Skip to content
  • Home
  • Aktuell
  • Tags
  • 0 Ungelesen 0
  • Kategorien
  • Unreplied
  • Beliebt
  • GitHub
  • Docu
  • Hilfe
Skins
  • Light
  • Brite
  • Cerulean
  • Cosmo
  • Flatly
  • Journal
  • Litera
  • Lumen
  • Lux
  • Materia
  • Minty
  • Morph
  • Pulse
  • Sandstone
  • Simplex
  • Sketchy
  • Spacelab
  • United
  • Yeti
  • Zephyr
  • Dark
  • Cyborg
  • Darkly
  • Quartz
  • Slate
  • Solar
  • Superhero
  • Vapor

  • Standard: (Kein Skin)
  • Kein Skin
Einklappen
ioBroker Logo

Community Forum

donate donate
  1. ioBroker Community Home
  2. Deutsch
  3. ioBroker Allgemein
  4. Modbus adapter

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.7k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.2k

Modbus adapter

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
modbus adaptermodbus
981 Beiträge 141 Kommentatoren 385.4k Aufrufe 64 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • BluefoxB Offline
    BluefoxB Offline
    Bluefox
    schrieb am zuletzt editiert von
    #193

    Paypal ist einfacher. Ich werde dann gleich bestellen.

    1 Antwort Letzte Antwort
    0
    • wendy2702W Online
      wendy2702W Online
      wendy2702
      schrieb am zuletzt editiert von
      #194

      @Bluefox:

      Paypal ist einfacher. Ich werde dann gleich bestellen. `
      Solltest schon was bekommen haben.

      Gruß

      Mirko

      Gesendet von iPhone mit Tapatalk

      Bitte keine Fragen per PN, die gehören ins Forum!

      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

      1 Antwort Letzte Antwort
      0
      • BluefoxB Offline
        BluefoxB Offline
        Bluefox
        schrieb am zuletzt editiert von
        #195

        Habe bestellt. Danke :P

        1 Antwort Letzte Antwort
        0
        • E Offline
          E Offline
          enricoh831
          schrieb am zuletzt editiert von
          #196

          So hab auch noch was zu gepackt…Hoffe am Wochenende läuft das denn endlich [emoji23] [emoji23] [emoji23]

          Gesendet von meinem Pixel mit Tapatalk

          1 Antwort Letzte Antwort
          0
          • wendy2702W Online
            wendy2702W Online
            wendy2702
            schrieb am zuletzt editiert von
            #197

            Hi,

            kannst mir einer von euch bei mbusd <-> Iobroker helfen? Also im Prinzip bei RTU over TCP?

            Ich habe auf einem zusätzlichen PI mbusd installiert und in iobroker einen weiteren Modbus Adapter so konfiguriert:

            999_modbus1.jpg

            Mbusd habe ich so gestartet:

             mbusd -v 2 -p /dev/ttyUSB0 -s 9600 -m 8N1 -P 502
            

            In meinem Zähler sehe ich wenn der Modbus Adapter läuft auch das Kommunikations Symbol aber ich bekomme einfach keine Werte.

            Im iobroker log kommt das:

            inMem	2017-01-19 12:00:55.827	debug	message modbus.1.* modbus.1.info.pollTime val=301, ack=true, ts=1484823655827, q=0, from=system.adapter.modbus.1, lc=1484823655827
            inMem	2017-01-19 12:00:55.827	debug	message modbus.1.* modbus.1.holdingRegisters.544_Strom_L1 val=, ack=true, ts=1484823655819, q=0, from=system.adapter.modbus.1, lc=1484823655819
            inMem	2017-01-19 12:00:55.525	debug	message modbus.1.* modbus.1.info.connection val=true, ack=true, ts=1484823655521, q=0, from=system.adapter.modbus.1, lc=1484823655521
            modbus.1	2017-01-19 12:00:55.518	info	Connected to slave 192.168.178.67
            modbus.1	2017-01-19 12:00:55.409	info	starting. Version 0.4.7 in /opt/iobroker/node_modules/iobroker.modbus, node: v4.7.2
            modbus.1	2017-01-19 12:00:55.398	debug	statesDB connected
            modbus.1	2017-01-19 12:00:55.387	debug	objectDB connected
            

            Ich weiß nicht was ich zum Auslesen der Holding register eintragen muss.

            Als ich den Zähler mit USB/RS-485 Adapter an meinem WIN7 PC hatte konnte ich die Uhrzeit z.B. mit diesen Einstellungen auslesen:

            999_rmms.jpg

            Im Modbus Adapter muss aber noch ein Eintrag bei "Typ" bei den Registern erfolgen und da habe ich keine Idee was ich auswählen muss.

            Habt ihr vielleicht eine Idee?

            Anbei die Modbus Beschreibung des Zählers den ich gerne auslesen möchte.

            999_diz-g_modbus-beschreibung-version-109_index01.pdf

            Danke und Gruß

            Bitte keine Fragen per PN, die gehören ins Forum!

            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

            1 Antwort Letzte Antwort
            0
            • wendy2702W Online
              wendy2702W Online
              wendy2702
              schrieb am zuletzt editiert von
              #198

              Ich hab es rausbekommen.

              So funktioniert es:

              999_register_settings.jpg

              999_objekte.jpg

              Gruß

              Bitte keine Fragen per PN, die gehören ins Forum!

              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

              1 Antwort Letzte Antwort
              0
              • T Offline
                T Offline
                ThomasD
                schrieb am zuletzt editiert von
                #199

                Hallo,

                erst mal nur auf die schnelle, in der Beschreibung sind die Adressen in Hex, im IOBroker brauchst du sie dezimal.

                In deinen Beispiel FE34 Datum/Uhrzeit entspricht Adresse 65076.

                Die Netzfrequenz sollte demnach bei Adresse 653 als float angezeigt werden.

                Sollte es noch nicht funktionieren melde dich noch einmal.

                Schöne Grüße

                ThomasD

                1 Antwort Letzte Antwort
                0
                • P Offline
                  P Offline
                  peet
                  schrieb am zuletzt editiert von
                  #200

                  Hallo zusammen,

                  vielen Dank an alle die an ioBroker aktiv mitwirken, sieht sehr spannend aus.

                  Ich möchte mein Haus mit einer Wago PFC100 750-8100 steuern, übergeordnet soll IOBroker über Modbus TCP mit der Wago kommunizieren.

                  Ich habe bereits erfolgreich testweise ein Ausgang schalten können aber es läuft noch nicht so wie ich es mir vorstelle.

                  Die Buttons werden über diskrete Ausgänge gesendet und Schalten indirekt die Ausgänge. Nun möchte ich den status der Ausgänge abfragen das gelingt mir nur über Eingangsregister. Ich würde aber stattdessen Diskrete Eingänge (also binär) verwenden.

                  In der Wago habe ich verschiedene Einstellungen versucht, die schlägt mir dann auch Adressen vor z.B. wenn Variable RW als Coil deklariert ist, wird Adresse >=32768 vorgeschlagen, als RO wird >= 0 vorgeschlagen. Mit den diskreten Ausgängen und Register klappt das auch wunderbar.

                  Könnt ihr mir bitte sagen was ich wo wie genau eintragen muss? Danke.

                  Anbei als Screenshots meine Einstellungen:
                  1921_bildschirmfoto_2017-01-21_um_00.37.38.png
                  1921_bildschirmfoto_2017-01-21_um_00.37.55.png
                  1921_bildschirmfoto_2017-01-21_um_00.38.05.png

                  Und ein Auszug aus dem Wago Handbuch:
                  1921_bildschirmfoto_2017-01-20_um_23.22.49.png

                  1 Antwort Letzte Antwort
                  0
                  • C Offline
                    C Offline
                    Christian L.
                    schrieb am zuletzt editiert von
                    #201

                    Hallo ich habe auch meine Steuerung auf einer Industrie Modbus Variante aufgebaut.

                    Möchte nun auch die den I/O Broker nach und nach einführen.

                    Welcher Abfragezyklus ist damit möglich?

                    Ich muss 6 32bit Register oder 12 16bit Register auslesen.

                    1 Antwort Letzte Antwort
                    0
                    • BluefoxB Offline
                      BluefoxB Offline
                      Bluefox
                      schrieb am zuletzt editiert von
                      #202

                      @Christian L.:

                      Hallo ich habe auch meine Steuerung auf einer Industrie Modbus Variante aufgebaut.

                      Möchte nun auch die den I/O Broker nach und nach einführen.

                      Welcher Abfragezyklus ist damit möglich? `
                      Hängt von deinem Rechner ab und natürlich von deiner Steuerung.

                      Sollte empirisch ermittelt werden. Ich kann mir gut vorstellen, dass IoB auf dem PC auch 50ms schaffen kann. (Bei deiner Menge)

                      1 Antwort Letzte Antwort
                      0
                      • BluefoxB Offline
                        BluefoxB Offline
                        Bluefox
                        schrieb am zuletzt editiert von
                        #203

                        @peet:

                        Hallo zusammen,

                        vielen Dank an alle die an ioBroker aktiv mitwirken, sieht sehr spannend aus.

                        Ich möchte mein Haus mit einer Wago PFC100 750-8100 steuern, übergeordnet soll IOBroker über Modbus TCP mit der Wago kommunizieren.

                        Ich habe bereits erfolgreich testweise ein Ausgang schalten können aber es läuft noch nicht so wie ich es mir vorstelle.

                        Die Buttons werden über diskrete Ausgänge gesendet und Schalten indirekt die Ausgänge. Nun möchte ich den status der Ausgänge abfragen das gelingt mir nur über Eingangsregister. Ich würde aber stattdessen Diskrete Eingänge (also binär) verwenden.

                        In der Wago habe ich verschiedene Einstellungen versucht, die schlägt mir dann auch Adressen vor z.B. wenn Variable RW als Coil deklariert ist, wird Adresse >=32768 vorgeschlagen, als RO wird >= 0 vorgeschlagen. Mit den diskreten Ausgängen und Register klappt das auch wunderbar.

                        Könnt ihr mir bitte sagen was ich wo wie genau eintragen muss? Danke.

                        Anbei als Screenshots meine Einstellungen:

                        Bildschirmfoto 2017-01-21 um 00.37.38.png

                        Bildschirmfoto 2017-01-21 um 00.37.55.png

                        Bildschirmfoto 2017-01-21 um 00.38.05.png

                        Und ein Auszug aus dem Wago Handbuch:

                        Bildschirmfoto 2017-01-20 um 23.22.49.png `

                        WER hat schon WAGO im Betrieb??

                        Geht das? Kann jemand How-To erstellen? Ich warte immer noch auf meinem Slave. Und es wird kein WAGO sein.

                        Bitte Wissen teilen. :D

                        1 Antwort Letzte Antwort
                        0
                        • C Offline
                          C Offline
                          Christian L.
                          schrieb am zuletzt editiert von
                          #204

                          Auf was für einen Slave wartest du den?

                          1 Antwort Letzte Antwort
                          0
                          • BluefoxB Offline
                            BluefoxB Offline
                            Bluefox
                            schrieb am zuletzt editiert von
                            #205

                            @Christian L.:

                            Auf was für einen Slave wartest du den? `
                            http://www.ebay.de/itm/291616203435?_tr … EBIDX%3AIT

                            1 Antwort Letzte Antwort
                            0
                            • P Offline
                              P Offline
                              peet
                              schrieb am zuletzt editiert von
                              #206

                              also ich habe jetzt ein HUB und Wireshark bersorgt. Leider werde ich daraus immer noch nicht schlau.

                              Egal wo ich was in der Variable steuer, es wird immer das gleiche gesendet.

                              Auszug Wireshark:
                              1921_bildschirmfoto_2017-01-27_um_23.40.39.png

                              Einstellung IOBroker:
                              1921_bildschirmfoto_2017-01-27_um_23.41.07.png

                              Einstellung Wago:
                              1921_bildschirmfoto_2017-01-27_um_23.47.15.png

                              Hat jemand eine Idee? Bitte um Hilfe.

                              Vielen Dank im voraus.

                              1 Antwort Letzte Antwort
                              0
                              • P Offline
                                P Offline
                                peet
                                schrieb am zuletzt editiert von
                                #207

                                Ok das Problem mit den diskreten Eingängen hat sich erledigt. Ich verstehe zwar nich warum aber nachdem ich mit verschiedenen höheren Zahlen probiert habe, klappt das jetzt.

                                Haut jetzt alles wie es soll hin.

                                1 Antwort Letzte Antwort
                                0
                                • Y Offline
                                  Y Offline
                                  ykuendig
                                  schrieb am zuletzt editiert von
                                  #208

                                  @wendy2702:

                                  OK.

                                  Nach dem ersten starten das ich das Device auswählen.

                                  Modbus_RTU_Device.JPG

                                  Wenn ich das gemacht habe, Speicher und beende kommt das im log:

                                  ! ````
                                  host.openmediavault 2017-01-17 14:55:27.723 info Restart adapter system.adapter.modbus.1 because enabled
                                  host.openmediavault 2017-01-17 14:55:27.723 error instance system.adapter.modbus.1 terminated with code 0 (OK)
                                  modbus.1 2017-01-17 14:55:27.715 info terminating
                                  modbus.1 2017-01-17 14:55:27.695 error at Socket.Emitter.emit (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-emitter/index.js:133:20)
                                  modbus.1 2017-01-17 14:55:27.695 error at Socket. (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-bind/index.js:21:15)
                                  modbus.1 2017-01-17 14:55:27.695 error at Manager.ondata (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/lib/manager.js:322:16)
                                  modbus.1 2017-01-17 14:55:27.695 error at Decoder.add (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/socket.io-parser/index.js:246:12)
                                  modbus.1 2017-01-17 14:55:27.695 error at Decoder.Emitter.emit (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/socket.io-parser/node_modules/component-emitter/index.js:134:20)
                                  modbus.1 2017-01-17 14:55:27.695 error at Decoder. (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-bind/index.js:21:15)
                                  modbus.1 2017-01-17 14:55:27.695 error at Manager.ondecoded (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/lib/manager.js:332:8)
                                  modbus.1 2017-01-17 14:55:27.695 error at Manager.Emitter.emit (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-emitter/index.js:133:20)
                                  modbus.1 2017-01-17 14:55:27.695 error at Manager. (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-bind/index.js:21:15)
                                  modbus.1 2017-01-17 14:55:27.695 error at Socket.onpacket (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/lib/socket.js:236:12)
                                  modbus.1 2017-01-17 14:55:27.695 error at Socket.onack (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/lib/socket.js:312:9)
                                  modbus.1 2017-01-17 14:55:27.695 error at Socket. (/opt/iobroker/node_modules/iobroker.js-controller/lib/adapter.js:1253:35)
                                  modbus.1 2017-01-17 14:55:27.695 error at /opt/iobroker/node_modules/iobroker.js-controller/lib/adapter.js:1365:21
                                  modbus.1 2017-01-17 14:55:27.695 error at /opt/iobroker/node_modules/iobroker.modbus/main.js:1332:13
                                  modbus.1 2017-01-17 14:55:27.695 error at clear (/opt/iobroker/node_modules/iobroker.modbus/main.js:1328:22)
                                  modbus.1 2017-01-17 14:55:27.695 error at Object.main.start (/opt/iobroker/node_modules/iobroker.modbus/main.js:1740:25)
                                  modbus.1 2017-01-17 14:55:27.695 error TypeError: Cannot read property 'on' of null
                                  modbus.1 2017-01-17 14:55:27.694 error uncaught exception: Cannot read property 'on' of null
                                  modbus.1 2017-01-17 14:55:27.693 error Cannot open port "/dev/ttyUSB1" [9600]: TypeError: Cannot read property 'complete' of undefined

                                  >! Ich weiß nur nicht warum der Port nicht geöffnet werden kann.
                                  >! Und wenn ich jetzt die Instanz wieder öffne, ist der Port Eintrag wieder weg bzw. nicht mehr sichtbar.
                                  >! Im Log kommt ständig:
                                  >! ````
                                  openmediavault	2017-01-17 15:07:07.966	info	host.openmediavault Restart adapter system.adapter.modbus.1 because enabled
                                  openmediavault	2017-01-17 15:07:07.966	error	host.openmediavault instance system.adapter.modbus.1 terminated with code 0 (OK)
                                  modbus.1	2017-01-17 15:07:07.939	error	modbus.1 TypeError: Cannot read property 'on' of null at Object.main.start (/opt/iobroker/node_modules/iobroker.modbus/main.js:1740:25) at clear (/opt/iobroker/node_modules/iobroker.modbus/mai
                                  modbus.1	2017-01-17 15:07:07.939	error	modbus.1 uncaught exception: Cannot read property 'on' of null
                                  modbus.1	2017-01-17 15:07:07.937	error	modbus.1 Cannot open port "/dev/ttyUSB1" [9600]: TypeError: Cannot read property 'complete' of undefined
                                  

                                  Mal alle USB Devices abgezogen und nur den USB-RS485 Adapter angeschlossen.

                                  Dann sehe ich das der ttyUSB0 wird. Aber auch wenn ich den als Port auswähle kommt die gleiche Fehlermeldung. `

                                  Ich habe das gleiche Problem.

                                  mein Log sieht so aus:

                                  `host.raspi3	2017-02-01 01:46:15.092	info	Do not restart adapter system.adapter.modbus.0 because disabled or deleted
                                  host.raspi3	2017-02-01 01:46:15.084	error	instance system.adapter.modbus.0 terminated with code 3 (Adapter disabled or invalid config)
                                  host.raspi3	2017-02-01 01:45:50.362	info	"system.adapter.modbus.0" disabled
                                  host.raspi3	2017-02-01 01:45:50.361	info	object change system.adapter.modbus.0
                                  host.raspi3	2017-02-01 01:45:49.076	info	instance system.adapter.javascript.0 terminated with code 0 (OK)
                                  javascript.0	2017-02-01 01:45:49.016	info	Adapter is disabled => stop
                                  host.raspi3	2017-02-01 01:45:48.993	info	stopInstance system.adapter.javascript.0 killing pid 30477
                                  host.raspi3	2017-02-01 01:45:48.992	info	stopInstance system.adapter.javascript.0
                                  host.raspi3	2017-02-01 01:45:48.988	info	"system.adapter.javascript.0" disabled
                                  host.raspi3	2017-02-01 01:45:48.987	info	object change system.adapter.javascript.0
                                  host.raspi3	2017-02-01 01:45:41.861	info	Restart adapter system.adapter.modbus.0 because enabled
                                  host.raspi3	2017-02-01 01:45:41.860	error	instance system.adapter.modbus.0 terminated with code 0 (OK)
                                  modbus.0	2017-02-01 01:45:41.795	info	terminating
                                  modbus.0	2017-02-01 01:45:41.750	error	at Socket.Emitter.emit (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-emitter/index.js:133:20)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Socket. (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-bind/index.js:21:15)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Manager.ondata (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/lib/manager.js:322:16)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Decoder.add (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/socket.io-parser/index.js:246:12)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Decoder.Emitter.emit (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/socket.io-parser/node_modules/component-emitter/index.js:134:20)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Decoder. (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-bind/index.js:21:15)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Manager.ondecoded (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/lib/manager.js:332:8)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Manager.Emitter.emit (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-emitter/index.js:133:20)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Manager. (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/node_modules/component-bind/index.js:21:15)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Socket.onpacket (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/lib/socket.js:236:12)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Socket.onack (/opt/iobroker/node_modules/iobroker.js-controller/node_modules/socket.io-client/lib/socket.js:312:9)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Socket. (/opt/iobroker/node_modules/iobroker.js-controller/lib/adapter.js:1253:35)
                                  modbus.0	2017-02-01 01:45:41.750	error	at /opt/iobroker/node_modules/iobroker.js-controller/lib/adapter.js:1365:21
                                  modbus.0	2017-02-01 01:45:41.750	error	at /opt/iobroker/node_modules/iobroker.modbus/main.js:1332:13
                                  modbus.0	2017-02-01 01:45:41.750	error	at clear (/opt/iobroker/node_modules/iobroker.modbus/main.js:1328:22)
                                  modbus.0	2017-02-01 01:45:41.750	error	at Object.main.start (/opt/iobroker/node_modules/iobroker.modbus/main.js:1740:25)
                                  modbus.0	2017-02-01 01:45:41.750	error	TypeError: Cannot read property 'on' of null
                                  modbus.0	2017-02-01 01:45:41.736	error	uncaught exception: Cannot read property 'on' of null
                                  modbus.0	2017-02-01 01:45:41.720	error	Cannot open port "/dev/ttyUSB0" [9600]: TypeError: Cannot read property 'complete' of undefined
                                  modbus.0	2017-02-01 01:45:40.406	info	starting. Version 0.4.7 in /opt/iobroker/node_modules/iobroker.modbus, node: v4.7.2
                                  ...
                                  ...
                                  modbus.0	2017-02-01 01:44:25.958	info	List of port: [{"comName":"/dev/ttyAMA0"},{"comName":"/dev/ttyUSB0","manufacturer":"FTDI","serialNumber":"FTDI_FT232R_USB_UART_A603O55Y","pnpId":"usb-FTDI_FT232R_USB_UART_A603O55Y-if00-port0","vendor[/code]`
                                  
                                  Der rs-485 Adapter stammt aus dem Laden mit dem blauen C.
                                  
                                  Wie kann ich  mich nützlich machen, damit das Problem behoben werden kann?
                                  

                                  Gruss Yves

                                  1 Antwort Letzte Antwort
                                  0
                                  • wendy2702W Online
                                    wendy2702W Online
                                    wendy2702
                                    schrieb am zuletzt editiert von
                                    #209

                                    Bluefox wollte sich die Hardware besorgen und dann untersuchen. Glaube bis dahin können wir nicht viel machen außer einen Workaround zu nutzen.

                                    Gesendet von iPhone mit Tapatalk Pro

                                    Bitte keine Fragen per PN, die gehören ins Forum!

                                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                    1 Antwort Letzte Antwort
                                    0
                                    • wendy2702W Online
                                      wendy2702W Online
                                      wendy2702
                                      schrieb am zuletzt editiert von
                                      #210

                                      Ich habe mir das auf einem PI installiert

                                      http://mbus.sourceforge.net

                                      Den USB-RS485 Adapter an den pi und das dann über den iobroker Modbus Adapter per TCP angesprochen.

                                      Gesendet von iPhone mit Tapatalk Pro

                                      Bitte keine Fragen per PN, die gehören ins Forum!

                                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                      1 Antwort Letzte Antwort
                                      0
                                      • Y Offline
                                        Y Offline
                                        ykuendig
                                        schrieb am zuletzt editiert von
                                        #211

                                        Aha; verstehe die Idee. Muss ich am Abend testen…

                                        Ich könnte auch vom pi die Daten an node-red senden oder per js vom alten python crawler pollen.

                                        Ist eh etwas trickig, da ich 2 modbus Zähler hab. Das lässt sich aktuell noch nicht mit dem Adapter instanzieren.

                                        Mal sehen wie's weiter geht. Habe nun gesehen, das auch schon ein SmartMeter Adapter gibt. :o

                                        Wenn der Modbus könnte ! oder man die zwei linken kann ... -> Es hört nie auf :lol:

                                        Gruss Yves

                                        1 Antwort Letzte Antwort
                                        0
                                        • wendy2702W Online
                                          wendy2702W Online
                                          wendy2702
                                          schrieb am zuletzt editiert von
                                          #212

                                          Du kannst doch auch zwei Modbus Adapter installieren

                                          Gesendet von iPhone mit Tapatalk Pro

                                          Bitte keine Fragen per PN, die gehören ins Forum!

                                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          756

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe