  4. FoxEss H3 Wechselrichter per Modbus in ioBroker

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.8k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.2k

FoxEss H3 Wechselrichter per Modbus in ioBroker

Geplant Angeheftet Gesperrt Verschoben Hardware
55 Beiträge 18 Kommentatoren 13.3k Aufrufe 15 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • R Rogni

    @homoran okay, Fehler von mir, ich hab alles unter Holding Register. kann ich die irgendwie rüberkopieren oder muß ich alle in per Hand in Eingangsregister eintragen?? Nochmal Danke, Hammer Antwortzeit !!! kann ich Dir dateien schicken?? Da ich unterschrieben habe das nicht zu veröffentlichen ;) Firmware is ne gute Frage.. Register hab ich nur mal ein paar der angegeben eingetragen, sonst kommen da ja Fehler ohne Ende.

    Dev ID ist die Geräte ID 247 (die muss auch so da stehen)

    TCP/serielle = TCP
    Mode = Master
    Slave Adresse = IP Adresse vom EW11
    Port = 502
    Geräte ID = 247
    Register. Max Leseanforderungslänge (Booleans) 128
    Register Unveränderte Zustände aktualisieren 100

    Zahlen runden auf 2
    Zeiten Datenabfrageintervall

    Zyklisches Abfrageintervall in Millisekunden (Nur relevant für Master) = 1500
    Wartezeit bis zum erneuten Verbinden 60000 ms

    Timeout für Leseanfragen in Millisekunden. Erfolgt innerhalb dieser Zeit keine Antwort von einem Slave, wird die Verbindung abgebrochen.
    Wartezeit Lesend= 60000 ms

    Wenn Impulse für Spulen verwendet werden, definiert dies das Intervall in Millisekunden, wie lang der Impuls ist.
    Impulszeit= 1000ms

    Wartezeit zwischen der Abfrage zweier unterschiedlicher Geräte-IDs in Millisekunden.
    Wartezeit = 50 ms

    Verzögerung zwischen zwei Leseanforderungen in Millisekunden. Standard 0.
    Leseintercall= 2 ms
    Schreibintervall = 0 ms

    Verzögerung zwischen zwei Schreibanforderungen in Millisekunden. Standard 0.
    Sonstige
    Protokollierung von Verbindungsfehlern deaktivieren

    Nix angekreuzt

    Ich habe 2 verschiedene PDF von Fox bekommen. Die eingetragenen aus dem "alten" Dokument funktionieren auch soweit alle. Mir fehlr da nur die Angabe von Meter (Chint). deswegen hatte ich Fox nochmal angeschrieben. in diesem Dokument sind die Register wieder ganz andere und der Teil den ich da abfrage funzt auch net.
    hier nochmal der Debug:

    modbus.0
    	2025-11-12 12:15:34.551	info	terminating
    modbus.0
    	2025-11-12 12:15:34.394	debug	Cleaning up request fifo.
    modbus.0
    	2025-11-12 12:15:34.394	debug	Clearing timeout of the current request.
    modbus.0
    	2025-11-12 12:15:34.393	debug	Socket closed
    modbus.0
    	2025-11-12 12:15:34.116	info	State value to set for "modbus.0.info.connection" has to be type "boolean" but received type "string"
    modbus.0
    	2025-11-12 12:15:34.076	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
    modbus.0
    	2025-11-12 12:15:34.076	debug	Plugin sentry destroyed
    modbus.0
    	2025-11-12 12:15:34.075	info	terminating
    modbus.0
    	2025-11-12 12:15:34.049	debug	Closing client on purpose.
    modbus.0
    	2025-11-12 12:15:34.047	info	Got terminate signal TERMINATE_YOURSELF
    modbus.0
    	2025-11-12 12:15:32.022	debug	[DevID_247/holdingRegs] Poll address 36148 - 2 registers
    modbus.0
    	2025-11-12 12:15:32.018	warn	[DevID_247/holdingRegs] Block 36132-36133: {}
    modbus.0
    	2025-11-12 12:15:32.017	debug	Received pdu describes an error.
    modbus.0
    	2025-11-12 12:15:28.151	debug	[DevID_247/holdingRegs] Poll address 36132 - 2 registers
    modbus.0
    	2025-11-12 12:15:28.147	warn	[DevID_247/holdingRegs] Block 36116-36117: {}
    modbus.0
    	2025-11-12 12:15:28.146	debug	Received pdu describes an error.
    modbus.0
    	2025-11-12 12:15:28.051	debug	[DevID_247/holdingRegs] Poll address 36116 - 2 registers
    modbus.0
    	2025-11-12 12:15:28.039	debug	[DevID_247/holdingRegs/32023] Calculation result = 6.7, type = number
    modbus.0
    	2025-11-12 12:15:28.039	debug	[DevID_247/holdingRegs/32023] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.039	debug	[DevID_247/holdingRegs/32023] Input Value = 67
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32021] Calculation result = 11696.2, type = number
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32021] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32021] Input Value = 116962
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32020] Calculation result = 0.1, type = number
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32020] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32020] Input Value = 1
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32018] Calculation result = 102, type = number
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32018] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.038	debug	[DevID_247/holdingRegs/32018] Input Value = 1020
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32017] Calculation result = 3.5, type = number
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32017] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32017] Input Value = 35
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32015] Calculation result = 15521.2, type = number
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32015] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32015] Input Value = 155212
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32014] Calculation result = 3.3000000000000003, type = number
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32014] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32014] Input Value = 33
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32012] Calculation result = 3473.3, type = number
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32012] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32012] Input Value = 34733
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32011] Calculation result = 0, type = number
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32011] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32011] Input Value = 0
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32009] Calculation result = 7047.400000000001, type = number
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32009] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.037	debug	[DevID_247/holdingRegs/32009] Input Value = 70474
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32008] Calculation result = 1.9000000000000001, type = number
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32008] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32008] Input Value = 19
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32006] Calculation result = 4532.8, type = number
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32006] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32006] Input Value = 45328
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32005] Calculation result = 6.2, type = number
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32005] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32005] Input Value = 62
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32003] Calculation result = 473.59000000000003, type = number
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32003] Formula = x*0.01
    modbus.0
    	2025-11-12 12:15:28.036	debug	[DevID_247/holdingRegs/32003] Input Value = 47359
    modbus.0
    	2025-11-12 12:15:28.034	debug	[DevID_247/holdingRegs/32002] Calculation result = 9.1, type = number
    modbus.0
    	2025-11-12 12:15:28.034	debug	[DevID_247/holdingRegs/32002] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:28.034	debug	[DevID_247/holdingRegs/32002] Input Value = 91
    modbus.0
    	2025-11-12 12:15:28.034	debug	[DevID_247/holdingRegs/32000] Calculation result = 17.9574, type = number
    modbus.0
    	2025-11-12 12:15:28.034	debug	[DevID_247/holdingRegs/32000] Formula = x*0.0001
    modbus.0
    	2025-11-12 12:15:28.034	debug	[DevID_247/holdingRegs/32000] Input Value = 179574
    modbus.0
    	2025-11-12 12:15:28.034	debug	[DevID_247/holdingRegs] Poll address 32000 DONE
    modbus.0
    	2025-11-12 12:15:27.882	debug	[DevID_247/holdingRegs] Poll address 32000 - 24 registers
    modbus.0
    	2025-11-12 12:15:27.869	debug	[DevID_247/holdingRegs/31037] Calculation result = 28, type = number
    modbus.0
    	2025-11-12 12:15:27.869	debug	[DevID_247/holdingRegs/31037] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.869	debug	[DevID_247/holdingRegs/31037] Input Value = 280
    modbus.0
    	2025-11-12 12:15:27.869	debug	[DevID_247/holdingRegs/31034] Calculation result = 242.60000000000002, type = number
    modbus.0
    	2025-11-12 12:15:27.868	debug	[DevID_247/holdingRegs/31034] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.868	debug	[DevID_247/holdingRegs/31034] Input Value = 2426
    modbus.0
    	2025-11-12 12:15:27.868	debug	[DevID_247/holdingRegs/31033] Calculation result = 55.6, type = number
    modbus.0
    	2025-11-12 12:15:27.868	debug	[DevID_247/holdingRegs/31033] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.868	debug	[DevID_247/holdingRegs/31033] Input Value = 556
    modbus.0
    	2025-11-12 12:15:27.868	debug	[DevID_247/holdingRegs/31032] Calculation result = 43, type = number
    modbus.0
    	2025-11-12 12:15:27.868	debug	[DevID_247/holdingRegs/31032] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.868	debug	[DevID_247/holdingRegs/31032] Input Value = 430
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31025] Calculation result = 50, type = number
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31025] Formula = x*0.01
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31025] Input Value = 5000
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31021] Calculation result = 0.30000000000000004, type = number
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31021] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31021] Input Value = 3
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31020] Calculation result = 0.4, type = number
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31020] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.867	debug	[DevID_247/holdingRegs/31020] Input Value = 4
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31019] Calculation result = 0.30000000000000004, type = number
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31019] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31019] Input Value = 3
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31018] Calculation result = 237.3, type = number
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31018] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31018] Input Value = 2373
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31017] Calculation result = 235.3, type = number
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31017] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.866	debug	[DevID_247/holdingRegs/31017] Input Value = 2353
    modbus.0
    	2025-11-12 12:15:27.865	debug	[DevID_247/holdingRegs/31016] Calculation result = 234, type = number
    modbus.0
    	2025-11-12 12:15:27.865	debug	[DevID_247/holdingRegs/31016] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.865	debug	[DevID_247/holdingRegs/31016] Input Value = 2340
    modbus.0
    	2025-11-12 12:15:27.865	debug	[DevID_247/holdingRegs/31015] Calculation result = 50, type = number
    modbus.0
    	2025-11-12 12:15:27.865	debug	[DevID_247/holdingRegs/31015] Formula = x*0.01
    modbus.0
    	2025-11-12 12:15:27.865	debug	[DevID_247/holdingRegs/31015] Input Value = 5000
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31011] Calculation result = 1.4000000000000001, type = number
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31011] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31011] Input Value = 14
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31010] Calculation result = 1.4000000000000001, type = number
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31010] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31010] Input Value = 14
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31009] Calculation result = 1.4000000000000001, type = number
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31009] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31009] Input Value = 14
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31008] Calculation result = 236.60000000000002, type = number
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31008] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31008] Input Value = 2366
    modbus.0
    	2025-11-12 12:15:27.864	debug	[DevID_247/holdingRegs/31007] Calculation result = 235.70000000000002, type = number
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31007] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31007] Input Value = 2357
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31006] Calculation result = 235.3, type = number
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31006] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31006] Input Value = 2353
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31004] Calculation result = 6.300000000000001, type = number
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31004] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31004] Input Value = 63
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31003] Calculation result = 379.8, type = number
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31003] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.863	debug	[DevID_247/holdingRegs/31003] Input Value = 3798
    modbus.0
    	2025-11-12 12:15:27.862	debug	[DevID_247/holdingRegs/31001] Calculation result = 1.3, type = number
    modbus.0
    	2025-11-12 12:15:27.862	debug	[DevID_247/holdingRegs/31001] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.862	debug	[DevID_247/holdingRegs/31001] Input Value = 13
    modbus.0
    	2025-11-12 12:15:27.862	debug	[DevID_247/holdingRegs/31000] Calculation result = 387.70000000000005, type = number
    modbus.0
    	2025-11-12 12:15:27.862	debug	[DevID_247/holdingRegs/31000] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:27.862	debug	[DevID_247/holdingRegs/31000] Input Value = 3877
    modbus.0
    	2025-11-12 12:15:27.862	debug	[DevID_247/holdingRegs] Poll address 31000 DONE
    modbus.0
    	2025-11-12 12:15:27.676	debug	[DevID_247/holdingRegs] Poll address 31000 - 43 registers
    modbus.0
    	2025-11-12 12:15:27.676	debug	[DevID_247] Poll start ---------------------
    modbus.0
    	2025-11-12 12:15:26.123	debug	[DevID_247/holdingRegs] Poll address 41000 DONE
    modbus.0
    	2025-11-12 12:15:26.037	debug	[DevID_247/holdingRegs] Poll address 41000 - 1 registers
    modbus.0
    	2025-11-12 12:15:26.035	warn	[DevID_247/holdingRegs] Block 38801-38819: {}
    modbus.0
    	2025-11-12 12:15:26.035	debug	Received pdu describes an error.
    modbus.0
    	2025-11-12 12:15:25.953	debug	[DevID_247/holdingRegs] Poll address 38801 - 19 registers
    modbus.0
    	2025-11-12 12:15:25.950	warn	[DevID_247/holdingRegs] Block 36200-36201: {}
    modbus.0
    	2025-11-12 12:15:25.950	debug	Received pdu describes an error.
    modbus.0
    	2025-11-12 12:15:25.864	debug	[DevID_247/holdingRegs] Poll address 36200 - 2 registers
    modbus.0
    	2025-11-12 12:15:25.862	warn	[DevID_247/holdingRegs] Block 36148-36149: {}
    modbus.0
    	2025-11-12 12:15:25.861	debug	Received pdu describes an error.
    modbus.0
    	2025-11-12 12:15:25.778	debug	[DevID_247/holdingRegs] Poll address 36148 - 2 registers
    modbus.0
    	2025-11-12 12:15:25.775	warn	[DevID_247/holdingRegs] Block 36132-36133: {}
    modbus.0
    	2025-11-12 12:15:25.774	debug	Received pdu describes an error.
    modbus.0
    	2025-11-12 12:15:25.409	debug	[DevID_247/holdingRegs] Poll address 36132 - 2 registers
    modbus.0
    	2025-11-12 12:15:25.407	warn	[DevID_247/holdingRegs] Block 36116-36117: {}
    modbus.0
    	2025-11-12 12:15:25.407	debug	Received pdu describes an error.
    modbus.0
    	2025-11-12 12:15:25.322	debug	[DevID_247/holdingRegs] Poll address 36116 - 2 registers
    modbus.0
    	2025-11-12 12:15:25.317	debug	[DevID_247/holdingRegs/32023] Calculation result = 6.7, type = number
    modbus.0
    	2025-11-12 12:15:25.317	debug	[DevID_247/holdingRegs/32023] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.317	debug	[DevID_247/holdingRegs/32023] Input Value = 67
    modbus.0
    	2025-11-12 12:15:25.317	debug	[DevID_247/holdingRegs/32021] Calculation result = 11696.2, type = number
    modbus.0
    	2025-11-12 12:15:25.317	debug	[DevID_247/holdingRegs/32021] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.317	debug	[DevID_247/holdingRegs/32021] Input Value = 116962
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32020] Calculation result = 0.1, type = number
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32020] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32020] Input Value = 1
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32018] Calculation result = 102, type = number
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32018] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32018] Input Value = 1020
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32017] Calculation result = 3.5, type = number
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32017] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32017] Input Value = 35
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32015] Calculation result = 15521.2, type = number
    modbus.0
    	2025-11-12 12:15:25.316	debug	[DevID_247/holdingRegs/32015] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32015] Input Value = 155212
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32014] Calculation result = 3.3000000000000003, type = number
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32014] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32014] Input Value = 33
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32012] Calculation result = 3473.3, type = number
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32012] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32012] Input Value = 34733
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32011] Calculation result = 0, type = number
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32011] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32011] Input Value = 0
    modbus.0
    	2025-11-12 12:15:25.315	debug	[DevID_247/holdingRegs/32009] Calculation result = 7047.400000000001, type = number
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32009] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32009] Input Value = 70474
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32008] Calculation result = 1.9000000000000001, type = number
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32008] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32008] Input Value = 19
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32006] Calculation result = 4532.8, type = number
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32006] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32006] Input Value = 45328
    modbus.0
    	2025-11-12 12:15:25.314	debug	[DevID_247/holdingRegs/32005] Calculation result = 6.2, type = number
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32005] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32005] Input Value = 62
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32003] Calculation result = 473.59000000000003, type = number
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32003] Formula = x*0.01
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32003] Input Value = 47359
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32002] Calculation result = 9.1, type = number
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32002] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32002] Input Value = 91
    modbus.0
    	2025-11-12 12:15:25.313	debug	[DevID_247/holdingRegs/32000] Calculation result = 17.9574, type = number
    modbus.0
    	2025-11-12 12:15:25.312	debug	[DevID_247/holdingRegs/32000] Formula = x*0.0001
    modbus.0
    	2025-11-12 12:15:25.312	debug	[DevID_247/holdingRegs/32000] Input Value = 179574
    modbus.0
    	2025-11-12 12:15:25.312	debug	[DevID_247/holdingRegs] Poll address 32000 DONE
    modbus.0
    	2025-11-12 12:15:25.174	debug	[DevID_247/holdingRegs] Poll address 32000 - 24 registers
    modbus.0
    	2025-11-12 12:15:25.166	debug	[DevID_247/holdingRegs/31037] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.166	debug	[DevID_247/holdingRegs/31034] Calculation result = 242.60000000000002, type = number
    modbus.0
    	2025-11-12 12:15:25.166	debug	[DevID_247/holdingRegs/31034] Input Value = 2426
    modbus.0
    	2025-11-12 12:15:25.166	debug	[DevID_247/holdingRegs/31034] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.166	debug	[DevID_247/holdingRegs/31037] Input Value = 280
    modbus.0
    	2025-11-12 12:15:25.166	debug	[DevID_247/holdingRegs/31037] Calculation result = 28, type = number
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31033] Calculation result = 55.6, type = number
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31033] Input Value = 556
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31032] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31025] Calculation result = 49.910000000000004, type = number
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31025] Input Value = 4991
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31021] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31020] Calculation result = 0.4, type = number
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31021] Input Value = 3
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31021] Calculation result = 0.30000000000000004, type = number
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31025] Formula = x*0.01
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31032] Input Value = 430
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31032] Calculation result = 43, type = number
    modbus.0
    	2025-11-12 12:15:25.165	debug	[DevID_247/holdingRegs/31033] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31020] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31019] Calculation result = 0.30000000000000004, type = number
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31019] Input Value = 3
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31018] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31017] Calculation result = 235.3, type = number
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31017] Input Value = 2353
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31016] Calculation result = 233.9, type = number
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31017] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31018] Input Value = 2372
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31018] Calculation result = 237.20000000000002, type = number
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31019] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.164	debug	[DevID_247/holdingRegs/31020] Input Value = 4
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31016] Input Value = 2339
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31015] Formula = x*0.01
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31011] Calculation result = 1.4000000000000001, type = number
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31011] Input Value = 14
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31010] Calculation result = 1.4000000000000001, type = number
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31011] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31015] Input Value = 4992
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31015] Calculation result = 49.92, type = number
    modbus.0
    	2025-11-12 12:15:25.163	debug	[DevID_247/holdingRegs/31016] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.162	debug	[DevID_247/holdingRegs/31010] Input Value = 14
    modbus.0
    	2025-11-12 12:15:25.162	debug	[DevID_247/holdingRegs/31009] Calculation result = 1.4000000000000001, type = number
    modbus.0
    	2025-11-12 12:15:25.162	debug	[DevID_247/holdingRegs/31010] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31009] Input Value = 14
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31008] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31007] Calculation result = 235.70000000000002, type = number
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31007] Input Value = 2357
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31006] Calculation result = 235.20000000000002, type = number
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31007] Formula = x*0.1
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31008] Input Value = 2364
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31008] Calculation result = 236.4, type = number
    modbus.0
    	2025-11-12 12:15:25.161	debug	[DevID_247/holdingRegs/31009] Formula = x*0.1
    
    HomoranH Nicht stören
    HomoranH Nicht stören
    Homoran
    Global Moderator Administrators
    schrieb am zuletzt editiert von
    #46

    @rogni sagte in FoxEss H3 Wechselrichter per Modbus in ioBroker:

    ich hab alles unter Holding Register.

    kann bei Chinesen durchaus sein.

    @rogni sagte in FoxEss H3 Wechselrichter per Modbus in ioBroker:

    Register hab ich nur mal ein paar der angegeben eingetragen, sonst kommen da ja Fehler ohne Ende.

    man fängt üblicherweise mit einemzum testen an.
    ein einziger Fehleintrag kann das Auslesen des gesamte Gerätes blockieren

    zu der Konfig:
    bitte keine Nacherzählungen, sondern Screenshots

    ich hab da schon einen Verdacht

    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

    R 1 Antwort Letzte Antwort
    0
    • HomoranH Homoran

      @rogni sagte in FoxEss H3 Wechselrichter per Modbus in ioBroker:

      ich hab alles unter Holding Register.

      kann bei Chinesen durchaus sein.

      @rogni sagte in FoxEss H3 Wechselrichter per Modbus in ioBroker:

      Register hab ich nur mal ein paar der angegeben eingetragen, sonst kommen da ja Fehler ohne Ende.

      man fängt üblicherweise mit einemzum testen an.
      ein einziger Fehleintrag kann das Auslesen des gesamte Gerätes blockieren

      zu der Konfig:
      bitte keine Nacherzählungen, sondern Screenshots

      ich hab da schon einen Verdacht

      R Offline
      R Offline
      Rogni
      schrieb am zuletzt editiert von
      #47

      @homoran
      Einstellungen:

      Bildschirmfoto 2025-11-12 um 13.03.30.png

      Bildschirmfoto 2025-11-12 um 13.03.08.png

      Verbindung:
      Bildschirmfoto 2025-11-12 um 13.04.47.png

      Gruß

      Erik :mrgreen: :mrgreen:

      HomoranH 1 Antwort Letzte Antwort
      0
      • R Rogni

        @homoran
        Einstellungen:

        Bildschirmfoto 2025-11-12 um 13.03.30.png

        Bildschirmfoto 2025-11-12 um 13.03.08.png

        Verbindung:
        Bildschirmfoto 2025-11-12 um 13.04.47.png

        HomoranH Nicht stören
        HomoranH Nicht stören
        Homoran
        Global Moderator Administrators
        schrieb am zuletzt editiert von
        #48

        @rogni stell das
        Screenshot_20251112-131621_Firefox.jpg
        mal testweise auf 1

        wenn das nichts hilft, bitte debug-log vom Instanzen Start

        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

        R 1 Antwort Letzte Antwort
        0
        • HomoranH Homoran

          @rogni stell das
          Screenshot_20251112-131621_Firefox.jpg
          mal testweise auf 1

          wenn das nichts hilft, bitte debug-log vom Instanzen Start

          R Offline
          R Offline
          Rogni
          schrieb am zuletzt editiert von Rogni
          #49

          @homoran den Wert auf 1 zu stellen hat nichts gebracht
          hier der Log:

          iobroker.current.html

          Gruß

          Erik :mrgreen: :mrgreen:

          1 Antwort Letzte Antwort
          0
          • DutchmanD Offline
            DutchmanD Offline
            Dutchman
            Developer Most Active Administrators
            schrieb am zuletzt editiert von
            #50

            falls es jemanden hilft, lief gerade gegen das selbe problem an... hier gibt es noch eine repo mit allen Modbus adresen: https://github.com/rsaemann/HA-FoxESS-H3-Modbus/wiki/H3-Modbus-Registers

            1 Antwort Letzte Antwort
            0
            • MartinPM Online
              MartinPM Online
              MartinP
              schrieb am zuletzt editiert von MartinP
              #51

              Ich habe da einmal eine kurze Frage zur Threaderöffnung:

              Die FoxEss Cloud und / oder FoxEss App ist ja doch recht langsam mit 5min Updatezeiten!!!

              Ich habe mir jetzt nicht alle 50 Beiträge Durchgelesen - aktuell kann man täglich 1440 Anfragen an die FoxEss Cloud über die API schicken. Das wäre eine Anfrage pro Minute.

              Ich frage in meinem Script alle 2 Minuten ab:
              https://forum.iobroker.net/topic/81178/gelöst-foxess-cloud-javascript-warnmeldungen/10?_=1764079881100

              Ausgehend von diesem Thread wollte ich nun wissen, ob der Takt herabgesetzt werden könnte, weil eh nur alle 5 Minuten neue Werte kommen ...
              Die Antwort ist nicht so einfach.

              In der Influx-DB landen Werte mit einem zeitlichen Abstand von 2 Minuten bis über 10 Minuten ...
              Da ich "nur Änderungen aufzeichnen" bei den Influx-Einstellungen für die aktuelle Leistung des Wechselrichters eingetragen habe, ist das Ablegen von Messwerten durchaus unregelmäßig...

              Weiß jemand, woher die Information "5 Minuten Updatezeit der FoxEss Cloud" kommt?

              Intel(R) Celeron(R) CPU N3000 @ 1.04GHz 8G RAM 480G SSD
              Virtualization : unprivileged lxc container (debian 12 on Proxmox 8.4.14)
              Linux pve 6.8.12-16-pve
              6 GByte RAM für den Container
              Fritzbox 6591 FW 8.03 (Vodafone Leih-Box)
              Remote-Access über Wireguard der Fritzbox

              1 Antwort Letzte Antwort
              0
              • R Offline
                R Offline
                Rogni
                schrieb am zuletzt editiert von Rogni
                #52

                @dutchmen das Repo kenn ich . Ich hab nen H3-10-E Inverter. Da sind auch net alle Adressen drauf. Die Abfrage vom Chint fehlt hier vollkommen. HAbe Fox angeschrieben, die bekommen es selber net auf die Reihe. Zumindest kann ich mit den Werten die ich da bekomme nix anfangen.

                Gruß

                Erik :mrgreen: :mrgreen:

                1 Antwort Letzte Antwort
                0
                • R Offline
                  R Offline
                  Rogni
                  schrieb am zuletzt editiert von
                  #53

                  Habe jetzt noch am Smartzähler einen Tasmota Lesekopf. Der bringt jetzt schön Verbrauchswerte. Gefühlt 10h mit der Taschenlampe vor dem Ding verbracht ;)
                  Die Woche kuck ich mir dann das Ganze mal an wie ich was mit den ganzen Werten bauen kann.

                  Gruß

                  Erik :mrgreen: :mrgreen:

                  1 Antwort Letzte Antwort
                  0
                  • MartinPM Online
                    MartinPM Online
                    MartinP
                    schrieb am zuletzt editiert von
                    #54

                    Gefühlt 10h mit der Taschenlampe vor dem Ding verbracht ;)

                    Ich bin hier im Forum auf die App "StromPIN" für Android-Smartphones hingewiesen worden ... Kostet nichts, und man kann damit eine vierstellige PIN mit Hilfe der Lampe im Smartphone übertragen.

                    Es soll sogar welche geben, die gratis sind...

                    Intel(R) Celeron(R) CPU N3000 @ 1.04GHz 8G RAM 480G SSD
                    Virtualization : unprivileged lxc container (debian 12 on Proxmox 8.4.14)
                    Linux pve 6.8.12-16-pve
                    6 GByte RAM für den Container
                    Fritzbox 6591 FW 8.03 (Vodafone Leih-Box)
                    Remote-Access über Wireguard der Fritzbox

                    1 Antwort Letzte Antwort
                    0
                    • R Offline
                      R Offline
                      Rogni
                      schrieb am zuletzt editiert von
                      #55

                      @martinp ja hab ich für das apple Smartfon, allerdings hat sich der EBZ Zähler wenig davon beeindrucken lassen ;)

                      Gruß

                      Erik :mrgreen: :mrgreen:

                      1 Antwort Letzte Antwort
                      0
                      Antworten
                      • In einem neuen Thema antworten
                      Anmelden zum Antworten
                      • Älteste zuerst
                      • Neuste zuerst
                      • Meiste Stimmen


                      Support us

                      ioBroker
                      Community Adapters
                      Donate

                      462

                      Online

                      32.4k

                      Benutzer

                      81.5k

                      Themen

                      1.3m

                      Beiträge
                      Community
                      Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                      ioBroker Community 2014-2025
                      logo
                      • Anmelden

                      • Du hast noch kein Konto? Registrieren

                      • Anmelden oder registrieren, um zu suchen
                      • Erster Beitrag
                        Letzter Beitrag
                      0
                      • Home
                      • Aktuell
                      • Tags
                      • Ungelesen 0
                      • Kategorien
                      • Unreplied
                      • Beliebt
                      • GitHub
                      • Docu
                      • Hilfe