Skip to content
  • Home
  • Recent
  • Tags
  • 0 Unread 0
  • Categories
  • Unreplied
  • Popular
  • GitHub
  • Docu
  • Hilfe
Skins
  • Light
  • Brite
  • Cerulean
  • Cosmo
  • Flatly
  • Journal
  • Litera
  • Lumen
  • Lux
  • Materia
  • Minty
  • Morph
  • Pulse
  • Sandstone
  • Simplex
  • Sketchy
  • Spacelab
  • United
  • Yeti
  • Zephyr
  • Dark
  • Cyborg
  • Darkly
  • Quartz
  • Slate
  • Solar
  • Superhero
  • Vapor

  • Default (No Skin)
  • No Skin
Collapse
ioBroker Logo

Community Forum

donate donate
  1. ioBroker Community Home
  2. Deutsch
  3. Tester
  4. Alpha Testing: OCPP Wallbox Adapter

NEWS

  • Jahresrückblick 2025 – unser neuer Blogbeitrag ist online! ✨
    BluefoxB
    Bluefox
    16
    1
    1.8k

  • Neuer Blogbeitrag: Monatsrückblick - Dezember 2025 🎄
    BluefoxB
    Bluefox
    13
    1
    895

  • Weihnachtsangebot 2025! 🎄
    BluefoxB
    Bluefox
    25
    1
    2.1k

Alpha Testing: OCPP Wallbox Adapter

Scheduled Pinned Locked Moved Tester
ocppwallboxadapter
448 Posts 49 Posters 120.3k Views 47 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • foxriver76F foxriver76

    @frank11 Hm also entweder habe ich da noch einen Bug oder irgendwas anderes stimmt nicht. Kannst du mal ein Screenshot zeigen vom chargeLimit und den darüberliegenden States.

    F Offline
    F Offline
    frank11
    wrote on last edited by
    #274

    @foxriver76

    Bildschirm­foto 2023-01-17 um 14.56.42.png

    foxriver76F 1 Reply Last reply
    0
    • F frank11

      @foxriver76

      Bildschirm­foto 2023-01-17 um 14.56.42.png

      foxriver76F Offline
      foxriver76F Offline
      foxriver76
      Developer
      wrote on last edited by
      #275

      @frank11 danke, ja schaut gut aus.

      Ah.. bitte keine Datenpunkte in Adaptern manuell erzeugen, den chargeLimitType bitte wieder löschen aus der configuration und den Channel NaN entsprechend auch löschen, ansonsten schaut das gut aus.

      Videotutorials & mehr

      Hier könnt ihr mich unterstützen.

      1 Reply Last reply
      0
      • foxriver76F foxriver76

        @fl4sh-0 JA der Connector 0 wird weiterhin angelegt, allerdings mit deutlich reduzierten States. Diese States haben lt. OCPP Standard eine besondere Bedeutung, z. B. lässt sich damit der Status aller Connectoren auf ein mal ändern und es werden auch Daten auf diese Connector ID teilweise gesendet.

        ìdTag kann vom Nutzer definiert werden und wird mit in die startTransaction gepackt, war mal ein Feature Request, ob das tatsächlich von WBs benötigt wird weiß ich nicht. Wohl nur wenn eine Local Auth Liste genutzt wird die nur bestimmte idTags zulässt. Ich kann gerne einbauen, dass der tatsächliche idTag ausgelesen wird, falls das für dich wichtig ist. Ich prüfe dann nur mal ob sich das beißt in einem State zum schreiben und lesen des Tags.

        numberPhases gleiches Spiel, sollte also möglich sein z. B. 1 zu setzen und er lädt einphasig (falls WB unterstützt) sprich was die WB daraus macht ist eine andere Frage.

        F Offline
        F Offline
        fL4sH 0
        wrote on last edited by fL4sH 0
        #276

        @foxriver76
        Moin, hier ist ein Auszug von den idTags die der ioBroker schreibt und von meinen RFID-Chips. Das funktioniert schon mal einwandfrei.

        365a37c9-adce-4989-952a-37afadc2a2cd-image.png

        Ich habe nur noch einen Fehler festgestellt. Bei der Ladung über einen RFID-Chip, ist es komischerweise egal ob der RFID-Chip in der Box registriert ist oder nicht. Man kann die Transaktion mit allen RFID-Chips starten und die Ladung beginnt. Obwohl in der Wallbox nur ein RFID-Chip autorisiert ist. Liegt das an der Wallbox selber oder wird die Autorisierung nicht geprüft ?

        1d671c30-dcde-45ea-8980-ed8d15d55a77-image.png

        Das sind die beiden RFID-Chips die nicht in der Wallbox hinterlegt sind.

        Vom Prinzip müsste die Logik ja sein das der idTag (RFID-Chip) der die Transaktion startet, diesen auch nur beenden kann.
        Jetzt könnte die Ladung auch von jemand fremden gestoppt werden!

        F foxriver76F 2 Replies Last reply
        0
        • F fL4sH 0

          @foxriver76
          Moin, hier ist ein Auszug von den idTags die der ioBroker schreibt und von meinen RFID-Chips. Das funktioniert schon mal einwandfrei.

          365a37c9-adce-4989-952a-37afadc2a2cd-image.png

          Ich habe nur noch einen Fehler festgestellt. Bei der Ladung über einen RFID-Chip, ist es komischerweise egal ob der RFID-Chip in der Box registriert ist oder nicht. Man kann die Transaktion mit allen RFID-Chips starten und die Ladung beginnt. Obwohl in der Wallbox nur ein RFID-Chip autorisiert ist. Liegt das an der Wallbox selber oder wird die Autorisierung nicht geprüft ?

          1d671c30-dcde-45ea-8980-ed8d15d55a77-image.png

          Das sind die beiden RFID-Chips die nicht in der Wallbox hinterlegt sind.

          Vom Prinzip müsste die Logik ja sein das der idTag (RFID-Chip) der die Transaktion startet, diesen auch nur beenden kann.
          Jetzt könnte die Ladung auch von jemand fremden gestoppt werden!

          F Offline
          F Offline
          fL4sH 0
          wrote on last edited by fL4sH 0
          #277

          @foxriver76
          Seid der neuen Version 0.11.1 kommen häufiger die Warnung das die Transaktion von der Ladesäule abgelehnt wird.

          e575978f-81d8-4fce-af89-c5641aaa9bac-image.png

          Anscheinend kommt dieser Fehler nur wenn man eine Transaktion startet und das Chargelimit vorher gesetzt wurde.

          foxriver76F 1 Reply Last reply
          0
          • F fL4sH 0

            @foxriver76
            Seid der neuen Version 0.11.1 kommen häufiger die Warnung das die Transaktion von der Ladesäule abgelehnt wird.

            e575978f-81d8-4fce-af89-c5641aaa9bac-image.png

            Anscheinend kommt dieser Fehler nur wenn man eine Transaktion startet und das Chargelimit vorher gesetzt wurde.

            foxriver76F Offline
            foxriver76F Offline
            foxriver76
            Developer
            wrote on last edited by
            #278

            @fl4sh-0 Gibt es beim beenden des Vorgangs auch eine Warnung, dass er in ein nicht existierendes Objekt schreibt? Ich hatte letztens, dass die WB beim Start die Verbindung verloren hat und sich eine eigene Transaktions-ID festgelegt hat und dann kennt der Adapter diese nicht und kann die Transaktion nicht stoppen.

            Videotutorials & mehr

            Hier könnt ihr mich unterstützen.

            F 1 Reply Last reply
            0
            • foxriver76F foxriver76

              @fl4sh-0 Gibt es beim beenden des Vorgangs auch eine Warnung, dass er in ein nicht existierendes Objekt schreibt? Ich hatte letztens, dass die WB beim Start die Verbindung verloren hat und sich eine eigene Transaktions-ID festgelegt hat und dann kennt der Adapter diese nicht und kann die Transaktion nicht stoppen.

              F Offline
              F Offline
              fL4sH 0
              wrote on last edited by
              #279

              @foxriver76 Beim Beenden des Vorgangs kommt keine Warnung, dass er in ein nicht existierendes Objekt schreibt.
              Die beiden Warnungen kommen lediglich wenn transactionActive=true und Chargelimit=6A vorher gesetzt wurde.
              Dann kommt die Warnung.

              Starting transaction has been rejected by charge point
              

              Wenn ich anschließend transactionActive=false setze und Chargelimit=6A immer noch gesetzt ist.

              Dann kommt diese Warnung.

              Stopping transaction has been rejected by charge point
              

              Wenn das Charglimit=0A kann die Transaktion ganz normal gestartet und gestoppt werden.

              F 1 Reply Last reply
              0
              • F fL4sH 0

                @foxriver76 Beim Beenden des Vorgangs kommt keine Warnung, dass er in ein nicht existierendes Objekt schreibt.
                Die beiden Warnungen kommen lediglich wenn transactionActive=true und Chargelimit=6A vorher gesetzt wurde.
                Dann kommt die Warnung.

                Starting transaction has been rejected by charge point
                

                Wenn ich anschließend transactionActive=false setze und Chargelimit=6A immer noch gesetzt ist.

                Dann kommt diese Warnung.

                Stopping transaction has been rejected by charge point
                

                Wenn das Charglimit=0A kann die Transaktion ganz normal gestartet und gestoppt werden.

                F Offline
                F Offline
                fL4sH 0
                wrote on last edited by fL4sH 0
                #280

                @foxriver76 Was mir noch aufgefallen ist, dass die MeterValues nach der Beendigung des Ladevorgangs einfrieren bzw. nicht mehr aktualisiert werden Die Daten werden erst aktualisiert werden wenn man den Adapter neu startet oder eine neue Transaktion beginnt. Ist dieses Verhalten normal ? Besteht die Möglichkeit das die MeterValues nach dem Beenden eines Ladevorgangs nochmal abgeholt werden ?

                8fffd335-2357-47bb-af2a-35d820df3554-image.png

                foxriver76F 1 Reply Last reply
                0
                • F fL4sH 0

                  @foxriver76 Was mir noch aufgefallen ist, dass die MeterValues nach der Beendigung des Ladevorgangs einfrieren bzw. nicht mehr aktualisiert werden Die Daten werden erst aktualisiert werden wenn man den Adapter neu startet oder eine neue Transaktion beginnt. Ist dieses Verhalten normal ? Besteht die Möglichkeit das die MeterValues nach dem Beenden eines Ladevorgangs nochmal abgeholt werden ?

                  8fffd335-2357-47bb-af2a-35d820df3554-image.png

                  foxriver76F Offline
                  foxriver76F Offline
                  foxriver76
                  Developer
                  wrote on last edited by
                  #281

                  @fl4sh-0 im configuration channel gibt es Werte um das Intervall festzulegen in dem die WB sendet. Im Intervall ClockAlignedDataInterval (Sekunden) werden alle Werte aus MeterValuesAlignedData gesendet.

                  Hier evtl. auch mal checken was in ChargingScheduleAllowedChargingRateUnit steht.

                  Videotutorials & mehr

                  Hier könnt ihr mich unterstützen.

                  F 2 Replies Last reply
                  0
                  • foxriver76F foxriver76

                    @fl4sh-0 im configuration channel gibt es Werte um das Intervall festzulegen in dem die WB sendet. Im Intervall ClockAlignedDataInterval (Sekunden) werden alle Werte aus MeterValuesAlignedData gesendet.

                    Hier evtl. auch mal checken was in ChargingScheduleAllowedChargingRateUnit steht.

                    F Offline
                    F Offline
                    fL4sH 0
                    wrote on last edited by
                    #282

                    @foxriver76 Ok, das werde ich mal prüfen.

                    Die Änderung vom idTag sieht gut aus.
                    4682686d-21ff-4b8b-9c6f-0fc62595483a-image.png

                    1 Reply Last reply
                    0
                    • foxriver76F foxriver76

                      @fl4sh-0 im configuration channel gibt es Werte um das Intervall festzulegen in dem die WB sendet. Im Intervall ClockAlignedDataInterval (Sekunden) werden alle Werte aus MeterValuesAlignedData gesendet.

                      Hier evtl. auch mal checken was in ChargingScheduleAllowedChargingRateUnit steht.

                      F Offline
                      F Offline
                      fL4sH 0
                      wrote on last edited by
                      #283

                      @foxriver76 said in Alpha Testing: OCPP Wallbox Adapter:

                      @fl4sh-0 im configuration channel gibt es Werte um das Intervall festzulegen in dem die WB sendet. Im Intervall ClockAlignedDataInterval (Sekunden) werden alle Werte aus MeterValuesAlignedData gesendet.

                      Hier evtl. auch mal checken was in ChargingScheduleAllowedChargingRateUnit steht.

                      Hier mal die drei Werte.
                      ddc2f292-2f69-463f-a6e1-2e18def0b7ea-image.png
                      d373a50f-7b2e-466e-9c8a-d6994cc7b5a7-image.png
                      e493f6e9-3050-4613-9c01-762e8ac985f6-image.png

                      Editierbar ist ClockAlignedDataInterval Wenn ich dort 55 Sek. eintrage aktualisiert er mir nur den Wert
                      0a5c54b8-96ca-46a6-9c7b-85989ea718fb-image.png und der ist meiner Meinung nach auch falsch.

                      foxriver76F 1 Reply Last reply
                      0
                      • F fL4sH 0

                        @foxriver76 said in Alpha Testing: OCPP Wallbox Adapter:

                        @fl4sh-0 im configuration channel gibt es Werte um das Intervall festzulegen in dem die WB sendet. Im Intervall ClockAlignedDataInterval (Sekunden) werden alle Werte aus MeterValuesAlignedData gesendet.

                        Hier evtl. auch mal checken was in ChargingScheduleAllowedChargingRateUnit steht.

                        Hier mal die drei Werte.
                        ddc2f292-2f69-463f-a6e1-2e18def0b7ea-image.png
                        d373a50f-7b2e-466e-9c8a-d6994cc7b5a7-image.png
                        e493f6e9-3050-4613-9c01-762e8ac985f6-image.png

                        Editierbar ist ClockAlignedDataInterval Wenn ich dort 55 Sek. eintrage aktualisiert er mir nur den Wert
                        0a5c54b8-96ca-46a6-9c7b-85989ea718fb-image.png und der ist meiner Meinung nach auch falsch.

                        foxriver76F Offline
                        foxriver76F Offline
                        foxriver76
                        Developer
                        wrote on last edited by foxriver76
                        #284

                        @fl4sh-0 Schau mal in MeterValuesSampledData sind die Datenpunkte die während einer Transaktion alle MeterValueSampleInterval Sekunden übertragen werden. Ohne aktive Transaktion werden wie vorher erwähnt alle ClockAlignedDataInterval Sekunden die Werte aus MeterValuesAlignedData übertragen, wenn du da die gleichen Werte haben möchtest, schreib den Inhalt von MeterValuesSampledData auch in MeterValuesAlignedData.

                        Warum der Wert falsch ist, kann ich aktuell nichts zu sagen.

                        Videotutorials & mehr

                        Hier könnt ihr mich unterstützen.

                        F 1 Reply Last reply
                        0
                        • foxriver76F foxriver76

                          @fl4sh-0 Schau mal in MeterValuesSampledData sind die Datenpunkte die während einer Transaktion alle MeterValueSampleInterval Sekunden übertragen werden. Ohne aktive Transaktion werden wie vorher erwähnt alle ClockAlignedDataInterval Sekunden die Werte aus MeterValuesAlignedData übertragen, wenn du da die gleichen Werte haben möchtest, schreib den Inhalt von MeterValuesSampledData auch in MeterValuesAlignedData.

                          Warum der Wert falsch ist, kann ich aktuell nichts zu sagen.

                          F Offline
                          F Offline
                          fL4sH 0
                          wrote on last edited by fL4sH 0
                          #285

                          @foxriver76

                          Wenn ich genau die gleich Werte wie in der MeterValuesSampledData eintrage, steht im Log Cannot change.....
                          Wenn ich mich auf 4 Werte beschränke, funktioniert die Aktualisierung zwar aber nur auf "Oberster Ebene"

                          a7a27308-14d4-47fd-996c-90589908c5a9-image.png

                          ocpp.0 2023-01-18 11:20:40.322	debug	{"connectorId":1,"meterValue":[{"timestamp":"2023-01-18T10:20:40.000Z","sampledValue":[{"value":"0.0","context":"Sample.Clock","format":"Raw","measurand":"Current.Import","location":"Inlet"},{"value":"6","context":"Sample.Clock","format":"Raw","measurand":"Current.Offered","location":"Inlet"},{"value":"1284601","context":"Sample.Clock","format":"Raw","measurand":"Energy.Active.Import.Register","location":"Inlet"},{"value":"0","context":"Sample.Clock","format":"Raw","measurand":"Power.Active.Import","location":"Inlet"}]}],"commandOcpp":"MeterValues"}
                          ocpp.0 2023-01-18 11:20:17.839	info	Changing configuration (device: /TACW1142021G1020) of "MeterValuesAlignedData" to "Current.Import,Current.Offered,Energy.Active.Import.Register,Power.Active.Import"
                          ocpp.0 2023-01-18 11:20:00.276	info	Received MeterValues from "/TACW1142021G1020.1"
                          ocpp.0 2023-01-18 11:20:00.276	debug	{"connectorId":1,"meterValue":[{"timestamp":"2023-01-18T10:20:00.000Z","sampledValue":[{"value":"1284601","context":"Sample.Clock","format":"Raw","measurand":"Energy.Active.Import.Register","location":"Inlet"},{"value":"0","context":"Sample.Clock","format":"Raw","measurand":"Power.Active.Import","location":"Inlet"},{"value":"2269","context":"Sample.Clock","format":"Raw","measurand":"Voltage","location":"Inlet"}]}],"commandOcpp":"MeterValues"}
                          ocpp.0 2023-01-18 11:19:46.662	debug	Received heartbeat from "/TACW1142021G1020"
                          ocpp.0 2023-01-18 11:19:46.661	debug	{"commandOcpp":"Heartbeat"}
                          ocpp.0 2023-01-18 11:19:43.338	warn	Cannot change confiuration of /TACW1142021G1020 (key: MeterValuesAlignedData, value: Current.Import,Current.Offered,Energy.Active.Import.Register,Power.Active.Import,Voltage): Rejected
                          

                          7fcda12c-a045-4301-b2b0-8157e4ddad43-image.png
                          Dieser Wert ist der Gesamtzähler der Wallbox sein.

                          foxriver76F 1 Reply Last reply
                          0
                          • F Offline
                            F Offline
                            frank11
                            wrote on last edited by
                            #286

                            Ich habe gerade irgendwas von RFID gelesen.

                            Ich lade im Moment nur ein Auto mit RFID-Karte als Authentifizierung.
                            Da kann man auslesen, mit welcher Karte geladen wurde?

                            Dann könnte das zweite BEV kommen.

                            foxriver76F 1 Reply Last reply
                            0
                            • F fL4sH 0

                              @foxriver76

                              Wenn ich genau die gleich Werte wie in der MeterValuesSampledData eintrage, steht im Log Cannot change.....
                              Wenn ich mich auf 4 Werte beschränke, funktioniert die Aktualisierung zwar aber nur auf "Oberster Ebene"

                              a7a27308-14d4-47fd-996c-90589908c5a9-image.png

                              ocpp.0 2023-01-18 11:20:40.322	debug	{"connectorId":1,"meterValue":[{"timestamp":"2023-01-18T10:20:40.000Z","sampledValue":[{"value":"0.0","context":"Sample.Clock","format":"Raw","measurand":"Current.Import","location":"Inlet"},{"value":"6","context":"Sample.Clock","format":"Raw","measurand":"Current.Offered","location":"Inlet"},{"value":"1284601","context":"Sample.Clock","format":"Raw","measurand":"Energy.Active.Import.Register","location":"Inlet"},{"value":"0","context":"Sample.Clock","format":"Raw","measurand":"Power.Active.Import","location":"Inlet"}]}],"commandOcpp":"MeterValues"}
                              ocpp.0 2023-01-18 11:20:17.839	info	Changing configuration (device: /TACW1142021G1020) of "MeterValuesAlignedData" to "Current.Import,Current.Offered,Energy.Active.Import.Register,Power.Active.Import"
                              ocpp.0 2023-01-18 11:20:00.276	info	Received MeterValues from "/TACW1142021G1020.1"
                              ocpp.0 2023-01-18 11:20:00.276	debug	{"connectorId":1,"meterValue":[{"timestamp":"2023-01-18T10:20:00.000Z","sampledValue":[{"value":"1284601","context":"Sample.Clock","format":"Raw","measurand":"Energy.Active.Import.Register","location":"Inlet"},{"value":"0","context":"Sample.Clock","format":"Raw","measurand":"Power.Active.Import","location":"Inlet"},{"value":"2269","context":"Sample.Clock","format":"Raw","measurand":"Voltage","location":"Inlet"}]}],"commandOcpp":"MeterValues"}
                              ocpp.0 2023-01-18 11:19:46.662	debug	Received heartbeat from "/TACW1142021G1020"
                              ocpp.0 2023-01-18 11:19:46.661	debug	{"commandOcpp":"Heartbeat"}
                              ocpp.0 2023-01-18 11:19:43.338	warn	Cannot change confiuration of /TACW1142021G1020 (key: MeterValuesAlignedData, value: Current.Import,Current.Offered,Energy.Active.Import.Register,Power.Active.Import,Voltage): Rejected
                              

                              7fcda12c-a045-4301-b2b0-8157e4ddad43-image.png
                              Dieser Wert ist der Gesamtzähler der Wallbox sein.

                              foxriver76F Offline
                              foxriver76F Offline
                              foxriver76
                              Developer
                              wrote on last edited by
                              #287

                              @fl4sh-0 Es gibt noch MeterValuesAlignedDataMaxLength und das gleiche für MeterValuesSampledDataMaxLength evtl. lässt sampled Data mehr Punkte zu als aligned data?

                              Videotutorials & mehr

                              Hier könnt ihr mich unterstützen.

                              F 1 Reply Last reply
                              0
                              • F frank11

                                Ich habe gerade irgendwas von RFID gelesen.

                                Ich lade im Moment nur ein Auto mit RFID-Karte als Authentifizierung.
                                Da kann man auslesen, mit welcher Karte geladen wurde?

                                Dann könnte das zweite BEV kommen.

                                foxriver76F Offline
                                foxriver76F Offline
                                foxriver76
                                Developer
                                wrote on last edited by
                                #288

                                @frank11 Ja der idTag sollte bei jeder Transaktion synchronisiert werden.

                                Videotutorials & mehr

                                Hier könnt ihr mich unterstützen.

                                F 1 Reply Last reply
                                0
                                • foxriver76F foxriver76

                                  @frank11 Ja der idTag sollte bei jeder Transaktion synchronisiert werden.

                                  F Offline
                                  F Offline
                                  frank11
                                  wrote on last edited by
                                  #289

                                  @foxriver76 OK, dann werde ich den Wert mal in die Datenbank mitloggen lassen.

                                  1 Reply Last reply
                                  0
                                  • F fL4sH 0

                                    @foxriver76
                                    Moin, hier ist ein Auszug von den idTags die der ioBroker schreibt und von meinen RFID-Chips. Das funktioniert schon mal einwandfrei.

                                    365a37c9-adce-4989-952a-37afadc2a2cd-image.png

                                    Ich habe nur noch einen Fehler festgestellt. Bei der Ladung über einen RFID-Chip, ist es komischerweise egal ob der RFID-Chip in der Box registriert ist oder nicht. Man kann die Transaktion mit allen RFID-Chips starten und die Ladung beginnt. Obwohl in der Wallbox nur ein RFID-Chip autorisiert ist. Liegt das an der Wallbox selber oder wird die Autorisierung nicht geprüft ?

                                    1d671c30-dcde-45ea-8980-ed8d15d55a77-image.png

                                    Das sind die beiden RFID-Chips die nicht in der Wallbox hinterlegt sind.

                                    Vom Prinzip müsste die Logik ja sein das der idTag (RFID-Chip) der die Transaktion startet, diesen auch nur beenden kann.
                                    Jetzt könnte die Ladung auch von jemand fremden gestoppt werden!

                                    foxriver76F Offline
                                    foxriver76F Offline
                                    foxriver76
                                    Developer
                                    wrote on last edited by
                                    #290

                                    @fl4sh-0 0.12.0

                                    • (foxriver76) the idTag for remote transactions is now ioBroker persistent over all transactions
                                    • (foxriver76) implemented the management of authentication list
                                    • (foxriver76) only create states if supported by profile (closes #22)
                                    • (foxriver76) increased stability on first connection

                                    Im Connector 0 sollte es eine authList geben, da die Tags Komma separiert eintragen, es wird auch probiert diese bei der WB lokal zu hinterlegen falls unterstützt, falls sie nicht mit dem OCPP Server verbunden ist. Ansonsten gleicht der Server bei jedem Authorize Request nun mit den hinterlegten Tags ab.

                                    Videotutorials & mehr

                                    Hier könnt ihr mich unterstützen.

                                    F 1 Reply Last reply
                                    0
                                    • foxriver76F foxriver76

                                      @fl4sh-0 0.12.0

                                      • (foxriver76) the idTag for remote transactions is now ioBroker persistent over all transactions
                                      • (foxriver76) implemented the management of authentication list
                                      • (foxriver76) only create states if supported by profile (closes #22)
                                      • (foxriver76) increased stability on first connection

                                      Im Connector 0 sollte es eine authList geben, da die Tags Komma separiert eintragen, es wird auch probiert diese bei der WB lokal zu hinterlegen falls unterstützt, falls sie nicht mit dem OCPP Server verbunden ist. Ansonsten gleicht der Server bei jedem Authorize Request nun mit den hinterlegten Tags ab.

                                      F Offline
                                      F Offline
                                      fL4sH 0
                                      wrote on last edited by fL4sH 0
                                      #291

                                      @foxriver76 Der idTag vom ioBroker sowie die von den RFID-Chip funktionieren einwandfrei und auch die Autorisierung läuft nun. Nicht hinterlegte RFID-Chip können eine aktive Transaktion nicht mehr abbrechen und der Vorgang läuft weiter.

                                      Bei meiner Wallbox ABB Terra AC werden die registrierten RFID-Chip aus der Wallbox gelesen und zugelassen. Ein Eintrag in der authList war in meinem Fall nicht notwendig.

                                      Super Update vielen Dank.

                                      F 1 Reply Last reply
                                      0
                                      • F fL4sH 0

                                        @foxriver76 Der idTag vom ioBroker sowie die von den RFID-Chip funktionieren einwandfrei und auch die Autorisierung läuft nun. Nicht hinterlegte RFID-Chip können eine aktive Transaktion nicht mehr abbrechen und der Vorgang läuft weiter.

                                        Bei meiner Wallbox ABB Terra AC werden die registrierten RFID-Chip aus der Wallbox gelesen und zugelassen. Ein Eintrag in der authList war in meinem Fall nicht notwendig.

                                        Super Update vielen Dank.

                                        F Offline
                                        F Offline
                                        frank11
                                        wrote on last edited by
                                        #292

                                        @fl4sh-0 Meine WB unterstützt ja Local Auth List. Es funktionieren aber nur die beiden RFID Masterkarten, wenn ich nicht die DaheimLaden Cloud benutze.

                                        Kann ich die anderen (2) RFID-Karten manuell mit dieser authList erlauben?

                                        Nicht das das wichtig wäre, wir werden wohl nicht mehr als zwei Elektrofahrzeuge bekommen.
                                        Aber besser haben als brauchen. :-D

                                        foxriver76F F 2 Replies Last reply
                                        0
                                        • F frank11

                                          @fl4sh-0 Meine WB unterstützt ja Local Auth List. Es funktionieren aber nur die beiden RFID Masterkarten, wenn ich nicht die DaheimLaden Cloud benutze.

                                          Kann ich die anderen (2) RFID-Karten manuell mit dieser authList erlauben?

                                          Nicht das das wichtig wäre, wir werden wohl nicht mehr als zwei Elektrofahrzeuge bekommen.
                                          Aber besser haben als brauchen. :-D

                                          foxriver76F Offline
                                          foxriver76F Offline
                                          foxriver76
                                          Developer
                                          wrote on last edited by
                                          #293

                                          @frank11 Soweit ich weiß, sollte das gehen.

                                          Videotutorials & mehr

                                          Hier könnt ihr mich unterstützen.

                                          1 Reply Last reply
                                          1
                                          Reply
                                          • Reply as topic
                                          Log in to reply
                                          • Oldest to Newest
                                          • Newest to Oldest
                                          • Most Votes


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          406

                                          Online

                                          32.6k

                                          Users

                                          82.1k

                                          Topics

                                          1.3m

                                          Posts
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Login

                                          • Don't have an account? Register

                                          • Login or register to search.
                                          • First post
                                            Last post
                                          0
                                          • Home
                                          • Recent
                                          • Tags
                                          • Unread 0
                                          • Categories
                                          • Unreplied
                                          • Popular
                                          • GitHub
                                          • Docu
                                          • Hilfe