  5. E3DC Hauskraftwerk steuern

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.2k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.9k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.2k

E3DC Hauskraftwerk steuern

Geplant Angeheftet Gesperrt Verschoben JavaScript
3.4k Beiträge 70 Kommentatoren 1.6m Aufrufe 61 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • bluebeanB bluebean

    @arnod
    Ähm, nun doch nochmal - sollte damit die Funktion nicht deaktiviert sein?

    Version: 1.1.2
    User Parameter 10_NotstromEntladen wird nicht mehr benötig und kann gelöscht werden. Wenn 10_minWertPrognose_kWh = 0, ist die Funktion: "Notstrom freigeben, wenn Prognose erreicht wird" deaktiviert.

    A Offline
    A Offline
    ArnoD
    schrieb am zuletzt editiert von
    #2085

    @bluebean
    Da hat sich im Script nichts geändert, da das in einer anderen Funktion verarbeitet wird.
    Kannst du das mal Logen und mir schicken, es wäre interessant, ob die Variable "NotstromVerwenden" in dem Zeitraum auf true steht.

    Wenn die PV-Leistung 100W erreicht, wird beim E3DC die Lade und Entladeleistung wieder eingeschaltet und ab dann ein Entladen vom Script solange verhindert bis Regelbeginn erreicht wird und ausreichend PV-Leistung vorhanden ist um die Batterie zu laden.
    Wenn aber danach z. B. keine Verbindung mehr zum E3DC vorhanden ist, kann das Script ein Entladen nicht verhindern.
    Unload kann hier auch eine Rolle spielen.
    Sind jetzt nur zwei mögliche Ursache von vielen, um das genauer zu analysieren, benötige ich hier das LOG File.

    Weißt du eventuell, welche Einstellungen um 6:44 aktiv waren?

    bluebeanB 1 Antwort Letzte Antwort
    0
    • A ArnoD

      @bluebean
      Da hat sich im Script nichts geändert, da das in einer anderen Funktion verarbeitet wird.
      Kannst du das mal Logen und mir schicken, es wäre interessant, ob die Variable "NotstromVerwenden" in dem Zeitraum auf true steht.

      Wenn die PV-Leistung 100W erreicht, wird beim E3DC die Lade und Entladeleistung wieder eingeschaltet und ab dann ein Entladen vom Script solange verhindert bis Regelbeginn erreicht wird und ausreichend PV-Leistung vorhanden ist um die Batterie zu laden.
      Wenn aber danach z. B. keine Verbindung mehr zum E3DC vorhanden ist, kann das Script ein Entladen nicht verhindern.
      Unload kann hier auch eine Rolle spielen.
      Sind jetzt nur zwei mögliche Ursache von vielen, um das genauer zu analysieren, benötige ich hier das LOG File.

      Weißt du eventuell, welche Einstellungen um 6:44 aktiv waren?

      bluebeanB Online
      bluebeanB Online
      bluebean
      schrieb am zuletzt editiert von bluebean
      #2086

      @arnod
      Warum wird beim Start des Scripts denn HeuteNotstromVerwenden=true und nicht false gesetzt?
      HeuteNotstromVerwenden taucht ansonsten ja nur noch in der Prüfung um 2 Uhr auf, wo es um das Nachladen auf Notstrom-SOC geht, und dafür wird ja explizit auf false geprüft (&& !HeuteNotstromVerwenden).

      1 Antwort Letzte Antwort
      0
      • bluebeanB bluebean

        @arnod said in E3DC Hauskraftwerk steuern:

        Muss ich mir ansehen, ob ich das bei den Änderungen übersehen habe.

        Sieht so aus, dass HeuteNotstromVerwenden = false ja erst um 12 Uhr gesetzt wird. Wenn das Script nach 12 Uhr gestartet wurde, setzt Du gleich am Anfang in Zeile 116 ja HeuteNotstromVerwenden=true
        Sollte da nicht zunächst false stehen? Der Wechsel auf HeuteNotstromVerwenden=true in den Prüfungen zur Freigabe läuft korrekt nur bei minWertPrognose_kWh >0 .

        A Offline
        A Offline
        ArnoD
        schrieb am zuletzt editiert von
        #2087

        Warum wird beim Start des Scripts denn HeuteNotstromVerwenden=true und nicht false gesetzt?

        Das ist so richtig.
        Die Variable verwende ich, um das Nachladen aus dem Netz zu verhindern, wenn die Notstromreserve verwendet werden darf.
        Sonst könnte es sein, dass um 1:00 Uhr z. B. die Notstromreserve freigegeben wird und um 2:00Uhr diese wieder aus dem Netz aufgefüllt wird.
        Um bei einem ungünstigen Neustart vom Script nicht erst aus dem Netz nachzuladen, setze ich die Variable erstmal auf true.

        Die ganze Regelung ist sehr komplex geworden, deswegen muss ich mir mal die Zeit nehmen und das etwas aufräumen.

        bluebeanB 1 Antwort Letzte Antwort
        0
        • A ArnoD

          Warum wird beim Start des Scripts denn HeuteNotstromVerwenden=true und nicht false gesetzt?

          Das ist so richtig.
          Die Variable verwende ich, um das Nachladen aus dem Netz zu verhindern, wenn die Notstromreserve verwendet werden darf.
          Sonst könnte es sein, dass um 1:00 Uhr z. B. die Notstromreserve freigegeben wird und um 2:00Uhr diese wieder aus dem Netz aufgefüllt wird.
          Um bei einem ungünstigen Neustart vom Script nicht erst aus dem Netz nachzuladen, setze ich die Variable erstmal auf true.

          Die ganze Regelung ist sehr komplex geworden, deswegen muss ich mir mal die Zeit nehmen und das etwas aufräumen.

          bluebeanB Online
          bluebeanB Online
          bluebean
          schrieb am zuletzt editiert von bluebean
          #2088

          @arnod
          Wäre es dann nicht sinnvoll, das Nachladen auf Notstrom-SOC nicht nachts um 2 Uhr zu machen, sondern besser am späten Nachmittag oder Abends, bspw. 19 Uhr? Entweder hat das dann die Sonne erledigt, sonst muss das Netz ran.
          Und die Funktion CheckPrognose() sollte im Negativ-Fall vielleicht nicht nur false zurückliefern, sondern auch eplizit HeuteNotstromVerwenden = false setzen.

          A 2 Antworten Letzte Antwort
          0
          • bluebeanB bluebean

            @arnod
            Wäre es dann nicht sinnvoll, das Nachladen auf Notstrom-SOC nicht nachts um 2 Uhr zu machen, sondern besser am späten Nachmittag oder Abends, bspw. 19 Uhr? Entweder hat das dann die Sonne erledigt, sonst muss das Netz ran.
            Und die Funktion CheckPrognose() sollte im Negativ-Fall vielleicht nicht nur false zurückliefern, sondern auch eplizit HeuteNotstromVerwenden = false setzen.

            A Offline
            A Offline
            ArnoD
            schrieb am zuletzt editiert von
            #2089

            @bluebean

            Könnte man machen, das Problem bleibt das gleiche, man muss wissen, ob das entladen gewollt ist, weil die Notstromreserve freigegeben wurde oder nicht gewollt, weil keine Sonne und der WR Strom verbraucht hat.

            2:00 Uhr, weil einige Strom zu Börsenpreise beziehen und um 2:00 Uhr in der Regel der Strom am günstigsten ist.

            bluebeanB 1 Antwort Letzte Antwort
            0
            • bluebeanB bluebean

              @arnod
              Wäre es dann nicht sinnvoll, das Nachladen auf Notstrom-SOC nicht nachts um 2 Uhr zu machen, sondern besser am späten Nachmittag oder Abends, bspw. 19 Uhr? Entweder hat das dann die Sonne erledigt, sonst muss das Netz ran.
              Und die Funktion CheckPrognose() sollte im Negativ-Fall vielleicht nicht nur false zurückliefern, sondern auch eplizit HeuteNotstromVerwenden = false setzen.

              A Offline
              A Offline
              ArnoD
              schrieb am zuletzt editiert von
              #2090

              @bluebean sagte in E3DC Hauskraftwerk steuern:

              Und die Funktion CheckPrognose() sollte im Negativ-Fall vielleicht nicht nur false zurückliefern, sondern auch eplizit HeuteNotstromVerwenden = false setzen.

              Schau dir mal die Funktion genau an, wann diese false liefert.
              Unter anderem auch, wenn der Verbrauch höher war als der Durchschnittsverbrauch vom Vortag und somit die Notstromreserve nicht mehr bis Sonnenaufgang reichen würde.

              Somit ist wieder folgender Fall möglich:
              Notstromreserve wurde um 0:00 Uhr freigegeben (HeuteNotstromVerwenden auf true).
              Da der Verbrauch aber zu hoch war, wurde diese um 1:30 Uhr wieder gesperrt (HeuteNotstromVerwenden auf false).
              Jetzt würde aber um 2:00 Uhr der Verbrauch aus dem Netz geladen werden.

              Deswegen bleibt HeuteNotstromVerwenden auf true und wird nur einmal um 12:00 Uhr Mittag auf false gesetzt.

              1 Antwort Letzte Antwort
              0
              • A ArnoD

                @bluebean

                Könnte man machen, das Problem bleibt das gleiche, man muss wissen, ob das entladen gewollt ist, weil die Notstromreserve freigegeben wurde oder nicht gewollt, weil keine Sonne und der WR Strom verbraucht hat.

                2:00 Uhr, weil einige Strom zu Börsenpreise beziehen und um 2:00 Uhr in der Regel der Strom am günstigsten ist.

                bluebeanB Online
                bluebeanB Online
                bluebean
                schrieb am zuletzt editiert von bluebean
                #2091

                @arnod
                Ich habe für mich jetzt mal in der Funktion CheckPrognose() am Ende ein HeuteNotstromVerwenden = false ergänzt und das Nachladen auf Notstrom-SOC auf 22 Uhr geschoben (da ist's auch schon günstig). Damit sollte doch eigentlich auch bei einem Start des Scripts nach 12 Uhr (und damit gesetzem HeuteNotstromVerwenden=true) und Batterie_SOC_Proz <= Notstrom_SOC_Proz keine Entladung unter Notstrom-SOC starten, wenn minWertPrognose_kWh = 0 ist.
                Oder hab ich hier einen logischen Fehler?

                        }else{
                            // Vor Sonnenaufgang
                            //if (DebugAusgabe){log(`CheckPrognose: Vor Sonnenaufgang`)}
                            let Tag = nextDayDate(0).slice(8,10);
                            let PrognoseMorgen_kWh = getState(`${instanz}.${PfadEbene1}.${PfadEbene2[2]}.PrognoseAuto_kWh_${Tag}`).val
                            //if (DebugAusgabe){log(`CheckPrognose: Reichweite ms =${ReichweiteTime_ms} Reichweite Stunden =${round((ReichweiteTime_ms-heute.getTime())/3600000,2)} sunriseEndTimeHeute_ms = ${sunriseEndTimeHeute_ms} sunriseEndTimeHeute Stunden =${round((sunriseEndTimeHeute_ms-heute.getTime())/3600000,2)} PrognoseMorgen_kWh =${PrognoseMorgen_kWh} minWertPrognose_kWh =${minWertPrognose_kWh}`)}
                            // Prüfen ob die Reichweite Batterie SOC größer ist als Sonnenaufgang + offset
                            if(ReichweiteTime_ms > sunriseEndTimeHeute_ms && PrognoseMorgen_kWh > minWertPrognose_kWh && minWertPrognose_kWh > 0){
                                // Batterie reicht bis zum Sonnenaufgang, es kann entladen werden
                                if (LogAusgabe && Notstrom_SOC_erreicht){log(`${Logparser1}-==== Freigabe Notstrom vor Sonnenaufgang. ====-${Logparser2}`)}
                                HeuteNotstromVerwenden = true;
                                return true
                            }
                    
                        }
                    HeuteNotstromVerwenden = false;
                    }
                    return false
                }
                
                A 1 Antwort Letzte Antwort
                0
                • bluebeanB bluebean

                  @arnod
                  Ich habe für mich jetzt mal in der Funktion CheckPrognose() am Ende ein HeuteNotstromVerwenden = false ergänzt und das Nachladen auf Notstrom-SOC auf 22 Uhr geschoben (da ist's auch schon günstig). Damit sollte doch eigentlich auch bei einem Start des Scripts nach 12 Uhr (und damit gesetzem HeuteNotstromVerwenden=true) und Batterie_SOC_Proz <= Notstrom_SOC_Proz keine Entladung unter Notstrom-SOC starten, wenn minWertPrognose_kWh = 0 ist.
                  Oder hab ich hier einen logischen Fehler?

                          }else{
                              // Vor Sonnenaufgang
                              //if (DebugAusgabe){log(`CheckPrognose: Vor Sonnenaufgang`)}
                              let Tag = nextDayDate(0).slice(8,10);
                              let PrognoseMorgen_kWh = getState(`${instanz}.${PfadEbene1}.${PfadEbene2[2]}.PrognoseAuto_kWh_${Tag}`).val
                              //if (DebugAusgabe){log(`CheckPrognose: Reichweite ms =${ReichweiteTime_ms} Reichweite Stunden =${round((ReichweiteTime_ms-heute.getTime())/3600000,2)} sunriseEndTimeHeute_ms = ${sunriseEndTimeHeute_ms} sunriseEndTimeHeute Stunden =${round((sunriseEndTimeHeute_ms-heute.getTime())/3600000,2)} PrognoseMorgen_kWh =${PrognoseMorgen_kWh} minWertPrognose_kWh =${minWertPrognose_kWh}`)}
                              // Prüfen ob die Reichweite Batterie SOC größer ist als Sonnenaufgang + offset
                              if(ReichweiteTime_ms > sunriseEndTimeHeute_ms && PrognoseMorgen_kWh > minWertPrognose_kWh && minWertPrognose_kWh > 0){
                                  // Batterie reicht bis zum Sonnenaufgang, es kann entladen werden
                                  if (LogAusgabe && Notstrom_SOC_erreicht){log(`${Logparser1}-==== Freigabe Notstrom vor Sonnenaufgang. ====-${Logparser2}`)}
                                  HeuteNotstromVerwenden = true;
                                  return true
                              }
                      
                          }
                      HeuteNotstromVerwenden = false;
                      }
                      return false
                  }
                  
                  A Offline
                  A Offline
                  ArnoD
                  schrieb am zuletzt editiert von ArnoD
                  #2092

                  @bluebean sagte in E3DC Hauskraftwerk steuern:

                  Damit sollte doch eigentlich auch bei einem Start des Scripts nach 12 Uhr (und damit gesetzem HeuteNotstromVerwenden=true) und Batterie_SOC_Proz <= Notstrom_SOC_Proz keine Entladung unter Notstrom-SOC starten, wenn minWertPrognose_kWh = 0 ist.

                  Das hat nichts mit dem Entladen bei minWertPrognose_kWh = 0 zu tun, sondern nur mit dem Nachladen aus dem Netz.
                  Ob entladen wird oder nicht ist nicht von der Variable HeuteNotstromVerwenden abhängig, sondern von der Variable NotstromVerwenden in der Funktion Ladesteuerung()

                  Habe jetzt die Variable umbenannt in HeuteNotstromVerbraucht, das trifft eher zu von der Verwendung. :-)

                  1 Antwort Letzte Antwort
                  0
                  • A ArnoD

                    @chris71 sagte in E3DC Hauskraftwerk steuern:

                    Wenn ich Batterie entladen durch Wallbox oder Wallbox priorisiert wähle, wird das nicht im Hauskraftwerk übernommen. zumindest zeigt es mir das nicht in der App an.

                    Das Script Charge-Control hat nichts mit der Wallbox zu tun. Es regelt auch nichts, was die Wallbox betrifft.
                    Beim Adapter e3dc rscp wurden einige Änderungen zum Thema Wallbox gemacht, die ich nicht mehr getestet habe, da ich meine über Modbus direkt steuere.
                    Bei Fragen zum Adapter e3dc rscp bitte in Github ein Issue aufmachen, damit der Adapter weiter optimiert wird.

                    Oder übernimmt CC die Werte und verarbeitet die Einstellungen ohne es im Hauskraftwerk zu ändern?

                    Das Script berücksichtigt hier keine Einstellungen, die beim Hauskraftwerk zur Ladepriorisierung der Wallbox gemacht werden. Bedeutet auch, wenn beim E3DC die Batterie Hauskraftwerk Vorrang hat, das Script die Ladeleistung trotzdem so weit wie notwendig begrenzt, um bis zum Eingestellten Ladeende den Eingestellten Ziel SOC zu erreichen. Was ja auch richtig ist, da der restliche Überschuss somit zum Laden vom Auto verwendet wird.

                    C Offline
                    C Offline
                    Chris71
                    schrieb am zuletzt editiert von
                    #2093

                    @arnod Danke für die Info. Habe ich mir schon gedacht.
                    Konnte heute endlich mal ein wenig testen. Wir hatten zwar wenig Sonneschein aber ein paar kwh konnte ich doch ins Auto laden.

                    1 Antwort Letzte Antwort
                    0
                    • A ArnoD

                      Manchmal hat man einfach ein Brett vorm Kopf, viermal den gleichen Fehler eingebaut. :woman-facepalming:

                      Neue Version Charge-Control auf GitHub hochgeladen.
                      Version: 1.2.7
                      Änderungen:

                      • Fehler behoben, dass die Batterie nicht mehr entladen wurde nach Regelende vor Ladeende.
                      A Offline
                      A Offline
                      ArnoD
                      schrieb am zuletzt editiert von ArnoD
                      #2094

                      Neue Version Charge-Control auf GitHub hochgeladen.
                      Version: 1.2.8
                      Änderungen:

                      • Fehler behoben, dass die Batterie entladen wurde, auch wenn Notstromreserve erreicht wurde.
                      • Ab dieser Version wird nur noch der e3dc-rscp Adapter benötigt, eine Anbindung über Modbus ist nicht mehr erforderlich.
                        Bitte prüfen, ob beim e3dc-rscp Adapter das Abfrageintervall für kurz (s) auf 2 steht und die folgenden Tag auf S eingestellt sind:

                      TAG_EMS_REQ_POWER_PV
                      TAG_EMS_REQ_POWER_BAT
                      TAG_EMS_REQ_POWER_HOME
                      TAG_EMS_REQ_POWER_GRID
                      TAG_EMS_REQ_POWER_ADD
                      TAG_EMS_REQ_BAT_SOC
                      TAG_WB_REQ_ENERGY_ALL

                      Die Views für VIS wurden auch angepasst, sodass der Modbus Adapter dann nicht mehr benötigt wird.

                      bluebeanB A A 3 Antworten Letzte Antwort
                      0
                      • A ArnoD

                        Neue Version Charge-Control auf GitHub hochgeladen.
                        Version: 1.2.8
                        Änderungen:

                        • Fehler behoben, dass die Batterie entladen wurde, auch wenn Notstromreserve erreicht wurde.
                        • Ab dieser Version wird nur noch der e3dc-rscp Adapter benötigt, eine Anbindung über Modbus ist nicht mehr erforderlich.
                          Bitte prüfen, ob beim e3dc-rscp Adapter das Abfrageintervall für kurz (s) auf 2 steht und die folgenden Tag auf S eingestellt sind:

                        TAG_EMS_REQ_POWER_PV
                        TAG_EMS_REQ_POWER_BAT
                        TAG_EMS_REQ_POWER_HOME
                        TAG_EMS_REQ_POWER_GRID
                        TAG_EMS_REQ_POWER_ADD
                        TAG_EMS_REQ_BAT_SOC
                        TAG_WB_REQ_ENERGY_ALL

                        Die Views für VIS wurden auch angepasst, sodass der Modbus Adapter dann nicht mehr benötigt wird.

                        bluebeanB Online
                        bluebeanB Online
                        bluebean
                        schrieb am zuletzt editiert von
                        #2095

                        @arnod
                        Wie kommt's, dass nun doch der schnelle modbus außen vorbleibt?
                        Reichen die Tweaks, um den rscp-Adapter auf Touren zu bekommen?

                        A 1 Antwort Letzte Antwort
                        0
                        • bluebeanB bluebean

                          @arnod
                          Wie kommt's, dass nun doch der schnelle modbus außen vorbleibt?
                          Reichen die Tweaks, um den rscp-Adapter auf Touren zu bekommen?

                          A Offline
                          A Offline
                          ArnoD
                          schrieb am zuletzt editiert von
                          #2096

                          @bluebean
                          Da ich gerade dabei war den Fehler zu korrigieren, habe ich den Adapter noch mal getestet, um die Systemauslastung zu prüfen.
                          Da es jetzt die Möglichkeit gibt, bei den Abfrageintervallen nicht benötigte Tag's mit N auszuklammern, ist die Systemauslastung in einem normalen Rahmen.
                          Die wichtigen Tag's werden alle 2 sek. abgefragt und ich konnte im direkten Vergleich mit dem Modbus Adapter keine Verzögerungen beim e3dc-rscp Adapter mehr feststellen.
                          Dachte mir das es ein Versuch wert ist.

                          Sollte aber jemand nur mit e3dc-rscp Adapter Probleme haben, ist es kein Problem den Modbus Adapter wieder optional im Script hinzuzufügen.

                          bluebeanB 1 Antwort Letzte Antwort
                          0
                          • A ArnoD

                            @bluebean
                            Da ich gerade dabei war den Fehler zu korrigieren, habe ich den Adapter noch mal getestet, um die Systemauslastung zu prüfen.
                            Da es jetzt die Möglichkeit gibt, bei den Abfrageintervallen nicht benötigte Tag's mit N auszuklammern, ist die Systemauslastung in einem normalen Rahmen.
                            Die wichtigen Tag's werden alle 2 sek. abgefragt und ich konnte im direkten Vergleich mit dem Modbus Adapter keine Verzögerungen beim e3dc-rscp Adapter mehr feststellen.
                            Dachte mir das es ein Versuch wert ist.

                            Sollte aber jemand nur mit e3dc-rscp Adapter Probleme haben, ist es kein Problem den Modbus Adapter wieder optional im Script hinzuzufügen.

                            bluebeanB Online
                            bluebeanB Online
                            bluebean
                            schrieb am zuletzt editiert von bluebean
                            #2097

                            Kleine Anmerkung für die Version 1.2.8: Im VIS für Charge Control wird der modbus noch verwendet für den Status EMS CTRL, außerdem auch noch für Autonomiezeit und Batteriekapazität in der Übersicht. Also nicht gleich modbus abklemmen und löschen.

                            A 1 Antwort Letzte Antwort
                            0
                            • bluebeanB bluebean

                              Kleine Anmerkung für die Version 1.2.8: Im VIS für Charge Control wird der modbus noch verwendet für den Status EMS CTRL, außerdem auch noch für Autonomiezeit und Batteriekapazität in der Übersicht. Also nicht gleich modbus abklemmen und löschen.

                              A Offline
                              A Offline
                              ArnoD
                              schrieb am zuletzt editiert von
                              #2098

                              @bluebean
                              Stimmt, das habe ich noch übersehen. Werde ich heute noch ändern.

                              1 Antwort Letzte Antwort
                              0
                              • jh537J Offline
                                jh537J Offline
                                jh537
                                schrieb am zuletzt editiert von
                                #2099

                                Hallo ArnoD, wenn der untere Ladekorridor deutlich größer als die Ladeleistung ist, müsste CC abschalten? Leider pendelt die LLeistung zwischen 0 und der berechn. Leistung. Wenn ich mit der Schwelle unter die Leistung gehe (einstelle) sind die On/Offs weg.
                                3079b329-ba35-4f16-813a-808c049d441f-grafik.png
                                7254eabf-39b3-4d68-92bd-c43c7df738bd-grafik.png

                                Zeit
                                	
                                Nachricht
                                javascript.0
                                	2023-04-10 08:29:45.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:29:39.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:29:36.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                javascript.0
                                	2023-04-10 08:29:36.007	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108176001)) ====- "}##
                                javascript.0
                                	2023-04-10 08:29:33.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:29:27.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:29:21.022	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:29:15.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:29:09.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:29:06.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                javascript.0
                                	2023-04-10 08:29:06.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108146000)) ====- "}##
                                javascript.0
                                	2023-04-10 08:29:00.018	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:55.740	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:48.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:42.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:36.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:33.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                javascript.0
                                	2023-04-10 08:28:33.007	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108113001)) ====- "}##
                                javascript.0
                                	2023-04-10 08:28:27.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:15.010	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:09.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:03.016	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:28:00.024	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                javascript.0
                                	2023-04-10 08:28:00.017	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108080001)) ====- "}##
                                javascript.0
                                	2023-04-10 08:27:54.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:27:48.020	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:27:42.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:27:36.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:27:30.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:27:27.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                javascript.0
                                	2023-04-10 08:27:27.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108047001)) ====- "}##
                                javascript.0
                                	2023-04-10 08:27:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:27:15.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:27:09.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:27:03.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:26:57.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                javascript.0
                                	2023-04-10 08:26:54.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                javascript.0
                                	2023-04-10 08:26:54.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108014001)) ====- "}##
                                javascript.0
                                	2023-04-10 08:26:48.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                javascript.0
                                	2023-04-10 08:26:42.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                javascript.0
                                	2023-04-10 08:26:36.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                javascript.0
                                	2023-04-10 08:26:30.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                javascript.0
                                	2023-04-10 08:26:24.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                javascript.0
                                	2023-04-10 08:26:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                javascript.0
                                	2023-04-10 08:26:21.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:195 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681107981001)) ====- "}##
                                javascript.0
                                	2023-04-10 08:26:18.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                
                                A 2 Antworten Letzte Antwort
                                0
                                • jh537J jh537

                                  Hallo ArnoD, wenn der untere Ladekorridor deutlich größer als die Ladeleistung ist, müsste CC abschalten? Leider pendelt die LLeistung zwischen 0 und der berechn. Leistung. Wenn ich mit der Schwelle unter die Leistung gehe (einstelle) sind die On/Offs weg.
                                  3079b329-ba35-4f16-813a-808c049d441f-grafik.png
                                  7254eabf-39b3-4d68-92bd-c43c7df738bd-grafik.png

                                  Zeit
                                  	
                                  Nachricht
                                  javascript.0
                                  	2023-04-10 08:29:45.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:39.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:36.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:36.007	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108176001)) ====- "}##
                                  javascript.0
                                  	2023-04-10 08:29:33.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:27.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:21.022	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:15.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:09.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:06.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                  javascript.0
                                  	2023-04-10 08:29:06.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108146000)) ====- "}##
                                  javascript.0
                                  	2023-04-10 08:29:00.018	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:55.740	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:48.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:42.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:36.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:33.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:33.007	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108113001)) ====- "}##
                                  javascript.0
                                  	2023-04-10 08:28:27.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:15.010	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:09.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:03.016	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:00.024	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                  javascript.0
                                  	2023-04-10 08:28:00.017	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108080001)) ====- "}##
                                  javascript.0
                                  	2023-04-10 08:27:54.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:48.020	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:42.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:36.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:30.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:27.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:27.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108047001)) ====- "}##
                                  javascript.0
                                  	2023-04-10 08:27:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:15.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:09.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:27:03.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:57.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:54.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:54.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108014001)) ====- "}##
                                  javascript.0
                                  	2023-04-10 08:26:48.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:42.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:36.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:30.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:24.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                  javascript.0
                                  	2023-04-10 08:26:21.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:195 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681107981001)) ====- "}##
                                  javascript.0
                                  	2023-04-10 08:26:18.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                  
                                  A Offline
                                  A Offline
                                  ArnoD
                                  schrieb am zuletzt editiert von
                                  #2100

                                  @jh537
                                  Ich versuche es mal bei mir nachzustellen, sollte jedenfalls nicht so sein.

                                  1 Antwort Letzte Antwort
                                  1
                                  • jh537J jh537

                                    Hallo ArnoD, wenn der untere Ladekorridor deutlich größer als die Ladeleistung ist, müsste CC abschalten? Leider pendelt die LLeistung zwischen 0 und der berechn. Leistung. Wenn ich mit der Schwelle unter die Leistung gehe (einstelle) sind die On/Offs weg.
                                    3079b329-ba35-4f16-813a-808c049d441f-grafik.png
                                    7254eabf-39b3-4d68-92bd-c43c7df738bd-grafik.png

                                    Zeit
                                    	
                                    Nachricht
                                    javascript.0
                                    	2023-04-10 08:29:45.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:39.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:36.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:36.007	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108176001)) ====- "}##
                                    javascript.0
                                    	2023-04-10 08:29:33.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:27.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:21.022	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:15.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:09.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:06.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                    javascript.0
                                    	2023-04-10 08:29:06.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108146000)) ====- "}##
                                    javascript.0
                                    	2023-04-10 08:29:00.018	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:55.740	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:48.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:42.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:36.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 197 M_Power = 197 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:33.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:33.007	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:197 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108113001)) ====- "}##
                                    javascript.0
                                    	2023-04-10 08:28:27.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:15.010	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:09.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:03.016	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:00.024	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                    javascript.0
                                    	2023-04-10 08:28:00.017	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108080001)) ====- "}##
                                    javascript.0
                                    	2023-04-10 08:27:54.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:48.020	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:42.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:36.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:30.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:27.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:27.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108047001)) ====- "}##
                                    javascript.0
                                    	2023-04-10 08:27:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:15.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:09.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:27:03.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:57.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 196 M_Power = 196 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:54.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:54.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:196 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681108014001)) ====- "}##
                                    javascript.0
                                    	2023-04-10 08:26:48.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:42.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:36.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:30.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:24.011	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:21.012	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie entladen stoppen 0W. Schritt = 2 LadenStoppen = true SET_POWER_MODE = 1 idle ====-"}##
                                    javascript.0
                                    	2023-04-10 08:26:21.006	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 2 M_Power:195 = Math.round(((Ladeende_Proz:75 - Batterie_SOC_Proz:64)*Speichergroesse_kWh:12*10*3600) / (tRegelende_milisek:1681132291255 - Zeit_aktuell_milisek:1681107981001)) ====- "}##
                                    javascript.0
                                    	2023-04-10 08:26:18.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 2 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 195 M_Power = 195 ====-"}##
                                    
                                    A Offline
                                    A Offline
                                    ArnoD
                                    schrieb am zuletzt editiert von
                                    #2101

                                    @jh537
                                    Kannst du bitte mal die Version 1.2.9 von Github testen.

                                    jh537J 1 Antwort Letzte Antwort
                                    1
                                    • A ArnoD

                                      @jh537
                                      Kannst du bitte mal die Version 1.2.9 von Github testen.

                                      jh537J Offline
                                      jh537J Offline
                                      jh537
                                      schrieb am zuletzt editiert von
                                      #2102

                                      @arnod Danke für fix :-)

                                      Leider lädt er trotz unterer Ladekor. 1180 W mit den errechneten 400 W. Aber er pendelt nicht mehr gegen 0.

                                      javascript.0
                                      	2023-04-10 16:34:36.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 452 M_Power = 452 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:34:30.023	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 452 M_Power = 452 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:34:24.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 452 M_Power = 452 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:34:18.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 452 M_Power = 452 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:34:12.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 451 M_Power = 452 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:34:12.007	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:452 = Math.round(((Ladeende2_Proz:85 - Batterie_SOC_Proz:78)* Speichergroesse_kWh:12 * 10 * 3600)/(tSommerladeende_milisek:1681143940597 - Zeit_aktuell_milisek:1681137252001)) ====- "}##
                                      javascript.0
                                      	2023-04-10 16:34:09.018	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:34:03.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:57.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:51.026	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:45.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:39.019	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 449 M_Power = 450 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:39.012	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:450 = Math.round(((Ladeende2_Proz:85 - Batterie_SOC_Proz:78)* Speichergroesse_kWh:12 * 10 * 3600)/(tSommerladeende_milisek:1681143940597 - Zeit_aktuell_milisek:1681137219006)) ====- "}##
                                      javascript.0
                                      	2023-04-10 16:33:33.016	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 448 M_Power = 448 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:27.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 448 M_Power = 448 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:21.016	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 448 M_Power = 448 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:15.018	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 448 M_Power = 448 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:09.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 447 M_Power = 448 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:09.009	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:448 = Math.round(((Ladeende2_Proz:85 - Batterie_SOC_Proz:78)* Speichergroesse_kWh:12 * 10 * 3600)/(tSommerladeende_milisek:1681143940597 - Zeit_aktuell_milisek:1681137189000)) ====- "}##
                                      javascript.0
                                      	2023-04-10 16:33:08.397	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== User Parameter UntererLadekorridor_2 wurde in 1180 geändert ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:06.031	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:33:00.033	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:32:54.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:32:48.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:32:42.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:32:36.109	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                      javascript.0
                                      	2023-04-10 16:32:36.059	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:446 = Math.round(((Ladeende2_Proz:85 - Batterie_SOC_Proz:78)* Speichergroesse_kWh:12 * 10 * 3600)/(tSommerladeende_milisek:1681143940597 - Zeit_aktuell_milisek:1681137156002)) ====- "}##
                                      
                                      A 1 Antwort Letzte Antwort
                                      0
                                      • jh537J jh537

                                        @arnod Danke für fix :-)

                                        Leider lädt er trotz unterer Ladekor. 1180 W mit den errechneten 400 W. Aber er pendelt nicht mehr gegen 0.

                                        javascript.0
                                        	2023-04-10 16:34:36.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 452 M_Power = 452 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:34:30.023	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 452 M_Power = 452 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:34:24.013	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 452 M_Power = 452 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:34:18.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 452 M_Power = 452 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:34:12.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 451 M_Power = 452 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:34:12.007	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:452 = Math.round(((Ladeende2_Proz:85 - Batterie_SOC_Proz:78)* Speichergroesse_kWh:12 * 10 * 3600)/(tSommerladeende_milisek:1681143940597 - Zeit_aktuell_milisek:1681137252001)) ====- "}##
                                        javascript.0
                                        	2023-04-10 16:34:09.018	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:34:03.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:57.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:51.026	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:45.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 450 M_Power = 450 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:39.019	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 449 M_Power = 450 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:39.012	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:450 = Math.round(((Ladeende2_Proz:85 - Batterie_SOC_Proz:78)* Speichergroesse_kWh:12 * 10 * 3600)/(tSommerladeende_milisek:1681143940597 - Zeit_aktuell_milisek:1681137219006)) ====- "}##
                                        javascript.0
                                        	2023-04-10 16:33:33.016	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 448 M_Power = 448 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:27.014	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 448 M_Power = 448 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:21.016	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 448 M_Power = 448 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:15.018	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 448 M_Power = 448 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:09.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 447 M_Power = 448 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:09.009	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:448 = Math.round(((Ladeende2_Proz:85 - Batterie_SOC_Proz:78)* Speichergroesse_kWh:12 * 10 * 3600)/(tSommerladeende_milisek:1681143940597 - Zeit_aktuell_milisek:1681137189000)) ====- "}##
                                        javascript.0
                                        	2023-04-10 16:33:08.397	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== User Parameter UntererLadekorridor_2 wurde in 1180 geändert ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:06.031	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:33:00.033	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:32:54.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:32:48.015	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:32:42.017	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:32:36.109	warn	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":"-==== Batterie laden. Schritt = 3 LadenStoppen = false Set_Power_Mode = 3 laden Set_Power_Value_W = 446 M_Power = 446 ====-"}##
                                        javascript.0
                                        	2023-04-10 16:32:36.059	info	script.js.common.Charge_Control: ##{"from":"Charge-Control", "message":" -==== 3 M_Power:446 = Math.round(((Ladeende2_Proz:85 - Batterie_SOC_Proz:78)* Speichergroesse_kWh:12 * 10 * 3600)/(tSommerladeende_milisek:1681143940597 - Zeit_aktuell_milisek:1681137156002)) ====- "}##
                                        
                                        A Offline
                                        A Offline
                                        ArnoD
                                        schrieb am zuletzt editiert von
                                        #2103

                                        @jh537
                                        Im Schritt 2 sollte es richtig funktionieren, habe es jetzt im Schritt 3 auch angepasst.
                                        Bitte nochmal die Version 1.2.9 testen.

                                        jh537J 2 Antworten Letzte Antwort
                                        1
                                        • A ArnoD

                                          Neue Version Charge-Control auf GitHub hochgeladen.
                                          Version: 1.2.8
                                          Änderungen:

                                          • Fehler behoben, dass die Batterie entladen wurde, auch wenn Notstromreserve erreicht wurde.
                                          • Ab dieser Version wird nur noch der e3dc-rscp Adapter benötigt, eine Anbindung über Modbus ist nicht mehr erforderlich.
                                            Bitte prüfen, ob beim e3dc-rscp Adapter das Abfrageintervall für kurz (s) auf 2 steht und die folgenden Tag auf S eingestellt sind:

                                          TAG_EMS_REQ_POWER_PV
                                          TAG_EMS_REQ_POWER_BAT
                                          TAG_EMS_REQ_POWER_HOME
                                          TAG_EMS_REQ_POWER_GRID
                                          TAG_EMS_REQ_POWER_ADD
                                          TAG_EMS_REQ_BAT_SOC
                                          TAG_WB_REQ_ENERGY_ALL

                                          Die Views für VIS wurden auch angepasst, sodass der Modbus Adapter dann nicht mehr benötigt wird.

                                          A Offline
                                          A Offline
                                          as
                                          schrieb am zuletzt editiert von
                                          #2104

                                          @arnod ?TAG_EMS_REQ_POWER_PV heißt dieses Register genau so
                                          bei mir werden viel mehr angezeigt dieser jedoch nicht - es gibt nur einen ähnlichen TAG_EMS_REQ_POWER_PV_AC........
                                          führt das dann zu fehlenden Werten o Fehlfunktion

                                          wie bekomme ich die Daten des E3DC Zusatzwechselrichter mit integriert, u das diese auch in die Kurven kommen aktuell zeigt er mir da keine Daten an
                                          Vielen Dank

                                          A 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          253

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe