NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.2k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.9k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.2k

Modbus Problem Waveshare und SDM72D

Geplant Angeheftet Gesperrt Verschoben Entwicklung
18 Beiträge 7 Kommentatoren 1.6k Aufrufe 6 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • S stromen

    Hallo,

    ich habe ein Problem mit dem Modbus.
    Ich verwende ein waveshare RS485 to ETH mit einem SDM72D

    Seit langem hat alles einwandfrei funktioniert, auf einmal nicht mehr.
    Verändert wurde nichts.
    Neustart durchgeführt, Kabel usw. überprüft.

    Hat jemand einen Tipp?

    47AE7ECB-B3A8-4E10-94DB-B1083A954CDC.jpeg

    8757EB9C-509D-4DC9-A180-37080060250D.jpeg

    8E0267C6-BA26-4D38-9E1E-216A435E5233.jpeg

    C488265A-C4E8-4F24-9FA5-0FB0325E6723.jpeg

    wendy2702W Online
    wendy2702W Online
    wendy2702
    schrieb am zuletzt editiert von wendy2702
    #2

    @stromen

    Habe ein eigenes Thema daraus gemacht da es nicht mit einer Sammlung zu tun hat.

    Zusätzlich poste die logs bitte vollständig im Debug Mode als Text in Code Tags </> und nicht als Screenshot.

    In deinem Screenshot sind die Logs auch noch abgeschnitten.

    War der Haken bei „Aliases benutzen“ wirklich schon immer gesetzt?

    Wie sehen die Register aus?

    Bitte keine Fragen per PN, die gehören ins Forum!

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    S 1 Antwort Letzte Antwort
    1
    • wendy2702W wendy2702

      @stromen

      Habe ein eigenes Thema daraus gemacht da es nicht mit einer Sammlung zu tun hat.

      Zusätzlich poste die logs bitte vollständig im Debug Mode als Text in Code Tags </> und nicht als Screenshot.

      In deinem Screenshot sind die Logs auch noch abgeschnitten.

      War der Haken bei „Aliases benutzen“ wirklich schon immer gesetzt?

      Wie sehen die Register aus?

      S Offline
      S Offline
      stromen
      schrieb am zuletzt editiert von
      #3

      @wendy2702

      Hallo,

      danke für die Antwort. Sorry, reiche ich hiermit nach.

      Ja, meines wissens war der Haken schon immer gesetzt.
      Habe aber auch inzwischen mehrere Konfigurationen durchprobiert. Es lief ja seit knapp 2 Monaten einwandfrei, und es wurde nichts geändert.

      E5387A4D-8ABD-4970-A20C-057EB282EE98.jpeg

      
      2023-04-10 12:08:17.052 - error: modbus.0 (759) Reconnect did not help, restart adapter
      2023-04-10 12:08:17.053 - info: modbus.0 (759) Terminated (START_IMMEDIATELY_AFTER_STOP): Without reason
      2023-04-10 12:08:17.599 - info: host.iobroker instance system.adapter.modbus.0 terminated with code 156 (START_IMMEDIATELY_AFTER_STOP)
      2023-04-10 12:08:17.599 - info: host.iobroker Restart adapter system.adapter.modbus.0 because enabled
      2023-04-10 12:08:18.630 - info: host.iobroker instance system.adapter.modbus.0 started with pid 774
      2023-04-10 12:08:19.755 - info: modbus.0 (774) starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
      2023-04-10 12:08:20.052 - info: modbus.0 (774) Connected to slave 192.168.1.200
      2023-04-10 12:08:25.059 - warn: modbus.0 (774) Error: undefined
      2023-04-10 12:08:25.060 - error: modbus.0 (774) Request timed out.
      2023-04-10 12:08:25.060 - error: modbus.0 (774) Client in error state.
      2023-04-10 12:08:25.061 - warn: modbus.0 (774) Poll error count: 1 code: {"err":"timeout","timeout":5000}
      2023-04-10 12:08:26.062 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
      2023-04-10 12:09:26.064 - info: modbus.0 (774) Connected to slave 192.168.1.200
      2023-04-10 12:09:31.066 - warn: modbus.0 (774) Error: undefined
      2023-04-10 12:09:31.067 - error: modbus.0 (774) Request timed out.
      2023-04-10 12:09:31.067 - error: modbus.0 (774) Client in error state.
      2023-04-10 12:09:31.068 - warn: modbus.0 (774) Poll error count: 2 code: {"err":"timeout","timeout":5000}
      2023-04-10 12:09:32.068 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
      2023-04-10 12:10:32.070 - info: modbus.0 (774) Connected to slave 192.168.1.200
      2023-04-10 12:10:37.072 - warn: modbus.0 (774) Error: undefined
      2023-04-10 12:10:37.072 - error: modbus.0 (774) Request timed out.
      2023-04-10 12:10:37.072 - error: modbus.0 (774) Client in error state.
      2023-04-10 12:10:37.073 - warn: modbus.0 (774) Poll error count: 3 code: {"err":"timeout","timeout":5000}
      2023-04-10 12:10:38.072 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
      2023-04-10 12:11:38.076 - info: modbus.0 (774) Connected to slave 192.168.1.200
      2023-04-10 12:11:43.078 - warn: modbus.0 (774) Error: undefined
      2023-04-10 12:11:43.078 - error: modbus.0 (774) Request timed out.
      2023-04-10 12:11:43.078 - error: modbus.0 (774) Client in error state.
      2023-04-10 12:11:43.079 - warn: modbus.0 (774) Poll error count: 4 code: {"err":"timeout","timeout":5000}
      2023-04-10 12:11:44.079 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
      2023-04-10 12:12:44.081 - info: modbus.0 (774) Connected to slave 192.168.1.200
      2023-04-10 12:12:49.083 - warn: modbus.0 (774) Error: undefined
      2023-04-10 12:12:49.084 - error: modbus.0 (774) Request timed out.
      2023-04-10 12:12:49.084 - error: modbus.0 (774) Client in error state.
      2023-04-10 12:12:49.084 - warn: modbus.0 (774) Poll error count: 5 code: {"err":"timeout","timeout":5000}
      2023-04-10 12:12:50.085 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
      2023-04-10 12:13:50.087 - info: modbus.0 (774) Connected to slave 192.168.1.200
      2023-04-10 12:13:55.089 - warn: modbus.0 (774) Error: undefined
      2023-04-10 12:13:55.089 - error: modbus.0 (774) Request timed out.
      2023-04-10 12:13:55.090 - error: modbus.0 (774) Client in error state.
      2023-04-10 12:13:55.090 - warn: modbus.0 (774) Poll error count: 6 code: {"err":"timeout","timeout":5000}
      2023-04-10 12:13:56.092 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
      2023-04-10 12:14:56.096 - info: modbus.0 (774) Connected to slave 192.168.1.200
      2023-04-10 12:15:01.098 - warn: modbus.0 (774) Error: undefined
      2023-04-10 12:15:01.099 - error: modbus.0 (774) Request timed out.
      2023-04-10 12:15:01.099 - error: modbus.0 (774) Client in error state.
      2023-04-10 12:15:01.100 - warn: modbus.0 (774) Poll error count: 7 code: {"err":"timeout","timeout":5000}
      2023-04-10 12:15:02.100 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
      
      
      HomoranH GlasfaserG 2 Antworten Letzte Antwort
      0
      • S stromen

        @wendy2702

        Hallo,

        danke für die Antwort. Sorry, reiche ich hiermit nach.

        Ja, meines wissens war der Haken schon immer gesetzt.
        Habe aber auch inzwischen mehrere Konfigurationen durchprobiert. Es lief ja seit knapp 2 Monaten einwandfrei, und es wurde nichts geändert.

        E5387A4D-8ABD-4970-A20C-057EB282EE98.jpeg

        
        2023-04-10 12:08:17.052 - error: modbus.0 (759) Reconnect did not help, restart adapter
        2023-04-10 12:08:17.053 - info: modbus.0 (759) Terminated (START_IMMEDIATELY_AFTER_STOP): Without reason
        2023-04-10 12:08:17.599 - info: host.iobroker instance system.adapter.modbus.0 terminated with code 156 (START_IMMEDIATELY_AFTER_STOP)
        2023-04-10 12:08:17.599 - info: host.iobroker Restart adapter system.adapter.modbus.0 because enabled
        2023-04-10 12:08:18.630 - info: host.iobroker instance system.adapter.modbus.0 started with pid 774
        2023-04-10 12:08:19.755 - info: modbus.0 (774) starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
        2023-04-10 12:08:20.052 - info: modbus.0 (774) Connected to slave 192.168.1.200
        2023-04-10 12:08:25.059 - warn: modbus.0 (774) Error: undefined
        2023-04-10 12:08:25.060 - error: modbus.0 (774) Request timed out.
        2023-04-10 12:08:25.060 - error: modbus.0 (774) Client in error state.
        2023-04-10 12:08:25.061 - warn: modbus.0 (774) Poll error count: 1 code: {"err":"timeout","timeout":5000}
        2023-04-10 12:08:26.062 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
        2023-04-10 12:09:26.064 - info: modbus.0 (774) Connected to slave 192.168.1.200
        2023-04-10 12:09:31.066 - warn: modbus.0 (774) Error: undefined
        2023-04-10 12:09:31.067 - error: modbus.0 (774) Request timed out.
        2023-04-10 12:09:31.067 - error: modbus.0 (774) Client in error state.
        2023-04-10 12:09:31.068 - warn: modbus.0 (774) Poll error count: 2 code: {"err":"timeout","timeout":5000}
        2023-04-10 12:09:32.068 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
        2023-04-10 12:10:32.070 - info: modbus.0 (774) Connected to slave 192.168.1.200
        2023-04-10 12:10:37.072 - warn: modbus.0 (774) Error: undefined
        2023-04-10 12:10:37.072 - error: modbus.0 (774) Request timed out.
        2023-04-10 12:10:37.072 - error: modbus.0 (774) Client in error state.
        2023-04-10 12:10:37.073 - warn: modbus.0 (774) Poll error count: 3 code: {"err":"timeout","timeout":5000}
        2023-04-10 12:10:38.072 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
        2023-04-10 12:11:38.076 - info: modbus.0 (774) Connected to slave 192.168.1.200
        2023-04-10 12:11:43.078 - warn: modbus.0 (774) Error: undefined
        2023-04-10 12:11:43.078 - error: modbus.0 (774) Request timed out.
        2023-04-10 12:11:43.078 - error: modbus.0 (774) Client in error state.
        2023-04-10 12:11:43.079 - warn: modbus.0 (774) Poll error count: 4 code: {"err":"timeout","timeout":5000}
        2023-04-10 12:11:44.079 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
        2023-04-10 12:12:44.081 - info: modbus.0 (774) Connected to slave 192.168.1.200
        2023-04-10 12:12:49.083 - warn: modbus.0 (774) Error: undefined
        2023-04-10 12:12:49.084 - error: modbus.0 (774) Request timed out.
        2023-04-10 12:12:49.084 - error: modbus.0 (774) Client in error state.
        2023-04-10 12:12:49.084 - warn: modbus.0 (774) Poll error count: 5 code: {"err":"timeout","timeout":5000}
        2023-04-10 12:12:50.085 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
        2023-04-10 12:13:50.087 - info: modbus.0 (774) Connected to slave 192.168.1.200
        2023-04-10 12:13:55.089 - warn: modbus.0 (774) Error: undefined
        2023-04-10 12:13:55.089 - error: modbus.0 (774) Request timed out.
        2023-04-10 12:13:55.090 - error: modbus.0 (774) Client in error state.
        2023-04-10 12:13:55.090 - warn: modbus.0 (774) Poll error count: 6 code: {"err":"timeout","timeout":5000}
        2023-04-10 12:13:56.092 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
        2023-04-10 12:14:56.096 - info: modbus.0 (774) Connected to slave 192.168.1.200
        2023-04-10 12:15:01.098 - warn: modbus.0 (774) Error: undefined
        2023-04-10 12:15:01.099 - error: modbus.0 (774) Request timed out.
        2023-04-10 12:15:01.099 - error: modbus.0 (774) Client in error state.
        2023-04-10 12:15:01.100 - warn: modbus.0 (774) Poll error count: 7 code: {"err":"timeout","timeout":5000}
        2023-04-10 12:15:02.100 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
        
        
        HomoranH Nicht stören
        HomoranH Nicht stören
        Homoran
        Global Moderator Administrators
        schrieb am zuletzt editiert von
        #4

        @stromen sagte in Modbus Problem Waveshare und SDM72D:

        Disconnected from slave 192.168.1.200

        wer ist das?

        ist der host online?
        per ping?
        im router!?

        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

        S 1 Antwort Letzte Antwort
        0
        • HomoranH Homoran

          @stromen sagte in Modbus Problem Waveshare und SDM72D:

          Disconnected from slave 192.168.1.200

          wer ist das?

          ist der host online?
          per ping?
          im router!?

          S Offline
          S Offline
          stromen
          schrieb am zuletzt editiert von
          #5

          @homoran

          Der waveshare RS485. Ich kann ganz normal per Weboberfläche darauf zugreifen. 571D051B-0543-4A3D-B825-981884694F8B.jpeg

          1 Antwort Letzte Antwort
          0
          • K Offline
            K Offline
            klassisch
            Most Active
            schrieb am zuletzt editiert von klassisch
            #6

            Die Adressen sind KEINE Alias Adresssen
            Mit Alias würden die beim SM120 so aussehen
            203267e3-435b-41b2-920b-0e6aa95e75f2-grafik.png
            Beim SDM630 so:
            6ae166c8-cb68-4607-9b5e-bc57378f2553-grafik.png

            S 1 Antwort Letzte Antwort
            0
            • K klassisch

              Die Adressen sind KEINE Alias Adresssen
              Mit Alias würden die beim SM120 so aussehen
              203267e3-435b-41b2-920b-0e6aa95e75f2-grafik.png
              Beim SDM630 so:
              6ae166c8-cb68-4607-9b5e-bc57378f2553-grafik.png

              S Offline
              S Offline
              stromen
              schrieb am zuletzt editiert von
              #7

              @klassisch

              Da hat sich wahrscheinlich beim herumprobieren etwas verstellt.

              Selbst wenn ich einen neuen Adapter anlege, mit Alias bekomme ich den timeout.

              K 1 Antwort Letzte Antwort
              0
              • S stromen

                @klassisch

                Da hat sich wahrscheinlich beim herumprobieren etwas verstellt.

                Selbst wenn ich einen neuen Adapter anlege, mit Alias bekomme ich den timeout.

                K Offline
                K Offline
                klassisch
                Most Active
                schrieb am zuletzt editiert von
                #8

                @stromen Laut log ist die Verbindung via Wavesahre i.O.
                Im Notfall neu aufbauen. HW-Verbindungen prüfen. Erst mal nur ein einzelnes Register bedaten.

                1 Antwort Letzte Antwort
                0
                • S stromen

                  @wendy2702

                  Hallo,

                  danke für die Antwort. Sorry, reiche ich hiermit nach.

                  Ja, meines wissens war der Haken schon immer gesetzt.
                  Habe aber auch inzwischen mehrere Konfigurationen durchprobiert. Es lief ja seit knapp 2 Monaten einwandfrei, und es wurde nichts geändert.

                  E5387A4D-8ABD-4970-A20C-057EB282EE98.jpeg

                  
                  2023-04-10 12:08:17.052 - error: modbus.0 (759) Reconnect did not help, restart adapter
                  2023-04-10 12:08:17.053 - info: modbus.0 (759) Terminated (START_IMMEDIATELY_AFTER_STOP): Without reason
                  2023-04-10 12:08:17.599 - info: host.iobroker instance system.adapter.modbus.0 terminated with code 156 (START_IMMEDIATELY_AFTER_STOP)
                  2023-04-10 12:08:17.599 - info: host.iobroker Restart adapter system.adapter.modbus.0 because enabled
                  2023-04-10 12:08:18.630 - info: host.iobroker instance system.adapter.modbus.0 started with pid 774
                  2023-04-10 12:08:19.755 - info: modbus.0 (774) starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.24
                  2023-04-10 12:08:20.052 - info: modbus.0 (774) Connected to slave 192.168.1.200
                  2023-04-10 12:08:25.059 - warn: modbus.0 (774) Error: undefined
                  2023-04-10 12:08:25.060 - error: modbus.0 (774) Request timed out.
                  2023-04-10 12:08:25.060 - error: modbus.0 (774) Client in error state.
                  2023-04-10 12:08:25.061 - warn: modbus.0 (774) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                  2023-04-10 12:08:26.062 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
                  2023-04-10 12:09:26.064 - info: modbus.0 (774) Connected to slave 192.168.1.200
                  2023-04-10 12:09:31.066 - warn: modbus.0 (774) Error: undefined
                  2023-04-10 12:09:31.067 - error: modbus.0 (774) Request timed out.
                  2023-04-10 12:09:31.067 - error: modbus.0 (774) Client in error state.
                  2023-04-10 12:09:31.068 - warn: modbus.0 (774) Poll error count: 2 code: {"err":"timeout","timeout":5000}
                  2023-04-10 12:09:32.068 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
                  2023-04-10 12:10:32.070 - info: modbus.0 (774) Connected to slave 192.168.1.200
                  2023-04-10 12:10:37.072 - warn: modbus.0 (774) Error: undefined
                  2023-04-10 12:10:37.072 - error: modbus.0 (774) Request timed out.
                  2023-04-10 12:10:37.072 - error: modbus.0 (774) Client in error state.
                  2023-04-10 12:10:37.073 - warn: modbus.0 (774) Poll error count: 3 code: {"err":"timeout","timeout":5000}
                  2023-04-10 12:10:38.072 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
                  2023-04-10 12:11:38.076 - info: modbus.0 (774) Connected to slave 192.168.1.200
                  2023-04-10 12:11:43.078 - warn: modbus.0 (774) Error: undefined
                  2023-04-10 12:11:43.078 - error: modbus.0 (774) Request timed out.
                  2023-04-10 12:11:43.078 - error: modbus.0 (774) Client in error state.
                  2023-04-10 12:11:43.079 - warn: modbus.0 (774) Poll error count: 4 code: {"err":"timeout","timeout":5000}
                  2023-04-10 12:11:44.079 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
                  2023-04-10 12:12:44.081 - info: modbus.0 (774) Connected to slave 192.168.1.200
                  2023-04-10 12:12:49.083 - warn: modbus.0 (774) Error: undefined
                  2023-04-10 12:12:49.084 - error: modbus.0 (774) Request timed out.
                  2023-04-10 12:12:49.084 - error: modbus.0 (774) Client in error state.
                  2023-04-10 12:12:49.084 - warn: modbus.0 (774) Poll error count: 5 code: {"err":"timeout","timeout":5000}
                  2023-04-10 12:12:50.085 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
                  2023-04-10 12:13:50.087 - info: modbus.0 (774) Connected to slave 192.168.1.200
                  2023-04-10 12:13:55.089 - warn: modbus.0 (774) Error: undefined
                  2023-04-10 12:13:55.089 - error: modbus.0 (774) Request timed out.
                  2023-04-10 12:13:55.090 - error: modbus.0 (774) Client in error state.
                  2023-04-10 12:13:55.090 - warn: modbus.0 (774) Poll error count: 6 code: {"err":"timeout","timeout":5000}
                  2023-04-10 12:13:56.092 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
                  2023-04-10 12:14:56.096 - info: modbus.0 (774) Connected to slave 192.168.1.200
                  2023-04-10 12:15:01.098 - warn: modbus.0 (774) Error: undefined
                  2023-04-10 12:15:01.099 - error: modbus.0 (774) Request timed out.
                  2023-04-10 12:15:01.099 - error: modbus.0 (774) Client in error state.
                  2023-04-10 12:15:01.100 - warn: modbus.0 (774) Poll error count: 7 code: {"err":"timeout","timeout":5000}
                  2023-04-10 12:15:02.100 - info: modbus.0 (774) Disconnected from slave 192.168.1.200
                  
                  
                  GlasfaserG Online
                  GlasfaserG Online
                  Glasfaser
                  schrieb am zuletzt editiert von Glasfaser
                  #9

                  @stromen sagte in Modbus Problem Waveshare und SDM72D:

                  und es wurde nichts geändert.

                  Deine Register sehen komisch aus ... 12 / 14 / 16 ...

                  sind eigentlich so wie @klassisch im Screenshot zeigt .

                  siehe auch dazu hier :

                  https://forum.iobroker.net/post/927264

                  Erstelle eine neue Instanz und trage alles neu ein !
                  Aber erstmal nur eine Registerabfrage ...

                  EDIT :

                  habe auch ein Waveshare mit einem SDM230V2

                  7590a425-b314-490e-999c-ba679d4a79fa-grafik.png
                  d0834e68-5178-4f4b-9528-6d2990d92c75-grafik.png

                  Synology 918+ 16GB - ioBroker in Docker v9 , VISO auf Trekstor Primebook C13 13,3" , Hikvision Domkameras mit Surveillance Station .. CCU RaspberryMatic in Synology VM .. Zigbee CC2538+CC2592 .. Sonoff .. KNX .. Modbus ..

                  1 Antwort Letzte Antwort
                  0
                  • S stromen

                    Hallo,

                    ich habe ein Problem mit dem Modbus.
                    Ich verwende ein waveshare RS485 to ETH mit einem SDM72D

                    Seit langem hat alles einwandfrei funktioniert, auf einmal nicht mehr.
                    Verändert wurde nichts.
                    Neustart durchgeführt, Kabel usw. überprüft.

                    Hat jemand einen Tipp?

                    47AE7ECB-B3A8-4E10-94DB-B1083A954CDC.jpeg

                    8757EB9C-509D-4DC9-A180-37080060250D.jpeg

                    8E0267C6-BA26-4D38-9E1E-216A435E5233.jpeg

                    C488265A-C4E8-4F24-9FA5-0FB0325E6723.jpeg

                    S Online
                    S Online
                    SmartHomer 0
                    schrieb am zuletzt editiert von
                    #10

                    @stromen
                    So ein Verhalten hatte ich bislang 1x bei einem meiner beiden SDM72 via USR-W610. Sämtliche Versuche mit Änderungen am Modbus-Adapter, am USR oder am ioBroker haben nichts gebracht. Letztlich habe ich den SDM72 an allen Phasen spannungsfrei geschaltet, damit er ausging (Display dunkel). Einige Sekunden gewartet, danach wieder eingeschaltet-und sofort hat wieder alles funktioniert. Irgendwie muss sich die Modbus-Schnittstelle des DSM72 „aufgehängt“ haben. Seitdem läuft wieder alles prima.

                    S 1 Antwort Letzte Antwort
                    1
                    • S SmartHomer 0

                      @stromen
                      So ein Verhalten hatte ich bislang 1x bei einem meiner beiden SDM72 via USR-W610. Sämtliche Versuche mit Änderungen am Modbus-Adapter, am USR oder am ioBroker haben nichts gebracht. Letztlich habe ich den SDM72 an allen Phasen spannungsfrei geschaltet, damit er ausging (Display dunkel). Einige Sekunden gewartet, danach wieder eingeschaltet-und sofort hat wieder alles funktioniert. Irgendwie muss sich die Modbus-Schnittstelle des DSM72 „aufgehängt“ haben. Seitdem läuft wieder alles prima.

                      S Offline
                      S Offline
                      stromen
                      schrieb am zuletzt editiert von
                      #11

                      @smarthomer-0

                      DANKE! Genau DAS war der Fehler. Habe am Abend nochmal ein iobroker Backup eingespielt um sicher zu sein das nicht irgendwas verstellt ist. Heute morgen habe ich den SDM72 vom Stom getrennt und sofort nach dem einschalten lieferte er Daten.

                      1 Antwort Letzte Antwort
                      2
                      • K Offline
                        K Offline
                        klassisch
                        Most Active
                        schrieb am zuletzt editiert von
                        #12

                        Frage: Hattet Ihr den dritten Anschluß "GND", "Earth" zwischen Zähler und dem Konverter verbunden?

                        S 1 Antwort Letzte Antwort
                        0
                        • K klassisch

                          Frage: Hattet Ihr den dritten Anschluß "GND", "Earth" zwischen Zähler und dem Konverter verbunden?

                          S Online
                          S Online
                          SmartHomer 0
                          schrieb am zuletzt editiert von
                          #13

                          @klassisch
                          Danke für Dein Interesse/Deine Nachfrage.
                          In meinem Fall:

                          A/B paarig verseiltes Aderpaar verwendet.
                          Schirm der Bus-Leitung einseitig aufgelegt auf dem G(ND)-Anschluss am SDM72.
                          Schirm nicht beidseitig aufgelegt
                          a) um keine "Brummschleifen" aufzubauen
                          b) weil der USR am RS485-Stecker keinen GND-Anschluss hat
                          Zur Potenzialtrennung der Schnittstelle etc lässt sich leider die Doku weder beim USR-W610
                          noch beim SDM72 aus.

                          Ich hatte mir überlegt, Abschluss-Widerstände einzubauen, falls das Problem nochmal auftritt
                          (was bislang nicht der Fall war, es funktioniert seit mehreren Wochen stabil).
                          Sollte mE aber eigentlich nicht erforderlich sein, weil die ModBus-Leitung nur ca. 1m lang ist,
                          keine weiteren Teilnehmer angeschlossen sind und ich auch nur mit 9.6kBaud fahre.

                          K 1 Antwort Letzte Antwort
                          1
                          • S SmartHomer 0

                            @klassisch
                            Danke für Dein Interesse/Deine Nachfrage.
                            In meinem Fall:

                            A/B paarig verseiltes Aderpaar verwendet.
                            Schirm der Bus-Leitung einseitig aufgelegt auf dem G(ND)-Anschluss am SDM72.
                            Schirm nicht beidseitig aufgelegt
                            a) um keine "Brummschleifen" aufzubauen
                            b) weil der USR am RS485-Stecker keinen GND-Anschluss hat
                            Zur Potenzialtrennung der Schnittstelle etc lässt sich leider die Doku weder beim USR-W610
                            noch beim SDM72 aus.

                            Ich hatte mir überlegt, Abschluss-Widerstände einzubauen, falls das Problem nochmal auftritt
                            (was bislang nicht der Fall war, es funktioniert seit mehreren Wochen stabil).
                            Sollte mE aber eigentlich nicht erforderlich sein, weil die ModBus-Leitung nur ca. 1m lang ist,
                            keine weiteren Teilnehmer angeschlossen sind und ich auch nur mit 9.6kBaud fahre.

                            K Offline
                            K Offline
                            klassisch
                            Most Active
                            schrieb am zuletzt editiert von
                            #14

                            @smarthomer-0 Bei 1m und 9600 Bd sehe ich keine Notwendigkeit für Absclußwiderstände.
                            Ich verbinde normaleweise die GND Leitungen auch nicht. Solange alles läuft. Sobald es aber Schwierigkeiten gäbe würde ich mit 1kOhm Widerstand starten und dann die Spannung messen. Könnte sein, daß sich statische Potentialdifferenzen aufgebaut haben und den RS485 Treiber jenseits der common mode Grenzen getrieben haben.
                            Der SDM72 und der USRiot haben keine Potentialtrennung.
                            Vielleicht hat der SDM72 eine SW Bug?
                            Abwarten. @Homoran hat einige von denen in Betrieb und nutzt eine Anbindung mit Potentialtrennung. Wir werden ja hören, wenn sich da was aufhängen sollte.

                            HomoranH S 2 Antworten Letzte Antwort
                            1
                            • K klassisch

                              @smarthomer-0 Bei 1m und 9600 Bd sehe ich keine Notwendigkeit für Absclußwiderstände.
                              Ich verbinde normaleweise die GND Leitungen auch nicht. Solange alles läuft. Sobald es aber Schwierigkeiten gäbe würde ich mit 1kOhm Widerstand starten und dann die Spannung messen. Könnte sein, daß sich statische Potentialdifferenzen aufgebaut haben und den RS485 Treiber jenseits der common mode Grenzen getrieben haben.
                              Der SDM72 und der USRiot haben keine Potentialtrennung.
                              Vielleicht hat der SDM72 eine SW Bug?
                              Abwarten. @Homoran hat einige von denen in Betrieb und nutzt eine Anbindung mit Potentialtrennung. Wir werden ja hören, wenn sich da was aufhängen sollte.

                              HomoranH Nicht stören
                              HomoranH Nicht stören
                              Homoran
                              Global Moderator Administrators
                              schrieb am zuletzt editiert von Homoran
                              #15

                              @klassisch sagte in Modbus Problem Waveshare und SDM72D:

                              Vielleicht hat der SDM72 eine SW Bug?
                              Abwarten. @Homoran hat einige von denen in Betrieb

                              dann habe ich eine andere Version, weil

                              @smarthomer-0 sagte in Modbus Problem Waveshare und SDM72D:

                              Letztlich habe ich den SDM72 an allen Phasen spannungsfrei geschaltet, damit er ausging (Display dunkel)

                              meine schalten ihr Display nach kurzer Zeit immer auf Dunkel.

                              kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                              der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                              S 1 Antwort Letzte Antwort
                              1
                              • HomoranH Homoran

                                @klassisch sagte in Modbus Problem Waveshare und SDM72D:

                                Vielleicht hat der SDM72 eine SW Bug?
                                Abwarten. @Homoran hat einige von denen in Betrieb

                                dann habe ich eine andere Version, weil

                                @smarthomer-0 sagte in Modbus Problem Waveshare und SDM72D:

                                Letztlich habe ich den SDM72 an allen Phasen spannungsfrei geschaltet, damit er ausging (Display dunkel)

                                meine schalten ihr Display nach kurzer Zeit immer auf Dunkel.

                                S Online
                                S Online
                                SmartHomer 0
                                schrieb am zuletzt editiert von SmartHomer 0
                                #16

                                @homoran
                                Danke, das muss ich dann noch präzisieren:
                                Die Zeit bis zum funktionalen "Dunkeltasten" des Display kann im Setup vom SDM eingestellt werden:
                                ea288674-3f3d-43b2-bfad-bc57bf160680-grafik.png
                                Was ich mit dem "dunklen Display" meinte ist, dass der SDM wirklich allphasig "spannungsfrei" ist und quasi einen Neustart (mitsamt ModBus) macht.
                                Ich suche gelegentlich mal meine SW-Version raus, wenn ich wieder am Zähler bin

                                1 Antwort Letzte Antwort
                                0
                                • K klassisch

                                  @smarthomer-0 Bei 1m und 9600 Bd sehe ich keine Notwendigkeit für Absclußwiderstände.
                                  Ich verbinde normaleweise die GND Leitungen auch nicht. Solange alles läuft. Sobald es aber Schwierigkeiten gäbe würde ich mit 1kOhm Widerstand starten und dann die Spannung messen. Könnte sein, daß sich statische Potentialdifferenzen aufgebaut haben und den RS485 Treiber jenseits der common mode Grenzen getrieben haben.
                                  Der SDM72 und der USRiot haben keine Potentialtrennung.
                                  Vielleicht hat der SDM72 eine SW Bug?
                                  Abwarten. @Homoran hat einige von denen in Betrieb und nutzt eine Anbindung mit Potentialtrennung. Wir werden ja hören, wenn sich da was aufhängen sollte.

                                  S Online
                                  S Online
                                  SmartHomer 0
                                  schrieb am zuletzt editiert von SmartHomer 0
                                  #17

                                  @klassisch @Homoran

                                  @smarthomer-0 sagte in Modbus Problem Waveshare und SDM72D:

                                  Ich suche gelegentlich mal meine SW-Version raus, wenn ich wieder am Zähler bin

                                  Ich habe nachgesehen:
                                  Die SW-Version meines SDM72DM-V2 MID ist 03 01.03

                                  9e966501-d6e7-4e50-a011-74a06db5d8d0-grafik.png

                                  1 Antwort Letzte Antwort
                                  1
                                  • M Offline
                                    M Offline
                                    Matis
                                    schrieb am zuletzt editiert von
                                    #18

                                    Könnte jemand so freundlich sein und die txt files für die Registerconfig des SDM72D-M hier einstellen, dass man nicht alles abtippen muß? Das wäre sehr nett!
                                    Ich hab schon danach gesucht, aber nichts gefunden.
                                    Vielen Dank!

                                    1 Antwort Letzte Antwort
                                    0
                                    Antworten
                                    • In einem neuen Thema antworten
                                    Anmelden zum Antworten
                                    • Älteste zuerst
                                    • Neuste zuerst
                                    • Meiste Stimmen


                                    Support us

                                    ioBroker
                                    Community Adapters
                                    Donate

                                    712

                                    Online

                                    32.4k

                                    Benutzer

                                    81.4k

                                    Themen

                                    1.3m

                                    Beiträge
                                    Community
                                    Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                    ioBroker Community 2014-2025
                                    logo
                                    • Anmelden

                                    • Du hast noch kein Konto? Registrieren

                                    • Anmelden oder registrieren, um zu suchen
                                    • Erster Beitrag
                                      Letzter Beitrag
                                    0
                                    • Aktuell
                                    • Tags
                                    • Ungelesen 0
                                    • Kategorien
                                    • Unreplied
                                    • Beliebt
                                    • GitHub
                                    • Docu
                                    • Hilfe