  4. Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.3k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.0k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.4k

Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
canbuscanbus adapterrotex hpsu
522 Beiträge 25 Kommentatoren 104.3k Aufrufe 20 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • crycodeC crycode

    @cb187 sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

    ich glaub die Dis haben sich alle ein wenig verschoben. 10A taucht zb auch in 180 auf usw

    Sehr merkwürdig. Kann ich mir kaum vorstellen, dass das von alleine passiert sein soll. Zumal das dann ja auch von der originalen Steuerung erkannt werden muss.
    Hat irgendwer sonst schonmal ähnliche Erfahrungen gemacht?

    @cb187 sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

    Haste irgendwann mal zeit das zu testen?

    Was genau soll ich testen? Zeitlich sieht es bei mir momentan auch eher knapp aus, sorry...

    C Offline
    C Offline
    cb187
    schrieb am zuletzt editiert von
    #199

    @crycode mir mal so nen datenpunkt fertig machen ich oben gepostet habe.Über 300 kommt nichts mehr an meldungen rein.

    C 1 Antwort Letzte Antwort
    0
    • C cb187

      @crycode mir mal so nen datenpunkt fertig machen ich oben gepostet habe.Über 300 kommt nichts mehr an meldungen rein.

      C Offline
      C Offline
      cb187
      schrieb am zuletzt editiert von
      #200

      @crycode Bildschirm­foto 2022-11-27 um 21.16.30.png

      Die werte habe ich jetzt einfach mal nach 301 eingefügt und da kommen jetzt die werte von 300 an.Aber Abfrage hab ich irgendwie noch nicht hinbekommen.Da stürzt die WP immer ab.Und setzen auch noch nicht

      1 Antwort Letzte Antwort
      0
      • hg6806H Offline
        hg6806H Offline
        hg6806
        Most Active
        schrieb am zuletzt editiert von hg6806
        #201

        @cb187
        Ich beschäftige mich auch mal wieder mit der Abtauproblematik der Rotex.
        Das Wetter ist halt leider prädestiniert für Abtauvorgänge. Zum Glück bei mir nur alle 1,5 - 2h.

        Dein Programm schaltet bei dir bei einem Abtauvorgang immer direkt auf Standby:

        fabe6e56-a00d-4508-af47-d53cf9eeea46-image.png

        Ist bei dir der CAN Befehl 680.fa0112-set auch wie folgt:
        d252f58a-cc97-4637-b0c6-67eee5b122d4-image.png

        Demnach schaltet das Gerät bei einem Abtauvorgang direkt auf Sommer-Betrieb (5) und Die Betriebsart dann auf Standby:

        ba9a62ef-6d5e-42b9-8dc2-a6f42cacc48b-image.png

        Abtauen 17:59 schaltet Modus auf Sommer, Betriebsart geht dann 18:00 auf Standby.

        Und wenn er auf Standby ist, kommt er da nie mehr raus:

        a69c73ce-b166-44fe-87cc-aaa20ad5f859-image.png

        Wie ist der Ablauf bei dir?

        C 1 Antwort Letzte Antwort
        0
        • C Offline
          C Offline
          cb187
          schrieb am zuletzt editiert von
          #202

          @hg6806 kann ich dir schicken mein script.Nutze es und läuft perfekt

          1 Antwort Letzte Antwort
          0
          • hg6806H hg6806

            @cb187
            Ich beschäftige mich auch mal wieder mit der Abtauproblematik der Rotex.
            Das Wetter ist halt leider prädestiniert für Abtauvorgänge. Zum Glück bei mir nur alle 1,5 - 2h.

            Dein Programm schaltet bei dir bei einem Abtauvorgang immer direkt auf Standby:

            fabe6e56-a00d-4508-af47-d53cf9eeea46-image.png

            Ist bei dir der CAN Befehl 680.fa0112-set auch wie folgt:
            d252f58a-cc97-4637-b0c6-67eee5b122d4-image.png

            Demnach schaltet das Gerät bei einem Abtauvorgang direkt auf Sommer-Betrieb (5) und Die Betriebsart dann auf Standby:

            ba9a62ef-6d5e-42b9-8dc2-a6f42cacc48b-image.png

            Abtauen 17:59 schaltet Modus auf Sommer, Betriebsart geht dann 18:00 auf Standby.

            Und wenn er auf Standby ist, kommt er da nie mehr raus:

            a69c73ce-b166-44fe-87cc-aaa20ad5f859-image.png

            Wie ist der Ablauf bei dir?

            C Offline
            C Offline
            cb187
            schrieb am zuletzt editiert von
            #203

            @hg6806

            Bildschirm­foto 2022-12-04 um 09.06.37.png

            Also eigentlich das selbe.Wenn abtauen erkannt schaltet solange in den Sommermodus bis sich abtauen ändert.
            Läuft bei mir so perfekt.

            hg6806H 1 Antwort Letzte Antwort
            0
            • C cb187

              @hg6806

              Bildschirm­foto 2022-12-04 um 09.06.37.png

              Also eigentlich das selbe.Wenn abtauen erkannt schaltet solange in den Sommermodus bis sich abtauen ändert.
              Läuft bei mir so perfekt.

              hg6806H Offline
              hg6806H Offline
              hg6806
              Most Active
              schrieb am zuletzt editiert von hg6806
              #204

              @cb187

              Geht bei mir nicht.
              Wie geschrieben, schaltet der Modus auf Sommer und die Betriebsart geht direkt auf Standby.

              Lt. FHEM muss noch "T Frostschutz" auf "Aus" gestellt werden.
              Ist bei mir lt. Heizung auch auf aus. Beim Wert T Frostschutz in ioBroker/CAN steht bei Wert 300.fa0a00 aber "-16" drin. Eigentlich geht der Wert nicht tiefer als -15.

              b1420ec8-4632-45b9-b314-ad8681be3c29-image.png

              Kannst du mal schauen wie der bei dir steht?

              C crycodeC 2 Antworten Letzte Antwort
              0
              • hg6806H hg6806

                @cb187

                Geht bei mir nicht.
                Wie geschrieben, schaltet der Modus auf Sommer und die Betriebsart geht direkt auf Standby.

                Lt. FHEM muss noch "T Frostschutz" auf "Aus" gestellt werden.
                Ist bei mir lt. Heizung auch auf aus. Beim Wert T Frostschutz in ioBroker/CAN steht bei Wert 300.fa0a00 aber "-16" drin. Eigentlich geht der Wert nicht tiefer als -15.

                b1420ec8-4632-45b9-b314-ad8681be3c29-image.png

                Kannst du mal schauen wie der bei dir steht?

                C Offline
                C Offline
                cb187
                schrieb am zuletzt editiert von cb187
                #205

                @hg6806 said in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                @cb187

                Geht bei mir nicht.
                Wie geschrieben, schaltet der Modus auf Sommer und die Betriebsart geht direkt auf Standby.

                Lt. FHEM muss noch "T Frostschutz" auf "Aus" gestellt werden.
                Ist bei mir lt. Heizung auch auf aus. Beim Wert T Frostschutz in ioBroker/CAN steht bei Wert 300.fa0a00 aber "-16" drin. Eigentlich geht der Wert nicht tiefer als -15.

                b1420ec8-4632-45b9-b314-ad8681be3c29-image.png

                Kannst du mal schauen wie der bei dir steht?

                Ich hab bei mir Frostschutz aus.can Abfrage ist auch -16.
                Ich frag mich warum deine in standby geht nach dem abtauen.

                1 Antwort Letzte Antwort
                0
                • hg6806H Offline
                  hg6806H Offline
                  hg6806
                  Most Active
                  schrieb am zuletzt editiert von hg6806
                  #206

                  Hmm, also wie bei dir. Seltsam.
                  Das AntiContinousHeating beim FHEM Modul hatte aber funktioniert.

                  Das Gerät taut erst gar nicht ab.
                  Wenn der Modus auf Sommer geschaltet wird, schaltet die Betriebsart direkt auf Standby.

                  Zum Glück haben wir über 4°C da habe ich gar kein Abtauen mehr.

                  Hier zur Info meine Abtauvorgänge der letzten 2 Tage:
                  c6effee3-f6b6-484f-bb8d-475e7aecb1b9-image.png

                  Ich habe zum Glück zwar keine 25Min. Zyklen, jedoch tuen die Verluste beim WW echt weh.

                  C 1 Antwort Letzte Antwort
                  0
                  • hg6806H hg6806

                    Hmm, also wie bei dir. Seltsam.
                    Das AntiContinousHeating beim FHEM Modul hatte aber funktioniert.

                    Das Gerät taut erst gar nicht ab.
                    Wenn der Modus auf Sommer geschaltet wird, schaltet die Betriebsart direkt auf Standby.

                    Zum Glück haben wir über 4°C da habe ich gar kein Abtauen mehr.

                    Hier zur Info meine Abtauvorgänge der letzten 2 Tage:
                    c6effee3-f6b6-484f-bb8d-475e7aecb1b9-image.png

                    Ich habe zum Glück zwar keine 25Min. Zyklen, jedoch tuen die Verluste beim WW echt weh.

                    C Offline
                    C Offline
                    cb187
                    schrieb am zuletzt editiert von
                    #207

                    @hg6806

                    Wir haben gerade um die 0 Grad und schnee matsch wetter.Habs jetzt aber erstmal weg bekommen mit den 25min zyklen.Aber schön nach dazu max 0,5 grad ww verlust ist schon cool.Welche Rotex hast du denn?
                    Ich hab die compact 8kw

                    hg6806H 1 Antwort Letzte Antwort
                    0
                    • C cb187

                      @hg6806

                      Wir haben gerade um die 0 Grad und schnee matsch wetter.Habs jetzt aber erstmal weg bekommen mit den 25min zyklen.Aber schön nach dazu max 0,5 grad ww verlust ist schon cool.Welche Rotex hast du denn?
                      Ich hab die compact 8kw

                      hg6806H Offline
                      hg6806H Offline
                      hg6806
                      Most Active
                      schrieb am zuletzt editiert von
                      #208

                      @cb187
                      Jepp, die habe ich auch. HPSU 508 compact BJ 2013/2014

                      C 1 Antwort Letzte Antwort
                      0
                      • hg6806H hg6806

                        @cb187
                        Jepp, die habe ich auch. HPSU 508 compact BJ 2013/2014

                        C Offline
                        C Offline
                        cb187
                        schrieb am zuletzt editiert von
                        #209

                        @hg6806 ah ok ichbhab die von 2016.Kann sein das dein Software stand nen anderer ist.Hab die version 5.Also kann gut sein das es da nen unterschied gibt.

                        1 Antwort Letzte Antwort
                        0
                        • Elektroniker86E Offline
                          Elektroniker86E Offline
                          Elektroniker86
                          schrieb am zuletzt editiert von
                          #210

                          Moin,

                          ich habe bemerkt , dass bei mir der Datenpunkt "T Absenkung SETZEN" fehlt. Oder ich habe ihn nicht gefunden.
                          Die Temperatur ABFRAGEN und IST Temperatur ist vorhanden.
                          Gibt es eine Möglichkeit diesen noch hinzuzufügen?

                          Vielen Dank im voraus!

                          Screenshot_20221207_132212.png

                          crycodeC 1 Antwort Letzte Antwort
                          0
                          • hg6806H Offline
                            hg6806H Offline
                            hg6806
                            Most Active
                            schrieb am zuletzt editiert von hg6806
                            #211

                            Und bei mir funktionieren die beiden Befehle
                            canbus.0.680.fa067e-set (Max Leistung Pumpe setzen)
                            und
                            canbus.0.680.fa067f-set (Min Leistung Pumpe setzen)
                            nicht. Wenn ich dort einen Wert eintrage und auch auf bestätigt setze, bleiben bei der Abfrage die Werte auf dem alten Stand.
                            Wenn ich es direkt an dem Gerät setze funktioniert es.

                            Hintergrund für die Verstellung ist, ich möchte die Pumpe im Standby Betrieb, bzw. wenn alle Stellglieder geschlossen sind, auf niedrige % setzen.
                            Warum auch immer läuft die dann auf dem max. Wert.

                            Zur Info. Wenn man den max. Wert von 95% auf 65% reduziert, spart man direkt 30-40W.

                            C crycodeC 2 Antworten Letzte Antwort
                            0
                            • hg6806H hg6806

                              Und bei mir funktionieren die beiden Befehle
                              canbus.0.680.fa067e-set (Max Leistung Pumpe setzen)
                              und
                              canbus.0.680.fa067f-set (Min Leistung Pumpe setzen)
                              nicht. Wenn ich dort einen Wert eintrage und auch auf bestätigt setze, bleiben bei der Abfrage die Werte auf dem alten Stand.
                              Wenn ich es direkt an dem Gerät setze funktioniert es.

                              Hintergrund für die Verstellung ist, ich möchte die Pumpe im Standby Betrieb, bzw. wenn alle Stellglieder geschlossen sind, auf niedrige % setzen.
                              Warum auch immer läuft die dann auf dem max. Wert.

                              Zur Info. Wenn man den max. Wert von 95% auf 65% reduziert, spart man direkt 30-40W.

                              C Offline
                              C Offline
                              cb187
                              schrieb am zuletzt editiert von
                              #212

                              @hg6806 jo bei mir läuft die immer sturr auf 60% min und max.Bei FBH wie ich immer wieder lese soll die Pumpe eh nicht modulieren.

                              hg6806H 1 Antwort Letzte Antwort
                              0
                              • C cb187

                                @hg6806 jo bei mir läuft die immer sturr auf 60% min und max.Bei FBH wie ich immer wieder lese soll die Pumpe eh nicht modulieren.

                                hg6806H Offline
                                hg6806H Offline
                                hg6806
                                Most Active
                                schrieb am zuletzt editiert von
                                #213

                                @cb187
                                Hmmm, gefühlt wäre doch eine höher Pumpenleistung besser bei etwas geringerer Vorlauftemperatur um die gleiche Heizleistung einer FBH zu bekommen.

                                C 1 Antwort Letzte Antwort
                                0
                                • hg6806H hg6806

                                  @cb187
                                  Hmmm, gefühlt wäre doch eine höher Pumpenleistung besser bei etwas geringerer Vorlauftemperatur um die gleiche Heizleistung einer FBH zu bekommen.

                                  C Offline
                                  C Offline
                                  cb187
                                  schrieb am zuletzt editiert von
                                  #214

                                  @hg6806 wenn alle Heizkreise auf sind dann geht bei 60% bei mir schon mindestens 920ltr die std durch.Ich benutze aber Straka Ego die den hydraulischen abgleich selber machen und da kann es auch weniger sein.Regelt sich alles von selbst.

                                  1 Antwort Letzte Antwort
                                  0
                                  • Elektroniker86E Offline
                                    Elektroniker86E Offline
                                    Elektroniker86
                                    schrieb am zuletzt editiert von Elektroniker86
                                    #215

                                    Moin,

                                    ich habe nach einem Neustart des Adapters ein Paar Warnungen und Fehler:

                                    
                                    
                                    canbus.0
                                    2022-12-13 18:03:21.740	info	starting. Version 1.3.1 in /opt/iobroker/node_modules/iobroker.canbus, node: v16.18.1, js-controller: 4.0.23
                                    host.iobroker-slave-wp
                                    2022-12-13 18:03:18.105	info	instance system.adapter.canbus.0 started with pid 8433
                                    host.iobroker-slave-wp
                                    2022-12-13 18:03:16.472	info	instance system.adapter.canbus.0 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.762	warn	Could not perform strict object check of state canbus.0.680.json: DB closed
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.756	warn	Failed parsing JSON from canbus.0.680.json: No state found
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.747	error	DB closed
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.746	error	Error: DB closed at Redis.sendCommand (/opt/iobroker/node_modules/ioredis/built/redis/index.js:636:24) at Redis.get (/opt/iobroker/node_modules/ioredis/built/commander.js:122:25) at StateRedisClient.setState (/opt/iobroker/node_modules/@iobroker/db-states-redis/lib/states/statesInRedisClient.js:657:40) at CanBusAdapter.setState (/opt/iobroker/node_modules/@iobroker/js-controller-adapter/src/lib/adapter/adapter.js:6485:35)
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.744	error	unhandled promise rejection: DB closed
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.744	error	Unhandled promise rejection. This error originated either by throwing inside of an async function without a catch block, or by rejecting a promise which was not handled with .catch().
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.743	warn	redis get canbus.0.680.json, error - Connection is closed.
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.740	warn	get state error: Connection is closed.
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.739	warn	Could not perform strict object check of state canbus.0.680.json: DB closed
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.725	warn	Failed parsing JSON from canbus.0.680.json: No state found
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.688	error	DB closed
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.688	error	Error: DB closed at Redis.sendCommand (/opt/iobroker/node_modules/ioredis/built/redis/index.js:636:24) at Redis.get (/opt/iobroker/node_modules/ioredis/built/commander.js:122:25) at StateRedisClient.setState (/opt/iobroker/node_modules/@iobroker/db-states-redis/lib/states/statesInRedisClient.js:657:40) at CanBusAdapter.setState (/opt/iobroker/node_modules/@iobroker/js-controller-adapter/src/lib/adapter/adapter.js:6485:35)
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.020	error	unhandled promise rejection: DB closed
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.019	error	Unhandled promise rejection. This error originated either by throwing inside of an async function without a catch block, or by rejecting a promise which was not handled with .catch().
                                    host.iobroker-slave-wp
                                    2022-12-13 18:03:15.391	info	stopInstance system.adapter.canbus.0 killing pid 647
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.015	warn	redis get canbus.0.680.json, error - Connection is closed.
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.013	warn	get state error: Connection is closed.
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.007	warn	Failed parsing JSON from canbus.0.680.json: No state found
                                    
                                    canbus.0
                                    2022-12-13 18:03:15.002	warn	redis get canbus.0.680.json, error - Connection is closed.
                                    
                                    canbus.0
                                    2022-12-13 18:03:14.488	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                    host.iobroker-slave-wp
                                    2022-12-13 18:03:14.387	info	stopInstance system.adapter.canbus.0 send kill signal
                                    
                                    canbus.0
                                    2022-12-13 18:03:14.486	info	terminating
                                    
                                    canbus.0
                                    2022-12-13 18:03:14.385	info	Got terminate signal TERMINATE_YOURSELF
                                    
                                    

                                    Läuft da irgendwas nicht richtig ?
                                    Hatte heute auch ein Ausfall der Heizung. (Fehlercode 81 Kommunikationsfehler)

                                    Kann das dadurch kommen?

                                    Vielen Dank im voraus!

                                    crycodeC 1 Antwort Letzte Antwort
                                    0
                                    • Elektroniker86E Elektroniker86

                                      Moin,

                                      ich habe nach einem Neustart des Adapters ein Paar Warnungen und Fehler:

                                      
                                      
                                      canbus.0
                                      2022-12-13 18:03:21.740	info	starting. Version 1.3.1 in /opt/iobroker/node_modules/iobroker.canbus, node: v16.18.1, js-controller: 4.0.23
                                      host.iobroker-slave-wp
                                      2022-12-13 18:03:18.105	info	instance system.adapter.canbus.0 started with pid 8433
                                      host.iobroker-slave-wp
                                      2022-12-13 18:03:16.472	info	instance system.adapter.canbus.0 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.762	warn	Could not perform strict object check of state canbus.0.680.json: DB closed
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.756	warn	Failed parsing JSON from canbus.0.680.json: No state found
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.747	error	DB closed
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.746	error	Error: DB closed at Redis.sendCommand (/opt/iobroker/node_modules/ioredis/built/redis/index.js:636:24) at Redis.get (/opt/iobroker/node_modules/ioredis/built/commander.js:122:25) at StateRedisClient.setState (/opt/iobroker/node_modules/@iobroker/db-states-redis/lib/states/statesInRedisClient.js:657:40) at CanBusAdapter.setState (/opt/iobroker/node_modules/@iobroker/js-controller-adapter/src/lib/adapter/adapter.js:6485:35)
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.744	error	unhandled promise rejection: DB closed
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.744	error	Unhandled promise rejection. This error originated either by throwing inside of an async function without a catch block, or by rejecting a promise which was not handled with .catch().
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.743	warn	redis get canbus.0.680.json, error - Connection is closed.
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.740	warn	get state error: Connection is closed.
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.739	warn	Could not perform strict object check of state canbus.0.680.json: DB closed
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.725	warn	Failed parsing JSON from canbus.0.680.json: No state found
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.688	error	DB closed
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.688	error	Error: DB closed at Redis.sendCommand (/opt/iobroker/node_modules/ioredis/built/redis/index.js:636:24) at Redis.get (/opt/iobroker/node_modules/ioredis/built/commander.js:122:25) at StateRedisClient.setState (/opt/iobroker/node_modules/@iobroker/db-states-redis/lib/states/statesInRedisClient.js:657:40) at CanBusAdapter.setState (/opt/iobroker/node_modules/@iobroker/js-controller-adapter/src/lib/adapter/adapter.js:6485:35)
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.020	error	unhandled promise rejection: DB closed
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.019	error	Unhandled promise rejection. This error originated either by throwing inside of an async function without a catch block, or by rejecting a promise which was not handled with .catch().
                                      host.iobroker-slave-wp
                                      2022-12-13 18:03:15.391	info	stopInstance system.adapter.canbus.0 killing pid 647
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.015	warn	redis get canbus.0.680.json, error - Connection is closed.
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.013	warn	get state error: Connection is closed.
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.007	warn	Failed parsing JSON from canbus.0.680.json: No state found
                                      
                                      canbus.0
                                      2022-12-13 18:03:15.002	warn	redis get canbus.0.680.json, error - Connection is closed.
                                      
                                      canbus.0
                                      2022-12-13 18:03:14.488	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                      host.iobroker-slave-wp
                                      2022-12-13 18:03:14.387	info	stopInstance system.adapter.canbus.0 send kill signal
                                      
                                      canbus.0
                                      2022-12-13 18:03:14.486	info	terminating
                                      
                                      canbus.0
                                      2022-12-13 18:03:14.385	info	Got terminate signal TERMINATE_YOURSELF
                                      
                                      

                                      Läuft da irgendwas nicht richtig ?
                                      Hatte heute auch ein Ausfall der Heizung. (Fehlercode 81 Kommunikationsfehler)

                                      Kann das dadurch kommen?

                                      Vielen Dank im voraus!

                                      crycodeC Offline
                                      crycodeC Offline
                                      crycode
                                      Developer
                                      schrieb am zuletzt editiert von
                                      #216

                                      @elektroniker86 Da hat irgendwas versucht den State canbus.0.680.json zu lesen, nachdem beim Stoppen des Adapters die Verbindung zur Datenbank getrennt wurde. Ist nicht weiter tragisch und sollte auch keine Probleme machen.

                                      Meine Adapter: discord | canbus | ds18b20 | odl | radiohead

                                      Elektroniker86E 1 Antwort Letzte Antwort
                                      1
                                      • Elektroniker86E Elektroniker86

                                        Moin,

                                        ich habe bemerkt , dass bei mir der Datenpunkt "T Absenkung SETZEN" fehlt. Oder ich habe ihn nicht gefunden.
                                        Die Temperatur ABFRAGEN und IST Temperatur ist vorhanden.
                                        Gibt es eine Möglichkeit diesen noch hinzuzufügen?

                                        Vielen Dank im voraus!

                                        Screenshot_20221207_132212.png

                                        crycodeC Offline
                                        crycodeC Offline
                                        crycode
                                        Developer
                                        schrieb am zuletzt editiert von
                                        #217

                                        @elektroniker86 sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                                        ich habe bemerkt , dass bei mir der Datenpunkt "T Absenkung SETZEN" fehlt.

                                        Ist jetzt in der latest-Config drin und kann von GitHub importiert werden. Bitte mal testen. :)

                                        Meine Adapter: discord | canbus | ds18b20 | odl | radiohead

                                        Elektroniker86E 1 Antwort Letzte Antwort
                                        1
                                        • hg6806H hg6806

                                          Und bei mir funktionieren die beiden Befehle
                                          canbus.0.680.fa067e-set (Max Leistung Pumpe setzen)
                                          und
                                          canbus.0.680.fa067f-set (Min Leistung Pumpe setzen)
                                          nicht. Wenn ich dort einen Wert eintrage und auch auf bestätigt setze, bleiben bei der Abfrage die Werte auf dem alten Stand.
                                          Wenn ich es direkt an dem Gerät setze funktioniert es.

                                          Hintergrund für die Verstellung ist, ich möchte die Pumpe im Standby Betrieb, bzw. wenn alle Stellglieder geschlossen sind, auf niedrige % setzen.
                                          Warum auch immer läuft die dann auf dem max. Wert.

                                          Zur Info. Wenn man den max. Wert von 95% auf 65% reduziert, spart man direkt 30-40W.

                                          crycodeC Offline
                                          crycodeC Offline
                                          crycode
                                          Developer
                                          schrieb am zuletzt editiert von
                                          #218

                                          @hg6806 sagte in Rotex HPSU / Daikin Altherma Wärmepumpe über ioBroker.canbus:

                                          Und bei mir funktionieren die beiden Befehle
                                          canbus.0.680.fa067e-set (Max Leistung Pumpe setzen)
                                          und
                                          canbus.0.680.fa067f-set (Min Leistung Pumpe setzen)
                                          nicht. Wenn ich dort einen Wert eintrage und auch auf bestätigt setze, bleiben bei der Abfrage die Werte auf dem alten Stand.
                                          Wenn ich es direkt an dem Gerät setze funktioniert es.

                                          Kannst du mal einen candump aufzeichnen und dabei die Werte am Gerät setzen?

                                          Meine Adapter: discord | canbus | ds18b20 | odl | radiohead

                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          712

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe