anderen Adaptern (hmip o.ä.) genügend Zeit geben, ebenfalls auf die Änderung zu reagieren.
Feedback ist wie immer willkommen...
Übrigens: ich suche support bei der Erstellung bzw. Update der Dokumentation. Bei Interesse bitte melden...
-
@chrisxy sagte in Test Adapter HeatingControl v2.8.x:
Mit welchem Wert Steuer ich dies am besten?
aus meiner Sicht sollte man den SetTemperature verwenden. Das funktioniert dann ähnlich wie eine direkte Änderung am Thermostat. Mit der 2.8.1 sollte das dann auch wieder funktionieren, da bis 2.8.0 der Adapter das ack-Flag direkt gesetzt hat, was dann dazu geführt hat, dass z.Bsp. der hmip-Adapter die geänderten Daten nicht ans Thermostat gesendet hat, weil das ack schon gesetzt war und hmip dann nicht mehr reagiert...
-
@passuff sagte in Test Adapter HeatingControl v2.8.x:
Wenn ich die Temperatur bei geöffnetem Fenster auf 12°C setze, wird die Temperatur als Sollwert übernommen. Ich möchte lediglich manuelle Eingriffe am Thermostat in das Profil übernehmen. Gibt es eine Möglichkeit dies so zu konfigurieren?
Das verstehe ich nicht... Wo änderst du die Temperatur? und wie soll der Adapter "manuelle" Eingriffe erkennen?
-
Das verstehe ich nicht... Wo änderst du die Temperatur? und wie soll der Adapter "manuelle" Eingriffe erkennen?
Der Adapter stellt bei geöffnetem Fenster auf 12 Grad . Das wird als override erkannt. Sollte so nicht sein, denke ich.
-
@passuff nein, das sollte so nicht sein...
Kannst du von dem Vorgang ein debug log erstellen? -
@rene_hm
Würde dir das gerne per PM senden. Wie geht das? Finde nur so einen dämlichen Chat. Ich habe keine Möglichkeit gefunden dort eine Datei zu senden. -
@passuff habe dir eine PM mit der email-Adresse geschickt...
-
@passuff kannst du mal die 2.8.2 versuchen, ob das Problem behoben ist?
-
Hi,
ist es möglich die Temperatur Datenpunkte auf ein Maximum zu begrenzen?
Ich steuere heatingcontrol über iQontrol und aktuell kann man theoretisch auch 100 als Wert auswählen.Ich kann zwar in iQontrol custom values hinterlegen, aber hab mich gefragt ob es nicht prinzipiell sinnvoll wäre die Datenpunkte mit einem Max value von zB 35 zu hinterlegen.
Ciao
Martin -
@rene_hm
Hallo, hab mit heute die 2.8.2 gezogen. Momentan wird bei mir alles auf override gestellt. Ich war jetzt mal ein paar Stunden weg und da hat er auch nicht überall auf Absenkung umgeschalten.
Hier noch ein kleiner Auszug vom Log.![622b38f3-aa2f-4ebe-864a-8cbf2ad6f4c6-image.png](/assets/uploads/files/1641474733108-622b38f3-aa2f-4ebe-864a-8cbf2ad6f4c6-image.png) code_text ```2022-01-06 09:40:55.849 - debug: heatingcontrol.0 (6609) ### handle state change acked alias.0.Heizung.Büro.SET {"val":20,"ack":true,"ts":1641458454117,"q":0,"from":"system.adapter.hm-rpc.1","user":"system.user.admin","lc":1641456363315} 2022-01-06 09:40:55.850 - debug: heatingcontrol.0 (6609) HandleStateChangeDevices alias.0.Heizung.Büro.SET 2022-01-06 09:40:55.850 - debug: heatingcontrol.0 (6609) CheckStateChangeDevice alias.0.Heizung.Büro.SET 2022-01-06 09:40:55.850 - debug: heatingcontrol.0 (6609) Büro ### ChangeStatus Thermostats_Target to {"val":20,"ack":true,"ts":1641458454117,"q":0,"from":"system.adapter.hm-rpc.1","user":"system.user.admin","lc":1641456363315} in auto 2022-01-06 09:40:55.851 - debug: heatingcontrol.0 (6609) Change Status target temperature in Büro to 20 (profile 20) in auto 2022-01-06 09:40:55.851 - debug: heatingcontrol.0 (6609) CheckManualMode Büro target 20 current manual target -99 state auto 2022-01-06 09:40:55.851 - debug: heatingcontrol.0 (6609) CheckStartManualMode Büro 2022-01-06 09:40:55.851 - debug: heatingcontrol.0 (6609) CheckStartManualMode: current target 19.75 new 20 2022-01-06 09:40:55.851 - debug: heatingcontrol.0 (6609) CheckTargetFromThermostat Büro 2022-01-06 09:40:55.852 - debug: heatingcontrol.0 (6609) Büro got target from thermostat as override: 20 2022-01-06 09:40:55.901 - debug: heatingcontrol.0 (6609) ### handle state change acked alias.0.Heizung.Büro.ACTUAL {"val":19.5,"ack":true,"ts":1641458454118,"q":0,"from":"system.adapter.hm-rpc.1","user":"system.user.admin","lc":1641458454118} 2022-01-06 09:40:55.905 - debug: heatingcontrol.0 (6609) HandleStateChangeDevices alias.0.Heizung.Büro.ACTUAL 2022-01-06 09:40:55.905 - debug: heatingcontrol.0 (6609) CheckStateChangeDevice alias.0.Heizung.Büro.ACTUAL 2022-01-06 09:40:55.905 - debug: heatingcontrol.0 (6609) ChangeStatus called, while already changing, push to list Büro Thermostats_Current {"val":19.5,"ack":true,"ts":1641458454118,"q":0,"from":"system.adapter.hm-rpc.1","user":"system.user.admin","lc":1641458454118} (1) 2022-01-06 09:40:56.010 - debug: heatingcontrol.0 (6609) ### handle state change !ack heatingcontrol.0.Rooms.Büro.TemperaturOverride {"val":20,"ack":false,"ts":1641458455963,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1640875745300} 2022-01-06 09:40:56.010 - debug: heatingcontrol.0 (6609) ChangeStatus called, while already changing, push to list Büro TemperaturOverride 20 (2) 2022-01-06 09:40:56.015 - debug: heatingcontrol.0 (6609) UpdateDPs for Büro auto 2022-01-06 09:40:56.091 - debug: heatingcontrol.0 (6609) AddStatusToLog skip Büro auto public holiday 19.75°C 2022-01-06 09:40:56.113 - debug: heatingcontrol.0 (6609) ChangeStatus recall cmd from list Büro Thermostats_Current {"val":19.5,"ack":true,"ts":1641458454118,"q":0,"from":"system.adapter.hm-rpc.1","user":"system.user.admin","lc":1641458454118} (1) 2022-01-06 09:40:56.115 - debug: heatingcontrol.0 (6609) Büro ### ChangeStatus Thermostats_Current to {"val":19.5,"ack":true,"ts":1641458454118,"q":0,"from":"system.adapter.hm-rpc.1","user":"system.user.admin","lc":1641458454118} in auto 2022-01-06 09:40:56.115 - debug: heatingcontrol.0 (6609) Change Status current temperature in Büro to 19.5 2022-01-06 09:40:56.115 - debug: heatingcontrol.0 (6609) HandleActors for Büro auto 2022-01-06 09:40:56.116 - debug: heatingcontrol.0 (6609) UpdateDPs for Büro auto 2022-01-06 09:40:56.200 - debug: heatingcontrol.0 (6609) AddStatusToLog skip Büro auto public holiday 19.75°C 2022-01-06 09:40:56.233 - debug: heatingcontrol.0 (6609) ChangeStatus recall cmd from list Büro TemperaturOverride 20 (0) 2022-01-06 09:40:56.234 - debug: heatingcontrol.0 (6609) Büro ### ChangeStatus TemperaturOverride to 20 in auto 2022-01-06 09:40:56.234 - debug: heatingcontrol.0 (6609) ChangeStatus Override 2022-01-06 09:40:56.276 - debug: heatingcontrol.0 (6609) Büro start override for 86400sec 2022-01-06 09:40:56.277 - debug: heatingcontrol.0 (6609) CalculateRoomTemperature for Büro override 2022-01-06 09:40:56.277 - debug: heatingcontrol.0 (6609) Büro override mode (incl. reduced): target 20 ( window open false 20) 2022-01-06 09:40:56.278 - debug: heatingcontrol.0 (6609) checking min temp with Rooms.Büro.MinimumTemperature 2022-01-06 09:40:56.279 - debug: heatingcontrol.0 (6609) got {"val":5,"ack":true,"ts":1635349393144,"q":0,"from":"system.adapter.heatingcontrol.0","user":"system.user.admin","lc":1635349393144} 2022-01-06 09:40:56.279 - debug: heatingcontrol.0 (6609) SetRoomTemperature started for Büro target 20 with offset -0.25 2022-01-06 09:40:56.328 - debug: heatingcontrol.0 (6609) Büro nothing to do to for alias.0.Heizung.Büro.SET , target 20 is already set 20 2022-01-06 09:40:56.329 - debug: heatingcontrol.0 (6609) HandleActors for Büro override 2022-01-06 09:40:56.329 - debug: heatingcontrol.0 (6609) UpdateDPs for Büro override
-
@martinschm ich hab die Begrenzung direkt an meinen HM Thermostaten hinterlegt, evtl. geht das bei deinen auch?!
-
@michi_pi said in Test Adapter HeatingControl v2.8.x:
@martinschm ich hab die Begrenzung direkt an meinen HM Thermostaten hinterlegt, evtl. geht das bei deinen auch?!
Übernimmt heatingcontrol die Werte dann?
Das sind doch eigene Datenpunkte des Adapters.
-
@martinschm sagte in Test Adapter HeatingControl v2.8.x:
ist es möglich die Temperatur Datenpunkte auf ein Maximum zu begrenzen?
Für die Pittini-vis habe ich so etwas gemacht. Da wird aber auch die Temperatur per pulldown-box eingestellt:
Die Datenpunkte selbst haben kein minimum oder maximum. Das wäre wahrscheinlich auch ein globales Feature und nicht adapter-spezifisch
-
@michi_pi sagte in Test Adapter HeatingControl v2.8.x:
Momentan wird bei mir alles auf override gestellt.
Kann es sein, dass dein Thermostat (oder irgendetwas zwischen Adapter und Thermostat) die Zielwerte auf ganze Zahlen rundet? oder wird die Zieltemperatur nicht immer an das Thermostat gesendet?
Das log sagt folgendes:
- beim Start des Adapters wird zunächst 20°C als Zieltemperatur an's Thermostat geschickt
- dann wird eine Zieltemperatur (inkl. offset) von 19,75°C berechnet und an's Thermostat geschickt. Das sehe ich im log für das Büro und auch im screen shot der vis (um 09:06:01)
- um 09:40:55 kommt vom Thermostat eine Zieltemperatur von 20°C zurück, obwohl vorher 19,75°C gesendet werden sollte
Der Unterschied wird nun als "Änderung vom Thermostat" interpretiert und es wird auf override geschaltet
@passuff sieht das bei dir ähnlich aus, oder ist das, was du mir beschrieben hast, noch etwas anderes?
-
@rene_hm said in Test Adapter HeatingControl v2.8.x:
@martinschm sagte in Test Adapter HeatingControl v2.8.x:
ist es möglich die Temperatur Datenpunkte auf ein Maximum zu begrenzen?
Für die Pittini-vis habe ich so etwas gemacht. Da wird aber auch die Temperatur per pulldown-box eingestellt:
Die Datenpunkte selbst haben kein minimum oder maximum. Das wäre wahrscheinlich auch ein globales Feature und nicht adapter-spezifisch
Hi,
ist der min/max value nicht etwas, das beim Anlegen des Datenpunkts gesetzt werden kann? Daher dachte ich, das es Adapter spezifisch wäre.
Ciao
Martin