  4. Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.4k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.0k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.6k

Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
canbuscanbus adapterrotex hpsu
522 Beiträge 25 Kommentatoren 104.5k Aufrufe 20 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • E earl80

    @cb187 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

    Modbus Zähler

    Ok, den kannte ich noch nicht. Hast den im Zählerschrank einbauen lassen, oder am Kabel von der WP?

    E Offline
    E Offline
    earl80
    schrieb am zuletzt editiert von
    #331

    @earl80 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

    @cb187 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

    Modbus Zähler

    Ok, den kannte ich noch nicht. Hast den im Zählerschrank einbauen lassen, oder am Kabel von der WP?

    1 Antwort Letzte Antwort
    0
    • E earl80

      @cb187 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

      Modbus Zähler

      Ok, den kannte ich noch nicht. Hast den im Zählerschrank einbauen lassen, oder am Kabel von der WP?

      HomoranH Nicht stören
      HomoranH Nicht stören
      Homoran
      Global Moderator Administrators
      schrieb am zuletzt editiert von
      #332

      @earl80 20230716_135341.jpg

      kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

      der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

      1 Antwort Letzte Antwort
      0
      • E earl80

        @cb187 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

        Modbus Zähler

        Ok, den kannte ich noch nicht. Hast den im Zählerschrank einbauen lassen, oder am Kabel von der WP?

        C Offline
        C Offline
        cb187
        schrieb am zuletzt editiert von
        #333

        @earl80 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

        @cb187 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

        Modbus Zähler

        Ok, den kannte ich noch nicht. Hast den im Zählerschrank einbauen lassen, oder am Kabel von der WP?

        Ja einfach auf die Hutschiene und die klemmen an die Drei Phasen fertig.

        E 1 Antwort Letzte Antwort
        0
        • C cb187

          @earl80 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

          @cb187 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

          Modbus Zähler

          Ok, den kannte ich noch nicht. Hast den im Zählerschrank einbauen lassen, oder am Kabel von der WP?

          Ja einfach auf die Hutschiene und die klemmen an die Drei Phasen fertig.

          E Offline
          E Offline
          earl80
          schrieb am zuletzt editiert von earl80
          #334

          @cb187
          So, der Shelly Pro 3EM ist eingebaut, per MQTT eingebunden und verrichtet seine Dinge. Mit was protokolliert man jetzt am besten seinen Verbrauch? sourceanalytix?

          C 1 Antwort Letzte Antwort
          0
          • E earl80

            @cb187
            So, der Shelly Pro 3EM ist eingebaut, per MQTT eingebunden und verrichtet seine Dinge. Mit was protokolliert man jetzt am besten seinen Verbrauch? sourceanalytix?

            C Offline
            C Offline
            cb187
            schrieb am zuletzt editiert von
            #335

            @earl80 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

            @cb187
            So, der Shelly Pro 3EM ist eingebaut, per MQTT eingebunden und verrichtet seine Dinge. Mit was protokolliert man jetzt am besten seinen Verbrauch? sourceanalytix?

            Zb.So mache ich es.

            1 Antwort Letzte Antwort
            0
            • crycodeC crycode

              Über meinen Adapter ioBroker.canbus (Adaptervorstellung im Forum) ist die Einbindung einer Rotex HPSU bzw. Daikin Altherma Wärmepumpe mittlerweile relativ einfach möglich.

              Um die Diskussionen bezüglich der Wärmepumpen etwas vom Adapter-Test zu entkoppeln nun dieses Thema hier.
              Alles vorangegangene ist im Adapter-Test-Thema zu finden.

              Dank der Mithilfe von @michael-wind, @cb187 und @shortcircuit0815 ist im Adapter auch eine vordefinierte Konfiguration für diese Wärmepumpen verfügbar, welche direkt geladen werden kann.
              (Ich selbst habe diese Hardware nicht!)

              @RaspiUser hat die Installation und Einrichtung in einer kurzen Anleitung zusammengefasst: Anleitung CAN Bus Installation.pdf

              Alle Angaben nach bestem Wissen und Gewissen, aber ohne Gewähr und jegliche Haftung für ggf. entstehende Schäden wird ausgeschlossen.


              Allgemeine Infos

              Auslesen und Setzen vieler Parameter der einzelnen Module der Wärmepumpe.
              Keine speziellen Zugriffsrechte erforderlich.
              Getestet mit Rotex HPSU compact 516 (Baujahr 2013/2017) und Altherma 3 ECH2O.

              Die Kommunikation auf dem CAN-Bus erfolgt hier mit 20 kbit/s und Nachrichten im Standard-Frame-Format (SFF).

              Die CAN-Nachrichten-ID ist jeweils die ID des sendenden Gerätes. Die Identifikation der einzelnen Nachrichteninhalte ist in den ersten Daten-Bytes der einzelnen Nachrichten enthalten.

              Gerät CAN-ID
              RoCon 10A
              Kessel 180
              HPSU Bedienmodul 300
              HPSU Heizmodul 500
              Remote-Software 680

              Zusätzliche Infos zum Aufbau der Nachrichten sind hier zu finden.


              Daten in ioBroker

              Damit Daten im ioBroker ankommen, müssen diese aktiv von der Wärmepumpe abgefragt werden. Dies kann beispielsweise vom Bedienmodul oder auch vom ioBroker aus über die entsprechenden States unter der Nachrichten-ID 680 erfolgen.

              Sollen Daten regelmäßig abgefragt werden, so kann in der Adapterkonfiguration beim entsprechenden Parser die Option Automatisch einen bestimmten Wert setzen mit dem gewünschten Intervall aktiviert werden.

              Änderungen an Einstellungen der Wäremepumpe sind über die -set-States unter der Nachrichten-ID 680 möglich.

              Damit beim Ändern von Werten die gesetzten Werte automatisch auch in ioBroker "ankommen", kann über den Javascript-Adapter ein eigenes Script erstellt werden, welches nach dem Ändern eines -set-States die zugehörige Abfrage triggern:

              /*
               * Aktuellen Wert automatisch nach dem Setzen eines Wertes abfragen, sofern möglich.
               */
              on({ id: /^canbus\.0\.680\..+-set$/, change: 'any', ack: true }, async (obj) => {
                const id = obj.id.replace(/-set$/, '');
                const exists = await existsObjectAsync(id);
                if (exists) {
                  await new Promise((resolve) => setTimeout(resolve, 500)); // 500ms warten, damit Änderung übernommen wurde
                  await setStateAsync(id, true);
                }
              });
              

              Technische Infos

              Kabellänge

              Die nutzbare Kabellänge ist vor allem vom verwendeten Kabeltyp und von der Baudrate abhängig.

              Bei dem Kabel sollte auf jeden Fall auf ein verdrilltes Adernpaar von CAN-H und CAN-L geachtet werden. Zudem ist besonders bei Längen über 1 m eine Schirmung immer gut. Ich habe hier sehr gute Erfahrungen mit S/FTP Kabeln, die sonst hauptsächlich für Ethernet eingesetzt werden, gemacht.

              Bei der hier verwendeten Baudrate von 20 kbit/s beträgt die maximale Kabellänge stolze 3,3 km. Dies hängt natürlich auch noch diversen anderen Faktoren mit ab, aber für den Einsatz in einem Gebäude sollte das locker ausreichen.

              B Offline
              B Offline
              bovi
              schrieb am zuletzt editiert von bovi
              #336

              Im Adaper ioBroker.canbus und im Blog habe ich sehr hilfreiche Hinweise gefunden - super und vielen Dank dafür!
              Damit kann ich nun an meiner Wärmepumpe - eine DAIKIN ALTHERMA ECHO 20 H/C 5kw , Baujahr 2018 - die bisherige Steuerung über die externen Anschlüsse EXT,SG, EVU
              und die Datenerfassung über externe Temperatursensoren ( DS1820 )
              "vom Sofa aus" erheblich erweitern und verfeinern.

              Mit dem angefügten Script habe ich nachfolgende Ergänzungen und Abweichungen bei meiner Wärmepumpe gefunden :

              sh can.sh 680#3100FA071B0000
              180#D200FA071B0001
              0001 ist der Wert bei einem Widerstand < 680 Ohm zwischen den Schaltkontakten EXT (J8 ), externe Betriebsartenumschaltung auf "Bereitschaft"
              bei offenen Kontakten ist der Wert 00FF d.h. keine externe Betriebsartenumschaltung
              Zwischenwerte habe ich (noch) nicht getestet.

              sh can.sh 680#3100FAC0F80000
              180#D200FAC0F80003
              0003 ist der Hex-Wert bei geschlossenen Schaltkontakten SG und/oder EVU , das Display zeigt dann "SG3" .
              Bei offenen Schaltkontakten kommt der Hex-Wert 0006 und das Display zeigt "SGN".

              sh can.sh 680#3100FA0A200000
              180#D200FA0A200004
              Relaistest, der Wert 0x0004 weist auf das Relais Nr 3 für Ventil 3UVB1
              Umwandlung per Python : Relais-Nr = int(math.log(int("Wert",16))/math.log(2)-1)

              sh can.sh 680#3100FAC1040000
              180#D200FAC1040011
              Der Wert 0x0011=17 , 3UVB ist die Stellung des Ventils 3UV DWH in %
              "TR2 abfragen" liefert bei mir falsche Werte.

              sh can.sh 680#3100FAC1020000
              180#D200FAC1020028
              Der Wert 0x0028=40 , BPV , ist die Stellung des Ventils 3UVB1 in %
              "TVBH abfragen" liefert bei mir falsche Werte.

              sh can.sh 680#3100FAC0FB0000
              180#D200FAC0FB0000
              Der Wert ist bei mir immer 0000, auch wenn BPV über 0% steht - ein Wechsel oder Verwechselung mit FAC102 (s.o)?

              Meine Fußbodenheizung reagiert erst nach ca. 4 Stunden auf Änderungen der Vorlauftemperatur und wird bei schnellen Änderungen der Außentemperatur und Sonneneinstahlung regelmäßig über- oder untersteuert. Daher prognostiziere ich mit dem raspi den Wärmebedarf mithilfe von Messdaten (insbesondere Temperatur und Globalstrahlung), den Einfallswinkeln der Sonne auf die Außenfenster und Wetterprognosen des DWD auf 4 Stunden voraus und führe diesen gezielt über Ventile mit Stellantrieben der Fußbodenheizung zu. Dadurch wird die Solltemperatur auch bei raschem Wetterwechsel auf +/- 0,3 °C eingehalten.
              Außerdem wird ein Energieüberschuß aus der PV-Anlage vorrangig für die Erwärmung des Puffer-Wasserspeichers der Wärmepumpe verwand (schließen der SG/EVU-Schaltkontakte) und bei Wärmebedarf über die EHS-Funktionen dem Puffer wieder entnommen.
              Der CAN-Anschluss der Wärmepumpe bietet nun bessere Regelungsmöglichkeiten "vom Sofa aus" oder über das Internet.

              @crycode can.sh

              1 Antwort Letzte Antwort
              2
              • RaspiUserR Offline
                RaspiUserR Offline
                RaspiUser
                schrieb am zuletzt editiert von RaspiUser
                #337

                @crycode said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                Da stimmt etwas mit dem vcan0-setup.sh Script nicht.

                ... da bin wieder (siehe #318) ... :cry:

                Ich habe (mußte) den ioBroker neu aufsetzen (... von Buster auf Bookworm). Bei dieser Gelegenheit habe ich die Adapter "aufgeräumt" und kein Backitup genutzt.
                Ich habe nach meiner damaligen Anleitung die CAN-Installation auf dem Pi erneut durchgeführt (die auf dem VCAN-Zero habe ich nicht angetastet) und bekomme eine ähnliche Fehlermeldung wie damals ...

                Job for vcan0-setup.service failed because the control process exited with error code.
                See "systemctl status vcan0-setup.service" and "journalctl -xeu vcan0-setup.service" for details.
                pi@ioBroker-Raspi:~ $ systemctl status vcan0-setup.service
                × vcan0-setup.service - Setup vcan0
                     Loaded: loaded (/etc/systemd/system/vcan0-setup.service; enabled; preset: enabled)
                     Active: failed (Result: exit-code) since Sat 2023-10-28 16:16:36 CEST; 1s ago
                    Process: 5363 ExecStart=/usr/local/sbin/vcan0-setup.sh start (code=exited, status=203/EXEC)
                   Main PID: 5363 (code=exited, status=203/EXEC)
                        CPU: 7ms
                
                Oct 28 16:16:36 ioBroker-Raspi systemd[1]: Starting vcan0-setup.service - Setup vcan0...
                Oct 28 16:16:36 ioBroker-Raspi (setup.sh)[5363]: vcan0-setup.service: Failed to execute /usr/local/sbin/vcan0-setup.sh: Exec format error
                Oct 28 16:16:36 ioBroker-Raspi (setup.sh)[5363]: vcan0-setup.service: Failed at step EXEC spawning /usr/local/sbin/vcan0-setup.sh: Exec format error
                Oct 28 16:16:36 ioBroker-Raspi systemd[1]: vcan0-setup.service: Main process exited, code=exited, status=203/EXEC
                Oct 28 16:16:36 ioBroker-Raspi systemd[1]: vcan0-setup.service: Failed with result 'exit-code'.
                Oct 28 16:16:36 ioBroker-Raspi systemd[1]: Failed to start vcan0-setup.service - Setup vcan0.
                pi@ioBroker-Raspi:~ $ journalctl -xeu vcan0-setup.service
                ░░ Support: https://www.debian.org/support
                ░░
                ░░ An ExecStart= process belonging to unit vcan0-setup.service has exited.
                ░░
                ░░ The process' exit code is 'exited' and its exit status is 203.
                Oct 28 16:17:22 ioBroker-Raspi systemd[1]: vcan0-setup.service: Failed with result 'exit-code'.
                ░░ Subject: Unit failed
                ░░ Defined-By: systemd
                ░░ Support: https://www.debian.org/support
                ░░
                ░░ The unit vcan0-setup.service has entered the 'failed' state with result 'exit-code'.
                Oct 28 16:17:22 ioBroker-Raspi systemd[1]: Failed to start vcan0-setup.service - Setup vcan0.
                ░░ Subject: A start job for unit vcan0-setup.service has failed
                ░░ Defined-By: systemd
                ░░ Support: https://www.debian.org/support
                ░░
                ░░ A start job for unit vcan0-setup.service has finished with a failure.
                ░░
                ░░ The job identifier is 44325 and the job result is failed.
                Oct 28 16:17:25 ioBroker-Raspi systemd[1]: Starting vcan0-setup.service - Setup vcan0...
                ░░ Subject: A start job for unit vcan0-setup.service has begun execution
                ░░ Defined-By: systemd
                ░░ Support: https://www.debian.org/support
                ░░
                ░░ A start job for unit vcan0-setup.service has begun execution.
                ░░
                ░░ The job identifier is 44399.
                Oct 28 16:17:25 ioBroker-Raspi (setup.sh)[5422]: vcan0-setup.service: Failed to execute /usr/local/sbin/vcan0-setup.sh: Exec format error
                Oct 28 16:17:25 ioBroker-Raspi (setup.sh)[5422]: vcan0-setup.service: Failed at step EXEC spawning /usr/local/sbin/vcan0-setup.sh: Exec format error
                ░░ Subject: Process /usr/local/sbin/vcan0-setup.sh could not be executed
                ░░ Defined-By: systemd
                ░░ Support: https://www.debian.org/support
                ░░
                ░░ The process /usr/local/sbin/vcan0-setup.sh could not be executed and failed.
                ░░
                ░░ The error number returned by this process is ERRNO.
                Oct 28 16:17:25 ioBroker-Raspi systemd[1]: vcan0-setup.service: Main process exited, code=exited, status=203/EXEC
                ░░ Subject: Unit process exited
                ░░ Defined-By: systemd
                ░░ Support: https://www.debian.org/support
                ░░
                ░░ An ExecStart= process belonging to unit vcan0-setup.service has exited.
                ░░
                ░░ The process' exit code is 'exited' and its exit status is 203.
                Oct 28 16:17:25 ioBroker-Raspi systemd[1]: vcan0-setup.service: Failed with result 'exit-code'.
                ░░ Subject: Unit failed
                ░░ Defined-By: systemd
                ░░ Support: https://www.debian.org/support
                ░░
                ░░ The unit vcan0-setup.service has entered the 'failed' state with result 'exit-code'.
                Oct 28 16:17:25 ioBroker-Raspi systemd[1]: Failed to start vcan0-setup.service - Setup vcan0.
                ░░ Subject: A start job for unit vcan0-setup.service has failed
                ░░ Defined-By: systemd
                ░░ Support: https://www.debian.org/support
                ░░
                ░░ A start job for unit vcan0-setup.service has finished with a failure.
                ░░
                ░░ The job identifier is 44399 and the job result is failed.
                lines 6417-6474/6474 (END)
                
                

                setupsh.jpg
                Ich kann nicht mehr nachvollziehen was ich damals "repariert" habe ...
                Kannst Du mit den vorliegenden Infos helfen ?

                EDIT:
                Ich habe meine alten Beiträge nochmal angeschaut ... ich habe damals an dem Problem #318 nicht weiter gemacht ... :face_with_head_bandage: :face_with_thermometer: :cold_sweat: könnte also ggf. etwas mit Bookworm zusammenhängen ...

                crycodeC 1 Antwort Letzte Antwort
                0
                • RaspiUserR RaspiUser

                  @crycode said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                  Da stimmt etwas mit dem vcan0-setup.sh Script nicht.

                  ... da bin wieder (siehe #318) ... :cry:

                  Ich habe (mußte) den ioBroker neu aufsetzen (... von Buster auf Bookworm). Bei dieser Gelegenheit habe ich die Adapter "aufgeräumt" und kein Backitup genutzt.
                  Ich habe nach meiner damaligen Anleitung die CAN-Installation auf dem Pi erneut durchgeführt (die auf dem VCAN-Zero habe ich nicht angetastet) und bekomme eine ähnliche Fehlermeldung wie damals ...

                  Job for vcan0-setup.service failed because the control process exited with error code.
                  See "systemctl status vcan0-setup.service" and "journalctl -xeu vcan0-setup.service" for details.
                  pi@ioBroker-Raspi:~ $ systemctl status vcan0-setup.service
                  × vcan0-setup.service - Setup vcan0
                       Loaded: loaded (/etc/systemd/system/vcan0-setup.service; enabled; preset: enabled)
                       Active: failed (Result: exit-code) since Sat 2023-10-28 16:16:36 CEST; 1s ago
                      Process: 5363 ExecStart=/usr/local/sbin/vcan0-setup.sh start (code=exited, status=203/EXEC)
                     Main PID: 5363 (code=exited, status=203/EXEC)
                          CPU: 7ms
                  
                  Oct 28 16:16:36 ioBroker-Raspi systemd[1]: Starting vcan0-setup.service - Setup vcan0...
                  Oct 28 16:16:36 ioBroker-Raspi (setup.sh)[5363]: vcan0-setup.service: Failed to execute /usr/local/sbin/vcan0-setup.sh: Exec format error
                  Oct 28 16:16:36 ioBroker-Raspi (setup.sh)[5363]: vcan0-setup.service: Failed at step EXEC spawning /usr/local/sbin/vcan0-setup.sh: Exec format error
                  Oct 28 16:16:36 ioBroker-Raspi systemd[1]: vcan0-setup.service: Main process exited, code=exited, status=203/EXEC
                  Oct 28 16:16:36 ioBroker-Raspi systemd[1]: vcan0-setup.service: Failed with result 'exit-code'.
                  Oct 28 16:16:36 ioBroker-Raspi systemd[1]: Failed to start vcan0-setup.service - Setup vcan0.
                  pi@ioBroker-Raspi:~ $ journalctl -xeu vcan0-setup.service
                  ░░ Support: https://www.debian.org/support
                  ░░
                  ░░ An ExecStart= process belonging to unit vcan0-setup.service has exited.
                  ░░
                  ░░ The process' exit code is 'exited' and its exit status is 203.
                  Oct 28 16:17:22 ioBroker-Raspi systemd[1]: vcan0-setup.service: Failed with result 'exit-code'.
                  ░░ Subject: Unit failed
                  ░░ Defined-By: systemd
                  ░░ Support: https://www.debian.org/support
                  ░░
                  ░░ The unit vcan0-setup.service has entered the 'failed' state with result 'exit-code'.
                  Oct 28 16:17:22 ioBroker-Raspi systemd[1]: Failed to start vcan0-setup.service - Setup vcan0.
                  ░░ Subject: A start job for unit vcan0-setup.service has failed
                  ░░ Defined-By: systemd
                  ░░ Support: https://www.debian.org/support
                  ░░
                  ░░ A start job for unit vcan0-setup.service has finished with a failure.
                  ░░
                  ░░ The job identifier is 44325 and the job result is failed.
                  Oct 28 16:17:25 ioBroker-Raspi systemd[1]: Starting vcan0-setup.service - Setup vcan0...
                  ░░ Subject: A start job for unit vcan0-setup.service has begun execution
                  ░░ Defined-By: systemd
                  ░░ Support: https://www.debian.org/support
                  ░░
                  ░░ A start job for unit vcan0-setup.service has begun execution.
                  ░░
                  ░░ The job identifier is 44399.
                  Oct 28 16:17:25 ioBroker-Raspi (setup.sh)[5422]: vcan0-setup.service: Failed to execute /usr/local/sbin/vcan0-setup.sh: Exec format error
                  Oct 28 16:17:25 ioBroker-Raspi (setup.sh)[5422]: vcan0-setup.service: Failed at step EXEC spawning /usr/local/sbin/vcan0-setup.sh: Exec format error
                  ░░ Subject: Process /usr/local/sbin/vcan0-setup.sh could not be executed
                  ░░ Defined-By: systemd
                  ░░ Support: https://www.debian.org/support
                  ░░
                  ░░ The process /usr/local/sbin/vcan0-setup.sh could not be executed and failed.
                  ░░
                  ░░ The error number returned by this process is ERRNO.
                  Oct 28 16:17:25 ioBroker-Raspi systemd[1]: vcan0-setup.service: Main process exited, code=exited, status=203/EXEC
                  ░░ Subject: Unit process exited
                  ░░ Defined-By: systemd
                  ░░ Support: https://www.debian.org/support
                  ░░
                  ░░ An ExecStart= process belonging to unit vcan0-setup.service has exited.
                  ░░
                  ░░ The process' exit code is 'exited' and its exit status is 203.
                  Oct 28 16:17:25 ioBroker-Raspi systemd[1]: vcan0-setup.service: Failed with result 'exit-code'.
                  ░░ Subject: Unit failed
                  ░░ Defined-By: systemd
                  ░░ Support: https://www.debian.org/support
                  ░░
                  ░░ The unit vcan0-setup.service has entered the 'failed' state with result 'exit-code'.
                  Oct 28 16:17:25 ioBroker-Raspi systemd[1]: Failed to start vcan0-setup.service - Setup vcan0.
                  ░░ Subject: A start job for unit vcan0-setup.service has failed
                  ░░ Defined-By: systemd
                  ░░ Support: https://www.debian.org/support
                  ░░
                  ░░ A start job for unit vcan0-setup.service has finished with a failure.
                  ░░
                  ░░ The job identifier is 44399 and the job result is failed.
                  lines 6417-6474/6474 (END)
                  
                  

                  setupsh.jpg
                  Ich kann nicht mehr nachvollziehen was ich damals "repariert" habe ...
                  Kannst Du mit den vorliegenden Infos helfen ?

                  EDIT:
                  Ich habe meine alten Beiträge nochmal angeschaut ... ich habe damals an dem Problem #318 nicht weiter gemacht ... :face_with_head_bandage: :face_with_thermometer: :cold_sweat: könnte also ggf. etwas mit Bookworm zusammenhängen ...

                  crycodeC Offline
                  crycodeC Offline
                  crycode
                  Developer
                  schrieb am zuletzt editiert von
                  #338

                  @raspiuser sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                  Failed to execute /usr/local/sbin/vcan0-setup.sh: Exec format error

                  Das wird das bzw. eines der Probleme sein.
                  Das stimmt etwas mit dem Script nicht. Am besten das noch mal neu erstellen und prüfen, dass da keine Leerzeichen, Tabs etc. direkt am Anfang sind.
                  Deinem Screenshot nach hast du in jeder Zeile entweder einen Tab oder ein paar Leerzeichen zu viel vorne. Das #!/bin/bash muss ganz links stehen. Die anderen Zeilen dann auch entsprechend weiter vorne (dort stört es aber von der Funktion her nicht).

                  Meine Adapter: discord | canbus | ds18b20 | odl | radiohead

                  1 Antwort Letzte Antwort
                  1
                  • RaspiUserR Offline
                    RaspiUserR Offline
                    RaspiUser
                    schrieb am zuletzt editiert von
                    #339

                    @crycode said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                    Deinem Screenshot nach hast du in jeder Zeile entweder einen Tab oder ein paar Leerzeichen zu viel

                    ... stimmt ... sogar bei copy & paste kann ich noch Fehler einbauen .... :clown_face: :cold_sweat: :confounded: :cry: :confused: :angry: :face_with_head_bandage:

                    Adapter ist grün .... Danke für deine Hilfe :+1:

                    1 Antwort Letzte Antwort
                    1
                    • hg6806H Offline
                      hg6806H Offline
                      hg6806
                      Most Active
                      schrieb am zuletzt editiert von hg6806
                      #340

                      Hallo nchmal,

                      ich kämpfe noch immer mit einer zu hohen CPU Auslastung.

                      Ich habe mittlerweile recht viele solcher Einträge:

                      2823d963-c05d-4bb2-9edc-de07cc25b536-image.png

                      und

                      144e1eb8-7a11-475d-8f10-0e256feb59c5-image.png

                      Woher kommt das? Löschen kann ich es leider nicht, der Löschen-Button ist ausgegraut.

                      Raw-States nicht mehr angehakt.

                      "htop" ist auch unauffällig:

                      f2e95591-47cb-4f92-a9ee-33956b843739-image.png

                      CAN steht bei ioBroker immer an 2. Stelle:

                      7fcaef79-dd5f-4e6f-a7e1-1a985c7346fb-image.png

                      Ich würde dann mal alles exportieren und einen Teil löschen

                      crycodeC 1 Antwort Letzte Antwort
                      0
                      • hg6806H hg6806

                        Hallo nchmal,

                        ich kämpfe noch immer mit einer zu hohen CPU Auslastung.

                        Ich habe mittlerweile recht viele solcher Einträge:

                        2823d963-c05d-4bb2-9edc-de07cc25b536-image.png

                        und

                        144e1eb8-7a11-475d-8f10-0e256feb59c5-image.png

                        Woher kommt das? Löschen kann ich es leider nicht, der Löschen-Button ist ausgegraut.

                        Raw-States nicht mehr angehakt.

                        "htop" ist auch unauffällig:

                        f2e95591-47cb-4f92-a9ee-33956b843739-image.png

                        CAN steht bei ioBroker immer an 2. Stelle:

                        7fcaef79-dd5f-4e6f-a7e1-1a985c7346fb-image.png

                        Ich würde dann mal alles exportieren und einen Teil löschen

                        crycodeC Offline
                        crycodeC Offline
                        crycode
                        Developer
                        schrieb am zuletzt editiert von
                        #341

                        @hg6806 Deinen Screenshots nach sieht die Auslastung doch gar nicht so hoch aus. 🤔

                        Mich machen die Nicht konfigurierten Nachrichten etwas stutzig. Da dürfte jede NachrichtenID eigentlich nur einmal auftauchen und auch nur, wenn sie wirklich nicht konfiguriert ist.
                        Hast du die zugehörige Option in den allgemeinen Einstellungen aktiviert? Falls ja mal bitte deaktivieren.
                        Welche Adapterversion hast du installiert?
                        Kannst du mir mal einen Export des gesamten Objeltbaums unter canbus.0 zukommen lassen? (gerne auch als PN)

                        Meine Adapter: discord | canbus | ds18b20 | odl | radiohead

                        hg6806H 1 Antwort Letzte Antwort
                        0
                        • crycodeC crycode

                          @hg6806 Deinen Screenshots nach sieht die Auslastung doch gar nicht so hoch aus. 🤔

                          Mich machen die Nicht konfigurierten Nachrichten etwas stutzig. Da dürfte jede NachrichtenID eigentlich nur einmal auftauchen und auch nur, wenn sie wirklich nicht konfiguriert ist.
                          Hast du die zugehörige Option in den allgemeinen Einstellungen aktiviert? Falls ja mal bitte deaktivieren.
                          Welche Adapterversion hast du installiert?
                          Kannst du mir mal einen Export des gesamten Objeltbaums unter canbus.0 zukommen lassen? (gerne auch als PN)

                          hg6806H Offline
                          hg6806H Offline
                          hg6806
                          Most Active
                          schrieb am zuletzt editiert von
                          #342

                          @crycode

                          Auf dem Pi5 sieht das im ersten Moment nicht viel aus.
                          Der CAN Adapter muss aber eigentlich nicht viel machen, liegt aber immer zwischen der Auslastung vom ganzen js-controller oder min. die Hälfte davon oder immer das 2-4 fache vom Javascript- Adapter und ich habe mal grob 50 Programme am Laufen, deshalb finde ich das im Vergleich schon viel.

                          Sollten eigentlich immer gelöscht werden.

                          21cd215b-1d95-4108-9b22-3f98bd0d4675-image.png

                          Stimmt, nach Adapterstart sind sie nun weg.
                          Hatte aber gestern den Pi5 ganz neu gebootet, da wurde anscheinend nichts gelöscht.

                          Installiert ist die 1.3.1

                          Anbei der Export.
                          canbus-messages.json

                          crycodeC 1 Antwort Letzte Antwort
                          0
                          • hg6806H hg6806

                            @crycode

                            Auf dem Pi5 sieht das im ersten Moment nicht viel aus.
                            Der CAN Adapter muss aber eigentlich nicht viel machen, liegt aber immer zwischen der Auslastung vom ganzen js-controller oder min. die Hälfte davon oder immer das 2-4 fache vom Javascript- Adapter und ich habe mal grob 50 Programme am Laufen, deshalb finde ich das im Vergleich schon viel.

                            Sollten eigentlich immer gelöscht werden.

                            21cd215b-1d95-4108-9b22-3f98bd0d4675-image.png

                            Stimmt, nach Adapterstart sind sie nun weg.
                            Hatte aber gestern den Pi5 ganz neu gebootet, da wurde anscheinend nichts gelöscht.

                            Installiert ist die 1.3.1

                            Anbei der Export.
                            canbus-messages.json

                            crycodeC Offline
                            crycodeC Offline
                            crycode
                            Developer
                            schrieb am zuletzt editiert von
                            #343

                            @hg6806 Nimm mal den Haken bei "Gesehene Nachrichten automatisch hinzufügen" raus. Das brauchst du im normalen Betrieb nicht und könnte durch die Checks dabei im Hintergrund durchaus etwas mehr Systemlast bringen.

                            Meine Adapter: discord | canbus | ds18b20 | odl | radiohead

                            C hg6806H 2 Antworten Letzte Antwort
                            0
                            • crycodeC crycode

                              @hg6806 Nimm mal den Haken bei "Gesehene Nachrichten automatisch hinzufügen" raus. Das brauchst du im normalen Betrieb nicht und könnte durch die Checks dabei im Hintergrund durchaus etwas mehr Systemlast bringen.

                              C Offline
                              C Offline
                              cb187
                              schrieb am zuletzt editiert von
                              #344

                              @crycode

                              Hi hab mal ne Frage hat jetzt nichts direkt mit diesem Adapter was zu tun aber mit Canbus selber.
                              Ich hab mir mal nen Esp32 bestellt und wollte mal den Canbus darüber testen.Da du dich ja ja so gut mit Canbus aus kennst, könntest du mir dabei mal helfen das in Esphome zuintegrieren?
                              Also die config mit zuerstellen.
                              Vielleicht interessiert dich das ja selber und hast List dazu.

                              Gruss Christoph

                              crycodeC 1 Antwort Letzte Antwort
                              0
                              • crycodeC crycode

                                @hg6806 Nimm mal den Haken bei "Gesehene Nachrichten automatisch hinzufügen" raus. Das brauchst du im normalen Betrieb nicht und könnte durch die Checks dabei im Hintergrund durchaus etwas mehr Systemlast bringen.

                                hg6806H Offline
                                hg6806H Offline
                                hg6806
                                Most Active
                                schrieb am zuletzt editiert von
                                #345

                                @crycode sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                                @hg6806 Nimm mal den Haken bei "Gesehene Nachrichten automatisch hinzufügen" raus. Das brauchst du im normalen Betrieb nicht und könnte durch die Checks dabei im Hintergrund durchaus etwas mehr Systemlast bringen.

                                Hat jetzt nicht wirklich was gebracht.
                                Echt seltsam.
                                Der CAN-Adapter steht halt immer an 2. Stelle bei der Auslastung von ioBroker und machen muss er ja eigentlich nicht viel.

                                crycodeC 1 Antwort Letzte Antwort
                                0
                                • hg6806H Offline
                                  hg6806H Offline
                                  hg6806
                                  Most Active
                                  schrieb am zuletzt editiert von hg6806
                                  #346

                                  Da im Moment bei dem Nass-kalten Wetter fleißig abgetaut wird, wollte ich wenigstens die Menge begrenzen, die darüber verloren geh.
                                  Dazu sollte man ja sobald auf "Abtauen" geschaltet wird auch Sommer schalten.

                                  Ich habe hier ein Programm von dir @cb187
                                  Doch leider schaltet die Heizung sobald der Modus auf Sommer geschaltet wird auf "Betriebsart Standby" und macht dann gar nicht mehr. Nicht mal ein Abtauen mit Heizungswasser.

                                  72a64c59-a66d-46fe-9cb2-bfa9b1450c0f-image.png

                                  Wieso geht das bei euch und bei mir nicht?

                                  C 1 Antwort Letzte Antwort
                                  0
                                  • hg6806H hg6806

                                    Da im Moment bei dem Nass-kalten Wetter fleißig abgetaut wird, wollte ich wenigstens die Menge begrenzen, die darüber verloren geh.
                                    Dazu sollte man ja sobald auf "Abtauen" geschaltet wird auch Sommer schalten.

                                    Ich habe hier ein Programm von dir @cb187
                                    Doch leider schaltet die Heizung sobald der Modus auf Sommer geschaltet wird auf "Betriebsart Standby" und macht dann gar nicht mehr. Nicht mal ein Abtauen mit Heizungswasser.

                                    72a64c59-a66d-46fe-9cb2-bfa9b1450c0f-image.png

                                    Wieso geht das bei euch und bei mir nicht?

                                    C Offline
                                    C Offline
                                    cb187
                                    schrieb am zuletzt editiert von
                                    #347

                                    @hg6806

                                    Ich glaub ich weiss warum das bei dir nicht geht, hast du die UWP so eingestellt das sie Frostschutz bei 0 hat?
                                    Wenn ja kannst sie ausschalten oder mit in die Steuerung einbauen.

                                    1 Antwort Letzte Antwort
                                    0
                                    • RaspiUserR Offline
                                      RaspiUserR Offline
                                      RaspiUser
                                      schrieb am zuletzt editiert von
                                      #348

                                      @crycode

                                      @raspiuser sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                                      Adapter ist grün .... Danke für deine Hilfe

                                      ... nachdem ich vor einiger Zeit den Adapter zum Laufen gebracht hatte (s.o.), wollte ich mir nun die Zeit nehmen um mich um die Einstellungen u.ä. zu kümmern .... und habe prompt wieder (Anfänger) Probleme:

                                      Es kommen keine Daten (lediglich ((null)) in den Objekten an, weder über Abfragen unter ID680 noch über Abruf am Bedienteil, das connection-Objekt ist true.
                                      In den Adapter Einstellungen habe ich lediglich die Konfiguration 1.7.0 importiert und vcan0 eingetragen, ansonsten nix angehakt.
                                      In PuTTY kommen die Daten, sowohl unter candump -tA -x can0 (ioBroker Raspi) als auch candump -tA -x vcan0 (Pi Zero an der Wärmepumpe)
                                      Im Log kommt diese Warnung ...

                                      canbus.0
                                      	2023-11-29 17:11:11.269	warn	Failed parsing JSON from canbus.0.680.json: No state found
                                      

                                      Danke für den A...tritt ....

                                      crycodeC 1 Antwort Letzte Antwort
                                      0
                                      • C cb187

                                        @crycode

                                        Hi hab mal ne Frage hat jetzt nichts direkt mit diesem Adapter was zu tun aber mit Canbus selber.
                                        Ich hab mir mal nen Esp32 bestellt und wollte mal den Canbus darüber testen.Da du dich ja ja so gut mit Canbus aus kennst, könntest du mir dabei mal helfen das in Esphome zuintegrieren?
                                        Also die config mit zuerstellen.
                                        Vielleicht interessiert dich das ja selber und hast List dazu.

                                        Gruss Christoph

                                        crycodeC Offline
                                        crycodeC Offline
                                        crycode
                                        Developer
                                        schrieb am zuletzt editiert von
                                        #349

                                        @cb187 sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                                        Ich hab mir mal nen Esp32 bestellt und wollte mal den Canbus darüber testen.Da du dich ja ja so gut mit Canbus aus kennst, könntest du mir dabei mal helfen das in Esphome zuintegrieren?

                                        Mit Esphome habe ich mich bislang überhaupt nicht beschäftigt und kann dir da wohl leider nicht viel weiter helfen. Meine Zeit ist aktuell auch etwas begrenzt für solche Basteleien. :(

                                        Meine Adapter: discord | canbus | ds18b20 | odl | radiohead

                                        1 Antwort Letzte Antwort
                                        0
                                        • hg6806H hg6806

                                          @crycode sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                                          @hg6806 Nimm mal den Haken bei "Gesehene Nachrichten automatisch hinzufügen" raus. Das brauchst du im normalen Betrieb nicht und könnte durch die Checks dabei im Hintergrund durchaus etwas mehr Systemlast bringen.

                                          Hat jetzt nicht wirklich was gebracht.
                                          Echt seltsam.
                                          Der CAN-Adapter steht halt immer an 2. Stelle bei der Auslastung von ioBroker und machen muss er ja eigentlich nicht viel.

                                          crycodeC Offline
                                          crycodeC Offline
                                          crycode
                                          Developer
                                          schrieb am zuletzt editiert von
                                          #350

                                          @hg6806 sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                                          Der CAN-Adapter steht halt immer an 2. Stelle bei der Auslastung von ioBroker und machen muss er ja eigentlich nicht viel.

                                          Seltsam... kann ich mir aktuell aber auch nicht wirklich erklären.
                                          Bei mir läuft der Adapter (allerdings mit anderer Hardware als "Gegenstelle" am Bus) mit nicht nennenswerter Auslastung.
                                          Im htop tauchte er bei dir doch auch nicht direkt auf, oder? Schau am besten noch mal mit htop -u iobroker nach...

                                          Meine Adapter: discord | canbus | ds18b20 | odl | radiohead

                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          737

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe