      Ben. 0 @kreuzundkwer last edited by

      @kreuzundkwer Du kannst bei den Registern in der Konfiguration einen Faktor von 0,1 hinterlegen, dann stimmt die Temperatur.

      K 1 Reply Last reply Reply Quote 0
      • K
        kreuzundkwer @Ben. 0 last edited by kreuzundkwer

        @ben-0 Danke dir. Habe mir nen Wolf gesucht ... Der Trick ist, dass man in den Erweiterten Modus umschalten muss. Wieder einen Schritt weiter.

        Nächste Frage: Wie kann ich Nachkommastellen anzeigen?

        unltdnetworx 1 Reply Last reply Reply Quote 0
        • unltdnetworx
          unltdnetworx Developer @kreuzundkwer last edited by

          @kreuzundkwer sagte in Stiebel-ISG - Modbus:

          Wie kann ich Nachkommastellen anzeigen?

          Die sollten automatisch angezeigt, außer du hast genau einen runden Wert. Dann wird, glaube ich, nicht ",0" angezeigt.

          K 1 Reply Last reply Reply Quote 0
          • unltdnetworx
            unltdnetworx Developer @kreuzundkwer last edited by

            @kreuzundkwer sagte in Stiebel-ISG - Modbus:

            modbus.0.inputRegisters.32005_Betriebsstatus-2

            Das ist bei mir auch so. Daher habe ich den bei mir entfernt. Vermutlich wird der nicht unterstützt bei deinem Heizungstyp.

            frana120500 1 Reply Last reply Reply Quote 0
            • frana120500
              frana120500 @unltdnetworx last edited by

              modbus.0.inputRegisters.32005_Betriebsstatus

              liefert bei mir auch leider nix. Lt. Tecalor müsste hierfür ein neues MFG eingesetzt werden, auf dem eine neuere Software läuft

              1 Reply Last reply Reply Quote 0
              • K
                kreuzundkwer @unltdnetworx last edited by

                @unltdnetworx sagte in Stiebel-ISG - Modbus:

                @kreuzundkwer sagte in Stiebel-ISG - Modbus:

                Wie kann ich Nachkommastellen anzeigen?

                Die sollten automatisch angezeigt, außer du hast genau einen runden Wert. Dann wird, glaube ich, nicht ",0" angezeigt.

                Sämtliche Temperaturen sind auf volle Grad gerundet. Der Zufall ist mir zu groß. Habe auch grade nochmal im ISG geprüft. Dort müssten Nachkommastellen vorhanden sein. An meinem vorherigen Screenshot sieht man ganz gut, dass Nachkommastellen eigentlich geliefert werden.
                Außentemperatur = 129 °C. Erwartet hätte ich 12,9. Durch die Ergänzung des Faktors wird die Nachkommastelle scheinbar gerundet. Das habe ich durch den Abgleich mit dem ISG herausgefunden.

                Hat noch jemand eine Idee, warum alle Adressen des holdingRegister 0 sind?

                unltdnetworx 1 Reply Last reply Reply Quote 0
                • unltdnetworx
                  unltdnetworx Developer @kreuzundkwer last edited by

                  @kreuzundkwer sagte in Stiebel-ISG - Modbus:

                  Erwartet hätte ich 12,9. Durch die Ergänzung des Faktors wird die Nachkommastelle scheinbar gerundet.

                  Dann stimmt hier auch der Faktor nicht. Hast du die neueste Version meiner Vorlage verwendet? Es gab zwischenzeitlich mal einen Fehler beim Konvertieren der Tabelle auf die neue Modbusversion. Der Faktor wurde dabei überall auf 1 gesetzt, was natürlich nicht für jeden Wert stimmt.

                  K 1 Reply Last reply Reply Quote 0
                  • K
                    kreuzundkwer @unltdnetworx last edited by

                    @unltdnetworx sagte in Stiebel-ISG - Modbus:

                    @kreuzundkwer sagte in Stiebel-ISG - Modbus:

                    Erwartet hätte ich 12,9. Durch die Ergänzung des Faktors wird die Nachkommastelle scheinbar gerundet.

                    Dann stimmt hier auch der Faktor nicht. Hast du die neueste Version meiner Vorlage verwendet? Es gab zwischenzeitlich mal einen Fehler beim Konvertieren der Tabelle auf die neue Modbusversion. Der Faktor wurde dabei überall auf 1 gesetzt, was natürlich nicht für jeden Wert stimmt.

                    Denke schon. Habe sie zumindest aus dem verlinkten GIT Repository heruntergeladen.
                    https://github.com/unltdnetworx/stiebel-modbus/tree/main/lueftungsintegralgeraet/modbus-adapter-version-3

                    Habs nicht genau kontrolliert. Es könnte aber sein, dass tatsächlich überall eine 1 als Faktor stand.

                    unltdnetworx 1 Reply Last reply Reply Quote 0
                    • unltdnetworx
                      unltdnetworx Developer @kreuzundkwer last edited by

                      @kreuzundkwer
                      Leider sind die alten falschen Werte noch in der Version 3.

                      Schau dir bitte die Tabelle der Version 2 an. Da Stimmen Faktor und Offset. Einfach die Werte mal vergleichen und evtl. händisch anpassen.

                      Komme leider in nächster Zeit nicht dazu die Werte anzupassen.

                      K 1 Reply Last reply Reply Quote 0
                      • K
                        kreuzundkwer @unltdnetworx last edited by

                        @unltdnetworx
                        Problem gefunden. Es waren nicht die Adressen, sondern die Konfiguration der modbus Instanz. "Zahlen runden auf" hatte ich auf 1 und nicht auf 2 stehen. Nachdem ich den Wert auf 2 geändert habe, sehe ich nun auch eine Nachkommastelle.

                        Jetzt suche ich noch weiter, warum die holdingRegisters alle auf 0 stehen. Vielleicht hat hier noch jemand eine Idee?
                        Kann ich irgendwie prüfen, ob meine Anlage (LWZ 303 Integral) hier überhaupt was ausspuckt?

                        K 1 Reply Last reply Reply Quote 0
                        • Q
                          Qlink last edited by

                          Hi Leute,

                          darf ich mal in die Runde fragen wie ihr es umgesetzt habt, dass die Heizung z.B. auf Knopfdruck oder bei bestimmten Bedingungen zu überheizen beginnt ?

                          Hab dazu keine Idee wie ich das erreichen könnte.

                          Danke für eure Hilfe.

                          Beste Grüße

                          unltdnetworx 1 Reply Last reply Reply Quote 0
                          • K
                            kreuzundkwer @kreuzundkwer last edited by

                            @kreuzundkwer
                            Könnten diese Meldungen ein Grund dafür sein, dass die holdingRegisters bei mir nur 0 anzeigen?
                            Habe grade alle vorhandenen gelöscht und sie neu importiert.

                            javascript.0
                            2022-10-20 11:14:50.023	warn	This object will not be created in future versions. Please report this to the developer.
                            javascript.0
                            2022-10-20 11:14:50.021	warn	Object modbus.0.inputRegisters.32003_BUS-Status is invalid: obj.common.states has an invalid type! Expected "object", received "string"
                            javascript.0
                            2022-10-20 11:14:50.020	warn	This object will not be created in future versions. Please report this to the developer.
                            javascript.0
                            2022-10-20 11:14:50.020	warn	Object modbus.0.inputRegisters.32002_Fehlerstatus is invalid: obj.common.states has an invalid type! Expected "object", received "string"
                            javascript.0
                            2022-10-20 11:14:50.018	warn	This object will not be created in future versions. Please report this to the developer.
                            javascript.0
                            2022-10-20 11:14:50.017	warn	Object modbus.0.holdingRegisters.44003_SG_Ready_Eingang2 is invalid: obj.common.states has an invalid type! Expected "object", received "string"
                            javascript.0
                            2022-10-20 11:14:50.015	warn	This object will not be created in future versions. Please report this to the developer.
                            javascript.0
                            2022-10-20 11:14:50.014	warn	Object modbus.0.holdingRegisters.44002_SG_Ready_Eingang1 is invalid: obj.common.states has an invalid type! Expected "object", received "string"
                            javascript.0
                            2022-10-20 11:14:50.013	warn	This object will not be created in future versions. Please report this to the developer.
                            javascript.0
                            2022-10-20 11:14:50.012	warn	Object modbus.0.holdingRegisters.44001_SG_Ready_ein-_und_ausschalten is invalid: obj.common.states has an invalid type! Expected "object", received "string"
                            javascript.0
                            2022-10-20 11:14:50.012	warn	This object will not be created in future versions. Please report this to the developer.
                            javascript.0
                            2022-10-20 11:14:50.011	warn	Object modbus.0.holdingRegisters.41027_Restart-ISG is invalid: obj.common.states has an invalid type! Expected "object", received "string"
                            javascript.0
                            2022-10-20 11:14:50.009	warn	This object will not be created in future versions. Please report this to the developer.
                            javascript.0
                            2022-10-20 11:14:50.008	warn	Object modbus.0.holdingRegisters.41001_Betriebsart is invalid: obj.common.states has an invalid type! Expected "object", received "string"
                            
                            unltdnetworx F 2 Replies Last reply Reply Quote 0
                            • unltdnetworx
                              unltdnetworx Developer @kreuzundkwer last edited by

                              @kreuzundkwer
                              Nein, leider nicht. Das ist nur eine Meldung, dass in einer zukünftigen Version die Typen der Datenpunkte anders sein müssen.

                              1 Reply Last reply Reply Quote 0
                              • unltdnetworx
                                unltdnetworx Developer @Qlink last edited by unltdnetworx

                                @qlink sagte in Stiebel-ISG - Modbus:

                                Hab dazu keine Idee wie ich das erreichen könnte.

                                Bei mir gibt es einen Punkt "modbus.0.holdingRegisters.44002_SG_Ready_Eingang1", der aktiviert bei mir mit "true" die Einstellungen, welche ich im ISG unter "Einstellungen > Energiemanagement" festgelegt habe. Bei "false" springt alles wieder auf Standard zurück.

                                Ich habe allerdings auch ein ISGplus. Keine Garantie, dass es das unter ISGweb auch gibt.

                                1 Reply Last reply Reply Quote 0
                                • S
                                  Schimi last edited by

                                  Hat jemand das Modbus Register für die VD-Starts bei WPM3i?

                                  der stiebel Adapter liest es aus und zeigt es an... Bei der Modbus Doku finde ich nichts für die Wärmepumpe nur die Lüftungsgeräte...

                                  1 Reply Last reply Reply Quote 0
                                  • Q
                                    Qlink last edited by

                                    @unltdnetworx

                                    Nein, den gibts nur beim ISG Plus ... 😞

                                    1 Reply Last reply Reply Quote 0
                                    • C
                                      C.K. 0 last edited by

                                      ich verzweifele hier noch…..Bei meinem ISG Plus leutet die X2 Leuchte dauerhaft rot. Modbus verbindet sich nicht. Woran liegt es?

                                      Thomas Braun 1 Reply Last reply Reply Quote 0
                                      • Thomas Braun
                                        Thomas Braun Most Active @C.K. 0 last edited by

                                        @c-k-0 An felhlenden LogFiles von dir?

                                        1 Reply Last reply Reply Quote 0
                                        • C
                                          C.K. 0 last edited by

                                          Wie bekomme ich die LogFiles?

                                          Thomas Braun 1 Reply Last reply Reply Quote 0
                                          • Thomas Braun
                                            Thomas Braun Most Active @C.K. 0 last edited by

                                            @c-k-0

                                            iob logs --watch | uniq
                                            

                                            Dann den Adapter neustarten, Ausgaben aus der Konsole hier in CodeTags eingebettet reinkopieren.

                                            C 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate
                                            FAQ Cloud / IOT
                                            HowTo: Node.js-Update
                                            HowTo: Backup/Restore
                                            Downloads
                                            BLOG

                                            625
                                            Online

                                            31.6k
                                            Users

                                            79.4k
                                            Topics

                                            1.3m
                                            Posts

                                            modbus stiebel-isg
                                            35
                                            486
                                            74118
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo