  4. Modbus adapter
    6.3k
Modbus adapter
modbus adaptermodbus
981 Beiträge 141 Kommentatoren 490.9k Aufrufe 64 Beobachtet
  • arteckA arteck
    @nwh irgendwo bekommst du ein timeout..
    stell mal bitte Abfrageintervall von 6000 auf 10000 (also von 6 sekunden abfrage auf 10)
    NWHN Offline
    NWHN Offline
    NWH
    #786
    @arteck Habe ich.
    Man kann sagen alle 15 sec. kommt so ein Pool Error
    modbus.0
    2023-05-31 07:48:10.636	debug	[DevID_3] Poll start ---------------------
    modbus.0
    2023-05-31 07:48:01.938	debug	[DevID_3/inputRegs] Poll address 30953 DONE
    modbus.0
    2023-05-31 07:48:00.585	warn	Poll error count: 3 code: "App Timeout"
    modbus.0
    2023-05-31 07:48:00.436	debug	[DevID_3/inputRegs] Poll address 30953 - 2 registers
    modbus.0
    2023-05-31 07:48:00.436	debug	[DevID_3/inputRegs/30775] Calculation result = 295, type = number
    modbus.0
    2023-05-31 07:48:00.435	debug	[DevID_3/inputRegs/30775] Formula = x = (x<0) ? 0:x
    modbus.0
    2023-05-31 07:48:00.435	debug	[DevID_3/inputRegs/30775] Input Value = 295
    modbus.0
    2023-05-31 07:48:00.435	debug	[DevID_3/inputRegs] Poll address 30775 DONE
    modbus.0
    2023-05-31 07:47:59.391	debug	[DevID_3/inputRegs] Poll address 30775 - 8 registers
    modbus.0
    2023-05-31 07:47:59.390	debug	[DevID_3/inputRegs] Poll address 30513 DONE
    modbus.0
    2023-05-31 07:47:57.734	debug	[DevID_3/inputRegs] Poll address 30513 - 26 registers
    modbus.0
    2023-05-31 07:47:57.733	debug	[DevID_3/inputRegs] Poll address 30201 DONE
    modbus.0
    2023-05-31 07:47:55.385	debug	[DevID_3/inputRegs] Poll address 30201 - 4 registers
    modbus.0
    2023-05-31 07:47:55.384	debug	[DevID_3] Poll start ---------------------
    modbus.0
    2023-05-31 07:47:49.600	debug	[DevID_3/inputRegs] Poll address 30953 DONE
    modbus.0
    2023-05-31 07:47:46.441	debug	[DevID_3/inputRegs] Poll address 30953 - 2 registers
    modbus.0
    2023-05-31 07:47:46.440	debug	[DevID_3/inputRegs/30775] Calculation result = 295, type = number
    modbus.0
    2023-05-31 07:47:46.440	debug	[DevID_3/inputRegs/30775] Formula = x = (x<0) ? 0:x
    modbus.0
    2023-05-31 07:47:46.440	debug	[DevID_3/inputRegs/30775] Input Value = 295
    modbus.0
    2023-05-31 07:47:46.440	debug	[DevID_3/inputRegs] Poll address 30775 DONE
    modbus.0
    2023-05-31 07:47:45.334	warn	Poll error count: 2 code: "App Timeout"
    modbus.0
    2023-05-31 07:47:44.639	debug	[DevID_3/inputRegs] Poll address 30775 - 8 registers
    modbus.0
    2023-05-31 07:47:44.638	debug	[DevID_3/inputRegs] Poll address 30513 DONE
    modbus.0
    2023-05-31 07:47:40.243	debug	[DevID_3/inputRegs] Poll address 30513 - 26 registers
    modbus.0
    2023-05-31 07:47:40.242	debug	[DevID_3/inputRegs] Poll address 30201 DONE
    modbus.0
    2023-05-31 07:47:40.133	debug	[DevID_3/inputRegs] Poll address 30201 - 4 registers
    modbus.0
    2023-05-31 07:47:40.132	debug	[DevID_3] Poll start ---------------------
    modbus.0
    2023-05-31 07:47:32.273	debug	[DevID_3/inputRegs] Poll address 30953 DONE
    modbus.0
    2023-05-31 07:47:30.081	warn	Poll error count: 1 code: "App Timeout"
    • NWHN NWH
      @arteck Habe ich.
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      modbus.0
      arteckA Offline
      arteckA Offline
      arteck
      #787
      @nwh und der WR ist normal erreichbar ? sowohl in der app als auch in browser ?
      mach den noch rein
      NWHN 1 Antwort Letzte Antwort
      • arteckA arteck
        mach den noch rein
        NWHN Offline
        NWHN Offline
        NWH
        #788
        @arteck Wenn ich das anklicke dann kommt das.
        Ja ist erreichbar.
        modbus.0
        2023-05-31 08:20:42.564	warn	Poll error count: 1 code: "App Timeout"
        modbus.0
        2023-05-31 08:20:30.838	warn	get state error: DB closed
        modbus.0
        2023-05-31 08:20:27.782	warn	Poll error count: 5 code: "App Timeout"
        modbus.0
        2023-05-31 08:20:12.532	warn	Poll error count: 4 code: "App Timeout"
        modbus.0
        2023-05-31 08:19:57.280	warn	Poll error count: 3 code: "App Timeout"
        modbus.0
        2023-05-31 08:19:42.027	warn	Poll error count: 2 code: "App Timeout"
        arteckA J 2 Antworten Letzte Antwort
        • NWHN NWH
          Ja ist erreichbar.
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          modbus.0
          arteckA Offline
          arteckA Offline
          arteck
          #789
          @nwh langsam gehen mir die Ideen aus
          • NWHN NWH
            Ja ist erreichbar.
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            modbus.0
            JoergH
            #790
            @nwh @arteck
            Hat der WR wirklich die ID 3??
            Wenn mehrere Geräte ID an ist, dann sollte er nur auf seine ID reagieren und ohne das auf jede Anfrage, oder nicht?
            Da würde ich mal versuchen was er bei anderen IDs auswirkt.
            Dann kannst Du auch mal "nur multiple write" anklicken....
            Ich habe mit einem WR von Sunsynk ein ähnliches Problem. Der wirft mir in unregelmäßigen Abständen auch mal ein timeoit raus, läuft aber prinzipiell. Bisher konnte ich das nicht lösen, aber außer "Schönheit der Arbeit" bisher auch nicht schlimm.
            • arteckA Offline
              arteckA Offline
              arteck
              #791
              @joergh sagte in Modbus adapter:
              3 ist die SMA voreingestellte...
              • arteckA arteck
                JoergH
                #792
                @arteck Nur warum reagiert er dann nicht auf diese wenn man "mehrere IDs" auswählt?
                Überträgt der Adapter sie denn korrekt statt nur Broadcast (0) zu senden?
                • J JoergH
                  NWHN Offline
                  NWHN Offline
                  NWH
                  schrieb am zuletzt editiert von NWH
                  #793
                  @joergh @arteck @Glasfaser
                  Ich habe jetzt "nur multiple write" angeklickt, leider keine Änderung.
                  Funktionieren tut es ja aber ca. alle 10 bis 15 min. kommt der Fehler
                  modbus.0
                  2023-05-31 10:39:06.841	warn	On error: {"code":"ERR_STREAM_WRITE_AFTER_END"}
                  modbus.0
                  2023-05-31 10:39:06.841	error	Client in error state.
                  modbus.0
                  2023-05-31 10:39:06.840	error	Socket Error
                  Solange es funktioniert geht es ja, aber gut sind die Fehler und Warnungen auf Dauer sicher nicht.
                  Hat das eigentlich auf die Ressourcen (CPU, Speicher usw.) eine Auswirkungen?
                  • NWHN NWH
                    modbus.0
                    modbus.0
                    modbus.0
                    arteckA Offline
                    arteckA Offline
                    arteck
                    #794
                    @nwh sagte in Modbus adapter:
                    wie kommst du da drauf.. dass es auf dauer nicht gut ist.. was erwartest du was passiert ????
                    • arteckA arteck
                      NWHN Offline
                      NWHN Offline
                      NWH
                      #795
                      @arteck Fehler sind auf Dauer nie gut, würde ich mal behaupten.
                      Ich erwarte gar nix, war nur eine Frage!
                      • NWHN NWH
                        arteckA Offline
                        arteckA Offline
                        arteck
                        #796
                        dann muss ich dein Weltbild zerstören.. Software ist nie fehlerfrei.. also auch wenn du nix siehst ..
                        lass laufen..
                        komisch ist ea aber schon
                        • NWHN NWH
                          modbus.0
                          modbus.0
                          modbus.0
                          JoergH
                          #797
                          @nwh
                          Die Fehlermeldung ist jetzt eine andere...
                          Tja, da hakelt er vielleicht alle 15 min. aus anderen Gründen. Wenn es so regelmäßig kommt, könnte es auch mit ganz anderen Dingen zu tun haben die alle 15 Minuten auf dem pi laufen und den Adapter im Timing stören...ist aber alles Spekulation. Spielt aber auch keine Rolle, wenn es nur so selten auftritt dass mal ein Datensatz nicht korrekt gelesen wird.
                          • arteckA arteck
                            lass laufen..
                            Sneak-L8
                            #798
                            @arteck Hallo zusammen,
                            seit zwei Tagen erhalte ich die bisher nur an manchen Tagen und dan nur alle ca. 6 Stunden auftretende Meldung dauerhaft:
                            modbus.1
                            	2023-06-19 11:25:11.429	info	(COMPACT) setState not processed because States database not connected
                            modbus.1
                            	2023-06-19 11:25:11.428	info	(COMPACT) Connected to slave 192.168.97.46
                            modbus.1
                            	2023-06-19 11:24:11.419	info	(COMPACT) setState not processed because States database not connected
                            modbus.1
                            	2023-06-19 11:24:11.418	info	(COMPACT) Disconnected from slave 192.168.97.46
                            modbus.1
                            	2023-06-19 11:24:10.421	error	(COMPACT) Reconnect did not help, restart adapter
                            modbus.1
                            	2023-06-19 11:24:10.420	info	(COMPACT) setState not processed because States database not connected
                            modbus.1
                            	2023-06-19 11:24:10.420	warn	(COMPACT) Poll error count: 1132 code: {"err":"timeout","timeout":5000}
                            modbus.1
                            	2023-06-19 11:24:10.419	error	(COMPACT) Client in error state.
                            modbus.1
                            	2023-06-19 11:24:10.418	error	(COMPACT) Request timed out.
                            modbus.1
                            	2023-06-19 11:24:10.417	warn	(COMPACT) Error: undefined
                            modbus.1
                            	2023-06-19 11:24:05.415	info	(COMPACT) setState not processed because States database not connected
                            modbus.1
                            	2023-06-19 11:24:05.414	info	(COMPACT) Connected to slave 192.168.97.46
                            modbus.1
                            	2023-06-19 11:23:05.408	info	(COMPACT) setState not processed because States database not connected
                            modbus.1
                            	2023-06-19 11:23:05.407	info	(COMPACT) Disconnected from slave 192.168.97.46
                            modbus.1
                            	2023-06-19 11:23:04.410	error	(COMPACT) Reconnect did not help, restart adapter
                            modbus.1
                            	2023-06-19 11:23:04.409	info	(COMPACT) setState not processed because States database not connected
                            modbus.1
                            	2023-06-19 11:23:04.409	warn	(COMPACT) Poll error count: 1131 code: {"err":"timeout","timeout":5000}
                            modbus.1
                            	2023-06-19 11:23:04.408	error	(COMPACT) Client in error state.
                            modbus.1
                            	2023-06-19 11:23:04.407	error	(COMPACT) Request timed out.
                            modbus.1
                            	2023-06-19 11:23:04.406	warn	(COMPACT) Error: undefined
                            Ich habe in der letzten Zeit weder den Raspi, NodeJs, noch Adapter upgedatet. Auch der WR (SMA TriPower TL1000-3) ist unverändert.
                            Plattform
                                linux
                            Betriebssystem
                                linux
                            Architektur
                                arm
                            CPUs
                            Geschwindigkeit
                                1400 MHz
                            Modell
                                ARMv7 Processor rev 4 (v7l)
                            RAM
                                923.14 MB
                            System-Betriebszeit
                                21:37:39
                            Node.js
                                v16.16.0 (Es gibt eine neuere Version: v16.20.0 - Empfohlene Version v18.16.0)
                            time
                                1687169029347
                            timeOffset
                                -120
                            Anzahl der Adapter
                                473
                            NPM
                                8.11.0
                            Datenträgergröße
                                28.98 GB
                            freier Festplattenspeicher
                                24.5 GB
                            Betriebszeit
                                21:54:23
                            Aktive Instanzen
                                24
                            Weg
                                /opt/iobroker/
                            Hostname
                                raspberrypi
                            Neustart des Raspi hat leider auchnichts gebracht.
                            Wie bei den anderen liefert der WR trotzdem brav alle Daten.
                            Ich kann die Meldungen in meiner Log-Überwachung auch auf ignore setzen, daber komishc ist das schon ...
                            Gibt es sonst noch Tipps?
                            • S Sneak-L8
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              modbus.1
                              Plattform
                                  linux
                              Betriebssystem
                                  linux
                              Architektur
                                  arm
                              CPUs
                              Geschwindigkeit
                                  1400 MHz
                              Modell
                              RAM
                                  923.14 MB
                              System-Betriebszeit
                                  21:37:39
                              Node.js
                              time
                                  1687169029347
                              timeOffset
                                  -120
                              Anzahl der Adapter
                                  473
                              NPM
                                  8.11.0
                              Datenträgergröße
                                  28.98 GB
                                  24.5 GB
                              Betriebszeit
                                  21:54:23
                              Aktive Instanzen
                                  24
                              Weg
                                  /opt/iobroker/
                              Hostname
                                  raspberrypi
                              arteckA Offline
                              arteckA Offline
                              arteck
                              #799
                              @sneak-l8 sagte in Modbus adapter:
                              gesehen
                              • arteckA arteck
                                gesehen
                                Sneak-L8
                                #800
                                @arteck Ja, muss ich noch machen. Das sollte aber nicht für die Meldungen verantwortlich sein, wenn sich am System nichts geändert hat.
                                Hattte testweise mal ein register, da ich e nicht brauche rausgenommen. Danach war kurz Ruhe. aber jetzt kommen die Meldungen wieder zuverlässig alle paar Minuten. Heute haben die Meldungen um 11:06 Uhr plötzich aufgehört. Mal sehen wie lange ...
                                HomoranH S 2 Antworten Letzte Antwort
                                • S Sneak-L8
                                  #801
                                  Dann ist ggf. zuviel los auf deinem Bus, oder das hier gesagte könnte zutreffen.
                                  • S Sneak-L8
                                    Sneak-L8
                                    #802
                                    @arteck Gerade habe ich noch im Log folgende Zeile gefunden:
                                    11:06:40.511	modbus.1	(COMPACT) Poll error count: 2425 code: "ReadInputRegisters: Invalid FC 0"
                                    Ist die Kommunikationsaienheit des WR vielleicht bei "end-of-lifetime"?
                                      Sneak-L8
                                      #803
                                      @homoran Physisch hab ich m.W. gar kein modbus. Ich frage ja alles direkt übers Netzwerk ab. Modbus-Verkabelung sagt mir nichts. Oder liegt die (ohne dass iches bemerkt habe) irgendwo zwischen WR und EnergyMeter? Wüsste nicht, welche Gerät sonst physisch per Modbus miteinander verbunden sein sollten.
                                      • S Sneak-L8
                                        #804
                                        @sneak-l8 also alles modbus tcp?
                                        und was für Konverter?
                                          Sneak-L8
                                          #805
                                          @homoran ja, alles modbus tcp
                                          Konverter? Vermutlich built-in im SMA TriPower TL-10000?