Solaredge - modbus
-
Hi all,
I have a SE8K-RWB48BFN4 with a three-phase Backup Interface (BIEU3P) and a SolarEdge Home Battery 48V (3 modules, 14.55 kWh). The hardware commissioning appears correct — BIEU3P is physically installed, RS485 wiring is in place, battery is charging/discharging normally.
However, during blackout tests the system does not hold island mode: loads power up for ~1 second, then the inverter shuts down, retries every 10-15 seconds in a loop.
Reading the inverter via Modbus TCP (port 1502) I found that register 63250 (proprietary SolarEdge, community-identified as "Backup Enable") reads 0 on my system.
My question: on your SE8K-RWB48 or SE10K-RWB48 with a working Backup Interface, what value does register 63250 return?
from pymodbus.client import ModbusTcpClient
client = ModbusTcpClient('YOUR_INVERTER_IP', port=1502, timeout=5)
client.connect()
r = client.read_holding_registers(address=63250, count=1, device_id=1)
print(f"Register 63250: {r.registers[0]}")
client.close()
I expect the value should be 1 on a correctly commissioned system, but I would appreciate confirmation from someone whose backup is actually working.
Thanks in advance. -
H Homoran verschob dieses Thema von Praktische Anwendungen (Showcase) am
Hey! Du scheinst an dieser Unterhaltung interessiert zu sein, hast aber noch kein Konto.
Hast du es satt, bei jedem Besuch durch die gleichen Beiträge zu scrollen? Wenn du dich für ein Konto anmeldest, kommst du immer genau dorthin zurück, wo du zuvor warst, und kannst dich über neue Antworten benachrichtigen lassen (entweder per E-Mail oder Push-Benachrichtigung). Du kannst auch Lesezeichen speichern und Beiträge positiv bewerten, um anderen Community-Mitgliedern deine Wertschätzung zu zeigen.