  4. Test Adapter OpenKNX 0.6.x

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.3k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.0k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.4k

Test Adapter OpenKNX 0.6.x

Geplant Angeheftet Gesperrt Verschoben Tester
577 Beiträge 72 Kommentatoren 162.1k Aufrufe 71 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • M maxx8888

    Hab ich auch installiert und läuft.

    Danke, perfekt!

    Zwei Frage hätte ich dennoch:
    Mir ist aufgefallen, daß die Pakete nach einem Adapter Neustart (alles wird neu eingelesen) so schnell durch den KNX Bus rauschen das meine Buslast auf 150% hoch marschiert. "Frames delay" ist auf 50ms -> sind 20 Pakete/s, das sollte ja eigentlich passen.

    Und 2:
    Bin noch nicht dahinter gekommen was da genau passiert, aber beim Adapter restart fahren einige meiner Raffstores für 1sec los. Wahrscheinlich hab nur ich irgendeinen Wurm drin, mit der Logik der Fensterkontakte.
    Aber wollte mal fragen ob wer was ähnliches gesehen hat.

    K Offline
    K Offline
    killroy2
    schrieb am zuletzt editiert von
    #216

    @maxx8888
    Was bedeutet das, 150% Buslast - wo hast du das gemessen oder gesehen? Real ist ja nach 100% schluss.

    Zu Punkt 2: kannst du mir ein Log oder irgendeine genauere Beschreibung zukommen lassen die auf einen Fehler vom Adapter hindeutet? Ist das Fehlerbild sein 0.1.19 vorhanden und geht es mit der vorgängerversion ohne diesen Fehler?

    M 1 Antwort Letzte Antwort
    0
    • C ChrisChros

      Hallo, ich habe aktuell folgende Fehlermeldungen die mir das Log-File fluten.

      
      openknx.0
      2022-02-13 22:23:24.345	error	
      [error] 2022-02-13 21:23:24.343 (idle): Incomplete/unparseable UDP packet: TypeError: Cannot read property 'current_value' of undefined at fsm.event
      (/opt/iobroker/node_modules/iobroker.openknx/main.js:505:64) at fsm.<anonymous>
      (/opt/iobroker/node_modules/machina/lib/webpack:/src/emitter.js:27:1) at arrayEach
      (/opt/iobroker/node_modules/lodash/lodash.js:530:11) at Function.forEach
      (/opt/iobroker/node_modules/lodash/lodash.js:9410:14) at fsm.emit
      (/opt/iobroker/node_modules/machina/lib/webpack:/src/emitter.js:25:1) at fsm.emitEvent
      (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:602:10) at fsm._onEnter
      (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:552:14) at fsm.transition
      (/opt/iobroker/node_modules/machina/lib/webpack:/src/BehavioralFsm.js:175:1) at fsm.Fsm.<computed> [as transition] 
      (/opt/iobroker/node_modules/machina/lib/webpack:/src/Fsm.js:80:1) at fsm.inbound_TUNNELING_REQUEST_L_Data.ind
      (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:340:16): 0610042000190413d2002900bce011fe241305008000000000
      

      Die Einträge sind erst seit heute. Momentan ist das Log-File schon 25 MB groß.
      Gefühlt kommt alle Sekunde ein eintrag.
      Woran kann das liegen?

      Gruß Chris

      K Offline
      K Offline
      killroy2
      schrieb am zuletzt editiert von
      #217

      @chrischros said in Test Adapter OpenKNX 0.1.x:

      rc/emitter.js:25:1) at fsm.emitEvent

      Kannst du mir sagen mit welchem KNX Datum das passiert und wie das Objekt dazu im IOB aussieht? Dann kann ich es nachstellen. Danke

      C 1 Antwort Letzte Antwort
      0
      • K killroy2

        @chrischros said in Test Adapter OpenKNX 0.1.x:

        rc/emitter.js:25:1) at fsm.emitEvent

        Kannst du mir sagen mit welchem KNX Datum das passiert und wie das Objekt dazu im IOB aussieht? Dann kann ich es nachstellen. Danke

        C Offline
        C Offline
        ChrisChros
        schrieb am zuletzt editiert von
        #218

        @killroy2 said in Test Adapter OpenKNX 0.1.x:

        @chrischros said in Test Adapter OpenKNX 0.1.x:

        rc/emitter.js:25:1) at fsm.emitEvent

        Kannst du mir sagen mit welchem KNX Datum das passiert und wie das Objekt dazu im IOB aussieht? Dann kann ich es nachstellen. Danke

        Was meinst du genau damit?

        Zur Info, ich hab gestern Abend den Adapter einmal neugestartet und seitdem ist ruhe. An der ganzen Konstellation wurde in der Zwischenzeit nichts geändert.

        K 1 Antwort Letzte Antwort
        0
        • C ChrisChros

          @killroy2 said in Test Adapter OpenKNX 0.1.x:

          @chrischros said in Test Adapter OpenKNX 0.1.x:

          rc/emitter.js:25:1) at fsm.emitEvent

          Kannst du mir sagen mit welchem KNX Datum das passiert und wie das Objekt dazu im IOB aussieht? Dann kann ich es nachstellen. Danke

          Was meinst du genau damit?

          Zur Info, ich hab gestern Abend den Adapter einmal neugestartet und seitdem ist ruhe. An der ganzen Konstellation wurde in der Zwischenzeit nichts geändert.

          K Offline
          K Offline
          killroy2
          schrieb am zuletzt editiert von
          #219

          @chrischros ich brauche Logs, Daten, ... wie ich den Fehler reproduzieren und analysieren kann. An der Codestelle ist erstmal nichts auffälliges und wird auch permanent durchlaufen.

          T 1 Antwort Letzte Antwort
          0
          • K killroy2

            @chrischros ich brauche Logs, Daten, ... wie ich den Fehler reproduzieren und analysieren kann. An der Codestelle ist erstmal nichts auffälliges und wird auch permanent durchlaufen.

            T Offline
            T Offline
            tombox
            schrieb am zuletzt editiert von
            #220

            @killroy2 Also für mich sieht die Codestelle nicht gut aus und der Fehler ist eigentlich klar weil es vorher kein check gibt

            Cannot read property 'current_value' of undefined
            (/opt/iobroker/node_modules/iobroker.openknx/main.js:505:64)
            
            1 Antwort Letzte Antwort
            0
            • N Offline
              N Offline
              netfriend
              schrieb am zuletzt editiert von
              #221

              Hallo,
              ich habe den openknx 0.1.15 über iobroker installiert. Das xml-File der ETS5 konnte ich nahezu fehlerfrei importieren. Ging relativ schnell, es waren 574 GAs, die 3 angemeckerten Fehler waren nachvollziehbar. Hatte die Zuweisung von DPTs zur GA vergessen. Nach einer Korrektur war der Import fehlerfrei möglich und der Adapter startet auch! Sieht schon mal sehr gut aus.
              Wenn man nun den Bus im Gruppenmonitor beobachtet und in openknx kontrolliert, füllen sich auch langsam die Objekte.

              Allerdings habe ich bei meinen Verbrauchszählern ein Problem. Über ein mdt-Tasterinferface, das als Verbrauchszähler konfiguriert ist, bekomme ich Impulse von meinem Wasserzähler.
              Das KO im Gerät ist als "DPT 12.1200 (4-Byte vorzeichenlos) Volumen Flüssigkeit (l)" parametriert.
              Im Gruppenmonitor wird mir dies auch korrekt angezeigt und ich sehe Werte.

              Im XML steht folgendes:

              <GroupAddress Name="Wasserzähler : Zähler" Address="1/5/10" DPTs="DPST-12-1200" />
              

              Im openknx-Objekt steht folgendes:

              {
                "_id": "openknx.0.Zentralfunktion.Verbrauchszähler.Wasserzähler_:_Zähler",
                "type": "state",
                "common": {
                  "desc": "Basetype: 4-byte unsigned value",
                  "min": 0,
                  "max": 4294967295,
                  "name": "Wasserzähler : Zähler",
                  "read": true,
                  "role": "state",
                  "type": "number",
                  "write": true
                },
                "native": {
                  "address": "1/5/10",
                  "answer_groupValueResponse": false,
                  "autoread": true,
                  "bitlength": 32,
                  "dpt": "DPT12.1200",
                  "valuetype": "basic"
                },
                "from": "system.adapter.openknx.0",
                "user": "system.user.admin",
                "ts": 1645115985826,
                "acl": {
                  "object": 1636,
                  "state": 1636,
                  "owner": "system.user.admin",
                  "ownerGroup": "system.group.administrator"
                }
              }
              

              Einerseits fehlt die unit (bei anderen GAs funktioniert das einwandfrei) und andererseits erhalte ich keine Werte.
              Wer kann helfen?
              Kann man beim openknx ein Log einschalten? In den Adaptereinstellungen habe ich dazu nichts gefunden (oder übersehen) und im Protokoll des iobroker taucht als "Quelle" kein "openknx" auf.

              Danke für Eure Unterstützung!

              T K 2 Antworten Letzte Antwort
              0
              • N netfriend

                Hallo,
                ich habe den openknx 0.1.15 über iobroker installiert. Das xml-File der ETS5 konnte ich nahezu fehlerfrei importieren. Ging relativ schnell, es waren 574 GAs, die 3 angemeckerten Fehler waren nachvollziehbar. Hatte die Zuweisung von DPTs zur GA vergessen. Nach einer Korrektur war der Import fehlerfrei möglich und der Adapter startet auch! Sieht schon mal sehr gut aus.
                Wenn man nun den Bus im Gruppenmonitor beobachtet und in openknx kontrolliert, füllen sich auch langsam die Objekte.

                Allerdings habe ich bei meinen Verbrauchszählern ein Problem. Über ein mdt-Tasterinferface, das als Verbrauchszähler konfiguriert ist, bekomme ich Impulse von meinem Wasserzähler.
                Das KO im Gerät ist als "DPT 12.1200 (4-Byte vorzeichenlos) Volumen Flüssigkeit (l)" parametriert.
                Im Gruppenmonitor wird mir dies auch korrekt angezeigt und ich sehe Werte.

                Im XML steht folgendes:

                <GroupAddress Name="Wasserzähler : Zähler" Address="1/5/10" DPTs="DPST-12-1200" />
                

                Im openknx-Objekt steht folgendes:

                {
                  "_id": "openknx.0.Zentralfunktion.Verbrauchszähler.Wasserzähler_:_Zähler",
                  "type": "state",
                  "common": {
                    "desc": "Basetype: 4-byte unsigned value",
                    "min": 0,
                    "max": 4294967295,
                    "name": "Wasserzähler : Zähler",
                    "read": true,
                    "role": "state",
                    "type": "number",
                    "write": true
                  },
                  "native": {
                    "address": "1/5/10",
                    "answer_groupValueResponse": false,
                    "autoread": true,
                    "bitlength": 32,
                    "dpt": "DPT12.1200",
                    "valuetype": "basic"
                  },
                  "from": "system.adapter.openknx.0",
                  "user": "system.user.admin",
                  "ts": 1645115985826,
                  "acl": {
                    "object": 1636,
                    "state": 1636,
                    "owner": "system.user.admin",
                    "ownerGroup": "system.group.administrator"
                  }
                }
                

                Einerseits fehlt die unit (bei anderen GAs funktioniert das einwandfrei) und andererseits erhalte ich keine Werte.
                Wer kann helfen?
                Kann man beim openknx ein Log einschalten? In den Adaptereinstellungen habe ich dazu nichts gefunden (oder übersehen) und im Protokoll des iobroker taucht als "Quelle" kein "openknx" auf.

                Danke für Eure Unterstützung!

                T Offline
                T Offline
                tombox
                schrieb am zuletzt editiert von
                #222

                @netfriend Der DPST-12-1200 ist nicht eingefügt.
                Eine Diskussion bezüglich Updates von DPT und anderen Fehlern findest du hier
                https://github.com/iobroker-community-adapters/ioBroker.openknx/issues/101#issuecomment-1022657106

                N 1 Antwort Letzte Antwort
                0
                • T tombox

                  @netfriend Der DPST-12-1200 ist nicht eingefügt.
                  Eine Diskussion bezüglich Updates von DPT und anderen Fehlern findest du hier
                  https://github.com/iobroker-community-adapters/ioBroker.openknx/issues/101#issuecomment-1022657106

                  N Offline
                  N Offline
                  netfriend
                  schrieb am zuletzt editiert von
                  #223

                  @tombox Danke für den Link. So wie ich das verstehe, sind die DPTs nur prinzipiell vorhanden, also der Datentyp wird interpretiert, aber die zahlreichen Unter-DPTs mit allen möglichen Einheiten nicht, richtig?

                  Ich habe nun den DPT von 12.1200 auf 12.001 (Counter pulses ohne Einheit) umgestellt. Nun bekomme ich Werte. Find ich schon einmal gut.
                  Was mich allerdings wundert: Bei meinem Gaszähler-Counter ist DPT 14.076 (Volumen m³) eingestellt. Lt. dem Link ist diese DPT auch nicht implementiert, ähnlich wie bei 12.1200. Aber hier bekomme ich Werte?

                  1 Antwort Letzte Antwort
                  0
                  • T Offline
                    T Offline
                    tombox
                    schrieb am zuletzt editiert von
                    #224

                    @netfriend
                    DPT 14.076 ist nicht enthalten. Ein Update ist für Mitte 2022 geplant.
                    Es ist außerdem nicht gewünscht das der Nutzer die Werte empfangen kann, wenn das DPT nicht vorhanden ist.

                    N 1 Antwort Letzte Antwort
                    0
                    • T tombox

                      @netfriend
                      DPT 14.076 ist nicht enthalten. Ein Update ist für Mitte 2022 geplant.
                      Es ist außerdem nicht gewünscht das der Nutzer die Werte empfangen kann, wenn das DPT nicht vorhanden ist.

                      N Offline
                      N Offline
                      netfriend
                      schrieb am zuletzt editiert von
                      #225

                      @tombox sagte in Test Adapter OpenKNX 0.1.x:

                      @netfriend
                      DPT 14.076 ist nicht enthalten. Ein Update ist für Mitte 2022 geplant.

                      Ok, das klingt gut!

                      Es ist außerdem nicht gewünscht das der Nutzer die Werte empfangen kann, wenn das DPT nicht vorhanden ist.

                      Ich hätte auch erwartet, wenn der xml-Import problemlos klappt, dass alle DPTs aus dem xml vorhanden sind und korrekt verwendet werden. Andernfalls hätte ich eine Fehlermeldung erwartet (z.B. DPT 14.076 nicht implementiert). Das würde so manchen Selbstzweifel :-) und Fehlersuche sparen.

                      1 Antwort Letzte Antwort
                      0
                      • C Offline
                        C Offline
                        ChrisChros
                        schrieb am zuletzt editiert von
                        #226

                        Hallo,
                        nach einem Restart des Raspberry über die Console bekomme ich wieder folgende Fehlermeldungen im Log:

                        2022-02-19 09:05:41.851  - info: host.raspberrypi instance system.adapter.openknx.0 started with pid 688
                        2022-02-19 09:05:44.832  - info: openknx.0 (688) starting. Version 0.1.19 in /opt/iobroker/node_modules/iobroker.openknx, node: v14.19.0, js-controller: 4.0.8
                        2022-02-19 09:05:44.870  - info: openknx.0 (688) Connecting to knx gateway:  10.10.20.2:3671   with phy. Adr: 1.1.253 minimum send delay: 50 ms
                        2022-02-19 09:05:44.872  - info: openknx.0 (688) /opt/iobroker/node_modules/iobroker.js-controller
                        2022-02-19 09:05:45.213  - error: openknx.0 (688) [error] 2022-02-19 08:05:45.157 (idle): Incomplete/unparseable UDP packet: TypeError: Cannot read property 'current_value' of undefined
                            at fsm.event (/opt/iobroker/node_modules/iobroker.openknx/main.js:505:64)
                            at fsm.<anonymous> (/opt/iobroker/node_modules/machina/lib/webpack:/src/emitter.js:27:1)
                            at arrayEach (/opt/iobroker/node_modules/lodash/lodash.js:530:11)
                            at Function.forEach (/opt/iobroker/node_modules/lodash/lodash.js:9410:14)
                            at fsm.emit (/opt/iobroker/node_modules/machina/lib/webpack:/src/emitter.js:25:1)
                            at fsm.emitEvent (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:602:10)
                            at fsm._onEnter (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:552:14)
                            at fsm.transition (/opt/iobroker/node_modules/machina/lib/webpack:/src/BehavioralFsm.js:175:1)
                            at fsm.Fsm.<computed> [as transition] (/opt/iobroker/node_modules/machina/lib/webpack:/src/Fsm.js:80:1)
                            at fsm.inbound_TUNNELING_REQUEST_L_Data.ind (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:340:16): 0610020800089300
                        2022-02-19 09:05:45.222  - error: openknx.0 (688) [error] 2022-02-19 08:05:45.220 (idle): Incomplete/unparseable UDP packet: TypeError: Cannot read property 'current_value' of undefined
                            at fsm.event (/opt/iobroker/node_modules/iobroker.openknx/main.js:505:64)
                            at fsm.<anonymous> (/opt/iobroker/node_modules/machina/lib/webpack:/src/emitter.js:27:1)
                            at arrayEach (/opt/iobroker/node_modules/lodash/lodash.js:530:11)
                            at Function.forEach (/opt/iobroker/node_modules/lodash/lodash.js:9410:14)
                            at fsm.emit (/opt/iobroker/node_modules/machina/lib/webpack:/src/emitter.js:25:1)
                            at fsm.emitEvent (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:602:10)
                            at fsm._onEnter (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:552:14)
                            at fsm.transition (/opt/iobroker/node_modules/machina/lib/webpack:/src/BehavioralFsm.js:175:1)
                            at fsm.Fsm.<computed> [as transition] (/opt/iobroker/node_modules/machina/lib/webpack:/src/Fsm.js:80:1)
                            at fsm.inbound_TUNNELING_REQUEST_L_Data.ind (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:340:16): 061004200019049301002900bce011fe240805008040f9999a
                        2022-02-19 09:05:45.236  - error: openknx.0 (688) [error] 2022-02-19 08:05:45.234 (idle): Incomplete/unparseable UDP packet: TypeError: Cannot read property 'current_value' of undefined
                        

                        Scheinbar hat der Adapter ab und zu Probleme sich bei einem Neustart des RPi richtig zu verbinden. Wenn ich den Adapter dann manuell über die WebPage neu starte gibt es anschließend keine Probleme mehr und der Adapter läuft ohne Probleme.

                        2022-02-19 09:54:02.013  - info: host.raspberrypi "system.adapter.openknx.0" disabled
                        2022-02-19 09:54:02.029  - info: host.raspberrypi stopInstance system.adapter.openknx.0 (force=false, process=true)
                        2022-02-19 09:54:02.059  - error: openknx.0 (688) [error] 2022-02-19 08:54:02.058 (idle): Incomplete/unparseable UDP packet: TypeError: Cannot read property 'current_value' of undefined
                            at fsm.event (/opt/iobroker/node_modules/iobroker.openknx/main.js:505:64)
                            at fsm.<anonymous> (/opt/iobroker/node_modules/machina/lib/webpack:/src/emitter.js:27:1)
                            at arrayEach (/opt/iobroker/node_modules/lodash/lodash.js:530:11)
                            at Function.forEach (/opt/iobroker/node_modules/lodash/lodash.js:9410:14)
                            at fsm.emit (/opt/iobroker/node_modules/machina/lib/webpack:/src/emitter.js:25:1)
                            at fsm.emitEvent (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:602:10)
                            at fsm._onEnter (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:552:14)
                            at fsm.transition (/opt/iobroker/node_modules/machina/lib/webpack:/src/BehavioralFsm.js:175:1)
                            at fsm.Fsm.<computed> [as transition] (/opt/iobroker/node_modules/machina/lib/webpack:/src/Fsm.js:80:1)
                            at fsm.inbound_TUNNELING_REQUEST_L_Data.ind (/opt/iobroker/node_modules/iobroker.openknx/lib/knx/src/FSM.js:340:16): 06100420001504936f002900bce011fe244d010080
                        2022-02-19 09:54:02.086  - info: openknx.0 (688) Got terminate signal TERMINATE_YOURSELF
                        2022-02-19 09:54:02.087  - info: host.raspberrypi stopInstance system.adapter.openknx.0 send kill signal
                        2022-02-19 09:54:02.088  - info: openknx.0 (688) terminating
                        2022-02-19 09:54:02.090  - info: openknx.0 (688) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                        2022-02-19 09:54:02.687  - info: host.raspberrypi instance system.adapter.openknx.0 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                        2022-02-19 09:58:10.065  - info: host.raspberrypi "system.adapter.openknx.0" enabled
                        2022-02-19 09:58:10.346  - info: host.raspberrypi instance system.adapter.openknx.0 started with pid 1625
                        2022-02-19 09:58:12.435  - info: openknx.0 (1625) starting. Version 0.1.19 in /opt/iobroker/node_modules/iobroker.openknx, node: v14.19.0, js-controller: 4.0.8
                        2022-02-19 09:58:12.475  - info: openknx.0 (1625) Connecting to knx gateway:  10.10.20.2:3671   with phy. Adr: 1.1.253 minimum send delay: 50 ms
                        2022-02-19 09:58:12.476  - info: openknx.0 (1625) /opt/iobroker/node_modules/iobroker.js-controller
                        2022-02-19 09:58:13.319  - info: openknx.0 (1625) Connected!
                        2022-02-19 09:58:13.788  - info: openknx.0 (1625) Found 934 valid KNX objects of 936 objects in adapter.
                        
                        K 1 Antwort Letzte Antwort
                        0
                        • N netfriend

                          Hallo,
                          ich habe den openknx 0.1.15 über iobroker installiert. Das xml-File der ETS5 konnte ich nahezu fehlerfrei importieren. Ging relativ schnell, es waren 574 GAs, die 3 angemeckerten Fehler waren nachvollziehbar. Hatte die Zuweisung von DPTs zur GA vergessen. Nach einer Korrektur war der Import fehlerfrei möglich und der Adapter startet auch! Sieht schon mal sehr gut aus.
                          Wenn man nun den Bus im Gruppenmonitor beobachtet und in openknx kontrolliert, füllen sich auch langsam die Objekte.

                          Allerdings habe ich bei meinen Verbrauchszählern ein Problem. Über ein mdt-Tasterinferface, das als Verbrauchszähler konfiguriert ist, bekomme ich Impulse von meinem Wasserzähler.
                          Das KO im Gerät ist als "DPT 12.1200 (4-Byte vorzeichenlos) Volumen Flüssigkeit (l)" parametriert.
                          Im Gruppenmonitor wird mir dies auch korrekt angezeigt und ich sehe Werte.

                          Im XML steht folgendes:

                          <GroupAddress Name="Wasserzähler : Zähler" Address="1/5/10" DPTs="DPST-12-1200" />
                          

                          Im openknx-Objekt steht folgendes:

                          {
                            "_id": "openknx.0.Zentralfunktion.Verbrauchszähler.Wasserzähler_:_Zähler",
                            "type": "state",
                            "common": {
                              "desc": "Basetype: 4-byte unsigned value",
                              "min": 0,
                              "max": 4294967295,
                              "name": "Wasserzähler : Zähler",
                              "read": true,
                              "role": "state",
                              "type": "number",
                              "write": true
                            },
                            "native": {
                              "address": "1/5/10",
                              "answer_groupValueResponse": false,
                              "autoread": true,
                              "bitlength": 32,
                              "dpt": "DPT12.1200",
                              "valuetype": "basic"
                            },
                            "from": "system.adapter.openknx.0",
                            "user": "system.user.admin",
                            "ts": 1645115985826,
                            "acl": {
                              "object": 1636,
                              "state": 1636,
                              "owner": "system.user.admin",
                              "ownerGroup": "system.group.administrator"
                            }
                          }
                          

                          Einerseits fehlt die unit (bei anderen GAs funktioniert das einwandfrei) und andererseits erhalte ich keine Werte.
                          Wer kann helfen?
                          Kann man beim openknx ein Log einschalten? In den Adaptereinstellungen habe ich dazu nichts gefunden (oder übersehen) und im Protokoll des iobroker taucht als "Quelle" kein "openknx" auf.

                          Danke für Eure Unterstützung!

                          K Offline
                          K Offline
                          killroy2
                          schrieb am zuletzt editiert von killroy2
                          #227

                          Hallo @netfriend,

                          eine Information zum Logging findest du zB im Readme auf NPM. Link dazu im Eingangspost.

                          DPT 12.1200 wird bis Version 0.1.19 nicht unterstütz, nur sein Basistyp DPT12. Vom Konzept können alle Telegramme unabhängig vom DPT gesendet und empfangen werden. Wenn ein DPT nicht nativ unterstütz wird gibt es eine Logeintrag. In deinem Beispiel fehlt dir die Einheit als Metainformation, was keine gravierende Einschränkung sein dürfte. Alle DPTs zu unterstützen ist eine Sisyphusaufgabe und einige davon sind mir noch nicht untergekommen. Die Erstellung passiert nach und nach. Die von dir beschriebenen nehme ich ins nächste Release auf.
                          Dass DPT 12.1200 bei dir nicht geht ist tatsächlich ein Fehler den ich bei mir reproduzieren konnte! Der Fehler ist im nächsten Release behoben.

                          Bitte lass dich hier nicht durch unqualifizierte Falschaussagen von Projektunbeteiligten verwirren.

                          N T 2 Antworten Letzte Antwort
                          1
                          • K killroy2

                            Hallo @netfriend,

                            eine Information zum Logging findest du zB im Readme auf NPM. Link dazu im Eingangspost.

                            DPT 12.1200 wird bis Version 0.1.19 nicht unterstütz, nur sein Basistyp DPT12. Vom Konzept können alle Telegramme unabhängig vom DPT gesendet und empfangen werden. Wenn ein DPT nicht nativ unterstütz wird gibt es eine Logeintrag. In deinem Beispiel fehlt dir die Einheit als Metainformation, was keine gravierende Einschränkung sein dürfte. Alle DPTs zu unterstützen ist eine Sisyphusaufgabe und einige davon sind mir noch nicht untergekommen. Die Erstellung passiert nach und nach. Die von dir beschriebenen nehme ich ins nächste Release auf.
                            Dass DPT 12.1200 bei dir nicht geht ist tatsächlich ein Fehler den ich bei mir reproduzieren konnte! Der Fehler ist im nächsten Release behoben.

                            Bitte lass dich hier nicht durch unqualifizierte Falschaussagen von Projektunbeteiligten verwirren.

                            N Offline
                            N Offline
                            netfriend
                            schrieb am zuletzt editiert von
                            #228

                            @killroy2 Danke für Deine Rückmeldung!
                            Prima, dass Du dich der Sache annimmst und dies im nächsten Release nachziehen möchtest! Das ist nicht selbstverständlich, ich weiß den Zeitaufwand, der darin steckt (Testen, versuchen nachzustellen, analysieren, beheben, wieder testen) sehr zu schätzen! Herzlichen Dank!
                            Prinzipiell hast Du Recht, dass die fehlenden Einheiten nicht sehr störend sind. Allerdings ist es bei mir (und wahrscheinlich bei den meisten) so, dass ich ein funktionierendes KNX-Projekt habe. Hier habe ich versucht, alles GAs ordentlich zu benennen und alles GAs und KOs die entsprechenden DPTs zuzuweisen (auch mit Einheiten, sofern von KNX vorgesehen).
                            Nun importiere ich mein xml in z.B. openknx und stelle fest, dass was nicht so angezeigt wird wie erwartet. Ich könnte damit leben, dass Einheiten fehlen, wenn die Werte korrekt angezeigt werden. Das war jetzt leider bei der 12.1200 nicht der Fall, damit musste ich mein KNX-Projekt anpassen und habe diese entsprechend auf 12.001 umgestellt. Ich wollte eigentlich vermeiden, dass ich am KNX-Projekt rumspiele war aber neugierig ob es dann funktioniert. Von daher wäre es mir persönlich am liebsten, wenn nicht implementierte DPTs dahingehend funktionieren indem der Basistyp verwendet wird und beim Import der xml-Datei ein enstsprechender Hinweis angezeigt wird. Damit würde ich mein KNX-Projekt unverändert lassen und warten/hoffen, dass dies mit einem künftigen Update in openknx behoben sein könnte.

                            Noch eine kurze Frage zum DPT 14.076. Den nutze ich für meinen Gaszähler. Wenn ich in der ETS dort z.B. den Wert 7,4 [m³] sende, sehe ich im Gruppenmonitor auch diesen Wert. In openknx wird aber 7,40000001 [m³] angezeigt.
                            Ist das hier ein Rundungsfehler oder woran liegt das? Parallel dazu habe ich noch den ioBroker-KNX-Adapter installiert, dort wird richtigerweise 7,4 [m³] angezeigt. Also gehe ich davon aus, dass am Bus der richtige Wert verfügbar ist.

                            Danke für Deine Hilfe!

                            1 Antwort Letzte Antwort
                            0
                            • K Offline
                              K Offline
                              killroy2
                              schrieb am zuletzt editiert von killroy2
                              #229

                              @chrischros
                              Kannst du die Stelle vom Log zeigen an dem die Fehler beginnen? Gibt es eine Möglichkeit den Fehler nachzustellen?
                              Du schreibst dass sich die Fehlermeldungen häufen wenn das Ereignis eintritt.
                              Annahme ist, dass der Adapter in einem inkonsistenten Zustand ist, und es nicht an äusseren Ereignissen liegt. Annahme ist auch, das Problem ist erst mit einer Änderung in der 0.1.19 Version sichtbar und bestand schon davor, die Auswirkung war aber weniger sichtbar. Mehr kann ich dazu noch nicht sagen.

                              C 1 Antwort Letzte Antwort
                              0
                              • K killroy2

                                @chrischros
                                Kannst du die Stelle vom Log zeigen an dem die Fehler beginnen? Gibt es eine Möglichkeit den Fehler nachzustellen?
                                Du schreibst dass sich die Fehlermeldungen häufen wenn das Ereignis eintritt.
                                Annahme ist, dass der Adapter in einem inkonsistenten Zustand ist, und es nicht an äusseren Ereignissen liegt. Annahme ist auch, das Problem ist erst mit einer Änderung in der 0.1.19 Version sichtbar und bestand schon davor, die Auswirkung war aber weniger sichtbar. Mehr kann ich dazu noch nicht sagen.

                                C Offline
                                C Offline
                                ChrisChros
                                schrieb am zuletzt editiert von
                                #230

                                @killroy2 said in Test Adapter OpenKNX 0.1.x:

                                Kannst du die Stelle vom Log zeigen an dem die Fehler beginnen?

                                Das ist der erste Log-Auszug. Das war direkt nach dem Restart des RPi über die Console.

                                @killroy2 said in Test Adapter OpenKNX 0.1.x:

                                Gibt es eine Möglichkeit den Fehler nachzustellen?

                                Ich werde nachher noch mal einen Reboot vom RPi machen und schauen ob es sich dann genauso verhält.

                                @killroy2 said in Test Adapter OpenKNX 0.1.x:

                                Du schreibst dass sich die Fehlermeldungen häufen wenn das Ereignis eintritt.

                                Ja, es werden dann fast sekündlich die gleichen Zeilen in der Log geschrieben.

                                @killroy2 said in Test Adapter OpenKNX 0.1.x:

                                Annahme ist, dass der Adapter in einem inkonsistenten Zustand ist, und es nicht an äusseren Ereignissen liegt. Annahme ist auch, das Problem ist erst mit einer Änderung in der 0.1.19 Version sichtbar und bestand schon davor, die Auswirkung war aber weniger sichtbar.

                                Ich denke auch das der Adapter dann irgendwie hängen bleibt. Vor 0.1.19 hatte ich zumindest keine solchen Einträge im Log. Allerdings hätte mir das auffallen müssen da der Adapter dann nicht auf grün ist. Laut der Ansicht in den Instanzen ist der Adapter mit dem Host verbunden und bekommt ein Lebenszeichen, beide haben einen grünen Harken.
                                Nur Verbindung mit Gerät oder Dienst besteht dann nicht.

                                1 Antwort Letzte Antwort
                                0
                                • C Offline
                                  C Offline
                                  ChrisChros
                                  schrieb am zuletzt editiert von
                                  #231

                                  Habe eben noch mal einen Neustart über die Console vom RPi ausgelöst und alles ist ganz normal gestartet. Keine Ahnung was heute morgen anders war.

                                  1 Antwort Letzte Antwort
                                  0
                                  • K Offline
                                    K Offline
                                    killroy2
                                    schrieb am zuletzt editiert von
                                    #232

                                    @netfriend said in Test Adapter OpenKNX 0.1.x:

                                    Noch eine kurze Frage zum DPT 14.076. Den nutze ich für meinen Gaszähler. Wenn ich in der ETS dort z.B. den Wert 7,4 [m³] sende, sehe ich im Gruppenmonitor auch diesen Wert. In openknx wird aber 7,40000001 [m³] angezeigt.
                                    Ist das hier ein Rundungsfehler oder woran liegt das? Parallel dazu habe ich noch den ioBroker-KNX-Adapter installiert, dort wird richtigerweise 7,4 [m³] angezeigt. Also gehe ich davon aus, dass am Bus der richtige Wert verfügbar ist.

                                    Auf dem Bus liegt der Wert 0x40eccccd der interpretiert werden muss.
                                    7.4 lässt sich mit Float nicht exakt darstellen, der nächste Wert ist 7.400000095367431640625. Die ETS schneidet oder rundet vermutlich den Wert der Mantisse. Ich habe dazu aber keine Doku gefunden. In der Spec wird nur auf IEEE 754 Single Precision verwiesen.

                                    1 Antwort Letzte Antwort
                                    0
                                    • K killroy2

                                      Hallo @netfriend,

                                      eine Information zum Logging findest du zB im Readme auf NPM. Link dazu im Eingangspost.

                                      DPT 12.1200 wird bis Version 0.1.19 nicht unterstütz, nur sein Basistyp DPT12. Vom Konzept können alle Telegramme unabhängig vom DPT gesendet und empfangen werden. Wenn ein DPT nicht nativ unterstütz wird gibt es eine Logeintrag. In deinem Beispiel fehlt dir die Einheit als Metainformation, was keine gravierende Einschränkung sein dürfte. Alle DPTs zu unterstützen ist eine Sisyphusaufgabe und einige davon sind mir noch nicht untergekommen. Die Erstellung passiert nach und nach. Die von dir beschriebenen nehme ich ins nächste Release auf.
                                      Dass DPT 12.1200 bei dir nicht geht ist tatsächlich ein Fehler den ich bei mir reproduzieren konnte! Der Fehler ist im nächsten Release behoben.

                                      Bitte lass dich hier nicht durch unqualifizierte Falschaussagen von Projektunbeteiligten verwirren.

                                      T Offline
                                      T Offline
                                      tombox
                                      schrieb am zuletzt editiert von
                                      #233

                                      @killroy2

                                      Welche zusätzliche Informatione als

                                      Cannot read property 'current_value' of undefined
                                      (/opt/iobroker/node_modules/iobroker.openknx/main.js:505:64)
                                      
                                      

                                      brauchst du noch? Dürfen Projektunbeteiligten den undefined check einbauen?

                                      Warum ist es eine Sisyphusaufgabe, wenn die KNXUltimate Engine schon alle DPTs unterstützt. Warum fixst du Fehler und DPTs die in der Engine, auf die du Mitte 2022 wechseln, willst schon behoben sind? Du hast doch ganz klar gesagt deine Timeline ist fix.

                                      K 1 Antwort Letzte Antwort
                                      0
                                      • T tombox

                                        @killroy2

                                        Welche zusätzliche Informatione als

                                        Cannot read property 'current_value' of undefined
                                        (/opt/iobroker/node_modules/iobroker.openknx/main.js:505:64)
                                        
                                        

                                        brauchst du noch? Dürfen Projektunbeteiligten den undefined check einbauen?

                                        Warum ist es eine Sisyphusaufgabe, wenn die KNXUltimate Engine schon alle DPTs unterstützt. Warum fixst du Fehler und DPTs die in der Engine, auf die du Mitte 2022 wechseln, willst schon behoben sind? Du hast doch ganz klar gesagt deine Timeline ist fix.

                                        K Offline
                                        K Offline
                                        killroy2
                                        schrieb am zuletzt editiert von
                                        #234

                                        @tombox Nein, ich habe den Fehler nicht vollständig durchdrungen. Aber du wirst sicher die Güte haben uns zu erklären wie der Fix geht.

                                        T 1 Antwort Letzte Antwort
                                        0
                                        • K killroy2

                                          @tombox Nein, ich habe den Fehler nicht vollständig durchdrungen. Aber du wirst sicher die Güte haben uns zu erklären wie der Fix geht.

                                          T Offline
                                          T Offline
                                          tombox
                                          schrieb am zuletzt editiert von tombox
                                          #235

                                          @killroy2

                                          const dp = this.gaList.getDpById(id);
                                          if (!dp) {
                                           this.log.warn("Ignoring " + evt + " cannot find DP for id: " + id);
                                          //this.log.info("DP size:" + this.gaList.dp.size
                                          // add more log to show the current state of the adapter
                                          return
                                          }
                                          
                                          K 1 Antwort Letzte Antwort
                                          -1
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          715

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe