  4. Test Adapter Alarm 3.6.x
    apollon77A
alarmalarmanlagealarmsystem
1.4k Beiträge 111 Kommentatoren 802.8k Aufrufe 115 Beobachtet
  • A avhoboken
    Hi @blauholsten,
    You English is much better than my German :).
    The last test in my previous example was triggering the outside sensor for which I would expect that the burglar alarm is triggered. However it doesn't....
    As next try I removed the Notification checkbox for both sensors. When "Scharf innen" is set, it won't give a log entry anymore when the inside sensor is triggered (as expected) but still the same warnung message "Alarmanlage meldet eine Warnung, Veränderung bei: Outside sensor test" when the outside sensor is triggered instead of a burglar alarm.
    The Burglar alarm object is also not set.
    So it doesn't work as you describe in your feedback, what should I change in my configuration?
    cc3301a0-1e96-4385-8c02-1d02f4d94609-image.png 3ebd167f-6b1b-4ed8-a7bd-7ebcd37e1d23-image.png
    blauholstenB
    blauholstenB
    blauholsten
    #1007
    @avhoboken
    Hey,
    It works all correctly, I think 🤔. At your new example you received a message because the outside sensor is still in the "sharp inside" circuit. Your system was set in the sharp inside mode!
    Please try the same situation, but set the system in sharp mode before you trigger your outside Sensor. See what happens 😜
    - Alarm Adapter
    • blauholstenB blauholsten
      @avhoboken
      Hey,
      A
      A
      avhoboken
      #1008
      @blauholsten ,
      Well, in that case (setting sharp mode) I get off course a nice burglar alarm when either of the sensors is triggered.
      Probably I misunderstand the function of "sharp inside". but let's turnaround the question, with setting the system in "sharp inside" mode, can a burglar alarm be triggered and if so, how should the sensor than be configured. Because the way I've configured it now I only get the "changes warning" with no alarm triggers.
      blauholstenB 1 Antwort Letzte Antwort
      • A avhoboken
        @blauholsten ,
        blauholstenB
        blauholstenB
        blauholsten
        #1009
        @avhoboken
        Okay, now I understand that situation.
        During sharp inside, the system goes not to the burglary, you have under info. a few states that's signal the trigger.
        All other things you can also handle with shortcuts.
        - Alarm Adapter
          @avhoboken
          A
          A
          avhoboken
          #1010
          @blauholsten
          Perfect, thanks again for all your help and patience!
          • K
            K
            KabaKoenig
            #1011
            Hallo, Erstmal danke für das überragende Projekt.
            Ich Teste jetzt schon 2 Tage verschiede Szenarien. Ich möchte gerne erreichen, wenn z.b. meine Frau die Alarmanlage SCHARF-INTERN schaltet, die Eingangstüre Alarmverzögert ist. So das ich wenn ich später nach hause komme durch die Tür eintreten kann und dann die Anlage unscharf schalten kann. z.b.20sec bis zur Alarm Auslösung. Ist das Möglich? Bei Extern-Scharf funktioniert das. Aber bei intern-scharf bekomme ich das nicht hin. Mach ich ein Fehler?
            Liebe Grüße
            Timo
            • K KabaKoenig
              Liebe Grüße
              Timo
              blauholstenB
              blauholstenB
              blauholsten
              #1012
              @kabakoenig
              die Funktionsweise setzte ich gerade um, bitte ein paar Tage Geduld. Danke
              - Alarm Adapter
                @kabakoenig
                K
                K
                KabaKoenig
                #1013
                @blauholsten
                Vielen Dank. Ich finde das richtig prima wie hier einem geholfen wird. Auch ein riesiges Lob von mir, so ein Projekt zu stemmen. Und ich glaube man hat es auch nicht immer einfach. Aber auch die ganze Community richtig stark.
                • blauholstenB
                  blauholstenB
                  blauholsten
                  schrieb am zuletzt editiert von blauholsten
                  #1014
                  ich habe in letzter Zeit einige Stunden in die Weiterentwicklung gesteckt. Für die Version 3.x.x. die auf GitHub liegt, brauche ich dringend Tester! Ich habe eine relativ große Sache umgestellt, und bevor ich das für alle veröffentliche, muss dies getestet werden. Vielleicht werden einige die Änderung nicht so gut finden, aber ich denke es macht sinn:
                  Ab Version 3.x.x, habe ich mich dazu entschieden den Alarm auch bei scharf innen auszulösen! Das verändert die Funktion des Adapters ein wenig. Es wird jetzt zwischen Sirene intern und extern unterschieden, hierzu ist zu beachten, dass es den Datenpunkt info.sharp_inside_siren nicht mehr gibt. Diesen bitte ggf. manuell löschen! Der Datenpunkt wurde durch status.siren_inside ersetzt, und entspricht der Innensirene. Es ist zu beachten, dass das auch ggf. bei den Verknüpfungen neu einzustellen ist. Möchte man dies Aussensirene auch bei innen Alarm auslösen, kann man das in den allgemeinen Einstellungen tun. DANKE FÜR DAS VERSTÄNDNIS, ABER ICH DENKE SO IST ES LOGISCHER!
                  Danke für´s Feedback im Voraus!
                  - Alarm Adapter
                    K
                    K
                    KabaKoenig
                    #1015
                    @blauholsten
                    Vielen Dank für die Weiterentwicklung.
                    Habe heute morgen mal zeit gehabt zu testen.
                    was mir aufgefallen ist:
                    • Wenn ich intern scharf schalte, und es ist noch nicht alles geschlossen kommt zwar eine Meldung das noch was offen ist, aber die Anlage geht trotzdem scharf.... ist das so gewollt?
                    • Wenn ein intern Alarm ausgelöst wird geht sirne_inside und sirene auf true. wenn ich nun deaktiviere geht nur sirne_inside auf false und sirene bleibt auf true und lässt sich nicht deaktivieren.
                    • Bei der Alarmgreis ausgelöst wird gehen auch beide Sirenen state auf true und es läst sich intern_sirene bei Deaktivierung nicht zurücksetzen. also genau umgekehrt als oben.
                    Von der ganzen sache finde ich es so logischer wie es nun angedacht ist..... In normalen Alarmanlagen für Privathäuser gibt es in der Regel immer ein Gesammtscharf und ein Internscharf die wie du es nun umgesetzt hast programiert werden können.
                    Wenn mir noch was auffällt schreibe ich es.
                    Und herzlichen Dank für die mühe
                    blauholstenB 2 Antworten Letzte Antwort
                    • K KabaKoenig
                      @blauholsten
                      blauholstenB
                      blauholstenB
                      blauholsten
                      #1016
                      @kabakoenig sagte in Test Adapter Alarm 3.x.x:
                      Eigentlich ja. Wenn du intern aktivierst bist du ja Zuhause und kannst darauf reagieren. Sollte es dennoch bedarf geben, kann ich es eventuell in den nächsten Versionen einbauen.
                      Fehler gefunden, Versuche ich heute Abend zu beheben.
                      Super, vielen Dank
                      - Alarm Adapter
                      • D
                        D
                        DarkDevil
                        #1017
                        ich habe gerade auf die letzte stable Version 2.2.1 aktualisiert.
                        Was sind denn die "telegram special parameters"? Könnte ich damit für den telegramm Adapter einen Empfänger angeben?
                        Aktuell läuft der Alamadapter mit einer eigenen Telegram Instanz.
                        • D DarkDevil
                          blauholstenB
                          blauholstenB
                          blauholsten
                          #1018
                          @darkdevil
                          Ja, oder Gruppe etc...
                          - Alarm Adapter
                          • K KabaKoenig
                            @blauholsten
                            blauholstenB
                            blauholstenB
                            blauholsten
                            #1019
                            @kabakoenig
                            Bitte GitHub Version 3.0.1 testen.
                            - Alarm Adapter
                              @kabakoenig
                              K
                              K
                              KabaKoenig
                              #1020
                              @blauholsten
                              Danke für deine Arbeit!!!
                              Kam gerade dazu es zu testen...
                              • Es werden immer noch bei Alarmauslösung beide Sirenen auf true gesetzt egal ob intern oder Extern. Was sich aber geändert hat ist die Deaktivierung beide Sirenen werden auf false gesetzt.
                              Du möchtest bestimmt erreichen das wenn intern scharf ist und ausgelöst wird, nur Sirene Intern auf true geht?
                              Und bei Extern scharf nur die extern Sirene auf true geht?
                              • Der Schalter bei den Haupteinstellungen "Außen Sirene bei Einbruch scharf innen aktivieren" hat keine Änderung gezeigt.
                              • K KabaKoenig
                                @blauholsten
                                blauholstenB
                                blauholstenB
                                blauholsten
                                #1021
                                @kabakoenig
                                Danke für deine Tests! Kannst du bitte nochmal testen? Bitte NEU von Github installieren. Ich hoffe jetzt geht es, man verliert manchmal voller Code die Übersicht!
                                - Alarm Adapter
                                  @kabakoenig
                                  K
                                  K
                                  KabaKoenig
                                  #1022
                                  @blauholsten
                                  Servus,
                                  Habe gerade noch einmal ausführlich getestet.
                                  • Bei intern scharf wird bei Auslösung nun nur siren_inside auf true gesetzt. Das ist gut!
                                  • Bei Extern scharf werden beide siren auf true gesetzt. könnte man so lassen. Ich finde es gut!
                                  • Egal ob Intern oder Extern scharf, alarm_flash löst bei Alarm aus. Ist das so gewollt? mich stört das nicht.
                                  • Schalter Haupteinstellungen ( Außensirne bei Einbruch scharf innen aktivieren ) funktioniert. Finde das gut!
                                  • Schalter Haupteinstellungen ( Aktivieren beim verlassen des Countdowns ) hat bei mir nicht funktioniert . Soll die Alarmanlage auslösen wenn mit Zeitverzögerung scharfgeschaltet wird und in dieser verzögerung eine kontakt auf geht ? Oder vestehe ich das falsch?
                                  So finde ich den Alarmadapter richtig gut. Finde ihn so in der neuen Version verständlicher. Und ist so aufgebaut wie eine Normale Hardware-Alarmanlage. Nur mit viel mehr möglichkeiten.
                                  Vielen dank für die Mühe und der Umsetzung👍 👍 👍
                                  • K KabaKoenig
                                    @blauholsten
                                    Servus,
                                    blauholstenB
                                    blauholstenB
                                    blauholsten
                                    #1023
                                    @blauholsten
                                    Servus,
                                    Nochmal Danke👍
                                    Nein das war so nicht gewollt, habe es in der 3.0.2 analog der Sirene gemacht.
                                    Diese Option hat folgende Funktion: Wenn du z.B. bei deiner Haustür das Häkchen setzt, die Anlage mit Verzögerung aktivierst und dann die Haustür schließt, wird der Countdown beendet und die Anlage scharf geschalten.
                                    Wenn jetzt keine Fehler mehr entdeckt werden, würde ich die Version die Tage in "latest" übergeben.
                                    - Alarm Adapter
                                      @blauholsten
                                      Servus,
                                      Nochmal Danke👍
                                      K
                                      K
                                      KabaKoenig
                                      #1024
                                      @blauholsten
                                      Habe noch einmal getestet.
                                      • Was mir aufgefallen ist das der Datenpunkt "deactivted" nicht auf true geht wenn die Anlage scharf Extern war und Deaktiviert wurde. Der Datenpunkt geht erst auf true wenn intern scharf geschalten wird.
                                      Sonst ist mir nichts aufgefallen.
                                      Danke für das umsetzen!!!
                                      • K KabaKoenig
                                        @blauholsten
                                        blauholstenB
                                        blauholstenB
                                        blauholsten
                                        #1025
                                        @kabakoenig Hallo,
                                        war auch ein Fehler, der scheint aber schon länger bestanden zu haben!
                                        Ich habe diesen behoben und die Version 3.0.3 ins latest gepublished
                                        - Alarm Adapter
                                          @kabakoenig Hallo,
                                          K
                                          K
                                          KabaKoenig
                                          #1026
                                          @blauholsten
                                          Servus,
                                          Danke für die tolle Umsetzung.
                                          Mir ist doch noch was aufgefallen.
                                          • es werden immer noch beide Sirenen auf true geschalten wenn:
                                          1. Auf dem Rider uberwachung, bei Alarm Kreis und scharf intern ein Haken gemacht wird. Wenn ich dann z.b. intern scharf schalte, werden dann beide Sirenen auf true gesetzt. Wenn ich nun den Haken bei Alarm Kreis herausnehme, geht nur die interne Sirene.
                                          2. Wenn alarm Kreis scharf geschalten wird wird bei Auslösung egal was in der Überwachung angekreuzt ist beide Sirenen auf true gesetzt.
                                          Ich hoffe du verstehst was ich meine😁
                                          84.1k